Planning Commission
The East Goshen Township Planning Commission is an advisory board to the Township Board of Supervisors. The Commission reviews all subdivision and land development applications, conditional use applications, zoning hearing board applications and makes recommendations to the Board of Supervisors. The Commission also reviews or drafts Zoning Ordinance Amendments. Each member is appointed by the Board of Supervisors.
- Composed of seven East Goshen Township residents each serving a four-year term.
- Formal Meetings are held the 4th Tuesday of each month at 7:00 P.M.
- Workshop Meeting are held on an as needed basis
- All township meetings are held at the Township Building and are open to the public
| Planning Commission Members | Term Expiration Date |
| John Stipe, Chair | 2026 |
| Dan Truitt, Vice Chair | 2027 |
| Daniel H. Daley | 2027 |
| Michael Koza | 2026 |
| Ernest Harkness | 2026 |
| Karen Martynick | 2029 |
| William Kaufman | 2029 |
| Larry Massaro, BOS Liaison | |
| Kelly Krause, Staff Liaison |
Draft Ordinance-Zoning Amendment Regulating Data Centers by Conditional Use 9.24.26
Click here to view – May 4th Documents for Malvern Institute and East Whiteland Special Study.
Related News
PLANNING COMMISSION CONSIDERS UPGRADES TO AQUA FACILITY
Wednesday, November 18, 2026
At its September meeting, the East Goshen Planning Commission reviewed a conditional use application from Aqua Pennsylvania to upgrade its Hunt Country well treatment facility located on Thorncroft Drive. The upgrade is required to meet new maximum contaminant levels (MCLs) for PFAS in drinking water that were enacted last year by the U.S. Environmental Protection […]
View ArticleFrom the Planning Commission: Addressing Potential Data Center Development in East Goshen Township
Wednesday, September 30, 2026
As the demand for artificial intelligence accelerates, municipalities throughout Pennsylvania have found themselves navigating complex regulations, legal challenges, and community debates about large-scale data centers. While no data center projects are currently proposed in East Goshen, township officials are proactively addressing potential impacts by updating zoning ordinances to create strict standards that will apply should […]
View ArticleDocuments
Back to the list | Open the original PDF
Notice: this accessible version was created automatically from the original document. The transcription may not be 100% accurate. It is provided for searching and for screen readers; please refer to the original document for the official version.
EAST GOSHEN TOWNSHIP
PLANNING COMMISSION
Meeting Agenda
Wednesday, February 1, 2017
7:00 PM
- Call to Order / Pledge of Allegiance and Moment of Silence
- Chairman will ask if anyone is going to record the meeting
- Review of Tracking Log / Determine need for Workshop Meeting Possible DVRPC Presentation on the aging demographics of the region (2/15/2017)
- Public Comment on Non-Agenda Items
- Approval of Minutes January 4, 2017
- Subdivision and Land Development Applications 1420 E. Strasburg Rd. (Brakman Property, SD/LD) Revised Plans dated 1/10/2017 Applicant Response Letter dated 1/12/2017 Pennoni Review Letter dated 1/26/2017; Revised Plans dated 1/10/2017; Applicant Response Letter dated 1/12/2017; Pennoni Review Letter dated 1/26/2017
- Conditional Uses and Variances
- Ordinance Amendments
- Old Business
- New Business
- 2017 Goals
- Any Other Matter
- Liaison Reports
- Correspondence
Bold Items indicate new information to review.
F:\Data\Shared Data\Agendas\Planning Commission7\PC AGENDA 02012017.doc
East Goshen Township
Planning Commission Tracking Log
| Application Name | Application (CU,LD,O, SD,V, SE, CA | Type (Sk, P, F) | Date Filed | Start Date | Date to Township Engineer | Date to CCPC | Date to Abutting Prop. / ABC's | Extension | PC NLT Action Date | BOS NLT Action Date | Hearing Date | Drop Dead date | Comments |
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 1420 E. Strasburg Rd. / Brakman-Gunnison | SD/LD | P/F | 5/18/16 | 6/1/16 | 5/19/16 | 5/19/16 | 5/20/16 | 3 | 3/1/17 | 3/21/17 | NA | 3/29/17 | |
| Bold = New Application or PC action required | |||||||||||||
| Completed in 2017 | |||||||||||||
F:\Data\Shared Data\ABC'S\Planning Commission\PC Tracking Log7\PC Tracking Log for 02012017.xlsx
Draft
EAST GOSHEN TOWNSHIP
PLANNING COMMISSION MEETING
January 4, 2017
The East Goshen Township Planning Commission held a regularly scheduled meeting on Wednesday, January 4, 2017 at 7:00 p.m. at the East Goshen Township building. Members present were: Chairman Adam Knox, Lori Kier, Jim McRee, Dan Daley, and Brad Giresi. Also present was Mark Gordon, Township Zoning Officer and Janet Emanuel, Township Supervisor.
COMMON ACRONYMS:
| BOS – Board of Supervisors | CPTF – Comprehensive Plan Task Force |
|---|---|
| BC – Brandywine Conservancy | CVS – Community Visioning Session |
| CB – Conservancy Board | SWM – Storm Water Management |
| CCPC – Chester Co Planning Commission |
A. FORMAL MEETING – 7:00 pm
- Adam called the meeting to order at 7:00 pm. He led the Pledge of Allegiance and a moment of silence to remember our troops.
- Adam asked if anyone would be recording the meeting and if there were any public comments about non-agenda items. There was no response.
- Adam reviewed the Tracking Log and determined no need for a workshop
- Adam noted that the minutes of the December 7, 2016 meeting were approved.
B. SUBDIVISION & LAND DEVELOPMENT APPLICATIONS
- 1420 E. Strasburg Road (Brakman Property) - Jim Brandolini was present representing the owner. Jim reviewed the revised plan for 1 existing home and 2 new homes. The layout for new home #2 has been changed so the stormwater will flow down the hill to E. Strasburg Road. They received a letter from the County with changes, which have been made. The neighbor on the other side of E. Strasburg has granted an easement to allow for better public sewer/water installation. Jim will submit the revised plan to the Township Engineer for review.
C. LIAISON REPORT
- Board of Supervisors – Janet reported that Senya has resigned from the Board. She explained the process to apply for the position. Send your application to Rick Smith.
D. OLD BUSINESS
- Goals for 2016 – Adam will make the presentation at the Annual ABC Meeting this Saturday. Goals for 2017 will be Paoli Pike Trail, Zoning Ordinance review and discuss emerging trends
- Zoning Ordinance Review – Signs – The Commission continued their review of Temporary Signs, Sections Q thru W covering off premises stand alone and land development signs. No changes were made.
ADJOURNMENT
There being no further business, Dan moved to adjourn the meeting. Adam seconded the motion. The meeting adjourned at 8:10 pm. The next regular meeting will be held on Wednesday, February 1, 2017 at 7:00 pm.
Respectfully submitted,
Ruth Kiefer, Recording Secretary
PC 1-4-17 draft
1
[Engineering Plan Drawing: Title Plan (Sheet 1 of 11) for Brakman Property Subdivision and Land Development Plan, showing 3 proposed lots along East Strasburg Road (S.R. 2010), location map (Scale 1" = 2000'), graphic scale (1" = 40'), and professional engineer seal for Victor Kelly, Jr., PE (No. 041308).]
Plan Labels: EAST STRASBURG ROAD (S.R. 2010, 50 FOOT WIDE LEGAL RIGHT OF WAY, POSTED SPEED LIMIT - 40 MPH), BROOK DRIVE, TRIBUTARY 7 OF EAST BRANCH CHESTER CREEK, FEMA 100-YR FLOODPLAIN ZONE A, 50' RIPARIAN BUFFER.
UPI 5306-0089-0000 N/F ANTOINETTE S. BRAKMAN DB 3529 PG 1960: GROSS AREA = 221,252.80 SQ FT (5.079 ACRES), NET AREA = 210,253.0 SF (4.827 ACRES).
LOT 1: GROSS LOT AREA (64,665.682 SF) (1.484 ACRES), NET LOT AREA (59,060.162 SF) (1.356 ACRES), EXISTING DWELLING, EXISTING SHED.
LOT 2: GROSS LOT AREA (54,624.745 SF) (1.254 ACRES), NET LOT AREA (54,162.765 SF) (1.243 ACRES).
LOT 3: GROSS LOT AREA (100,219.753 SF) (2.301 ACRES), NET LOT AREA (90,877.001 SF) (2.086 ACRES), EXISTING SHED (TBR).
Adjoiners: UPI 5306B 0054 0000 N/F DANIEL E. CHERRY DB 8962, PG 505; UPI 5306B 0052 0000 N/F WILLIAM E. LEIGH DB 484, PG 105; UPI 5306B 0051 0000 N/F CHRISTINE V. KAPLAN DB 4941, PG 1427; UPI 5306B 0046 0000 N/F JOSEPH P. LYONS DB X-49, PG 85; UPI 5306B 0047 0000 N/F JOHN M. DONOHUE DB 2670, PG 502; UPI 5306 0090 0000 N/F JOSEPH M. & CAROLE A. MATTHEWS DB 6136, PG 953; UPI 5306 0090 0100 N/F CHRISTOPHER N. & DEBORAH FALCONE DB 8774, PG 511; UPI 5306B 0004 0000 N/F ROBERT & SHIRLEY SULLIVAN DB U-61, PG 290; UPI 5306B 0003 0000 N/F DENISE DANIELLE JORDAN DB 9077, PG 2274; UPI 5306 8002 0000 N/F JOSEPH E. ERDELJAC JR DB 2574, PG 272; UPI 5306 8004 0000 N/F JOSEPH E. ERDELJAC JR DB 2574, PG 272; UPI 5306B 0039 0000 N/F DIRK & JAAN L. TROLTENIER DB 6476 PG 1417; UPI 5306B 0038 0000 N/F CHARLES W. & SUE ELLEN HENDRICKSON DB 5067 PG 531.
IMPERVIOUS COVERAGE SUMMARY
| Coverage Category | Lot Area | Building Coverage | Percent Building | Driveway / Future Impervious | Total Impervious Coverage | Percent Impervious |
|---|---|---|---|---|---|---|
| EXISTING IMPERVIOUS COVERAGE | 221,252.8 SF / 5.079 AC | 3,132 SF | 1.42% | 8,673 SF | 11,805 SF | 5.33% |
| PROPOSED IMPERVIOUS COVERAGE (LOT 1) | 59,060.162 SF / 1.356 AC | 2,657 SF | 4.50% | 8,759 SF | 11,416 SF | 19.33% |
| PROPOSED IMPERVIOUS COVERAGE (LOT 2) | 54,162.765 SF / 1.243 AC | 2,341 SF | 4.32% | 5,944 SF / 500 SF | 8,785 SF | 16.22% |
| PROPOSED IMPERVIOUS COVERAGE (LOT 3) | 90,877.001 SF / 2.086 AC | 2,734 SF | 3.01% | 2,082 SF / 500 SF | 5,316 SF | 5.85% |
LEGEND:
- STEEP SLOPES (15% TO 25%)
- STEEP SLOPES (OVER 25%)
- CONCRETE SURFACE
- EXISTING WETLANDS LINE
- STREAM LINE
- FLOOD HAZARD DISTRICT LINE
- EXISTING INTERMEDIATE CONTOUR
- EXISTING INDEX CONTOUR
- EXISTING WOODS / TREE LINE
- ADJOINER LINE
- EXISTING STORM SEWER LINE
- EXISTING RIGHT-OF-WAY LINE
- EXISTING PAVING
- EXISTING SOILS LINE (NoB2 / EC)
- PROPOSED INTERMEDIATE CONTOUR (528)
- PROPOSED INDEX CONTOUR (530)
- PROPOSED SPOT ELEVATION (X 513.4)
- PROPOSED STORM SEWER LINE
- PROPOSED SANITARY SEWER LINE
- PROPOSED WATER LINE
- PROPOSED WOODS / TREE LINE
- SUPER SILT FENCE
- LIMIT OF DISTURBANCE
- NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- STABILIZED RIP-RAP CONSTRUCTION ENTRANCE
PENNSYLVANIA ONE CALL: (800) 242-1776 | UPI No. 5306-0089-0000 | SYSTEM SERIAL NUMBER: 20160320567
SHEET INDEX:
| Sheet Title | Sheet Number |
|---|---|
| TITLE PLAN | SHEET 1 OF 11 |
| CONSTRUCTION IMPROVEMENTS PLAN PLAN | SHEET 2 OF 11 |
| EXISTING CONDITIONS PLAN | SHEET 3 OF 11 |
| PCSM & GRADING PLAN | SHEET 4 OF 11 |
| PCSM NON-STRUCTURAL BMP PLAN | SHEET 5 OF 11 |
| PCSM NOTES & DETAILS SHEET | SHEET 6 OF 11 |
| EROSION & SEDIMENT CONTROL PLAN | SHEET 7 OF 11 |
| E&SC NOTES & DETAILS SHEET | SHEET 8 OF 11 |
| ENTRANCE ROAD PLAN AND PROFILE | SHEET 9 OF 11 |
| SANITARY SEWER PROFILE AND DETAILS | SHEET 10 OF 11 |
| LANDSCAPE PLAN | SHEET 11 OF 11 |
GENERAL NOTES:
1. RECORD OWNER: ANTOINETTE BRAKMAN, 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380, UPI 5306-0089-0000 (TAX #53-6-89), PHONE: (610) 436-0152, DEED REFERENCES: DB. 3529, PG. 1960.
EQUITABLE OWNER: JIM BRANDOLINI, GUNNISON DEVELOPMENT CO., LLC, 1200 BURNING BUSH LANE, WEST CHESTER, PA 19380, PHONE: (610) 640-9174.
2. SITE ADDRESS: 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380
3. TRACT AREA: 221,252.8 SQ. FT / 5.079 ACRES (GROSS); LESS 40' ROAD RIGHT-OF-WAY: 17,152.849 SQ. FT. / 0.394 ACRES; NET TRACT AREA: 4.685 ACRES (NET)
4. BOUNDARY AND PARTIAL TOPOGRAPHY FROM FIELD SURVEY PERFORMED BY COMMONWEALTH ENGINEERS, INC., APRIL 2016. BENCHMARK: NO. 4 REBAR FOUND, NORTHEAST CORNER OF SITE, DATUM: ASSUMED USGS.
5. WETLANDS DELINEATION BY VORTEX ENVIRONMENTAL, INC. AND SURVEYED BY COMMONWEALTH ENGINEERS, INC. IN MAY 2016.
6. SOILS CLASSIFICATIONS FROM THE UNITED STATES DEPARTMENT OF AGRICULTURE (USDA) NATURAL RESOURCE CONSERVATION DISTRICT WEB SOIL SURVEY, IN AUGUST, 2014.
