The East Goshen Township Planning Commission is an advisory board to the Township Board of Supervisors. The Commission reviews all subdivision and land development applications, conditional use applications, zoning hearing board applications and makes recommendations to the Board of Supervisors.  The Commission also reviews or drafts Zoning Ordinance Amendments. Each member is appointed by the Board of Supervisors.

  • Composed of seven East Goshen Township residents each serving a four-year term.
  • Formal Meetings are held the 4th Tuesday of each month at 7:00 P.M.
  • Workshop Meeting are held on an as needed basis
  • All township meetings are held at the Township Building and are open to the public
Planning Commission Members Term Expiration Date
John Stipe, Chair  2026
Dan Truitt, Vice Chair 2027
Daniel H. Daley 2027
Michael Koza 2026
Ernest Harkness 2026
Karen Martynick 2029
William Kaufman 2029
Larry Massaro, BOS Liaison
Kelly Krause, Staff Liaison

 

Draft Ordinance-Zoning Amendment Regulating Data Centers by Conditional Use 9.24.26

Click here to view – May 4th Documents for Malvern Institute and East Whiteland Special Study.

Related News

PLANNING COMMISSION CONSIDERS UPGRADES TO AQUA FACILITY

Wednesday, November 18, 2026

At its September meeting, the East Goshen Planning Commission reviewed a conditional use application from Aqua Pennsylvania to upgrade its Hunt Country well treatment facility located on Thorncroft Drive. The upgrade is required to meet new maximum contaminant levels (MCLs) for PFAS in drinking water that were enacted last year by the U.S. Environmental Protection […]

View Article

From the Planning Commission: Addressing Potential Data Center Development in East Goshen Township

Wednesday, September 30, 2026

As the demand for artificial intelligence accelerates, municipalities throughout Pennsylvania have found themselves navigating complex regulations, legal challenges, and community debates about large-scale data centers. While no data center projects are currently proposed in East Goshen, township officials are proactively addressing potential impacts by updating zoning ordinances to create strict standards that will apply should […]

View Article

More News

Documents

Notice: this accessible version was created automatically from the original document. The transcription may not be 100% accurate. It is provided for searching and for screen readers; please refer to the original document for the official version.

EAST GOSHEN TOWNSHIP PLANNING COMMISSION

East Goshen Township Administration Building 1580 Paoli Pike, 2nd Floor, West Chester, PA 19380 Meeting Agenda Tuesday, June 24, 2025, at 7:00 PM

Planning Commission Members: Ernest Harkness, Chairman John Stipe, Vice Chairman Daniel H. Daley Michael Koza Mike Pagnanelli Fred Pioggia Dan Truitt John Hertzog, BOS Liaison Kelly Krause, Zoning Officer/Staff Liaison Agenda Items:

1. Call to Order / Pledge of Allegiance and Moment of Silence

2. Chairman will ask if anyone is going to record the meeting.

3. Review of Tracking Log / Determine need for Workshop Meeting

4. Public Comment on Non-Agenda Items

5. Approval of Minutes a. April 22, 2025

6. Acknowledge Receipt of New Applications (Initial Submission) a. Subdivision and Land Development Applications b. Conditional Uses Applications c. Zoning Hearing Board Variances d. Ordinance Amendments

7. Old Business- a. 1344 Morstein Road- K.A. Thomas, Preliminary/Final 2 Lot Subdivision Plan

8. New Business

9. Liaison Reports

10. Correspondence

11. Announcements

12. Next Meeting – Tuesday, July 22, 2025 at 7:00 PM

13. Adjournment

Bold Items indicate new information to review or discuss.

PROJECT DESCRIPTION Date Filed Start Date

Twp. Engineer

Review

CCPC Review

Conserv.

Board Review

Extension

Date

PC Deadline

Meeting

BOS Deadline

Meeting

Hearing

Date

Final Action Deadline (90 days)

Comments

1344 Morstein Road- K.A. Thomas 2 Lot Subdivision 5/28/2025 6/24/2025 6/17/2025 pending 6/11/2025 n/a 8/19/2025 9/16/2025 n/a 9/22/2025 Preliminary plan reviewed by the Planning Commisson on 11/26/2024

10-Year Comprehensive Plan Review n/a 4/22/2025 n/a n/a n/a n/a n/a n/a n/a na/ Pending direction from BoS- per PC request discussed at BoS

meeting on 5/20/2025

1338 Morstein Road- WCU Foundation 16 Lot Subdivision 2/5/2024 2/27/2024 9/13/2024 n/a n/a 7/31/2025 n/a 7/15/2025 n/a 7/31/2025 Finalization of agreements and plan revisions- Extention granted

until 7/31/2025

PROJECTS COMPLETED IN 2025

Bold = New application or action required

East Goshen Township Planning Commission

Application Tracking Log

June 18, 2025

PENDING PROJECTS

PC 4-22-25 draft 1

DRAFT 1 EAST GOSHEN TOWNSHIP 2 PLANNING COMMISSION MEETING 3 April 22, 2025 4 5 The East Goshen Township Planning Commission held their regular monthly meeting on Tuesday, 6 April 22, 2025 at 7:00 pm in the Township Building. 7 Members present are highlighted: 8 Chair – Ernest Harkness 9 Vice Chair – John Stipe 10 Dan Daley 11 Michael Koza 12 Michael Pagnanelli 13 Fred Pioggia 14 Dan Truitt 15 16 Also present was: 17 Kelly A. Krause, Zoning Officer 18 John Hertzog , BOS Liaison 19 Nathan Cline, Township Engineer 20 Mark Thompson, Township Solicitor 21 22 COMMON ACRONYMS: 23 BOS – Board of Supervisors CPTF – Comprehensive Plan Task Force 24 BC – Brandywine Conservancy CVS – Community Visioning Session 25 CB – Conservancy Board SWM – Storm Water Management 26 CCPC – Chester Co Planning Commission ZHB – Zoning Hearing Board 27 28 FORMAL MEETING – 7 p.m. 29 1. Ernest called the meeting to order at 7:00 pm. He led the Pledge of Allegiance and asked for a 30 moment of silence to remember our first responders, police, military, and all who protect us. 31 2. Ernest asked if anyone would be recording the meeting and if there were any public 32 comments about non-agenda items. There was no response. 33 3. The tracking log was checked and no need for a workshop meeting. 34 4. The minutes of the December 10, 2024 meeting were approved. 35 36 CHAIRMAN’S REPORT – 37 None 38 39 REORGANIZATION 40 Since this is the first meeting in 2025, Reorganization is necessary. 41 1. Mike nominated Ernest for Chairman. 42 Dan T. mentioned that in the Planning Commission Bylaws, Article IV, Section 5, Officers are elected for 43 a one-year term that commences in January and cannot serve more than two consecutive years in the same 44 office. So, he feels a motion has to be made to change that for this election since Ernest has already 45 served two years. Ernest made a motion to waive the two year requirement. John seconded the motion. 46 The motion passed by a vote of 4 to one. Dan T. was opposed. 47 Fred seconded Mike’s nomination of Ernest for Chairman. The motion passed unanimously. 48 2. Mike nominated John S. for Vice Chairman. Since John has held this office for 2 years, Ernest made a 49 motion to waive the two year requirement. John seconded the motion. The motion passed by a vote of 4 50 to one. Dan T. was opposed. 51 Ernest seconded Mike’s nomination of John S. for Vice Chairman. The motion passed unanimously. 52 Acknowledge Receipt of New Applications (initial Submission)- None 53

