Board of Supervisors

The Board of Supervisors acts as the legislative branch of Township government. They are responsible for adopting and amending ordinances and establishing Township policy. They approve all subdivision and land development plans, as well as any other matter requiring official action of the Township.

 


  • Five members, serving six-year terms
  • Meetings begin at 7:00 PM on the 1st and 3rd Tuesday of the month.
  • Meetings will be held on the 2nd, 4th, and 5th Tuesday of the month as needed.
  • All township meetings are held at the Township Building and are open to the public.
  • View our meetings live via Zoom.
  • View township meetings on YouTube.
  • Executive Sessions are not public meetings

 

Board of Supervisors Term Expiration Date
 Cody Bright, Chair 2027
Barbara Emery, Vice Chair 2029
Peter Hicks 2029
Ann Duffield 2031
Larry Massaro 2031

Visit our YouTube Channel for meeting video recordings.

Resolutions

 

Documents

Notice: this accessible version was created automatically from the original document. The transcription may not be 100% accurate. It is provided for searching and for screen readers; please refer to the original document for the official version.

AGENDA
EAST GOSHEN TOWNSHIP
BOARD OF SUPERVISORS
Tuesday, November 22, 2011

The Board will meet in Executive Session to conduct interviews for ABC Positions from 7:00 pm – 7:30 pm. Formal Meeting will commence afterwards.

  1. Call to Order
  2. Pledge of Allegiance
  3. Moment of Silence – Supervisor Carmen Battavio
  4. Ask if Anyone is Recording the Meeting?
  5. Public Comment – Hearing of Residents (Optional)
  6. Chairman’s Report Announce Board met in Executive Session on November 15 to discuss a personnel matter.; Announce the Statement of Valuations
  7. Public Hearing
  8. Police/EMS Report – 3 rd Tuesday Chief Dumond – Monthly Activity Report – Oct. 2011; Jerry Fokas, Sr. – President Goshen Fire Co. – EMS Report – Oct. 2011
  9. Financial Report – 4 th Tuesday – Brian McCool Review 2012 Other Funds Budget
  10. Old Business Consider TAG Park & Recreation Board Recommendations; Consider ABC Chairmen Email Accounts
  11. New Business Consider v. 2.4 Police Proposed Budget; Select Date for Annual Planning Session – January 7 th or January 14 th , 2012; Consider Doc Star Replacement; Consider QVC Tax Appeal; Consider HVAC System Assessment; Consider Scope of Work Proposal
  12. Any Other Matter
  13. Approval of Minutes Nov. 15, 2011
  14. Treasurer’s Report Report – Nov. 17, 2011
  15. Review Action List
  16. Correspondence, Reports of Interest Acknowledge Sunoco Remediation Report
  17. Meetings & Dates of Importance: Nov. 21, 2011 Deer Committee 7:00 pm Nov. 22, 2011 Thanksgiving Holiday Market 12 – 3 pm Board of Supervisors 7:00 pm Nov. 24 & 25, 2011 Thanksgiving Holiday

F:\Data\Shared Data\Agendas\Board of Supervisors\2011\11222011.doc

Nov. 28, 2011 West Chester Area Council of Govt’s
(Meeting in Thornbury Township)
7:00 pm
Dec. 1, 2011 Park & Rec Board 7:00 pm
Dec. 3, 2011 New York City Holiday Trip
Dec. 6, 2011 Board of Supervisors 7:00 pm
Dec. 7, 2011 Pension Committee 1:00 pm
Planning Commission 7:00 pm
Dec. 8, 2011 Historical Commission 7:00 pm
Dec. 12, 2011 Municipal Authority 7:00 pm
Dec. 16, 2011 Township Holiday Party
Dec. 20, 2011 Park & Rec Board w/s 10:00 am
Board of Supervisors 7:00 pm
Dec. 21, 2011 Friends of EGT 501c3 7:00 pm
Dec. 26, 2011 Christmas Holiday
Offices Closed
  1. Public Comment – Hearing of Residents
  2. Adjournment

The Chairperson, in his or her sole discretion, shall have the authority to rearrange the agenda in order to accommodate the needs of other board members, the public or an applicant.

F:\Data\Shared Data\Agendas\Board of Supervisors\2011\11222011.doc

POLICE BUDGET WILL BE DISTRIBUTED
AT THE MEETING

There will be two [handwritten: 3] items under Any Other Matter

You need to adopt a resolution designating Barb as the agent to apply for PUMA and FEMA money

Suggest that we include money in the 2012 Budget for the Community Development Commission

[Handwritten note: Memo Re: East Goshen Township Veterans]

PEMA-DAP -2

DESIGNATION OF AGENT RESOLUTION

FOR: FEMA 4025 - Hurricane Irene
(Enter Name of Disaster or Number)

BE IT RESOLVED BY Board of Supervisors OF EAST GOSHEN TOWNSHIP
        (Governing Body)                                                     (Public Entity)

THAT Barbara L. Phillips, Staff Accountant
        (Name of Applicant Agent)                                                  (Title)

IS HERBY AUTHORIZED TO EXECUTE FOR AND IN BEHALF OF
EAST GOSHEN TOWNSHIP, CHESTER County,
        (Public Entity)                                 (County)

a public entity established under the laws of the Commonwealth of Pennsylvania, all required forms and documents for the purpose of obtaining financial assistance under the Robert T. Stafford Disaster Relief and Emergency Assistance Act (Public Law 93-288 as amended by Public Law 100-707).

Passed and approved this ____________________ day of ____________________, 20____.

[Stamp: RECEIVED AFTER AGENDA WAS PRINTED]

____________________, ____________________, ____________________
(Name)          (Title)          (Signature)

____________________, ____________________, ____________________
(Name)          (Title)          (Signature)

____________________, ____________________, ____________________
(Name)          (Title)          (Signature)

____________________, ____________________, ____________________
(Name)          (Title)          (Signature)

____________________, ____________________, ____________________
(Name)          (Title)          (Signature)

CERTIFICATION

I, ____________________, duly appointed and ____________________
(Name)          (Title)

of ____________________, do hereby certify that the above is a true and correct copy of
(Public Entity)

a resolution passed and approved by the ____________________
(Governing Body)

of ____________________ on the ____________________ day of ____________________, 20____.
(Public Entity)

____________________          ____________________          ____________________
(Signature)          (Official Position)          (Date)

Memo
East Goshen Township
1580 Paoli Pike
West Chester, PA 19380
Voice (610) 692-7171
Fax (610) 425-8950
E-mail rsmith@eastgoshen.org

[Stamp: RECEIVED AFTER AGENDA WAS PRINTED]

Date: November 18, 2011
To: Board of Supervisors
From: Rick Smith, Township Manager
Re: Community Development Commission

We should create a line/section in the budget for the Community Development Commission. It would be in the Code Function.

I would suggest the following

Wages 500
Materials and Supplies 1,000
General Expense 2,000

F:\Data\Shared Data\ABC'S\Community Development Commission\Memo re Budget 111811.doc

ASSESSMENT OFFICE
CHESTER COUNTY, PENNSYLVANIA

Statement of real estate subject to taxation in your district for the coming year.

Louis F. Smith, Jr.
1580 Paoli Pk.
West Chester, PA. 19380

STATEMENT OF VALUATIONS

Real Estate Valuation (Including Mobile Homes) $ 1,628,940,936
Public Utilities Valuation $ 495,160

I hereby certify that the foregoing statement is a true and correct summary of all assessments within East Goshen for the year ending October 31, 2011.

[Signature: Jeffrey A. Laudenslager]
Director Of Assessment

Date of Notification: November 14, 2011

2009 Assessment $1,643,578,445
2010 Assessment $1,642,311,226

MONTHLY ACTIVITY REPORT
WESTTOWN EAST GOSHEN THORNBURY TOTAL
MONTHLY ACTIVITY REPORT FOR OCTOBER 2011
UCR CLASS
Part I ARSONS 0 0 0 0
Part I ASSAULTS 0 0 0 0
Part I BURGLARY 1 0 1 2
Part I MURDER AND MANSLAUGHTER 0 0 0 0
Part I RAPE 0 0 0 0
Part I RETAIL THEFT 1 0 2 3
Part I ROBBERY 0 0 0 0
Part I THEFTS 7 5 6 18
Part II CRIMINAL MISCHIEF 6 10 1 17
Part II DISORDERLY CONDUCT 19 24 7 50
Part II D.U.I. 2 3 1 6
Part II HARASSMENT 5 3 0 8
Part II STOLEN VEHICLES 0 0 0 0
Part II RECOVERED STOLEN VEHICLES 1 0 0 1
ACCIDENTS 34 20 14 68
    FATAL 0 0 0 0
    PEDESTRIAN 1 0 0 1
    HIT & RUN 1 4 2 7
    INJURED PERSONS 4 7 0 11
ALARMS 23 32 26 81
AMBULANCE CALLS 28 79 5 112
    Medical Facility Ambulance calls 11 56 0 67
ANIMAL COMPLAINTS 9 11 3 23
ARRESTS AND CITATIONS 8 9 8 25
BUSINESS DOOR OPEN 0 0 0 0
DISABLED VEHICLES 8 5 2 15
FAMILY DISTURBANCES 2 8 0 10
FIRE CALLS 16 20 3 39
HUNTING CALLS 1 0 0 1
INCIDENTS 108 121 15 244
KEYS LOCKED 11 7 0 18
MISCELLANEOUS CALLS 23 11 2 36
WESTTOWN EAST GOSHEN THORNBURY TOTAL
MISSING PERSONS 0 0 0 0
LOCATED 0 0 0 0
MOTOR VEHICLE VIOLATIONS 71 37 15 123
911 HANG UP CALLS 11 32 1 44
PARKING VIOLATIONS 3 0 0 3
SUICIDE 0 0 0 0
SUSPICIOUS CONDITIONS 26 28 9 63
VACATION CHECKS 3 6 2 11
POLICE RADIO ROOM CALLS* 462 607 156 1225
PERCENTAGE BY INDIVIDUAL TOWNSHIPS - 38% 49% 13% 100%
MONTHLY
YEAR TO DATE PERCENTAGE BY 38% 49% 13% 100%
INDIVIDUAL TOWNSHIPS
*NUMBERS ARE PARTIAL BREAKDOWN OF POLICE RADIO ROOM CALLS