7. UNDERGROUND UTILITIES SHOWN HEREON WERE PLOTTED FROM OBSERVABLE EVIDENCE AT THE TIME OF SURVEY AND THROUGH INFORMATION PROVIDED BY THE UTILITY COMPANIES WHICH SERVICE/OCCUPY THE SITE. THE SITE CONTRACTOR MUST VERIFY LOCATION AND DEPTH OF ALL UNDERGROUND UTILITIES AND FACILITIES PRIOR TO BEGINNING CONSTRUCTION.
8. THE SITE IS SERVED BY PUBLIC WATER (AQUA PA).
9. EXISTING SANITARY SYSTEM PRESENT ON SITE BUT NOT LOCATED.
10. EXISTING IRON PINS ARE SHOWN AS THUS "O".
11. THE DEVELOPER SHALL CONFORM TO OR CAUSE CONFORMANCE WITH ALL OF THE APPLICABLE REQUIREMENTS OF THIS PLAN AND THE EAST GOSHEN TOWNSHIP ZONING ORDINANCE AND SUBDIVISION AND LAND DEVELOPMENT ORDINANCE AS WELL AS OTHER APPLICABLE LOCAL, STATE AND FEDERAL LAWS, STATUTES, REGULATIONS AND ORDINANCES.
12. THE DEVELOPER SHALL NOTIFY UNDERGROUND UTILITY USERS AT LEAST THREE DAYS PRIOR TO THE COMMENCEMENT OF CONSTRUCTION IN ACCORDANCE WITH PA ACT 287 OF 1974, AS AMENDED BY ACT 187 OF 1996.
13. FEMA FLOODPLAIN BOUNDARY TAKEN FROM FLOOD INSURANCE RATE MAP, PANEL 215F, MAP NUMBER 42029C0215F, DATED SEPTEMBER 29, 2006.
14. THIS PROJECT IS LOCATED IN THE WATERSHED OF TRIBUTARY 7 OF EAST BRANCH CHESTER CREEK WHICH HAS THE DESIGNATION OF TROUT STOCK FISHES (TSF, MF) BY THE COMMONWEALTH OF PENNSYLVANIA.
15. THIS PROJECT PROPOSES THE SUBDIVISION OF THE EXISTING LOT INTO 3 SEPARATE LOTS WITH EACH LOT TO BE SERVED BY PUBLIC WATER AND PUBLIC SEWER. PUBLIC SEWER TO BE THROUGH LOW PRESSURE FORCE MAIN TIED INTO AN EXISTING MANHOLE AS SHOWN.
SURVEY REFERENCE NOTES
1. PLAN ENTITLED "BOUNDARY SURVEY PLAN FOR MS. ANTOINETTE BRAKMAN", PREPARED BY R.H. SMITH SURVEYORS, DATED MARCH 27, 2007.
2. PLAN ENTITLED "REVERSE SUBDIVISION/SUBDIVISION PLAN FOR MICHAEL RIZZO", PREPARED BY BRANDYWINE VALLEY ENGINEERS, A DIVISION OF VOLLMER ASSOCIATES, LLP, CONSULTING ENGINEERS AND LAND SURVEYORS, DATED NOVEMBER 30, 2001.
3. PECO BLANKET RIGHT-OF-WAY CONTAINED IN MISCELLANEOUS DB. 81, PG 452.
4. PLAN ENTITLED "THE GAMBONE BROTHERS INC.", PREPARED BY HENRY S. CONREY INC., DIVISION OF CHESTER VALLEY ENGINEERS, DATED JUNE 6, 1973 (LAST REVISED SEPTEMBER 9, 1973).
ZONING: R-2 LOW DENSITY RESIDENTIAL DISTRICT
| Requirement | REQUIRED | EXISTING | PROVIDED LOT 1 | PROVIDED LOT 2 | PROVIDED LOT 3 |
|---|---|---|---|---|---|
| MINIMUM LOT AREA (NET) | 1 ACRE | 4.685 AC | 1.356 AC | 1.243 AC | 2.086 AC |
| MINIMUM LOT WIDTH AT BUILDING SETBACK LINE | 150' | 409' | 170' | 150' | 180' |
| MINIMUM LOT WIDTH AT STREET LINE | 60' | 409' | 170' | 60' | 180' |
| MAXIMUM BUILDING COVERAGE | 25% | 1.42% | 4.50% | 4.32% | 3.01% |
| MAXIMUM TOTAL IMPERVIOUS COVERAGE | 35% | 5.33% | 19.33% | 16.22% | 5.85% |
| MAXIMUM BUILDING HEIGHT (STORIES) | 3 | 2 | 2 | 2 | 2 |
| MAXIMUM BUILDING HEIGHT (FEET) | 35' | 30' | 30' | 30' | 30' |
| MINIMUM FRONT YARD | 45' | 45' | 45' MIN. | 45' MIN. | 45' MIN. |
| AVERAGE FRONT YARD | 60' | 60' | 60' | 60' | 60' |
| MINIMUM SIDE YARD | 20' | 20' | 20' MIN. | 20' MIN. | 20' MIN. |
| MINIMUM REAR YARD | 50' | 50' | 50' MIN. | 50' MIN. | 50' MIN. |
WAIVER REQUESTS:
1. S.A.L.D.O. SECTION 205-31 FINAL PLAN TO BE SUBMITTED AFTER APPROVAL OF A PRELIMINARY PLAN. THE APPLICANT REQUESTS THAT THE PLAN BE SUBMITTED AS A PRELIMINARY/FINAL PLAN.
CERTIFICATIONS & SIGNATURE BLOCKS
COMMONWEALTH OF PENNSYLVANIA, COUNTY OF CHESTER: Equitable Owner acknowledgment block for JIM BRANDOLINI (GUNNISON DEVELOPMENT CO., LLC) and NOTARY PUBLIC.
APPROVED BY THE BOARD OF SUPERVISORS OF EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PENNSYLVANIA (CHAIRMAN, VICE CHAIRMAN, MEMBER).
APPROVED BY PLANNING COMMISSION OF EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PENNSYLVANIA (CHAIRMAN).
APPROVED BY TOWNSHIP ENGINEER OF EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PENNSYLVANIA (TOWNSHIP ENGINEER).
REVIEWED BY THE CHESTER COUNTY PLANNING COMMISSION (CCPC FILE NUMBER, PLANNING COMMISSION SECRETARY).
RECORDED IN THE OFFICE OF THE RECORDER OF DEEDS OF CHESTER COUNTY AT WEST CHESTER, PENNSYLVANIA (DEPUTY RECORDER OF DEEDS).
STATEMENT OF COMPLIANCE: Signed by VICTOR KELLY, JR., PE.
UNDERGROUND UTILITY USERS
- PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA 19312, (610) 648-7702
- AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
- EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
- VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 592-4151
- COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
- WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475
| REV. No. | DATE | DESCRIPTION |
|---|---|---|
| 5 | 1/10/17 | PER CCCD REVIEW LETTER DATED 1/4/17 |
| 4 | 12/19/16 | CHANGES TO SANITARY SEWER DESIGN |
| 3 | 12/12/16 | PER CCCD REVIEW LETTER DATED 12/8/16 |
| 2 | 10/11/16 | PER TWP REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT |
| 1 | 5/23/16 | PER PADEP REVIEW LETTER DATED 5/18/16 |
TITLE PLAN
SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY
EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA
COMMONWEALTH ENGINEERS, INC., 114 EAST LANCASTER AVENUE ~ SECOND FLOOR, DOWNINGTOWN, PA 19335, TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004, COMENG@CEI-1.COM
DATE: MAY 17, 2016 | SCALE: 1"=40' | SURVEY: MBS | DRAWN: TT | CHECKED: VK | DRAWING NO. 201541-(C) | SHEET: 1 OF: 11
Note: some text on this page could not be read reliably. Please see the original PDF for this page.
[Engineering Plan Drawing: Construction Improvements Plan (Sheet 2 of 11) for Brakman Property, showing proposed houses on Lots 2 and 3, rain gardens, driveway and utility easements, proposed water lines and meter pits along East Strasburg Road, and proposed 4" PVC gravity sewer laterals and 1 1/4" LPSS grinder pump connection.]
Plan Callouts:
TIE 6" PVC TO EXISTING MH (SANITARY MANHOLE RIM=384.37, INV.=378.0)
6" PVC TO BE DIRECTIONALLY DRILLED
BORING PIT: TIE PROPOSED WATER LINE TO EXISTING WATER MAIN ALONG EAST STRASBURG RD.
PROPOSED MH TOP=394.0, INV.=386.8
3 METER PITS TO BE PROVIDED FOR EACH SEPARATE WATER LINE
PROPOSED WATER LINE (3 SEPARATE LINES FROM EACH HOUSE TO TIE INTO EXISTING WATER MAIN AS SHOWN)
PULL-OFF AREA
SEWER CONNECTION TO EXISTING SEPTIC SYSTEM TO BE DISCONNECTED. EXISTING SEPTIC SYSTEM TO BE PUMPED OUT, FILLED, AND ABANDONED SUBJECT TO CHESTER COUNTY HEALTH DEPARTMENT APPROVAL.
3 SEPARATE PROPOSED 4" PVC GRAVITY SEWER LATERALS (C.O. TOP=406.5 INV.=403.1; C.O. TOP=406.9 INV.=403.1; C.O. TOP=407.1 INV.=403.1; C.O. TOP=423.8 INV.=419.9; C.O. TOP=423.9 INV.=419.9; C.O. TOP=428.5 INV.=423.1; C.O. TOP=428.6 INV.=423.1; C.O. TOP=429.5 INV.=424.4; C.O. TOP=429.6 INV.=424.4; C.O. TOP=431.6 INV.=426.4; C.O. TOP=431.8 INV.=427.8)
LOT 2: FF=434.0, GF=432.0, BF=424.0 WALKOUT; LOT 2 RAIN GARDEN BOTTOM ELEV.=422.0; 2' WIDE BERM ELEV.=423.5; 15' LONG EMERGENCY SPILLWAY ELEV.=423.0; PROPOSED ELECTRIC LINE
LOT 3: FF=422.0, GF=420.0, BF=412.0 WALKOUT; PROPOSED 1 1/4" LPSS; GRINDER PUMP INV.=411.0; LOT 3 RAIN GARDEN BOTTOM ELEV.=407.0; 2' WIDE BERM ELEV.=409.0; 15' LONG EMERGENCY SPILLWAY ELEV.=408.5
REQUIRED REGULATORY APPROVALS:
1) NPDES PERMIT (PADEP/CCCD) - APPROVAL STATUS: PENDING
2) PLANNING MODULE (PADEP) - STATUS: EXEMPTION APPROVAL LETTER OBTAINED 12/17/16
3) SANITARY SEWER (MUNICIPAL AUTHORITY) - STATUS: SEWER AVAILABILITY LETTER OBTAINED 5/10/16
4) WATER (AQUA) - STATUS: WATER AVAILABILITY LETTER OBTAINED 5/2/16
5) HIGHWAY OCCUPANCY PERMIT (PENNDOT) - APPROVAL STATUS: PENDING
6) FIRE PLANNING (FIRE MARSHALL) - NOT APPLICABLE
7) HISTORIC RESOURCE (HISTORIC COMMITTEE) - NOT APPLICABLE
8) LANDSCAPING (CONSERVANCY BOARD) - PENDING
LEGEND:
- STEEP SLOPES (15% TO 25%)
- STEEP SLOPES (OVER 25%)
- CONCRETE SURFACE
- EXISTING WETLANDS LINE
- STREAM LINE
- FLOOD HAZARD DISTRICT LINE
- EXISTING INTERMEDIATE CONTOUR
- EXISTING INDEX CONTOUR
- EXISTING WOODS / TREE LINE
- ADJOINER LINE
- EXISTING STORM SEWER LINE
- EXISTING RIGHT-OF-WAY LINE
- EXISTING PAVING
- EXISTING SOILS LINE (NoB2 / EC)
- PROPOSED INTERMEDIATE CONTOUR (528)
- PROPOSED INDEX CONTOUR (530)
- PROPOSED SPOT ELEVATION (X 513.4)
- PROPOSED STORM SEWER LINE
- PROPOSED SANITARY SEWER LINE
- PROPOSED WATER LINE
- PROPOSED WOODS / TREE LINE
- SUPER SILT FENCE
- LIMIT OF DISTURBANCE
- NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- STABILIZED RIP-RAP CONSTRUCTION ENTRANCE
PENNSYLVANIA ONE CALL: (800) 242-1776 | UPI No. 5306-0089-0000 | SYSTEM SERIAL NUMBER: 20160320567
GENERAL NOTES:
1. RECORD OWNER: ANTOINETTE BRAKMAN, 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380, UPI 5306-0089-0000 (TAX #53-6-89), PHONE: (610) 436-0152, DEED REFERENCES: DB. 3529, PG. 1960.
EQUITABLE OWNER: JIM BRANDOLINI, GUNNISON DEVELOPMENT CO., LLC, 1200 BURNING BUSH LANE, WEST CHESTER, PA 19380, PHONE: (610) 640-9174.
2. SITE ADDRESS: 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380
3. TRACT AREA: 221,252.8 SQ. FT / 5.079 ACRES (GROSS); LESS 40' ROAD RIGHT-OF-WAY: 17,152.849 SQ. FT. / 0.394 ACRES; NET TRACT AREA: 4.685 ACRES (NET)
4. BOUNDARY AND PARTIAL TOPOGRAPHY FROM FIELD SURVEY PERFORMED BY COMMONWEALTH ENGINEERS, INC., APRIL 2016. BENCHMARK: NO. 4 REBAR FOUND, NORTHEAST CORNER OF SITE, DATUM: ASSUMED USGS.
5. WETLANDS DELINEATION BY VORTEX ENVIRONMENTAL, INC. AND SURVEYED BY COMMONWEALTH ENGINEERS, INC. IN MAY 2016.
6. SOILS CLASSIFICATIONS FROM THE UNITED STATES DEPARTMENT OF AGRICULTURE (USDA) NATURAL RESOURCE CONSERVATION DISTRICT WEB SOIL SURVEY, IN AUGUST, 2014.
7. UNDERGROUND UTILITIES SHOWN HEREON WERE PLOTTED FROM OBSERVABLE EVIDENCE AT THE TIME OF SURVEY AND THROUGH INFORMATION PROVIDED BY THE UTILITY COMPANIES WHICH SERVICE/OCCUPY THE SITE. THE SITE CONTRACTOR MUST VERIFY LOCATION AND DEPTH OF ALL UNDERGROUND UTILITIES AND FACILITIES PRIOR TO BEGINNING CONSTRUCTION.
