Planning Commission
The East Goshen Township Planning Commission is an advisory board to the Township Board of Supervisors. The Commission reviews all subdivision and land development applications, conditional use applications, zoning hearing board applications and makes recommendations to the Board of Supervisors. The Commission also reviews or drafts Zoning Ordinance Amendments. Each member is appointed by the Board of Supervisors.
- Composed of seven East Goshen Township residents each serving a four-year term.
- Formal Meetings are held the 4th Tuesday of each month at 7:00 P.M.
- Workshop Meeting are held on an as needed basis
- All township meetings are held at the Township Building and are open to the public
| Planning Commission Members | Term Expiration Date |
| John Stipe, Chair | 2026 |
| Dan Truitt, Vice Chair | 2027 |
| Daniel H. Daley | 2027 |
| Michael Koza | 2026 |
| Ernest Harkness | 2026 |
| Karen Martynick | 2029 |
| William Kaufman | 2029 |
| Larry Massaro, BOS Liaison | |
| Kelly Krause, Staff Liaison |
Draft Ordinance-Zoning Amendment Regulating Data Centers by Conditional Use 9.24.26
Click here to view – May 4th Documents for Malvern Institute and East Whiteland Special Study.
Related News
PLANNING COMMISSION CONSIDERS UPGRADES TO AQUA FACILITY
Wednesday, November 18, 2026
At its September meeting, the East Goshen Planning Commission reviewed a conditional use application from Aqua Pennsylvania to upgrade its Hunt Country well treatment facility located on Thorncroft Drive. The upgrade is required to meet new maximum contaminant levels (MCLs) for PFAS in drinking water that were enacted last year by the U.S. Environmental Protection […]
View ArticleFrom the Planning Commission: Addressing Potential Data Center Development in East Goshen Township
Wednesday, September 30, 2026
As the demand for artificial intelligence accelerates, municipalities throughout Pennsylvania have found themselves navigating complex regulations, legal challenges, and community debates about large-scale data centers. While no data center projects are currently proposed in East Goshen, township officials are proactively addressing potential impacts by updating zoning ordinances to create strict standards that will apply should […]
View ArticleDocuments
Back to the list | Open the original PDF
Notice: this accessible version was created automatically from the original document. The transcription may not be 100% accurate. It is provided for searching and for screen readers; please refer to the original document for the official version.
EAST GOSHEN TOWNSHIP
PLANNING COMMISSION
Agenda
Wednesday, November 4, 2009
7:00 PM
- Call to Order / Pledge of Allegiance
- Review of Tracking Log / Determine need for Workshop Meeting
- Public Comment on Non-Agenda Items
- Approval of Minutes October 7, 2009
- Acknowledge Receipt of New Applications Mark/Helen McGinley, 19 School Lane (V)
- Subdivision Plans
- Land Development Plans 1661 E. Strasburg Rd, Mullen Property (Lot 2, Ashbridge Farm)
- Conditional Uses and Variances Clearwire US LLC, 21 Edgewood Rd. (C/U); Mark /Helen McGinley, 19 School Lane (V)
- Ordinance Amendments
- Old Business Discussion on “Traditions” Ind. Living Fac. project in West Goshen; Sample Generator Ordinance
- New Business Riparian Buffers: consider increasing riparian buffer to 100’
- Any Other Matter
- Meetings and Dates of Importance November 3, 2009 Election day – no meetings November 4, 2009 Board of Supervisors ws 9:00 AM November 4, 2009 Planning Commission 7:00 PM November 5, 2009 Park & Recreation 7:00 PM November 9, 2009 Municipal Authority 7:00 PM November 10, 2009 Board of Supervisors 7:00PM November 11, 2009 Veterans Day – Office closed November 11, 2009 Conservancy Board 7:00 PM November 12, 2009 Historical Commission 7:00 PM November 16, 2009 Deer Committee 7:00 PM November 17, 2009 Board of Supervisors ws 7:00 PM November 18, 2009 Zoning Hearing - McGinley 7:30 PM November 24, 2009 Board of Supervisors 7:00 PM November 26, 2009 Office closed November 27, 2009 Office closed
- Correspondence
- Goals
Adjournment
• Bold Items indicate that the Planning Commission has new information to review for that application.
REMINDER – Newsletter Article Submission Due Date:
| Article Due Date | Delivery date |
|---|---|
| November 10, 2009 | January 1, 2010 |
F:\Data\Shared Data\Agendas\Planning Commission\2009\PC AGENDA 110409.doc
EAST GOSHEN TOWNSHIP
PLANNING COMMISSION
APPLICATION HISTORY
Wednesday, November 4, 2009
7:00 PM
1. SUBDIVISON PLANS
Sullivan’s Grove, Greenhill Road (S/D)
| February 4, 2008 | E.B. Walsh - Re-submission Plans |
|---|---|
| February 8, 2008 | Yerkes – Review of Pre/Final Plan |
| February 2008 | DEP – Sewage facilities |
| March 27, 2008 | Landscape Plans |
| April 15, 2008 | Yerkes, Landscape Review |
| May 2008 | Sewage Facilities Planning Module |
| May 29, 2008 | Extension letter until 7/15/08 |
| June 13, 2008 | e-mail from Conservancy Board |
| June 25, 2008 | Extension letter until 9/20/08 |
| September 4, 2008 | Extension letter until November 30, 2008 |
| September 2008 | Plans – Landscape |
| September 11, 2008 | CCCD – review |
| September 29, 2008 | DEP – Discharge for Stormwater |
| October 29, 2008 | Yerkes – Landscape Review |
| November 12, 2008 | Wooldridge Construction – extension |
| January 27, 2009 | Preliminary/Final Revised Landscape plan |
| January 28, 2009 | Wooldridge – Extension period |
| February 25, 2009 | Yerkes – Landscape Review |
| May 7, 2009 | Wooldridge Construction - Extension |
| May 11, 2009 | Yerkes – Review of Preliminary/Final Plan |
| May 26, 2009 | DEP – Planning Module for L/D |
| July 29, 2009 | Wooldridge Construction – extension |
| September 8, 2009 | E.B. Walsh – Re-submission #6 |
| September 28, 2009 | E.B. Walsh – prelim/final subdivision plans Plans |
| September 28, 2009 | Yerkes – Review of Prelim/Final Plan |
| September 29, 2009 | Memo – draft motion |
November 4, 2009
Matthew/Christine Mullen, 1645 E. Strasburg Rd (L/D)
| August 18, 2009 | application |
|---|---|
| October 13, 2009 | Yerkes – Stormwater Mgt & Erosion Review |
| October 26, 2009 | CCPC – Pre/Final Land Development |
2. CONDITIONAL USES/VARIANCES
Clearwire US LLC, 21 Edgewood Rd, (C/U)
| August 27, 2009 | Application Plans Coverage legends |
|---|---|
| August 26, 2009 | Aco Property Advisors, - C/U permit |
| August 26, 2009 | Aco Property Advisors - narrative |
| September 25, 2009 | Yerkes – C/U Plan Review |
| September 29, 2009 | Draft motions |
| October 5, 2009 | Ramaker & Assoc. responses to Yerkes |
| October 6, 2009 | Plans |
| October 27, 2009 | Yerkes – Conditional Use Plan Review |
Mark/Helen McGinley, 19 Schoolhouse Lane (V)
| Plans | |
|---|---|
| January 12, 2005 | Zoning decision/property 19 Schoolhouse Ln |
| October 27, 2009 | 1,000’ notification |
| October 30, 2009 | M. Gordon – Draft motion |
3. ORDINANCE AMENDMENTS
4. ANY OTHER MATTER
5. ZONING AMENDMENTS
November 4, 2009
Planning Commission Application Tracking Log
B. TRACKING LOG
1 pg
10/29/2009
| Application Name | Application (CU,LD,O, SD,V, SE, CA) | Type (Sk, P, F) | Date Filed | Start Date | Date to Yerkes/Consultant | Date to CCPC | Date to Abutting Prop. / ABC's | Extension | PC NLT Action Date | BOS NLT Action Date | Hearing Date | Drop Dead date |
|---|---|---|---|---|---|---|---|---|---|---|---|---|
| Clearwire US (21 Edgewood Rd.) | CU | P/F | 8/28/09 | 8/28/09 | 9/11/09 | n/a | 9/16/09 | 1 | 11/4/09 | 10/20/09 | 11/18/09 | 11/26/09 |
| 1661 E. Strasburg Rd. (Mullen) | LD | P/F | 9/24/09 | 10/7/09 | 9/25/09 | 9/25/09 | 9/28/09 | 1 | 1/13/10 | 12/22/09 | n/a | 2/2/10 |
| 19 School Ln. (McGinley) | V | P/F | 10/9/09 | 10/10/09 | n/a | n/a | 10/27/09 | 11/4/09 | 11/17/09 | 11/18/09 | 12/8/09 |
Bold = New Application or PC action required
F:\Data\Shared Data\ABC'S\Planning Commission\PC Tracking Log\2009\PC Tracking Log for 110409.xls
D. MINUTES
2 pgs
EAST GOSHEN TOWNSHIP
PLANNING COMMISSION MEETING
October 7, 2009
The East Goshen Township Planning Commission held their regularly scheduled meeting on October 7, 2009 at the East Goshen Township building. Chairman Senya Isayeff, Vice-Chair George Martynick and members Megann Hedgecock, Albert Zuccarello, and Peter Mylonas were present. Also present were Township Zoning Officer Mark Gordon, Ginny Newlin (Conservancy Board), Marty Shane (BOS), and Don McConathy (BOS), along with Mr. Ed McFalls.