MONTHLY ACTIVITY REPORT FOR OCTOBER 2011

CAR # YEAR/MAKE/MODEL UNIT USER ENDING MILEAGE LAST MONTH TOTAL DISTRICT COURT DISBURSEMENTS AMOUNTS
67-44 2008 DODGE CHARGER ADMINISTRATION CHIEF DUMOND 68428 67172 1256 EAST GOSHEN TWP $1,332.42
67-30 2004 FORD CROWN VIC DETECTIVES DET. BRETZ 75566 74764 802 THORNBURY TWP $7,152.50
67-55 2011 DODGE CHARGERS DETECTIVES DET. BALCHUNIS 7515 5891 1624 WESTTOWN TWP $4,360.75
67-36 2006 FORD EXPEDITION DETECTIVES GORMAN 112973 111768 1205
67-38 2007 FORD CROWN VIC DETECTIVES DET. LARGE 74547 73785 762
67-40 2007 FORD EXPEDITION DETECTIVES DET. RAGNI 76115 75219 896
67-54 2011 FORD EXPLORER DETECTIVES DET/SGT. CAHILL 20612 18120 2492
2002 FORD EXPLORER DETECTIVES UNDERCOVER 87887 87765 122
67-11 1996 JEEP CHEROKEE DETECTIVES UNDERCOVER 153709 153595 114
67K90 2003 FORD CROWN VIC K9 K-9 81100 80500 600
67-32 2006 FORD CROWN VIC TRAFFIC 1ST LINE PATROL 51385 50847 538
67-42 2008 FORD EXPEDITION TRAFFIC 1ST LINE PATROL 58564 57577 987
67-53 2010 DODGE CHARGER TRAFFIC 1ST LINE PATROL (UNMARKED) 13622 12972 650
67-46 2009 DODGE CHARGER PATROL 1ST LINE PATROL 60806 59238 1568
67-47 2009 DODGE CHARGER PATROL 1ST LINE PATROL 80475 78275 2200
67-48 2009 DODGE CHARGER PATROL 1ST LINE PATROL 62310 59169 3141
67-49 2009 DODGE DURANGO PATROL 1ST LINE PATROL 62167 60655 1512
67-50 2010 DODGE CHARGER PATROL 1ST LINE PATROL 42524 40432 2092
67-51 2010 DODGE CHARGER PATROL 1ST LINE PATROL 48068 45481 2587
67-52 2010 DODGE CHARGER PATROL 1ST LINE PATROL (UNMARKED) 40552 37384 3168
67-56 2011 DODGE CHARGER PATROL 1ST LINE PATROL 3797 2529 1268
67-57 2011 DODGE CHARGER PATROL 1ST LINE PATROL 3948 2393 1555
67-58 2011 FORD EXPLORER PATROL 1ST LINE PATROL 3226 1608 1618
TOTAL MILES 32757

East Goshen Township          Final Report – Oct 2010          Township Advisory Group (TAG)

Formalize and Expand Relationship with the YMCA (90)

Summary / Short Description:

East Goshen’s parks are a centerpiece of the township and must be protected at all costs. However, since many residents do not directly benefit from the Park and Recreation services provided by the township, these programs should be self-funding / self-sustaining. In addition to rationalizing the breadth of Park and Recreation services provided by the township and increasing the level of sponsorship, the township should seek to formalize their relationship the West Chester YMCA. A more robust relationship with the YMCA could result in significant revenue increases for the township and increased utilization of the township’s natural resources.

Background / Context / Rationale:

Currently, various Park and Recreation programs (clinics, classes, trips), etc. appear to be covering their expenses and/or making a minimal profit. However, when the salary and benefits of the Director of Recreation are allocated to each of the programs, the net loss for the Park and Recreation programs has exceeded $50,000 to $75,000 per year for the last 5 years. This does not account for the fees associated with maintaining the park as those fees will be incurred (in general) in order to maintain the park regardless of whether or not these programs exist.

The West Chester YMCA is thriving. They have reached record membership levels and have provided highly valued services to many of East Goshen’s residents. However, in meeting with the YMCA executive team, the TAG learned the West Chester YMCA has met its capacity in a variety of ways. As an example, due to the physical constraints of their property, they are unable to expand their summer camp program which provides a fun and safe environment for children throughout the summer months. In addition, many of the YMCA’s sports programs leverage elementary school fields throughout the area. Unfortunately, the fees for these fields are increasing every year and many of them pale in comparison to the fields that are available in East Goshen Park. It appears that the YMCA would be willing to pay a premium if they were able to further leverage the township’s ball fields.

The West Chester YMCA desperately wants to expand their relationship with East Goshen but they are hesitant to approach the Board of Supervisors without being asked. They are huge contributor to the local community and they could bring so much more if they were provided with the means to do. Moreover, the YMCA’s vision – “To be a catalyst for improving the quality of life in our community” – is well aligned with the township’s vision – “Endeavor to be one of the premier communities in Chester County by continually improving the quality of life while at the same time, managing growth and development in a manner consistent with the protection of our environment and preservation of our natural and historic resources”. To that end, the TAG believes that the township can make far better use of their natural resources by creating a partnership with the YMCA.

81

East Goshen Township          Final Report – Oct 2010          Township Advisory Group (TAG)

Specific Recommendations and Considerations:

  • Request a detailed proposal from the YMCA that illustrates how they would leverage East Goshen Park to expand their summer camp program
  • Request a detailed proposal from the YMCA that illustrates how they would leverage East Goshen Park to increase their usage of the ball fields
  • Develop a long-term strategy to partially or fully privatize and significantly expand upon the Park and Recreation programs, services and events

Ease of Implementation (i.e. effort): Medium

Costs: Low

Benefits: High

Probability of Capturing Benefits: High

Benefits:

  • Assume the annual net loss for the Park and Recreation Program is eliminated = $50,000 to $75,000 (very conservative)
  • Improved and expanded Park and Recreation programs and services

Total Estimated One Time Benefits: Not applicable

Total Estimated Recurring Benefits: $50,000 to $75,000 annually

Costs:

  • Not applicable

Total Estimated One Time Costs: Not applicable

Total Estimated Recurring Costs: Not applicable

Related Recommendations:

  • Self-Sustaining Park & Recreation Programs (104)
  • Institute Park and Recreation Sponsorship Program (88)
  • Increase Fees for Ball Fields (48)

82

AREA CODE 610
692-7171
www.eastgoshen.org

PARK & RECREATION BOARD
EAST GOSHEN TOWNSHIP

CHESTER COUNTY
1580 PAOLI PIKE, WEST CHESTER, PA 19380-6199

November 16, 2011

[Stamp: RECEIVED BY: ____________________
NOV 16 2011]

East Goshen Township Board of Supervisors
1580 Paoli Pike
West Chester, PA 19380

RE: Partnership with the West Chester YMCA

Dear Board of Supervisors:

At our meeting on November 15, 2011 the Park and Recreation Board approved the following motion: “The Park Board is not in favor of the partnership with the YMCA and wants to continue with the current system for permitting the fields, pavilions and other facilities”. The motion passed with 6 for and one abstention.

Respectfully yours,

[Signature: Ruth Scadding]

Ruth Scadding
Chairman of the Park Board

U:\FRANK\YMCA\2011 proposal for partnership with Y\Partnership letter from PB to BOS\Ruth to BOS 111611.docx

Memo

Date: November 9, 2011
November 17, 2011
From: Rick Smith, Township Manager
To: Board of Supervisors
Re: ABC Chairman Email Accounts

We tested the ABC Chairman email accounts and they are active and functioning. However, the majority consensus among the ABC Chairmen is that these accounts are not being used. The suggestion was made to do away with email accounts for the chairpersons and have all ABC email come to the administration email address (egtadmin@eastgoshen.org). Email could then be forwarded, if necessary, to the pertinent chairperson for handling.

Following up on the discussion at the meeting on November 15, Bee.net can set up the ABC Chair e-mail accounts so that the e-mails would be forwarded to the ABC Chair’s personal e-mail account and have the system send an copy to the web mail which would then be archived.

This would ensure that an ABC would know about any e-mails that are sent to them in their official capacity and eliminate the need for them to check their web mail account.

However, if they responded to the resident using their personal e-mail, the response would not be archived. We could solve this problem by requiring that the ABC Chair should “cc” the staff liaison on any response.

We could also require that the ABC Chair and ABC members “cc” the staff liaison on any e-mails they send concerning Township business.

-If you agree I will revise the e-mail resolution to address this issue.

F:\Data\Shared Data\Information Systems\E MAIL\BOS Memo Chair email accounts 111711.docF:\Data\Shared Data\Information Systems\E MAIL\BOS Memo Chair email accounts.doc

Memorandum

East Goshen Township
1580 Paoli Pike
West Chester, PA 19380
Voice: 610-692-7171
Fax: 610-692-8950
E-mail: mgordon@eastgoshen.org

Date: 11/14/2011
To: Board of Supervisors
Cc: Rick Smith, Township Manager
From: Mark Gordon, Township Zoning Officer
Re: DocStar System Replacement

Dear Board Members,

The Township Administration Finance and Code Departments use a Document Management System to electronically file documents, DocStar. The hardware for the current system is 4.5 years old and out of warrantee. I have been discussing the replacement and upgrade options with our DocStar consultants, ImageNet. ImageNet has provided us a proposal for a new DocStar Server Upgrade to include software updates, 3 yr extended warrantee, delivery, setup, installation, and configuration.