8. THE SITE IS SERVED BY PUBLIC WATER (AQUA PA).
9. EXISTING SANITARY SYSTEM PRESENT ON SITE BUT NOT LOCATED.
10. EXISTING IRON PINS ARE SHOWN AS THUS "O".
11. THE DEVELOPER SHALL CONFORM TO OR CAUSE CONFORMANCE WITH ALL OF THE APPLICABLE REQUIREMENTS OF THIS PLAN AND THE EAST GOSHEN TOWNSHIP ZONING ORDINANCE AND SUBDIVISION AND LAND DEVELOPMENT ORDINANCE AS WELL AS OTHER APPLICABLE LOCAL, STATE AND FEDERAL LAWS, STATUTES, REGULATIONS AND ORDINANCES.
12. THE DEVELOPER SHALL NOTIFY UNDERGROUND UTILITY USERS AT LEAST THREE DAYS PRIOR TO THE COMMENCEMENT OF CONSTRUCTION IN ACCORDANCE WITH PA ACT 287 OF 1974, AS AMENDED BY ACT 187 OF 1996.
13. FEMA FLOODPLAIN BOUNDARY TAKEN FROM FLOOD INSURANCE RATE MAP, PANEL 215F, MAP NUMBER 42029C0215F, DATED SEPTEMBER 29, 2006.
14. THIS PROJECT IS LOCATED IN THE WATERSHED OF TRIBUTARY 7 OF EAST BRANCH CHESTER CREEK WHICH HAS THE DESIGNATION OF TROUT STOCK FISHES (TSF, MF) BY THE COMMONWEALTH OF PENNSYLVANIA.
15. THIS PROJECT PROPOSES THE SUBDIVISION OF THE EXISTING LOT INTO 3 SEPARATE LOTS WITH EACH LOT TO BE SERVED BY PUBLIC WATER AND PUBLIC SEWER. PUBLIC SEWER TO BE THROUGH LOW PRESSURE FORCE MAIN TIED INTO AN EXISTING MANHOLE AS SHOWN.
SURVEY REFERENCE NOTES
1. PLAN ENTITLED "BOUNDARY SURVEY PLAN FOR MS. ANTOINETTE BRAKMAN", PREPARED BY R.H. SMITH SURVEYORS, DATED MARCH 27, 2007.
2. PLAN ENTITLED "REVERSE SUBDIVISION/SUBDIVISION PLAN FOR MICHAEL RIZZO", PREPARED BY BRANDYWINE VALLEY ENGINEERS, A DIVISION OF VOLLMER ASSOCIATES, LLP, CONSULTING ENGINEERS AND LAND SURVEYORS, DATED NOVEMBER 30, 2001.
3. PECO BLANKET RIGHT-OF-WAY CONTAINED IN MISCELLANEOUS DB. 81, PG 452.
4. PLAN ENTITLED "THE GAMBONE BROTHERS INC.", PREPARED BY HENRY S. CONREY INC., DIVISION OF CHESTER VALLEY ENGINEERS, DATED JUNE 6, 1973 (LAST REVISED SEPTEMBER 9, 1973).
ZONING: R-2 LOW DENSITY RESIDENTIAL DISTRICT
| Requirement | REQUIRED | EXISTING | PROVIDED LOT 1 | PROVIDED LOT 2 | PROVIDED LOT 3 |
|---|---|---|---|---|---|
| MINIMUM LOT AREA (NET) | 1 ACRE | 4.685 AC | 1.356 AC | 1.243 AC | 2.086 AC |
| MINIMUM LOT WIDTH AT BUILDING SETBACK LINE | 150' | 409' | 170' | 150' | 180' |
| MINIMUM LOT WIDTH AT STREET LINE | 60' | 409' | 170' | 60' | 180' |
| MAXIMUM BUILDING COVERAGE | 25% | 1.42% | 4.50% | 4.32% | 3.01% |
| MAXIMUM TOTAL IMPERVIOUS COVERAGE | 35% | 5.33% | 19.33% | 16.22% | 5.85% |
| MAXIMUM BUILDING HEIGHT (STORIES) | 3 | 2 | 2 | 2 | 2 |
| MAXIMUM BUILDING HEIGHT (FEET) | 35' | 30' | 30' | 30' | 30' |
| MINIMUM FRONT YARD | 45' | 45' | 45' MIN. | 45' MIN. | 45' MIN. |
| AVERAGE FRONT YARD | 60' | 60' | 60' | 60' | 60' |
| MINIMUM SIDE YARD | 20' | 20' | 20' MIN. | 20' MIN. | 20' MIN. |
| MINIMUM REAR YARD | 50' | 50' | 50' MIN. | 50' MIN. | 50' MIN. |
UNDERGROUND UTILITY USERS
- PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA 19312, (610) 648-7702
- AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
- EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
- VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 592-4151
- COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
- WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475
| REV. No. | DATE | DESCRIPTION |
|---|---|---|
| 5 | 1/10/17 | PER CCCD REVIEW LETTER DATED 1/4/17 |
| 4 | 12/19/16 | CHANGES TO SANITARY SEWER DESIGN |
| 3 | 12/12/16 | PER CCCD REVIEW LETTER DATED 12/8/16 |
| 2 | 10/11/16 | PER TWP REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT |
| 1 | 5/23/16 | PER PADEP REVIEW LETTER DATED 5/18/16 |
CONSTRUCTION IMPROVEMENTS PLAN
SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY
EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA
COMMONWEALTH ENGINEERS, INC., 114 EAST LANCASTER AVENUE ~ SECOND FLOOR, DOWNINGTOWN, PA 19335, TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004, COMENG@CEI-1.COM
DATE: MAY 17, 2016 | SCALE: 1"=40' | SURVEY: MBS | DRAWN: TT | CHECKED: VK | DRAWING NO. 201541-(C) | SHEET: 2 OF: 11
[Engineering Plan Drawing: Existing Conditions Plan (Sheet 3 of 11) for Brakman Property, showing existing topography, contours, existing dwelling and sheds, trees to be removed (TBR), wetlands, floodplain, and 50' riparian buffer.]
Plan Callouts:
IMPERVIOUS AREA TO BE PERMANENTLY REMOVED AND REPLACED WITH NEW IMPERVIOUS AREA (TOTAL AREA=726 SQ. FT)
IMPERVIOUS AREA TO BE PERMANENTLY REMOVED AND REPLACED WITH LAWN COVER (TOTAL AREA=2050 SQ. FT)
GROSS AREA = 221,252.80 SQ FT (5.079 ACRES); NET AREA = 210,253.0 SF (4.827 ACRES)
EXISTING DWELLING, EXISTING SHED, EXISTING SHED (TBR), APPROXIMATE LOCATION OF EXISTING SEPTIC SYSTEM
LEGEND:
- STEEP SLOPES (15% TO 25%)
- STEEP SLOPES (OVER 25%)
- CONCRETE SURFACE
- EXISTING WETLANDS LINE
- STREAM LINE
- FLOOD HAZARD DISTRICT LINE
- EXISTING INTERMEDIATE CONTOUR
- EXISTING INDEX CONTOUR
- EXISTING WOODS / TREE LINE
- ADJOINER LINE
- EXISTING STORM SEWER LINE
- EXISTING RIGHT-OF-WAY LINE
- EXISTING PAVING
- EXISTING SOILS LINE (NoB2 / EC)
- PROPOSED INTERMEDIATE CONTOUR (528)
- PROPOSED INDEX CONTOUR (530)
- PROPOSED SPOT ELEVATION (X 513.4)
- PROPOSED STORM SEWER LINE
- PROPOSED SANITARY SEWER LINE
- PROPOSED WATER LINE
- PROPOSED WOODS / TREE LINE
- SUPER SILT FENCE
- LIMIT OF DISTURBANCE
- NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- STABILIZED RIP-RAP CONSTRUCTION ENTRANCE
PENNSYLVANIA ONE CALL: (800) 242-1776 | UPI No. 5306-0089-0000 | SYSTEM SERIAL NUMBER: 20160320567
UNDERGROUND UTILITY USERS
- PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA 19312, (610) 648-7702
- AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
- EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
- VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 592-4151
- COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
- WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475
| REV. No. | DATE | DESCRIPTION |
|---|---|---|
| 5 | 1/10/17 | PER CCCD REVIEW LETTER DATED 1/4/17 |
| 4 | 12/19/16 | CHANGES TO SANITARY SEWER DESIGN |
| 3 | 12/12/16 | PER CCCD REVIEW LETTER DATED 12/8/16 |
| 2 | 10/11/16 | PER TWP REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT |
| 1 | 5/23/16 | PER PADEP REVIEW LETTER DATED 5/18/16 |
EXISTING CONDITIONS PLAN
SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY
EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA
COMMONWEALTH ENGINEERS, INC., 114 EAST LANCASTER AVENUE ~ SECOND FLOOR, DOWNINGTOWN, PA 19335, TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004, COMENG@CEI-1.COM
DATE: MAY 17, 2016 | SCALE: 1"=40' | SURVEY: MBS | DRAWN: TT | CHECKED: VK | DRAWING NO. 201541-(C) | SHEET: 3 OF: 11
[Engineering Plan Drawing: PCSM & Grading Plan (Sheet 4 of 11) for Brakman Property, showing proposed grading contours, NPDES boundary, limit of disturbance (66,038 SQ. FT. = 1.52 ACRES), Lot 2 and Lot 3 rain gardens and drainage areas, level spreaders, grass swale, and utility connections.]
Plan Callouts:
NPDES BOUNDARY; LIMIT OF DISTURBANCE = 66,038 SQ. FT. = 1.52 ACRES; LINE OF INTEREST #1; LINE OF INTEREST #2
CONSTRUCT RAILROAD TIE RETAINING WALL AROUND EXISTING UTILITY POLE
7'x7' RIPRAP PAD, R-3 STONE, DEPTH=9"
PROPOSED GRASS SWALE (TRAPEZOIDAL), 2:1 SIDE SLOPES, 1' BOTTOM WIDTH, DEPTH=1.5', SLOPE=10.3% (LINED WITH NAG S150 OR EQUAL)
LOT 3 RAIN GARDEN DRAINAGE AREA; 24 L.F. 8" PVC @ 2.1% SLOPE; 8" PVC ELBOW/RISER W/ DRAINAGE GRATE TG=408.0, INV.=406.0; 10' LONG x 3' WIDE LEVEL SPREADER TOP=408.0, 8" PIPE (FULLY PERF.) INV.=405.5, BOTTOM=405.0; ROOF DRAIN COLLECTION PIPING SYSTEM (FOR ROOF DRAINS ON SOUTH SIDE OF HOUSE) TO TIE INTO RAIN GARDEN AS SHOWN (GUTTER GUARDS REQUIRED ON ROOF DRAINS TIED TO THIS SYSTEM)
LOT 2 RAIN GARDEN DRAINAGE AREA; 8" PVC ELBOW/RISER W/ DRAINAGE GRATE TG=422.5, INV.=420.5; 15' LONG x 3' WIDE LEVEL SPREADER TOP=421.5, 8" PIPE (FULLY PERF.) INV.=420.0, BOTTOM=419.5; 16 L.F. 8" PVC @ 3.1% SLOPE
SOIL IDENTIFICATION:
| SYMBOL | DESCRIPTION | HYDROLOGIC GROUP | DEPTH TO WATER | DEPTH TO BEDROCK |
|---|---|---|---|---|
| UrB | URBAN LAND-GLADSTONE COMPLEX, 0 TO 8 PERCENT SLOPES | A | >80" | 60"-100" |
| UrD | URBAN LAND-GLADSTONE COMPLEX, 0 TO 8 PERCENT SLOPES | A | >80" | 60"-100" |
SOIL USE LIMITATIONS & RESOLUTIONS:
ONLY THOSE LIMITATIONS TO ON-SITE SOILS AS DESCRIBED BY APPENDIX E OF THE 2012 EROSION CONTROL MANUAL ARE ADDRESSED BELOW.
| USE LIMITATION | PROPOSED RESOLUTION(S) |
|---|---|
| 1. CUTBANKS CAVE (UrB,UrD) | ALL APPLICABLE OSHA STANDARDS AND REGULATIONS WILL BE IMPLEMENTED. |
| 2. CORROSIVENESS TO CONCRETE AND/OR STEEL (UrB,UrD) | CHEMICAL PRE-TREATMENT OF ANY CONCRETE ENDWALLS TO PROVIDE ANTI-CORROSIVE PROPERTIES. |
| 3. EASILY ERODIBLE (UrB,UrD) | EROSION CONTROL MATTING IS PROPOSED AS APPROPRIATE. |
| 4. HYDRIC SOILS/INCLUSIONS (UrB,UrD) | LIMITED DISTURBANCE IN ANY POTENTIAL HYDRIC AREAS. |
| 5. SLOW PERCOLATION (UrB,UrD) | ON-SITE TESTING WAS PERFORMED TO ENSURE ADEQUATE PERCOLATION FOR BMP FACILITIES. |
| 6. FROST ACTION (UrB,UrD) | FROST ACTION IS NOT EXPECTED TO AFFECT PROPOSED FACILITIES. |
| 7. SHRINK/SWELL (UrB,UrD) | SHRINK/SWELL IS NOT EXPECTED TO AFFECT PROPOSED FACILITIES. |
FINAL CERTIFICATION REQUIREMENTS, NOTICE OF TERMINATION, SITE GEOLOGY & WASTE DISPOSAL
FINAL CERTIFICATION REQUIREMENTS: Record Drawings certification statement from a licensed professional under 18 Pa. C.S.A. Section 4904 and 25 Pa. Code Chapter 102.
NOTICE OF TERMINATION REQUIREMENTS: Submission of Notice of Termination to the Conservation District under 25 Pa. Code 102.22(a)(2), 102.4, and 102.8.
SITE GEOLOGY: THE ENTIRE SITE IS UNDERLAIN BY FELSIC GNEISS PER THE PADEP EMAPPA WEBSITE.
CONSTRUCTION WASTE DISPOSAL NOTE: Removal, recycling, or disposal of building materials and waste products in accordance with 25 PA Code 260.1 et seq., 271.1 et seq. and 287.1 et seq.
OFFER OF BLANKET EASEMENT: Blanket stormwater management easement in favor of East Goshen Township.
PCSM PLAN REVISIONS: Signed by (JIM BRANDOLINI) (DATE).
PCSM PLAN CERTIFICATION: Signed by (VICTOR KELLY, JR., PE) (DATE) certifying compliance with East Goshen Township Stormwater Management Ordinance (Chapter 195).