PC 4-22-25 draft 2

1 Subdivision and Land Development Applications - None 2 3 CONDITIONAL USES AND VARIANCES - None 4 5 ZONING HEARING BOARD VARIANCES - None 6 7 ORDINANCE AMENDMENTS - None 8 9 OLD BUSINESS -None 10 11 NEW BUSINESS – 12 1. 2015 Comprehensive Plan - The Township Comprehensive Plan has to be reviewed every 10 years. 13 Ernest suggested that everyone look for items that have been completed and can be removed. He asked 14 John H. for the BOS to tell the PC what kind of review they want. 15 John H. mentioned the TND (Town Center) with possible apartments above the shops. John S. pointed 16 out that the town center has come back. Dan T. feels that there is a theme to put more people in the 17 township, but residents don’t want that. They don’t want apartments above the shops. 18 Fred mentioned that he was on a committee for the 2015 Plan. The Town Center was discussed. The 19 Plan was reviewed by the Chester County Planning Commission. One thing that was done was the traffic 20 lights on Rt. 30 are timed better and they put LED lights in them which cuts the cost substantially. 21 Mike suggested that items that still need to be done should be updated first. 22 John S. commented that after the BOS gives their recommendation, the PC can update and then include 23 comments from the other ABCs. He mentioned that 10 years ago they formed a Task Force, and the 24 process was long. 25 Kelly spoke about the open lots in 2015 and how many remain and how many houses were built. 26 Ernest mentioned that Dan D. could not be at this meeting, but he emailed a list of comments to Ernest. 27 Ernest will write a letter from the PC and send it to John H. to present to the BOS. 28 29 LIAISON REPORTS 30 1. Board of Supervisors – John H. reported that it has been quiet. They are having only one meeting per 31 month. 32 33 ANY OTHER MATTER –None. 34 35 36 CORRESPONDENCE - None 37 38 39 ADJOURNMENT 40 There being no further business, John S. made a motion to adjourn the meeting. Dan T. seconded the 41 motion. The meeting was adjourned at 7:45 pm. 42 The next meeting will be held on Tuesday May 27, 2025 at 7 p.m. 43 44 Respectfully submitted, 45 46 47 48 49 Ruth Kiefer, Recording Secretary 50

Memorandum East Goshen Township 1580 Paoli Pike West Chester, PA 19380 610-692-7171 ext. 3103 kkrause@eastgoshen.org Date: June 18, 2025 To: East Goshen Township Planning Commission From: Kelly A. Krause, Zoning Officer Re: 1344 Morstein Road- 2 Lot Preliminary/Final Subdivision Plan _____________________________________________________________________________ The Township Staff has received a Preliminary/Final Subdivision Plan application for 1344 Morstein Road. The proposal is to develop the property into two (2) single family residential lots, accessed by private road. Background information:

• The existing lot contains one existing single-family dwelling on 5.5 acres with multiple structures. • The property was subdivided in 1998 from one lot into two lots, as they exist today. • A sketch plan was presented to the Planning Commission for the creation of two new lots (three parcels total). • A preliminary plan was reviewed by the Planning Commission on November 26, 2024, revised to create one new lot with the existing house to remain, shown on the plan as Lot 2. • The preliminary plan also proposed an easement on Lot 2 (existing house) for the construction and maintenance of the required stormwater facilities for the new house proposed on Lot 1. The proposed boundary line has been adjusted to accommodate the stormwater facility on Lot 1 without the need for an easement. Waivers Requested: §205-31.A to receive concurrent preliminary/final plan approval §205-52.A to not provide curbing on the proposed private street Comments: 1344 & 1344 A Morstein Road are currently accessed by a private “driveway”, as defined in §205-7 of the Subdivision and Land Development Ordinance, which is permitted access for a maximum of two residential parcels. Additionally, 1342 Morstein Road has access from both Morstein Road and the existing private drive. The existing driveway is proposed to become a private street, with a cartway width of 20 feet where 22 feet is the minimum required. §205-44E(2) allows the Board of Supervisors to reduce the minimum width to 20 feet if a cul-de-sac street is proposed and meets the following standards:

A cul-de-sac street is a minor street. Turnaround shall have a right-of-way diameter of 120 feet. Turnaround cartway paving width shall be 40 feet with a ten-foot radius center island. See Appendix and Subsection E(1) and (2). In lieu of a cul-de-sac, a 30’x 39.7’ turnaround access easement is proposed on Lot 1.

158 West Gay Street, Suite 300 T: 610-429-8907 www.pennoni.com West Chester, PA 19380 Page 1 of 7

June 17, 2025

EGOST 00141

Attn: Kelly Krause Director of Code Enforcement, Zoning Officer East Goshen Township 1580 Paoli Pike West Chester, PA 19380

RE: Thomas, 1344 Morstein Road Preliminary/Final Subdivision & Land Development Plan – 2nd Review

Dear Kelly:

As requested, we have reviewed the following information, prepared by Edward B. Walsh & Associates, Inc., regarding the referenced submission:

• “Preliminary/Final Subdivision Plans for 1344 Morstein Road” (nine sheets) dated April 11, 2024, last revised May 19, 2025;

• “Stormwater Management Report and Narrative for 1344 Morstein Road” dated August 20, 2024;

• Sewage Facilities Planning Module Application Mailer; and

• Application and supporting documents.