ImageNet also does Large Format Scanning (i.e. subdivision and land development plans) for upload into the document management system. We have previously scanned over 1,300 plan sheets and Image Net can move these into DocStar, however we have approximately 900+ plan sheets that need to be scanned and coded so they can be easily indexed and securely backed up so the information is not lost if the physical plan is. ImageNet provided a proposal to do this work in conjunction with the purchase of the upgraded hardware and software package.

I also asked ImageNet to provide a proposal for the scanning of all 7900+ Property TPN Files into the DocStar system. This information is used very often and it would be very helpful to have the historical information available at your fingertips and at times files do go missing so this would ensure that an electronic back up would exist.

F:\Data\Shared Data\Code Dept\DocStar\Memo to BOS DocStar 11142011A.doc

DocStar Server Upgrade

Includes 3 yr ext warrantee Purchase $20,966.00
Per Mo. Total
60 Mo Lease $398.34 $23,900.40
48 Mo Lease $479.16 $22,999.68
Additional 2 Yr warrantee (5yr) $5,640 $2,820.00 per yr

Large Format Scanning

Scan 900 images and import into Docstar Purchase $2,115 $2.35 per page
Per Mo. Total
60 Mo Lease $51.24 $3,074.40
48 Mo Lease $60.76 $2,916.48

Property TPN Files

Scan 7900 Property tax parcel files Purchase $8,930 $1.13 per file
Per Mo. Total
60 Mo Lease $209.61 $12,576.60
48 Mo Lease $248.58 $11,931.84

Recommendation:

I recommend that the Board authorize the Staff to enter into a contract with ImageNet to do the following:

  1. Replace the DocStar Server Purchase $20,966
  2. Scan, index and upload all large format plans into DocStar. Purchase $2,115
  3. Scan, index and upload all Tax Parcel files into DocStar. Purchase $8,930

F:\Data\Shared Data\Code Dept\DocStar\Memo to BOS DocStar 11142011A.doc

Memo
East Goshen Township

Date: November 15, 2011
To: Board of Supervisors
From: Rick Smith, Township Manager
Re: HVAC System Assessment

On November 1, Ken Kauffman presented his assessment of the Township Building HVAC System. The Board requested some additional information and I received that today. You need to decide where we go from here.

Assuming that the Board wants to upgrade the HVAC system I would suggest that you consider two factors. The first being the 20 year life cycle cost of each system.

The existing system has a 20 year operating life cycle cost of $789,208. This is the baseline from which the other options should be compared. Option 2 (gas furnace) and Option 3 (VAV system) both have operating life cycle costs in excess of the baseline so I would eliminate them.

Option 1 (high efficiency water source heat pumps) has an estimated operating life cycle cost of $729,300 which represents a savings of $59,980 or (8%) from the baseline. Option 4 (geothermal) has an estimated operating life cycle cost of $654,700 which represents a savings of $134,580 or (17%).

We would save an additional $74,600 in operating costs from the baseline if we went with Option 4 (geothermal) instead of Option 1 (high efficiency water source heat pumps).

The second factor is the initial installation cost.

The installation cost of Option 1 (high efficiency water source heat pumps) is $385,875. The installation cost of Option 4 (geothermal) is estimated at $500,250 which is only $114,375 more than Option 1.

It would seem that the $134,580 we will save operating Option 4 (Geo thermal) will more then offset the $114,375 higher first cost.

Finally if we go with Option 1 at the end of 20 years we essentially start over. If we go with Option 4 we start over with a geothermal system in the ground that is paid for.

I would suggest proceeding with Option 4. We will be celebrating our 200th anniversary in a few years. We have been in our present location for over 40 years and I do not see use moving anytime in the future.

F:\Data\Shared Data\Public Works Dept\Buildings\Twp. Bldg. 1580 Paoli Pike\HVAC\Needs Analysis\Memo to BoS 111511.doc

HVAC STUDY
November 15, 2011

OPERATING COSTS

OPERATING COSTS LIFE CYCLE 20 YEAR LIFE CYCLE COST SAVINGS FROM BASELINE
BASELINE EXISTING $39,464 20 $789,280 $0
1 WSHP $36,465 20 $729,300 $59,980
2 GAS $53,276 20 $1,065,520 -$276,240
3 VAV $52,092 20 $1,041,840 -$252,560
4 GEO $32,735 20 $654,700 $134,580
% savings from from baseline
20 year savings from base line with option 1 $59,980
Annual savings from base line with option 1 $2,999 8%
20 year savings from base line with option 4 $134,580
Annual savings from base line with option 4 $6,729 17%
20 year savings from option 1 with option 4 $74,600
Annual savings from option 1 with option 4 $3,730

FIRST COSTS

FIRST COST
BASELINE EXISTING 0
1 WSHP $385,875
2 GAS $311,750
3 VAV $677,875
4 GEO $500,250

Increase from option 1 to option 4          $114,375

F:\Data\Shared Data\Public Works Dept\Buildings\Twp. Bldg. 1580 Paoli Pike\HVAC\Needs Analysis\Book1.xls

Rick Smith

From: Ken Kauffman [kenk@mooreengineering.com]
Sent: Tuesday, November 15, 2011 11:57 AM
To: Rick Smith
Subject: East Goshen Questions

Rick,

I have researched the two open questions discussed at the township meeting and have the following additional information:

Q – What would be the cost for eliminating the ceiling plenum issues in the existing facility:

A – That is not easy to determine until we determine the full scope of the work. The cost associated with this part of the scope is directly related to the other potential work that is outlined in the study. For example, if you are going to do a complete system replacement, then the ceilings and lights would need to be removed and reinstalled or replaced. This simplifies the cost of adding the ductwork needed to eliminate the plenum because the ceiling is not in the way. If you just want to fix the plenum issue, then you would need to include the costs for the ceilings in the number. That is one of the reasons that I excluded it in the estimates. All this stated, I would estimate that the cost to eliminate the plenums would be in the $65,000 to $85,000 range.

Q – What was the cost of the well system for the similar project I referenced in the Selinsgrove PA area?

A – That project was very similar in size and the cost of the field portions was around $150,000. There was an excessive amount of water on that site that needed to be dealt with under the E&S plan. We are estimating that the cost to handle the runoff is in the $20,000 to $30,000 range.

I hope this addresses the two items that needed further research and clarification. Please contact me if you have additional open questions.

Ken

Kenneth L. Kauffman, PE, LEED AP
Vice President
MOORE ENGINEERING COMPANY
3637 Columbia Avenue
Lancaster, PA 17603
717-285-3141
www.mooreengineering.com

1

HVAC System Assessment

for

East Goshen Township Building

October 25, 2011

[Photograph of the two-story brick East Goshen Township Building with a flagpole in front.]

MEC
MOORE ENGINEERING COMPANY

3637 Columbia Avenue - Lancaster, PA 17603
Phone 717.285.3141- Fax 717.285.2443
www.mooreengineering.com

Introduction

Moore Engineering Company (MEC) was contracted by East Goshen Township to review the HVAC system at their office facility on Paoli Pike and provide feedback based on the following outlined scope of work:

  • 1. Assess the viability of the current HVAC system
  • 2. Identify what can be done to the current HVAC system to reduce O&M costs
  • 3. Identify alternatives to the current HVAC system
  • 4. Provide the projected cost for each alternative
  • 5. Provide the estimated cost savings to the Township for each alternative

To perform these tasks, we surveyed the building and the site, reviewed the as-built documents provided, and estimated the heating and cooling loads for the building using block load calculations. The findings are summarized in the attached report.

Existing System Overview and Condition

The existing facility is currently heated and cooled with a water source heat pump system. This system includes a gas fired boiler, an outdoor cooling tower, two pumps, a two pipe distribution system, multiple water source heat pumps, ductwork distribution systems, and automatic temperature controls. There is also a central ventilation system installed to provide the zones with outdoor air.

Water source heat pump systems are generally quite efficient for central block type buildings with multiple interior spaces. The general layout of the Township building does have zoning that would provide the zone diversity that generally makes water source heat pumps a viable system solution.

Through the course of our evaluation we have determined that the equipment has been well maintained and is in working order. Some components are new as a result of recent replacement.

Equipment List - August 10, 2011 - East Goshen Township HVAC Equipment

LocationQTYTypeManfacturerModelUnit #
Township Building1Gas BoilerWeil - McLainUltra 230
2Closed loop 3 HP PumpsTaco
1Cooling TowerEvapcoATW33A
1Chemical feed system for EVAPCO Tower.
1Make Up Air UnitBraschM115E
2Cabinet HeatersErincraftECH-A-34
5Wall HeatersErincraftAWH720
3Unit HeatersReznorRTN-75-40
2Unit HeatersReznorRTN-60-40
1Propeller FanPenn Ventilator
1Water Source Heat PumpClimate MasterHS019GSZGLBMCSAB-1
1Water Source Heat PumpClimate MasterHS006GSZGRBMCSAB-2
1Water Source Heat PumpClimate MasterHS030GSZGLBMCSAB-3
1Water Source Heat PumpClimate MasterHS015GSZGLSMCSA1-1
1Water Source Heat PumpClimate MasterGCH018BC30CLBS1-2
1Water Source Heat PumpClimate MasterHS009GSZGRBMCSA1-3
1Water Source Heat PumpClimate MasterTCH018AGC30CRSS1-4
1Water Source Heat PumpClimate MasterGRH009AGD30CRSS1-5
1Water Source Heat PumpClimate MasterHS019GSZGLBMCSA1-6
1Water Source Heat PumpClimate MasterHS019GSZGRBMCSA1-7
1Water Source Heat PumpClimate MasterHS009GSZGLBMCSA1-8
1Water Source Heat PumpClimate MasterHS009GSZGLBMCSA1-9
1Water Source Heat PumpClimate MasterHS012GSZGRBMCSA1-10
1Water Source Heat PumpClimate MasterGCH009BGC30CRBS1-11
1Water Source Heat PumpClimate MasterHS019GSZGRBMCSA1-12
1Water Source Heat PumpClimate MasterGCH030BGD30CLBS2-1
There is no unit 2-22-2
1Water Source Heat PumpClimate MasterGCH024BGC30CLSS2-3
1Water Source Heat PumpClimate MasterHS072HSZGLSMCSA2-4
1Water Source Heat PumpClimate MasterGSH070AHC30CLSS2-5
1Water Source Heat PumpClimate MasterTCH018AGC30CRSS2-6
1Water Source Heat PumpClimate MasterHS009GSZGLBMSA2-7
1Water Source Heat PumpClimate MasterHS012GSZGLBMCSA2-8
1Water Source Heat PumpClimate MasterHS006GSZGLBMCSA2-9
1Water Source Heat PumpClimate MasterHS015GSZGLSMCSA2-10
1Water Source Heat PumpClimate MasterGCH018BGD30CRSS2-11
1Water Source Heat PumpClimate MasterTCH012AGC30CLSS2-12

