Municipal Authority
The East Goshen Municipal Authority will acquire, hold, construct, improve, maintain, operate, own and lease, either in the capacity of lessor or leasee, sewers, sewer systems or parts thereof, sewage treatment works, including works for treating and disposing of industrial waste, for the Township of East Goshen and other such territory as it may be authorized to serve in a fiscally responsible and environmentally safe manner.
The Municipal Authority is an appointed board which functions independently of the others. The Municipal Authority owns the Township sewer system and is responsible for providing sewers to those areas deemed necessary by the Board of Supervisors.
- Five members, serving five-year terms
- Meetings are on the 2nd Monday of the month at 7:00 P.M.
- All township meetings are held at the Township Building and open to the public
| Authority Members | Term Expiration Date |
| Kevin Cummings, Chairman | 2026 |
| John Stipe, Vice Chairman |
2029 |
| Dana Pizzarro, Secretary | 2026 |
| Sean Ellsworth, Assistant Secretary/Treasurer | 2028 |
| Walter Wujcik, Treasurer | 2028 |
| Pennoni Associates, Engineer | |
| Patrick M. McKenna, Esq. | |
| Peter Hicks, BoS Liaison | |
| Kevin Miller, Staff Liaison |
Documents
Back to the list | Open the original PDF
Notice: this accessible version was created automatically from the original document. The transcription may not be 100% accurate. It is provided for searching and for screen readers; please refer to the original document for the official version.
Lynn Werkheiser
From: Michael Ellis <MEllis@Pennoni.com>
Sent: Friday, August 8, 2025 12:06 AM
To: Mark Miller; Ridley STP Lab; Lynn Werkheiser
Cc: Haley Zuritsky; Erika Addison; John Rengepis; Nathan M. Cline
Subject: RCSTP Arc Flash Study Report - FINAL
Attachments: EGMAU25005 - RCSTP SC-Coord-AF Study.pdf
Hi All,
We met virtually with Lenni Electric to discuss their review of the draft Arc Flash report. We made a few minor updates thereafter, and the final signed & sealed report is attached. This can be provided to the MA for Monday’s packet for their reference.
The recommendations remain the same as in the draft report. It is our understanding that Lenni has already implemented the recommendations and that updated labels have already been installed. If so, no further action is needed at this time regarding this study.
Mark – The actual effort to complete the study was more than we had initially scoped, and I would like to respectfully request supplemental funding for a portion of that additional effort. There were at least 15 breakers in the MCC that were not clearly visible even when the panels were opened. Additional effort was needed to research the specific breakers manufacturer, model number, AIC ratings, etc. via internet searches. Project submittals were vetted to verify the model(s) was accurate, and the arc flash computer model had to be iteratively updated as a result. Our proposal was based on an assumption that “all equipment are clearly labeled and that all equipment ratings are readily visible without opening panels. Effort is not included to research equipment ratings via internet searches or other means. Should research be required, additional effort will be billed in accordance with Pennoni’s rate schedule.” We are tracking well under budget on our 2025 General Service task order so we would like to discuss if the portion of supplemental effort on this project can be applied against a portion of the remaining General Services budget. I will call to discuss the effort and feasibility of this request in more detail.
Thanks!
Mike
Michael Ellis, PE
Municipal Division Manager
Pennoni
Christiana Executive Campus, 121 Continental Drive, Suite 207 | Newark, DE 19713
Direct: +1 302-351-5236 | Mobile: +1 302-561-4235
www.pennoni.com | MEllis@Pennoni.com
From: Erika Addison <eaddison@Pennoni.com>
Sent: Thursday, May 29, 2025 3:21 PM
To: Mark Miller (mmiller@eastgoshen.org) <mmiller@eastgoshen.org>; Ridley STP Lab <ridley2@eastgoshen.org>
Cc: Michael Ellis <MEllis@Pennoni.com>; Haley Zuritsky <HZuritsky@Pennoni.com>
Subject: RCSTP Arc Flash Study Report
Importance: High
Good afternoon,
1
Please see the attached draft of the arc flash study report for the RCSTP. In short, we are recommending the replacement of a few breakers in panels MCC-1 and CBH and the replacement of a couple of arc flash labels.
Would you be available sometime next week to have a short call with us to finalize this draft report and to discuss any questions you may have? We would like to have the report finalized before the next municipal authority meeting.
Thanks,
Erika
Erika Addison, PE
Pennoni
Christiana Executive Campus, 121 Continental Drive, Suite 207 | Newark, DE 19713
Direct: +1 302-351-5263
www.pennoni.com | eaddison@Pennoni.com
[Logo: "The What's Possible Podcast" icon featuring a hardhat and microphone]
What's Possible Podcast Episode 1
2
Ridley Creek Sewage Treatment Plant (RCSTP) Protective Device Coordination & Arc Flash Study
West Chester, PA
Submitted To:
East Goshen Municipal Authority
Mark Miller, Public Works Director
1580 Paoli Pike
West Chester, PA 19380
[Seal: Commonwealth of Pennsylvania Registered Professional Engineer John P. Rengepis, No. PE077024]
John P. Rengepis
John Rengepis, PE
Senior Electrical Engineer
Professional Engineer: Pennsylvania – No. PE077024
Haley Zuritsky
Associate Electrical Engineer
Arc Flash Report
EGMAU25005
July 22, 2025
Pennoni
U:\Accounts\EGMAU\EGMAU25005 - RCSTP Arc Flash Study\DOCUMENTS\Arc Flash Report\EGMAU25005 - RCSTP SC-Coord-AF Study.docx
TABLE OF CONTENTS
| Executive Summary | 1 |
|---|---|
| Introduction | 1 |
| Input Data | 2 |
| Information Gathering | 2 |
| Utility Electric Service | 2 |
| Generator Contribution | 3 |
| Feeders | 3 |
| Transformers | 3 |
| Short Circuit Study | 3 |
| Short Circuit Analysis Basics | 3 |
| Motor Contribution to Short Circuit Current | 4 |
| Calculation Results and Conclusion | 4 |
| Coordination Study | 5 |
| Overcurrent Device Coordination Basics | 5 |
| Molded Case Circuit Breakers (MCCBs) | 5 |
| Transformer Protection | 6 |
| Generator Protection | 6 |
| Overcurrent Device Coordination Results and Analysis | 6 |
| Arc Flash Study | 7 |
| Arc Flash Risk Assessment Calculation Method | 7 |
| Scenarios | 7 |
| Arc Flash Risk Assessment Results | 7 |
| Conclusion | 8 |
| Table 1: NFPA 70E-2018 Table 130.7(C)(15)(c) | 9 |
| Appendices | 11 |
| Appendix A: Input Data | 11 |
| Appendix B: One Line Diagram | 16 |
| Appendix C: Short Circuit One-Line Results | 18 |
| Appendix D: Equipment Duty Scenario Comparison Report | 22 |
| Appendix E: Time-Current Curves of Selected Protective Device Coordination | 27 |
| Appendix F: Arc Flash Hazard Scenario Comparison Report | 33 |
| Appendix G: Arc Flash One-Line Results | 40 |
| Appendix H: Arc Flash Sample Labels | 44 |
| Appendix I: Utility, Transformer, & Generator Information | 47 |
Executive Summary
Pennoni has been contracted to perform an Arc Flash Study of the updated electrical system for the Ridley Creek Sewage Treatment Plant in West Chester, PA. The system underwent updates since the last arc flash study done in 2011. These changes include replacing the existing 400KW “Generator 1” with a new 450KW generator, transferring panel CBH to be fed by “Generator 1.
This report includes a short circuit study, an overcurrent protection device coordination study, and an arc flash study. All studies were performed using Easypower software version 11.0 for Windows.
Input data used in this study were obtained from vendor cutsheets, design drawings, and site visit observations and photos. Short circuit, HV fuse, and utility transformer data were provided by the utility.
Protective devices within the electrical equipment and power systems have (SCCR) Short-Circuit- Current-Ratings, which are the maximum short-circuit current the equipment can withstand (without being damaged) and/or (AIC) Available-Interrupting-Current ratings which are the maximum short circuit amps the protection devices can safely interrupt. The unit of measurement, Amps RMS Symmetrical, is the same for SCCR and AIC ratings. A short-circuit study is performed to calculate the maximum short-circuit current possible at each point of interest in an electrical system. A comparison is then made between the calculated short-circuit current and the short-circuit ratings of the equipment and the interrupting capacity of each protective device, to determine if the electrical equipment can safely withstand the available short-circuit current and if the protective device can safely interrupt the short-circuit current, that would be present at that point (node) in the electrical distribution system. A properly coordinated system is one in which all components are adequately protected, and a minimum number of protective devices will operate to safely isolate a fault condition, and to minimize the interruption of service to the rest of the system.
Electrical system changes within the facility or in the utility system can have a significant impact on the results of this power system analysis. To account for this, three different scenarios were analyzed: (1) The system operating at full utility calculated short circuit levels, (2) the system operating at 50% utility short circuit current, and (3) The system operating at the generator short circuit current. Utility short circuit contribution was received from the Philadelphia Electric Company (PECO) as shown in Appendix I.
The short circuit study evaluates the adequacy of the Fully Rated electrical distribution equipment illustrated in the electrical one-line diagram. The study determines the maximum available short-circuit current at each bus location.
The coordination study evaluates the protective device current settings against all other “upstream” devices so that a system outage, caused by an overcurrent event, is limited in effecting as little of the electrical infrastructure as possible. This is accomplished by coordinating breaker settings so that lower “stream” devices (affecting smaller branches of the electrical system) trip before upstream devices. This process is referred to as selective coordination.
The arc flash study establishes the flash protection boundary around electrical equipment within which a worker exposed to an arcing fault may expect to receive injury if not adequately protected. The analysis determines the incident energy levels at specific working distances from the equipment, which is then used to select the appropriate personal protective equipment (PPE) to be worn when working within the flash protection boundary. Please note however, that high incident energy conditions present in a particular location in the gear may not have a “PPE” solution and must be turned off prior to being accessed and /or worked upon. Arc flash labels are provided in the report.
Introduction
The Ridley Creek Sewage Treatment Plant has undergone changes to its existing electrical infrastructure since a previous study was conducted in 2011. These changes include replacing the existing 400KW “Generator 1” with a new 450KW generator, transferring panel CBH to be fed by “Generator 1”.
This report includes a short circuit study, an overcurrent protection device coordination study, and an arc flash study. Each study was performed using EasyPower's analysis focuses (modules) and are to verify the
1
adequacy of electrical equipment ratings, protective device coordination within various levels of the electrical distribution systems, and arc flash hazards. The studies cover the facility's power distribution system from its point of connection to the utility service and generator through the system down to the panelboard and motor level.
Input data used in this study were obtained from vendor cutsheets, design drawings, and site visit observations and photos. Short circuits, HV fuse, and utility transformer data were provided by the utility.
To complete this study, the following scenarios were considered:
- System operating at 100% Utility Short Circuit Current
- System operating at 50% Utility Short Circuit Current
- System operating on Generator Short Circuit Current
The worst-case scenarios were then used to determine the analysis presented in the report.
This report is sub-divided into the following sections:
- Executive Summary
- Introduction
- System Description
- Short-Circuit Study: Description of all standards and procedures used in calculating short-circuit currents for the facility
- Coordination Study: Includes standards and procedures used in evaluating system coordination, also included are the suggested protective device settings for the adjustable protective devices and plots of time-current curves
- Arc Flash Study: Include standards and procedures used in evaluating the arc flash energy levels for the equipment throughout the facility. A tabulation of incident energy, recommended working distance and personnel protective equipment (PPE) is also provided, as well as equipment warning labels
- Appendixes: Contain EASYPOWER input data, various simulation reports and single line power riser models. This section contains material that could not easily be included within the body of the written document. Appendix A: Input Data; Appendix B: Original one-line diagram and EasyPower one-line diagram; Appendix C: Short circuit one-line diagram; Appendix D: Equipment duty scenario comparison report; Appendix E: Time-current curves of selected protective device coordination; Appendix F: Arc flash hazard scenario comparison report; Appendix G: Arc flash one-line diagram; Appendix H: Arc flash sample labels; Appendix I: Utility provided Short Circuit, Fuse, and Transformer information at the point of service
(The short circuit one-line diagram, arc flash one-line diagram, and arc flash report sections are further divided by 100% of the utility fault current, 50% of the utility fault current, and generator fault current.)
Input Data
Information Gathering
The system model was created from design drawings, submittals, and site visit photos. All input data is documented in Appendix A of this report.
Utility Electric Service
2
The incoming service for the electrical distribution system for the RCSTP is provided by PECO. The 480Y/277V service is fed from a utility 1000KVA, 33000Y/19052V - 480Y/277V Y-Y pad-mounted transformer with 5.72% impedance and protected by three (3) upstream S&C Co. SMU-20 80E fuses. The 3-phase fault is 2,215A with X/R = 5.3, and the 1 phase fault current is 1,639A with X/R = 4.4.
Generator Contribution
Two generators are used to provide auxiliary power to RCSTP. Generator 1 is 450kW/562.5kVA and provides standby power to MCC-1, MCC-2, and panel CBH. Generator 2 is 500kW/625kVA and provides standby power to MCC-3. Both generators are 480V, 3ph, 1800 RPM, Diesel, and are installed adjacent to the existing exterior MDP switchboard.
Feeders
All major feeders within the system have been included in the model. The input data includes conductor size (AWG/kcmil) and type (aluminum or copper), number of conductors per phase, conduit material (magnetic or non-magnetic), and length. From this data, conductor impedance is calculated utilizing IEEE 242 (Recommended Practice for Electrical Power Distribution and Coordination of Industrial and Commercial Power Systems).
When feeder lengths were not provided by others verified field efforts, the lengths were estimated from building plans, assuming that overhead conduit runs are parallel and perpendicular to building structure and underground conduit runs are straight. When conductor sizes were not provided and could not be field verified, conductor sizes were assumed based on NEC table 301.16. In this case it is assumed that the feeders are properly sized based on the size of the upstream overcurrent device.
Transformers
All three-phase transformers within the system have been included in the system model. Ratings for each transformer include kVA, primary and secondary voltages, winding configurations, percent impedance (%Z) and X/R ratio. Typical X/R ratios were assumed for small try-type transformers. In some cases, percent impedance values were assumed when actual data was not available.
Short Circuit Study
Short Circuit Analysis Basics
A short circuit analysis is the fundamental portion of any power system study. In order to perform subsequent analysis, such as load flow, overcurrent device coordination, or arc flash hazard analysis, the power system must be modeled in its entirety and short circuit values must be calculated at all major buses within the distribution system.
A short circuit analysis is utilized for the following purposes:
- Low-Voltage Overcurrent Device Interrupting Rating (AIC) Evaluation – determine the adequacy of low-voltage overcurrent devices (such as circuit breakers, fuses, etc.) by comparing the calculated short circuit duty to the device's interrupting rating (AIC rating).
- Withstanding Rating (Short Circuit Current Rating) Evaluation – determine the adequacy of electrical components with are not capable of interrupting fault current (such as equipment bussing, transfer switches, non-fused disconnect switches, etc.) by comparing the calculated short circuit duty to the components withstand rating or SCCR (Short Circuit Current Rating).
- Time-Current Curve (TCC) Cut-Off Points – each overcurrent device's time-current curve ends at the maximum available short circuit current at the device's terminals. The cutoff point aids in coordination of overcurrent devices.
- Arc Flash Bolted Fault Current – in order to calculate the arc flash incident energy levels, the bolted fault current at each bus must be calculated.
The short circuit analysis was completed utilizing the Short Circuit module of EasyPower. The calculation procedures are based on recommendations included in ANSI standards C37.13, C37.010, and C37.5. The
3
program calculates the maximum available three-phase and single line-to-ground fault current without any reduction due to current-limiting overcurrent devices which may be present. The calculated short circuit values are RMS symmetrical amperes and are comparable with the RMS symmetrical short circuit ratings of electrical equipment.
Electrical distribution equipment must be able to withstand and/or interrupt the most severe fault duty that it may be subjected to at its location in the system. In particular, NEC section 110.9 requires circuit breakers to have a sufficient rating for interrupting the maximum available fault current present at their line side terminals. For locations where calculated fault currents exceed the ratings of the equipment, recommendations for corrective actions are provided.
Electrical equipment manufacturers provide their equipment's short circuit interrupting or withstanding rating in symmetrical RMS current values. However in reality, fault currents are not exclusively symmetrical. At the inception of a fault, system reactance (X) and resistances (R), in addition to the time that the fault occurs on the alternating current (AC) voltage waveform, will introduce a component of asymmetry. This asymmetrical component lasts only for the first few cycles after the initial fault occurs. The duration and magnitude of this component depends on the composition of all system components that provide a contributing source to the fault location.
Due to this, actual asymmetrical faults can only be estimated. The capability of overcurrent devices to interrupt an asymmetrical fault must be based upon the maximum possible asymmetrical fault current at its location within the electrical distribution system.
Motor Contribution to Short Circuit Current
Any motor that is running at the time of a fault will temporarily act as a generator and contribute fault current due to its rotational kinetic energy. This fault contribution only lasts for the first few cycles of a fault. At the motor's terminals, the fault contribution is equal to the motor's load current rating (FLA) divided by its sub-transient reactance.
For the purpose of this study, typical data from Easypower was used for each motor's sub-transient reactance.
In order to document the worst-case short circuit current levels, the short circuit analysis assumes that all modeled motors are running at the time of the fault. Motors that are fed by VFDs which have bypass contactors are assumed to be in bypass mode, thus able to contribute fault current. Motors that are fed by VFDs which do not have bypass contactors have not been considered as a motor contribution.
Calculation Results and Conclusion
Maximum short circuit values were calculated for each bus within the system model. The three-phase fault was considered. X/R ratios for the fault type were calculated for use in as asymmetrical fault current derating (adjustment) factor, when the calculated X/R ratio exceeds the rated (test) X/R ratio for a given low-voltage device. The resulting maximum short circuit duty was calculated from the three-phase current.
Three scenarios were considered in order to determine the highest short circuit level at each bus. These scenarios include:
- System operating at 100% Utility Short Circuit Current
- System operating at 50% Utility Short Circuit Current
- System operating on Generator Short Circuit Current
The detailed results of the short circuit analysis for each scenario are documented in Appendices C and D. Appendix C includes three single-line diagrams, one for each scenario, identifying how the short circuit current changes as it goes through each bus. Appendix D includes an Equipment Duty Scenario Comparison Report that identifies which scenario has the highest fault current and compares it to either the Interrupting Rating (AIC) or Short Circuit Current Rating (SCCR) for each bus, panel, motor, etc.
The results of this evaluation of existing equipment capabilities have determined that the branch breakers in MCC-1 and panel CBH have lower AIC ratings than the calculated faults. Under rated breakers have the
4
potential to create hazardous conditions when subjected to a fault condition. Equipment may become inoperable or may catastrophically explode under certain conditions.
Recommendations
It is recommended that the branch breakers in panels MCC-1 and CBH to be replaced with (at a minimum) breakers with 22kAIC ratings.
It is also recommended that the facility provide safety measures until these conditions are remedied. All other equipment is adequately sized, having short circuit current ratings higher than the calculated short circuit current.
The electrical power distribution system in the one-line configuration represents the interconnection between electrical equipment and all data/parameters. This is required to make the successful short circuit calculation and analysis. The short circuit results show worst-case short circuit values at bus locations in the electrical system.
Coordination Study
Overcurrent Device Coordination Basics
An overcurrent device coordination study is the process of selecting settings for overcurrent devices, such that operation of the devices will occur in a specified order to minimize interruption due to a system disturbance (short circuit, ground fault, or overload condition). This selective coordination (or selectivity) of overcurrent devices will open the overcurrent device nearest to the system distribution while allowing the remainers of the system to remain in operation. Non-selective operation of overcurrent devices may result in unnecessary outages to portions of the electrical distribution system.
The NEC defines Selective Coordination as:
Localization of an overcurrent condition to restrict outages to the circuit or equipment affected by the selection and installation of overcurrents, from overload to the maximum available fault current, and for the full range of overcurrent protective device opening times associated with those overcurrents.
The COORDINATION module in EasyPower was used to complete the overcurrent device coordination study. The methodology used in this analysis is based upon the recommendations in IEEE 242 “IEEE Recommended Practice for Protection and Coordination of Industrial and Commercial Power Systems” and in part on professional experience. During this process, a series of overcurrent devices are examined by overlaying each overcurrent device's time-current characteristic curve (TCC) on a log-log plot.
Determining the most appropriate setting for adjustable overcurrent devices in any system is more of an art than a science, because it is usually not possible for overcurrent devices in series to be completely coordinated for all ranges of possible fault current Coordination often stops short of complete selectivity when an acceptable compromise is reached between maximum protection and maximum selectivity. In addition, arc flash levels must be evaluated and limited, when possible, by reducing overcurrent device settings.
Molded-case Circuit Breakers (MCCBs)
The molded-case circuit breaker is the simplest, least expensive, and most commonly used circuit breaker in the industry. As such, their trip characteristics are of particular importance. The most common type of molded case circuit breaker is the thermal-magnetic type, which contains a thermal portion for overload protection and magnetic portion for short circuit and ground fault protection.
On the TCC of a molded case circuit breaker, there is a band with two distinct borders. The left-most border represents the minimum unlatched time, which is the time when the circuit breaker begins its unlatching
5
(tripping) sequence. The right-most border represents the maximum interrupting time, which is the total time it will take the circuit breaker to separate its contact and extinguish the arc between internal contacts.