LEGEND:
- STEEP SLOPES (15% TO 25%)
- STEEP SLOPES (OVER 25%)
- CONCRETE SURFACE
- EXISTING WETLANDS LINE
- STREAM LINE
- FLOOD HAZARD DISTRICT LINE
- EXISTING INTERMEDIATE CONTOUR
- EXISTING INDEX CONTOUR
- EXISTING WOODS / TREE LINE
- ADJOINER LINE
- EXISTING STORM SEWER LINE
- EXISTING RIGHT-OF-WAY LINE
- EXISTING PAVING
- EXISTING SOILS LINE (NoB2 / EC)
- PROPOSED INTERMEDIATE CONTOUR (528)
- PROPOSED INDEX CONTOUR (530)
- PROPOSED SPOT ELEVATION (X 513.4)
- PROPOSED STORM SEWER LINE
- PROPOSED SANITARY SEWER LINE
- PROPOSED WATER LINE
- PROPOSED WOODS / TREE LINE
- SUPER SILT FENCE
- LIMIT OF DISTURBANCE
- NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- STABILIZED RIP-RAP CONSTRUCTION ENTRANCE
PENNSYLVANIA ONE CALL: (800) 242-1776 | UPI No. 5306-0089-0000 | SYSTEM SERIAL NUMBER: 20160320567
GENERAL NOTES:
1. RECORD OWNER: ANTOINETTE BRAKMAN, 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380, UPI 5306-0089-0000 (TAX #53-6-89), PHONE: (610) 436-0152, DEED REFERENCES: DB. 3529, PG. 1960.
EQUITABLE OWNER: JIM BRANDOLINI, GUNNISON DEVELOPMENT CO., LLC, 1200 BURNING BUSH LANE, WEST CHESTER, PA 19380, PHONE: (610) 640-9174.
2. SITE ADDRESS: 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380
3. TRACT AREA: 221,252.8 SQ. FT / 5.079 ACRES (GROSS); LESS 40' ROAD RIGHT-OF-WAY: 17,152.849 SQ. FT. / 0.394 ACRES; NET TRACT AREA: 4.685 ACRES (NET)
4. BOUNDARY AND PARTIAL TOPOGRAPHY FROM FIELD SURVEY PERFORMED BY COMMONWEALTH ENGINEERS, INC., APRIL 2016. BENCHMARK: NO. 4 REBAR FOUND, NORTHEAST CORNER OF SITE, DATUM: ASSUMED USGS.
5. WETLANDS DELINEATION BY VORTEX ENVIRONMENTAL, INC. AND SURVEYED BY COMMONWEALTH ENGINEERS, INC. IN MAY 2016.
6. SOILS CLASSIFICATIONS FROM THE UNITED STATES DEPARTMENT OF AGRICULTURE (USDA) NATURAL RESOURCE CONSERVATION DISTRICT WEB SOIL SURVEY, IN AUGUST, 2014.
7. UNDERGROUND UTILITIES SHOWN HEREON WERE PLOTTED FROM OBSERVABLE EVIDENCE AT THE TIME OF SURVEY AND THROUGH INFORMATION PROVIDED BY THE UTILITY COMPANIES WHICH SERVICE/OCCUPY THE SITE. THE SITE CONTRACTOR MUST VERIFY LOCATION AND DEPTH OF ALL UNDERGROUND UTILITIES AND FACILITIES PRIOR TO BEGINNING CONSTRUCTION.
8. THE SITE IS SERVED BY PUBLIC WATER (AQUA PA).
9. EXISTING SANITARY SYSTEM PRESENT ON SITE BUT NOT LOCATED.
10. EXISTING IRON PINS ARE SHOWN AS THUS "O".
11. THE DEVELOPER SHALL CONFORM TO OR CAUSE CONFORMANCE WITH ALL OF THE APPLICABLE REQUIREMENTS OF THIS PLAN AND THE EAST GOSHEN TOWNSHIP ZONING ORDINANCE AND SUBDIVISION AND LAND DEVELOPMENT ORDINANCE AS WELL AS OTHER APPLICABLE LOCAL, STATE AND FEDERAL LAWS, STATUTES, REGULATIONS AND ORDINANCES.
12. THE DEVELOPER SHALL NOTIFY UNDERGROUND UTILITY USERS AT LEAST THREE DAYS PRIOR TO THE COMMENCEMENT OF CONSTRUCTION IN ACCORDANCE WITH PA ACT 287 OF 1974, AS AMENDED BY ACT 187 OF 1996.
13. FEMA FLOODPLAIN BOUNDARY TAKEN FROM FLOOD INSURANCE RATE MAP, PANEL 215F, MAP NUMBER 42029C0215F, DATED SEPTEMBER 29, 2006.
14. THIS PROJECT IS LOCATED IN THE WATERSHED OF TRIBUTARY 7 OF EAST BRANCH CHESTER CREEK WHICH HAS THE DESIGNATION OF TROUT STOCK FISHES (TSF, MF) BY THE COMMONWEALTH OF PENNSYLVANIA.
15. THIS PROJECT PROPOSES THE SUBDIVISION OF THE EXISTING LOT INTO 3 SEPARATE LOTS WITH EACH LOT TO BE SERVED BY PUBLIC WATER AND PUBLIC SEWER. PUBLIC SEWER TO BE THROUGH LOW PRESSURE FORCE MAIN TIED INTO AN EXISTING MANHOLE AS SHOWN.
SURVEY REFERENCE NOTES
1. PLAN ENTITLED "BOUNDARY SURVEY PLAN FOR MS. ANTOINETTE BRAKMAN", PREPARED BY R.H. SMITH SURVEYORS, DATED MARCH 27, 2007.
2. PLAN ENTITLED "REVERSE SUBDIVISION/SUBDIVISION PLAN FOR MICHAEL RIZZO", PREPARED BY BRANDYWINE VALLEY ENGINEERS, A DIVISION OF VOLLMER ASSOCIATES, LLP, CONSULTING ENGINEERS AND LAND SURVEYORS, DATED NOVEMBER 30, 2001.
3. PECO BLANKET RIGHT-OF-WAY CONTAINED IN MISCELLANEOUS DB. 81, PG 452.
4. PLAN ENTITLED "THE GAMBONE BROTHERS INC.", PREPARED BY HENRY S. CONREY INC., DIVISION OF CHESTER VALLEY ENGINEERS, DATED JUNE 6, 1973 (LAST REVISED SEPTEMBER 9, 1973).
STORMWATER TEST PIT INFORMATION:
INFILTRATION TESTING PERFORMED WITH A DOUBLE-RING INFILTROMETER
| TEST PIT ID | INFILTRATION RATE | TESTING DEPTH | TESTING ELEVATION | LIMITING ZONE DEPTH | LIMITING ZONE DESCRIPTION |
|---|---|---|---|---|---|
| LOT 2 | 2.50 IN/HR | 36" | 420.3 | 61" | ROCK ENCOUNTERED |
| LOT 3 | 2.25 IN/HR | 24" | 406.6 | 48" | ROCK ENCOUNTERED |
RECEIVING WATERSHED NOTICE:
THIS PROJECT IS WHOLLY LOCATED WITHIN THE WATERSHED OF TRIBUTARY 7 OF EAST CHESTER CREEK, A WATERSHED DESIGNATED TROUT STOCK FISHERY, MIGRATORY FISHERY (TSF, MF) BY THE COMMONWEALTH OF PENNSYLVANIA.
UNDERGROUND UTILITY USERS
- PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA 19312, (610) 648-7702
- AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
- EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
- VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 592-4151
- COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
- WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475
| REV. No. | DATE | DESCRIPTION |
|---|---|---|
| 5 | 1/10/17 | PER CCCD REVIEW LETTER DATED 1/4/17 |
| 4 | 12/19/16 | CHANGES TO SANITARY SEWER DESIGN |
| 3 | 12/12/16 | PER CCCD REVIEW LETTER DATED 12/8/16 |
| 2 | 10/11/16 | PER TWP REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT |
| 1 | 5/23/16 | PER PADEP REVIEW LETTER DATED 5/18/16 |
PCSM & GRADING PLAN
SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY
EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA
COMMONWEALTH ENGINEERS, INC., 114 EAST LANCASTER AVENUE ~ SECOND FLOOR, DOWNINGTOWN, PA 19335, TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004, COMENG@CEI-1.COM
DATE: MAY 17, 2016 | SCALE: 1"=40' | SURVEY: MBS | DRAWN: TT | CHECKED: VK | DRAWING NO. 201541-(C) | SHEET: 4 OF: 11
Note: some text on this page could not be read reliably. Please see the original PDF for this page.
PCSM NON-STRUCTURAL BMP PLAN
SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY
East Goshen Township, Chester County, PA. Commonwealth Engineers, Inc., 114 East Lancaster Avenue ~ Second Floor, Downingtown, PA 19335, Telephone: (610) 518-9003 ~ Fax: (610) 518-9004, comeng@cei-1.com. Date: May 17, 2016. Scale: 1"=40'. Survey: MBS. Drawn: TT. Checked: VK. Drawing No. 201541-(C). Sheet 5 of 11.
[Site plan drawing with hatched protected areas, NPDES boundary, Brook Drive and East Strasburg Road, Lot 2 and Lot 3, pull-off area, FEMA 100-yr floodplain Zone A, Tributary 7 of East Branch Chester Creek, location map (scale 1"=2000'), graphic scale 1"=40'.]
- Area of protected sensitive/special value features = 117,634 sq. ft. = 2.70 acres
- Area of minimized total disturbed area = 38,507 sq. ft. = 0.88 acres
- Limit of disturbance = 66,038 sq. ft. = 1.52 acres
- Area of disconnection from storm sewers = 2,971 sq. ft.
- Line of Interest #1
- Line of Interest #2
SITE STABILIZATION STANDARDS
Upon completion or temporary cessation of the earth disturbance activity that will exceed 4 days, or any stage thereof, the project site shall be immediately stabilized with the appropriate temporary or permanent stabilization. During non-germinating periods hay or straw mulch must be applied at the rate of three (3) tons per acre. (Remaining small print of this block is too small to transcribe reliably.)
FINAL SITE STABILIZATION REQUIREMENTS
An area shall be considered to have achieved final stabilization when it has a minimum uniform 70% perennial vegetative cover with a density sufficient to resist accelerated erosion and subsurface characteristics sufficient to resist sliding and other movements. (Remaining small print not reliably legible.)
GEOLOGIC OR SOIL CONDITIONS POLLUTION
There are no known naturally occurring geologic or soils conditions on this site that may have the potential to cause pollution during construction or after earth disturbance activities are completed and PCSM BMPs are operational. Should such conditions be detected, the owner shall contact the plan engineer and the Chester County Conservation District to discuss remedial actions.
GEOTEXTILE STABILIZATION REQUIREMENTS
All disturbed slopes steeper than 3:1 (33%) shall be immediately stabilized with an approved erosion control geotextile fabric (North American Green C125 or an approved equivalent), permanent seeding, and lime as prescribed.
TEMPORARY SITE STABILIZATION REQUIREMENTS
Upon completion or temporary cessation of the earth disturbance activity that will exceed four (4) days, the project site shall be immediately stabilized with the appropriate temporary or permanent stabilization. Hay or straw mulch shall be applied at 3.0 tons per acre. (Remaining small print not reliably legible.)
UNFORESEEN EROSION CONDITIONS
- Should any unforeseen erosive conditions develop during construction, the contractor shall take the action to remedy such conditions and to prevent damage to adjacent properties. Stockpiles of wood chips, hay bales, crushed stone, and other acceptable mulches shall be held in readiness to immediately address emergency erosion and sedimentation problems.
- The contractor is advised to become thoroughly familiar with all of the provisions of Appendix 64, Erosion Control Rules and Regulations, Title 25, Part 1, Department of Environmental Protection, Sub-Part C, Protection of Natural Resources, Article II, Water Resources, Chapter 102, Erosion Control.
- Construction operations shall be carried out in such a manner that all erosion and air pollution is minimized; state and local law concerning pollution abatement shall be observed.
- Measures for the protection of existing trees and shrubs shall be taken by the contractor to eliminate unnecessary damage.
A copy of these erosion and sedimentation pollution control plans must be posted and available at the construction site in accordance with state and federal law.
POST CONSTRUCTION STORMWATER BMPS
Post construction stormwater BMPs are permanent facilities that cannot be removed or altered without approval of the Township.
POST-CONSTRUCTION STORMWATER MANAGEMENT DESIGN
This site will utilize two (2) primary stormwater management facilities to control the post-development peak rates of stormwater runoff and stormwater volume for the site in accordance with PADEP BMP guidelines. The stormwater management facilities shall be constructed and maintained to the specifications described in the plans and will accomplish the following:
- Preserve the integrity of stream channels and protect the physical, biological and chemical qualities of the receiving stream through reduction of post-development peak rates and volumes of stormwater runoff and the mitigation of thermal impacts.
- Prevent the increase in stormwater runoff through retention of intercepted overland runoff.
- Capture and remove the increase in stormwater runoff volume through the proposed rain garden facilities that will provide infiltration and evapotranspiration of the increase in stormwater runoff volume from pre-development to post-development conditions for the 2-year storm event.
In addition, the following non-structural practices are promoted to reduce the structural post-construction stormwater management requirements: minimize impervious areas by proposing only the minimum impervious cover necessary for the viability of the proposed use; maximize protection of existing drainage features and vegetation by discharging each rain garden through an energy dissipating device; minimize land clearing and grading by strictly delineating limits of proposed earth disturbance; minimize soil compaction by strictly delineating limits of proposed earth disturbance; utilize other structural and non-structural BMPs via infiltration, vegetative filtration, detention and restricted release of overland runoff, and protection of existing drainage features and vegetation.
RECEIVING WATERSHED NOTICE
This project is wholly located within the watershed of Tributary 7 of East Chester Creek, a watershed designated trout stock fishery; migratory fishery (TSF; MF) by the Commonwealth of Pennsylvania.
INFILTRATION FACILITY PROTECTION NOTICE
All proposed underground stormwater infiltration facilities proposed with these plans must be protected during construction from soil compaction and sediment contamination at all times. (Remaining small print not reliably legible.)
INFILTRATION FACILITY FAILURE NOTICE
Stormwater infiltration BMP failure is defined as the BMP no longer providing the benefit or performance it was intended to provide. (Remaining small print not reliably legible, including the reference to standing water longer than 3 days and contacting the Township.)