East Goshen Township Building - HVAC System Analysis | Page 2 of 12

The main concerns found during the analysis are as follows:

  • Water Source heat pumps (WSHP) are nearing 20 years old and are at the end of their typical life expectancy. ASHRAE publishes a typical service life for water source heat pumps of 19 years.
  • The cooling tower is nearing 20 years old and is at the end of its typical life expectancy. ASHRAE publishes a typical service life for cooling towers of 20 years.
  • The loop pumps are nearing 20 years old and have exceeded their typical life expectancy. ASHRAE publishes a typical service life for inline water pumps of 10 years.
  • The older WSHP units do not meet current energy standards.
  • The cooling tower is no longer efficient and needs to be replaced.
  • The flue vent system for the gas boiler does not appear to match the listed requirements in the online installation manual. This should be further evaluated and modified if required.
  • The building outdoor air ventilation system does meet current standards for delivery or air volume.
  • The boiler size appears to be slightly undersized based on an estimated building load.
  • The facility uses a plenum ceiling return and ventilation delivery system. This method can cause operation, temperature control, and system efficiency issues. It also creates a dusty environment above the ceiling which clogs filters and traps.
  • It appears that some condensate drains are connected directly to the sanitary system. This does not meet the current code and provides a path for sewer gasses to be pulled into the HVAC airstream (if a trap dries out).
  • WSHP systems are in the ceiling limited cavity and are difficult to maintain.

[Photographs showing existing mechanical equipment and ceiling installations: top right shows ductwork in ceiling cavity; middle right shows outdoor cooling tower; bottom left shows mechanical piping and valves; bottom center shows gas boiler; bottom right shows ceiling plenum and ductwork.]

East Goshen Township Building - HVAC System Analysis
Page 3 of 12

Option 1 – Upgrade the existing Water Source Heat Pump System

As noted previously, the building configuration makes a WSHP system a viable option. Modifying and modernizing the existing system provides value in first cost and can result in operational savings. Our general recommendations for upgrade include the following:

  1. Replace the existing inefficient and aging components. The older water source heat pumps operated at an efficiency of 9.5 EER and 3.9 COP. Newer models can be provided that operate at 18.0 EER and 5.9 COP. This is a major improvement in the efficiency of the equipment.
  2. Replace the aging and inefficient cooling tower. The existing treatment system seems to be in good condition and can remain.
  3. Provide new circulation pumps with variable speed drives. Install two way control valves on the WSHP units to allow the flow to be reduced when the systems are not in operation. This will result in significant pumping horsepower reduction. Currently the pumps operate at full speed continuously.
  4. Install a second boiler to increase the heating capacity. While the heat pump system will operate at lower loop water temperatures, maintaining a 70 F loop temperature will increase the efficiency of each heat pump and reduce the amount of electricity used in the heating process.
  5. Install a new energy recovery ventilation system that will precondition the outdoor air. Upsize the new boiler so that hot water can be provided for reheat in lieu of the 120 KW electric heating coil.
  6. Modify the condensate system to be code compliant.

Because we are not currently in the design process, we cannot confirm if all of our recommended modifications can be implemented. If the project enters a design phase, further sizing, evaluation, and discussion with staff would be required to see if some proposed modifications are feasible. They will require us to modify floor plans, ceiling elevations, etc. That may be possible in some areas, but not in others. For this reason, we have not included these costs in the estimates but list them below for future consideration and evaluation.

  1. Eliminate the plenum system and provided fully ducted outdoor air and returns. This may be difficult in some areas as a result of ceiling cavity constraints.
  2. Relocate the heat pumps, when possible, to closets on the floor level to allow for easier service.

[Photographs: top right shows a vertical water source heat pump cabinet; middle right shows an outdoor cooling tower; bottom right shows an indoor mechanical closet with an American flag hanging adjacent.]

East Goshen Township Building - HVAC System Analysis
Page 4 of 12

The WSHP system has the following advantages and disadvantages:

ADVANTAGES

  • Simultaneous heating and cooling
  • High efficiency boilers provide good modulation and loop control
  • Supply ductwork can be reused
  • Loop piping system can be reused
  • Very competitive as a result of multiple manufacturers
  • Outdoor condensing units are not required

DISADVANTAGES

  • Outdoor cooling tower is required
  • Water treatment is required
  • The cooling tower increases the use of water through the evaporation process

East Goshen Township Building - HVAC System Analysis
Page 5 of 12

Option 2 – Gas Furnaces with Split System Air Conditioners

Like the WSHP system, this system is capable of providing simultaneous heating and cooling. Each zone would have a high efficiency gas furnace with an outdoor condensing unit. Outdoor air would be introduced directly into the space through an energy recovery unit as we are recommending in Option #1. The heat in the energy recovery unit would be hot water off the existing boiler. The zones would be fully ducted and include control similar to the existing configuration.

The gas furnaces would utilize PVC pipe for flues and intakes. If the zoning remains the same, there would be 26 PVC flue pipes and 26 PVC intake pipes that would be required to run to the exterior through the roof or the outside walls. We would also need to located 26 outdoor condensing units around the site. This will be a design challenge from an aesthetic standpoint.

A new gas service would be required along with a new interior distribution system. New regulators would be needed, but they would be located outside the facility at the meter. We estimate that the new gas main in the building would be no larger than 4".

ADVANTAGES

  • Simultaneous heating and cooling
  • Gas is an efficient way to heat a building
  • The equipment is very competitive
  • Supply ductwork could be reused if the zoning remains the same

DISADVANTAGES

  • Exterior venting will be difficult to conceal on the building exterior
  • Multiple outdoor condensing units will be difficult to locate around the perimeter of the building
  • Some new site noise as a result of the compressors
  • Piping system cannot be reused
  • A new gas service and supply pipe will be required
  • Equipment historically has a shorter life than the other options

[Photographs: indoor gas furnace units (left) and an outdoor condensing unit (right).]

East Goshen Township Building - HVAC System Analysis
Page 6 of 12

Option 3 – VAV System with Chilled Water Cooling and Hot Water Heating

This system is capable of providing simultaneous heating and cooling. An additional boiler would be provided along with a new outdoor central chiller. Four pipes and separate pumps would be used for the system to allow for simultaneous heating and cooling. Ducted chilled/hot water air handlers would be located in the basement to provide 55 F air to VAV boxes located in each zone. The 55 F air volume is varied and/or heated with a hot water coil (in the VAV box) to maintain the zone set point. Hot water would be distributed to each VAV box from the boiler system. The existing piping would be insulated and reused for the reheat loop.

Outdoor air ventilation would be provided through the air handler to all spaces. An energy recovery ventilation wheel would be provided in the unit to reduce the cost of preconditioning the air. New areaways will be required to handle the outdoor air and relief air systems associated with the air handlers.

The chiller would be an air cooled unit that would be located where the existing tower is currently installed. A sound enclosure may be required depending on the projected sound level of the unit. The existing piping to the tower is likely undersized cannot be reused. Further evaluation would be required.

ADVANTAGES

  1. Best control due to VAV box reheat
  2. Excellent comfort level
  3. Existing supply ductwork can be reused
  4. Existing piping can likely be reused for the reheat coils
  5. Outdoor condensing units are not required.

DISADVANTAGES

  1. This option will require the use of additional space in the basement.
  2. New areaways will be required.
  3. Outdoor chillers can be noisy if not properly treated.
  4. Higher first cost than some other options.

[Photographs: variable air volume (VAV) terminal box (left), Airstack/Multistack air-cooled modular chiller (center), and red mechanical circulation pump (right).]

East Goshen Township Building - HVAC System Analysis
Page 7 of 12

Option 4 – Geothermal Heat Pump System

This system is very similar to the WSHP system except that it utilizes a well field in lieu of the boiler and the tower. For this option we would reuse the existing supply ductwork and loop water piping. The piping would need to be insulated as a result of the lower temperatures associated with a geothermal system. The existing heat pumps recently replaced could not be reused in this scenario as they are not geothermal compatible.

The boiler would be retained and used for preconditioning the outdoor air off a new energy recovery ventilator. This will eliminate the need to electric heat and keep the energy costs minimized.

A major part of the cost of this system is the well field. An analysis of the soil geology will be required to determine if the site is adequate for a Geothermal System. We have estimated the well field size and cost based on other Geothermal Systems installed in similar facilities. Based on the information received, the water table is quite high in this area. This can cause some complication when drilling and could increase the cost of the installation. It does, however, help with the soil conductivity and help to reduce the amount of bore holes required. If this option is considered, a test bore will be required to determine the actual soil conditions and the conductivity. That information is necessary to properly size the well field.