The majority of thermal-magnetic molded case circuit breakers rated 225A or less are not adjustable. Many rated 250A or greater have an adjustable instantaneous setting (typically 5-10x of their current rating). In order for molded case circuit breakers to be self-protecting, they must trip instantaneously for fault currents above their instantaneous trip level (typically no more than 10x their current rating). On a TCC, this can appear as in overlap in the lower decade (0.01-0.1 sec).
When molded case circuit breakers are applied in series, they can be selectively coordinated when there is sufficient impedance between the two devices to limit the maximum available short circuit current at the downstream molded case circuit breaker to a values less than the instantaneous setting of the upstream molded case circuit breaker. Selective coordination can also be achieved when using specific combinations of molded case circuit breakers which have been tested and certified by the manufacturer to selectively coordinate.
When there is insufficient impedance in the system between molded case circuit breakers connected in series to selective coordinate, the TCCs will overlap in the instantaneous trip regions. This area of non-coordination is generally viewed as acceptable when the following factors are considered
- The cutoff points on TCCs of overcurrent devices are based three-phase bolted faults. Bolted faults are low to zero impedance; whereas typical fault impedances are greater than this bolted level so that actual cutoff point on the TCC will be less than shown.
- Most faults occur at the end of branch circuits serving motors, lighting panels, and control panels. This added distance/impedance to the fault will significantly reduce fault levels and thus, reduce the probability of not achieving selectivity. Ground faults, which typically have very high impedance values are much more common than three-phase faults.
Transformer Protection
ANSI/IEEE standards (C57.109 for liquid-cooled and C57.12.59 for air-cooled transformers) identity two types of damage that potentially can occur when a transformer is exposed to through-fault currents. The first is thermal damage, which is caused by resistive heating of conductors and insulation material within the transformer. The second type of damage mechanical, which is caused by the large magnetic forces that act on the windings and structural components of the transformer during a through-fault. The thermal and mechanical damage curve for the primary and secondary windings have been included on the transformer TCCs. Additional factors that are considered in the selection of transformer protective devices are full load currents and magnetizing inrush currents.
For small 480-208Y/120V distribution transformers (225kVA or less), coordination is typically not able to be achieved between the primary and secondary overcurrent devices. This lack of selectivity is acceptable considering that the operation of either overcurrent device will result in the same loss of service.
Generator Protection
Two curves have been produced for each generator in the system. The first curve is the generator decrement curve, which represents the maximum current what will be produced by the generator during the initial few cycles of a short circuit. The second curve is the thermal damage curve, which takes into consideration both the thermal and mechanical stresses which the generator is exposed to during short circuit conditions.
Overcurrent Device Coordination Results and Analysis
Appendix E of this report includes the Time-Current Curves for overcurrent devices. There are three instances of non-coordination that are discussed below. In all other instances, the coordination study shows acceptable levels of selectivity.
The descriptions of the plots included are as follows:
- MCC-1 Generator and MCC-2 Generator TCCs (GEN-1 CB) “GEN-1” circuit breaker (CB) overlaps with “B-1A CB” in the instantaneous region and overlaps
6
with “MCC-1 Main CB” in the short-time delay region. However, when attempting to coordinate the GEN-1 CB by increasing the instantaneous setting, this increases the arc flash hazard. This is because the generator produces a much lower short circuit current than a normal source, and therefore increases the fault clearing time. All other breakers in this TCC are coordinated.
- MCC-3 Generator TCC (GEN-2 CB) “GEN-2” circuit breaker (CB) overlaps with “MCC-3-ESBH” in the instantaneous region and overlaps with “MCC-3 Main” in the longtime delay region. However, this is acceptable because of the same reasons stated above and because all downstream breakers of “GEN-2” are in series and therefore will not impact other equipment. All other breakers in this TCC are coordinated.
- MCC-1 Utility and MCC-3 Utility (MDP-MAIN CB) “MDP-MAIN CB” overlaps slightly with fused disconnect switch“FS-1” in the long-time delay and short-time pickup regions. Decreasing the long-time band and short-time pickup settings on the “MDP-MAIN CB” breaker would create coordination but it does not effect the arc flash hazard. All other breakers in this TCC are coordinated.
Arc Flash Study
Arc Flash Risk Assessment Calculation Method
The arc flash risk assessment has been performed according to NFPA 70E-2018, which uses methodologies and equations from IEEE-1584-2018 (IEEE Guide for Performing Arc Flash Hazard Calculations). In addition, IEEE 1584.1-2013 (IEEE Guide for the Specification and Deliverable Requirements for an Arc Flash Hazard Calculation Study in Accordance with IEEE 1584) was utilized as a basis for the scope and deliverables of this analysis.
IEEE 1584 equations for calculating incident energy and arc flash boundaries are based on statistical analysis and curve fitting of available test data. An IEEE working group produced the data from tests it performed to produce models of incident energy.
IEEE 1584 equations can be used for systems that meet the following criteria:
- 0.208kV to 15kV; three-phase
- 50Hz or 60Hz
- 700A to 106,000 bolted fault current
- 13mm to 152mm conductor gaps
Equipment rated at 240V or less with a fault current less than 25kA shall have standard level of an arc flash category of “Level 1”. This is based on criteria evaluated with reference to the 2018 NFPA 70E Table 130.7(C)(15)(a) “Arc-Flash PPE Categories for Alternating Current (ac) Systems.
Scenarios
The following scenarios were used to determine the worst-case Arc Flash Hazard.
Scenario 1 - System operating on 100% Utility Fault Current (Base case).
Scenario 2 - System operating on 50% Utility Fault Current (50P Utility kA Values).
Scenario 3 – System operating on generator (Generator).
The scenario comparison report is documented in Appendix F and the detailed single-line diagram for each result is documented in Appendix G
Arc Flash Risk Assessment Results
The arc flash hazard evaluation program provides results as follows:
- Bus Name - Equipment designation at bus location.
- Voltage - Voltage at the bus in kV.
- Upstream Protective Device Name.
7
- Bus Bolted Fault in kA – The three-phase bolted fault current at the analyzed bus (in kA)
- Bus Arc Fault in kA – The fault current flowin through an electrical arc plasma (in kA).
- Trip Time – The time required for the overcurrent protective device to operate (in seconds).
- Clearing Time – The time required for the overcurrent protective device to clear a fault.
- Arc Flash Boundary – The working distance at which the incident energy is equal to 1.2 cal/cm 2 , the level at which a person could receive a 2 nd degree burn. Only qualified persons with appropriate PPE are permitted within this boundary when energized parts are exposed (in inches).
- Working Distance – The distance between the potential arc source inside the equipment and the head/torso of the worker performing the task. Typical working distances are provided by IEEE 1584 based on the equipment voltage and type (switchgear, MCC, panelboard, etc.)(in inches).
- Incident Energy – The amount of thermal energy impressed on a surface, a certain distance from the source, generated during an electrical arc event (measured in calories per square centimeter (cal/cm 2 ) at a given working distance).
Conclusion
The evaluation results are shown as follows:
- Table 1: Personal Protection Equipment Categories and Descriptions (PPE).
- Appendix F: Arc Flash Hazard Scenario Comparison Report.
- Appendix G: Arc Flash Single-Line Diagrams for each scenario.
All equipment downstream of the overcurrent protective devices for the utility and generator have incident energies equal to or less than 7.0 cal/cm2 requiring PPE levels of 2 or less. The utility and generator upstream of the protective devices have incident energies higher than 40.0 cal/cm2 and require that work only be done when electrical equipment is de-energized.
8
Table 1: NFPA 70E-2018 Table 130.7(C)(15)(c)
| PPE Category | PPE/ Clothing Description | Incident Energy (cal/cm2) |
|---|---|---|
| Refer to Arc Flash Hazard Identification and task to be performed in accordance with NFPA 70E. Shirt (long sleeve) and pants (long) or coverall or untreated natural fiber. |
0.0 - 1.2 cal/cm2 | |
| 1 | Arc-Rated Clothing, Minimum Arc Rating of 4cal/cm2. Arc-rated long-sleeve shirt and pants or arc-rated-coverall Arc-rated face shield or arc flash suit hood Arc-rated jacket, parka, rainwear, or hard hat liner (AN) Protective Equipment Hard hat Safety glasses or safety goggles (SR) Hearing protection (ear canal inserts) Heavy duty leather gloves Leather footwear (AN) |
1.2 - 4.0 cal/cm2 |
| 2 | Arc-Rated Clothing, Minimum Arc Rating of 8 cal/cm2. Arc-rated long-sleeve shirt and pants or arc-rated-coverall Arc-rated flash suit hood or arc-rated face shield and arc-rated balaclava Arc-rated jacket, parka, rainwear, or hard hat liner (AN) Protective Equipment Hard hat Safety glasses or safety goggles (SR) Hearing protection (ear canal inserts) Heavy duty leather gloves Leather footwear |
4.0 - 8.0 cal/cm2 |
9
| PPE Category | PPE/ Clothing Description | Incident Energy (cal/cm2) |
|---|---|---|
| 3 | Arc-Rated Clothing Selected so that the System Arc Rating Meets the Required Minimum Arc Rating of 25 cal/cm2. Arc-rated long-sleeve shirt (AR) Arc-rated pants (AR) Arc-rated coverall (AR) Arc-rated arc flash suit jacket (AR) Arc-rated arc flash suit pants (AR) Arc-rated arc flash suit hood Arc-rated gloves Arc-rated jacket, parka, rainwear, or hard hat liner (AN) Protective Equipment Hard hat Safety glasses or safety goggles (SR) Hearing protection (ear canal inserts) Leather footwear |
8.0 - 25.0 cal/cm2 |
| 4 | Arc-Rated Clothing Selected so that the System Arc Rating Meets the Required Minimum Arc Rating of 40 cal/cm2. Arc-rated long-sleeve shirt (AR) Arc-rated pants (AR) Arc-rated coverall (AR) Arc-rated arc flash suit jacket (AR) Arc-rated arc flash suit pants (AR) Arc-rated arc flash suit hood Arc-rated gloves Arc-rated jacket, parka, rainwear, or hard hat liner (AN) Protective Equipment Hard hat Safety glasses or safety goggles (SR) Hearing protection (ear canal inserts) Leather footwear |
25.0 - 40.0 cal/cm2 |
| Dangerous! No appropriate PPE can be found. Work only on de-energized electrical equipment. |
40.0 - 999.0 cal/cm2 |
10
Appendices
Appendix A:
Input Data
11
Database Report using Configuration 'HSZ'
EasyPower v11.0.1.8039 5/18/2025 U:\...\EGMAU25005.dez
EasyPower LLC.
| Buses | Base kV | Service | Equipment | AF Option | Electrode Gap (mm) | Enclosure Height (in) | Enclosure Width (in) | Enclosure Depth (in) |
|---|---|---|---|---|---|---|---|---|
| 800A FUSE DS BUS | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| CBH | 0.48 | 3PH-4W | Panelboard | TCC | 25 | 14 | 12 | 10.402 |
| CSPP | 0.48 | 3PH-4W | Panelboard | TCC | 25 | 14 | 12 | 10.402 |
| CV-51 | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| CV-52 | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| EF-3 | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| EF-4 | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| FDR TO CBH | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| FDR TO MCC-1 | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| GEN-1 | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| GEN-2 | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| MCC-1 | 0.48 | 3PH-4W | Switchgear | TCC | 32 | 20 | 20 | 20 |
| MCC-2 | 0.48 | 3PH-4W | Panel | TCC | 25 | 14 | 12 | 5.701 |
| MDP | 0.48 | 3PH-4W | Switchgear | TCC | 32 | 20 | 20 | 20 |
| ME-10 | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| ME-11 | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| ME-61A | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| ME-61B | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| ME-63 | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| ME-64 | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| ME-65 | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| OF-1 CB | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| OH DOOR | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| P-11 | 0.48 | 3PH-4W | VFD | TCC | 32 | 20 | 20 | 20 |
| P-12 | 0.48 | 3PH-4W | VFD | TCC | 32 | 20 | 20 | 20 |
| P-13 | 0.48 | 3PH-4W | VFD | TCC | 32 | 20 | 20 | 20 |
| P-41 | 0.48 | 3PH-4W | VFD | TCC | 32 | 20 | 20 | 20 |
| P-42 | 0.48 | 3PH-4W | VFD | TCC | 32 | 20 | 20 | 20 |
| P-43 | 0.48 | 3PH-4W | VFD | TCC | 32 | 20 | 20 | 20 |
| P-61 | 0.48 | 3PH-4W | Other | TCC | 32 | 20 | 20 | 20 |
| SCCP | 0.48 | 3PH-4W | Panel | TCC | 25 | 14 | 12 | 5.701 |
| T-PECO PRI | 33 | 3PH-4W | Transformer Terminal | TCC | 254 | |||
| T-PECO SEC | 0.48 | 3PH-4W | Transformer Terminal | TCC | 32 | 20 | 20 | 20 |
| Panels | Service | Base kV | Main Bus Rating (A) | Panel SC Rating (kA) | Incoming Device Type | Conn Watts | Conn kVA | Conn FLA |
|---|---|---|---|---|---|---|---|---|
| ECBL | 3PH-4W | 0.208 | 60 | 42 | Main Breaker | 0 | 0 | 0 |
| ESBH | 3PH-4W | 0.48 | 42 | Main Breaker | 0 | 0 | 0 | |
| ESBL | 3PH-4W | 0.208 | 100 | 22 | Main Breaker | 0 | 0 | 0 |
| PNL-1 | 3PH-4W | 0.208 | 60 | 42 | Main Breaker | 0 | 0 | 0 |
| UWCP | 3PH-4W | 0.48 | 40 | 42 | Main Lug Only | 19999.8 | 20 | 24.056 |
| MCCs | Base kV | Service | MCC SC Rating (kA) | Conn kVA | Conn FLA | Int MF (<50) | X"dv or Xlr (>50) | R1 pu (>50) | X1 pu (>50) |
|---|---|---|---|---|---|---|---|---|---|
| FCP #1 | 0.48 | 3PH-4W | 42 | 3.585 | 4.312 | 100000 | 16.7 | 1000 | 1e+06 |
| FCP #2 | 0.48 | 3PH-4W | 42 | 3.585 | 4.312 | 100000 | 16.7 | 1000 | 1e+06 |
| MCC-3 | 0.48 | 3PH-4W | 42 | 237.509 | 285.679 | 100000 | 16.7 | 1000 | 1e+06 |
| Utilities | AC/DC | Service | To Bus ID | Base kV | Util kV | 3Ph SC1 | Fault Unit | SLG SC1 |
|---|---|---|---|---|---|---|---|---|
| PECO UTILITY | AC | 3PH-4W | T-PECO PRI | 33 | 34.5 | 2.215 | Amps | 1.639 |
| Generators | Service | To Bus ID | Rating | No of Phases | Gen kV (LL) | Gen kV (LN) | Conn | RatingUnit | Type |
|---|---|---|---|---|---|---|---|---|---|
| GEN-1 | 3PH-4W | GEN-1 | 562.5 | 3 | 0.48 | 0.277 | YG | kVA | SYN-SPA |
| GEN-2 | 3PH-4W | GEN-2 | 625 | 3 | 0.48 | 0.277 | YG | kVA | SYN-SPA |
| Generators | Power Factor | Efficiency | RPM | X/R | Ctl Bus | X''dv | X'dv | X0 | R1 pu |
|---|---|---|---|---|---|---|---|---|---|
| GEN-1 | 0.8 | 0.95 | 1800 | 21.098 | GEN-1 | 11 | 15 | 9 | 0.0927 |
| GEN-2 | 0.8 | 0.95 | 1800 | 21.098 | GEN-2 | 9 | 13 | 8 | 0.0683 |
| Generators | X1 pu | R0 pu | X0 pu | Xd | T''d | T'd | Ta |
|---|---|---|---|---|---|---|---|
| GEN-1 | 1.956 | 0.0758 | 1.6 | 280 | 0.012 | 0.08 | 0.019 |
| GEN-2 | 1.44 | 0.0607 | 1.28 | 335 | 0.012 | 0.08 | 0.017 |
| Cables | No of Phases | From Bus ID | To Bus ID | To Base kV | Size | Length | Rating (A) |
|---|---|---|---|---|---|---|---|
| C-26 | 3 | CBH | CV-51 | 0.48 | 12 | 30 | 25 |