WORKSHOP SESSION – 7:00pm
Senya reviewed the agenda for the evening.
Members reviewed and corrected the minutes of September 2, 2009. Megann abstained from motion due to her absence from the last meeting. Discussion turned to Sullivan’s Grove and Ed McFalls then presented a brief description of the development plan and added that the golf course would be open to the residents of East Goshen. Mr. McFalls mentioned that he is unsure when construction would start, but noted that everything is in place at this time and a conservative start date of construction would be 2011.
FORMAL SESSION
A. Pledge of Allegiance
Senya called the meeting to order at 7:31pm. George led those in attendance in the pledge.
B. Approval of Minutes
George moved that the minutes of September 2nd, 2009 be approved as amended in the workshop session. Senya noted that a motion would not be passed on the September minutes until next month’s meeting due to the absence of a few members of the PC.
C. New Applications
Clearwire US LLC- has requested an extension.
Sullivan’s Grove subdivision- Senya noted that after 5 years on the books, the PC is ready to make a recommendation to the BOS to approve Sullivan’s Grove. Al motioned to recommend and Peter seconded the motion.
1422 Paoli Pike- the potential buyers of this property, Dr. and Mr. Zelinsky were present along with their representative, John Smirga. The potential buyers are proposing to convert the current property into a medical practice with the main building be used as an office/reception area. The existing barn will be razed and the current 3 car garage will stay to provide extra parking to the practice. There is a proposed 1-story addition to be used as patient rooms. Al questioned the history and date of the original home and it is thought to date back to the 1840’s. Peter asked if the addition will be of the same motif as the existing property, at which the potential buyers answered yes.
John Smirga noted that this is a non-conforming lot/structure and they will need a conditional use, then a variance. Marty questioned if the potential buyers have worked with the Historic Commission, Mark replied that they have attended a HC meeting and added that the HC is supportive. Senya advised the buyers that the PC is supportive but the code requires the potential buyers to go before the BOS. Senya also added that he encouraged
| 10/07/2009 | PC MINUTES | Page 1 of 2 |
|---|
2 of 2
the use of the property for a medical practice for there are not enough medical practices in East Goshen and the PC appreciates that Dr. Zelensky wants to practice in this area.
D. New Business
Adaptive Re-Use Signage Ordinance Amendment- Peter made a motion to approve the amendment and George seconded the motion. No further public comment or discussion was heard. The motion passed unanimously.
Public Comment:
Senya asked those in attendance if they had any comments that did not appear on the agenda. At this time Ginny Newlin for the Conservancy Board commented on the destruction of the woodlands around the pavilions at the YMCA. A portion of the woodlands have been cleared and wood chips appear over a large area. It was the understanding of the Conservancy Board that the woodlands would not be cleared. Ginny, on behalf of the Conservancy Board wanted to bring this to the attention of the PC. Senya asked if a representative from the YMCA was present during the inspection by the Conservancy Board. Don McConathy asked Mark Gordon to look into this further and report back to the BOS. It was added that this should not be a PC issue and that the BOS would like to look into further. Marty added that it is Mark’s responsibility to be sure that the Y is in compliance with its agreement.
E. Adjournment
Motion to adjourn the meeting was made by George and seconded by Al. The meeting adjourned at 8:45 p.m.
Please note that the clean-up day has been tentatively rescheduled to November 14th.
Respectfully submitted,____________________________________________________
Linda Jones, Recording Secretary
| 10/07/2009 | PC MINUTES | Page 2 of 2 |
|---|
OCT-13-2009(TUE) 11:39 Yerkes WC#1 (FAX)6106400771
G. MULLEN
2.
6 pgs
Yerkes
Yerkes Associates, Inc. Consulting Engineers / Site Planners / Land Surveyors
October 13, 2009
East Goshen Township
1580 Paoli Pike
West Chester, Pennsylvania 19380
Attn: Mark Gordon, Township Zoning Officer
Re: Matthew J. and Christine Mullen – 1645 East Strasburg Road
Stormwater Management & Erosion and Sediment Control Plan Review
Dear Mark:
The following plans, correspondence and report submitted by Site Engineering Concepts, LLC have been received by our office for review:
Plans, dated 08-13-09, Site Plans by Site Engineering Concepts, LLC & Landscaping Plans & Details by DePallo Design & Planning:
- Sheet 1 of 5: Proposed PCSM Plan / Site Plan
- Sheet 2 of 5: Erosion 7 Sedimentation Control Plan
- Sheet 3 of 5: Landscape Plan
- Sheet 4 of 5: Rain Garden Landscape plan
- Sheet 5 of 5: Landscape Detail
Correspondence
- Individual NPDES Application, includes PADEP BMP Worksheets 1,2,3,4, 5,10 for Drainage Areas 1 & 2, Worksheet 10 and Criteria & Credits Checklists BMP 5.4.1 & 5.6.1, dated 08-13-09
- Subsurface Permeability Evaluation prepared by Piedmont Environmental Group, Inc., dated 11-08-07
Reports, dated 08-13-09:
- Stormwater Management Analysis, dated 03-03-09
- E&S Plan Calculations
This property had previously been submitted for Land Development plan review by the former owner/applicants Eustace and Suzanne Mita. A review was issued on December 25, 2007. Subsequently, the plan was withdrawn by the Mita's on February 25, 2008. The current plans have been substantially revised and this plan submission is considered a new application by the owner/applicants Mathew J. and Christine Mullen.
The site is located and is accessed from the north side of East Strasburg Road via an overgrown gravel driveway situated between Christine Lane and Wyllpen Circle opposite the
Professional services since 1874
1444 Phoenixville Pike, P.O. Box 1568, West Chester, PA 19380-0078 / Tel: 610-644-4254 / Fax: 610-640-0771
OCT-13-2009(TUE) 11:39 Yerkes WC#1 (FAX)6106400771 P. 003/007 86
Mathew J and Christine Mullen – 1645 East Strasburg Road
October 13, 2009
Page 2 of 6
intersection with Springhouse Lane. The site is situated within the R-2 Low Density Suburban Residential Zoning District. The parcel is also known as Lot #2 of the Ashbridge Farm Subdivision being 19.74 acres gross. The site is currently undeveloped with meadow, woodland, individual trees. The proposed construction includes a new dwelling with attached garage, driveway, courtyard, patio area, walkways and parking area. Stormwater management is to be provided by a series of five rain gardens and an underground infiltration bed. The new dwelling is to be served by on-site water and on-site sewer.
The plans have been reviewed for compliance with applicable Township Ordinances and per site research. The following comments must be satisfactorily addressed before plan approval is recommended:
Subdivision and Land Development Ordinance
- Sections 205-(30&33).B (3): The name of the record owner and applicant and the source(s) of title to the land being developed, as shown by the records of the County Recorder of Deeds, should be provided. The plan should specifically note that the Mullen’s are the owners and/or applicants.; The deed book and page number refer to in General Note #2 is the previous property owners or the Mita's deed, the current deed book and page number for the Mullen’s should be noted on the plan.
- Sections 205-(30&33).B (7) & 205-65.B: All lot corners should be clearly identified by either a monument or an iron pin. The northwestern corner should have either a “pin found” or a “pin to be set” designation added to the plan.
- Sections 205-(30&33).B (8) & 205-35.B: Location and elevation of the bench mark to which contour elevations refer should be noted. Where reasonable and practical, datum used shall be United States Geodetic Survey (USGS) from a known, established benchmark. The location and elevation of a benchmark is missing and should be noted on the plan.
- Sections 205-(30&33).B (10), Section 205-35.C & 304.B.(4&5): The site plan should identify the location and ownership of all existing sewer lines, water lines, fire hydrants, utility transmission lines, culverts, bridges, railroads, watercourses, trees, wetlands, easements, rights-of-way and other significant man-made or natural features within the proposed subdivision and within 50 feet from the boundaries of the proposed subdivision. As part of the previous plan submission review, it was observed that Verizon facilities are located in the vicinity of the proposed driveway. All utility lines located in the vicinity of the proposed driveway should be indicated on the site plan.; The approved subdivision plan indicates that the FEMA 100-yr. floodplain boundary extends onto the northeastern corner of the parcel. FEMA mapping, however, has been revised since subdivision approval. The plan should be revised as necessary to reflect current FEMA mapping.
Professional services since 1874
1444 Phoenixville Pike, P. O. Box 1568, West Chester, PA 19380-0078 / Tel: 610-644-4254 / Fax: 610-640-0771
OCT-13-2009(TUE) 11:40 Yerkes WC#1 (FAX)6106400771 P. 004/007 86
Mathew J and Christine Mullen – 1645 East Strasburg Road
October 13, 2009
Page 3 of 6
- Sections 205-(30&33).B (12): The cartway width for East Strasburg Road should be noted on the site plan.
- Section 205-33.B (19): The site plan should note that the parcel is also known as Lot #2 of the approved Ashbridge Farm Subdivision.