ADVANTAGES

  • The only truly “Green” system being considered
  • Simultaneous heating and cooling
  • No visible outdoor equipment
  • No associated site noise
  • Lowest energy consumption option
  • Lowest maintenance cost option

DISADVANTAGES

  • Major site disturbance would occur with the new well field
  • Well field may have an effect on the parking lots
  • Piping system will need to be insulated
  • Highest first cost
  • Glycol will be required in the piping system

[Photographs: vertical geothermal heat pump unit (top right), geothermal manifold and piping system (bottom left), and geothermal well drilling rig in operation on site (bottom right).]

East Goshen Township Building - HVAC System Analysis
Page 8 of 12

System Option Life Cycle Cost Summary

The following is a general economic comparative summary of the four options based on typical costs for the systems as well as estimated operational costs. The Annual Operational Cost estimates listed include both estimated utility costs and maintenance costs. These numbers are for comparative purposes only. They are for general system comparison only.

Option # HVAC System *Cost/SF Typical System Life Expectancy Total First Cost Annual Operating Cost Average Owning and Operating Cost
Baseline Existing System NA NA NA $39,464 NA
1 Water Source Heat Pumps $24.75 20 $358,875 $36,465 $80,520
2 Gas Furnaces with Split System Air Conditioners $21.50 15 $311,750 $53,276 $97,162
3 VAV System with Chilled Water Cooling and Hot Water Heating $46.75 20 $677,875 $52,092 $130,943
4 Geothermal Heat Pump System $34.50 20 $500,250 $32,735 $89,441

*Note that costs include new drop ceilings in the areas of work, but not new lighting

East Goshen Township Building - HVAC System Analysis
Page 9 of 12

Summary

Based entirely on economics, we would recommend Option 1. Please note that despite the economic advantage of this option, the Township may wish to pursue another option based on specific advantages and disadvantages. We have included a brief list of some other recommendations based on various criteria as follows:

Evaluation Criteria Recommended System
1st Choice 2nd Choice 3rd Choice
Lowest Energy Use Option 4 Option 1 Option 3
Lowest First Cost Option 2 Option 1 Option 4
Lowest 20 year Maintenance Cost Option 4 Option 1 Option 3
Least Central Mechanical Space Required Option 4 Option 2 Option 1
Lowest Site Noise Option 4 Option 1 Option 2
Least Visible Site Equipment Option 4 Option 3 Option 1
Best Humidity Control Option 3 Option 1,4 Option 2
Least Disruptive Install Option 1

The selection process for the HVAC system should include a review of the economics, the above criteria, as well as other intangible factors.

East Goshen Township Building - HVAC System Analysis
Page 10 of 12

Other Energy Issues

Per our proposal we indicated that we would present other energy saving opportunities that we noted during our review of facility. These have not been included in the listed cost estimates but can be budgeted as needed.

  1. Upgrade the interior lighting systems. The systems currently installed are generally T-12 fluorescent lighting systems. These systems can use as much as 2.5 watts per SF. These lamps are being phased out and will soon become difficult to purchase. If you replace the ceiling to install new HVAC systems, replacement of the lights would make a lot of sense. New T-8 or T-5 lighting can be installed which typically run at under 1 watt per SF.
  2. It was noted that some of the insulation above the upper floor ceiling is loose and should be reattached.
  3. The plans indicated that the attic insulation thickness is 6” of batt which is equivalent to an R-12. This thickness of insulation was standard 20 years ago, but does not meet current energy code levels. The current code level of insulation would be R-38 or 12” of batt.
  4. Flow controls could be added to the plumbing fixtures to reduce the amount of water used – both hot and cold.
  5. Additional temperature controls could be provided to provide global setback of temperatures and loop control. All the new thermostats should be programmable type for added energy savings.

Our office entered your utility data into the Energy Star portfolio manager benchmarking tool to see how your facility stacks up against other similar facilities. The general results are outlined on the following page.

East Goshen Township Building - HVAC System Analysis
Page 11 of 12

FOR YOUR RECORDS ONLY. DO NOT SUBMIT TO EPA.

Please keep this Facility Summary for your own records; do not submit it to EPA. Only the Statement of Energy Performance (SEP), Data Checklist and Letter of Agreement need to be submitted to EPA when applying for the ENERGY STAR.

Facility
EGT
Paoli Pike
West Chester, PA 19380
Facility Owner
N/A
Primary Contact for this Facility
N/A

General Information

EGT
Gross Floor Area Excluding Parking: (ft²) 23,479
Year Built 1992
For 12-month Evaluation Period Ending Date: May 31, 2011

Facility Space Use Summary

Building
Space Type Office
Gross Floor Area(ft2) 23,500
Weekly operating hours 60
Workers on Main Shift 30
Number of PCs 30
Percent Cooled 50% or more
Percent Heated 50% or more

Energy Performance Comparison

Performance Metrics Evaluation Periods Comparisons
Current
(Ending Date 05/31/2011)
Baseline
(Ending Date 05/31/2011)
Rating of 75 Target National Average
Energy Performance Rating 59 59 75 N/A 50
Energy Intensity
Site (kBtu/ft2) 77 77 63 N/A 85
Source (kBtu/ft2) 167 167 137 N/A 185
Energy Cost
$/year $ 39,464.15 $ 39,464.15 $ 32,331.52 N/A $ 43,713.82
$/ft2/year $ 1.68 $ 1.68 $ 1.38 N/A $ 1.85
Greenhouse Gas Emissions
MtCO2e/year 174 174 143 N/A 193
kgCO2e/ft2/year 7 7 6 N/A 8

More than 50% of your building is defined as Office. Please note that your rating accounts for all of the spaces listed. The National Average column presents energy performance data your building would have if your building had an average rating of 50.

Notes:
o - This attribute is optional.
d - A default value has been supplied by Portfolio Manager.

East Goshen Township Building - HVAC System Analysis
Page 12 of 12

CENTER FOR SOCIAL AND ECONOMIC POLICY RESEARCH
AT
WEST CHESTER UNIVERSITY OF PENNSYLVANIA

SCOPE OF WORK PROPOSAL

EAST GOSHEN COMPENSATION AND BENEFITS ANALYSIS

NOVEMBER 8TH, 2011

PREPARED BY DR. JEFFERY OSGOOD
& DR. R. LORRAINE BERNOTSKY
(610)425-7447

EAST GOSHEN TOWNSHIP COMPENSATION AND BENEFITS ANALYSIS

PROPOSAL SUMMARY

East Goshen Township is seeking to conduct a comprehensive examination of its compensation practices. The purpose of this project is to identify the extent to which the township’s compensation policies are appropriate given market considerations and the Board of Supervisor’s fiduciary responsibilities to the citizens of the township. The Center for Social and Economic Policy Research (CSEPR) will examine and evaluate the classification, compensation and benefit plans for all township employees.

The end product of the study, as detailed in the Proposed Work Scope, will include recommendations for the following: a classification schedule, job descriptions, and compensation table for employees; a total compensation comparison with other similarly situated municipalities and similar positions in the private sector as defined by the client; and manuals that create policies that address both compensation and benefits and employee evaluation and recognition. Any questions or clarifications may be directed to Dr. Jeffery Osgood at (610) 425-5000 ext. 2440 or josgood@wcupa.edu.

PROPOSED WORK SCOPE

The CSEPR shall develop recommendations for a compensation and classification system of positions that cover all township employees.

1. Job Description Evaluations and Revision

Create, modify and/or update job descriptions for all positions in compliance with the ADA and other applicable federal and state statutes. Specifically, essential functions will be identified in each job description. The CSEPR shall determine whether the duties performed by each employee actually reflect the duties of the job title/description assigned to that employee and, if not, recommend the appropriate job title and description for the employee. The CSEPR shall also include a list of necessary or required qualifications, including education, for each position that reflect the minimum level necessary to successfully complete the required functions.

Center for Social and Economic Policy Research at West Chester University of PA
1

2. Compensation and Benefit Analysis Survey

The CSEPR shall perform a compensation and benefit survey of several communities comparable to East Goshen in size, population and economic climate. These shall be selected in consultation with the client. Private sector comparisons will be made where such comparative analysis is representative of a compensation structure that is applicable to municipal hiring.

3. Compensation Schedule

Utilizing the market survey results and comparable job descriptions, the CSEPR shall prepare a recommended compensation plan, salary schedule and benefits offerings to correspond to the updated job descriptions.

4. Compensation and Benefit Policies Manual

At the conclusion of the study, the CSEPR shall provide a Compensation and Evaluation manual to be utilized by the township to objectively evaluate new or revised positions following the conclusion of the study. The manual shall describe the methodology used by the CSEPR to undertake the study and how it can be maintained and utilized by the township in the future, including the detailed evaluation criteria.

5. Employee Performance Evaluation and Recognition Manual

At the conclusion of the study, the CSEPR shall provide an Employee Performance Evaluation and Recognition manual to be utilized by the township to objectively evaluate employee performance and recognize particular areas of performance that are or may become of interest to the Township i.e. recognition and reward of employees whose work or suggestions significantly and measurably increases productivity and saves money for the Township. Such manual shall also include recommendations for incentive pay, performance pay and/or other supplemental compensation.

Center for Social and Economic Research at West Chester University of PA
2

TIMELINE AND DELIVERABLES

The stages at which data collection and analysis for this study could take place are somewhat flexible. However, it is the recommendation of the CSEPR that the stages for this project follow the order and the timeline detailed in the charts below in order to provide a timely completion date for the client.

EAST GOSHEN COMPENSATION AND BENEFITS ANALYSIS SCHEDULE

[Gantt chart showing project phases across Jan/Feb, March/April, May/June, July/August, and September, color-coded by Development, Data Collection, and Data Analysis.]