The applicant and owner, Kyong-Aie Thomas, proposes to subdivide UPI #53-1-11.1 (±5.5 acres) into two (2) lots. There is an existing house to remain (Lot 2) and a new single-family dwelling with associated driveways and stormwater (Lot 1). The site is located at the south side of the intersection of Morstein Road (T-387) and Amstel Way (T-531), within the R-2 Low Density Suburban Residential Zoning District. Both public water and sanitary sewer are proposed.

This was previously submitted as a sketch plan proposing three (3) lots; two (2) lots are now proposed.

The applicant is requesting the following two (2) waivers:

1. From §205-31.A to allow for a combined preliminary/final plan submission. 2. From §205-52.A to not require curbing on the proposed private street.

We offer the following comments:

ZONING

1. Please clarify if any accessory uses currently exist. (§240-9.E)

Resolved. The applicant has clarified that no accessory uses currently exist on the tract.

2. Flag lots shall meet the minimum lot width established in the applicable zoning district. (§240-23.B(2)(b)[2][a]) The flag portion of Lot 2 is only 50 feet wide rather than 60 feet; this appears to be an existing non-conformity. We will defer to the Zoning Officer.

Resolved. The flag portion of Lot 2 has been widened up to the private road right-of-way to be 60 feet wide.

EGOST00141 1344 Morstein Road Kelly Krause, Zoning Officer June 17, 2025 Page 2 of 7

U:\Accounts\EGOST\EGOST00141 - Thomas, 1344 Morstein Rd\DOCUMENTS\Pennoni 1344 Morstein Prelim Final Rev LTR 2025-06-17.docx

3. The applicant shall prove to the satisfaction of the Township that the proposed driveway will have adequate access for emergency vehicles. (§240-23.B(2)(b)[2][d]) Please see Fire Marshal’s October 17, 2024 memorandum.

Pending. The applicant has provided responses to the Fire Marshal’s memo. Defer to Township Fire Marshal.

4. It appears that the headwaters of a stream may exist at the rear of proposed Lots 1 and 2; in addition to locating the stream, the applicant should confirm via a qualified professional if wetlands exist in the area. (§240-25.D) Additionally, note the riparian buffer requirements of §195-15.T.

Resolved. The applicant has stated that the stream is not located on the tract. Additionally, a wetlands survey was performed and no wetlands exist within 100 feet of the area of disturbance. See General Note No. 18.

5. A Class II Historic resource is located at 1331 Greenhill Road, south of the proposed site. If there is any disturbance within 250 of the exterior walls of the resource(s), a Historical Resource Impact Study is required. (§240-38.10(A)(1))

Resolved. The applicant has stated that there will be no disturbance within 250 feet of the historic resources as there is no development proposed on Lot 2.

6. If the applicant is proposing restrictions, easements and/or covenants for the development, they shall be submitted to the Township for review prior to approval of the final development plans (§240-27.F); note:

a. At a minimum, this will be required for the proposed private road and stormwater management; b. We recommend documentation regarding the existing shared driveway be provided; c. Confirmation that the conversion to a private road is feasible is needed, as it appears two adjacent

parcels have access currently; and d. These adjacent parcels may need to co-applicants; further discussion with the Township Solicitor may

be required. Outstanding. The applicant has stated that the maintenance agreement for the private road will be submitted for review prior to final plan signing; defer to Township Solicitor.

SUBDIVISION AND LAND DEVELOPMENT

7. If the applicant intends to submit the plans as a joint preliminary/final plans submission, a waiver shall be requested from the requirement of preliminary plan approval.

Pending. This waiver request has been added to the Sheet 1.

8. There appear to be discrepancies between the metes and bounds of the submission and previous recorded plans; the project’s surveyor should review and confirm. (§205-30.C(2)(b))

Resolved. The general notes have been updated to confirm the boundary provided is consistent with the deed of record.

9. Submission should include full documentation of any proposed homeowners' association, covenants or other such proposed association and/or restrictions governing the subdivision and/or land development. (§205- 30.C(4)(i)) General Note No. 11 states that a Homeowners Association will be created and be responsible for the maintenance of the private road. Draft documents outlining responsibilities of the HOA should be submitted to the Township Solicitor for review. Outstanding. The applicant has stated that the HOA documents along with a maintenance agreement for the private road will be submitted for review; defer to Township Solicitor.

10. The net lot areas shall be added to the plans. (§205-33.B(19))

Resolved. The net lot areas for both lots have been indicated on the plans.

EGOST00141 1344 Morstein Road Kelly Krause, Zoning Officer June 17, 2025 Page 3 of 7

U:\Accounts\EGOST\EGOST00141 - Thomas, 1344 Morstein Rd\DOCUMENTS\Pennoni 1344 Morstein Prelim Final Rev LTR 2025-06-17.docx

11. PADEP sewage facilities planning module exemption approval shall be provided. (§205-33.B(22))

Pending. The applicant has stated that the sewage facilities planning exemption module has been submitted to DEP.

12. As part of a preliminary plan submission for any land development application where the tract proposed to be developed is located within 660 feet of the center line of any hazardous liquid pipeline or natural gas transmission pipeline, a Pipeline Awareness Study shall be submitted. (§205.40.1.A(1)) Note multiple pipelines existing in the area.

Resolved. The applicant has stated that per the County mapping, no pipelines are located within 660 feet of the tract.

13. All streets, whether public or private, shall be constructed in accordance with Township regulations. (§205- 42.G) The applicant is proposing to widen the existing shared driveway and has provided a detail. Further clarification may be required as to how the existing road will meet the detail requirements, such as depths of subbase, crown and similar, in addition to Fire Marshall requirements; a full reconstruction appears to be necessary.

Pending. The road construction detail provided shows full depth paving and crowning of the road. The applicant should clarify how this will be achieved with the existing roadway to remain.

14. No cul-de-sac is being proposed and the only turnaround area is located within an access easement on the driveway of Lot 1. (§205-50.B) Please see Fire Marshal’s October 17, 2024 memorandum.

Pending. The applicant has provided responses to the Fire Marshal’s memo. Defer to Township Fire Marshal.

15. The cartway width for a minor or local street shall be 22 feet; only 20 feet is proposed, though the Code has some provisions for reductions. (§205-45.G) Further discussion appears warranted.