- Section 205-33.B (21) (e): All easements or rights-of-way, public or private, and any limitations on such easements or rights-of-way shall be shown and accurately identified on the plan. The site plan indicates a trail easement along the northern and eastern property lines. The plan should include a note to identify the easement beneficiary or owner and list any restrictions, limitations, and responsibilities associated with the trail easement.
- Sections 205-33.B (22) (a), 205-68.D & E - The applicant shall comply with all requirements of the Chester County Health Department and the Pennsylvania Department of Environmental Protection and shall so certify prior to final plan approval.
- Section 205-30.C.1.g – The plans indicates that the PennDot Minimum Use Driveway Highway Occupancy Permit had been filed as part of the original Ashbridge Farm Subdivision in 2002. Typically these permits are valid for one year from date of issuance. Evidence or notification from PADOT should be provided to the Township confirming that a highway occupancy permit has been extended and will be issued prior to plan approval. Otherwise a new HOP will need to be obtained.
- Section 205-57.D (1): The driveway grades should be noted on the plan. The driveway grade within the right-of-way should be no greater than 5% and no more than 10% for 25 ft. from the right-of-way. All other driveway grades should be noted. Additionally, the driveway highpoint should be indicated.
- Section 205-57.D (2): A detail should be placed on the plan for the driveway paving specifications per this section. A driveway construction detail for the remainder of the driveway should also be provided.
- Section 205-57.D (3): The driveway width within the limits of the Strasburg Road right-of-way should be noted to be no less than 12 feet. The driveway width for the remainder of the driveway should also be noted.
- Section 205-66.E - All proposed on-site residential water supply systems shall have a permit certified by the Chester County Health Department. The proposed type of water supply should be added to the plan and proposed well locations and/or public water tie-in locations should also be shown.
Conservation Plan, Erosion and Sedimentation Control, Chapter 195, Ord. No. 129-M-03, SLDO 205-35 & 37, Chapter 131
Professional services since 1874
1444 Phoenixville Pike, P. O. Box 1568, West Chester, PA 19380-0078 / Tel: 610-644-4254 / Fax: 610-640-0771
OCT-13-2009(TUE) 11:40 Yerkes WC#1 (FAX)6106400771 P. 005/007 4 of 6
Mathew J and Christine Mullen – 1645 East Strasburg Road
October 13, 2009
Page 4 of 6
- Section 205-35.E: An inconsistency exists between the seed mix specifications on Sheet 2 and the meadow and lawn seed specifications on Sheet 5. Either one set of seed specifications should be provided for the site or the locations where the different seed mixes are to be applied should be more clearly indicated.
- Section 205-35.F: The site plan should include notations indicating all trees or portions of tree masses to be cleared.
- Sections 304.C.2 & 407.A: In accordance with Chapter 102, a NPDES permit is required if the area of disturbance is more than 1 acre. The plan proposes an area of disturbance of 3.1 acres and, therefore, an NPDES Permit is required. An application has been made to the Chester County Conservation District for an NPDES Individual Permit. Approval and issuance of an NPDES Individual Permit will be required for plan approval.
Stormwater Management Chapter 195, Ord. No. 129-M-03 & SDLO 205-37
- Section 304.D.1 & 304.D.3: All stormwater management facilities are to be located on the plan and described in detail and all design calculations, assumptions and criteria should be provided. The standpipe for the Rain Garden #1 is modeled in the calculations with a 2 ft. diameter opening, but the plan indicates a 1.5 ft. diameter opening. Either the calculations and/or the Rain Garden design should be adjusted for consistency.; Rain Garden #1 detail on Sheet 1 should be addressed as follows: The location, size, invert and material of the inlet pipe should be shown and noted. The size, invert and material of the outlet pipe should be noted. The 440.4’ elevation should be indicated. The location, size, invert, and material of the inlet pipe and rip-rap should be shown and noted on the detail for Rain Garden #3 and #4.; The location, size, invert and material of the inlet pipe should be shown and noted.; The size, invert and material of the outlet pipe should be noted.; The 440.4’ elevation should be indicated.; The location, size, invert, and material of the inlet pipe and rip-rap should be shown and noted on the detail for Rain Garden #3 and #4.; The location of the infiltration testing should be shown on the plan.; All berm and spillway locations should be labeled on the plan.; A detail for all the BMP “Snouts” should be provided.; The slope or grade requirements for the drainage swales should be noted on the swale detail on Sheet 1.
- Section 304.B.19: A statement, to be signed by the landowner, acknowledging the stormwater management system to be a permanent fixture that can only be altered or removed only after approval of a revised plan by the Township should be added to the plan.
- Section 304.B.20: The following certification to be completed by the design engineer should be added to the site plan: “(Design Engineer), on this date (date of signature), has reviewed and hereby certifies that the drainage plan meets all design standards and criteria of the East Goshen Township Stormwater Management Ordinance”.
Professional services since 1874
1444 Phoenixville Pike, P. O. Box 1568, West Chester, PA 19380-0078 / Tel: 610-644-4254 / Fax: 610-640-0771
OCT-13-2009(TUE) 11:40 Yerkes WC#1 (FAX)6106400771 P. 006/007 5 of 6
Mathew J and Christine Mullen – 1645 East Strasburg Road
October 13, 2009
Page 5 of 6
Landscaping Plan
20. Section 205-36.C: Floodplain areas within and adjacent to the tract should be identified. The floodplain boundary location should be identified as noted by comment #4.
21. Section 205-36.F: The location and type of all proposed landscaping and/or ground cover in buffer areas, common open space, and entrances should be appropriately identified.
a. There is an unlabeled evergreen tree along the existing gravel drive which should be identified on Sheet 3.
b. Notes for all Rain Gardens incorrectly refer to Sheet 5, but should note Sheet 4 for the planting schedule and enlarged details.
c. Soil amendments noted in the rain garden details on Sheet 1 are typical generic quantities as required by the PADEP Manual, but specifications for the type of soil amendments should be noted on the plans. It is recommended that soil tests be conducted prior to finalizing soil amendments that will reveal any nutrient deficiencies.
22. Section 205-36.G: The landscape plan should include a full plantings list showing the proper botanical and common name along with the size and grade.
a. Spacing for IRIS VERSICOLOR in Rain Garden #1 has not been specified on Sheet 4.
b. The following should be addressed for Rain Gardens #2 through 5 on sheet 4:
i. The incorrect quantity specified for ACER RUBRUM.
ii. Grasses/Perennials/Groundcovers – Substituting plugs for trees as shrubs as recommended by PA BMP manual is acceptable, however the proposed spacing for the plugs should be revised to a minimum of 12" O.C. The current proposed spacing is not suitable for the survival rate and maturation rate of the plugs.
iii. 50% or more of the plug species proposed are designated "wetland" species. Due to Rain Garden #3 having to endure both wet and dry conditions it is recommended that the following species be reconsidered:
- Asclepias incarnate
- Calamagrostis Canadensis
- Hibiscus moscheutos
- Iris versicolor
- Juncus effuses
- Scirpus cyperinus
- Carex stricta
- Verbena hastata
c. The following items should be addressed on Sheet 5:
i. An incorrect quantity is specified for CERCIS CANADENSIS.
ii. FRANXINUS (ASH) species have a high susceptibility of disease, another species should be selected.
Professional services since 1874
1444 Phoenixville Pike, P. O. Box 1568, West Chester, PA 19380-0078 / Tel: 610-644-4254 / Fax: 610-640-0771
OCT-13-2009(TUE) 11:40 Yerkes WC#1 (FAX)6106400771 P. 007/007 6 of 6
Mathew J and Christine Mullen – 1645 East Strasburg Road
October 13, 2009
Page 6 of 6
23. General Landscaping Comment: Plugs should be included in the guarantee period in note Number 17, Sheet 5.
General Comments
25. Signature blocks for approval and an owner's plan acknowledgment statement should be added to the site plan if the plan is to be recorded.
26. The erosion and sediment control plan should include protective measures to prevent disturbance to the primary and replacement septic system absorption areas.
27. The site plan should note the amount of future impervious coverage that may be installed based upon the stormwater management design.
28. The zoning schedule on sheet 1 should note the height of the proposed house.
The plans should be revised in accordance with the above comments. Please do not hesitate to call if you have any questions concerning this review.
Sincerely,
YERKES ASSOCIATES, INC.
Charles E. Jackson III
Michael Conrad, P.E.
CC: SITE Engineering Concepts, LLC, Robert Lambert, P.E.
Professional services since 1874
1444 Phoenixville Pike, P. O. Box 1568, West Chester, PA 19380-0078 / Tel: 610-644-4254 / Fax: 610-640-0771
G. MULLEN 2. 4 pgs
Official seals: SEAL OF CHESTER COUNTY, PENNSYLVANIA; GOVERNOR CHESTER-WILLIAM PENN PROPRIETOR AND 83.
THE COUNTY OF CHESTER
COMMISSIONERS: Terence Farrell, Carol Aichele, Kathi Cozzone
RONALD T. BAILEY, AICP, Executive Director
PLANNING COMMISSION, Government Services Center, Suite 270, 601 Westtown Road, P.O. Box 2747, West Chester, PA 19380-0990, (610) 344-6285 Fax: (610) 344-6515
October 26, 2009
RECEIVED BY: OCT 28 2009
Louis F. Smith Jr., Manager, East Goshen Township, 1580 Paoli Pike, West Chester, PA 19380
Re: Preliminary/Final Land Development – Matthew J. & Christine Mullen # 11063-5 – East Goshen Township
Dear Mr. Smith:
A preliminary/final land development plan entitled “Matthew J. & Christine Mullen,” prepared by Site Engineering Concepts, LLC, and dated August 13, 2009, was received by this office on September 28, 2009. The land development is situated on the north side of Strasburg Road (State Route 2010) at its intersection with Springhouse Lane and involves the construction of a single-family residence on a 19.74 acre site (UPI #53-4-134.2). Vehicular access will be provided from an existing driveway entrance on Strasburg Road. The project site, which will be served by on-site water and sewer, is located in the R-2 Residential zoning district.