Phase of WorkJan/FebMarch/AprilMay/JuneJuly/AugustSeptember
Job Description Evaluation & RevisionData Analysis
Develop Compensation SurveyDevelopment
Collect Compensation Survey ResultsData CollectionData Collection
Analyze Survey DataData AnalysisData Analysis
Develop Compensation ScheduleDevelopmentDevelopmentDevelopment
Develop Compensation Policies ManualDevelopmentDevelopmentDevelopment
Develop Employee Evaluation & Recognition ManualDevelopmentDevelopmentDevelopment
Consensus Meetings/ReportingData AnalysisData Analysis

Legend: Development | Data Collection | Data Analysis

Center for Social and Economic Research at West Chester University of PA | 3

The deliverables for the phases of work are as follows:

Phase of Work Deliverables
Job Description Evaluation and Revision
  • Revised job descriptions for all municipal employees
  • Identification of essential job functions for each position
  • Identification of the necessary or required qualifications for each position
Compensation and Benefits Analysis Survey/Compensation Schedule
  • Survey instrument
  • Data analysis
  • Respondent database file
  • Development of Compensation Schedule based on survey findings
Compensation and Benefits Manual
  • Identification of best practices in municipal compensation and benefits
  • Development of a Compensation and Benefits manual
Employee Evaluation and Recognition Manual
  • Meeting with client to determine additional areas of performance and incentive pay and recognition to include in manual
  • Identification of best practices in employee evaluation and recognition
  • Development of an Employee Evaluation and Recognition manual
Consensus Meetings and Development of Final Reports1
  • Consensus meetings with client to finalize all deliverables
  • Multiple training sessions on how to use the new policies and procedures
  • MS Word and Web-ready (PDF) file of all deliverables

1 The CSEPR will provide electronic copies of all reports which may be placed on the web at the discretion of the client. This proposal does not include web hosting of the reports or the data by the CSEPR.

Center for Social and Economic Research at West Chester University of PA
4

Memorandum

East Goshen Township
1580 Paoli Pike
West Chester, PA 19380
Voice: 610-692-7171
Fax: 610-692-8950
E-mail: mgordon@eastgoshen.org

[Stamp: RECEIVED AFTER AGENDA WAS PRINTED]

Date: 11/18/2011
To: Rick Smith, Township Manager
Cc: Board of Supervisors
From: Mark Gordon, Township Zoning Officer
Re: East Goshen Township Veterans’

Rick,

I attended the West Chester Men’s Service Club Veterans Day Dinner Last with Senya, Marty and Carmen and met a bunch of great East Goshen Vets. Senya and I started discussing how the Township can improve the awareness of Veterans’ programs for our Township Veterans.

In college I worked for the VA as a Penn State student liaison for the GI Bill Financial Aid programs. I helped Penn State Veterans wade through the challenges of the VA Financial Aid programs. I was also an officer in my Veterans Service Fraternity where I worked on many programs for Veterans in the Harrisburg area.

As I work through my own challenges and experiences dealing with VA benefits I’m realizing that these programs can be confusing however there are resources that can help veterans overcome these hurdles and that’s where I think I can provide an additional service to East Goshen Township Veterans.

Senya and I spoke with Paul Andriole, Chester County Director of Veterans’ Affairs; he agreed that the biggest challenge is making Veterans aware of the resources available to them and liked the idea of a local municipal veterans’ liaison to improve awareness for Chester County Veterans. I know I can assist East Goshen Veterans in finding the right person or agency to assist them. This would simply be an additional informational service we could offer and something I would enjoy doing and one that I know will enhance the welfare of East Goshen Township Veterans.

C:\Documents and Settings\nscheiderman\Local Settings\Temporary Internet Files\Content.Outlook\SD443LJR\Memo to BOS 11172011.doc

Memo

East Goshen Township
1580 Paoli Pike
West Chester, PA 19380
Voice (610) 692-7171
Fax (610) 425-8950
E-mail rsmith@eastgoshen.org

Date: November 17, 2011
To: Board of Supervisors
From: Rick Smith, Township Manager
Re: Sunoco Remediation Report

We received the 2011 third quarter report from Sunoco. They have pumped and treated 266,356 gallons of ground water during this reporting period, Of the 24 test wells only 6 of them have a MTBE reading above <1 ug/l. A complete copy of the report is available for review at the Township Building.

F:\Data\Shared Data\Property Management\53-4\53-4-2 (1431 Paoli Pike)\Sunoco\Memo to BOS 111711.doc

ENVIRONMENTAL ALLIANCE

  • Engineering
  • Remediation
  • Consulting

October 31, 2011

Ms. Lauren Mapleton
Pennsylvania Department of Environmental Protection
Southeast Regional Office
2 East Main Street
Norristown, PA 19401

RECEIVED
BY:
NOV - 9 2011

RE: SUNOCO STATION #0004-7969
1425 PAOLI PIKE
WEST CHESTER, PA
PADEP Facility ID No. 15-20353

Dear Ms. Mapleton:

Enclosed please find the Remedial Action Progress Report prepared by Environmental Alliance, Inc. (EAI) on behalf of Sunoco, Inc. for the above referenced site. This report is based on PA Code Title 25 Chapter 245 Requirements and presents a summary of the analytical results from the most recent groundwater sampling event conducted at this site on July 6, 2011.

Please feel free to contact the undersigned if you have any questions or comments regarding this report.

Sincerely,
ENVIRONMENTAL ALLIANCE, INC.
Christopher Thoeny, P.G. (PA #PG004864)
Project Geologist

Enclosure

c: Fiona Livingston – Sunoco, Inc. (R&M)
Yvonne Monti – Sunoco, Inc. (R&M)
ICF International – T. Aubel (Claim #06-186)
Goodman Properties - Phil Gray – Phoenix GeoEnvironmental, LLC
Rick Smith – East Goshen Township

J:\EAI_files\PCG\Sun\2199_Paoli Pike\RAPR's\3Q11 RAPR\3Q11 RAPR 2199.doc

5341 Limestone Road Wilmington, DE 19808
302-234-4400 302-234-1535 Fax www.envalliance.com

Remedial Action Progress Report
Third Quarter 2011

Sunoco Station # 0004-7969
1425 Paoli Pike
West Chester, PA

General Information

Sunoco Remediation Associate:Fiona Livingston
Consultant:Environmental Alliance, Inc. (Alliance)
5341 Limestone Road
Wilmington, DE 19808
EAI Program Manager:Joe Rossi
EAI Project Manager:Tom Murphy
PADEP Case Manager:Lauren Mapleton – PADEP Southeast Regional Office
PADEP Facility ID#:15-20353
County:Chester
Municipality:East Goshen Township

SITE OVERVIEW

  • The site is an active retail gasoline station and A-Plus convenience store.

SITE HISTORY

  • In July of 1989, Sunoco retained Groundwater and Environmental Services, Inc. (GES) to conduct a hydrogeologic investigation upon the acquisition of the Site. GES installed 4 monitoring wells along with collecting soil samples and an initial groundwater sampling event. Analytical results indicated the presence of total BTEX and total petroleum hydrocarbons (TPH) in the two samples that were located nearest the underground storage tank (UST) field.
  • In the fall of 1989, Sunoco upgraded the UST system onsite. Upgrade activities included: the removal of four 4,000 gallon steel USTs which were replaced with three 10,000 gallon fiberglass USTs and the removal of two 550 gallon heating and waste oil tanks that were replaced with two 275 gallon aboveground storage tanks (ASTs).
  • In December 1992 and January 1993, Sunoco completed service station upgrades, which included the abandonment of the on-site water supply well.
  • In January 1995, the Pennsylvania Department of Environmental Resources (PADER) issued a letter in which no further investigative activities were deemed necessary. Subsequently, all monitoring wells were abandoned by B. L. Myers on January 27, 1995.
  • In October 2006, Sunoco upgraded the dispensers and product piping at the Site. During upgrade activities contamination was detected beneath one of the dispensers and was confirmed through a grab soil sample. Benzene was detected above Pennsylvania

Page 1

ENVIRONMENTAL ALLIANCE

Department of Environmental Protection (PADEP) statewide health standard (SHS) and a notice of release (NOR) was submitted to the PADEP by EAI on October 16, 2006.

  • On January 17 th and 18 th , 2007, EAI conducted soil borings and the installation of four monitoring wells. The monitoring wells were sampled on February 6 th and April 25 th , 2007.
  • In August 2007, EAI submitted a Site Characterization Report (SCR) to the PADEP. The SCR was disapproved based on further site characterization being needed.
  • On September 19 th and 20 th , 2007, EAI installed an additional four monitoring wells to help further delineate any potential migration of contaminants of concern.
  • In accordance with a letter from the PADEP dated March 3, 2008 EAI conducted an extensive well search, in which no drinking wells were identified between the Site and the closest down-gradient sensitive receptor, Ridley Creek.
  • On September 3, 2008, EAI installed two offsite monitoring wells and one onsite monitoring well. The offsite wells (MW-9 and MW-10) were installed for further horizontal delineation of potential contaminants of concern. The onsite well (MW-7B) was installed for vertical delineation of potential contaminants of concern.
  • In December 2008, a slug test was performed on monitoring well MW-7B to calculate the hydraulic conductivity of the bedrock aquifer beneath the site.
  • On May 27 th and 28 th , 2009 EAI installed three offsite deep monitoring wells (MW-9B, MW-10B, and MW-11B) and two onsite deep monitoring wells (MW-2B and MW-8B).
  • On November 3 rd through 5 th , 2009 EAI installed three offsite monitoring wells (MW-12 through 14) and four offsite deep monitoring wells (MW-5B, MW-12B, MW-13B, and MW-14B).
  • On November 9, 2009, Alliance submitted a Status Report for Site Characterization to the PADEP.
  • On February 1, 2010, Alliance submitted a Site Characterization Report (SCR) to the PADEP selecting the Site Specific Standard (SSS) as the clean up standard for the site. The SCR was approved by the PADEP in a letter dated April 21, 2010.
  • On June 10, 2010, Alliance submitted a Remedial Action Plan (RAP) to the PADEP in which a groundwater pump and treat remediation system was selected as the remedial strategy for the site. The RAP was approved by the PADEP in a letter dated July 21, 2010.
  • Start up/shake down procedures for the groundwater remediation system were initiated on June 15, 2010. The permanent operation date for the groundwater remediation system is June 28, 2010.