| C-27 | 3 | CBH | CV-52 | 0.48 | 12 | 30 | 25 |
| FDR FR 800A DS TO ATS-1 | 3 | 800A FUSE DS BUS | ATS-1:Src Bus 1 | 0.48 | 300 | 20 | 855 |
| FDR FR ATS-1 TO MCC-2 | 3 | ATS-1:Load Bus | MCC-2 | 0.48 | 250 | 10 | 510 |
| FDR FR ATS-2 TO MCC-3 | 3 | ATS-2:Load Bus | MCC-3 | 0.48 | 500 | 10 | 1140 |
| FDR FR GEN-1 TO ATS-1 | 3 | ATS-1:Src Bus 2 | GEN-1 | 0.48 | 300 | 40 | 855 |
| FDR FR GEN-2 TO ATS-2 | 3 | ATS-2:Src Bus 2 | GEN-2 | 0.48 | 500 | 145 | 1140 |
| FDR FR MDP TO 800A DS | 3 | MDP | 800A FUSE DS BUS | 0.48 | 300 | 30 | 855 |
| FDR FR MDP TO ATS-2 | 3 | MDP | ATS-2:Src Bus 1 | 0.48 | 500 | 90 | 1140 |
| FDR T-PECO TO MDP | 3 | T-PECO SEC | MDP | 0.48 | 500 | 5 | 1900 |
| FDR TO CBH PT1 | 3 | ATS-1:Load Bus | FDR TO CBH | 0.48 | 500 | 10 | 380 |
| FDR TO CBH PT2 | 3 | FDR TO CBH | CBH | 0.48 | 500 | 10 | 380 |
| FDR TO CSPP | 3 | CBH | CSPP | 0.48 | 1 | 65 | 130 |
| FDR TO EF-3 | 3 | CBH | EF-3 | 0.48 | 12 | 40 | 25 |
| FDR TO EF-4 | 3 | CBH | EF-4 | 0.48 | 12 | 60 | 25 |
| FDR TO ESBH | 3 | MCC-3 | ESBH | 0.48 | 6 | 33 | 65 |
| FDR TO FCP #1 | 3 | MCC-3 | FCP #1 | 0.48 | 12 | 70 | 25 |
| FDR TO FCP #2 | 3 | MCC-3 | FCP #2 | 0.48 | 12 | 70 | 25 |
| FDR TO ME-10 | 3 | SCCP | ME-10 | 0.48 | 12 | 20 | 25 |
| FDR TO ME-11 | 3 | SCCP | ME-11 | 0.48 | 12 | 20 | 25 |
| FDR TO ME-63 | 3 | CSPP | ME-63 | 0.48 | 12 | 10 | 25 |
| FDR TO ME-64 | 3 | CSPP | ME-64 | 0.48 | 12 | 10 | 25 |
| FDR TO ME-65 | 3 | CBH | ME-65 | 0.48 | 12 | 40 | 25 |
| FDR TO OH DOOR | 3 | CBH | OH DOOR | 0.48 | 12 | 60 | 25 |
| FDR TO SCCP | 3 | MCC-2 | SCCP | 0.48 | 12 | 20 | 25 |
| FDR TO UWCP | 3 | MCC-3 | UWCP | 0.48 | 8 | 80 | 50 |
| FED FR 800 DS SW TO MCC1-1 | 3 | ATS-1:Load Bus | FDR TO MCC-1 | 0.48 | 500 | 5 | 380 |
| FDR FR 800 DS SW TO MCC1-2 | 3 | FDR TO MCC-1 | MCC-1 | 0.48 | 500 | 5 | 380 |
| 2W Transformers | No of Phases | From Bus ID | From Base kV | To Base kV | Type | Temp | MVA | Z | Z0 |
|---|---|---|---|---|---|---|---|---|---|
| T-ECBL | 3 | MCC-2 | 0.48 | 0.208 | Dry | 65 | 0.015 | 4.5 | 3.825 |
| T-PECO | 3 | T-PECO PRI | 33 | 0.48 | Oil | 65 | 1 | 5.72 | 4.862 |
| T-PR1 | 3 | MCC-1 | 0.48 | 0.208 | Dry | 65 | 0.015 | 4.5 | 3.825 |
| TX-1 | 3 | ESBH | 0.48 | 0.208 | Dry | 65 | 0.03 | 2.86 | 2.431 |
| 2W Transformers | X/R | To Bus ID | To Conn | From Conn |
|---|---|---|---|---|
| T-ECBL | 1.553 | ECBL | YG | D |
| T-PECO | 5.677 | T-PECO SEC | YG | YG |
| T-PR1 | 1.553 | PNL-1 | YG | D |
| TX-1 | 1.602 | ESBL | YG | D |
LV Breakers
| LV Breakers | Base kV | Breaker Mfr | Breaker Style | Trip | Trip Style | Frame (A) | Trip (A) | SC Int kA | Inst Setting | Inst (A) |
|---|---|---|---|---|---|---|---|---|---|---|
| ATS-1 CB | 0.48 | GE | SKL8 | SST | MCCB SK | 800 | 800 | 65 | Max | 8705 |
| ATS-2 | 0.48 | GE | SKL12 | SST | MCCB SK | 1200 | 1000 | 65 | Max | 10180 |
| B-1A BREAKER | 0.48 | SQD | FA | TMGN | FA | 100 | 100 | 18 | Fixed | |
| B-1B BREAKER | 0.48 | SQD | FA | TMGN | FA | 100 | 100 | 18 | Fixed | |
| B-1C BREAKER | 0.48 | SQD | FA | TMGN | FA | 100 | 100 | 18 | Fixed | |
| B-2 BREAKER | 0.48 | SQD | FA | TMGN | FA | 100 | 100 | 18 | Fixed | |
| CBH MAIN CB | 0.48 | GE | SGL4 | SST | MCCB SG | 400 | 400 | 42 | Max | 4080 |
| CSPP CB | 0.48 | GE | SELA 3P | SST | MCCB SE | 150 | 80 | 65 | Max | 999 |
| CV-51 CB | 0.48 | GE | TEY | TMGN | TEY | 100 | 20 | 14 | Fixed | |
| CV-52 CB | 0.48 | GE | TEY | TMGN | TEY | 100 | 20 | 14 | Fixed | |
| EF-3 CB | 0.48 | GE | TEY | TMGN | TEY | 100 | 20 | 14 | Fixed | |
| EF-4 CB | 0.48 | GE | TEY | TMGN | TEY | 100 | 20 | 14 | Fixed | |
| GEN-1 CB | 0.48 | SQD | PJ-800 AF | SST | MCCB | 800 | 800 | 65 | 1.5 | 1200 |
| GEN-2 CB | 0.48 | SQD | PJ | SST | MCCB | 1200 | 1000 | 65 | 1.5 | 1500 |
| MCC-1 MAIN CB | 0.48 | GE | SGL4 | SST | MCCB SG | 400 | 400 | 65 | Max | 4080 |
| MCC-2 MAIN CB | 0.48 | GE | SGL6 | SST | MCCB SG | 600 | 400 | 65 | Max | 4050 |
| MDP MAIN CB | 0.48 | GE | SS-20 | SST | ICCB | 2000 | 2000 | 65 | 15 | 30000 |
| ME-61A CB | 0.48 | GE | SEDA 3P | SST | MCCB SE | 150 | 70 | 18 | Max | 863 |
| ME-61B | 0.48 | GE | SEDA 3P | SST | MCCB SE | 150 | 70 | 18 | Max | 863 |
| ME-63 CB | 0.48 | GE | SEDA 3P | SST | MCCB SE | 150 | 20 | 18 | Max | 254 |
| ME-64 CB | 0.48 | GE | SEDA 3P | SST | MCCB SE | 150 | 20 | 18 | Max | 254 |
| ME-65 CB | 0.48 | GE | TEY | TMGN | TEY | 100 | 20 | 14 | Fixed | |
| OF-1 CB | 0.48 | GE | SELA 3P | SST | MCCB SE | 150 | 50 | 65 | Max | 637 |
| OH DOOR CB | 0.48 | GE | TEY | TMGN | TEY | 100 | 20 | 14 | Fixed | |
| P-11 CB | 0.48 | GE | SELA 3P | SST | MCCB SE | 150 | 70 | 65 | Max | 863 |
| P-12 CB | 0.48 | GE | SELA 3P | SST | MCCB SE | 150 | 70 | 65 | Max | 863 |
| P-13 CB | 0.48 | GE | SELA 3P | SST | MCCB SE | 150 | 70 | 65 | Max | 863 |
| P-41 CB | 0.48 | GE | SELA 3P | SST | MCCB SE | 150 | 40 | 65 | Max | 501 |
| P-42 CB | 0.48 | GE | SELA 3P | SST | MCCB SE | 150 | 40 | 65 | Max | 501 |
| P-43 CB | 0.48 | GE | SELA 3P | SST | MCCB SE | 150 | 40 | 65 | Max | 501 |
| P-61 CB | 0.48 | GE | SEDA 3P | SST | MCCB SE | 150 | 20 | 18 | Max | 254 |
| PANEL ECBL CB | 0.48 | GE | SELA 3P | SST | MCCB SE | 150 | 30 | 65 | Max | 415 |
| PANEL PR1 BREAKER | 0.48 | SQD | FA | TMGN | FA | 100 | 30 | 18 | Fixed | |
| SCCP CB | 0.48 | GE | SELA 3P | SST | MCCB SE | 150 | 20 | 65 | Max | 254 |
| SCCP MAIN CB | 0.48 | <None> | <None> | SST | 25 | 25 | 65 |
Fuses
| Fuses | No of Phases | On Bus | Base kV | Options | Fuse Mfr | Fuse Type | Fuse Style |
|---|---|---|---|---|---|---|---|
| 800A FUSE DS | 3 | 800A FUSE DS BUS | 0.48 | Fused Switch | Littelfuse | POWR-PRO | KLPC(L) |
| FS-1 | 3 | T-PECO PRI | 33 | Fuse Only | S&C | SMU | SMU-20 |
| Fuses | Model | Library kV | Size | SC Int kA | SC Test X/R |
|---|---|---|---|---|---|
| 800A FUSE DS | 0.6 | 800A | 200 | 4.9 | |
| FS-1 | Standard Speed | 38 | 80E | 10 | 15 |
Switches
| Switches | On Bus | Base kV | Normal State | Cont Current (A) | Assumed Open Time |
|---|---|---|---|---|---|
| ATS-1:Switch 1 | ATS-1:Load Bus | 0.48 | Closed | 0 | 30 |
| ATS-2:Src Bus 1 | ATS-2:Src Bus 1 | 0.48 | Closed | 0 | 30 |
| OF11 DS | OF-1 CB | 0.48 | Closed | 60 | 30 |
Motors
| Motors | No of Phases | To Bus ID | Base kV | Motor kV | HP or kW | RPM | FLA | Power Factor | Efficiency |
|---|---|---|---|---|---|---|---|---|---|
| B-1A | 3 | MCC-1 | 0.48 | 0.46 | 50 | 1800 | 0.9 | 0.924 | |
| B-1B | 3 | MCC-1 | 0.48 | 0.46 | 50 | 1800 | 0.89 | 0.93 | |
| B-1C | 3 | MCC-1 | 0.48 | 0.46 | 50 | 1800 | 0.9 | 0.924 | |
| B-2 | 3 | MCC-1 | 0.48 | 0.46 | 50 | 1800 | 0.9 | 0.924 | |
| CV-51 | 3 | CV-51 | 0.48 | 0.46 | 2 | 1800 | 3.4 | 0.82 | 0.91 |
| CV-52 | 3 | CV-52 | 0.48 | 0.46 | 2 | 1800 | 3.4 | 0.82 | 0.91 |
| EF-3 | 3 | EF-3 | 0.48 | 0.46 | 1 | 1800 | 2.1 | 0.82 | 0.91 |
| EF-4 | 3 | EF-4 | 0.48 | 0.46 | 5 | 1800 | 7.6 | 0.82 | 0.91 |
| ME-10 | 3 | ME-10 | 0.48 | 0.46 | 5 | 1800 | 7.6 | 0.82 | 0.91 |
| ME-11 | 3 | ME-11 | 0.48 | 0.46 | 2 | 1800 | 3.4 | 0.82 | 0.91 |
| ME-61A | 3 | ME-61A | 0.48 | 0.46 | 30 | 1800 | 40 | 0.82 | 0.91 |
| ME-61B | 3 | ME-61B | 0.48 | 0.46 | 30 | 1800 | 40 | 0.82 | 0.91 |
| ME-63 | 3 | ME-63 | 0.48 | 0.46 | 3 | 1800 | 4.8 | 0.82 | 0.91 |
| ME-64 | 3 | ME-64 | 0.48 | 0.46 | 3 | 1800 | 4.8 | 0.82 | 0.91 |
| ME-65 | 3 | ME-65 | 0.48 | 0.46 | 3 | 1800 | 4.8 | 0.82 | 0.91 |
| OF-1 | 3 | OF-1 CB | 0.48 | 0.46 | 25 | 1800 | 34 | 0.82 | 0.91 |
| OH DOOR | 3 | OH DOOR | 0.48 | 0.46 | 0.8 | 1800 | 0.82 | 0.91 | |
| P-11 | 3 | P-11 | 0.48 | 0.46 | 30 | 1800 | 40 | 0.82 | 0.91 |
| P-12 | 3 | P-12 | 0.48 | 0.46 | 30 | 1800 | 40 | 0.82 | 0.91 |
| P-13 | 3 | P-13 | 0.48 | 0.46 | 30 | 1800 | 40 | 0.82 | 0.91 |
| P-41 | 3 | P-41 | 0.48 | 0.46 | 15 | 1800 | 21 | 0.82 | 0.91 |
| P-42 | 3 | P-42 | 0.48 | 0.46 | 15 | 1800 | 21 | 0.82 | 0.91 |
| P-43 | 3 | P-43 | 0.48 | 0.46 | 15 | 1800 | 21 | 0.82 | 0.91 |
| P-61 | 3 | P-61 | 0.48 | 0.46 | 7.5 | 1800 | 11 | 0.82 | 0.91 |
ATSs
| ATSs | Base kV | Service | Working Distance (in) | Electrode Gap (mm) | Model |
|---|---|---|---|---|---|
| ATS-1 | 0.48 | 3PH-4W | 18 | 32 | Switch |
| ATS-2 | 0.48 | 3PH-4W | 18 | 32 | Switch |
Appendix B:
One Line Diagram
Pennoni
16
Note: some text on this page could not be read reliably. Please see the original PDF for this page.
RCSTP ONE-LINE DIAGRAM - 100% UTILITY
[Electrical one-line diagram showing the RCSTP power distribution system under 100% utility operation, including utility feed, transformers, generators, automatic transfer switches, motor control centers, panels, feeders, circuit breakers, VFDs, and motor loads.]
Utility Feed, Main Distribution Panel (MDP), and Generators
- PECO UTILITY (33.0 kV) to T-PECO PRI via PM-1
- T-PECO (1000 kVA, 33 - 0.48 kV, 5.72%) to T-PECO SEC
- FDR T-PECO TO MDP: 5-(3-1/C 500 kcmil) to MDP MAIN CB (1600 A) and bus MDP
- MDP branches: ATS-1 CB (800 A) via FDR FR MDP TO 800A DS (3-(3-1/C 300 kcmil)) to 800A FUSE DS (800A) / 800A FUSE DS BUS, then FDR FR 800A DS TO ATS-1 (3-(3-1/C 300 kcmil)) to ATS-1; and ATS-2 CB (1200 A) via FDR FR MDP TO ATS-2 (3-(3-1/C 500 kcmil)) to ATS-2
- GEN-1 (450 kW, 562.5 kVA) via GEN-1 CB (800 A) and FDR FR GEN-1 TO ATS-1 (3-(3-1/C 300 kcmil)) to ATS-1
- GEN-2 (500 kW, 625 kVA) via GEN-2 CB (1000 A) and FDR FR GEN-2 TO ATS-2 (3-(3-1/C 500 kcmil)) to ATS-2
ATS-1 Downstream Distribution (MCC-1, CBH, CSPP, MCC-2)
- FED FR 800 DS SW TO MCC1-1 (1-(3-1/C 500 kcmil)) to FDR TO MCC-1, then FDR FR 800 DS SW TO MCC1-2 (1-(3-1/C 500 kcmil)) to MCC-1 MAIN CB (400 A) and bus MCC-1
- MCC-1 branches: PANEL PR1 BREAKER to T-PR1 (15 kVA, 0.48 - 0.208 kV, 4.5%) and PNL-1 (10.0 kVA); M-1A BREAKER to M-1A (50 HP); M-1B BREAKER to M-1B (50 HP); M-1C BREAKER to M-1C (50 HP); M-2 BREAKER to M-2 (50 HP)
- FDR TO CBH PT1 (1-(3-1/C 500 kcmil)) to FDR TO CBH, then FDR TO CBH PT2 (1-(3-1/C 500 kcmil)) to CBH MAIN CB (400 A) and bus CBH
- CBH branches: CSPP CB via FDR TO CSPP (1-(3-1/C 1 AWG)) to CSPP; ME-65 CB via FDR TO ME-65 (1-(3-1/C 12 AWG)) to ME-65 (1.5 HP); EF-3 CB via FDR TO EF-3 (1-(3-1/C 12 AWG)) to EF-3 (2 HP); EF-4 CB via FDR TO EF-4 (1-(3-1/C 12 AWG)) to EF-4 (2 HP); OH DOOR CB via FDR TO OH DOOR (1-(3-1/C 12 AWG)) to OH DOOR (0.5 HP); CV-51 CB via C-26 (1-(3-1/C 12 AWG)) to CV-51 (2 HP); CV-52 CB via C-27 (1-(3-1/C 12 AWG)) to CV-52 (2 HP)
- CSPP branches: PM-7 CB via PM-7 VFD to PM-7 (7.5 HP); ME-66A CB via ME-66A VFD to ME-66A (10 HP); ME-66B CB via ME-66B VFD to ME-66B (10 HP); ME-63 CB via FDR TO ME-63 (1-(3-1/C 12 AWG)) to ME-63 (1.5 HP); ME-64 CB via FDR TO ME-64 (1-(3-1/C 12 AWG)) to ME-64 (1.5 HP)
- FDR FR ATS-1 TO MCC-2 (2-(3-1/C 250 kcmil)) to MCC-2 MAIN CB (600 A) and bus MCC-2
- MCC-2 branches: PM-11 CB via PM-11 VFD to PM-11 (20 HP); PM-12 CB via PM-12 VFD to PM-12 (20 HP); PM-31 CB via PM-31 VFD to PM-31 (15 HP); PM-32 CB via PM-32 VFD to PM-32 (15 HP); PM-41 CB via PM-41 VFD to PM-41 (7.5 HP); PM-42 CB via PM-42 VFD to PM-42 (7.5 HP); SCCP CB via FDR TO SCCP (1-(3-1/C 12 AWG)) to SCCP, feeding ME-10 (0.5 HP) via FDR TO ME-10 (1-(3-1/C 12 AWG)) and ME-11 (0.5 HP) via FDR TO ME-11 (1-(3-1/C 12 AWG)); OP-1 CB to OP-1 (25 HP); PANEL ECBL CB to T-ECBL (15 kVA, 0.48 - 0.208 kV, 4.5%) and ECBL (15.0 kVA)
ATS-2 Downstream Distribution (MCC-3)
- FDR FR ATS-2 TO MCC-3 (3-(3-1/C 500 kcmil)) to MCC-3 MAIN CB (1200 A) and bus MCC-3
- MCC-3 branches: FDR TO FCP #1 (1-(3-1/C 12 AWG)) to FCP #1 (20.8 kVA, 25.0 A); FDR TO FCP #2 (1-(3-1/C 12 AWG)) to FCP #2 (20.8 kVA, 25.0 A); FDR TO UWCP (1-(3-1/C 8 AWG)) to UWCP (31.6 kVA, 38.0 A); FDR TO ESBH (1-(3-1/C 6 AWG)) to ESBH, TX-1 (30 kVA, 0.48 - 0.208 kV, 2.86%), and ESBL (10.0 kVA)
Appendix C:
Short Circuit One-Line Results
Pennoni
18
Note: some text on this page could not be read reliably. Please see the original PDF for this page.
RCSTP SHORT CIRCUIT ONE-LINE DIAGRAM - 100% UTILITY
[Electrical short-circuit one-line diagram showing fault current values across the RCSTP power distribution system under 100% utility operation.]
Utility Feed, Main Distribution Panel (MDP), and Generators
- PECO UTILITY (33.0 kV) to T-PECO PRI via PM-1, T-PECO, T-PECO SEC, and FDR T-PECO TO MDP to MDP MAIN CB and bus MDP
- MDP branches: ATS-1 CB via FDR FR MDP TO 800A DS to 800A FUSE DS / 800A FUSE DS BUS and FDR FR 800A DS TO ATS-1 to ATS-1; ATS-2 CB via FDR FR MDP TO ATS-2 to ATS-2
- GEN-1 via GEN-1 CB and FDR FR GEN-1 TO ATS-1 to ATS-1; GEN-2 via GEN-2 CB and FDR FR GEN-2 TO ATS-2 to ATS-2
Downstream Panels and Loads
- MCC-1 (fed via FED FR 800 DS SW TO MCC1-1, FDR TO MCC-1, FDR FR 800 DS SW TO MCC1-2, and MCC-1 MAIN CB): PANEL PR1 BREAKER to T-PR1 and PNL-1; M-1A BREAKER to M-1A; M-1B BREAKER to M-1B; M-1C BREAKER to M-1C; M-2 BREAKER to M-2
- CBH (fed via FDR TO CBH PT1, FDR TO CBH, FDR TO CBH PT2, and CBH MAIN CB): CSPP CB via FDR TO CSPP to CSPP; ME-65 CB via FDR TO ME-65 to ME-65; EF-3 CB via FDR TO EF-3 to EF-3; EF-4 CB via FDR TO EF-4 to EF-4; OH DOOR CB via FDR TO OH DOOR to OH DOOR; CV-51 CB via C-26 to CV-51; CV-52 CB via C-27 to CV-52
- CSPP: PM-7 CB via PM-7 VFD to PM-7; ME-66A CB via ME-66A VFD to ME-66A; ME-66B CB via ME-66B VFD to ME-66B; ME-63 CB via FDR TO ME-63 to ME-63; ME-64 CB via FDR TO ME-64 to ME-64
- MCC-2 (fed via FDR FR ATS-1 TO MCC-2 and MCC-2 MAIN CB): PM-11 CB via PM-11 VFD to PM-11; PM-12 CB via PM-12 VFD to PM-12; PM-31 CB via PM-31 VFD to PM-31; PM-32 CB via PM-32 VFD to PM-32; PM-41 CB via PM-41 VFD to PM-41; PM-42 CB via PM-42 VFD to PM-42; SCCP CB via FDR TO SCCP to SCCP, FDR TO ME-10 to ME-10, and FDR TO ME-11 to ME-11; OP-1 CB to OP-1; PANEL ECBL CB to T-ECBL and ECBL
- MCC-3 (fed via FDR FR ATS-2 TO MCC-3 and MCC-3 MAIN CB): FDR TO FCP #1 to FCP #1; FDR TO FCP #2 to FCP #2; FDR TO UWCP to UWCP; FDR TO ESBH to ESBH, TX-1, and ESBL
Note: some text on this page could not be read reliably. Please see the original PDF for this page.
RCSTP SHORT CIRCUIT ONE-LINE DIAGRAM - 80% UTILITY
[Electrical short-circuit one-line diagram showing fault current values across the RCSTP power distribution system under 80% utility operation.]
Utility Feed, Main Distribution Panel (MDP), and Generators
- PECO UTILITY (33.0 kV) to T-PECO PRI via PM-1, T-PECO, T-PECO SEC, and FDR T-PECO TO MDP to MDP MAIN CB and bus MDP
- MDP branches: ATS-1 CB via FDR FR MDP TO 800A DS to 800A FUSE DS / 800A FUSE DS BUS and FDR FR 800A DS TO ATS-1 to ATS-1; ATS-2 CB via FDR FR MDP TO ATS-2 to ATS-2
- GEN-1 via GEN-1 CB and FDR FR GEN-1 TO ATS-1 to ATS-1; GEN-2 via GEN-2 CB and FDR FR GEN-2 TO ATS-2 to ATS-2
Downstream Panels and Loads
- MCC-1 (fed via FED FR 800 DS SW TO MCC1-1, FDR TO MCC-1, FDR FR 800 DS SW TO MCC1-2, and MCC-1 MAIN CB): PANEL PR1 BREAKER to T-PR1 and PNL-1; M-1A BREAKER to M-1A; M-1B BREAKER to M-1B; M-1C BREAKER to M-1C; M-2 BREAKER to M-2
- CBH (fed via FDR TO CBH PT1, FDR TO CBH, FDR TO CBH PT2, and CBH MAIN CB): CSPP CB via FDR TO CSPP to CSPP; ME-65 CB via FDR TO ME-65 to ME-65; EF-3 CB via FDR TO EF-3 to EF-3; EF-4 CB via FDR TO EF-4 to EF-4; OH DOOR CB via FDR TO OH DOOR to OH DOOR; CV-51 CB via C-26 to CV-51; CV-52 CB via C-27 to CV-52
- CSPP: PM-7 CB via PM-7 VFD to PM-7; ME-66A CB via ME-66A VFD to ME-66A; ME-66B CB via ME-66B VFD to ME-66B; ME-63 CB via FDR TO ME-63 to ME-63; ME-64 CB via FDR TO ME-64 to ME-64
- MCC-2 (fed via FDR FR ATS-1 TO MCC-2 and MCC-2 MAIN CB): PM-11 CB via PM-11 VFD to PM-11; PM-12 CB via PM-12 VFD to PM-12; PM-31 CB via PM-31 VFD to PM-31; PM-32 CB via PM-32 VFD to PM-32; PM-41 CB via PM-41 VFD to PM-41; PM-42 CB via PM-42 VFD to PM-42; SCCP CB via FDR TO SCCP to SCCP, FDR TO ME-10 to ME-10, and FDR TO ME-11 to ME-11; OP-1 CB to OP-1; PANEL ECBL CB to T-ECBL and ECBL
- MCC-3 (fed via FDR FR ATS-2 TO MCC-3 and MCC-3 MAIN CB): FDR TO FCP #1 to FCP #1; FDR TO FCP #2 to FCP #2; FDR TO UWCP to UWCP; FDR TO ESBH to ESBH, TX-1, and ESBL
Note: some text on this page could not be read reliably. Please see the original PDF for this page.