Outstanding. The applicant is requesting that cartway width of 20 be accepted. The Code states that “at the sole discretion of the Township Supervisors, the right-of-way of a minor street may be reduced to 40 feet and the cartway width of a minor street may be reduced to 18 feet for properties of one acre or more.” However, this only applies to cul-de-sac streets. As there is no existing or proposed cul-de-sac at the end of the private road, a waiver may be warranted.

16. A minimum clear sight triangle of 75 feet (as measured from the center-line intersections of two streets) shall be provided at all intersections. The minimum clear sight triangle shall be increased to 100 feet if either street is a collector street. No physical obstruction, planting, berm or grade shall obscure vision above a height of two feet in such triangle. (§205-49.A) There appears to be existing vegetation in the area that may need to be removed; it is unclear if this is on the applicant’s or adjacent properties.

Resolved. The applicant has added the required clear sight triangle of 75 feet at the intersection of the private road and Morstein Road. General Note No. 16 on the Cover Sheet has also been added to note that all existing vegetation above two feet obstructing the clear sight at this intersection must be removed.

17. Curbs shall be required on all streets. (§205-52.A)

Pending. The applicant has requested a waiver from this requirement. The waiver request has been added to the Sheet 1.

STORMWATER

18. The plans indicate 0.924 acres of disturbed area; if the project disturbs more than one acre, a PADEP NPDES permit will be required.

Acknowledged.

EGOST00141 1344 Morstein Road Kelly Krause, Zoning Officer June 17, 2025 Page 4 of 7

U:\Accounts\EGOST\EGOST00141 - Thomas, 1344 Morstein Rd\DOCUMENTS\Pennoni 1344 Morstein Prelim Final Rev LTR 2025-06-17.docx

19. The peak flow rate of the post construction two-year, twenty-four-hour design storm shall be reduced to the predevelopment peak flow rate of one-year, twenty-four-hour duration precipitation, using the SCS Type II distribution; please revise the calculations using the SCS Type II distribution (§195-21.A).

Resolved. SCS Type II distribution calculations are now provided.

20. For regulated activities involving new development, for areas that are woods, predevelopment calculations shall assume ground cover of woods in good condition, and all other areas shall assume ground cover of meadow. Please clarify the ground cover assumptions utilized. (§195-23.D(1)).

Resolved. This item has been addressed.

21. The drainage area boundary indicated on the Pre-Developed and Post-Developed Drainage Area Plans should be revised. It appears that the bypass area does not correlate with the Type "M" inlet #2, however this inlet discharges to the bypass area. The drainage area boundary appears to follow the Limit of Disturbance, and not the actual flow based on existing and proposed contours.

Resolved. This item has been addressed.

22. Drainage area dividing line in the pre-construction, and post-construction conditions may need to be revised. It appears that the Bypass area does not correlate with the inlet located in the driveway. Further the drainage area boundary appears to follow the LOD, not the true flow conditions; typically, drainage area dividing lines are perpendicular to contours.

Resolved. This item has been addressed.

23. Additional topography is required for adjacent properties to confirm the drainage area boundaries, notably properties along the proposed driveway.

Resolved. This item has been addressed. Additional topography has been added to the plans

24. We recommend the grading around “End Section #1” be revised to create a swale to the proposed infiltration basin.

Resolved. This item has been addressed.

25. On the Post Construction Drainage Area Plan, it appears that the TC line is the same for the pre-construction condition. Post-construction Tc lines should follow post-construction layout, also it appears the flow arrows are indicated backwards. Bypass Tc and Post-construction to SWM Tc lines should be indicated separately.

Resolved. This item has been addressed.

26. Please clarify how the curve number was determined for the “Pre-development for volume controls” Hydrograph Report. The values listed in the composite calculations do not match with the information for grass and impervious covers.

Resolved. This item has been addressed.

27. Roof drain locations and discharge locations shall be indicated. ((§195-20.O).

Resolved. A note has been added to the plan.

28. Please clarify the purpose, extent and condition of the existing 18” RCP and 18” HDPE that are indicated on Lot 2. It is unclear if additional easements exist or may be necessary.

Resolved. The 18” RCP and 18” HDPE are existing pipes for an adjacent subdivision.

29. Please add the infiltration test location to the plan.

EGOST00141 1344 Morstein Road Kelly Krause, Zoning Officer June 17, 2025 Page 5 of 7

U:\Accounts\EGOST\EGOST00141 - Thomas, 1344 Morstein Rd\DOCUMENTS\Pennoni 1344 Morstein Prelim Final Rev LTR 2025-06-17.docx

Resolved. This item has been addressed.

30. Please provide basin input data to confirm the plan/details are consistent with the calculations.

Resolved. This item has been addressed.

SANITARY SEWER

31. Please clarify why the Sewage Facilities Planning Module (SFPM) is for 1.5 EDUs and the sewage flows are 400 gpd. The SFPM should be revised to utilize the Township’s standard flow rate of 225 gpd/EDU and the number of EDUs shall be whole numbers. Additionally, one lot is existing and already connected to the East Goshen sanitary sewer system. The SFPM should indicate that 1 EDU and a portion of the sewage flow is already existing.

Resolved. This item has been addressed.

32. Please clarify how the existing lot connects to the Township’s sanitary sewer system. The plan indicates a force main coming out of the existing building that abruptly ends at the southern property line without connecting to anything.

Resolved. This item has been addressed.

33. The proposed force main cannot connect to the existing force main. The sanitary sewer for the proposed lot must directly connect to the Township’s sanitary sewer system. Additionally, no grinder pump is proposed for this force main.

The proposed force main design has been revised, and a grinder pump is now proposed. However, the following design items must be addressed:

a. The new force main is proposed to be located within an existing sanitary sewer easement. However,

the existing easement agreement does not explicitly state that new work can occur within the easement. Additionally, the existing easement agreement is not for the new subdivided lot. The developer must acquire written approval, which may be a new easement, from the underlying property owner. The Municipal Authority Solicitor should provide direction on the form of the approval and whether it should be recorded. b. An easement is required from Lot 2 for the construction and maintenance of the proposed force main. c. The force main should be located within the middle of the easement. The force main is currently

proposed to be very close to the UPI 53-1-44 property line. Additionally, the force main is very close to the existing utility pole. d. The manhole in which the proposed force main connects to is incorrectly depicted as a terminal

manhole. It is our understanding that the existing sewer flows through the manhole from north to south towards Culbertson Drive. Pipes and elevations need to be surveyed and updated on the plans accordingly. e. Grinder pumps shall reduce domestic sewage to a fine slurry and shall have the characteristics to

produce flows of at least 10 gpm under all conditions (§188-33.B(3)). While the proposed grinder pump only discharges at 7.8 gpm at 80 psig, we are not opposed to the use of this grinder pump. Due to the length of the force main, the force main diameter would need to be increased to achieve the 10 gpm flow, which would extend the detention time and could create solids and odor issues. We are thereby not opposed to a waiver/relief of this requirement. f. Discharge piping connected to a Township manhole shall enter the manhole at the top of the bench. Internal drops are not permitted (§188-33.D(6)).