LEGEND
- Steep slopes (15% to 25%)
- Steep slopes (over 25%)
- Concrete surface
- Existing wetlands line
- Stream line
- Flood hazard district line
- Existing intermediate contour
- Existing index contour
- Existing woods / tree line
- Adjoiner line
- Existing storm sewer line
- Existing right-of-way line
- Existing paving
- Existing soils line
- Proposed intermediate contour
- Proposed index contour
- Proposed spot elevation
- Proposed storm sewer line
- Proposed sanitary sewer line
- Proposed water line
- Proposed woods / tree line
- Super silt fence
- Limit of disturbance
- North American Green S150 temporary geotextile blanket (or approved equal)
- North American Green SC250 permanent geotextile blanket (or approved equal)
- Stabilized rip-rap construction entrance
PENNSYLVANIA ONE CALL
Pennsylvania One Call System serial number 20160320567. UPI No. 5306-0089-0000.
UNDERGROUND UTILITY USERS
- Philadelphia Electric Company, 1050 Swedesford Road, Berwyn, PA 19312, (610) 648-7702
- Aqua PA, 762 W. Lancaster Ave., Bryn Mawr, PA 19010, (877) 987-2782
- East Goshen Township, 1580 Paoli Pike, West Chester, PA 19380, (610) 692-7171
- Verizon Pennsylvania Inc., 900 Race Street, 6th Floor, Philadelphia, PA 19107, (215) 592-4151
- Comcast, Rt. 82 and Monacy Rd., P.O. Box 351, Coatesville, PA 19320, (800) 934-6489
- Williams (Transco Gas), 2800 Post Oak Boulevard, Houston, TX 77056, (800) 440-8475
| Rev. No. | Date | Description |
|---|---|---|
| 5 | 1/10/17 | Per CCCD review letter dated 1/4/17 |
| 4 | 12/19/16 | Changes to sanitary sewer design |
| 3 | 12/12/16 | Per CCCD review letter dated 12/8/16 |
| 2 | 10/11/16 | Per Twp review letter dated 6/1/16 and revised layout |
| 1 | 5/23/16 | Per PADEP review letter dated 5/18/16 |
6 COMMONWEALTH ENGINEERS, INC.
1) The project site is currently a combination of woods, meadow, and lawn with one existing dwelling and two existing sheds. There is also an existing septic system on the site. Stormwater runoff drains off the site from east to west into Tributary 7 of East Branch Chester Creek (TSF, MF). 2) This site achieves the requirements of East Goshen Township Stormwater Management Ordinance Section 195-18 by controlling stormwater runoff to pre-development conditions. These requirements are displayed throughout the PCSM Plans, E&SPC Plans, and the corresponding reports. 3) This site achieves the requirements of East Goshen Township Stormwater Management Ordinance Sections 195-15 through 195-25 through the use of a variety of stormwater BMP's (rain gardens) and conveyance systems (swales) to control stormwater runoff to pre-development conditions while complying with the design standards stated in the above stormwater management ordinance sections. 4) This project proposes the construction of 2 new dwellings and new paved driveway areas. Stormwater runoff from the new buildings will be directed to individual on-lot rain gardens through overland flow or roof drain collection piping systems. These rain gardens will retain and infiltrate runoff for the various design storms. Erosion and sediment control will be achieved primarily through the use of silt fences. 5) The project proposes no adverse effects on adjacent or downstream properties or conveyance systems since the project proposed the use of stormwater BMP's that will control stormwater runoff to pre-development conditions for various design storm events and that will retain runoff volume onsite for the 2-year storm. 6) The project implements water quality BMP's in the form of conserving of riparian buffers and minimizing of total disturbed areas. 7) Construction of this project is anticipated to begin the winter of 2017 and end the summer of 2017. 8) This project will be constructed as a single phase.
[Engineering Plan Drawing: Erosion & Sediment Control Plan (Sheet 7 of 11) for Brakman Property, showing super silt fences (SSF #01 through SSF #08), rock construction entrances, topsoil stockpiles, compost sock concrete washout station, orange construction fence, rock filter, proposed grass swale, and NAG S150 lining.]
Plan Callouts:
ROCK CONSTRUCTION ENTRANCE; TOPSOIL STOCKPILE; COMPOST SOCK CONCRETE WASHOUT STATION
SUPER SILT FENCE (SSF #01, SSF #02, SSF #03, SSF #04, SSF #05, SSF #06, SSF #07, SSF #08)
ROCK FILTER; NAG S150 LINING (OR APPROVED EQUAL); ORANGE CONSTRUCTION FENCE
PROPOSED GRASS SWALE (TRAPEZOIDAL), 2:1 SIDE SLOPES, 1' BOTTOM WIDTH, DEPTH=1.5', SLOPE=10.3% (LINED WITH NAG S150 OR EQUAL)
LIMIT OF DISTURBANCE = 66,038 SQ. FT. = 1.52 ACRES
CONSTRUCTION OVERSIGHT, EROSION CONTROL & CERTIFICATION NOTES
CONSTRUCTION OVERSIGHT REQUIREMENTS: Engineering construction oversight for proposed stormwater BMPs; additional soil testing prior to installation of infiltration BMPs.
CONSTRUCTION WASTE DISPOSAL NOTE: Removal, recycling, or disposal of building materials and waste products in accordance with 25 PA Code 260.1, 271.1, and 287.1.
EROSION CONTROL PLAN REVISION NOTICE: Chester County Conservation District approval required prior to revisions.
SEDIMENT TRACKING NOTICE: Sediment tracked onto any roadway or sidewalk shall be returned to the construction site by the end of each workday.
NOTICE OF TERMINATION REQUIREMENTS & FINAL CERTIFICATION REQUIREMENTS: Notice of Termination and Record Drawings certification under 25 Pa. Code Chapter 102 and 18 Pa. C.S.A. Section 4904.
OVERALL SEQUENCE OF CONSTRUCTION:
Pre-construction meeting at least 7 days before earthmoving begins. Protect infiltration facilities and rain gardens from sediment-laden runoff. Immediate stabilization upon cessation of earth disturbance exceeding 4 days.
1. CLEARLY DELINEATE ALL PROPOSED DISTURBANCE LIMITS AND TREES TO BE PROTECTED.
2. INSTALL THE STABILIZED ROCK CONSTRUCTION ENTRANCES.
3. INSTALL SUPER SILT FENCES AS SHOWN ON EROSION & SEDIMENT CONTROL PLAN.
4. INSTALL COMPOST SOCK CONCRETE WASHOUT STATION.
5. BEGIN CLEARING AND GRUBBING OF AREAS FOR THE PROPOSED BUILDINGS AND DRIVEWAY AREAS.
6. REMOVE THE EXISTING SHED AS NOTED ON THE PLANS.
7. PERFORM GRADING OPERATIONS FOR DRIVEWAY AREAS AND AROUND PROPOSED BUILDINGS. INSTALL EROSION CONTROL LINING ON NEWLY GRADED AREAS.
8. CONSTRUCT GRASS SWALE #1, RIP-RAP PAD, AND ASSOCIATED EROSION CONTROL LINING. IMMEDIATELY INSTALL ROCK FILTER AS SHOWN ON PLAN.
9. CONSTRUCT BUILDINGS.
10. INSTALL UTILITIES (10.1. Backfill utility trenches the same day; 10.2. Restore and stabilize utility earth disturbance immediately).
11. PAVE DRIVEWAY AREAS.
12. (CRITICAL STAGE) ONCE ALL UPSTREAM AREAS ARE STABILIZED IN ACCORDANCE WITH FINAL SITE STABILIZATION REQUIREMENTS, REMOVE ORANGE CONSTRUCTION FENCES AND INSTALL THE RAIN GARDENS FOR LOT 2 AND LOT 3 (SEE SEPARATE "RAIN GARDEN SEQUENCE OF CONSTRUCTION" ON SHEET 6, PCSM NOTES AND DETAILS). INSTALL EROSION CONTROL LINING ON NEWLY GRADED AREAS.
13. IMMEDIATELY STABILIZE ANY DORMANT DISTURBANCE WITH PERMANENT SEED MIXTURE, MULCH AT 3 TONS/AC, AND LIME AND FERTILIZER AS PRESCRIBED.
14. STABILIZE ALL DISTURBANCE AREAS.
15. ONCE ALL FEATURES HAVE BEEN CONSTRUCTED AND ALL DISTURBANCE STABILIZED, REMOVE THE SUPER SILT FENCES, ROCK FILTER, AND REMAINDER OF THE ROCK CONSTRUCTION ENTRANCE.
16. FILE AN NPDES PERMIT NOTICE OF TERMINATION FORM WITH THE CONSERVATION DISTRICT.
Note: Critical stages of the sequence of construction are circled and require inspection by the site engineer.
STANDARD E&S CONTROL PLAN NOTES (1-37), PLAN REFERENCE & WATERSHED NOTICE
Standard Chester County Conservation District / PADEP Erosion and Sediment Control Notes 1 through 37 (covering pre-construction notification, PA One Call 1-800-242-1776, topsoil stockpiling, clean fill, dewatering, weekly and post-runoff BMP inspections, compaction, seeding, and stabilization).
PLAN REFERENCE NOTE: THIS EROSION & SEDIMENT CONTROL PLAN IS ASSOCIATED WITH THE "PCSM & GRADING PLAN" (SHEET 4) OF THE FULL SITE PLAN SET TITLED "BRAKMAN PROPERTY" AND DATED 5/17/16.
RECEIVING WATERSHED NOTICE: THIS PROJECT IS WHOLLY LOCATED WITHIN THE WATERSHED OF TRIBUTARY 7 OF EAST CHESTER CREEK, A WATERSHED DESIGNATED TROUT STOCK FISHERY, MIGRATORY FISHERY (TSF, MF) BY THE COMMONWEALTH OF PENNSYLVANIA.
LEGEND:
- STEEP SLOPES (15% TO 25%)
- STEEP SLOPES (OVER 25%)
- CONCRETE SURFACE
- EXISTING WETLANDS LINE
- STREAM LINE
- FLOOD HAZARD DISTRICT LINE
- EXISTING INTERMEDIATE CONTOUR
- EXISTING INDEX CONTOUR
- EXISTING WOODS / TREE LINE
- ADJOINER LINE
- EXISTING STORM SEWER LINE
- EXISTING RIGHT-OF-WAY LINE
- EXISTING PAVING
- EXISTING SOILS LINE (NoB2 / EC)
- PROPOSED INTERMEDIATE CONTOUR (528)
- PROPOSED INDEX CONTOUR (530)
- PROPOSED SPOT ELEVATION (X 513.4)
- PROPOSED STORM SEWER LINE
- PROPOSED SANITARY SEWER LINE
- PROPOSED WATER LINE
- PROPOSED WOODS / TREE LINE
- SUPER SILT FENCE
- LIMIT OF DISTURBANCE
- NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- STABILIZED RIP-RAP CONSTRUCTION ENTRANCE
PENNSYLVANIA ONE CALL: (800) 242-1776 | UPI No. 5306-0089-0000 | SYSTEM SERIAL NUMBER: 20160320567
UNDERGROUND UTILITY USERS
- PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA 19312, (610) 648-7702
- AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
- EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
- VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 592-4151
- COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
- WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475
| REV. No. | DATE | DESCRIPTION |
|---|---|---|
| 5 | 1/10/17 | PER CCCD REVIEW LETTER DATED 1/4/17 |
| 4 | 12/19/16 | CHANGES TO SANITARY SEWER DESIGN |
| 3 | 12/12/16 | PER CCCD REVIEW LETTER DATED 12/8/16 |
| 2 | 10/11/16 | PER TWP REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT |
| 1 | 5/23/16 | PER PADEP REVIEW LETTER DATED 5/18/16 |
EROSION & SEDIMENT CONTROL PLAN
SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY
EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA
COMMONWEALTH ENGINEERS, INC., 114 EAST LANCASTER AVENUE ~ SECOND FLOOR, DOWNINGTOWN, PA 19335, TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004, COMENG@CEI-1.COM
DATE: MAY 17, 2016 | SCALE: 1"=40' | SURVEY: MBS | DRAWN: TT | CHECKED: VK | DRAWING NO. 201541-(C) | SHEET: 7 OF: 11
8 COMMONWEALTH ENGINEERS, INC.
STANDARD CONSTRUCTION DETAIL #3-16 PUMPED WATER FILTER BAG
STANDARD CONSTRUCTION DETAIL #11-1 EROSION CONTROL BLANKET INSTALLATION
STANDARD CONSTRUCTION DETAIL #3-1 ROCK CONSTRUCTION ENTRANCE
STANDARD CONSTRUCTION DETAIL #4-14 ROCK FILTER STANDARD CONSTRUCTION DETAIL #4-10 SUPER SILT FENCE
[Engineering Plan Drawing: Entrance Driveway Plan & Profile (Sheet 9 of 11) for Brakman Property, showing Plan View of entrance driveway off East Strasburg Road (Scale 1"=40'), Profile View of Driveway Entrance (Scale 1"=4' Vertical, 1"=40' Horizontal), and Profile View of Right Sight Distance Line (Scale 1"=4' Vertical, 1"=40' Horizontal).]
PLAN VIEW (SCALE: 1"=40')
- EAST STRASBURG ROAD (S.R. 2010, 50 FOOT WIDE LEGAL RIGHT OF WAY, POSTED SPEED LIMIT - 40 MPH)
Left Sight Distance: MINIMUM SAFE STOPPING DISTANCE = 305', AVAILABLE SIGHT DISTANCE = 455'
Right Sight Distance: MINIMUM SAFE STOPPING DISTANCE = 395', AVAILABLE SIGHT DISTANCE = 395' (to EP: 3+95.00)
Driveway Alignment Stations: BP: 0+00.00, PC: 0+23.88, PT: 0+99.82, PC: 1+22.50, PT: 1+46.76, PC: 1+80.33, PT: 2+35.66, EP: 2+41.38
2:1 SIDE SLOPES; PULL-OFF AREA; CONSTRUCT RAILROAD TIE RETAINING WALL AROUND EXISTING UTILITY POLE
PROFILE VIEW (DRIVEWAY ENTRANCE) (SCALE: 1"=4' VERTICAL; 1"=40' HORIZONTAL)
Stations from -0+50 to 3+00, Elevations from 380 to 420:
GRADE BREAK STA = 0+11.62, ELEV = 388.82 (-2.00% slope)
STA: 0+15.62, ELEV: 388.74 (-4.00% slope)
STA: 0+41.00, ELEV: 389.76 (10.00% slope)
STA: 0+66.00, ELEV: 392.26 (13.54% slope to Proposed Grade)
GRADE BREAK STA = 2+41.38, ELEV = 416.00
Station Elevations: STA 0+00 (388.94 / 388.93), STA 1+00 (399.28 / 399.27), STA 2+00 (411.88 / 411.88)
PROFILE VIEW (RIGHT SIGHT DISTANCE LINE) (SCALE: 1"=4' VERTICAL; 1"=40' HORIZONTAL)
Stations from -0+50 to 4+50, Elevations from 385 to 420:
Shows SIGHT DISTANCE LINE, EXISTING GRADE, and PROPOSED GRADE
Station Elevations: STA 0+00 (389.39 / 389.39), STA 1+00 (403.20 / 403.20), STA 2+00 (409.87 / 409.86), STA 3+00 (413.84 / 413.83)
SIGHT DISTANCE NOTE:
SIGHT DISTANCES TO BE FIELD VERIFIED POST-CONSTRUCTION TO CONFIRM PROPER SIGHT DISTANCES ARE MET.