RCSTP SHORT CIRCUIT ONE-LINE DIAGRAM - GENERATOR
[Electrical short-circuit one-line diagram showing fault current values across the RCSTP power distribution system under generator operation.]
Utility Feed, Main Distribution Panel (MDP), and Generators
- PECO UTILITY (33.0 kV) to T-PECO PRI via PM-1, T-PECO, T-PECO SEC, and FDR T-PECO TO MDP to MDP MAIN CB and bus MDP
- MDP branches: ATS-1 CB via FDR FR MDP TO 800A DS to 800A FUSE DS / 800A FUSE DS BUS and FDR FR 800A DS TO ATS-1 to ATS-1; ATS-2 CB via FDR FR MDP TO ATS-2 to ATS-2
- GEN-1 via GEN-1 CB and FDR FR GEN-1 TO ATS-1 to ATS-1; GEN-2 via GEN-2 CB and FDR FR GEN-2 TO ATS-2 to ATS-2
Downstream Panels and Loads
- MCC-1 (fed via FED FR 800 DS SW TO MCC1-1, FDR TO MCC-1, FDR FR 800 DS SW TO MCC1-2, and MCC-1 MAIN CB): PANEL PR1 BREAKER to T-PR1 and PNL-1; M-1A BREAKER to M-1A; M-1B BREAKER to M-1B; M-1C BREAKER to M-1C; M-2 BREAKER to M-2
- CBH (fed via FDR TO CBH PT1, FDR TO CBH, FDR TO CBH PT2, and CBH MAIN CB): CSPP CB via FDR TO CSPP to CSPP; ME-65 CB via FDR TO ME-65 to ME-65; EF-3 CB via FDR TO EF-3 to EF-3; EF-4 CB via FDR TO EF-4 to EF-4; OH DOOR CB via FDR TO OH DOOR to OH DOOR; CV-51 CB via C-26 to CV-51; CV-52 CB via C-27 to CV-52
- CSPP: PM-7 CB via PM-7 VFD to PM-7; ME-66A CB via ME-66A VFD to ME-66A; ME-66B CB via ME-66B VFD to ME-66B; ME-63 CB via FDR TO ME-63 to ME-63; ME-64 CB via FDR TO ME-64 to ME-64
- MCC-2 (fed via FDR FR ATS-1 TO MCC-2 and MCC-2 MAIN CB): PM-11 CB via PM-11 VFD to PM-11; PM-12 CB via PM-12 VFD to PM-12; PM-31 CB via PM-31 VFD to PM-31; PM-32 CB via PM-32 VFD to PM-32; PM-41 CB via PM-41 VFD to PM-41; PM-42 CB via PM-42 VFD to PM-42; SCCP CB via FDR TO SCCP to SCCP, FDR TO ME-10 to ME-10, and FDR TO ME-11 to ME-11; OP-1 CB to OP-1; PANEL ECBL CB to T-ECBL and ECBL
- MCC-3 (fed via FDR FR ATS-2 TO MCC-3 and MCC-3 MAIN CB): FDR TO FCP #1 to FCP #1; FDR TO FCP #2 to FCP #2; FDR TO UWCP to UWCP; FDR TO ESBH to ESBH, TX-1, and ESBL
Appendix D:
Equipment Duty Scenario Comparison Report
Pennoni
22
Short Circuit Equipment Duty - Scenario Comparison Report Worst Case Duty
EasyPower v11.0.1.8039 5/22/2025 12:54:43 PM
U:\Accounts\EGMAU\...\DESIGN\EGMAU25005.dez
Pennoni Associates Inc. (Serial #C2-49329-2L)
Page 1/4
| Bus Name | Equipment Name | Worst Case | Scenario | Fault Type | Vpu | Bus Base kV | Bus Ph | Manufacturer | Style | Test Standard | 1/2 Cycle Rating (kA) | 1/2 Cycle Duty (kA) | 1/2 Cycle Duty (%) | Comments |
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 800A FUSE DS BUS | 800A FUSE DS | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | Littelfuse | KLPC(L) | ANSI-SYM | 200.000 | 18.181 | -90.9% | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | Littelfuse | KLPC(L) | ANSI-SYM | 200.000 | 16.258 | -91.9% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | Littelfuse | KLPC(L) | ANSI-SYM | 200.000 | 17.768 | -91.1% | ||||
| CBH | CBH MAIN CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SGL4 | ANSI-SYM | 65.000 | 18.098 | -72.2% | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SGL4 | ANSI-SYM | 65.000 | 16.437 | -74.7% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SGL4 | ANSI-SYM | 65.000 | 8.075 | -87.6% | ||||
| CSPP CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 18.175 | -72.0% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 16.515 | -74.6% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 8.157 | -87.5% | ||||
| CV-51 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 19.190 | 37.1% | VIOLATION | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 17.501 | 25.0% | VIOLATION | |||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 8.996 | -35.7% | ||||
| CV-52 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 19.190 | 37.1% | VIOLATION | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 17.501 | 25.0% | VIOLATION | |||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 8.996 | -35.7% | ||||
| EF-3 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 19.195 | 37.1% | VIOLATION | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 17.506 | 25.0% | VIOLATION | |||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 9.003 | -35.7% | ||||
| EF-4 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 19.173 | 37.0% | VIOLATION | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 17.484 | 24.9% | VIOLATION | |||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 8.978 | -35.9% | ||||
| ME-65 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 19.184 | 37.0% | VIOLATION | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 17.495 | 25.0% | VIOLATION | |||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 8.990 | -35.8% | ||||
| OH DOOR CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 19.199 | 37.1% | VIOLATION | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 17.510 | 25.1% | VIOLATION | |||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 9.007 | -35.7% | ||||
| CSPP | ME-61A CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 12.796 | -28.9% | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 12.022 | -33.2% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 6.563 | -63.5% | ||||
| ME-61B | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 12.796 | -28.9% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 12.022 | -33.2% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 6.563 | -63.5% | ||||
| ME-63 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 12.778 | -29.0% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 12.004 | -33.3% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 6.545 | -63.6% | ||||
| ME-64 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 12.778 | -29.0% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 12.004 | -33.3% |
Short Circuit Equipment Duty - Scenario Comparison Report Worst Case Duty
EasyPower v11.0.1.8039 5/22/2025 12:54:43 PM
U:\Accounts\EGMAU\...\DESIGN\EGMAU25005.dez
Pennoni Associates Inc. (Serial #C2-49329-2L)
Page 2/4
| Bus Name | Equipment Name | Worst Case | Scenario | Fault Type | Vpu | Bus Base kV | Bus Ph | Manufacturer | Style | Test Standard | 1/2 Cycle Rating (kA) | 1/2 Cycle Duty (kA) | 1/2 Cycle Duty (%) | Comments |
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 6.545 | -63.6% | ||||
| P-61 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 12.796 | -28.9% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 12.022 | -33.2% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SEDA 3P | ANSI-SYM | 18.000 | 6.563 | -63.5% | ||||
| ECBL | [Main] | X | Base Case | 3-Phase | 1.00 | 0.208 | 3 | SQD | QO | ANSI-SYM | 10.000 | 0.907 | -90.9% | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.208 | 3 | SQD | QO | ANSI-SYM | 10.000 | 0.905 | -90.9% | ||||
| Generator | 3-Phase | 1.00 | 0.208 | 3 | SQD | QO | ANSI-SYM | 10.000 | 0.883 | -91.2% | ||||
| ESBH | [Lowest] | X | Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | TEY | ANSI-SYM | 14.000 | 7.096 | -49.3% | |
| Base Case | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 42.000 | 11.390 | -72.9% | ||||||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 42.000 | 10.836 | -74.2% | ||||||
| [Main] | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SGLA 3P | ANSI-SYM | 65.000 | 11.390 | -82.5% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SGLA 3P | ANSI-SYM | 65.000 | 10.836 | -83.3% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SGLA 3P | ANSI-SYM | 65.000 | 7.096 | -89.1% | ||||
| ESBL | [Lowest] | X | Base Case | 3-Phase | 1.00 | 0.208 | 3 | ANSI-SYM | 22.000 | 2.631 | -88.0% | |||
| 50 Percent Utility | 3-Phase | 1.00 | 0.208 | 3 | ANSI-SYM | 22.000 | 2.616 | -88.1% | ||||||
| Generator | 3-Phase | 1.00 | 0.208 | 3 | ANSI-SYM | 22.000 | 2.473 | -88.8% | ||||||
| [Main] | X | Base Case | 3-Phase | 1.00 | 0.208 | 3 | GE | THQB | ANSI-SYM | 22.000 | 2.631 | -88.0% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.208 | 3 | GE | THQB | ANSI-SYM | 22.000 | 2.616 | -88.1% | ||||
| Generator | 3-Phase | 1.00 | 0.208 | 3 | GE | THQB | ANSI-SYM | 22.000 | 2.473 | -88.8% | ||||
| FCP #1 | [Main] | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | SQD | FAL | ANSI-SYM | 18.000 | 2.097 | -88.4% | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | SQD | FAL | ANSI-SYM | 18.000 | 2.088 | -88.4% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | SQD | FAL | ANSI-SYM | 18.000 | 2.036 | -88.7% | ||||
| FCP #2 | [Main] | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | SQD | FAL | ANSI-SYM | 18.000 | 2.097 | -88.4% | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | SQD | FAL | ANSI-SYM | 18.000 | 2.088 | -88.4% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | SQD | FAL | ANSI-SYM | 18.000 | 2.036 | -88.7% | ||||
| GEN-1 | GEN-1 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | SQD | PJ-800 AF | ANSI-SYM | 65.000 | 7.404 | -88.6% | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | SQD | PJ-800 AF | ANSI-SYM | 65.000 | 7.404 | -88.6% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | SQD | PJ-800 AF | ANSI-SYM | 65.000 | 7.042 | -89.2% | ||||
| GEN-2 | GEN-2 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | SQD | PJ | ANSI-SYM | 65.000 | 10.054 | -84.5% | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | SQD | PJ | ANSI-SYM | 65.000 | 10.054 | -84.5% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | SQD | PJ | ANSI-SYM | 65.000 | 9.768 | -85.0% | ||||
| MCC-1 | B-1A BREAKER | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 19.065 | 5.9% | VIOLATION |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 17.360 | -3.6% | Warning | |||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 8.742 | -51.4% | ||||
| B-1B BREAKER | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 19.063 | 5.9% | VIOLATION | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 17.359 | -3.6% | Warning | |||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 8.740 | -51.4% | ||||
| B-1C BREAKER | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 19.065 | 5.9% | VIOLATION |
Short Circuit Equipment Duty - Scenario Comparison Report Worst Case Duty
EasyPower v11.0.1.8039 5/22/2025 12:54:43 PM
U:\Accounts\EGMAU\...\DESIGN\EGMAU25005.dez
Pennoni Associates Inc. (Serial #C2-49329-2L)
Page 3/4
| Bus Name | Equipment Name | Worst Case | Scenario | Fault Type | Vpu | Bus Base kV | Bus Ph | Manufacturer | Style | Test Standard | 1/2 Cycle Rating (kA) | 1/2 Cycle Duty (kA) | 1/2 Cycle Duty (%) | Comments |
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 17.360 | -3.6% | Warning | |||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 8.742 | -51.4% | ||||
| B-2 BREAKER | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 19.065 | 5.9% | VIOLATION | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 17.360 | -3.6% | Warning | |||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 8.742 | -51.4% | ||||
| MCC-1 MAIN CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SGL4 | ANSI-SYM | 65.000 | 17.149 | -73.6% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SGL4 | ANSI-SYM | 65.000 | 15.478 | -76.2% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SGL4 | ANSI-SYM | 65.000 | 6.967 | -89.3% | ||||
| PANEL PR1 BREAKER | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 19.374 | 7.6% | VIOLATION | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 17.671 | -1.8% | Warning | |||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | SQD | FA | ANSI-SYM | 18.000 | 9.101 | -49.4% | ||||
| MCC-2 | MCC-2 MAIN CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SGL6 | ANSI-SYM | 65.000 | 18.782 | -71.1% | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SGL6 | ANSI-SYM | 65.000 | 16.990 | -73.9% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SGL6 | ANSI-SYM | 65.000 | 8.199 | -87.4% | ||||
| OF-1 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 18.822 | -71.0% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 17.029 | -73.8% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 8.240 | -87.3% | ||||
| P-11 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 18.949 | -70.8% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 17.156 | -73.6% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 8.380 | -87.1% | ||||
| P-12 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 18.949 | -70.8% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 17.156 | -73.6% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 8.380 | -87.1% | ||||
| P-13 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 18.949 | -70.8% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 17.156 | -73.6% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 8.380 | -87.1% | ||||
| P-41 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 18.949 | -70.8% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 17.156 | -73.6% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 8.380 | -87.1% | ||||
| P-42 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 18.949 | -70.8% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 17.156 | -73.6% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 8.380 | -87.1% | ||||
| P-43 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 18.949 | -70.8% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 17.156 | -73.6% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 8.380 | -87.1% | ||||
| PANEL ECBL CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 18.949 | -70.8% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 17.156 | -73.6% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 8.380 | -87.1% |
Short Circuit Equipment Duty - Scenario Comparison Report Worst Case Duty
EasyPower v11.0.1.8039 5/22/2025 12:54:43 PM
U:\Accounts\EGMAU\...\DESIGN\EGMAU25005.dez
Pennoni Associates Inc. (Serial #C2-49329-2L)
Page 4/4
| Bus Name | Equipment Name | Worst Case | Scenario | Fault Type | Vpu | Bus Base kV | Bus Ph | Manufacturer | Style | Test Standard | 1/2 Cycle Rating (kA) | 1/2 Cycle Duty (kA) | 1/2 Cycle Duty (%) | Comments |
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| SCCP CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 18.909 | -70.9% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 17.117 | -73.7% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 8.339 | -87.2% | ||||
| MCC-3 | [Lowest] | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 42.000 | 18.411 | -56.2% | |||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 42.000 | 16.709 | -60.2% | ||||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 42.000 | 8.811 | -79.0% | ||||||
| [Main] | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SKL12 | ANSI-SYM | 65.000 | 17.937 | -72.4% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SKL12 | ANSI-SYM | 65.000 | 16.235 | -75.0% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SKL12 | ANSI-SYM | 65.000 | 8.795 | -86.5% | ||||
| MDP | ATS-1 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SKL8 | ANSI-SYM | 65.000 | 18.986 | -70.8% | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SKL8 | ANSI-SYM | 65.000 | 16.888 | -74.0% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SKL8 | ANSI-SYM | 65.000 | 18.716 | -71.2% | ||||
| ATS-2 | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SKL12 | ANSI-SYM | 65.000 | 19.969 | -69.3% | ||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SKL12 | ANSI-SYM | 65.000 | 17.868 | -72.5% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SKL12 | ANSI-SYM | 65.000 | 18.716 | -71.2% | ||||
| MDP | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 65.000 | 20.181 | -69.0% | ||||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 65.000 | 18.144 | -72.1% | ||||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 65.000 | 18.276 | -71.9% | ||||||
| MDP MAIN CB | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SS-20 | ANSI-SYM | 65.000 | 18.512 | -71.5% | |||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SS-20 | ANSI-SYM | 65.000 | 16.415 | -74.7% | ||||
| X | Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SS-20 | ANSI-SYM | 65.000 | 18.716 | -71.2% | |||
| OF-1 CB | OF-1 CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 18.822 | -71.0% | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 17.029 | -73.8% | ||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | GE | SELA 3P | ANSI-SYM | 65.000 | 8.240 | -87.3% | ||||
| PNL-1 | [Main] | X | Base Case | 3-Phase | 1.00 | 0.208 | 3 | SQD | QO | ANSI-SYM | 10.000 | 0.906 | -90.9% | |
| 50 Percent Utility | 3-Phase | 1.00 | 0.208 | 3 | SQD | QO | ANSI-SYM | 10.000 | 0.905 | -91.0% | ||||
| Generator | 3-Phase | 1.00 | 0.208 | 3 | SQD | QO | ANSI-SYM | 10.000 | 0.882 | -91.2% | ||||
| SCCP | SCCP MAIN CB | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 65.000 | 6.485 | -90.0% | |||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 65.000 | 6.358 | -90.2% | ||||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 65.000 | 4.992 | -92.3% | ||||||
| T-PECO PRI | FS-1 | X | Base Case | 3-Phase | 1.00 | 33.000 | 3 | S&C | SMU-20 | ANSI-SYM | 10.000 | 2.119 | -78.8% | |
| 50 Percent Utility | 3-Phase | 1.00 | 33.000 | 3 | S&C | SMU-20 | ANSI-SYM | 10.000 | 1.059 | -89.4% | ||||
| Generator | 3-Phase | 1.00 | 33.000 | 3 | S&C | SMU-20 | ANSI-SYM | 10.000 | 2.119 | -78.8% | ||||
| UWCP | [Lowest] | X | Base Case | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 42.000 | 4.433 | -89.4% | |||
| 50 Percent Utility | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 42.000 | 4.383 | -89.6% | ||||||
| Generator | 3-Phase | 1.00 | 0.480 | 3 | ANSI-SYM | 42.000 | 3.978 | -90.5% |
Appendix E:
Time-Current Curves of Selected Protective Device Coordination
Pennoni
27
EasyPower® TIME-CURRENT CURVES: ~MCC-1 GENERATOR
[Time-current coordination curve graph and accompanying single-line diagram for ~MCC-1 GENERATOR.]
Title Block
- Pennoni Associates Inc.
- EasyPower® TIME-CURRENT CURVES
- ~MCC-1 GENERATOR
- FAULT:
- DATE: 5/7/2025
- BY:
- REVISION: 1
- EGMAU25005
Graph Axes
- Horizontal Axis: CURRENT IN AMPERES X 10 AT 480 VOLTS (.5 .6 .8 1 2 3 4 5 6 7 8 9 10 2 3 4 5 6 7 8 9 100 2 3 4 5 6 7 8 9 1000 2 3 4 5 6 7 8 9 10000)
- Vertical Axis: TIME IN SECONDS (.01 .02 .03 .04 .05 .06 .07 .08 .09 .1 .2 .3 .4 .5 .6 .7 .8 .9 1 2 3 4 5 6 7 8 9 10 20 30 40 50 60 70 80 90 100 200 300 400 500 600 700 800 900 1000)
Curve Annotations and Settings
- GEN-1 FLA
- GEN-1 CB : Square D Elect.Trip 1.0I, Sensor = 800, Plug = 800, Cur Set = 1 (800A), LT Band = Fixed, Inst = 1.5 (1200A)
- MCC-1 MAIN CB : GE Spectra RMS, Frame = 400AF(400), Plug = 400, Cur Set = 1 (400A), LT Band = Fixed, STPU = Max (2000A), ST Delay = Fixed, ST Delay I²t = In, Inst = 4080A
- B-1A BREAKER : SQD F Frame, FA, Frame = 100A (100AT), Trip = 100
- GEN-1
- B-1A : 50HP, Induction, Full Voltage
- FDR FR GEN-1 TO ATS-1 : 3 - 300 kcmil CU
- FDR FR 800 DS SW TO MCC1-2 : 1 - 500 kcmil CU
- FED FR 800 DS SW TO MCC1-1 : 1 - 500 kcmil CU
- MCC-1 MAIN CB / B-1A BREAKER : 6967A / 8622A
One-Line Diagram Labels
- GEN-1 (562.5 kVA, 11%, 15%, 9%)
- GEN-1 CB (SQD PJ-800 AF, 800/800A)
- GEN-1
- FDR FR GEN-1 TO ATS-1
- ATS-1
- FED FR 800 DS SW TO MCC1-1
- FDR TO MCC-1
- FDR FR 800 DS SW TO MCC1-2
- MCC-1 MAIN CB (GE SGL4, 400/400A)
- MCC-1
- B-1A BREAKER (SQD FA, 100/100A)
- B-1A (50 HP, Induction, 16.7%)
EasyPower® TIME-CURRENT CURVES: ~MCC-2 GENERATOR
[Time-current coordination curve graph and accompanying single-line diagram for ~MCC-2 GENERATOR.]
Title Block
- Pennoni Associates Inc.