EGOST00141 1344 Morstein Road Kelly Krause, Zoning Officer June 17, 2025 Page 6 of 7

U:\Accounts\EGOST\EGOST00141 - Thomas, 1344 Morstein Rd\DOCUMENTS\Pennoni 1344 Morstein Prelim Final Rev LTR 2025-06-17.docx

g. We recommend that the force main be directionally drilled into or immediately adjacent to the manhole

to avoid additional road and landscaped island disturbance. Additionally, a note needs to be added to the plan that requires the Township to approve the contractor that will be making the connection to the manhole, a pre-construction meeting with the Township must occur at least 7 days prior to construction and the contractor must provide the Township with a certificate of insurance for any damage caused to the manhole. h. Discharge piping must be either PVC SDR 21 or HDPE DR11 (§188-33.D(3)). The various callouts and

details for the discharge piping are inconsistent in material type. i. The invert information for the proposed force main, existing force main, and existing manhole to be connected to is inconsistent throughout the plan set. j. Several trees/shrubs appear to be located on top of the proposed force main.

34. Sanitary sewer pipe (proposed and existing), grinder pump, and construction details shall be provided.

Sanitary sewer pipe, grinder pump, and construction details have been provided. However, details for trench restoration in lawn areas shall also be provided.

35. A grinder pump operation and maintenance agreement will be required.

Outstanding. The design consultant acknowledged an agreement will be provided.

GENERAL

36. A note should be added to the plans stating that the stop bar and stop sign shall be field located with the Township Traffic Engineer.

Resolved. This note has been added to the plans, see General Note No. 13.

37. The proposed stormwater for Lot 1 is partially located on Lot 2 via a proposed easement. There appears to be ample space for Lot 1 to be enlarged to encompass the entire stormwater basin to reduce the complications of such an arrangement.

Resolved. The lot lines for Lot 1 have been revised so that the entirety of the stormwater BMP is located within Lot 1.

38. We recommend all plan sheets be recorded.

Resolved. General Note No. 14 has been added to the plans stating all sheets must be recorded.

39. Please note additionally:

a. Fire Marshal - October 17, 2024 b. County Planning - Pending c. East Goshen Conservancy Board - Pending

EGOST00141 1344 Morstein Road Kelly Krause, Zoning Officer June 17, 2025 Page 7 of 7

U:\Accounts\EGOST\EGOST00141 - Thomas, 1344 Morstein Rd\DOCUMENTS\Pennoni 1344 Morstein Prelim Final Rev LTR 2025-06-17.docx

Should you have any further questions or comments, please contact the undersigned.

Sincerely, PENNONI ASSOCIATES INC.

Nathan M. Cline, PE Township Engineer

cc (via e-mail): Township Team Project Team

Memorandum East Goshen Township 1580 Paoli Pike West Chester, PA 19380 Voice: 610-692-7171 Fax: 610-692-8950 E-mail: dbrady@eastgoshen.org Date: June 17, 2025 To: Zoning Officer From: Duane J. Brady Sr., East Goshen Township Fire Marshal Re: 1344 Morstein Road Subdivision Plan Application Dear Zoning Officer, The Township Fire Marshal has reviewed the Revised Subdivision Plan dated May 19, 2025, for the creation of a new two lot Subdivision. The plan shows that the road will be a private road with one new lot and one existing lot. I provide following comments: All code information is from the International Fire Code 2018 Edition (IFC) and East Goshen Township Code Chapter 205 Subdivision and Land Development section 205-30 Preliminary plan requirements, Part C.3.D.

1. Private road (fire access road) shall be installed to carry a minimum of 75,000 pounds as required for a fire access road. IFC 2018 section 503.2.3 Surface. Resolved. 2. Private road (fire access road) shall be installed with a grade that does not exceed 10 percent in grade. 2018 section 503.2.7 Grade. Resolved. 3. Private road (fire access road) shall meet the required apparatus turning requirements. As required in the IFC 2018 section 503.2 Specifications. Resolved. 4. Private road (fire access road) the private road is required to have Fire Lane No Parking signs if the minimum of 20 feet width is installed. 2018 section 503.3 Marking. Pending. No Parking Sign needs to read Fire Lane No Parking. 5. Private road (fire access road) shall meet the required apparatus turning requirements. As required in the IFC 2018 section 503.2 Specifications. Resolved. 6. Driveway (fire access road) a driveway is considered a fire access road and shall be a minimum of twenty feet as required pre the IFC 2018 section 503.2. specifications. Resolved. 7. The driveway (fire access road) shall be installed to carry a minimum of 75,000 pounds as required for a fire access road. IFC 2018 section 503.2.3 Surface. Resolved. 8. The driveway (fire access road) shall be installed with a grade that does not exceed 10 percent in grade. 2018 section 503.2.7 Grade. Resolved.

9. The driveway (fire access road) shall meet the required apparatus dead ends requirements. 2018 section 503.2.5 Dead ends. Please provide a Fire Turck Pathway Plan showing the requirements will meet code. Resolved. 10. Fire hydrant, locations are not marked or located on the plans. Resolved. 11. Fire hydrants show existing locations of hydrants in the area and distance to new development. Resolved. 12. Fire hydrant will the new fire hydrant/s installed system be private or public. Resolved. No new fire hydrant is being installed. 13. Fire hydrants and fire flow rate must meet the IFC 2018 code requirements. Resolved. 14. Provide the size of the largest dwelling unit to calculate the required fire flow rate for the development. Resolved. 15. Provide the existing available fire flow rate to the development. Pending. Fire flow rate is required at building permit application. 16. East Goshen Township Code Chapter 205 Subdivision and Land Development section 205-30 Preliminary plan requirements, Part C.3.D. requires size and location of fire hydrants be shown on plans. Fire hydrants were not marked on plans. Resolved. 17. The existing driveway is a shared driveway with 1344 A Morstein Road. If an easement exists for the driveway, please provide a copy as this may affect this project. Resolved. Sincerely, Duane J. Brady Sr. Duane J. Brady Sr. East Goshen Township Fire Marshal