LEGEND:
- STEEP SLOPES (15% TO 25%)
- STEEP SLOPES (OVER 25%)
- CONCRETE SURFACE
- EXISTING WETLANDS LINE
- STREAM LINE
- FLOOD HAZARD DISTRICT LINE
- EXISTING INTERMEDIATE CONTOUR
- EXISTING INDEX CONTOUR
- EXISTING WOODS / TREE LINE
- ADJOINER LINE
- EXISTING STORM SEWER LINE
- EXISTING RIGHT-OF-WAY LINE
- EXISTING PAVING
- EXISTING SOILS LINE (NoB2 / EC)
- PROPOSED INTERMEDIATE CONTOUR (528)
- PROPOSED INDEX CONTOUR (530)
- PROPOSED SPOT ELEVATION (X 513.4)
- PROPOSED STORM SEWER LINE
- PROPOSED SANITARY SEWER LINE
- PROPOSED WATER LINE
- PROPOSED WOODS / TREE LINE
- SUPER SILT FENCE
- LIMIT OF DISTURBANCE
- NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- STABILIZED RIP-RAP CONSTRUCTION ENTRANCE
PENNSYLVANIA ONE CALL: (800) 242-1776 | UPI No. 5306-0089-0000 | SYSTEM SERIAL NUMBER: 20160320567
UNDERGROUND UTILITY USERS
- PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA 19312, (610) 648-7702
- AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
- EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
- VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 592-4151
- COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
- WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475
| REV. No. | DATE | DESCRIPTION |
|---|---|---|
| 5 | 1/10/17 | PER CCCD REVIEW LETTER DATED 1/4/17 |
| 4 | 12/19/16 | CHANGES TO SANITARY SEWER DESIGN |
| 3 | 12/12/16 | PER CCCD REVIEW LETTER DATED 12/8/16 |
| 2 | 10/11/16 | PER TWP REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT |
| 1 | 5/23/16 | PER PADEP REVIEW LETTER DATED 5/18/16 |
ENTRANCE DRIVEWAY PLAN & PROFILE
SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY
EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA
COMMONWEALTH ENGINEERS, INC., 114 EAST LANCASTER AVENUE ~ SECOND FLOOR, DOWNINGTOWN, PA 19335, TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004, COMENG@CEI-1.COM
DATE: MAY 17, 2016 | SCALE: AS SHOWN | SURVEY: MBS | DRAWN: TT | CHECKED: VK | DRAWING NO. 201541-(C) | SHEET: 9 OF: 11
[Engineering Plan Drawing: Sanitary Sewer Profile and Details (Sheet 10 of 11) for Brakman Property, showing Type "A" Standard Manhole detail, Sanitary Sewer Trench detail, Grinder Pump Detail (Environment One Corporation Model DH071 / DR071, Drawing NA0050P02), Sanitary Sewer Plan View (Scale 1"=40'), and Profile View from Existing MH to C.O. (Scale 1"=4' Vertical, 1"=40' Horizontal).]
CONSTRUCTION DETAILS
- TYPE "A" STANDARD MANHOLE (NOT TO SCALE): Section A-A and Plan Below Line B-B, showing manhole frame and cover, precast reinforced concrete eccentric cone top section, riser section, manhole steps (12"-16" centers), invert channel, poured-in-place concrete base on 6" min. 2B stone, and Manhole Notes 1-14.
SANITARY SEWER TRENCH (NOT TO SCALE): Showing final grade, topsoil seed and mulch, suitable backfill, min. 6" cover and min. 6" bedding 2B stone around 4" SDR 35 PVC or 1 1/4" Schedule 40 PVC sanitary sewer pipe (pipe diameter plus 12"), and Trench Notes 1-2.
GRINDER PUMP DETAIL (NOT TO SCALE): Environment One Sewer Systems (e one) Model DH071 / DR071 Detail Sheet NA0050P02 (HDPE tank, 70 gallon capacity, semi-positive displacement type pump driven by 1 HP motor). Note: GRINDER PUMP TO BE USED AS SHOWN ON LOT 3 (OR APPROVED EQUAL).
PLAN VIEW (SCALE: 1"=40') & INSTALLATION NOTES:
Shows sanitary sewer alignment from Lot 3 (Proposed 1 1/4" LPSS, Grinder Pump INV.=411.0) and Lots 1 & 2 (3 separate proposed 4" PVC gravity sewer laterals) to Proposed MH (TOP=394.0, INV.=386.8) and 6" PVC to be directionally drilled to Tie 6" PVC to Existing MH (RIM=384.37, INV.=378.0).
1) SANITARY PIPE TO BE INSTALLED AS SHOWN USING FITTINGS (45 DEGREES OR LESS) AS APPROPRIATE.
2) GRINDER PUMP DISCHARGE PIPING SHALL BE BEDDED IN EITHER SAND OR SCREENINGS. THE BEDDING SHALL BE AT LEAST 4 INCHES THICK. AFTER THE DISCHARGE PIPING HAS BEEN TESTED AND INSPECTED, AN ADDITIONAL 12 INCHES OF SAND OR SCREENINGS SHALL BE PLACED OVER THE PIPE.
3) ALL GRAVITY SEWER PIPES FROM THE HOUSES TO INCLUDE A FRESH AIR VENT, A BUILDING TRAP, AND CLEANOUTS (AS SHOWN ON THE PLAN) TO BE INSTALLED PER EAST GOSHEN TOWNSHIP ORDINANCE SECTION 188-31.C.
PROFILE VIEW (EXISTING MH TO C.O.) (SCALE: 1"=4' VERTICAL; 1"=40' HORIZONTAL)
Stations from -1+00 to 5+00, Elevations from 375 to 440:
EXISTING MH: TOP=384.37, INV.=378.0 (APPROX.)
EXISTING 8" WATER LINE: INV.=386.7 (APPROX.) (1.9' clearance)
PROPOSED 6" PVC to PROPOSED MH: TOP=394.0, INV.=386.8
INV.=392.0 (3.5' cover)
PROPOSED CLEANOUT: TOP=407.1, INV.=403.1
PROPOSED 4" PVC; NOTE: SANITARY PIPE TO BE INSTALLED AS SHOWN USING FITTINGS AS APPROPRIATE
PROPOSED CLEANOUT: TOP=423.8, INV.=419.9
PROPOSED CLEANOUT: TOP=428.6, INV.=423.1
PROPOSED CLEANOUT: TOP=429.6, INV.=424.4
LEGEND:
- STEEP SLOPES (15% TO 25%)
- STEEP SLOPES (OVER 25%)
- CONCRETE SURFACE
- EXISTING WETLANDS LINE
- STREAM LINE
- FLOOD HAZARD DISTRICT LINE
- EXISTING INTERMEDIATE CONTOUR
- EXISTING INDEX CONTOUR
- EXISTING WOODS / TREE LINE
- ADJOINER LINE
- EXISTING STORM SEWER LINE
- EXISTING RIGHT-OF-WAY LINE
- EXISTING PAVING
- EXISTING SOILS LINE (NoB2 / EC)
- PROPOSED INTERMEDIATE CONTOUR (528)
- PROPOSED INDEX CONTOUR (530)
- PROPOSED SPOT ELEVATION (X 513.4)
- PROPOSED STORM SEWER LINE
- PROPOSED SANITARY SEWER LINE
- PROPOSED WATER LINE
- PROPOSED WOODS / TREE LINE
- SUPER SILT FENCE
- LIMIT OF DISTURBANCE
- NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- STABILIZED RIP-RAP CONSTRUCTION ENTRANCE
PENNSYLVANIA ONE CALL: (800) 242-1776 | UPI No. 5306-0089-0000 | SYSTEM SERIAL NUMBER: 20160320567
UNDERGROUND UTILITY USERS
- PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA 19312, (610) 648-7702
- AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
- EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
- VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 592-4151
- COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
- WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475
| REV. No. | DATE | DESCRIPTION |
|---|---|---|
| 5 | 1/10/17 | PER CCCD REVIEW LETTER DATED 1/4/17 |
| 4 | 12/19/16 | CHANGES TO SANITARY SEWER DESIGN |
| 3 | 12/12/16 | PER CCCD REVIEW LETTER DATED 12/8/16 |
| 2 | 10/11/16 | PER TWP REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT |
| 1 | 5/23/16 | PER PADEP REVIEW LETTER DATED 5/18/16 |
SANITARY SEWER PROFILE AND DETAILS
SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY
EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA
COMMONWEALTH ENGINEERS, INC., 114 EAST LANCASTER AVENUE ~ SECOND FLOOR, DOWNINGTOWN, PA 19335, TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004, COMENG@CEI-1.COM
DATE: MAY 17, 2016 | SCALE: AS SHOWN | SURVEY: MBS | DRAWN: TT | CHECKED: VK | DRAWING NO. 201541-(C) | SHEET: 10 OF: 11
Note: some text on this page could not be read reliably. Please see the original PDF for this page.
[Engineering Plan Drawing: Landscape Plan (Sheet 11 of 11) for Brakman Property, showing existing trees, trees to be removed (TBR), tree protection zones, proposed houses on Lots 2 and 3, and tree removal quantities table.]
TREE REMOVAL AND PROTECTION NOTES
1. NEITHER PORTIONS OF TREE MASSES NOR SPECIMEN TREES SHALL BE CLEARED UNLESS ABSOLUTELY NECESSARY. ALL REASONABLE EFFORTS SHALL BE MADE TO PRESERVE THE EXISTING TREES.
2. TREES TO BE RETAINED AFTER DEVELOPMENT MUST BE PROTECTED FROM DAMAGE DURING CONSTRUCTION ACTIVITIES:
A. PROTECTION FROM MECHANICAL INJURY AND CONSTRUCTION:
1) Enclose trees at the edge of the Tree Protection Zone (TPZ) with snow fence or other fencing at least 4 feet above ground on posts set no more than 12 feet apart.
2) No construction equipment, dirt, rocks, debris, or materials within the TPZ.
3) Trees shall not be used for roping, cables, signs or fencing; no nails or spikes driven into trees.
4) Heavy equipment operators shall not operate or park within the TPZ.
5) Exposed roots damaged during construction shall be protected and cleanly pruned.
6) Tree limbs damaged during construction shall be laterally pruned immediately.
7) Construction debris shall not be disposed of within the dripline.
8) Trenching and root pruning shall not take place within the TPZ.
9) Root pruning only when necessary, no more than one side of root system in a given year (optimum timing is autumn).
10) Feeder roots shall not be cut closer than 25 feet to tree trunks.
B. PROTECTION FROM GRADE CHANGE:
1) Raising the grade: install a system of gravel and drain tiles at old soil level opening into a dry well built around the trunk, or a retaining wall between existing grade and higher grade.
2) Lowering the grade: terrace the grade, or place a retaining wall between existing grade and lower grade.
LANDSCAPE NOTE
FOUNDATION PLANTINGS TO BE PROVIDED BY BUILDER.
TREE REMOVAL QUANTITIES
| SUBDIVISION AND LAND DEVELOPMENT ORDINANCE SECTION | QUANTITY OF EXISTING TREES ON SITE | QUANTITY OF TREES ALLOWED TO BE REMOVED | QUANTITY OF TREES TO BE REMOVED | PERCENTAGE OF TREES TO BE REMOVED |
|---|---|---|---|---|
| 205-61C | 336 | 67 | 42 | 12.5 |
LEGEND:
- STEEP SLOPES (15% TO 25%)
- STEEP SLOPES (OVER 25%)
- CONCRETE SURFACE
- EXISTING WETLANDS LINE
- STREAM LINE
- FLOOD HAZARD DISTRICT LINE
- EXISTING INTERMEDIATE CONTOUR
- EXISTING INDEX CONTOUR
- EXISTING WOODS / TREE LINE
- ADJOINER LINE
- EXISTING STORM SEWER LINE
- EXISTING RIGHT-OF-WAY LINE
- EXISTING PAVING
- EXISTING SOILS LINE (NoB2 / EC)
- PROPOSED INTERMEDIATE CONTOUR (528)
- PROPOSED INDEX CONTOUR (530)
- PROPOSED SPOT ELEVATION (X 513.4)
- PROPOSED STORM SEWER LINE
- PROPOSED SANITARY SEWER LINE
- PROPOSED WATER LINE
- PROPOSED WOODS / TREE LINE
- SUPER SILT FENCE
- LIMIT OF DISTURBANCE
- NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
- STABILIZED RIP-RAP CONSTRUCTION ENTRANCE
PENNSYLVANIA ONE CALL: (800) 242-1776 | UPI No. 5306-0089-0000 | SYSTEM SERIAL NUMBER: 20160320567
GENERAL NOTES:
1. RECORD OWNER: ANTOINETTE BRAKMAN, 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380, UPI 5306-0089-0000 (TAX #53-6-89), PHONE: (610) 436-0152, DEED REFERENCES: DB. 3529, PG. 1960.
EQUITABLE OWNER: JIM BRANDOLINI, GUNNISON DEVELOPMENT CO., LLC, 1200 BURNING BUSH LANE, WEST CHESTER, PA 19380, PHONE: (610) 640-9174.
2. SITE ADDRESS: 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380
3. TRACT AREA: 221,252.8 SQ. FT / 5.079 ACRES (GROSS); LESS 40' ROAD RIGHT-OF-WAY: 17,152.849 SQ. FT. / 0.394 ACRES; NET TRACT AREA: 4.685 ACRES (NET)
4. BOUNDARY AND PARTIAL TOPOGRAPHY FROM FIELD SURVEY PERFORMED BY COMMONWEALTH ENGINEERS, INC., APRIL 2016. BENCHMARK: NO. 4 REBAR FOUND, NORTHEAST CORNER OF SITE, DATUM: ASSUMED USGS.
5. WETLANDS DELINEATION BY VORTEX ENVIRONMENTAL, INC. AND SURVEYED BY COMMONWEALTH ENGINEERS, INC. IN MAY 2016.
6. SOILS CLASSIFICATIONS FROM THE UNITED STATES DEPARTMENT OF AGRICULTURE (USDA) NATURAL RESOURCE CONSERVATION DISTRICT WEB SOIL SURVEY, IN AUGUST, 2014.