This plan is reviewed by the Chester County Planning Commission in accord with the provisions of Section 502 of the Pennsylvania Municipalities Planning Code (MPC). This report does not review the plan for compliance to all aspects of your ordinance, as this is more appropriately done by agents of the Township. We offer the following comments on the proposed land development for your consideration:
BACKGROUND:
1. The Chester County Planning Commission has previously reviewed a subdivision and a land development proposal involving this site. CCPC# 11063-2 (“Ashbridge Farm”), dated February 6, 2002, addressed the creation of 10 lots from a 187 acre site, was approved by the Township on March 19, 2002. This proposal involves the construction of a single-family residence on Lot 2 of the previously approved subdivision plan.
The County Planning Commission previously reviewed an earlier version of this land development submission on January 4, 2008 (CCPC# 11063-4). According to our records, this previous land development submission has not been approved by the Township.
LANDSCAPES:
2. The 1996 Chester County Comprehensive Plan, Landscapes, designates the area of the proposed land development as a Suburban Landscape. Suburban Landscapes include areas where infrastructure and public services have been, or should be, extended to accommodate residential
E-mail: ccplanning@chesco.org • www.landscapes2.org • Web site: www.chesco.org/planning
2 of 4
Page: 2, October 26, 2009, Re: Preliminary/Final Land Development – Matthew J. & Christine Mullen # 11063-5 – East Goshen Township
development and shopping and employment centers. Landscapes encourages design flexibility and a mix of density and uses, either through revitalization or infill, within the Suburban Landscape. The location of this land development proposal is consistent with the Suburban Landscape as shown on the Livable Landscapes Map, as last amended October 14, 2003.
PRIMARY ISSUES:
3. The plan and 2005 aerial photography indicate that a portion of the site is wooded. If development is to occur within the woodlands, the removal of trees should be limited to the minimum area needed for the dwelling and support facilities and the limit of tree removal should be shown on the plan. Any grading within the area of the dripline (the perimeter of the tree's branches) of the trees to be preserved increases the possibility of tree damage.
4. The site is located in an area designated by the Pennsylvania Department of Environmental Protection (DEP) as a Special Protection Watershed. Special Protection Watersheds are important because Chester County’s High Quality and Exceptional Value Watersheds may be especially sensitive to degradation and pollution that could result from development. The DEP may impose stricter limitations on proposed wastewater discharges in these watersheds, and DEP also encourages that special care be exercised in the design and construction of stormwater control facilities in these areas.
The DEP suggests that “Best Management Practices” (BMPs) be used for stormwater control, as recommended in The Pennsylvania Stormwater Best Management Practices Manual. This document is available from the Chester County Conservation District or directly from DEP via the web at: http://www.depweb.state.pa.us/watershedmgmt/cwp/view.asp?a=1437&q=518682, then select Best Management Practices (BMP) Manual. Toolbox # 32-1, in the Landscapes Community Planning Handbook Volume I, (CCPC, 1997) also contains an explanation of BMPs as well as a sample BMP ordinance. BMPs can be used to recreate pre-development conditions on all construction projects through the use of natural and manmade features such as retention and infiltration basins, pervious pavement, biofilters, grass swales, curbless streets, and other environmentally-sensitive design techniques. Project engineers are encouraged to examine these, as well as other BMPs. Addressing these issues in the initial plan submission should assist in expediting plan approval.
Additionally, the following map note should appear on all erosion and sediment pollution control plans:
“The site is located in an area designated by the Pennsylvania Department of Environmental Protection as a Special Protection Watershed, and extreme care should be exercised in all disturbance activities to prevent degradation of the waters of the Commonwealth. All disturbed areas on which work has been, or will be stopped, must be promptly stabilized with appropriate temporary or permanent stabilization measures.”
3 of 4
Page: 3, October 26, 2009, Re: Preliminary/Final Land Development – Matthew J. & Christine Mullen # 11063-5 – East Goshen Township
ADMINISTRATIVE NOTES:
5. The item on the attached checklist should be addressed and reflected in the proposed land development.
6. A minimum of five (5) copies of the plan should be presented at the Chester County Planning Commission for endorsement to permit recording of the final plan in accord with the procedures of Act 247, The Pennsylvania Municipalities Planning Code, and to meet the requirements of the Recorder of Deeds, the Assessment Office, and the Health Department.
RECOMMENDATION: The Commission recommends that the issues raised in this letter be addressed and all Township requirements be satisfied before action is taken on this plan.
Sincerely,
Ronald T. Bailey, AICP, Secretary
RTB/PF
Attachment
cc: Matthew J. and Christine A. Mullen; Site Engineering Concepts, LLC; Albert J. Giannantonio, P.E., Township Engineer; Chester County Health Department; Chester County Conservation District
4 of 4
THE COUNTY OF CHESTER
Chester County Planning Commission
601 Westtown Road, Suite 270
P.O Box 2747
West Chester, PA 19380-0990
Board of County Commissioners
Chester County, Pennsylvania
MUNICIPALITY: East Goshen Township
CCPC FILE: # 11063-5
DATE: October 26, 2009
The following agencies should be contacted regarding this subdivision or land development:
[ ] Pennsylvania Department of Transportation (PennDOT): A PennDOT permit is required for new or revised access and should be identified on the final plan as required by Section 508(6) of the Municipalities Planning Code.
[ ] U.S. Army Corps of Engineers and Pennsylvania Department of Environmental Protection (DEP): Placement of fill in wetlands is regulated by the Corps of Engineers in accordance with Section 404 of the Clean Water Act (1977) with DEP under Chapter 105 Rules and Regulations for the Bureau of Dams and Waterway Management. The applicant should contact these agencies to determine if the proposed activity will require a permit and provide the municipality with documentation of this contact and of any subsequent permit(s) before action on this plan is taken.
[ ] Pennsylvania Department of Environmental Protection (DEP): The applicant should contact DEP to determine whether a stream encroachment permit is necessary for the proposed road, driveway, or sanitary sewer line crossing in accordance with Section 205.293 of its rules and regulations and provide the municipality with documentation of this contact and the requirements of DEP before action on this plan is taken.
[X] Chester County Health Department (CCHD): A copy of the plan should be submitted to the CCHD for their review and comment on the proposed sewage disposal and/or water supply. The municipality from the appropriate authority and company prior to final plan approval, if applicable, should receive confirmation on the availability of sufficient sewer and water capacity.
[ ] Chester County Conservation District (CCCD): The applicant should contact the office of the CCCD for information and clarification on erosion control measures. The provisions of the Commonwealth Erosion Control Regulations may apply to the project and may require an Earth Disturbance Permit or a National Pollutant Discharge Elimination System permit for discharge of stormwater from construction activities.
H. CLEARWIRE
1.
5 pgs
RAMAKER & ASSOCIATES, INC.
Consulting Engineers
October 5, 2009
East Goshen Township
1580 Paoli Pike
West Chester, PA 19380
Telephone: (601) 692-7171
ATTN: Mark Gordon, Township Zoning Officer
SUBJECT: Drawing Review Response
PROJECT: Edgewood Road Water Tank (Clearwire site #PA-PHL0699)
21 Edgewood Road, West Chester, PA 19382
Ramaker & Associates Project # 15672
Dear Mr. Gordon:
This letter is in response to the September 25, 2009 drawing review performed by Yerkes Associates, Inc. (Yerkes), on behalf of the East Goshen Township, for Clear Wireless, LLC (Clearwire) site number PA-PHL0699. This proposed Clearwire telecommunications site is a co-location with an existing Sprint site on the water tank located at 21 Edgewood Road in West Chester, Pennsylvania.
Per the comments of Yerkes, Ramaker & Associates, Inc. (Ramaker) has modified the drawings for the proposed construction project. Our written responses regarding the action(s) taken for each relevant line item comment are as follows:
3) Overall site plan, sheet S-1, added to drawing set.
4) General note added to drawing set, sheets A-1 and A-2, "All proposed antenna, coax, mounts, etc. on tank shall be painted to match tank exterior. Final color to be approved by municipality".
5) General note added to drawing set, sheets A-1 and A-2.
7) Available parking areas have been identified on sheets S-1 and A-1.
8) a. Signature block added to sheet S-1.
b. A boundary survey was not available or performed at this existing telecommunications site and thus abutting parcel owner information was not available.
c. Parcel boundary and distances per the original Nextel lease added to sheet S-1.
e. Location of existing above ground utilities added to sheets S-1 and A-1.
f. Certification statement and signature lines added to sheet S-1.
10) General note added to drawing set, sheets A-1 and A-2.
12) General note added to drawing set, sheets A-1 and A-2.
13) General note added to drawing set, sheets A-1 and A-2.