From: East Goshen Township To: East Goshen Township Planning Commission Conservancy Board 1580 Paoli Pike 1580 Paoli Pike West Chester, PA 19380 West Chester, PA 19380 Attn: Kelly Krause, Zoning Officer Dan Flynn, (Chair)

June 18, 2025 Re: 1344 Morstein Rd – 2 LotPreminimary/Final Subdivision Plan

Dear Kelly;

Per Planning Commission request, the Conservancy Board reviewed engineered drawings to 1338 Morstein Rd at the regular monthly meeting on 6/11/2025. Plans reviewed and discussed are as prepared by Edward B. Walsh & Associates, Inc., dated 4/11/24, Plotted 5/28/25, Sheets 1-10. A engineer from Walsh & Associates, Adam Brewer, was in attendanceto answer questions.

The East Goshen Conservancy Board (EGTCB) offers the following comments based on that review….

1. Plan shows existing landscape with trees to be removed (see EXISTING FEATURES PLAN, SHT 2) marked on the plan and species/trunk dia. Listed; There is concern about the number of trees bring removed, especially along the driveway. Regarding the trees along the new private road, it is understood that the drive width must be a minimum of 20’ per referenced fire code. Along with the proposed new native maple trees, an adequate number of understory shrubs should be added to insure full screening of the drive from existing residences and the new private road and provide sufficient asthetic appeal. The understory shrubs should be of a native variety.

2. The EGTCB requests that the township monitor the planting of the new trees and shrubs initially and in a year or so after planting to insure proper planting/maintenance methods are being followed.

3. It was verified by the project engineer that the HOA will maintain the private drive and associated trees and shrubs in proper condition, replace those that die off in perpetuity and East Goshen Township bears no responsibility for maintenance/removal/replacement of the tress/shrubs along the new private road.

4. Regarding the rainwater drainage system, the storm runoff on the property generally runs to the east side of the new residential property property then heads to the infiltration basin. The private road drain into two ‘M’ inlets, spills onto the south lawn then drains into the infiltration basin. The infiltration basin seeeps out onto the east side slopes. Plan notes state there are no waterways affected by this development. EGTCB had questions concerning the maintenance of the drainage system. The plan stipulates inspections of the drainage system, including the infiltration system by a registered engineer at designated time intervals. The project engineered confirmed the inspections and any resultant maintenance/repair work is the responsibilty of the home owner. The township’s responsibilty is limited to review of the homeowner’s engineer’s report and enforcement only. In the event the homeowner did not maintain the drainage system, the township would perform the required maintenance and be reimbursed for all costs by the homeowner (the easement for the infiltration basin clarifies this also?).

6. EGTCB had some questions about whether or not all the itmes listed on the plant schedule on Landscape Plan, page 6 of 10, are native Pennsylvania. Please verify all plantings are native species.

The following comments are based on a first hand observation of site conditions:

1a. From Morstein to the first driveway, the "trees" being removed are actually Japanese lace leaf maples which are dwarf trees.  The lace leaf maples are only about five feet tall and sit very close to the driveway.  Removal is clearly necessary and replacing with some native trees as we suggested will be an improvement.

2a. From the first driveway to where the new lot will be, there is a line of 19 beautiful fairly mature trees which seem to be American red maples.  While a measurement of the diameter of the trunks wasn’t taken, they appear to be larger than described to us.  These trees sit a little farther back from the driveway than the lace leaf maples and provide some screening for the neighboring lot.  It’s not known if there is any way to save these trees but doing so is desireable.  In lieu of saving these trees, at the very least, there should be a one for one replacement.

3a. Understanding that the requirement is for the private road to be 20 feet wide new private road, it looked like they might be able to make up some of that width on the side of the driveway that doesn't have any trees.  There isn't much room on that side but utilizing what is there might provide sufficient width to save the red maples on the other side.

4a.  With the addition of just one house, a 20 feet wide private road seems excessive especially when you see the property.  The setting of the property is very "bucolic" and a road that wide will definitely change the "feel" and, of course, require the removal of the trees. Twenty feet is wider than the street some folks live on elsewhere in the township. This is an observation and not one intended to interfere with the township firecode which, I assume, takes precedence.

Any questions, please feel free to contace me.

Regards,

Dan Flynn Chairman East Goshen Township Conservancy Board.

Memorandum East Goshen Township 1580 Paoli Pike West Chester, PA 19380 610-692-7171 ext. 3103 kkrause@eastgoshen.org Date: June 4, 2025 To: East Goshen Township Conservancy Board From: Kelly A. Krause, Zoning Officer Re: 1344 Morstein Road- 2 Lot Preliminary/Final Subdivision Plan _____________________________________________________________________________ A Preliminary/Final Subdivision Plan application for the property located at 1344 Morstein Road has been submitted to allow an existing 5.5 acre lot to be subdivided into two (2) single family residential lots, accessed by private road. The property is located within the R-2 Low Density Residential District (§240-9), which requires a minimum lot area of one (1) acre. The existing single-family dwelling will remain on Lot 2, and will contain 3.174 (net) acres. A new single-family dwelling is proposed on Lot 1, and will contain a lot area of 1.346 (net) acres. The site contains areas of Steep Slope (15% to 25% , and 25%+), most significantly located near the easterly boundary line of the tract, and concentrated on proposed Lot 1. No streams are located on the subject property, and no wetlands are located within 100 feet of the proposed earth disturbance. Forty- four (44) trees are proposed to be removed, and replaced with eleven (11) trees and twenty-two (22) shrubs. The applicant has requested waivers from the following sections of the East Goshen Township Code:

• §205-31.A to receive concurrent preliminary/final plan approval • §205-52.A to not provide curbing on the proposed private street In accordance with §205-32 of the EGT Subdivision and Land Development Ordinance, we request that the Conservancy Board review and provide comments on the proposed plan to be forwarded to the Planning Commission for consideration.

PRELIMINARY/FINAL TITLE PLAN - SUBDIVISION PLAN FOR 1344 MORSTEIN ROAD

Engineering subdivision title plan drawing for 1344 Morstein Road (UPI No. 53-1-11.1), East Goshen Township, Chester County, PA, showing Lot 1 (1.373 acres gross, 1.346 acres net) and Lot 2 (3.473 acres gross, 3.174 acres net), private road right-of-way off Morstein Road opposite Amstel Way, location map, legend, zoning data, impervious cover breakdown, sheet index, general notes, waiver requests, and certification blocks.