- EasyPower® TIME-CURRENT CURVES
- ~MCC-2 GENERATOR
- FAULT:
- DATE: 5/22/2025
- BY:
- REVISION: 1
- EGMAU25005
Graph Axes
- Horizontal Axis: CURRENT IN AMPERES X 10 AT 480 VOLTS (.5 .6 .8 1 2 3 4 5 6 7 8 9 10 2 3 4 5 6 7 8 9 100 2 3 4 5 6 7 8 9 1000 2 3 4 5 6 7 8 9 10000)
- Vertical Axis: TIME IN SECONDS (.01 .02 .03 .04 .05 .06 .07 .08 .09 .1 .2 .3 .4 .5 .6 .7 .8 .9 1 2 3 4 5 6 7 8 9 10 20 30 40 50 60 70 80 90 100 200 300 400 500 600 700 800 900 1000)
Curve Annotations and Settings
- GEN-1 FLA
- OF-1 : 25HP, Induction, Full Voltage
- GEN-1
- GEN-1 CB : Square D Elect.Trip 1.0, Sensor = 800, Plug = 800, Cur Set = 1 (800A), LT Band = Fixed, Inst = 1.5 (1200A)
- OF-1 CB : GE Spectra RMS, Frame = 60A (50AT), Plug = 50, Cur Set = 1 (50A), LT Band = Fixed, STPU = Max (350A), ST Delay = Fixed, ST Delay I²t = In, Inst = 637A
- MCC-2 MAIN CB : GE Spectra RMS, Frame = 600AF(400), Plug = 400, Cur Set = 1 (400A), LT Band = Fixed, STPU = Max (2000A), ST Delay = Fixed, ST Delay I²t = In, Inst = 4050A
- FDR FR ATS-1 TO MCC-2 / FDR FR GEN-1 TO ATS-1 : 2 - 250 kcmil CU / 3 - 300 kcmil CU
- OF-1 CB / MCC-2 MAIN CB : 8199A / 8240A
One-Line Diagram Labels
- GEN-1 (562.5 kVA, 11%, 15%, 9%)
- GEN-1 CB (SQD PJ-800 AF, 800/800A)
- GEN-1
- FDR FR GEN-1 TO ATS-1
- ATS-1
- FDR FR ATS-1 TO MCC-2
- MCC-2 MAIN CB (GE SGL6, 400/600A)
- MCC-2
- OF-1 CB (GE SELA 3P, 150/50A)
- OF-1 CB
- OF-1 DS (60 A)
- OF-1 (25 HP, Induction, 16.7%)
EasyPower® TIME-CURRENT CURVES: ~MCC-3 GENERATOR
[Time-current coordination curve graph and accompanying single-line diagram for ~MCC-3 GENERATOR.]
Title Block
- Pennoni Associates Inc.
- EasyPower® TIME-CURRENT CURVES
- ~MCC-3 GENERATOR
- FAULT:
- DATE: 5/7/2025
- BY:
- REVISION: 1
- EGMAU25005
Graph Axes
- Horizontal Axis: CURRENT IN AMPERES X 10 AT 480 VOLTS (.5 .6 .8 1 2 3 4 5 6 7 8 9 10 2 3 4 5 6 7 8 9 100 2 3 4 5 6 7 8 9 1000 2 3 4 5 6 7 8 9 10000)
- Vertical Axis: TIME IN SECONDS (.01 .02 .03 .04 .05 .06 .07 .08 .09 .1 .2 .3 .4 .5 .6 .7 .8 .9 1 2 3 4 5 6 7 8 9 10 20 30 40 50 60 70 80 90 100 200 300 400 500 600 700 800 900 1000)
Curve Annotations and Settings
- GEN-2 FLA
- GEN-2
- MCC-3 - Main : GE Spectra RMS, Frame = 1200AF(1000), Plug = 1000, Cur Set = 1 (1000A), LT Band = Fixed, STPU = Max (5000A), ST Delay = Fixed, ST Delay I²t = In, Inst = 10180A
- MCC-3 - ESBH : GE Spectra RMS, Frame = 250AF(200), Plug = 200, Cur Set = 1 (200A), LT Band = Fixed, STPU = Max (1000A), ST Delay = Fixed, ST Delay I²t = In, Inst = 2000A
- MCC-3 - FCP #2 : GE Spectra RMS, Frame = 30A (20AT), Plug = 20, Cur Set = 1 (20A), LT Band = Fixed, STPU = Max (137A), ST Delay = Fixed, ST Delay I²t = In, Inst = 254A
- MCC-3 - FCP #1 : GE Spectra RMS, Frame = 30A (20AT), Plug = 20, Cur Set = 1 (20A), LT Band = Fixed, STPU = Max (137A), ST Delay = Fixed, ST Delay I²t = In, Inst = 254A
- MCC-3 - UWCP : GE Spectra RMS, Frame = 60A (40AT), Plug = 40, Cur Set = 1 (40A), LT Band = Fixed, STPU = Max (256A), ST Delay = Fixed, ST Delay I²t = In, Inst = 501A
- FDR FR GEN-2 TO ATS-2 : 3 - 500 kcmil CU
- GEN-2 CB : Square D Elect.Trip 1.0I, Sensor = 1000, Plug = 1000, Cur Set = 1 (1000A), LT Band = Fixed, Inst = 1.5 (1500A)
- FDR FR ATS-2 TO MCC-3 : 3 - 500 kcmil CU
- MCC-3 - Main / MCC-3 - FCP #2 : 8795A / 11858A
One-Line Diagram Labels
- GEN-2 (625 kVA, 9%, 13%, 8%)
- GEN-2 CB (SQD PJ, 1200/1000A)
- GEN-2
- FDR FR GEN-2 TO ATS-2
- ATS-2
- FDR FR ATS-2 TO MCC-3
- MCC-3 (MCC, 217 HP, 0 kVA)
EasyPower® TIME-CURRENT CURVES: MCC-1
[Time-current coordination curve graph and accompanying single-line diagram for MCC-1.]
Title Block
- Pennoni Associates Inc.
- EasyPower® TIME-CURRENT CURVES
- MCC-1
- FAULT:
- DATE: 5/7/2025
- BY:
- REVISION: 1
- EGMAU25005
Graph Axes
- Horizontal Axis: CURRENT IN AMPERES X 100 AT 480 VOLTS (.2 .3 .4 .5 .6 .8 1 2 3 4 5 6 7 8 9 10 2 3 4 5 6 7 8 9 100 2 3 4 5 6 7 8 9 1000 2 3 4 5 6 7)
- Vertical Axis: TIME IN SECONDS (.01 .02 .03 .04 .05 .06 .07 .08 .09 .1 .2 .3 .4 .5 .6 .7 .8 .9 1 2 3 4 5 6 7 8 9 10 20 30 40 50 60 70 80 90 100 200 300 400 500 600 700 800 900 1000 2000 3000)
Curve Annotations and Settings
- T-PECO FLA
- T-PECO : 1000 kVA, 5.72%
- FS-1 : S&C, SMU, SMU-20, 80E
- B-1A BREAKER : SQD F Frame, FA, Frame = 100A (100AT), Trip = 100
- B-1A : 50HP, Induction, Full Voltage
- MCC-1 MAIN CB : GE Spectra RMS, Frame = 400AF(400), Plug = 400, Cur Set = 1 (400A), LT Band = Fixed, STPU = Max (2000A), ST Delay = Fixed, ST Delay I²t = In, Inst = 4080A
- ATS-1 CB : GE Spectra RMS, Sensor = 800AF(800), Plug = 800, Cur Set = 1 (800A), LT Band = Fixed, STPU = Max (4000A), ST Delay = Fixed, ST Delay I²t = In, Inst = 6705A
- 800A FUSE DS : Littelfuse, POWR-PRO, KLPC(L), 800A
- MDP MAIN CB : GE MVT-PM, Sensor = 2000, Plug = 2000, Cur Set = 1 (2000A), LT Band = 3, STPU = 9 (18000A), ST Delay = Int, ST Delay I²t = Out, Inst = 15 (30000A)
- FDR FR MDP TO 800A DS : 3 - 300 kcmil CU
- FED FR 800 DS SW TO MCC1-1 : 1 - 500 kcmil CU
- FDR FR 800A DS TO ATS-1 : 3 - 300 kcmil CU
- T-PECO : 1000 kVA, INRUSH
- FDR T-PECO TO MDP : 5 - 500 kcmil CU
- FDR FR 800 DS SW TO MCC1-2 : 1 - 500 kcmil CU
- MCC-1 MAIN CB / B-1A BREAKER : 17149A / 18762A
- FS-1 : 2847A
One-Line Diagram Labels
- T-PECO PRI
- FS-1 (S&C SMU-20, 80E)
- T-PECO (1000 kVA, 33 - 0.48 kV, 5.72%)
- T-PECO SEC
- FDR T-PECO TO MDP
- MDP MAIN CB (GE SS-20, 2000/2000A)
- MDP
- ATS-1 CB (GE SKL8, 800/800A)
- FDR FR MDP TO 800A DS
- 800A FUSE DS (Littelfuse KLPC(L), 800A)
- 800A FUSE DS BUS
- FDR FR 800A DS TO ATS-1
- ATS-1
- FED FR 800 DS SW TO MCC1-1
- FDR TO MCC-1
- FDR FR 800 DS SW TO MCC1-2
- MCC-1 MAIN CB (GE SGL4, 400/400A)
- MCC-1
- B-1A BREAKER (SQD FA, 100/100A)
- B-1A (50 HP, Induction, 16.7%)
EasyPower® TIME-CURRENT CURVES: MCC-3
[Time-current coordination curve graph and accompanying single-line diagram for MCC-3.]
Title Block
- Pennoni Associates Inc.
- EasyPower® TIME-CURRENT CURVES
- MCC-3
- FAULT:
- DATE: 5/8/2025
- BY:
- REVISION: 1
- EGMAU25005
Graph Axes
- Horizontal Axis: CURRENT IN AMPERES X 100 AT 480 VOLTS (.5 .6 .8 1 2 3 4 5 6 7 8 9 10 2 3 4 5 6 7 8 9 100 2 3 4 5 6 7 8 9 1000 2 3 4 5 6 7 8 9 10000)
- Vertical Axis: TIME IN SECONDS (.01 .02 .03 .04 .05 .06 .07 .08 .09 .1 .2 .3 .4 .5 .6 .7 .8 .9 1 2 3 4 5 6 7 8 9 10 20 30 40 50 60 70 80 90 100 200 300 400 500 600 700 800 900 1000)
Curve Annotations and Settings
- T-PECO FLA
- FS-1 : S&C, SMU, SMU-20, 80E
- T-PECO : 1000 kVA, 5.72%
- MDP MAIN CB : GE MVT-PM, Sensor = 2000, Plug = 2000, Cur Set = 1 (2000A), LT Band = 3, STPU = 9 (18000A), ST Delay = Int, ST Delay I²t = Out, Inst = 15 (30000A)
- MCC-3 - UWCP : GE Spectra RMS, Frame = 60A (40AT), Plug = 40, Cur Set = 1 (40A), LT Band = Fixed, STPU = Max (256A), ST Delay = Fixed, ST Delay I²t = In, Inst = 501A
- MCC-3 - ESBH : GE Spectra RMS, Frame = 250AF(200), Plug = 200, Cur Set = 1 (200A), LT Band = Fixed, STPU = Max (1000A), ST Delay = Fixed, ST Delay I²t = In, Inst = 2000A
- MCC-3 - Main : GE Spectra RMS, Sensor = 1200AF(1000), Plug = 1000, Cur Set = 1 (1000A), LT Band = Fixed, STPU = Max (5000A), ST Delay = Fixed, ST Delay I²t = In, Inst = 10180A
- MCC-3 - FCP #1 : GE Spectra RMS, Frame = 30A (20AT), Plug = 20, Cur Set = 1 (20A), LT Band = Fixed, STPU = Max (137A), ST Delay = Fixed, ST Delay I²t = In, Inst = 254A
- ATS-2 : GE Spectra RMS, Sensor = 1200AF(1000), Plug = 1000, Cur Set = 1 (1000A), LT Band = Fixed, STPU = Max (5000A), ST Delay = Fixed, ST Delay I²t = In, Inst = 10180A
- MCC-3 - FCP #2 : GE Spectra RMS, Frame = 30A (20AT), Plug = 20, Cur Set = 1 (20A), LT Band = Fixed, STPU = Max (137A), ST Delay = Fixed, ST Delay I²t = In, Inst = 254A
- T-PECO : 1000 kVA, INRUSH
- FDR T-PECO TO MDP : 5 - 500 kcmil CU
- FDR FR MDP TO ATS-2 : 3 - 500 kcmil CU
- FDR FR ATS-2 TO MCC-3 : 3 - 500 kcmil CU
- MCC-3 - Main / MCC-3 - FCP #2 : 17937A / 21985A
- FS-1 : 2847A
One-Line Diagram Labels
- T-PECO PRI
- FS-1 (S&C SMU-20, 80E)
- T-PECO (1000 kVA, 33 - 0.48 kV, 5.72%)
- T-PECO SEC
- FDR T-PECO TO MDP
- MDP MAIN CB (GE SS-20, 2000/2000A)
- MDP
- ATS-2 (GE SKL12, 1200/1000A)
- FDR FR MDP TO ATS-2
- ATS-2
- FDR FR ATS-2 TO MCC-3
- MCC-3 (MCC, 217 HP, 0 kVA)
Appendix F:
Arc Flash Hazard Scenario Comparison Report
Pennoni
33
Arc Flash Hazard - Scenario Comparison Report
EasyPower v11.0.1.8039 5/22/2025 12:49:04 PM
U:\Accounts\EGMAU\...\DESIGN\EGMAU25005.dez
Pennoni Associates Inc. (Serial #C2-49329-2L)
Page 1/6
| Arc Fault Bus Name | Worst Case | Scenario | Arc Fault Bus kV | Upstream Trip Device Name | Equip Type | Electrode Configuration | Electrode Gap (mm) | Bus Bolted Fault (kA) | Bus Arc Fault (kA) | Trip Time (sec) | Arc Time (sec) | Est Arc Flash Boundary (inches) | Working Distance (inches) | Incident Energy (cal/cm2) | PPE Level | Comments |
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| Bus: 800A FUSE DS BUS | ||||||||||||||||
| 800A FUSE DS BUS | X | 50 Percent Utility | 0.48 | ATS-1 CB | Other | VCB | 32 | 15.816 | 10.402 | 0.167 | 0.167 | 41.2 | 18 | 4.5 | 2 | |
| 800A FUSE DS BUS | Base Case | 0.48 | ATS-1 CB | Other | VCB | 32 | 18.211 | 13.630 | 0.026 | 0.026 | 15.6 | 18 | 1 | |||
| 800A FUSE DS BUS | Generator | 0.48 | ATS-1 CB | Other | VCB | 32 | 17.743 | 13.288 | 0.026 | 0.026 | 14.9 | 18 | 0.9 | |||
| Bus: ATS-1 | ||||||||||||||||
| ATS-1 | X | 50 Percent Utility | 0.48 | ATS-1 CB | ATS | VCB | 32 | 15.544 | 10.224 | 0.173 | 0.173 | 41.6 | 18 | 4.6 | 2 | |
| ATS-1 | Base Case | 0.48 | ATS-1 CB | ATS | VCB | 32 | 17.869 | 13.380 | 0.027 | 0.027 | 15.5 | 18 | 0.9 | |||
| ATS-1 | Generator | 0.48 | GEN-1 CB | ATS | VCB | 32 | 6.536 | 4.773 | 0.05 | 0.05 | 11.6 | 18 | 0.6 | |||
| Bus: ATS-2 | ||||||||||||||||
| ATS-2 | X | 50 Percent Utility | 0.48 | ATS-2 | ATS | VCB | 32 | 15.132 | 9.953 | 0.284 | 0.284 | 55.4 | 18 | 7.2 | 2 | |
| ATS-2 | Base Case | 0.48 | ATS-2 | ATS | VCB | 32 | 16.885 | 11.098 | 0.229 | 0.229 | 52 | 18 | 6.5 | 2 | ||
| ATS-2 | Generator | 0.48 | GEN-2 CB | ATS | VCB | 32 | 7.897 | 5.818 | 0.05 | 0.05 | 13 | 18 | 0.7 | |||
| Bus: CBH | ||||||||||||||||
| CBH | X | 50 Percent Utility | 0.48 | ATS-1 CB | Panelboard | VCB | 25 | 14.844 | 10.032 | 0.179 | 0.179 | 40 | 18 | 4.3 | 2 | |
| CBH | Base Case | 0.48 | ATS-1 CB | Panelboard | VCB | 25 | 16.948 | 11.445 | 0.031 | 0.031 | 14.7 | 18 | 0.9 | |||
| CBH | Generator | 0.48 | GEN-1 CB | Panelboard | VCB | 25 | 6.418 | 4.810 | 0.05 | 0.05 | 11.1 | 18 | 0.6 | |||
| Bus: CSPP | ||||||||||||||||
| CSPP | 50 Percent Utility | 0.48 | CSPP CB | Panelboard | VCB | 25 | 11.387 | 8.739 | 0.022 | 0.022 | 9.8 | 18 | 0.5 | |||
| CSPP | X | Base Case | 0.48 | CBH MAIN CB | Panelboard | VCB | 25 | 12.215 | 8.234 | 0.025 | 0.025 | 10.2 | 18 | 0.5 | ||
| CSPP | Generator | 0.48 | CSPP CB | Panelboard | VCB | 25 | 5.841 | 4.357 | 0.025 | 0.025 | 6.9 | 18 | 0.3 | |||
| Bus: CV-51 | ||||||||||||||||
| CV-51 | 50 Percent Utility | 0.48 | CV-51 CB | Other | VCB | 32 | 4.527 | 3.245 | 0.016 | 0.016 | 4.3 | 18 | 0.1 | |||
| CV-51 | X | Base Case | 0.48 | CV-51 CB | Other | VCB | 32 | 4.581 | 3.286 | 0.016 | 0.016 | 4.3 | 18 | 0.1 | ||
| CV-51 | Generator | 0.48 | CV-51 CB | Other | VCB | 32 | 3.935 | 2.801 | 0.016 | 0.016 | 3.9 | 18 | 0.1 | |||
| Bus: CV-52 | ||||||||||||||||
| CV-52 | 50 Percent Utility | 0.48 | CV-52 CB | Other | VCB | 32 | 4.527 | 3.245 | 0.016 | 0.016 | 4.3 | 18 | 0.1 | |||
| CV-52 | X | Base Case | 0.48 | CV-52 CB | Other | VCB | 32 | 4.581 | 3.286 | 0.016 | 0.016 | 4.3 | 18 | 0.1 | ||
| CV-52 | Generator | 0.48 | CV-52 CB | Other | VCB | 32 | 3.935 | 2.801 | 0.016 | 0.016 | 3.9 | 18 | 0.1 | |||
| Bus: EF-3 | ||||||||||||||||
| EF-3 | 50 Percent Utility | 0.48 | EF-3 CB | Other | VCB | 32 | 3.512 | 2.485 | 0.016 | 0.016 | 3.6 | 18 | 0.1 | |||
| EF-3 | X | Base Case | 0.48 | EF-3 CB | Other | VCB | 32 | 3.541 | 2.507 | 0.016 | 0.016 | 3.6 | 18 | 0.1 | ||
| EF-3 | Generator | 0.48 | EF-3 CB | Other | VCB | 32 | 3.207 | 2.259 | 0.016 | 0.016 | 3.4 | 18 | 0.1 | |||
The test results are a function of specific humidity, barometric pressure, temperature, arc distance, and many other variables. These parameters will NOT be the same in your application. These results should be applied only by experienced engineers in the application of Arc-flash hazards. EasyPower makes no warranty concerning the accuracy of these results as applied to real world scenarios.
For integrated calculations, the fault currents displayed are just before 'Arc Time'.