1120 Dallas Street, Sauk City, Wisconsin 53583 ▲ Voice: 608-643-4100 Fax: 608-643-7999
Web: http://www.ramaker.com
2 of 5
October 6, 2009
Page 2 of 2
Revised design drawings prepared by Ramaker, revision 6 dated 10/06/09, shall be submitted in conjunction with this response letter. If you have any questions or comments, please feel free to contact me at our office, (608) 643-4100.
Sincerely,
RAMAKER & ASSOCIATES, INC.
Jason L. Frazier
Project Manager
PA-PHL0699 Response Letter 100109.doc
3 of 5
RAMAKER & ASSOCIATES, INC.
Consulting Engineers
October 5, 2009
East Goshen Township
1580 Paoli Pike
West Chester, PA 19380
Telephone: (601) 692-7171
ATTN: Mark Gordon, Township Zoning Officer
SUBJECT: Drawing Review Response
PROJECT: Edgewood Road Water Tank (Clearwire site #PA-PHL0699)
21 Edgewood Road, West Chester, PA 19382
Ramaker & Associates Project # 15672
Dear Mr. Gordon:
This letter is in response to the September 25, 2009 drawing review performed by Yerkes Associates, Inc. (Yerkes), on behalf of the East Goshen Township, for Clear Wireless, LLC (Clearwire) site number PA-PHL0699. This proposed Clearwire telecommunications site is a co-location with an existing Sprint site on the water tank located at 21 Edgewood Road in West Chester, Pennsylvania.
Per the comments of Yerkes, Ramaker & Associates, Inc. (Ramaker) has modified the drawings for the proposed construction project. Our written responses regarding the action(s) taken for each relevant line item comment are as follows:
3) Overall site plan, sheet S-1, added to drawing set.
4) General note added to drawing set, sheets A-1 and A-2, "All proposed antenna, coax, mounts, etc. on tank shall be painted to match tank exterior. Final color to be approved by municipality".
5) General note added to drawing set, sheets A-1 and A-2.
7) Available parking areas have been identified on sheets S-1 and A-1.
8) a. Signature block added to sheet S-1.
b. A boundary survey was not available or performed at this existing telecommunications site and thus abutting parcel owner information was not available.
c. Parcel boundary and distances per the original Nextel lease added to sheet S-1.
e. Location of existing above ground utilities added to sheets S-1 and A-1.
f. Certification statement and signature lines added to sheet S-1.
10) General note added to drawing set, sheets A-1 and A-2.
12) General note added to drawing set, sheets A-1 and A-2.
13) General note added to drawing set, sheets A-1 and A-2.
1120 Dallas Street, Sauk City, Wisconsin 53583 ▲ Voice: 608-643-4100 Fax: 608-643-7999
Web: http://www.ramaker.com
4 of 5
October 6, 2009
Page 2 of 2
Revised design drawings prepared by Ramaker, revision 6 dated 10/06/09, shall be submitted in conjunction with this response letter. If you have any questions or comments, please feel free to contact me at our office, (608) 643-4100.
Sincerely,
RAMAKER & ASSOCIATES, INC.
Jason L. Frazier
Project Manager
PA-PHL0699 Response Letter 100109.doc
5 of 5
RAMAKER & ASSOCIATES, INC.
October 5, 2009
Clear Wireless, LLC
Philadelphia Metro Market
1210 Northbrook Drive, Suite 420
Trevose, PA 19053
SUBJECT: STRUCTURAL EVALUATION SUMMARY
SITE: CLEARWIRE SITE ID#: PA-PHL0699
21 EDGEWOOD ROAD
WEST CHESTER, PA 19382
RAMAKER & ASSOCIATES, INC. PROJECT NO. 15672
To Whom It May Concern:
This letter summarizes the structural evaluation conducted by Ramaker & Associates, Inc. (Ramaker) for Clearwire, in regard to their PA-PHL0699 tower site. Clearwire is proposing to co-locate with the existing Nextel installation already present at this water tank site.
Nextel is currently located on the subject standpipe water tower, which is approximately 100 feet tall. Nextel currently has twelve sectorized panel antennas located on top of the tank at a centerline elevation of 107 feet. The antennas are mounted to three sector frame mounts that are welded to the roof of the tank.
Clearwire is proposing to install one (1) Andrew VHLP2.5-11 dish, one (1) Andrew PXF-52 dish, one (1) DragonWave 3-foot 18GHz dish, and three (3) KMW HB-X-WM-17-65-00T panel antennas. The panel antennas shall be installed at a centerline elevation of 107 feet and the dishes shall be installed, on the same mast pipe, but below the panel antennas, at a centerline elevation of 103 feet. The Clearwire pipe mount shall be a minimum P3STD Sch. 40 pipe. Two stiff arm single angle L2x2x1/4-inch braces are required to be installed at each vertical pipe mount that Clearwire is proposing to utilize. The braces shall be installed if they do not currently exist.
A full structural analysis was not provided but the additional wind load and moment from the proposed installation is minimal when compared to the overturning forces produced by the tank itself. Therefore, it is anticipated that the existing water tower will provide adequate strength under proposed loading conditions. Details of the proposed installation are shown within the associated Construction Drawings prepared by Ramaker. It is assumed that the existing Nextel antenna frame was installed correctly per the original design, has been properly maintained, and is in good condition with no corroded, missing, or deteriorated members.
If you have any questions or comments, please do not hesitate to contact our office.
Sincerely,
RAMAKER & ASSOCIATES, INC.
Thomas E. Moore
Project Engineer
Michael L. Pinske, P.E.
Supervising Engineer
[Seal: COMMONWEALTH OF PENNSYLVANIA, REGISTERED PROFESSIONAL ENGINEER, MICHAEL L. PINSKE, PE076173]
1120 Dallas Street, Sauk City, Wisconsin 53583 ▲ Voice: 608-643-4100 Fax: 608-643-7999
Web: http://www.ramaker.com
OCT-27-2009(TUE) 12:19 Yerkes WC#1 (FAX)6106400771 P. 002/008
H. CLEARWIRE
1.
7 pgs
Yerkes
Yerkes Associates, Inc. Consulting Engineers / Site Planners / Land Surveyors
October 27, 2009
East Goshen Township
1580 Paoli Pike
West Chester, Pennsylvania 19380
Attn: Mark Gordon, Township Zoning Officer
Re: Clearwire US, LLC - 25 Edgewood Road
Conditional Use Plan Review
Dear Mark:
The following plans prepared by Ramaker & Associates, Inc. have been submitted to this office for review:
- Title Sheet - sheet T-1
- Overall Site Plan – sheet S-1
- Site Plan – sheet A-1
- Elevation – sheet A-2
- Details and Notes – sheet A-3
- Coax Color Coding – sheet A-4
- Equipment Details – sheet A-5
- Cabinet Specifications – sheet A-6
- Utility Plan – sheet E-1
- Grounding Plan – sheet E-2
- Grounding Details – sheets E-3 and E-4
All plans have a latest revision date of October 6, 2009. The plan submission also included a plan submission letter dated October 5, 2009 and a structural evaluation summary letter dated October 5, 2009.
The parcel owner is Aqua Pennsylvania, Inc. (formerly Philadelphia Suburban Water Co.) and the applicant is Clearwire US, LLC. The 9,075 square foot parcel is located south of West Chester Pike between Edgewood Road and the Summit House Condominium. The parcel contains an approximately 102 foot high water tower, driveway, communication equipment pads and shelters, trees, and fencing. The plan depicts the installation of three panel antennas and three parabolic antennas at the top of the water tower and two equipment cabinets on Sprint's leased platform area at the base of the tower.
All comments from my previous review letter of September 25, 2009 have been satisfactorily addressed except for the following that are numbered as they appeared previously:
Professional services since 1874
1444 Phoenixville Pike, P.O. Box 1568, West Chester, PA 19380-0078 / Tel: 610-644-4254 / Fax: 610-640-0771
OCT-27-2009(TUE) 12:19 Yerkes WC#1 (FAX)6106400771 P. 003/008 2 of 7
Clearwire - Edgewood Road
October 27, 2009
Page 2 of 3
Zoning Ordinance
1. Section 240-31.C.3.h.2.e - Within the R-5 Zoning District, Conditional Use approval is required to locate communication antennas on an existing water tower and to install support equipment on the ground. The requirements for Conditional Use approval must be addressed to the Board's satisfaction.
2. Section 240-31.C.3.h.2.e.ii – The applicant shall demonstrate to the Board's satisfaction that the proposed antenna location and antenna height are necessary to provide satisfactory coverage. The applicant shall also demonstrate that the proposed location will obviate the need for the erection of a communication antenna support structure in another location where the same is permitted.
3. Section 240-31.C (3) (h) [2] [e] [iii]: A site plan depicting all buildings and structures located on contiguous properties should be provided.
4. Section 240-31.C(3) (h) [2] [e] [iv]: Concealment or other reasonably appropriate stealth measures to camouflage or conceal antennas, such as the use of neutral materials that hide antennas, shall be incorporated into the site plan design. Measures to conceal or camouflage the proposed antennas shall be incorporated into the site plan to the Board's satisfaction. General note 1 on sheets A-1 and A-2 states "All proposed antennas, coax, mounts, etc. on tank shall be painted to match tank exterior. Final color shall be approved by municipality."