7. UNDERGROUND UTILITIES SHOWN HEREON WERE PLOTTED FROM OBSERVABLE EVIDENCE AT THE TIME OF SURVEY AND THROUGH INFORMATION PROVIDED BY THE UTILITY COMPANIES WHICH SERVICE/OCCUPY THE SITE. THE SITE CONTRACTOR MUST VERIFY LOCATION AND DEPTH OF ALL UNDERGROUND UTILITIES AND FACILITIES PRIOR TO BEGINNING CONSTRUCTION.
8. THE SITE IS SERVED BY PUBLIC WATER (AQUA PA).
9. EXISTING SANITARY SYSTEM PRESENT ON SITE BUT NOT LOCATED.
10. EXISTING IRON PINS ARE SHOWN AS THUS "O".
11. THE DEVELOPER SHALL CONFORM TO OR CAUSE CONFORMANCE WITH ALL OF THE APPLICABLE REQUIREMENTS OF THIS PLAN AND THE EAST GOSHEN TOWNSHIP ZONING ORDINANCE AND SUBDIVISION AND LAND DEVELOPMENT ORDINANCE AS WELL AS OTHER APPLICABLE LOCAL, STATE AND FEDERAL LAWS, STATUTES, REGULATIONS AND ORDINANCES.
12. THE DEVELOPER SHALL NOTIFY UNDERGROUND UTILITY USERS AT LEAST THREE DAYS PRIOR TO THE COMMENCEMENT OF CONSTRUCTION IN ACCORDANCE WITH PA ACT 287 OF 1974, AS AMENDED BY ACT 187 OF 1996.
13. FEMA FLOODPLAIN BOUNDARY TAKEN FROM FLOOD INSURANCE RATE MAP, PANEL 215F, MAP NUMBER 42029C0215F, DATED SEPTEMBER 29, 2006.
14. THIS PROJECT IS LOCATED IN THE WATERSHED OF TRIBUTARY 7 OF EAST BRANCH CHESTER CREEK WHICH HAS THE DESIGNATION OF TROUT STOCK FISHES (TSF, MF) BY THE COMMONWEALTH OF PENNSYLVANIA.
15. THIS PROJECT PROPOSES THE SUBDIVISION OF THE EXISTING LOT INTO 3 SEPARATE LOTS WITH EACH LOT TO BE SERVED BY PUBLIC WATER AND PUBLIC SEWER. PUBLIC SEWER TO BE THROUGH LOW PRESSURE FORCE MAIN TIED INTO AN EXISTING MANHOLE AS SHOWN.
SURVEY REFERENCE NOTES
1. PLAN ENTITLED "BOUNDARY SURVEY PLAN FOR MS. ANTOINETTE BRAKMAN", PREPARED BY R.H. SMITH SURVEYORS, DATED MARCH 27, 2007.
2. PLAN ENTITLED "REVERSE SUBDIVISION/SUBDIVISION PLAN FOR MICHAEL RIZZO", PREPARED BY BRANDYWINE VALLEY ENGINEERS, A DIVISION OF VOLLMER ASSOCIATES, LLP, CONSULTING ENGINEERS AND LAND SURVEYORS, DATED NOVEMBER 30, 2001.
3. PECO BLANKET RIGHT-OF-WAY CONTAINED IN MISCELLANEOUS DB. 81, PG 452.
4. PLAN ENTITLED "THE GAMBONE BROTHERS INC.", PREPARED BY HENRY S. CONREY INC., DIVISION OF CHESTER VALLEY ENGINEERS, DATED JUNE 6, 1973 (LAST REVISED SEPTEMBER 9, 1973).
UNDERGROUND UTILITY USERS
- PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA 19312, (610) 648-7702
- AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
- EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
- VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 592-4151
- COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
- WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475
| REV. No. | DATE | DESCRIPTION |
|---|---|---|
| 5 | 1/10/17 | PER CCCD REVIEW LETTER DATED 1/4/17 |
| 4 | 12/19/16 | CHANGES TO SANITARY SEWER DESIGN |
| 3 | 12/12/16 | PER CCCD REVIEW LETTER DATED 12/8/16 |
| 2 | 10/11/16 | PER TWP REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT |
| 1 | 5/23/16 | PER PADEP REVIEW LETTER DATED 5/18/16 |
LANDSCAPE PLAN
SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY
EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA
COMMONWEALTH ENGINEERS, INC., 114 EAST LANCASTER AVENUE ~ SECOND FLOOR, DOWNINGTOWN, PA 19335, TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004, COMENG@CEI-1.COM
DATE: MAY 17, 2016 | SCALE: 1"=40' | SURVEY: MBS | DRAWN: TT | CHECKED: VK | DRAWING NO. 201541-(C) | SHEET: 11 OF: 11
Memorandum
East Goshen Township
1580 Paoli Pike
West Chester, PA 19380
Voice: 610-692-7171
Fax: 610-692-8950
E-mail: mgordon@eastgoshen.org
Date: 1/26/2017
To: Planning Commission
From: Mark Gordon, Township Zoning Officer [initials: MG]
Re: 1420 E. Strasburg Rd. - SD/LD Application
Dear Commissioners,
The Township has received revised subdivision documents for the Brakman SD/LD application. As you know, this is a 5 acre wooded parcel in the R-2 District, is proposed to be subdivided into three lots. The property will use the existing driveway on E. Strasburg Rd. however alignment and sight distance modifications will be made to improve safety in accordance with the PennDOT approval. The existing home will be saved and two new Single Family homes will be constructed. All three new lots will be served by public water and public sanitary sewer. The applicant is seeking the Planning Commission recommendation for approval to include the following waiver from the Subdivision Ordinance:
- 205-31 - Combine Prelim and Final Plan Approval Staff has no objection to this request.
The Township engineer, staff, the applicants engineer and the applicant have worked closely over the last 6+ months on a number of the major issues identified during the initial discussions in the summer of 2016. Some of the major issues were:
- Tree removal and the absence of a tree plan or landscape plan
- Location of SWM rain gardens
- The extend of the grading proposed
- Sanitary Sewer
- Driveway access and safety
The applicant has addressed most of the main issues in the revised plan submission however there are still details to be cleaned up. At this time staff is not recommending approval by the PC at this time due to the number of outstanding comments on the engineers' letter and the absence of a Landscape Plan and a recommendation from the Conservancy Board.
The Township has until March 29, 2017 to render a decision on this application, which would require a Planning Commission recommendation on or before March 15th.
F:\Data\Shared Data\Property Management\53-6\53-6-89 (1420 E. Strasburg Rd.)\2016 SD application\Memo to PC 01262017.doc
Pennoni
One South Church Street
Second Floor
West Chester, PA 19382
T: 610-429-8907
F: 610-429-8918
www.pennoni.com
January 26, 2017
EGOS 0118
Mark A. Gordon
Director of Code Enforcement/Zoning Officer
East Goshen Township
1580 Paoli Pike
West Chester, PA 19380
RE: 1420 E. Strasburg Road, Brakman Property
Preliminary/Final Subdivision and Land Development – 3rd Submission
Dear Mark:
As requested, we have reviewed the following information, prepared by Commonwealth Engineers, Inc., regarding the referenced submission:
- “Subdivision and Land Development Plan for Brakman Property” (ten sheets) dated May 17, 2016, last revised October 11, 2016;
- “Post-Construction Stormwater Management Plan Narrative prepared for Brakman Property” dated May 17, 2016, last revised October 24, 2016; and
- Subdivision and Land Development application and supporting documents.
The owner, Antoinette Brakman, proposes to subdivide UPI No. 53-6-89 (5.079 acres) into three residential lots; new single family dwellings are proposed for both Lot 2 (1.243 acre) and Lot 3 (2.086 acre). There is an existing dwelling on Lot 1 that will remain. All lots will be served by on-site water and public sanitary sewer. The parcel is located on the south side of E. Strasburg Road (SR 2010), 400± feet east of its intersection with Lochwood Lane, within the R-2 Low Density Residential zoning district. A shared driveway will provide access to all three lots.
The applicant has requested the following waiver:
- From §205.1 requiring a preliminary plan submission.
The following comments from our December 5, 2016 review letter remain outstanding (new comments in italics):
SANITARY SEWER
- The elevations of the existing manhole on the Kaplan property should be field surveyed to confirm the actual elevations. Remains outstanding. The manhole needs to be field surveyed now that a gravity sewer connection is proposed.
EGOS 0118
January 26, 2017
Page 2
Mark A. Gordon, Zoning Officer
1420 E. Strasburg Road, Brakman Property
- We recommend the inclusion of an additional detail showing the connection of the LPSS lines to the new manhole. Detail and notes should include, at minimum: LPSS discharge pipes to enter connecting manhole at bottom of manhole.; Details on discharge piping into flow channel within manhole.; That manhole wall openings should be precast with A-lok gaskets. The sewage system has been redesigned to no longer discharge the force main into this manhole. However, a detail should be included that shows the connection/orientation of the three 4-inch PVC gravity lines into the new manhole with flow channel(s).
- We recommend that interior of the new manhole be lined with a Duraplate-type liner, or equal, since the manhole will be subject to hydrogen sulfide deterioration from the pressure sewers. The interior of the existing manhole on the Kaplan property should also be lined with a Sprayroq polyurethane liner, or equal, to mitigate the same deterioration. An additional manhole has been proposed on the subject property with Standard Manhole Detail Note #14 on Sheet 10 stating that any manhole receiving force main discharge should be lined with a PVC liner. For clarity, this note should call out the referenced manhole specifically and state that it shall receive a Duraplate-type PVC liner or approved equal.
- We recommend the inclusion of additional details or notes regarding the gravity sewer lateral from the house to the grinder pump including, at minimum, pipe material, size, cleanout, trap, and vent cap. Installation Note #3 has been added on Sheet 10 that all gravity sewer pipes should be installed as per §188-31.C. This note should also reference the “East Goshen Township Sewer Lateral/Building Sewer Detail” if not including the detail on this plans. We recommend that the detail be added to the plans to ensure compliance.
- Plan views propose the Lot 3 grinder pump invert elevation as 411.0 feet. Proposed grade at this location is approximately 420 feet. The literature submitted for the E/ONE model DH071-93/DR071-93 grinder pump shows that cover to grade above the 4-inch gravity invert is only 55-inches. This is not consistent with the elevations on the plan.
- Plans notes should state that there shall be a spare pump on-site. (§188-33.B.(2)(a))
- The sewer system design has been revised to eliminate grinder pumps from Lots 1 and 2 in favor of gravity sewer systems. Lot 3 retains the grinder pump and now has a proposed pressure sewer for approximately 150 feet whereupon it transitions to a 4-inch PVC gravity sewer at a cleanout. An additional manhole has been proposed on the subject property, and directional drilling is proposed for the new main to connect to the existing manhole on the Kaplan property. Comments on the redesign follow: We typically do not recommend horizontal directional drilling (HDD) gravity sewers due to the rocky conditions in the area and potential of the drill and ultimately the sewer to fluctuate vertically and horizontally resulting in sags and blockages. We also question the feasibility to drill directly into the existing manhole and pull the pipe through. However, since the sewer is proposed with a steep approx. 9% slope, we would not object to HDD in this case under the following conditions and at the Applicant’s own risk; if the conditions are not met, the Applicant would need to remove and replace the sewer, likely via open cut, with an acceptable sewer line at his cost: The pipe should be fused HDPE DR11 instead of PVC.; The pipe should be fused HDPE DR11 instead of PVC.
EGOS 0118
January 26, 2017
Page 3
Mark A. Gordon, Zoning Officer
1420 E. Strasburg Road, Brakman Property
- It shall pass a mandrel test for the installed pipe size. It shall pass a CCTV inspection to the satisfaction of the Township. It shall pass a lamp test to the satisfaction of the Township. The pipe shall pass a pressure test.; It shall pass a mandrel test for the installed pipe size.; It shall pass a CCTV inspection to the satisfaction of the Township.; It shall pass a lamp test to the satisfaction of the Township.; The pipe shall pass a pressure test.; The proposed gravity sewer main shall be 8″ diameter instead of 6-inch diameter. (§205-71.B.(4)(d)[1]); When sewer lines are designed with a grade in excess of 20%, steep slope anchors shall be installed. (§205-71.B.(4)(d)[3]) One section of the gravity sewer laterals, from approximately 1+65 to 1+90 on the Sheet 10 profile, has a slope of approximately 40%. Steep slope anchors need to be included in the design for this stretch of piping with details added to the plans.; Cleanouts need to be added to each lateral pipe at the right of way line. (§188-31.C.(3)(a)) The Township will then be responsible for the laterals from cleanouts to manhole.; A note should be added to the plans that the 8-inch sewer main and the proposed manhole will be dedicated to East Goshen Township.; A transition coupling detail should be added for the Lot 3 pipe transition from pressure to gravity sewer.; A detail should be added for the connection of the proposed gravity sewer main to the existing manhole on the Kaplan property indicating that the manhole will be cored and the opening sealed with a Link-Seal modular seal or approved equal. Additionally, we recommend the new sewer enter the manhole at the top of the existing bench to avoid having to core cut the bench, and a cast-in-place concrete channel should be constructed above the existing bench to convey flow into the existing channel.; The horizontal separation distance between all the proposed water lines and the sewer lines should be a minimum of 10 feet.; On Sheet 7, silt fence or filter sock should be added along the location of the existing manhole and proposed sewer on the Kaplan property if any earth disturbance will occur during sewer construction.; The profile view (Sheet 10) indicates that the existing water main has less than 3 feet of cover. We understand this is the depth at which Aqua believes the main MAY be located. The Applicant should consider installing the sewer main a little deeper at this location to minimize the risk of a conflict, specifically since the new manhole may not be deep enough to address such a conflict.
- The proposed sanitary sewer laterals are within 2 feet to the easement line, which provides a limited area for maintenance in the future. (§188-31.B.(8)) We recommend the easement width be increased or lateral locations adjusted to provide at least 5 feet to the edge of the easement.
- The following comments are in regards to the new Standard Manhole detail and notes on Sheet 10: The manhole cover adjustment note should only reference precast grade rings; the reference to bricks should be deleted.; In lieu of a separate cover detail, a note should be added that the manhole cover should read “East Goshen Municipal Authority Sanitary Sewer”. Notes should also be added which state that the manhole shall be traffic rated, bolted down, and watertight.; We question why the base is stated to be cast-in-place. We suggest a precast base be used instead.; Note #11 – Manhole steps should be steel reinforced polypropylene. Reference to aluminum should be deleted.; Note #12 – A note should be added to clarify that this is to be a 4 feet diameter manhole, or the note be revised to require a 4 feet diameter manhole for “up to 15-inch pipes”.