Page 2/6
Arc Flash Hazard - Scenario Comparison Report
EasyPower v11.0.1.8039 5/22/2025 12:49:04 PM
U:\Accounts\EGMAU\... \DESIGN\E\EGMAU25005.dez
Pennoni Associates Inc. (Serial #C2-49329-2L)
| Arc Fault Bus Name | Worst Case | Scenario | Arc Fault Bus kV | Upstream Trip Device Name | Equip Type | Electrode Configuration | Electrode Gap (mm) | Bus Bolted Fault (kA) | Bus Arc Fault (kA) | Trip Time (sec) | Arc Time (sec) | Est Arc Flash Boundary (inches) | Working Distance (inches) | Incident Energy (cal/cm2) | PPE Level | Comments |
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| EF-4 | 50 Percent Utility | 0.48 | EF-4 CB | Other | VCB | 32 | 2.428 | 1.686 | 0.016 | 0.016 | 2.8 | 18 | 0.1 | |||
| X | Base Case | 0.48 | EF-4 CB | Other | VCB | 32 | 2.440 | 1.695 | 0.016 | 0.016 | 2.8 | 18 | 0.1 | |||
| Generator | 0.48 | EF-4 CB | Other | VCB | 32 | 2.321 | 1.608 | 0.016 | 0.016 | 2.7 | 18 | 0.1 | ||||
| FDR TO CBH | X | 50 Percent Utility | 0.48 | ATS-1 CB | Other | VCB | 32 | 15.186 | 9.989 | 0.181 | 0.181 | 42.1 | 18 | 4.7 | 2 | |
| Base Case | 0.48 | ATS-1 CB | Other | VCB | 32 | 17.398 | 11.428 | 0.031 | 0.031 | 15.5 | 18 | 0.9 | ||||
| Generator | 0.48 | GEN-1 CB | Other | VCB | 32 | 6.477 | 4.728 | 0.05 | 0.05 | 11.6 | 18 | 0.6 | ||||
| FDR TO MCC-1 | X | 50 Percent Utility | 0.48 | ATS-1 CB | Other | VCB | 32 | 15.186 | 9.989 | 0.181 | 0.181 | 42.2 | 18 | 4.7 | 2 | |
| Base Case | 0.48 | ATS-1 CB | Other | VCB | 32 | 17.422 | 11.444 | 0.031 | 0.031 | 15.5 | 18 | 0.9 | ||||
| Generator | 0.48 | GEN-1 CB | Other | VCB | 32 | 6.486 | 4.735 | 0.05 | 0.05 | 11.6 | 18 | 0.6 | ||||
| GEN-1 | 50 Percent Utility | 0.48 | [Manual Time] | Other | VCB | 32 | 4.096 | 2.921 | 0 | 1000 | 4000.3 | 18 | 6751.5 | Extreme Danger | ||
| Base Case | 0.48 | [Manual Time] | Other | VCB | 32 | 4.096 | 2.921 | 0 | 1000 | 4000.3 | 18 | 6751.5 | Extreme Danger | |||
| X | Generator | 0.48 | [Manual Time] | Other | VCB | 32 | 4.096 | 2.921 | 0 | 1000 | 4000.4 | 18 | 6751.7 | Extreme Danger | ||
| GEN-2 | 50 Percent Utility | 0.48 | [Manual Time] | Other | VCB | 32 | 5.562 | 4.030 | 0 | 1000 | 4945.3 | 18 | 9474.9 | Extreme Danger | ||
| Base Case | 0.48 | [Manual Time] | Other | VCB | 32 | 5.562 | 4.030 | 0 | 1000 | 4945.3 | 18 | 9474.9 | Extreme Danger | |||
| X | Generator | 0.48 | [Manual Time] | Other | VCB | 32 | 5.562 | 4.030 | 0 | 1000 | 4945.3 | 18 | 9474.9 | Extreme Danger | ||
| MCC-1 | X | 50 Percent Utility | 0.48 | ATS-1 CB | Switchgear | VCB | 32 | 14.844 | 9.763 | 0.189 | 0.189 | 42.7 | 18 | 4.8 | 2 | |
| Base Case | 0.48 | ATS-1 CB | Switchgear | VCB | 32 | 16.995 | 11.169 | 0.033 | 0.033 | 15.7 | 18 | 1 | ||||
| Generator | 0.48 | GEN-1 CB | Switchgear | VCB | 32 | 6.436 | 4.697 | 0.05 | 0.05 | 11.5 | 18 | 0.6 | ||||
| MCC-2 | X | 50 Percent Utility | 0.48 | ATS-1 CB | Panel | VCB | 25 | 15.335 | 10.364 | 0.168 | 0.168 | 30.5 | 18 | 2.8 | 1 | |
| Base Case | 0.48 | ATS-1 CB | Panel | VCB | 25 | 17.593 | 13.541 | 0.027 | 0.027 | 11.5 | 18 | 0.6 | ||||
| Generator | 0.48 | GEN-1 CB | Panel | VCB | 25 | 6.504 | 4.877 | 0.05 | 0.05 | 8.7 | 18 | 0.4 |
The test results are a function of specific humidity, barometric pressure, temperature, arc distance, and many other variables. These parameters will NOT be the same in your application. These results should be applied only by experienced engineers in the application of Arc-flash hazards. EasyPower makes no warranty concerning the accuracy of these results as applied to real world scenarios.
For integrated calculations, the fault currents displayed are just before 'Arc Time'.
Arc Flash Hazard - Scenario Comparison Report
EasyPower v11.0.1.8039 5/22/2025 12:49:04 PM
U:\Accounts\EGMAU\...\DESIGN\E\EGMAU25005.dez
Pennoni Associates Inc. (Serial #C2-49329-2L)
Page 3/6
| Arc Fault Bus Name | Worst Case | Scenario | Arc Fault Bus kV | Upstream Trip Device Name | Equip Type | Electrode Configuration | Electrode Gap (mm) | Bus Bolted Fault (kA) | Bus Arc Fault (kA) | Trip Time (sec) | Arc Time (sec) | Est Arc Flash Boundary (inches) | Working Distance (inches) | Incident Energy (cal/cm2) | PPE Level | Comments |
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| Bus: MDP | ||||||||||||||||
| MDP | X | 50 Percent Utility | 0.48 | [Manual Time] | Switchgear | VCB | 32 | 16.238 | 12.179 | 0 | 1000 | 10281.7 | 18 | 30516.7 | Extreme Danger | |
| MDP | Base Case | 0.48 | [Manual Time] | Switchgear | VCB | 32 | 18.276 | 11.991 | 0 | 1000 | 10266.6 | 18 | 30444.9 | Extreme Danger | ||
| MDP | Generator | 0.48 | [Manual Time] | Switchgear | VCB | 32 | 18.276 | 11.991 | 0 | 1000 | 10266.6 | 18 | 30444.7 | Extreme Danger | ||
| Bus: ME-10 | ||||||||||||||||
| ME-10 | 50 Percent Utility | 0.48 | SCCP CB | Other | VCB | 32 | 3.502 | 2.478 | 0.025 | 0.025 | 4.8 | 18 | 0.1 | |||
| ME-10 | X | Base Case | 0.48 | SCCP CB | Other | VCB | 32 | 3.535 | 2.502 | 0.025 | 0.025 | 4.8 | 18 | 0.1 | ||
| ME-10 | Generator | 0.48 | SCCP CB | Other | VCB | 32 | 3.138 | 2.208 | 0.025 | 0.025 | 4.5 | 18 | 0.1 | |||
| Bus: ME-11 | ||||||||||||||||
| ME-11 | 50 Percent Utility | 0.48 | SCCP CB | Other | VCB | 32 | 3.502 | 2.478 | 0.025 | 0.025 | 4.8 | 18 | 0.1 | |||
| ME-11 | X | Base Case | 0.48 | SCCP CB | Other | VCB | 32 | 3.535 | 2.502 | 0.025 | 0.025 | 4.8 | 18 | 0.1 | ||
| ME-11 | Generator | 0.48 | SCCP CB | Other | VCB | 32 | 3.138 | 2.208 | 0.025 | 0.025 | 4.5 | 18 | 0.1 | |||
| Bus: ME-61A | ||||||||||||||||
| ME-61A | 50 Percent Utility | 0.48 | ME-61A VFD | Other | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.1 | 18 | 0 | Out of IEEE 1584-2018 range. | ||
| ME-61A | X | Base Case | 0.48 | ME-61A VFD | Other | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.1 | 18 | 0 | Out of IEEE 1584-2018 range. | |
| ME-61A | Generator | 0.48 | ME-61A VFD | Other | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.1 | 18 | 0 | Out of IEEE 1584-2018 range. | ||
| Bus: ME-61B | ||||||||||||||||
| ME-61B | 50 Percent Utility | 0.48 | ME-61B VFD | Other | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.1 | 18 | 0 | Out of IEEE 1584-2018 range. | ||
| ME-61B | X | Base Case | 0.48 | ME-61B VFD | Other | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.1 | 18 | 0 | Out of IEEE 1584-2018 range. | |
| ME-61B | Generator | 0.48 | ME-61B VFD | Other | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.1 | 18 | 0 | Out of IEEE 1584-2018 range. | ||
| Bus: ME-63 | ||||||||||||||||
| ME-63 | 50 Percent Utility | 0.48 | CBH MAIN CB | Other | VCB | 32 | 7.315 | 5.370 | 0.025 | 0.025 | 8 | 18 | 0.3 | |||
| ME-63 | X | Base Case | 0.48 | CBH MAIN CB | Other | VCB | 32 | 7.561 | 5.560 | 0.025 | 0.025 | 8.1 | 18 | 0.3 | ||
| ME-63 | Generator | 0.48 | ME-63 CB | Other | VCB | 32 | 4.976 | 3.585 | 0.025 | 0.025 | 6.3 | 18 | 0.2 | |||
| Bus: ME-64 | ||||||||||||||||
| ME-64 | 50 Percent Utility | 0.48 | CBH MAIN CB | Other | VCB | 32 | 7.315 | 5.370 | 0.025 | 0.025 | 8 | 18 | 0.3 | |||
| ME-64 | X | Base Case | 0.48 | CBH MAIN CB | Other | VCB | 32 | 7.561 | 5.560 | 0.025 | 0.025 | 8.1 | 18 | 0.3 | ||
| ME-64 | Generator | 0.48 | ME-64 CB | Other | VCB | 32 | 4.976 | 3.585 | 0.025 | 0.025 | 6.3 | 18 | 0.2 | |||
The test results are a function of specific humidity, barometric pressure, temperature, arc distance, and many other variables.
These parameters will NOT be the same in your application. These results should be applied only by experienced engineers in the application of Arc-flash hazards. EasyPower makes no warranty concerning the accuracy of these results as applied to real world scenarios.
For integrated calculations, the fault currents displayed are just before 'Arc Time'.
Page 4/6
Arc Flash Hazard - Scenario Comparison Report
EasyPower v11.0.1.8039 5/22/2025 12:49:04 PM
U:\Accounts\EGMAU\... \DESIGN\E\EGMAU25005.dez
Pennoni Associates Inc. (Serial #C2-49329-2L)
| Arc Fault Bus Name | Worst Case | Scenario | Arc Fault Bus kV | Upstream Trip Device Name | Equip Type | Electrode Configuration | Electrode Gap (mm) | Bus Bolted Fault (kA) | Bus Arc Fault (kA) | Trip Time (sec) | Arc Time (sec) | Est Arc Flash Boundary (inches) | Working Distance (inches) | Incident Energy (cal/cm2) | PPE Level | Comments |
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| ME-65 | 50 Percent Utility | 0.48 | ME-65 CB | Other | VCB | 32 | 3.518 | 2.489 | 0.016 | 0.016 | 3.6 | 18 | 0.1 | |||
| X | Base Case | 0.48 | ME-65 CB | Other | VCB | 32 | 3.547 | 2.511 | 0.016 | 0.016 | 3.6 | 18 | 0.1 | |||
| Generator | 0.48 | ME-65 CB | Other | VCB | 32 | 3.215 | 2.264 | 0.016 | 0.016 | 3.4 | 18 | 0.1 | ||||
| OF-1 CB | 50 Percent Utility | 0.48 | MCC-2 MAIN CB | Other | VCB | 32 | 15.791 | 11.846 | 0.025 | 0.025 | 13.8 | 18 | 0.8 | |||
| X | Base Case | 0.48 | MCC-2 MAIN CB | Other | VCB | 32 | 17.593 | 13.178 | 0.025 | 0.025 | 14.8 | 18 | 0.9 | |||
| Generator | 0.48 | GEN-1 CB | Other | VCB | 32 | 6.504 | 4.748 | 0.05 | 0.05 | 11.6 | 18 | 0.6 | ||||
| OH DOOR | 50 Percent Utility | 0.48 | OH DOOR CB | Other | VCB | 32 | 2.414 | 1.676 | 0.016 | 0.016 | 2.8 | 18 | 0.1 | |||
| X | Base Case | 0.48 | OH DOOR CB | Other | VCB | 32 | 2.426 | 1.685 | 0.016 | 0.016 | 2.8 | 18 | 0.1 | |||
| Generator | 0.48 | OH DOOR CB | Other | VCB | 32 | 2.304 | 1.596 | 0.016 | 0.016 | 2.7 | 18 | 0.1 | ||||
| P-11 | 50 Percent Utility | 0.48 | P11-VFD | VFD | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.2 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| X | Base Case | 0.48 | P11-VFD | VFD | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.2 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| Generator | 0.48 | P11-VFD | VFD | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.2 | 18 | 0 | Out of IEEE 1584 -2018 range. | |||
| P-12 | 50 Percent Utility | 0.48 | P12-VFD | VFD | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.2 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| X | Base Case | 0.48 | P12-VFD | VFD | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.2 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| Generator | 0.48 | P12-VFD | VFD | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.2 | 18 | 0 | Out of IEEE 1584 -2018 range. | |||
| P-13 | 50 Percent Utility | 0.48 | P13 VFD | VFD | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.2 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| X | Base Case | 0.48 | P13 VFD | VFD | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.2 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| Generator | 0.48 | P13 VFD | VFD | VCB | 32 | 0.054 | 0.032 | 0.2 | 0.2 | 1.2 | 18 | 0 | Out of IEEE 1584 -2018 range. | |||
| P-41 | 50 Percent Utility | 0.48 | P-41 VFD | VFD | VCB | 32 | 0.027 | 0.015 | 0.2 | 0.2 | 0.7 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| X | Base Case | 0.48 | P-41 VFD | VFD | VCB | 32 | 0.027 | 0.015 | 0.2 | 0.2 | 0.7 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| Generator | 0.48 | P-41 VFD | VFD | VCB | 32 | 0.027 | 0.015 | 0.2 | 0.2 | 0.7 | 18 | 0 | Out of IEEE 1584 -2018 range. |
The test results are a function of specific humidity, barometric pressure, temperature, arc distance, and many other variables. These parameters will NOT be the same in your application. These results should be applied only by experienced engineers in the application of Arc-flash hazards. EasyPower makes no warranty concerning the accuracy of these results as applied to real world scenarios.
For integrated calculations, the fault currents displayed are just before 'Arc Time'.
Page 5/6
Arc Flash Hazard - Scenario Comparison Report
EasyPower v11.0.1.8039 5/22/2025 12:49:04 PM
U:\Accounts\EGMAU\... \DESIGN\E\EGMAU25005.dez
Pennoni Associates Inc. (Serial #C2-49329-2L)
| Arc Fault Bus Name | Worst Case | Scenario | Arc Fault Bus kV | Upstream Trip Device Name | Equip Type | Electrode Configuration | Electrode Gap (mm) | Bus Bolted Fault (kA) | Bus Arc Fault (kA) | Trip Time (sec) | Arc Time (sec) | Est Arc Flash Boundary (inches) | Working Distance (inches) | Incident Energy (cal/cm2) | PPE Level | Comments |
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| P-42 | 50 Percent Utility | 0.48 | P-42 VFD | VFD | VCB | 32 | 0.027 | 0.015 | 0.2 | 0.2 | 0.7 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| X | Base Case | 0.48 | P-42 VFD | VFD | VCB | 32 | 0.027 | 0.015 | 0.2 | 0.2 | 0.7 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| Generator | 0.48 | P-42 VFD | VFD | VCB | 32 | 0.027 | 0.015 | 0.2 | 0.2 | 0.7 | 18 | 0 | Out of IEEE 1584 -2018 range. | |||
| P-43 | 50 Percent Utility | 0.48 | P-43 VFD | VFD | VCB | 32 | 0.027 | 0.015 | 0.2 | 0.2 | 0.7 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| X | Base Case | 0.48 | P-43 VFD | VFD | VCB | 32 | 0.027 | 0.015 | 0.2 | 0.2 | 0.7 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| Generator | 0.48 | P-43 VFD | VFD | VCB | 32 | 0.027 | 0.015 | 0.2 | 0.2 | 0.7 | 18 | 0 | Out of IEEE 1584 -2018 range. | |||
| P-61 | 50 Percent Utility | 0.48 | P-61 VFD | Other | VCB | 32 | 0.014 | 0.007 | 0.2 | 0.2 | 0.5 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| X | Base Case | 0.48 | P-61 VFD | Other | VCB | 32 | 0.014 | 0.007 | 0.2 | 0.2 | 0.5 | 18 | 0 | Out of IEEE 1584 -2018 range. | ||
| Generator | 0.48 | P-61 VFD | Other | VCB | 32 | 0.014 | 0.007 | 0.2 | 0.2 | 0.5 | 18 | 0 | Out of IEEE 1584 -2018 range. | |||
| SCCP | 50 Percent Utility | 0.48 | SCCP CB | Panel | VCB | 25 | 6.260 | 4.686 | 0.025 | 0.025 | 5.4 | 18 | 0.2 | |||
| X | Base Case | 0.48 | SCCP CB | Panel | VCB | 25 | 6.407 | 4.801 | 0.025 | 0.025 | 5.4 | 18 | 0.2 | |||
| Generator | 0.48 | SCCP CB | Panel | VCB | 25 | 4.696 | 3.464 | 0.025 | 0.025 | 4.5 | 18 | 0.1 | ||||
| T-PECO PRI | 50 Percent Utility | 33 | [Manual Time] | Transformer Terminal | VCB | 254 | 1.059 | 1.059 | 0 | 1000 | 4808 | 31 | 28866.2 | Extreme Danger | Out of IEEE 1584 -2018 range. | |
| X | Base Case | 33 | [Manual Time] | Transformer Terminal | VCB | 254 | 2.119 | 2.119 | 0 | 1000 | 6799.6 | 31 | 57732.4 | Extreme Danger | Out of IEEE 1584 -2018 range. | |
| Generator | 33 | [Manual Time] | Transformer Terminal | VCB | 254 | 2.119 | 2.119 | 0 | 1000 | 6799.6 | 31 | 57732.4 | Extreme Danger | Out of IEEE 1584 -2018 range. | ||
| T-PECO SEC | X | 50 Percent Utility | 0.48 | [Manual Time] | Transformer Terminal | VCB | 32 | 16.317 | 12.237 | 0 | 1000 | 10314.7 | 18 | 30673 | Extreme Danger | |
| Base Case | 0.48 | [Manual Time] | Transformer Terminal | VCB | 32 | 18.376 | 12.054 | 0 | 1000 | 10302.9 | 18 | 30617.4 | Extreme Danger | |||
| Generator | 0.48 | [Manual Time] | Transformer Terminal | VCB | 32 | 18.376 | 12.054 | 0 | 1000 | 10302.9 | 18 | 30617.2 | Extreme Danger | |||
| FCP #1 | 50 Percent Utility | 0.48 | MCC-3 | MCC | VCB | 25 | 2.083 | 1.473 | 0.025 | 0.025 | 3.2 | 18 | 0.1 | |||
| X | Base Case | 0.48 | MCC-3 | MCC | VCB | 25 | 2.093 | 1.481 | 0.025 | 0.025 | 3.2 | 18 | 0.1 | |||
| Generator | 0.48 | MCC-3 | MCC | VCB | 25 | 2.035 | 1.437 | 0.025 | 0.025 | 3.1 | 18 | 0.1 |
The test results are a function of specific humidity, barometric pressure, temperature, arc distance, and many other variables. These parameters will NOT be the same in your application. These results should be applied only by experienced engineers in the application of Arc-flash hazards. EasyPower makes no warranty concerning the accuracy of these results as applied to real world scenarios.
For integrated calculations, the fault currents displayed are just before 'Arc Time'.
Arc Flash Hazard - Scenario Comparison Report
EasyPower v11.0.1.8039 5/22/2025 12:49:04 PM
U:\Accounts\EGMAU\...\DESIGN\E\EGMAU25005.dez
Pennoni Associates Inc. (Serial #C2-49329-2L)
Page 6/6
| Arc Fault Bus Name | Worst Case | Scenario | Arc Fault Bus kV | Upstream Trip Device Name | Equip Type | Electrode Configuration | Electrode Gap (mm) | Bus Bolted Fault (kA) | Bus Arc Fault (kA) | Trip Time (sec) | Arc Time (sec) | Est Arc Flash Boundary (inches) | Working Distance (inches) | Incident Energy (cal/cm2) | PPE Level | Comments |
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| MCC: FCP #2 | ||||||||||||||||
| FCP #2 | 50 Percent Utility | 0.48 | MCC-3 | MCC | VCB | 25 | 2.083 | 1.473 | 0.025 | 0.025 | 3.2 | 18 | 0.1 | |||
| FCP #2 | X | Base Case | 0.48 | MCC-3 | MCC | VCB | 25 | 2.093 | 1.481 | 0.025 | 0.025 | 3.2 | 18 | 0.1 | ||
| FCP #2 | Generator | 0.48 | MCC-3 | MCC | VCB | 25 | 2.035 | 1.437 | 0.025 | 0.025 | 3.1 | 18 | 0.1 | |||
| MCC: MCC-3 | ||||||||||||||||
| MCC-3 | X | 50 Percent Utility | 0.48 | ATS-2 | MCC | VCB | 25 | 15.017 | 10.149 | 0.274 | 0.274 | 52.1 | 18 | 6.6 | 2 | |
| MCC-3 | Base Case | 0.48 | ATS-2 | MCC | VCB | 25 | 16.742 | 11.308 | 0.22 | 0.22 | 49 | 18 | 5.9 | 2 | ||
| MCC-3 | Generator | 0.48 | GEN-2 CB | MCC | VCB | 25 | 7.868 | 5.954 | 0.05 | 0.05 | 12.5 | 18 | 0.7 | |||
| Panel: ECBL | ||||||||||||||||
| ECBL | 50 Percent Utility | 0.208 | ECBL | Panel | VCB | 25 | 0.903 | 0.000 | 0 | 0 | 48 | 18 | 2 | 1 | ||
| ECBL | X | Base Case | 0.208 | ECBL | Panel | VCB | 25 | 0.905 | 0.000 | 0 | 0 | 48 | 18 | 2 | 1 | |
| ECBL | Generator | 0.208 | ECBL | Panel | VCB | 25 | 0.851 | 0.000 | 0 | 0 | 48 | 18 | 2 | 1 | ||
| Panel: ESBH | ||||||||||||||||
| ESBH | 50 Percent Utility | 0.48 | MCC-3 | Panel | VCB | 25 | 10.408 | 7.965 | 0.025 | 0.025 | 7.7 | 18 | 0.3 | |||
| ESBH | X | Base Case | 0.48 | MCC-3 | Panel | VCB | 25 | 11.019 | 8.448 | 0.025 | 0.025 | 8 | 18 | 0.3 | ||
| ESBH | Generator | 0.48 | MCC-3 | Panel | VCB | 25 | 6.826 | 5.131 | 0.025 | 0.025 | 5.7 | 18 | 0.2 | |||
| Panel: ESBL | ||||||||||||||||
| ESBL | 50 Percent Utility | 0.208 | ESBL | Panel | VCB | 25 | 0.000 | 0.000 | 0 | 0 | 48 | 18 | 2 | 1 | ||
| ESBL | X | Base Case | 0.208 | ESBL | Panel | VCB | 25 | 0.000 | 0.000 | 0 | 0 | 48 | 18 | 2 | 1 | |
| ESBL | Generator | 0.208 | ESBL | Panel | VCB | 25 | 0.000 | 0.000 | 0 | 0 | 48 | 18 | 2 | 1 | ||
| Panel: PNL-1 | ||||||||||||||||
| PNL-1 | 50 Percent Utility | 0.208 | PNL-1 | Panel | VCB | 25 | 0.902 | 0.000 | 0 | 0 | 18 | 18 | 2 | 1 | ||
| PNL-1 | X | Base Case | 0.208 | PNL-1 | Panel | VCB | 25 | 0.905 | 0.000 | 0 | 0 | 18 | 18 | 2 | 1 | |
| PNL-1 | Generator | 0.208 | PNL-1 | Panel | VCB | 25 | 0.850 | 0.000 | 0 | 0 | 18 | 18 | 2 | 1 | ||
| Panel: UWCP | ||||||||||||||||
| UWCP | 50 Percent Utility | 0.48 | MCC-3 | Panel | VCB | 25 | 4.287 | 3.147 | 0.025 | 0.025 | 4.1 | 18 | 0.1 | |||
| UWCP | X | Base Case | 0.48 | MCC-3 | Panel | VCB | 25 | 4.345 | 3.192 | 0.025 | 0.025 | 4.2 | 18 | 0.1 | ||
| UWCP | Generator | 0.48 | MCC-3 | Panel | VCB | 25 | 3.874 | 2.829 | 0.025 | 0.025 | 3.8 | 18 | 0.1 | |||
The test results are a function of specific humidity, barometric pressure, temperature, arc distance, and many other variables.