6. Section 240-31.C.3.h.2.n – Where antenna(e) are proposed to be attached to an existing structure, a structural engineer shall certify that both the structure and the antenna(e) and their appurtenances meet minimum industry standards for structural integrity. A structural analysis and inspection report should be included with the conditional use application.
Comments regarding the Structural Evaluation Summary Letter are outlined in the attached October 26, 2009 review letter prepared by James A. Koppenhaver, P.E.
8. Section 240-31.C (3) (h) [2] (q): The plan shall comply with requirements of Chapter 205, Subdivision and Land Development Ordinance as follows:
a. Section 205-33.A.3 – Signature blocks for approval should be added to the site plan. A copy of the format established by the Township is attached.
b. Section 205-33.B.5 – The site plan should note the names, deed book, and page number of all abutting parcel owners.
c. Section 205-33.B.7 – The location of the parcel boundary should be indicated on the plan and be described with bearings and distances.
Professional services since 1874
1444 Phoenixville Pike, P.O. Box 1568, West Chester, PA 19380-0078 / Tel: 610-644-4254 / Fax: 610-640-0771
OCT-27-2009(TUE) 12:19 Yerkes WC#1 (FAX)6106400771 P. 004/008 3 of 7
Clearwire - Edgewood Road
October 27, 2009
Page 3 of 3
f. Section 205-33.B.17 – A certification statement of ownership and plan acknowledgement should be added to the site plan and be signed and notarized by the parcel owner. A copy of a typical plan acknowledgment statement is attached.
9. Section 240-31.C (3) (h) [2] [t]: A description of the anticipated maintenance needs, including frequency of service, personnel needs, equipment needs, and the traffic safety and noise impacts of such maintenance should be provided with the application.
11. Section 240-31.C (3) (h) [2] [x]: Proof of notification of all owners within 1,000 ft. of the communications site should be provided to the Board.
The plan submission should be revised in accordance with the above comments. Please contact this office if you have any questions concerning this review.
Sincerely,
YERKES ASSOCIATES, INC:
Michael Conrad, P.E.
Cc: ACO Property Advisors, Inc.
Professional services since 1874
1444 Phoenixville Pike, P.O. Box 1568, West Chester, PA 19380-0078 / Tel: 610-644-4254 / Fax: 610-640-0771
OCT-27-2009(TUE) 12:19 Yerkes WC#1 (FAX)6106400771 P. 005/008 4 of 7
Yerkes
Yerkes Associates, Inc. Consulting Engineers / Site Planners / Land Surveyors
October 26, 2009
East Goshen Township
1580 Paoli Pike
West Chester, PA 19380
Attn: Mr. Mark A. Gordon, Township Zoning Officer
Re: Clear Wireless - Additional Antenna Mounts on Water Tower at 21 Edgewood Road
Structural Review
Dear Mark:
Our office has received a structural evaluation summary from Ramaker & Associates, Inc., Michael L. Pinske, P.E. The letter summarizes Clearwire's proposal to install three (3) dishes at a center line elevation of 103' and three (3) panel antennas installed at a center line elevation of 107'.
The antennas shall be installed on Sch. 40 mast pipe mounted to three (3) Nextel Sector Frame Mounts that are presently welded to the roof of the tank. Two (2) stiff arm single angle braces shall be installed at each vertical pipe mount.
A full structural analysis was not provided but the additional wind load and moment from the proposed antennas are minimal when compared to the overturning forces produced by the tank itself. The structural evaluation summary anticipates that the existing water tower will provide adequate strength for the loading conditions of the proposed antennas. The structural evaluation summary also assumes that the existing Nextel antenna frame was installed per the original design, has been properly maintained, and is in good condition with no corroded, missing, or deteriorated members.
Note 6 on the construction drawings for the proposed installation require the contractor to perform a safety inspection prior to commencing the work and that Clearwire should be notified of safety hazards that could cause damage to property. Note 7 on the drawings states that tower modifications, if required, are to be completed before the installation of the antennas.
The following comments should be addressed prior to issuance of the permit for the proposed antenna installation:
1. Zoning Ordinance Section 240-31.C.3.h.2.[l] – The applicant shall submit to the Township proof of the annual inspection of the antenna support structures by an
Professional services since 1874
1444 Phoenixville Pike, P.O. Box 1568, West Chester, PA 19380-0078 / Tel: 610-644-4254 / Fax: 610-640-0771
OCT-27-2009(TUE) 12:19 Yerkes WC#1 (FAX)6106400771 P. 006/008 5 of 7
October 26, 2009
Clear Wireless - 21 Edgewood Road
Structural Review
Page 2 of 2
independent professional engineer as required by ANSI/EIA/TIA-222-E Code. Special attention shall be given to the attachment points of the mount framing to the roof of the tank. These connections shall be checked for signs of stress, fatigue, cracks, and rust. The contractor should not be permitted to complete this inspection. Based on the results of such inspection, the Board of Supervisors may require repair of the support structure.
2. Zoning Ordinance Section 240-31.C.3.h.2.[n] – Prior to the Township's issuance of a permit authorizing construction and erection of the antennas, a structural engineer registered in Pennsylvania shall issue a written certification of the installations ability to meet the structural standards of the ANSI/EIA/TIA-222-E Code. The engineer shall certify the proper construction of the existing Nextel antenna support structures and certify that both the existing structures and the antennae and their appurtenances meet minimum industry standards for structural integrity.
The engineer shall certify that the existing Nextel antenna frame was installed per the original design, has been properly maintained, and is in good condition with no corroded, missing, or deteriorated members.
Approval of the antenna installation cannot be recommended until the above comments have been satisfactorily addressed.
If you have any questions please call me at 484-794-9949.
YERKES ASSOCIATES, INC.
James A. Koppenhaver, P.E.
Structural Consultant
Cc: Michael Conrad, P.E., Yerkes Associates, Inc.
Professional services since 1874
1444 Phoenixville Pike, P.O. Box 1568, West Chester, PA 19380-0078 / Tel: 610-644-4254 / Fax: 610-640-0771
OCT-27-2009(TUE) 12:19 Yerkes WC#1 (FAX)6106400771 P. 007/008
6 of 7
Plan drawing excerpt on left showing boundary line and road labels: FOUND; WOODEN FENCE POST & RAIL (3 RAILS); R2 ZONING; LEGAL RIGHT OF WAY LINE; IDA LANE; 50' R/W; LEGAL RIGHT OF WAY LINE.
REVIEWED by the Planning Commission of East Goshen Township, Chester County, Pa., this ________ day of ____________, 20___.
| Signature | Signature |
|---|---|
| Chairman | Member |
| Vice-Chairman | Member |
| Member | Member |
| Member |
APPROVED by the Board of Supervisors of East Goshen Township, Chester County, Pa., this ________ day of ____________, 20___.
| Signature | Signature |
|---|---|
| Chairman | Supervisor |
| Vice-Chairman | Supervisor |
| Supervisor |
REVIEWED by the Chester County Planning Commission this ________ day of ____________, 20___.
Secretary
APPROVED by the East Goshen Township Engineer;
Date
Recorded in the Office of the Recorder of Deeds of Chester County at West Chester, Pennsylvania in Plan book ________, Page ________, on the ________ day of ____________, 20___.
(Deputy) Recorder of Deeds
OCT-27-2009(TUE) 12:19 Yerkes WC#1 (FAX)6106400771 P. 008/008 7 of 7
[Legal acknowledgment fragment: ... OF CHESTER ... A.D. ... ary ania, ... on, I the he said ... poration it all obtained aid an may]
COMMONWEALTH OF PENNSYLVANIA COUNTY OF CHESTER
On the ___________day of _________________A.D. 20___ before me, the subscriber, a Notary Public of the Commonwealth of Pennsylvania, residing in ___________________________, personally appeared ___________________ who acknowledges himself to be the _________ ______________________ of _________________ ________________________, a Corporation, and that as such to do so, he executed the foregoing plan by signing the name of the said Corporation by himself as ________________ ________________________ that the said Corporation is the owner of the designated land, that all necessary approval of the plan has been obtained and is endorsed thereon and that the said Corporation desires that the foregoing plan may be duly recorded.
____________________________________
Notary Public
My Commission Expires:____________________________
[Plan drawing fragment: FOREST / SITE / EAST GOSHEN TOWNSHIP]
[Site plan drawing: R2 ZONING, STONE FOUND, N76°52'14"E 63.50', STREAM, STONE FOUND, 60939 SF TOTAL, -4213 SF ROAD R/W, 56726 SF NET = 1.302 AC., 2 STORY STUCCO, STONE & VINYL BUILDING, DOORSILL ELEV=481.18, WOODEN FENCE POST & RAIL (3 RAILS), S77°57'16"W 246...]
[Approval block fragment: REVIEWED by the Planning Commission of East Goshen Township, Chester County ... day of ... Chairman, Vice-Chairman, Member ... APPROVED by the Board of Supervisors of East Goshen Township, Chester County ... day of ...]
11. McGinley
2.
5 pgs
[Stamp: RECEIVED JAN 12 2005 By ________]
IN RE: THE APPLICATION OF CHRISTIAN KACALA
BEFORE THE ZONING HEARING BOARD OF EAST GOSHEN TOWNSHIP
CHESTER COUNTY, PENNSYLVANIA
DECISION
The Zoning Hearing Board of East Goshen Township, Chester County, Pennsylvania (the "Board"), after proper advertisement, met at approximately 7:30 P.M. on Wednesday, December 15, 2004 to hear evidence on the case. Applicant, Christian Kacala, seeks a variance from the twenty (20) foot minimum side yard requirement of Section 240-10G of the Zoning Chapter of the East Goshen Township Code ("Code") with respect to the property located at 19 School Lane, East Goshen Township, Chester County, Pennsylvania (the "Property"). The Applicant, Christian Kacala, appeared on behalf of himself.