EGOS 0118
January 26, 2017
Page 4
Mark A. Gordon, Zoning Officer
1420 E. Strasburg Road, Brakman Property
GENERAL
- A Sight Distance Note was added to Sheet 9 as requested. This note should appear on a plan that is to be recorded.
- A Landscaping Note appears on Sheet 11 indicating foundation plantings are to be provided by the builder. A plan should be provided indicating proposed plantings.
- Per the PaDEP BMP Manual it is recommended that additional plantings, such as shrubs and trees, be included in the rain garden area, per PaDEP specifications. The applicant should present a planting detail identifying plant species to be used and the number of plantings.
- Please additionally note the status of the following reviews/permits: NPDES Permit (PaDEP/CCCD) (§195-15.C(2), -16.A, -17.A) – Correspondence has not yet been received.; Planning Module (PaDEP) (§240-24.F, §205-33.B(22)(a)) – Exemption approval letter dated 12/17/16.; Sanitary Sewer (Municipal Authority) – Correspondence has not yet been received.; Water (Aqua) – Will Serve letter dated May 2, 2016.; Highway Occupancy Permit (PennDOT) – Correspondence has not yet been received.; Fire Planning (Fire Marshal) – Not applicable.; Historic Resource (Historical Comm.) – Not applicable.; Landscaping (Conservancy Board) – Comments via January 19, 2017 e-mail.
The existing deed for the parcel, proposed draft legal descriptions for Lots 1, 2 and 3, and all other easements associated with the property (driveway, utility, sewer, etc.) and the Kaplan property should be provided to the Township. All legal descriptions, easements and agreements are subject to review and approval by the Township Solicitor.
The applicant is reminded that a stormwater O&M agreement as well as a Grinder Pump Station O&M agreement shall be executed with the Township prior to plan recording.
Should you have any further questions or comments, please contact the undersigned.
Sincerely,
PENNONI
[signature: Nathan M. Cline]
Nathan M. Cline, PE
Township Engineer
cc: Rick Smith, Township Manager (via e-mail)
Gunnison Development Co., LLC (via e-mail)
Thomas Tran, P.E., Commonwealth Engineers, Inc. (via e-mail)
Mike Ellis, PE (via e-mail)
COMMONWEALTH ENGINEERS, INC.
114 East Lancaster Avenue ~ Second Floor ~ Downingtown, PA 19335
Telephone: (610) 518-9003 ~ Fax: (610) 518-9004 ~ comeng@cei-1.com
January 12, 2017
Mr. Mark A. Gordon
Director of Code Enforcement/Zoning Office
East Goshen Township
1580 Paoli Pike
West Chester, PA 19380
Re: Brakman Property, 1420 E. Strasburg Road
Preliminary/Final Subdivision and Land Development
Dear Mr. Gordon:
The following revisions are offered in response to Review Letter dated June 1, 2016 issued by Nathan M. Cline, P.E. of Pennoni, Township Engineer, for the above-referenced plan submission. Pennoni comments are shown in italics. Commonwealth Engineers, Inc., responses are shown in bold.
ZONING
- A clear sight triangle and the required sight distance per §240-23.D (11) should be indicated at the proposed driveway. The plan indicates the minimum required sight distance has been met; to the east, it meets the minimum requirement exactly. Further, it appears there are trees within the right-of-way and along the property frontage to be removed. Therefore, we recommend that the sight distance be field verified post-construction to confirm property sight distances are met. A note on the plan should be added. 1. A note labeled as “Sight Distance Note” has been added to Sheet 9.
SUBDIVISION & LAND DEVELOPMENT
- Regarding trees, the Applicant should review §205-61 and §205-63 regarding existing trees, replacement of trees and the protection of existing trees during construction. Per the Code, the property is considered a wooded lot (§205-7), as it has two or more viable, noninvasive trees, six inches or greater in diameter breast height (dbh), per every 1,500 square feet of gross lot area, exclusive of street right-of-way. The Applicant previously provided a Tree Survey Plan and Tree Survey Count of all trees and their conditions, and has updated the plans accordingly. On Sheet 9, the Applicant indicates there are 375 existing trees. However, per the definition, trees that are dead, invasive or within the street right-of-way do not count towards
PROFESSIONAL CIVIL ENGINEERING
COMMONWEALTH ENGINEERS, INC.
| TO: | East Goshen Township |
|---|---|
| RE: | 1420 E. Strasburg Rd, Brakman Property |
| DATE: | January 12, 2017 |
| PAGE: | 2 |
the total count. Please revise the calculation on Sheet 9 accordingly. Note further that lines 139-147 are missing in the previously provided Tree Survey Count.
2. The calculation on the Landscape Plan (now Sheet 11) has been revised accordingly. A revised tree survey summary is included with this submission.
- Street trees with a minimum caliper of three inches shall be provided where deemed advisable by the Planning Commission and/or Supervisors. (§205-62). We defer to the Township. 3. It was decided at a meeting on 12/14/16 between the township, the township engineer, and the applicant that the township would support that the placement of new street trees for this project would not be required.
STORMWATER MANAGEMENT
- A planting plan for the raingardens in accordance with the PA BMP Manual is recommended. The Applicant has indicated that the rain gardens will be planted with a seed mix, however, the detail notes that mulch is to be applied after planting. Consideration shall be given to the impacts of mulch application on seed germination and growth. 4. The details and construction sequence associated with the rain garden installations have been revised by the removal of the references to the installation of mulch at the bottom of the rain gardens.
- The Applicant has indicated that Rooftop Disconnection non-structural volume credits are being utilized to reduce the post-construction 2-year storm event runoff volume. Per the PaDEP BMP Manual checklist provided, one of the items states that the contributing rooftop area to each disconnection point shall be 500 square feet or less. However, the entire roof areas are being discharged at single points at each rain garden. 5. Rooftop Disconnection is no longer being used as a credit toward the non-structural BMP calculations. Sheet 5 and the PCSM Report have been revised accordingly. Also note that now only one roof drain collection piping system is being proposed (to divert roof drainage of the south side of the Lot 3 house to the rain garden).
- The Applicant has indicated that Disconnection from Storm Sewers non-structural volume credits are being utilized to reduce the post-construction 2-year storm event runoff volume. Per the PaDEP BMP Manual
COMMONWEALTH ENGINEERS, INC.
TO: East Goshen Township
RE: 1420 E. Strasburg Rd, Brakman Property
DATE: January 12, 2017
PAGE: 3
checklist provided, one of the items states that the vegetated disconnection area shall have a maximum slope of 5%. The downhill slopes along a long stretch of the driveway appear to exceed this threshold. The amount of impervious area considered for disconnection should be recalculated accordingly.
6. The amount of impervious area being considered for credit has been revised as shown on Sheet 5. The PCSM report has been revised accordingly.
7. Per §195-24.B, one foot of freeboard is required above the maximum pool elevation computed when the facility functions for the one-hundred-year proposed conditions inflow. Pages 66 and 67 of the narrative indicate that only 0.35 feet and 0.33 feet are provided for the Lot 2 and Lot 3 rain gardens, respectively.
7. The maximum pool elevation for the 100-year storm for both rain gardens is equal to the top of the grate of the outlet pipe since the rain gardens have been sized to retain on site the entire 100-year storm. The top of the grate for both rain gardens is located 1 foot below the berm elevation. The emergency spillway calculations provided in the PCSM Report are presented only to demonstrate the adequacy of the spillway to convey the 100-year storm in the event of failure of the rain gardens and the clogging of the outlet grates.
SANITARY SEWER
8. A product submittal for the proposed grinder pump which includes the manufacturer's detail sheet, pump curve, and installation instructions shall be provided for review. The grinder pump unit and piping needs to comply with the specifications of §188-33. Additionally, the grinder pump system piping size, material, depth, method of connection to the existing manhole, and other information to demonstrate compliance with the requirements of the Township Ordinance shall be shown on the plans. A profile of the LPSS shall also be provided since there are a few significant grade changes and a utility crossing(s) along the proposed route (§188-33.A. (3).(a)-(d)).
Remains outstanding.
8. Grinder pump product information is included with this submission. Applicable details are shown on the plan. Also, the sanitary sewer design has been changed to be mostly a gravity sewer system as discussed with township staff. A profile of the majority of the system is provided on Sheet 10.
9. We anticipate a Sewage Facilities Planning Module will be required by PaDEP for this project, in lieu of an exemption/waiver, since one sewer pipe carries wastewater from more than one dwelling. A Sewage Facilities Planning Application Mailer shall be submitted to PaDEP to initiate this process (§205-33.B (22)).
COMMONWEALTH ENGINEERS, INC.
TO: East Goshen Township
RE: 1420 E. Strasburg Rd, Brakman Property
DATE: January 12, 2017
PAGE: 4
The Applicant submitted the Mailer. We anticipate an exemption/waiver will now be applicable since separate pipes are proposed for each house; however, the comment remains outstanding until PaDEP Planning approval or exemption is obtained.
9. An exemption approval letter dated 12/7/16 was obtained and is included with this submission.
10. An air release valve may be needed on the common LPSS since the subject property is much higher than the roadway and higher than the connection manhole in Brook Drive.
Remains outstanding, pending analysis of elevation submittal of the LPSS.
10. The valve should no longer be required because of the significant change to the sanitary sewer design which is now mostly gravity sewer.
11. We do not anticipate that the bend along the shared driveway can be directionally drilled. We recommend a more direct path to the connecting manhole.
11. The layout of the pipe to be directionally drilled has been revised accordingly.
12. The elevations of the existing manhole on the Kaplan property should be field surveyed to confirm the actual elevations.
12. The top elevations of the existing manhole were field surveyed.
13. We recommend that LPSS lines not connect directly to the existing manhole on the Kaplan property due to the 90-degree angle of orientation of the LPSS with the sewer main, unknown physical condition of the manhole, and extent of LPSS on private property. We instead recommend a new manhole be constructed on the south side of East Strasburg Road with a gravity sewer extension from the existing manhole on the Kaplan property. All three LPSS lines should then connect directly to the new manhole. That gravity extension and manhole could be dedicated to the Township, and the full extent of all LPSS lines would be private.
13. The plans have been revised accordingly.
14. We recommend the inclusion of an additional detail showing the connection of the LPSS lines to the new manhole. Detail and notes should include, at minimum:
a. LPSS discharge pipes to enter connecting manhole at bottom of manhole.
COMMONWEALTH ENGINEERS, INC.
TO: East Goshen Township
RE: 1420 E. Strasburg Rd, Brakman Property
DATE: January 12, 2017
PAGE: 5
a. This comment should no longer be applicable because of the significant change to the sanitary sewer design which is now mostly gravity sewer.
b. Details on discharge piping into flow channel within manhole.
b. This comment should no longer be applicable because of the significant change to the sanitary sewer design which is now mostly gravity sewer.
c. That manhole wall openings should be precast with A-lok gaskets
c. This comment should no longer be applicable because of the significant change to the sanitary sewer design which is now mostly gravity sewer.
15. We recommend that interior of the new manhole be lined with a Duraplate-type liner, or equal, since the manhole will be subject to hydrogen sulfide deterioration from the pressure sewers. The interior of the existing manhole on the Kaplan property should also be lined with a Sprayron polyurethane.
15. Pressure sewers are no longer being proposed at the manhole connection.
16. We recommend the pipe routing be revised to eliminate bends greater than 45 degrees within the LPSS, OR to include notes that multiple 45 or 22.5 degree bends will be used at those locations where sharp turns must occur.
16. A note labeled as "Installation Note" has added to Sheet 10.
17. A utility easement on the Kaplan property is required as indicated on the plans.
17. The utility easement has been revised accordingly per the revised sanitary sewer design.
18. §188-33.D. (3) – Grinder pump discharge piping shall be minimum 1-1/4 inch; the proposed piping is only 1-inch.
18. The Grinder Pump (now only on Lot 3) discharge pipe has been labeled as 1-1/4 inch.
19. §188-33.D. (9). (a) – Plans should indicate that, where LPSS is installed via open cut trench, discharge piping shall be bedded in either sand or screenings. The bedding shall be at least 4 inches thick. After the discharge piping has been tested and inspected, an additional 12 inches of sand or screenings shall be placed over the pipe.
COMMONWEALTH ENGINEERS, INC.
TO: East Goshen Township
RE: 1420 E. Strasburg Rd, Brakman Property
DATE: January 12, 2017
PAGE: 6
19. The above information has been included as part of the note labeled as "Installation Note" on Sheet 10.
20. We recommend the inclusion of additional details or notes regarding the gravity sewer lateral from the house to the grinder pump including, at minimum, pipe material, size, cleanout, trap, and vent cap.
20. Details and notes (under "Installation Notes") have been added to Sheet 10. Also, cleanouts have been added to all gravity sewers as appropriate.
GENERAL
21. Please additional note the status of the following reviews/permits:
a. NPDES Permit (PaDEP/CCCD) (§195-15.C (2), -16.A, -17.A) – Not applicable. Correspondence has not yet been received.
a. A status chart has been added to Sheet 2.
b. Planning Module (PaDEP) (§240-24.F, §205-33.B(22)(a)) – Correspondence has not yet been received.
b. A status chart has been added to Sheet 2.
c. Sanitary Sewer (Municipal Authority) – Correspondence has not yet been received.
c. A status chart has been added to Sheet 2.
d. Water (Aqua) – Will Serve Letter dated May 2, 2016.
d. A status chart has been added to Sheet 2.
e. Highway Occupancy Permit (PaDOT) – Correspondence has not yet been received.
e. A status chart has been added to Sheet 2.
f. Fire Planning (Fire Marshal) – Not applicable.
f. A status chart has been added to Sheet 2.
g. Historic Resource (Historical Comm.) – Not applicable.
COMMONWEALTH ENGINEERS, INC.
TO: East Goshen Township
RE: 1420 E. Strasburg Rd, Brakman Property
DATE: January 12, 2017
PAGE: 7
g. A status chart has been added to Sheet 2.
h. Landscaping (Conservancy Board) – Correspondence has not yet been received.
h. A status chart has been added to Sheet 2.
22. The existing deed for the parcel, proposed draft legal descriptions for Lots 1, 2 and 3 and all other easements associated with the property (driveway, utility, sewer, etc.) should be provided to the Township. All legal descriptions, easements and agreements are subject to review and approval by the Township Solicitor.
22. The existing deed is provided with this submission. Documents for proposed items are pending.
23. The Applicant is reminded that a Stormwater O&M Agreement as well as a Grinder Pump Station O&M Agreement shall be executed with the Township prior to plan recording.
23. Noted.
We hope that the above plan revisions satisfy your requirements. If you have any questions or need further clarification of the revisions we have made, please feel free to contact me.
Sincerely,
[Signature: Thomas Tran]
Thomas Tran, P.E.
Project Engineer
cc: Gunnison Development Co., LLC