These parameters will NOT be the same in your application. These results should be applied only by experienced engineers in the application of Arc-flash hazards. EasyPower makes no warranty concerning the accuracy of these results as applied to real world scenarios.
For integrated calculations, the fault currents displayed are just before 'Arc Time'.
Appendix G:
Arc Flash One-Line Results
Pennoni
40
Note: some text on this page could not be read reliably. Please see the original PDF for this page.
RCSTP — ARC FLASH ONE-LINE DIAGRAM — 100% UTILITY
[Electrical one-line diagram for RCSTP under the 100% Utility scenario showing utility service, transformers, generators, automatic transfer switches, motor control centers, panels, feeders, and arc flash boundary and incident energy annotations.]
Main Service, Utility & Generators
- PECO UTILITY
- T-PECO PRI — 8789.8" AFB, 1792.6 cal/cm² @ 18", Extreme Danger
- FS-1
- T-PECO
- T-PECO SEC — 10266.6" AFB, 30444.9 cal/cm² @ 18", Extreme Danger
- FDR T-PECO TO MDP
- MDP (MDP MAIN CB, ATS-1 CB, ATS-2) — 10266.6" AFB, 30444.9 cal/cm² @ 18", Extreme Danger
- FDR FR MDP TO 800A DS / 800A FUSE DS / 800A FUSE DS BUS — 31.8" AFB, 1.9 cal/cm² @ 18", 1
- FDR FR 800A DS TO ATS-1
- GEN-1 / GEN-1 CB / FDR FR GEN-1 TO ATS-1 — 4948.1" AFB, 8551.3 cal/cm² @ 18", Extreme Danger
- ATS-1 — 19.7" AFB, 0.9 cal/cm² @ 18", 1
- FDR FR MDP TO ATS-2
- GEN-2 / GEN-2 CB / FDR FR GEN-2 TO ATS-2 — 4948.1" AFB, 8551.3 cal/cm² @ 18", Extreme Danger
- ATS-2 — 49.0" AFB, 5.9 cal/cm² @ 18", 2
- FDR FR ATS-2 TO MCC-3
MCC-1 & PNL-1
- FDR FR 800 DSW TO MCC 1-2
- MCC-1 (MCC-1 MAIN CB) — 23.7" AFB, 1.0 cal/cm² @ 18", 1
- PANEL PNL1 BREAKER → T-PNL1 → PNL-1 — 18" AFB, 2.0 cal/cm² @ 18", 1
- B-1A BREAKER → B-1A
- B-1B BREAKER → B-1B
- B-1C BREAKER → B-1C
- B-2 BREAKER → B-2
- FDR TO CBH — 13.7" AFB, 0.5 cal/cm² @ 18"
- FDR TO CBH PT2
CBH & CEFP
- CBH (CBH MAIN CB — 19.8" AFB, 0.9 cal/cm² @ 18") — 14.7" AFB, 0.5 cal/cm² @ 18"
- FDR TO CBH / FDR TO CBH PT3
- CEFP CB → FDR TO CEFP
- ME-65 CB → FDR TO ME-65 → ME-65 — 5.4" AFB, 0.1 cal/cm² @ 18"
- EF-1 CB → FDR TO EF-1 → EF-1 — 5.0" AFB, 0.1 cal/cm² @ 18"
- EF-4 CB → FDR TO EF-4 → EF-4 — 5.3" AFB, 0.1 cal/cm² @ 18"
- OH DOOR CB → FDR TO OH DOOR → OH DOOR — 5.3" AFB, 0.1 cal/cm² @ 18"
- CU-1 CB → C-26 → CU-1 — 6.3" AFB, 0.1 cal/cm² @ 18"
- CU-2 CB → C-27 → CU-2 — 6.3" AFB, 0.1 cal/cm² @ 18"
- CEFP — 10.2" AFB, 0.3 cal/cm² @ 18"
- P-61 CB → P-61 VFD → P-61 — 4.7" AFB, 0.0 cal/cm² @ 18"
- ME-61A CB → ME-61A VFD → ME-61A — 1.1" AFB, 0.0 cal/cm² @ 18"
- ME-61B CB → ME-61B VFD → ME-61B — 1.1" AFB, 0.0 cal/cm² @ 18"
- ME-63 CB → FDR TO ME-63 → ME-63 — 8.1" AFB, 0.3 cal/cm² @ 18"
- ME-64 CB → FDR TO ME-64 → ME-64 — 8.1" AFB, 0.3 cal/cm² @ 18"
MCC-2, SCCP, DP-1 & ECBL
- FDR FR ATS-1 TO MCC-2
- MCC-2 (MCC-2 MAIN CB) — 16.9" AFB, 0.6 cal/cm² @ 18"
- P-11 CB → P-11 VFD → P-11 — 1.2" AFB, 0.0 cal/cm² @ 18"
- P-12 CB → P-12 VFD → P-12 — 1.2" AFB, 0.0 cal/cm² @ 18"
- P-13 CB → P-13 VFD → P-13 — 1.2" AFB, 0.0 cal/cm² @ 18"
- P-41 CB → P-41 VFD → P-41 — 8.7" AFB, 0.6 cal/cm² @ 18"
- P-42 CB → P-42 VFD → P-42 — 8.7" AFB, 0.6 cal/cm² @ 18"
- P-43 CB → P-43 VFD → P-43 — 8.7" AFB, 0.6 cal/cm² @ 18"
- SCCP CB → FDR TO SCCP → SCCP (SCCP MAIN CB) — 3.8" AFB, 0.1 cal/cm² @ 18"
- FDR TO ME-10 → ME-10 — 4.8" AFB, 0.1 cal/cm² @ 18"
- FDR TO ME-11 → ME-11 — 4.8" AFB, 0.1 cal/cm² @ 18"
- DP-1 CB (14.4" AFB, 0.5 cal/cm² @ 18") → DP1-TB → DP-1 — 4.8" AFB, 0.1 cal/cm² @ 18"
- PANEL ECBL CB → T-ECBL → ECBL — 48" AFB, 2.0 cal/cm² @ 18", 1
MCC-3, FCP #1, FCP #2, ESBH, ESBL & UWCP
- MCC-3 — 49.0" AFB, 5.9 cal/cm² @ 18", 2
- FDR TO FCP #1 → FCP #1 — 3.7" AFB, 0.1 cal/cm² @ 18"
- FDR TO FCP #2 → FCP #2 — 3.2" AFB, 0.1 cal/cm² @ 18"
- FDR TO ESBH → ESBH (8.0" AFB, 0.3 cal/cm² @ 18") → TX-1 → ESBL — 48" AFB, 2.0 cal/cm² @ 18", 1
- FDR TO UWCP → UWCP — 4.2" AFB, 0.1 cal/cm² @ 18"
Note: some text on this page could not be read reliably. Please see the original PDF for this page.
RCSTP — ARC FLASH ONE-LINE DIAGRAM — 50% UTILITY
[Electrical one-line diagram for RCSTP under the 50% Utility scenario showing utility service, transformers, generators, automatic transfer switches, motor control centers, panels, feeders, and arc flash boundary and incident energy annotations.]
Main Service, Utility & Generators
- PECO UTILITY
- T-PECO PRI — 6226.4" AFB, 897.8 cal/cm² @ 18", Extreme Danger
- FS-1
- T-PECO
- T-PECO SEC — 10281.7" AFB, 30516.7 cal/cm² @ 18", Extreme Danger
- FDR T-PECO TO MDP
- MDP (MDP MAIN CB, ATS-1 CB, ATS-2) — 10281.7" AFB, 30516.7 cal/cm² @ 18", Extreme Danger
- FDR FR MDP TO 800A DS / 800A FUSE DS / 800A FUSE DS BUS — 35.1" AFB, 2.2 cal/cm² @ 18", 1
- FDR FR 800A DS TO ATS-1
- GEN-1 / GEN-1 CB / FDR FR GEN-1 TO ATS-1 — 4948.1" AFB, 8551.3 cal/cm² @ 18", Extreme Danger
- ATS-1 — 19.7" AFB, 0.9 cal/cm² @ 18", 1
- FDR FR MDP TO ATS-2
- GEN-2 / GEN-2 CB / FDR FR GEN-2 TO ATS-2 — 4948.1" AFB, 8551.3 cal/cm² @ 18", Extreme Danger
- ATS-2 — 52.1" AFB, 6.6 cal/cm² @ 18", 2
- FDR FR ATS-2 TO MCC-3
MCC-1 & PNL-1
- FDR FR 800 DSW TO MCC 1-2
- MCC-1 (MCC-1 MAIN CB) — 23.5" AFB, 1.0 cal/cm² @ 18", 1
- PANEL PNL1 BREAKER → T-PNL1 → PNL-1 — 18" AFB, 2.0 cal/cm² @ 18", 1
- B-1A BREAKER → B-1A
- B-1B BREAKER → B-1B
- B-1C BREAKER → B-1C
- B-2 BREAKER → B-2
- FDR TO CBH — 13.5" AFB, 0.5 cal/cm² @ 18"
- FDR TO CBH PT2
CBH & CEFP
- CBH (CBH MAIN CB — 19.6" AFB, 0.9 cal/cm² @ 18") — 14.5" AFB, 0.5 cal/cm² @ 18"
- FDR TO CBH / FDR TO CBH PT3
- CEFP CB → FDR TO CEFP
- ME-65 CB → FDR TO ME-65 → ME-65 — 5.4" AFB, 0.1 cal/cm² @ 18"
- EF-1 CB → FDR TO EF-1 → EF-1 — 5.0" AFB, 0.1 cal/cm² @ 18"
- EF-4 CB → FDR TO EF-4 → EF-4 — 5.3" AFB, 0.1 cal/cm² @ 18"
- OH DOOR CB → FDR TO OH DOOR → OH DOOR — 5.3" AFB, 0.1 cal/cm² @ 18"
- CU-1 CB → C-26 → CU-1 — 6.3" AFB, 0.1 cal/cm² @ 18"
- CU-2 CB → C-27 → CU-2 — 6.3" AFB, 0.1 cal/cm² @ 18"
- CEFP — 10.1" AFB, 0.3 cal/cm² @ 18"
- P-61 CB → P-61 VFD → P-61 — 4.7" AFB, 0.0 cal/cm² @ 18"
- ME-61A CB → ME-61A VFD → ME-61A — 1.1" AFB, 0.0 cal/cm² @ 18"
- ME-61B CB → ME-61B VFD → ME-61B — 1.1" AFB, 0.0 cal/cm² @ 18"
- ME-63 CB → FDR TO ME-63 → ME-63 — 8.0" AFB, 0.3 cal/cm² @ 18"
- ME-64 CB → FDR TO ME-64 → ME-64 — 8.0" AFB, 0.3 cal/cm² @ 18"
MCC-2, SCCP, DP-1 & ECBL
- FDR FR ATS-1 TO MCC-2
- MCC-2 (MCC-2 MAIN CB) — 16.6" AFB, 0.6 cal/cm² @ 18"
- P-11 CB → P-11 VFD → P-11 — 1.2" AFB, 0.0 cal/cm² @ 18"
- P-12 CB → P-12 VFD → P-12 — 1.2" AFB, 0.0 cal/cm² @ 18"
- P-13 CB → P-13 VFD → P-13 — 1.2" AFB, 0.0 cal/cm² @ 18"
- P-41 CB → P-41 VFD → P-41 — 8.7" AFB, 0.6 cal/cm² @ 18"
- P-42 CB → P-42 VFD → P-42 — 8.7" AFB, 0.6 cal/cm² @ 18"
- P-43 CB → P-43 VFD → P-43 — 8.7" AFB, 0.6 cal/cm² @ 18"
- SCCP CB → FDR TO SCCP → SCCP (SCCP MAIN CB) — 3.8" AFB, 0.1 cal/cm² @ 18"
- FDR TO ME-10 → ME-10 — 4.8" AFB, 0.1 cal/cm² @ 18"
- FDR TO ME-11 → ME-11 — 4.8" AFB, 0.1 cal/cm² @ 18"
- DP-1 CB (14.1" AFB, 0.5 cal/cm² @ 18") → DP1-TB → DP-1 — 4.8" AFB, 0.1 cal/cm² @ 18"
- PANEL ECBL CB → T-ECBL → ECBL — 48" AFB, 2.0 cal/cm² @ 18", 1
MCC-3, FCP #1, FCP #2, ESBH, ESBL & UWCP
- MCC-3 — 52.1" AFB, 6.6 cal/cm² @ 18", 2
- FDR TO FCP #1 → FCP #1 — 3.7" AFB, 0.1 cal/cm² @ 18"
- FDR TO FCP #2 → FCP #2 — 3.2" AFB, 0.1 cal/cm² @ 18"
- FDR TO ESBH → ESBH (7.7" AFB, 0.3 cal/cm² @ 18") → TX-1 → ESBL — 48" AFB, 2.0 cal/cm² @ 18", 1
- FDR TO UWCP → UWCP — 4.1" AFB, 0.1 cal/cm² @ 18"
Note: some text on this page could not be read reliably. Please see the original PDF for this page.
RCSTP — ARC FLASH ONE-LINE DIAGRAM — GENERATOR
[Electrical one-line diagram for RCSTP under the Generator scenario showing utility service, transformers, generators, automatic transfer switches, motor control centers, panels, feeders, and arc flash boundary and incident energy annotations.]
Main Service, Utility & Generators
- PECO UTILITY
- T-PECO PRI — 8789.8" AFB, 1792.6 cal/cm² @ 18", Extreme Danger
- FS-1
- T-PECO
- T-PECO SEC — 10266.6" AFB, 30444.7 cal/cm² @ 18", Extreme Danger
- FDR T-PECO TO MDP
- MDP (MDP MAIN CB, ATS-1 CB, ATS-2) — 10266.6" AFB, 30444.7 cal/cm² @ 18", Extreme Danger
- FDR FR MDP TO 800A DS / 800A FUSE DS / 800A FUSE DS BUS — 31.8" AFB, 1.9 cal/cm² @ 18", 1
- FDR FR 800A DS TO ATS-1
- GEN-1 / GEN-1 CB / FDR FR GEN-1 TO ATS-1 — 4948.1" AFB, 8551.3 cal/cm² @ 18", Extreme Danger
- ATS-1 — 12.7" AFB, 0.5 cal/cm² @ 18"
- FDR FR MDP TO ATS-2
- GEN-2 / GEN-2 CB / FDR FR GEN-2 TO ATS-2 — 4948.1" AFB, 8551.3 cal/cm² @ 18", Extreme Danger
- ATS-2 — 12.5" AFB, 0.7 cal/cm² @ 18"
- FDR FR ATS-2 TO MCC-3
MCC-1 & PNL-1
- FDR FR 800 DSW TO MCC 1-2
- MCC-1 (MCC-1 MAIN CB) — 15.7" AFB, 0.5 cal/cm² @ 18"
- PANEL PNL1 BREAKER → T-PNL1 → PNL-1 — 18" AFB, 2.0 cal/cm² @ 18", 1
- B-1A BREAKER → B-1A
- B-1B BREAKER → B-1B
- B-1C BREAKER → B-1C
- B-2 BREAKER → B-2
- FDR TO CBH — 10.6" AFB, 0.3 cal/cm² @ 18"
- FDR TO CBH PT2
CBH & CEFP
- CBH (CBH MAIN CB — 13.6" AFB, 0.5 cal/cm² @ 18") — 11.5" AFB, 0.4 cal/cm² @ 18"
- FDR TO CBH / FDR TO CBH PT3
- CEFP CB → FDR TO CEFP
- ME-65 CB → FDR TO ME-65 → ME-65 — 5.1" AFB, 0.1 cal/cm² @ 18"
- EF-1 CB → FDR TO EF-1 → EF-1 — 4.7" AFB, 0.1 cal/cm² @ 18"
- EF-4 CB → FDR TO EF-4 → EF-4 — 5.0" AFB, 0.1 cal/cm² @ 18"
- OH DOOR CB → FDR TO OH DOOR → OH DOOR — 5.0" AFB, 0.1 cal/cm² @ 18"
- CU-1 CB → C-26 → CU-1 — 5.8" AFB, 0.1 cal/cm² @ 18"
- CU-2 CB → C-27 → CU-2 — 5.8" AFB, 0.1 cal/cm² @ 18"
- CEFP — 8.5" AFB, 0.2 cal/cm² @ 18"
- P-61 CB → P-61 VFD → P-61 — 4.7" AFB, 0.0 cal/cm² @ 18"
- ME-61A CB → ME-61A VFD → ME-61A — 1.1" AFB, 0.0 cal/cm² @ 18"
- ME-61B CB → ME-61B VFD → ME-61B — 1.1" AFB, 0.0 cal/cm² @ 18"
- ME-63 CB → FDR TO ME-63 → ME-63 — 6.3" AFB, 0.2 cal/cm² @ 18"
- ME-64 CB → FDR TO ME-64 → ME-64 — 6.3" AFB, 0.2 cal/cm² @ 18"
MCC-2, SCCP, DP-1 & ECBL
- FDR FR ATS-1 TO MCC-2
- MCC-2 (MCC-2 MAIN CB) — 11.7" AFB, 0.3 cal/cm² @ 18"
- P-11 CB → P-11 VFD → P-11 — 1.2" AFB, 0.0 cal/cm² @ 18"
- P-12 CB → P-12 VFD → P-12 — 1.2" AFB, 0.0 cal/cm² @ 18"
- P-13 CB → P-13 VFD → P-13 — 1.2" AFB, 0.0 cal/cm² @ 18"
- P-41 CB → P-41 VFD → P-41 — 8.7" AFB, 0.6 cal/cm² @ 18"
- P-42 CB → P-42 VFD → P-42 — 8.7" AFB, 0.6 cal/cm² @ 18"
- P-43 CB → P-43 VFD → P-43 — 8.7" AFB, 0.6 cal/cm² @ 18"
- SCCP CB → FDR TO SCCP → SCCP (SCCP MAIN CB) — 3.6" AFB, 0.1 cal/cm² @ 18"
- FDR TO ME-10 → ME-10 — 4.5" AFB, 0.1 cal/cm² @ 18"
- FDR TO ME-11 → ME-11 — 4.5" AFB, 0.1 cal/cm² @ 18"
- DP-1 CB (10.9" AFB, 0.3 cal/cm² @ 18") → DP1-TB → DP-1 — 4.6" AFB, 0.1 cal/cm² @ 18"
- PANEL ECBL CB → T-ECBL → ECBL — 48" AFB, 2.0 cal/cm² @ 18", 1
MCC-3, FCP #1, FCP #2, ESBH, ESBL & UWCP
- MCC-3 — 12.5" AFB, 0.7 cal/cm² @ 18"
- FDR TO FCP #1 → FCP #1 — 3.6" AFB, 0.1 cal/cm² @ 18"
- FDR TO FCP #2 → FCP #2 — 3.1" AFB, 0.1 cal/cm² @ 18"
- FDR TO ESBH → ESBH (5.7" AFB, 0.2 cal/cm² @ 18") → TX-1 → ESBL — 48" AFB, 2.0 cal/cm² @ 18", 1
- FDR TO UWCP → UWCP — 3.8" AFB, 0.1 cal/cm² @ 18"
Appendix H:
Arc Flash Sample Labels
Pennoni
44
DANGER
Arc Flash and Shock Hazard
Appropriate PPE Required
| 333' - 4" | Flash Hazard Boundary | |
|---|---|---|
| 6751.5 | cal/cm2 Flash Hazard at 18.0 Inches | |
| Extreme Danger | PPE Level - Do not Work on Energized Equipment! | |
| 0.48 | kV Shock Hazard when cover is removed | |
| 3' - 6" | Limited Approach | Fault Current : 6.144 KA |
| 1' - 0" | Restricted Approach - Class 00 Voltage Gloves | |
Equipment Name: GEN-1
Fed From:
Report: EGMAU25005.RPT.ARC FLASH STUDY
Date: MAY 19TH, 2025
Pennoni
WARNING
Arc Flash and Shock Hazard
Appropriate PPE Required
| 3' - 7" | Flash Hazard Boundary | |
|---|---|---|
| 4.8 | cal/cm2 Flash Hazard at 18.0 Inches | |
| 2 | PPE Level - Arc-rated long-sleeve shirt and pants or arc-rated-coverall, Arc-rated face shield and arc-rated balaclava or arc flash suit hood, Arc-rated jacket, parka, rainwear, or hard hat liner, hard hat, Safety glasses or goggles, hearing protection, leather gloves and footwear. Refer to NFPA 70E-2018 Table 130.7(C)(15)(c). | |
| 0.48 | kV Shock Hazard when cover is removed | |
| 3' - 6" | Limited Approach | Fault Current : 16.65 KA |
| 1' - 0" | Restricted Approach - Class 00 Voltage Gloves | |
Equipment Name: MCC-1
Fed From: MDP
Report: EGMAU25005.RPT.ARC FLASH STUDY
Date: MAY 19TH, 2025
Pennoni
Pennoni
45
WARNING
Arc Flash and Shock Hazard
Appropriate PPE Required
| 2' - 6" | Flash Hazard Boundary | |
|---|---|---|
| 2.8 | cal/cm2 Flash Hazard at 18.0 Inches | |
| 1 | PPE Level - Arc-rated long-sleeve shirt and pants or arc-rated-coverall, Arc-rated face shield or arc flash suit hood, Arc-rated jacket, parka, rainwear, or hard hat liner, hard hat, Safety glasses or goggles, hearing protection, leather gloves and footwear. Refer to NFPA 70E-2018 Table 130.7(C)(15)(c). | |
| 0.48 | kV Shock Hazard when cover is removed | |
| 3' - 6" | Limited Approach | Fault Current : 17.157 KA |
| 1' - 0" | Restricted Approach - Class 00 Voltage Gloves | |
Equipment Name: MCC-2
Fed From: MDP
Report: EGMAU25005.RPT.ARC FLASH STUDY
Date: MAY 19TH, 2025
Pennoni
WARNING
Arc Flash and Shock Hazard
Appropriate PPE Required
| 0' - 8" | Flash Hazard Boundary | |
|---|---|---|
| 0.3 | cal/cm2 Flash Hazard at 18.0 Inches | |
| PPE Level - Shirt (long sleeve) and pants (long) or coverall or untreated natural fiber. Refer to NFPA 70E-2018 Table 130.7(C)(15)(c). | ||
| 0.48 | kV Shock Hazard when cover is removed | |
| 3' - 6" | Limited Approach | Fault Current : 10.836 KA |
| 1' - 0" | Restricted Approach - Class 00 Voltage Gloves | |
Equipment Name: ESBH
Fed From: MCC-3
Report: EGMAU25005.RPT.ARC FLASH STUDY
Date: MAY 19TH, 2025
Pennoni
Pennoni
46
Appendix I:
Utility, Transformer, & Generator Information
Pennoni
47
peco
AN EXELON COMPANY
Thursday, April 17, 2025
Subject: EAST GOSHEN MUNICIPAL AUTHORITY
34.5 kV Service Fault Duty
Hello,
As requested, the following 34.5 kV fault current information is provided to assist in your electrical system studies for EAST GOSHEN MUNICIPAL AUTHORITY, 1751 TOWNE DRIVE, WEST CHESTER. The maximum fault current from PECO-Energy's circuit is 10,000 Amps, symmetrical (X/R=26) and the minimum is estimated at 1,200 Amps, symmetrical. An estimation of the actual fault currents at the customer's 34.5 kV service substation, at this time is:
| GOSHEN_351 | |
|---|---|
| 3 PHASE Amps @ 34.5 kV | 2,215 Sym Amps X/R = 5.3 |
| 1 PHASE Amps @ 34.5 kV | 1,639 Sym Amps X/R = 4.4 |
| Circuit Length | 39,530 Ft |
The estimated values of fault current may change at any time, without notice to the customer. The value may range from the guaranteed maximum to the estimated minimum. Arc flash analysis SHALL be conducted using the worst case scenario and NOT solely from the values listed in the table above. It is the responsibility of the recipient of this letter to determine the worst case conditions.