Present at the hearing were Zoning Hearing Board Members, Chairman, Joseph Neff Ewing, Jr., Esquire, Member, Janet L. Emanuel, and Member, John T. Nicholson, Esquire. Also present were Joyce Tarsi, Zoning Hearing Board Secretary, and Ross A. Unruh, Esquire, Solicitor for the Zoning Hearing Board. At the conclusion of the hearing, the Board voted unanimously to grant the requested variance. The Applicant waived the time period in the Pennsylvania Municipalities Planning Code ("MPC") with respect to the issuance and service of this written Decision.
I. FINDINGS OF FACT
1. The Property is located at 19 School Lane, East Goshen Township, Chester County, Pennsylvania, which is in the R-3 Medium Density Residential District.
2. The following exhibits were presented and accepted into evidence at the hearing:
B-1 - Application;
B-2 - Proof of publication;
H:\Documents\Diane\EGZHB\KacalaDec.doc January 11, 2005
2 of 5
B-3 - Affidavit of Posting;
B-4 - Notice to neighboring property owners;
B-5 - December 2, 2004 East Goshen Township Planning Commission letter;
B-6 - December 8, 2004 East Goshen Township Board of Supervisors letter;
A-1 - Floor plan;
A-2 - Site plan; and
A-3 - Site plan with handwritten notation showing location of proposed dwelling unit.
The Code and Map are incorporated herein by reference.
3. Applicant is the owner of the Property.
4. The Property is one hundred seventy-six (176) feet deep, but only fifty (50) feet wide.
5. Applicant is proposing to construct on the Property a modular home which will be twenty (20) feet wide and fifty-two (52) feet long.
6. In order to comply with the twenty (20) foot side yard requirement, the Applicant would be required to construct a ten (10) foot wide house, which is neither reasonable nor practical.
7. When Applicant purchased the Property there was a dilapidated structure on the Property which was twenty-four (24) feet wide. Applicant has removed this structure.
8. What Applicant is proposing to construct will be less non-conforming than the structure which he removed.
9. Applicant proposes to fill and cap the existing well on the Property.
2
H:\Documents\Diane\EGZHB\KacalaDec.doc January 11, 2005
3 of 5
10. The proposed house will be built into the slope at the rear of the Property.
11. Parking will be off-street and in a garage which will be underneath the home.
12. What Applicant is proposing to construct will be similar to the housing stock and the setbacks of the housing stock in the neighborhood.
13. This Board has granted similar variances for other properties in the neighborhood.
14. Between the meeting with the Board of Supervisors and this Zoning Hearing Board, the Applicant endeavored to address neighbor concerns.
15. No one appeared to oppose the application.
16. The Board of Supervisors took no position on the application.
17. The Planning Commission recommended against granting the application, but noted that if the application were granted that the Applicant should be required to comply with the steep slope provisions in the Code.
18. The granting of the variance appears to be consistent with the spirit, intent and purpose of the Code.
19. The granting of the variance is the minimum required to afford reasonable use of the Property.
20. The granting of the requested variance appears to be in harmony with the general purpose and intent of the Code, and will not be injurious to the neighborhood, or otherwise detrimental to the public health, safety and welfare of the community.
II. DISCUSSION
Section 904 of the Code empowers the Zoning Hearing Board to grant variances from the terms of the Code. The MPC and existing case decisions provide that variances from a zoning
3
H:\Documents\Diane\EGZHB\KacalaDec.doc January 11, 2005
4 of 5
ordinance may be granted owing to any physical circumstance or condition of the property which cause unnecessary hardship, and which hardship is not self-created. In addition, it has recently been established that applicants for a dimensional variance need not be held to the same strict standards imposed on applicants for a use variance. Hertzberg v. Zoning Board of Adjustment of the City of Pittsburgh, 721 A.2d 43 (Pa. 1998).
With respect to the encroachment into the side yards, the Board first notes that Applicant is proposing to encroach into the side yards less than what had existed with the prior structure. In addition, due to the narrow width of the Property (i.e., only fifty (50) feet wide) the variance requested is the minimum necessary to make reasonable use of the Property. Either under the specific standards in the MPC or more relaxed standards for dimensional variances established by the Pennsylvania Supreme Court, the Board believes that the Applicant is entitled to the required variance.
III. CONCLUSIONS OF LAW
1. The Applicant's request is the minimum necessary to permit reasonable use of the Property.
2. Applicant has established entitlement to the dimensional variance.
3. So long as the Applicant complies with the conditions set forth herein, Applicant's request for the variance shall not be injurious to the neighborhood or otherwise detrimental to the public welfare.
IV. ORDER
AND NOW, this _________ day of ________________, 2005, Applicant, Christian Kacala, is HEREBY GRANTED a variance from the twenty (20) foot side yard setback requirement of Section 240-10G of the Code in order to install the proposed modular home on his Property located at 19 School Lane, East Goshen Township, Chester County, Pennsylvania as more
4
H:\Documents\Diane\EGZHB\KacalaDec.doc January 11, 2005
5 of 5
particularly depicted in the Exhibits and provided that Applicant complies with all Township Codes and regulations, particularly the steep slope regulations.
| ATTEST: | EAST GOSHEN TOWNSHIP ZONING HEARING BOARD |
|---|---|
| [Signature: Joseph Neff Ewing, Jr.] _________________________________ Joseph Neff Ewing, Jr., Esquire |
|
| [Signature: Janet L. Emanuel] _________________________________ Janet L. Emanuel |
|
| [Signature: John T. Nicholson] _________________________________ John T. Nicholson, Esquire |
5
[Handwritten top right: H. McGinley
2.
1 pg.]
610-692-7171
www.eastgoshen.org
BOARD OF SUPERVISORS
EAST GOSHEN TOWNSHIP
CHESTER COUNTY
1580 PAOLI PIKE, WEST CHESTER, PA 19380-6199
October 27, 2009
Dear Property Owner:
The purpose of this letter is to inform you that mark and Helen McGinley, 77 Dilworthtown Rd., Thornton, PA 19373, have submitted an application for a variance to the Township. The applicant would like to construct a single-family detached dwelling unit on his property at 19 School Lane.
The applicant is requesting a variance from the 20-foot minimum side yard requirement for the dwelling. The existing lot is only 50 feet wide so the variance, if granted would result in only a fifteen foot side yards.
The Zoning Hearing Board will hold a public hearing to consider the variance application and decide whether or not to grant the requested variance.
The Planning Commission will review the application and make a recommendation to the Zoning Hearing Board. The Board of Supervisors may, if they choose, take a position on this application. The public meetings for the project's review and potential approval are as follows:
November 4, 2009 Planning Commission meeting (7:30 pm - workshop at 7:00 pm)
November 17, 2009 Board of Supervisors (8:00 pm - workshop at 7:00 pm)
November 18, 2009 Zoning Hearing Board Public Hearing (7:30 pm)
All public hearings, meetings, and workshops are open to the public and they are held at the Township Building, 1580 Paoli Pike. The application is available for review at the Township Building during normal business hours. Any person who wishes to attend the hearing and has a disability and/or requires an auxiliary aid, service or other accommodation to observe or participate in the hearing, he or she should contact Joyce A. Tarsi at (610) 692-7171 to discuss how those needs may be accommodated.
Should you have any questions or need additional information, please call me at (610) 692-7171, or email me at mgordon@eastgoshen.org.
Sincerely,
[Signature: Mark Gordon]
Mark Gordon
Township Zoning Officer
Cc: Mark and Helen McGinley
Authority, Boards and Commissions
F:\Data\Shared Data\Property Management\53-6g\53-6g-23 19 School Lane\Variance 2009\1000 foot letter 102709.doc
[Handwritten top right: H. McGinley
2.
1 pg.]
Memorandum
East Goshen Township
1580 Paoli Pike
West Chester, PA 19380
Voice: 610-692-7171
Fax: 610-692-8950
E-mail: mgordon@eastgoshen.org
Date: 10/30/2009
To: Planning Commission
From: Mark Gordon, Township Zoning Officer [Signature: MG]
Re: 19 School Lane
Dear Commision Members,
19 School Lane has been before this commission in the past for the same variance request and subsequently was granted this relief by the ZHB due to the narrow lot width. The variance expired and there is a new owner now. This property would be required to have a 10 foot wide house. The applicant is requesting relief of 5 feet on each side yard setback.
Draft Motion:
I move that we recommend that the Board of Supervisors support this variance request allowing 15 foot side yard setbacks due to the narrowness of the lot.
F:\Data\Shared Data\Property Management\53-6g\53-6g-23 19 School Lane\Variance 2009\Draft motion 103009.doc
[Handwritten top right: K. NEW BUSINESS
1.
5 pgs]
[Stamp: FILE COPY]
Memo
East Goshen Township
1580 Paoli Pike
West Chester, PA 19380
Voice (610) 692-7171
Fax (610) 425-8950
E-mail rsmith@eastgoshen.org
Date: October 6, 2009
To: Board of Supervisors
From: Rick Smith, Township Manager
Re: Increase Buffers to 100 feet.