SITE INFORMATION

Well Specifications: Fourteen 2-inch diameter shallow monitoring wells (MW-1 through MW-14); Eight 2-inch diameter deep wells (MW-2B, MW-5B, MW-9B, MW-10B, MW-11B, MW-12B, MW-13B, & MW-14B); Two 6-inch diameter deep wells (MW-7B, & MW-8B)
Geology: Soils consist of greenish gray and orange clay and micaceous silt underlain by Precambrian age, medium grained felsic gneiss. Depth to bedrock reported during

Page 2

ENVIRONMENTAL ALLIANCE

drilling ranged from 20-feet (MW-14B) to 48-feet (MW-8B). Bedrock is gradationally overlain by a thick mantle of saprolite identified in most borings.
Groundwater Elevation: From July 6 2011:
Shallow – 82.68 feet (MW-12 and MW-8) to 74.62 feet (MW-14)
Deep – 83.22 feet (MW-5B) to 74.57 feet (MW-14B)
Hydraulic Gradient: From April 2010 (last sampling event under non-pumping conditions):
Shallow - 0.014 feet per foot to the northeast
Deep - 0.018 feet per foot to the northeast
Hydraulic Conductivity: 4.75 feet per day (shallow); 1.75 feet per day (deep)
Groundwater Sampling Frequency: Quarterly
Analytical Method: Benzene, Toluene, Ethylbenzene, Total Xylenes (BTEX), Methyl tertiary-butyl ether (MTBE), Isopropylbenzene, Naphthalene via Environmental Protection Agency (EPA) Method 8260B.
Soil Quality: Soil quality data from October 2006 dispenser sampling indicated Benzene above SHS at sample Disp/Line 2. Soil quality data from well installation in January 2007, indicated MTBE above SHS at MW-3 (11-12 feet).
Separate-Phase Hydrocarbons: Separate-phase hydrocarbons (SPH) have never been detected in the site monitoring wells.

RISK ASSESSMENT

Potentially Sensitive Receptors: There are 34 known wells identified by the Environmental Data Resources Inc. radius report (utilizing the Federal and Pennsylvania well databases) within a 0.5-mile radius. The East Branch of Ridley Creek lies approximately 900 feet northeast of the site.
Closest Known Well: One Federal Public Supply well was identified within a one-half mile radius to the east of the site.
Municipal Water Supply: Aqua Pennsylvania, Inc.

SITE ACTIVITIES THIS REPORTING PERIOD

  • Liquid-level data and groundwater quality samples were collected from thirteen shallow monitoring wells (MW- 1 through MW-5 and MW-7 through MW-14) and ten deep monitoring wells (MW-2B, MW-5B, and MW-7B through MW-14B) on July 6, 2011. A map depicting groundwater elevation and analytical data for the shallow (overburden) and deep (shallow bedrock) monitoring wells are included as Figures 1 and 2, respectively. Historical groundwater elevation and analytical data is summarized in Table 1. A copy of the laboratory results is included in Appendix A.

Page 3

ENVIRONMENTAL ALLIANCE

  • System operations and maintenance (O&M) visits were performed throughout the reporting period. Historical dissolved-phase hydrocarbon recovery data is summarized in Table 2. Groundwater system performance graphs are included as Appendix B.
  • System sampling was conducted in accordance with the National Pollutant Discharge Elimination System (NPDES) Permit for the Site. The system sampling analytical data is summarized in Table 3. Laboratory analytical reports from the system sampling are included as Appendix C.

REMEDIATION SYSTEM INFORMATION

  • Type of System: Groundwater Pump and Treat System
  • Permanent Operation Dates: June 28, 2010 to present
  • Extraction Points: MW-1, MW-2, and MW-7B.
  • Extraction Points Utilized: MW-7B.
  • Recovery Equipment: Grundfos ES-7 Electric Submersible Pump
  • Liquid-Phase Treatment Equipment: GeoTech Lo-Profile Air Stripper, (2) 200 lb. liquid granular activated carbon (LGAC) vessels
  • Groundwater Discharge Location: Storm Sewer
  • Gallons pumped and treated this Reporting Period: 266,356
  • Average Groundwater Recovery Rate this Reporting Period: 2.01 GPM
  • Total Dissolved-Phase MTBE Recovered to Date: 64.84 pounds

FUTURE SITE ACTIVITIES

  • Quarterly groundwater monitoring and sampling will continue with a sampling event scheduled in October 2011.
  • Continue to operate the groundwater pump and treat remediation system with regularly scheduled O&M visits.
  • Weekly O&M visits will continue to maintain system operational efficiency and prevent fouling of transfer pumps and other mineral scaling issues.
  • Continue to collect bi-monthly system samples and submit monthly Discharge Monitoring Reports (DMR) in accordance with the NPDES Permit.

ATTACHMENTS

Figure 1Groundwater Analytical and Gradient Map - Overburden (Shallow) Wells July 6, 2011
Figure 2Groundwater Analytical and Gradient Map - Shallow Bedrock (Deep) Wells July 6, 2011
Table 1Groundwater Elevation Data and Analytical Summary
Table 2Dissolved Phase Hydrocarbon Recovery Data
Table 3System Analytical Summary
Appendix AGroundwater Sampling Laboratory Analytical Reports
Appendix BGroundwater System Performance Graphs
Appendix CSystem Sampling Laboratory Analytical Reports

Page 4

ENVIRONMENTAL ALLIANCE

TABLE 1
GROUNDWATER ELEVATION DATA AND ANALYTICAL SUMMARY
SUNOCO STATION #0004-7969
PAOLI PIKE
WEST CHESTER, PA
Well Date Depth to Water Depth to Product Water Elevation Constituents of Concern (ug/l)
Benzene Toluene Ethyl-benzene Xylenes MTBE Isopropyl-benzene Naph-thalene
PA Act 2 UA ≤2500 TDS NR 5 1,000 700 10,000 20 3,500 100
MW-1
TOC
100.20
02/06/07 17.64 -- 82.56 < 1 < 1 < 1 < 1 1,300 < 2 < 4
04/25/07 15.92 -- 84.28 < 1 < 1 < 1 < 1 1,800 < 2 < 4
08/22/07 18.50 -- 81.70 < 1 < 1 < 1 < 1 880 < 2 < 4
10/18/07 20.02 -- 80.18 < 1 < 1 < 1 < 1 500 < 2 < 4
01/02/08 18.85 -- 81.35 < 1 < 1 < 1 < 1 1,000 < 2 < 4
04/09/08 17.09 -- 83.11 < 1 < 1 < 1 < 1 1,700 < 2 < 4
07/28/08 19.30 -- 80.90 < 1 < 1 < 1 < 1 2,000 < 2 < 4
10/06/08 20.59 -- 79.61 < 1 < 1 < 1 < 1 3,600 < 2 < 4
01/06/09 19.23 -- 80.97 < 2 < 2 < 2 < 2 4,900 < 4 < 8
04/02/09 19.83 -- 80.37 < 2 < 2 < 2 < 2 3,700 < 4 < 8
100.20 06/12/09 18.33 -- 81.87 -- -- -- -- -- -- --
07/02/09 18.08 -- 82.12 < 1 < 1 < 1 < 1 8,000 < 2 < 4
10/06/09 19.04 -- 81.16 < 5 < 5 < 5 < 5 7,900 < 10 < 20
11/20/09 18.09 -- 82.11 -- -- -- -- -- -- --
12/08/09 18.04 -- 82.16 -- -- -- -- -- -- --
01/20/10 17.02 -- 83.18 < 2 < 2 < 2 < 2 6,600 < 4 < 8
04/22/10 14.74 -- 85.46 < 1 < 1 < 1 < 1 3,000 < 2 < 4
07/27/10 17.92 -- 82.28 < 1 < 1 < 1 < 1 160 < 2 < 4
10/07/10 19.78 -- 80.42 < 1 < 1 < 1 < 1 81 < 2 < 4
01/06/11 19.02 -- 81.18 < 1 < 1 < 1 < 1 81 < 2 < 4
04/13/11 16.93 -- 83.27 < 1 < 1 < 1 < 1 34 < 2 < 4
07/06/11 18.03 -- 82.17 < 1 < 1 < 1 < 1 37 < 2 < 4