LEGEND

  • EXISTING FENCE
  • EXISTING SIGN
  • EXISTING CURB
  • EXISTING EDGE OF PAVING/DRIVEWAY
  • PROPOSED EDGE OF PAVING/DRIVEWAY
  • WIDENING OF EXISTING DRIVE
  • EXISTING BUILDING
  • PROPOSED BUILDING

ZONING DATA (R-2 ZONING DISTRICT)

RequirementREQUIREDLOT 1LOT 2
MINIMUM LOT AREA1 ACRE1.346 AC3.174 AC
MINIMUM LOT WIDTH150 FEET AT BUILDING LINE / 60 FEET AT STREET LINE290 FT / 60 FT274 FT / 50 FT (FLAG LOT)
MINIMUM FRONT YARD60 FEET / 60 FEET AVERAGE60 FT60 FT
MINIMUM SIDE YARD20 FEET20 FT20 FT
MINIMUM REAR YARD50 FEET50 FT50 FT
MAXIMUM COVERAGE25% BUILDINGS / 35% TOTAL2,446 SF, 4.17% / 5,384 SF, 9.18%2,800 SF, 2.02% / 11,807 SF, 8.54%

IMPERVIOUS COVER BREAKDOWN

FeatureLOT 1LOT 2
HOUSE2,446 SF2,800 SF
DRIVEWAY2,686 SF7,062 SF
ACCESSORY BUILDINGS-504 SF
SIDEWALK/PATIO252 SF1,441 SF
TOTAL5,384 SF11,807 SF

LOCATION MAP

SCALE: 1"=800'. Labels: WEST WHITELAND TOWNSHIP, EAST GOSHEN TOWNSHIP, WEST GOSHEN TOWNSHIP, ROUTE 202, MORSTEIN RD., MASTER WAY, GREAT OAK DR., PINEHURST RD., HIGHGATE RD., ALLEN LN., SITE, GREENHILL RD., JOSHUA DR., BOOT RD.

Plan Drawing Callouts and Adjoining Owners

  • MORSTEIN RD. POSTED SPEED LIMIT = 35 MPH, LEGAL RIGHT-OF-WAY 50 FT. R/W, AMSTEL WAY
  • REQUIRED SIGHT DISTANCE = 350', PROVIDED = 923'; REQUIRED SIGHT DISTANCE = 340', PROVIDED = 834'; 75' CLEAR SIGHT TRIANGLE
  • 24" SOLID WHITE LINE, R1-1 STOP SIGN, 50 FT WIDE RIGHT OF WAY, PRIVATE ROAD 20 FT WIDE, NO PARKING SIGN, END PRIVATE ROAD RIGHT OF WAY, TURN-AROUND ACCESS EASEMENT AREA=0.027 AC.
  • LOT 1: AREA: 1.373 ACRES (GROSS), 1.346 ACRES (NET), BUILDING SETBACK
  • LOT 2: AREA: 3.473 AC. (GROSS), 3.174 AC. (NET), 2 STORY SINGLE FAMILY DWELLING, 8' HIGH WIRE FENCE, GREENHOUSE, CHICKEN COOP, SHED, PROPOSED 20 FT WIDE SANITARY SEWER EASEMENT, EXISTING 20 FT WIDE SANITARY SEWER EASEMENT
  • N/L JOANN & GARY PETERS, D.B. 6255, PG. 2189, UPI 53-1-11.4
  • N/L AMY D. KOVACH, D.B. 8968, PG. 2002, UPI 53-1-11.2
  • N/L IAN REGINO, D.B. 9325, PG. 403, UPI 53-10-138
  • N/L LENA D. & GILFORD J. ROY, D.B. 10034, PG. 0371, UPI 53-1-12.1
  • N/L PATRICIA A. PICKARD & ROBERT J. PICKARD SR., D.B. 4895, PG. 279, UPI 53-1-40
  • N/L MAJA N. PATTON, D.B. 10579, PG. 2184, UPI 53-1-41
  • N/L GINA J. DADDAZIO & STEVEN P. DADDAZIO, D.B. 9207, PG. 169, UPI 53-1-42
  • N/L JESSICA E. STRAGHAN, D.B. 8308, PG. 526, UPI 53-1-43
  • N/L CAROLINE BARBARA TOMLINSON & ALBERT BRYAN TOMLINSON, D.B. 10760, PG. 360, UPI 53-1-44
  • N/L MARYELLEN & ROBERT VOEGEL, D.B. 4851, PG. 114, UPI 53-1-45
  • N/L CHRISTOPHER CARFAGNE & DEBORAH ANN CARFAGNE, D.B. 3927, PG. 382, UPI 53-1-10.1

GENERAL NOTES:

1. BOUNDARY, EXISTING FEATURES AND TOPOGRAPHIC INFORMATION IS FROM A FIELD SURVEY PERFORMED BY EDWARD B. WALSH & ASSOCIATES, INC. ON APRIL 11, 2024.

2. BOUNDARY SURVEY WAS BASED UPON DEEDS OF RECORD. A TITLE REPORT WAS NOT PROVIDED, THEREFORE, THE SURVEY MAY NOT DEPICT ALL RIGHTS, EASEMENTS, ETC. ATTACHED TO THE PROPERTY THAT A CURRENT AND COMPLETE TITLE REPORT MAY DISCLOSE.

3. OWNER OF RECORD: KYONG-AIE THOMAS

4. SITE ADDRESS: 1344 MORSTEIN RD., WEST CHESTER, PA 19380

5. RECORDING INFORMATION: DEED BOOK 10543, PAGE 119 RECORDED AT THE CHESTER COUNTY RECORDER OF DEEDS. BEING UPI 53-1-11.1 AT THE CHESTER COUNTY TAX BUREAU.

6. BEARING BASIS FOR THE SURVEY AS SHOWN ARE REFERENCED TO NAD 83, PA STATE PLANE COORDINATE SYSTEM, SOUTH ZONE AS DERIVED FROM GPS OBSERVATIONS. THE SURVEY WAS BASED UPON THE RECORD DEED RECORDED IN DEED BOOK 10543 PAGE 119 AND ADJUSTED TO THE LOCATIONS OF EVIDENCE FOUND IN THE FIELD. THE PROPERTY SHOWN HEREON IS THE SAME PROPERTY DESCRIBED IN SAID DEED.