This customer receives 34,500 Volt service and owns, operates, and maintains all of the 34,500 Volt service equipment and transformers. You should verify service switch, fuse, circuit breaker, and transformer ratings with the customer.
The next available upstream overcurrent device for GOSHEN_351 from the customer service fuse is:
- PECO's PLANEBROOK-351 Recloser with a RM-2 controller set as follows: Phase Elements 680 Amp primary pick-up, Kyle-162 Curve No Instantaneous; 680 Amp primary pick-up, Kyle-162 Curve; No Instantaneous; Ground Element 400 Amp primary pick-up, Kyle-162 Curve No Instantaneous; 400 Amp primary pick-up, Kyle-162 Curve; No Instantaneous
Our comments do not relieve the designer of the responsibility for an adequate design. He has the responsibility that the installation is in accordance with the National Electrical Code, the National Electrical Safety Code and other codes which apply.
If you have any questions concerning these comments, please contact me at PECOCustomerEngineering@exeloncorp.com.
Sincerely,
Uday Arora
Grid Connection Engineering - Customer Engineering
peco
AN EXELON COMPANY
file:///C:/Users/E189369/OneDrive%20-%20Exelon/Desktop/thisfaultstudy.html[4/17/2025 1:39:35 PM]
[Single Line Diagram engineering drawing for 33,000 Volt 3-Phase 4-Wire Service for East Goshen Municipal Authority, 1751 Towne Drive, West Chester, PA, by PECO Energy Company, Drawing No. H-235724-4.]
SINGLE LINE DIAGRAM — 33,000 VOLT 3Ø 4-W SERVICE
EAST GOSHEN MUNICIPAL AUTH.
1751 TOWNE DRIVE
WEST CHESTER, PA.
PECO ENERGY COMPANY
ROUTE CUSTOC
H-235724
GOSHEN-351
- 3 - 1 X # 1/0 OPEN WIRE WITH 1 - 1/0 AL NEUTRAL
- [2] COMPENSATED TO REGISTER AT SERVICE VOLTAGE
- 1 - COOPER CO. TYPE M-FORCE (CAT # M3H11FC3H) LOAD BREAK SW. 900 AMP 38KV 20,000A FAULT CLOSE RATING, OMOB — POLE MOUNTED
- 3 - L.A.'S 27KV OHIO BRASS CO. TYPE PVR (CAT # 221622) DISTRIBUTION CLASS
- 3 - FUSES S&C CO. TYPE SMU-20 80E 34.5 KV (10,000 AIC ) — POLE MOUNTED
- 1-3Ø GE CO. XFMR. 1,000KVA CLASS OA 33,000GY/19052-480Y/277V. TAPS ± 2-2.5% 150KV BIL IMP 5.72% S/N M996136B7 IEX= 0.341% NO LOAD LOSS: 1748 WATTS LOAD LOSS: 12,254 WATTS
- 3B26P — PECO METER EQUIPT. [2]
- 3 - V.T.'S 288-120 VOLTS
- 3 - C.T.'S 800/5
CONTRACTOR: CLINGER ELECTRIC
SERVICE DATE: 2010
CUSTOMER OWNS, OPERATES & MAINTAINS ALL FACILITIES EXCEPT PECO METERING EQUIPMENT
| NO. | DATE | DESCRIPTION | BY | APPR. |
|---|---|---|---|---|
| 4 | 04/27/11 | EC# 145633 CHANGED: CIRC. FROM LINE-3500P3 | JCB | JLD |
USE LATEST REVISION
| DRAWN | CHKD | CHECKED | INSPECTED | DATE | DRAWING NO. |
|---|---|---|---|---|---|
| RLC | EFr. | 10/7/85 | H-235724-4 |
QUAD# 48B3D4 | T-0553 | SIGNATURES AS PER ORIGINAL
Our energy working for you.™
Cummins Power Generation
Bill of Material
Cummins Sales and Service - East Region
2727 Ford Road
Bristol PA 19007 United States
P# 96095
January 8, 2020
Project Name: Ridley Creek Pump Station, East Goshen MUA
Premium Power Services
505 Schoolhouse Rd
Kennett Square, PA 19348
| Item | Description | Qty |
|---|---|---|
| Diesel Genset: 60Hz-450/410kW | ||
| 450DFEJ | Genset-Diesel,60Hz,450kW-Standby Rating | 1 |
| A331-2 | Duty Rating-Standby Power | 1 |
| L170-2 | Emissions Certification, EPA, Tier 2, NSPS CI Stationary Emergency | 1 |
| F202-2 | Enclosure-Steel, SndAtt, Level 2,Base Mtd,w/ExhSys | 1 |
| C207-2 | Fuel Tank-Subbase,850 Gallon,UL142 Compliant | 1 |
| R002-2 | Voltage-277/480,3 Phase,Wye,4 Wire | 1 |
| B246-2 | Alternator-60 Hz, 12 Lead, Limited Range, 125/105C | 1 |
| H703-2 | Generator Set Control-PowerCommand 2.3 | 1 |
| H536-2 | Display Language-English | 1 |
| H678-2 | Display-Control, LCD | 1 |
| K631-2 | Relays-Genset Status, User Configured | 1 |
| KU32-2 | Relay - Alarm Shutdown | 1 |
| H609-2 | Control Mounting-Left Facing | 1 |
| A292-2 | Heater-Alternator, 120 Volt AC | 1 |
| KU94-2 | CB -Right Only | 1 |
| KC62-2 | Circuit Breaker-800A,Right CB on Right side,3-Pole,UL 600,IEC 690 100% | 1 |
| KB72-2 | CB -Bottom Entry, Right | 1 |
| KM69-2 | Auxiliarycontacts/Tripalarm-Single Circuit Breaker | 1 |
| KM72-2 | Shunttrip-24vdc,Single Circuit Breaker | 1 |
| P175-2 | Enclosure Color-Green,Steel Enclosure | 1 |
| L163-2 | Listing, ULC-S601-07 | 1 |
| C127-2 | Separator-Fuel/Water | 1 |
| B786-2 | Battery Charger-12 Amp, Regulated | 1 |
| E074-2 | Engine Cooling-Radiator, 50C Ambient | 1 |
| H389-2 | Shutdown-Low Coolant Level | 1 |
| H557-2 | Coolant Heater-208/240/480V, Below 40F Ambient Temp | 1 |
| D041-2 | Engine Air Cleaner-Normal Duty | 1 |
Cummins
Alternator data sheet
Frame size: HC5C
Characteristics
Weights: Wound stator assembly: 1288 lb (580 kg) Rotor assembly: 1052 lb (474 kg) Complete assembly: 2804 lb (1263 kg) Maximum speed: 2250 rpm Excitation current: Full load: 1.72 Amps No load: 0.40 Amps Insulation system: Class H throughout3 Ø Ratings (0.8 power factor)
(Based on specific temperature rise at 40 °C ambient temperature)
| 60 Hz (winding no) | 50 Hz (winding no) | |||||||
|---|---|---|---|---|---|---|---|---|
| 110/190 220/380 |
120/208 240/416 |
139/240 277/480 |
347/600 | 110/190 220/380 |
120/208 240/415 |
127/220 254/440 |
||
| (311/312) | (311/312) | (311/312) | (07/17) | (311/312) | (311/312) | (311/312) | ||
| 150 °C Rise ratings | kW | 400 | 440 | 500 | 476 | 382 | 382 | 382 |
| kVA | 500 | 550 | 625 | 595 | 477 | 477 | 477 | |
| 125 °C Rise ratings | kW | 384 | 420 | 475 | 450 | 360 | 360 | 360 |
| kVA | 480 | 525 | 594 | 562 | 450 | 450 | 450 | |
| 105 °C Rise ratings | kW | 350 | 385 | 430 | 412 | 320 | 320 | 320 |
| kVA | 438 | 481 | 538 | 515 | 400 | 400 | 400 | |
| 80 °C Rise ratings | kW | 304 | 336 | 376 | 358 | 280 | 280 | 280 |
| kVA | 380 | 420 | 470 | 448 | 350 | 350 | 350 | |
Reactances (per unit ±10%)
(Based on full load at 125 °C rise rating)
| 110/190 220/380 |
120/208 240/416 |
139/240 277/480 |
347/600 | 110/190 220/380 |
120/208 240/415 |
127/220 254/440 |
|
|---|---|---|---|---|---|---|---|
| Synchronous | 4.32 | 3.94 | 3.35 | 3.35 | 3.26 | 2.73 | 2.43 |
| Transient | 0.19 | 0.18 | 0.15 | 0.15 | 0.16 | 0.13 | 0.12 |
| Subtransient | 0.14 | 0.13 | 0.11 | 0.11 | 0.12 | 0.10 | 0.09 |
| Negative sequence | 0.26 | 0.24 | 0.20 | 0.20 | 0.19 | 0.16 | 0.15 |
| Zero sequence | 0.12 | 0.11 | 0.09 | 0.09 | 0.11 | 0.09 | 0.08 |
Motor starting
| Broad range | 600 | Broad range | ||
|---|---|---|---|---|
| Maximum kVA | (90% sustained voltage) | 1749 | 1749 | 1749 |
Time constants
| (sec) | Broad range | 600 | Broad range | |
|---|---|---|---|---|
| Transient | 0.080 | 0.080 | 0.080 | |
| Subtransient | 0.012 | 0.012 | 0.012 | |
| Open circuit | 2.000 | 2.000 | 2.000 | |
| DC | 0.017 | 0.017 | 0.017 |
Windings
| (@ 20 °C) | Broad range | 600 | Broad range | |
|---|---|---|---|---|
| Stator resistance | (Ohms per phase) | 0.0136 | 0.0210 | 0.0136 |
| Rotor resistance | (Ohms) | 1.5500 | 1.5500 | 1.5500 |
| Number of leads | 12 | 6 | 12 |
Single phase power can be taken up to 40% of 3 phase-ratings
Cummins Inc.
Data and specification subject to change without notice
ADS-305 (10/17)
Cummins Sales and Service
Project: East Goshen Municipal Authority
Bill of Material
| Feature Code | Description | Qty |
|---|---|---|
|
DFEK Install-US-Stat 500DFEK A331-2 L170-2 L090-2 0170 R002-2 B258-2 A292-2 F202-2 P175-2 C209-2 L163-2 C127-2 H609-2 H703-2 H678-2 KP74-2 H536-2 KU94-2 3250 KC62-2 3251 KB72-2 KM69-2 KM72-2 D041-2 B786-2 E074-2 H389-2 H557-2 L026-2 L189-2 L050-2 A412-2 |
DFEK Commercial Diesel Generator Set, 500kW Standby 60Hz U.S. EPA, Stationary Emergency Application 500DFEK, Diesel Genset, 60Hz, 500kW-Standby Rating Duty Rating - Standby Power (ESP) Emission Certification, EPA, Tier 2, NSPS CI Stationary Emergency Listing - UL 2200 None-Vibration Isolators-Normal Duty Voltage - 277/480, 3 Phase, Wye, 4 Wire Alternator - 60Hz, 12 Lead, Extended Range, 125/105C Alternator Heater, 120 Volt AC Steel Sound Attenuated Level 2 Enclosure, with Exhaust System Enclosure Color - Green, Steel Fuel Tank - Sub Base, 1700 Gallon, UL142 Compliant Listing, ULC - S601 - 07 Fuel Water Separator Control Mounting - Left Facing PowerCommand 2.3 Controller LCD Control Display Stop Switch - Emergency, Externally Mounted Control Display Language - English Circuit Breaker or Entrance Box or Terminal Box - Right Only Circuit Breaker or Terminal Box, Left-None Circuit Breaker - 800A, Right Circuit Breaker on Right side, 3 - Pole, UL 600, IEC 690 100% Circuit Breaker or Entrance Box or Terminal Box, Left-None Bottom Entry, Right Auxiliary contacts/Trip Alarm - Single Circuit Breaker Shunt Trip - 24 Volts DC, Single Circuit Breaker Engine Air Cleaner - Normal Duty External Battery Charger - 12 Amp, Regulated Engine Cooling - Radiator, 50C Ambient Shutdown - Low Coolant Level Coolant Heater - 208/240/480 Volts AC, Below 40F Ambient Temperature Cummins Certified Test Record Standby 5 Year 2500 Hour Parts+Labor+Travel Literature - English Packing - None, Base Mounted Housing |
1 |
|
OTECD OTEC1000 A046-7 A035-7 B001-7 A028-7 A044-7 A042-7 R026-7 M034-7 C110-7 G007-7 |
OTECD, OTEC Transfer Switch-Electronic Control: 800A/1000A OTEC1000, Transfer Switch, PowerCommand, 1000 Amp Listing - UL 1008/CSA Certification Application - Utility to Genset Cabinet - Type 1 Poles - 3 (Solid Neutral) Frequency - 60 Hz System - 3 Phase, 3 or 4 Wire Voltage - 480 Volts AC Genset Starting Battery - 24V DC PC40 Control Transfer Switch Warranty - 5 Year Comprehensive |
1 |
| A053C813 | Emergency Stop Switch Kit-Remote | 1 |
| 0300-5929-02 | Annunciator-Panel Mounted With Enclosure (RS485) | 1 |
| NSBOP26 | Equipment ships direct genset on open truck ATS in enclosed trailer | 1 |
| NSBOP34 | Equipment supply only proposal based on 011923 email trail | 1 |
NOTES:
Proposal is for equipment only, offloading, rigging, and installation by others.
Page 1 of 1
Cummins
Alternator data sheet
Frame size: HC5F
Characteristics
Weights: Wound stator assembly: 1776 lb (800 kg) Rotor assembly: 1512 lb (681 kg) Complete assembly: 3738 lb (1684 kg) Maximum speed: 2250 rpm Excitation current: Full load: 1.72 Amps No load: 0.40 Amps Insulation system: Class H throughout3 Ø Ratings (0.8 power factor)
(Based on specific temperature rise at 40° C ambient temperature)
| 60 Hz (winding no) | 50 Hz (winding no) [crossed out] | |||||||
|---|---|---|---|---|---|---|---|---|
| 110/190 220/380 |
120/208 240/416 |
139/240 277/480 |
347/600 | 110/190 220/380 |
120/208 240/415 |
127/220 254/440 |
||
| (311/312) | (311/312) | (311/312) | (07/17) | (311/312) | (311/312) | (311/312) | ||
| 150° C rise ratings | kW | 570 | 625 | 700 | 700 | 568 | 568 | 552 |
| kVA | 713 | 781 | 875 | 875 | 710 | 710 | 690 | |
| 125° C rise ratings | kW | 538 | 590 | 660 | 660 | 536 | 536 | 520 |
| kVA | 673 | 738 | 825 | 825 | 670 | 670 | 650 | |
| 105° C rise ratings | kW | 500 | 550 | 600 | 600 | 496 | 496 | 480 |
| kVA | 625 | 688 | 750 | 750 | 620 | 620 | 600 | |
| 80° C rise ratings | kW | 440 | 484 | 528 | 528 | 432 | 432 | 416 |
| kVA | 550 | 605 | 660 | 660 | 540 | 540 | 520 | |
Reactances (per unit ± 10%)
(Based on full load at 125° C rise rating)
| 110/190 220/380 |
120/208 240/416 |
139/240 277/480 |
347/600 | 110/190 220/380 |
120/208 240/415 |
127/220 254/440 |
|
|---|---|---|---|---|---|---|---|
| Synchronous | 3.64 | 3.33 | 2.80 | 2.80 | 2.90 | 2.43 | 2.10 |
| Transient | 0.17 | 0.15 | 0.13 | 0.13 | 0.17 | 0.14 | 0.12 |
| Subtransient | 0.12 | 0.11 | 0.09 | 0.09 | 0.11 | 0.09 | 0.08 |
| Negative sequence | 0.23 | 0.21 | 0.18 | 0.18 | 0.18 | 0.15 | 0.13 |
| Zero sequence | 0.10 | 0.09 | 0.08 | 0.08 | 0.08 | 0.07 | 0.06 |
Motor starting
| Broad range | 600 | Broad range | ||
|---|---|---|---|---|
| Maximum kVA | (90% sustained voltage) | 2429 | 2429 | 1769 |
Time constants
| (sec) | Broad range | 600 | Broad range | |
|---|---|---|---|---|
| Transient | 0.080 | 0.080 | 0.080 | |
| Subtransient | 0.012 | 0.012 | 0.012 | |
| Open circuit | 2.500 | 2.500 | 2.500 | |
| DC | 0.019 | 0.019 | 0.019 |
Windings
| (@ 20° C) | Broad range | 600 | Broad range | |
|---|---|---|---|---|
| Stator resistance | (Ohms per phase) | 0.0062 | 0.0098 | 0.0062 |
| Rotor resistance | (Ohms) | 2.1600 | 2.1600 | 2.1600 |
| Number of leads | 12 | 6 | 12 |
Single phase power can be taken up to 40% of 3 phase- ratings