ENVIRONMENTAL ALLIANCE

TABLE 1
GROUNDWATER ELEVATION DATA AND ANALYTICAL SUMMARY
SUNOCO STATION #0004-7969
PAOLI PIKE
WEST CHESTER, PA
Well Date Depth to Water Depth to Product Water Elevation Constituents of Concern (ug/l)
Benzene Toluene Ethyl-benzene Xylenes MTBE Isopropyl-benzene Naph-thalene
PA Act 2 UA ≤2500 TDS NR 5 1,000 700 10,000 20 3,500 100
MW-4
TOC
99.77
02/06/07 17.00 -- 82.77 < 2 < 2 < 2 < 2 12,000 < 4 < 8
04/25/07 15.22 -- 84.55 < 1 < 1 < 1 < 1 2,500 < 2 < 4
08/22/07 17.44 -- 82.33 < 2 < 2 < 2 < 2 6,200 < 4 < 8
10/18/07 19.45 -- 80.32 < 1 < 1 < 1 < 1 5,600 < 2 < 4
01/02/08 17.83 -- 81.94 < 1 < 1 < 1 < 1 2,900 < 2 < 4
04/09/08 14.94 -- 84.83 3 < 1 < 1 < 1 240 < 2 < 4
07/28/08 18.49 -- 81.28 < 1 < 1 < 1 < 1 1,400 < 2 < 4
10/06/08 19.86 -- 79.91 < 1 < 1 < 1 < 1 1,200 < 2 < 4
01/06/09 18.54 -- 81.23 < 1 < 1 < 1 < 1 1,200 < 2 < 4
TOC*
99.66
04/02/09 19.10 -- 80.67 < 1 < 1 < 1 < 1 900 < 2 < 4
06/12/09 12.36 -- 87.30 -- -- -- -- -- -- --
07/02/09 17.34 -- 82.32 < 1 < 1 < 1 < 1 290 < 2 < 4
10/06/09 16.94 -- 82.72 < 1 < 1 < 1 < 1 99 < 2 < 4
11/20/09 17.34 -- 82.32 -- -- -- -- -- -- --
12/08/09 17.16 -- 82.50 -- -- -- -- -- -- --
01/20/10 16.32 -- 83.34 < 1 < 1 < 1 < 1 220 < 2 < 4
04/22/10 14.23 -- 85.43 < 1 < 1 < 1 < 1 31 < 2 < 4
07/27/10 16.76 -- 82.90 < 1 < 1 < 1 < 1 25 < 2 < 4
10/07/10 18.11 -- 81.55 < 1 < 1 < 1 < 1 88 < 2 < 4
01/06/11 18.29 -- 81.37 < 1 < 1 < 1 < 1 41 < 2 < 4
04/13/11 15.81 -- 83.85 < 1 < 1 < 1 < 1 30 < 2 < 4
07/06/11 17.29 -- 82.37 < 1 < 1 < 1 < 1 2 < 2 < 4

Page 5 of 16

ENVIRONMENTAL ALLIANCE

TABLE 1
GROUNDWATER ELEVATION DATA AND ANALYTICAL SUMMARY
SUNOCO STATION #0004-7969
PAOLI PIKE
WEST CHESTER, PA
Well Date Depth to Water Depth to Product Water Elevation Constituents of Concern (ug/l)
Benzene Toluene Ethyl-benzene Xylenes MTBE Isopropyl-benzene Naph-thalene
PA Act 2 UA ≤2500 TDS NR 5 1,000 700 10,000 20 3,500 100
MW-7
TOC
99.27
10/18/07 19.35 -- 79.92 < 1 < 1 < 1 < 1 130 < 2 < 4
01/02/08 18.09 -- 81.18 < 1 < 1 < 1 < 1 3,100 < 2 < 4
03/14/08 16.47 -- 82.80 < 2 < 2 < 2 < 2 8,100 < 4 < 8
04/09/08 17.2 -- 82.07 < 5 < 5 < 5 < 5 8,300 < 10 < 20
07/28/08 18.56 -- 80.71 < 1 < 1 < 1 < 1 2,000 < 2 < 4
10/06/08 19.83 -- 79.44 < 1 < 1 < 1 < 1 2,100 < 2 < 4
01/06/09 18.37 -- 80.90 < 2 < 2 < 2 < 2 5,300 < 4 < 8
TOC*
99.27
04/02/09 19.02 -- 80.25 < 2 < 2 < 2 < 2 2,700 < 4 < 8
06/12/09 17.46 -- 81.81 -- -- -- -- -- -- --
07/02/09 17.24 -- 82.03 < 1 < 1 < 1 < 1 3,800 < 2 < 4
10/06/09 18.22 -- 81.05 < 1 < 1 < 1 < 1 1,700 < 2 < 4
11/20/09 17.26 -- 82.01 -- -- -- -- -- -- --
12/08/09 17.19 -- 82.08 -- -- -- -- -- -- --
01/20/10 16.02 -- 83.25 < 1 < 1 < 1 < 1 480 < 2 < 4
04/22/10 13.96 -- 85.31 < 1 < 1 < 1 < 1 1 < 2 < 4
07/27/10 19.27 -- 80.00 < 1 < 1 < 1 < 1 < 1 < 2 < 4
10/07/10 22.92 -- 76.35 < 1 < 1 < 1 < 1 34 < 2 < 4
01/06/11 18.24 -- 81.03 < 1 < 1 < 1 < 1 170 < 2 < 4
04/13/11 18.39 -- 80.88 < 1 < 1 < 1 < 1 45 < 2 < 4
07/06/11 19.38 -- 79.89 < 1 < 1 < 1 < 1 1 < 2 < 4

Page 8 of 16

ENVIRONMENTAL ALLIANCE

TABLE 1
GROUNDWATER ELEVATION DATA AND ANALYTICAL SUMMARY
SUNOCO STATION #0004-7969
PAOLI PIKE
WEST CHESTER, PA
Well Date Depth to Water Depth to Product Water Elevation Constituents of Concern (ug/l)
Benzene Toluene Ethyl-benzene Xylenes MTBE Isopropyl-benzene Naph-thalene
PA Act 2 UA ≤2500 TDS NR 5 1,000 700 10,000 20 3,500 100
MW-7B
TOC
99.14
TOC*
99.09
09/22/08 19.61 -- 79.53 < 50 < 50 < 50 < 50 63,000 < 100 < 200
10/06/08 19.70 -- 79.44 < 10 < 10 < 10 < 10 52,000 < 20 < 40
01/06/09 18.22 -- 80.92 < 10 < 10 < 10 < 10 62,000 < 20 < 40
04/02/09 18.88 -- 80.26 < 20 < 20 < 20 < 20 47,000 < 40 < 80
06/12/09 17.42 -- 81.67 -- -- -- -- -- -- --
07/02/09 17.10 -- 81.99 < 10 < 10 < 10 < 10 54,000 < 20 < 40
10/06/09 18.07 -- 81.02 < 5 < 5 7 < 5 33,000 < 10 < 20
11/20/09 17.11 -- 81.98 -- -- -- -- -- -- --
12/08/09 17.03 -- 82.06 -- -- -- -- -- -- --
01/20/10 16.09 -- 83.00 < 10 < 10 < 10 < 10 23,000 < 20 < 40
04/22/10 13.28 -- 85.81 < 10 32 < 10 29 15,000 < 20 < 40
07/27/10 25.75 -- 73.34 < 5 < 5 < 5 < 5 11,000 < 10 < 20
10/07/10 32.26 -- 66.83 < 5 < 5 < 5 < 5 8,400 < 10 < 20
01/07/11 17.55 -- 81.54 < 5 < 5 < 5 < 5 9,000 < 10 < 20
04/13/11 25.02 -- 74.07 < 3 < 3 < 3 < 3 7,700 < 5 < 10
07/06/11 25.88 -- 73.21 < 4 < 4 < 4 < 4 8,400 < 8 < 16

ENVIRONMENTAL ALLIANCE

TABLE 1
GROUNDWATER ELEVATION DATA AND ANALYTICAL SUMMARY
SUNOCO STATION #0004-7969
PAOLI PIKE
WEST CHESTER, PA
Well Date Depth to Water Depth to Product Water Elevation Constituents of Concern (ug/l)
Benzene Toluene Ethyl-benzene Xylenes MTBE Isopropyl-benzene Naph-thalene
PA Act 2 UA ≤2500 TDS NR 5 1,000 700 10,000 20 3,500 100
MW-11
TOC*
100.22
06/12/09 20.34 -- 79.88 < 1 < 1 < 1 < 1 1,100 < 2 < 4
07/02/09 20.19 -- 80.03 < 1 < 1 < 1 < 1 350 < 2 < 4
10/06/09 20.74 -- 79.48 < 1 < 1 < 1 < 1 170 < 2 < 4
11/20/09 19.89 -- 80.33 -- -- -- -- -- -- --
12/08/09 19.95 -- 80.27 -- -- -- -- -- -- --
01/20/10 19.94 -- 80.28 < 1 < 1 < 1 < 1 140 < 2 < 4
04/22/10 17.14 -- 83.08 < 1 < 1 < 1 < 1 22 < 2 < 4
07/27/10 19.32 -- 80.90 < 1 < 1 < 1 < 1 160 < 2 < 4
10/07/10 21.59 -- 78.63 < 1 < 1 < 1 < 1 380 < 2 < 4
01/06/11 20.75 -- 79.47 < 1 < 1 < 1 < 1 55 < 2 < 4
04/13/11 18.55 -- 81.67 < 1 < 1 < 1 < 1 30 < 2 < 4
07/06/11 20.14 -- 80.08 < 1 < 1 < 1 < 1 120 < 2 < 4
MW-11B
TOC*
100.51
06/12/09 20.55 -- 79.96 < 2 < 2 < 2 < 2 4,400 < 4 < 8
07/02/09 19.94 -- 80.57 < 1 < 1 < 1 < 1 4,700 < 2 < 4
10/06/09 21.02 -- 79.49 < 1 < 1 < 1 < 1 890 < 2 < 4
11/20/09 20.17 -- 80.34 -- -- -- -- -- -- --
12/08/09 20.22 -- 80.29 -- -- -- -- -- -- --
01/20/10 19.21 -- 81.30 < 1 < 1 < 1 < 1 780 < 2 < 4
04/22/10 16.79 -- 83.72 < 1 < 1 < 1 < 1 470 < 2 < 4
07/27/10 19.56 -- 80.95 < 1 < 1 < 1 < 1 440 < 2 < 4
10/07/10 21.85 -- 78.66 < 1 < 1 < 1 < 1 450 < 2 < 4
01/06/11 21.01 -- 79.50 < 1 < 1 < 1 < 1 610 < 2 < 4
04/13/11 18.82 -- 81.69 < 1 < 1 < 1 < 1 430 < 2 < 4
07/06/11 20.41 -- 80.10 < 2 < 2 < 2 < 2 3,100 < 4 < 8

ENVIRONMENTAL ALLIANCE