The Conservancy Board has recommended that the Township increase the buffer area along streams from 50 feet to 100 feet.
Attached are sections of a Township map upon which we plotted the streams (blue), the existing 50 feet setback (red), the proposed 100 setback (green) and the floodplain (purple).
I made that assumption that if the 100 setback was contained entirely within the floodplain the property would not be impacted since that land area was already restricted.
I have highlighted in yellow those parcels (yellow) that would affected.
of those parcels (yellow) that would effected. MI made that assumption that if the 100 setback
[Handwritten bottom right:
To PC
For Recommendation
10/13/09
BoS]
F:\Data\Shared Data\ABC'S\Conservancy Board\Memo to BoS re 100 foot stream buffer 100609.doc
[Handwritten top right: 2 of 5]
[Illustration of tree foliage and branches on top and right margin]
EAST GOSHEN
CONSERVANCY
September 9, 2009
Supervisors
East Goshen Township
Dear Supervisors,
As I am sure you are aware, there is a coalition of groups in Pennsylvania, including Clean Water Action, which is pressing the state to require a 100 foot buffer along all streams whenever new development occurs. Chester County is also recommending this.
Buffers help filter out pollution from runoff, prevent erosion and flooding, provide important habitat, and help reduce drinking water treatment costs. They are good for Pennsylvania's environment and economy.
We are one of the 192 Pennsylvania municipalities which have stream buffer rules, but we are not part of the 30% which have required a buffer of 100' or more in width.
The Conservancy Board would like to suggest that we consider joining that 30%.
Thank you for your consideration.
Sincerely,
[Signature: Bryan Delmonte]
Bryan Delmonte, Vice –Chairman,
Conservancy Board
1580 PAOLI PIKE, WEST CHESTER, PA. 19380
3 of 5
Map of property parcels, streets, and stream corridor buffer contours in East Goshen Township (sheet 3 of 5).
Map Labels
- MILL STREA
- HERSHEY MILL RD
- JACKSON LA
- UPTON CI
- GARRETT LA
- RENNARD LA
- FRANKLIN WY
- CHANDLER DR
- MILL DR
- EATON WY
- NEWBURY LA
- ILL DR
- TULIP DR
- BARKWAY LA
- ALLAN LA
- HIGHGATE RD
- WATERFORD RD
- YOUNGS LA
- WEXFORD CI
- KENNETT WY
- GREAT OAK CI
- AMSTEL WY
- RT 202
- MORSTEIN RD
- KILLERN LA
- MARY JANE LA
- JOSHUA LA
- GREENHILL RD
- CULBERTSON DR
- BOOT RD
- WINDSOR DR
- WILSON DR
485 (handwritten)
Map of property parcels, streets, and stream corridor buffer contours in East Goshen Township (sheet 4 of 5).
Map Labels
- GENERALS
- ENTERPRISE DR
- PAOLI PK
- MEADOW DR
- RESERVOIR RD
- PINE ROCK RD
- LARCH LA
- STAGHORN WY
- BRAMBLE LA
- ELLIS LA
- MARK DR
- BALDWIN DR
- COOPER CI
- VALLEY CI
- STRASBURG RD
- BROOK DR
- WEST C
- PARK AV
- ID LA
5 of 5
Map of property parcels, streets, and stream corridor buffer contours in East Goshen Township (sheet 5 of 5).
Map Labels
- BOOT RD
- DR
- SUFFOLK DOWNS
- THORNCROFT DR
- TOWNSHIP LINE RD
- CHOWNING DR
- TOWNE DR
- OFIELD LA
- R
- N MILL RD
[Stamp top right: FYI]
610-692-7171
www.eastgoshen.org
BOARD OF SUPERVISORS
EAST GOSHEN TOWNSHIP
CHESTER COUNTY
1580 PAOLI PIKE, WEST CHESTER, PA 19380-6199
October 27, 2009
Mr. Thomas Logan
1373 Enterprise Drive
West Chester PA 19380
Re: T.P.N. 53-4-155 (CTDI, 1334 Enterprise Drive)
Parking Complaints
Dear Mr. Logan:
Thank you for taking the time to meet with me, Ralph Brown, and Gary Althouse on October 14th to discuss the facility operations and the numerous complaints about the parking and traffic circulation issues at the CTDI facility (1334 Enterprise Drive). I have the following observations and concerns and request your formal response.
Parking at 1334 has become particularly hazardous and is causing dangerous and inconvenient circumstances for the surrounding businesses and motorists circulating through the associated driveway connecting the Goshen Executive Center and Enterprise Drive. The Conditional Use approval for this property states that there shall be one parking space per employee on the largest shift. You indicated during my visit of the facility, that the largest shift has 88+ employees, and that the facility has 70 parking spaces. I have enclosed a copy of the Conditional Use approval for your use.
Please outline for the Township how you plan to accommodate the parking condition as outlined in the approval.
Thank you for your cooperation. Should you have any questions, please contact me at mgordon@eastgoshen.org.
Sincerely,
[Signature: Mark A. Gordon]
Mark A. Gordon
Township Zoning Officer
CC: Board of Supervisors
Planning Commission
Enclosure
F:\Data\Shared Data\Property Management\53-4\53-4-155 (1334 Enterprise Drive)\parking Letter 102709.doc
AREA CODE 215
692-7171
BOARD OF SUPERVISORS
EAST GOSHEN TOWNSHIP
CHESTER COUNTY
1580 PAOLI PIKE, WEST CHESTER, PA. 19380
July 22, 1992
[Stamp: RECEIVED AUG - 7 1992 EAST GOSHEN TOWNSHIP]
Mr. Gerald Parsons
Communications Test Design, Inc.
1373 Enterprise Dr.
West Chester, PA 19380
RE: Conditional Use Application
1334 Enterprise Drive
Tax Parcel #53-4-155
Dear Mr. Parsons:
At the hearing held Tuesday, July 21, 1992, the Board of Supervisors unanimously approved your request to utilize the building at 1334 Enterprise Drive as a multiple principle use building, pursuant to Section 403.3a of the Township Zoning Ordinance, with the following uses:
1) repair and assembly of electronic equipment including computer hardware, pursuant to Section 403.2(h),
2) research and development of computer software packages, pursuant to Section 403.s(i) and
3) short term warehousing of equipment which will be transferred to CTDI's repair shops for testing and repair, pursuant to Section 403.3(b).
This approval is conditioned upon the following:
1) Any HVAC unit added to the roof of the building shall be screened in accordance with the requirements of Section 403.6(b).
2) The applicant shall paint all of the existing HVAC units brown.
3) All dumpsters and/or recycling containers shall be screened in accordance with Section 506.3(d).
BOARD OF SUPERVISORS
EAST GOSHEN TOWNSHIP
Page 2
4) A parking space shall be provided for each employee on the largest shift and the parking lot shall be lined in accordance with Section 512.3(b) and (j).
5) Loading docks shall be screened with a minimum of ten eight foot trees; the type and placement to be decided by the applicant and the Township Conservancy Board.
6) All signs shall be reviewed and approved by the Township Planning Commission prior to the issuance of a permit.
At the hearing, you verbally acknowledged your acceptance of these conditions. I would appreciate it if you would also sign the enclosed copy of this letter and return it to me for my file.
If you have any questions, please contact me.
Sincerely yours,
[Signature: Rick]
Louis F. Smith, Jr.
Township Manager
LFS/dlc
enclosure
cc: Planning Commission
Conservancy Board
Thomas Oeste, Esq.
I understand and accept the aforementioned conditions.
| Acknowledgment | Date |
|---|---|
| [Signature] _________________________________ Communications Test Design, Inc. |
[Handwritten: 8-7-92] _________________________________ Date |
Memorandum
East Goshen Township
1580 Paoli Pike
West Chester, PA 19380
Voice: 610-692-7171
Fax: 610-692-8950
E-mail: mgordon@eastgoshen.org
Date: 10/22/2009
To: Charles Proctor
From: Mark Gordon, Township Zoning Officer [Signature: MG]
Re: Wireless Communications Questions
Dear Chuck,
As per the conversations at the last Planning Commission meeting I captured some questions that they would like you to send on to your Son-In-Law for consideration and review for the conference call during the 11/4/09 meeting. I will have a telephone available and this will fall in right after review of minutes and administrative matters, so he can expect the call around 7:15 pm. Here are the questions the PC came up with. Let me know if you have any questions.
- What is the wireless industry interpretation of the federal law with respect to wireless communication facility (WCF) cites in residential areas?
- How long will current wireless communication infrastructure technologies be feasible before it is obsolete, i.e. traditional towers vs. satellite or some other technology?
- We have enclosed our wireless communication ordinance for your review, do you see any major areas where we could improve it?
- What feasibility is there for multiple providers to use the same wireless network, towers and antennas?
- What is the distance limitation of "Line of Site" from Phone to Tower?
- Our ordinance outlines "microwave bonding" under Antenna support structure safety, which is highlighted for you. What experience do you have with this phenomenon and is it a common occurrence in the industry?
- What are the health hazards associated with wireless communication tower antenna and equipment, RF energy, and cellular / wireless phones?
F:\Data\Shared Data\ABC'S\Planning Commission\Wireless Communication Questions 102209 Final.doc