7. VERTICAL DATUM - NAVD 88

8. LOT AREA = 240,226.21 SQ. FT. (5.515 ACRES)

9. UTILITY LOCATIONS SHOWN HEREON ARE BASE UPON VISIBLE EVIDENCE, SUPPLEMENTED WITH INFORMATION SHOWN ON UTILITY COMPANY PLANS. EDWARD B. WALSH & ASSOCIATES, INC. (EBWA) DOES NOT GUARANTEE THE ACCURACY OF THE LOCATIONS OF EXISTING SUBSURFACE UTILITY LINES, STRUCTURES, ETC. SHOWN ON THESE PLANS, NOR DOES EBWA GUARANTEE THAT ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC. ARE SHOWN.

10. THE PROPOSED LOT WILL CONNECT TO PUBLIC SANITARY SEWER AND WATER SUPPLY.

11. A HOMEOWNERS ASSOCIATION WILL BE CREATED AND WILL BE RESPONSIBLE FOR THE MAINTENANCE OF THE PRIVATE ROAD LOCATED IN THE 50 FT WIDE RIGHT OF WAY AREA.

12. THE EXISTING AND PROPOSED USES OF THE LOTS ARE RESIDENTIAL.

13. THE STOP BAR AND STOP SIGN SHALL BE FIELD LOCATED WITH THE TOWNSHIP ENGINEER.

14. ALL PLAN SHEETS MUST BE RECORDED.

15. AN NPDES PERMIT WILL BE REQUIRED IF SITE DISTURBANCE EXCEEDS ONE ACRE DURING CONSTRUCTION.

16. NO PHYSICAL OBSTRUCTION, PLANTING, BERM OR GRADE MAY OBSCURE VISION ABOVE A HEIGHT OF TWO FEET IN THE CLEAR SIGHT TRIANGLE. ALL EXISTING VEGETATION MUST BE REMOVED.

17. THE STORMWATER SYSTEM ON LOT 1 IS DESIGNED FOR 6,800 SF OF IMPERVIOUS AREA ON LOT 1.

18. THERE ARE NO STREAMS ON THE TRACT. EBWA WETLANDS SPECIALIST PERFORMED A SITE SURVEY AND CONCLUDED THERE ARE NO WETLANDS WITHIN 100 FEET OF THE PROPOSED DISTURBANCE.

19. THE PRIVATE ROAD RIGHT OF WAY WILL PROVIDE ACCESS AND UTILITY RIGHTS FOR EXISTING PARCELS 53-1-11.2 AND 53-10-138 IN ADDITION TO LOTS 1 AND 2 OF THIS SUBDIVISION.

20. IRON PINS SHALL BE SET AT PROPERTY CORNERS DENOTED WITH THE "●" SYMBOL.

SHEET INDEX

Sheet TitleSheet Number
TITLE PLAN1 OF 10
EXISTING FEATURES PLAN2 OF 10
CONSTRUCTION IMPROVEMENT PLAN3 OF 10
EROSION & SEDIMENTATION CONTROL PLAN4 OF 10
POST CONSTRUCTION STORMWATER MANAGEMENT PLAN5 OF 10
LANDSCAPE PLAN6 OF 10
PROFILE SHEET7 OF 10
DETAIL SHEET8-10 OF 10

SUBDIVISION & LAND DEVELOPMENT ORDINANCE WAIVER REQUESTS

1. SECTION 205-31.A: A WAIVER IS REQUESTED TO ALLOW A COMBINED PRELIMINARY AND FINAL REVIEW AND APPROVAL PROCESS.

2. SECTION 205-52.A: A WAIVER IS REQUESTED TO NOT REQUIRE CURBING ON THE PROPOSED PRIVATE STREET.

Property Owners Certification:

The landowner acknowledges that, per the provisions of the East Goshen Township Stormwater Management Ordinance, it is unlawful to modify, remove, fill, landscape, alter or impair the effectiveness of, or place any structure, other vegetation, yard waste, brush cuttings, or other waste or debris into any permanent stormwater management BMP or conveyance described in this O&M plan or to allow the BMP conveyance to exist in a condition which does not conform to this O&M plan, without written approval from the Township. The individual lot owner, his/her heirs, assigns or successors, shall be responsible for the perpetual maintenance of the said facilities. A blanket stormwater management easement is provided over the private the property in favor of East Goshen Township to allow the Township and its agent one perpetual access to the proposed stormwater facilities. The Township is granted the right, but not the duty, to access and conduct periodic inspections and to undertake other actions that may be necessary to enforce the requirements of the Township's Stormwater Management Ordinance or of any applicable O&M plan or O&M agreement. If the property owner, his/her heirs, assigns or successors fails in any way to maintain the said facilities or causes these facilities to be altered or removed, upon written notification by the Township, the defects shall promptly be corrected by property owner. Upon the owner's failure to correct the defect within the time specified by the Township, the owner, his/her heirs, assigns or successors do hereby authorize the Township and/or their contractor to enter upon the said property and cause the repair, maintenance, and/or correction to be made; a lien may be filed against the property for the cost of all corrections including applicable engineering and/or attorney's fees. The Township is under no obligation to take any action. All subsequent real estate transactions, the existence of these stormwater facilities and their maintenance responsibilities shall be disclosed to the new owners. Any revision to the approved SWM site plan shall be submitted to the Township along with an Erosion & Sedimentation Control Plan for review and approval.

SIGNATURE | DATE | NAME

ENGINEER CERTIFICATION:

I, ________________, ON THIS DATE _______________, HEREBY CERTIFY THAT TO THE BEST OF KNOWLEDGE THAT THE SWM SITE PLAN MEETS ALL DESIGN STANDARDS AND CRITERIA OF THE EAST GOSHEN TOWNSHIP ORDINANCE NO. 129-F "EAST GOSHEN TOWNSHIP STORMWATER MANAGEMENT ORDINANCE."

SIGNATURE | NAME

OWNER OF RECORD

KYONG-AIE THOMAS
1344 MORSTEIN RD.
WEST CHESTER, PA 19380
D.B. 10543 PG. 119

Certifications and Approvals

COMMONWEALTH OF PENNSYLVANIA COUNTY OF CHESTER: On the ___ day of ___, A.D. 20___ before me, the subscriber, a Notary Public of the Commonwealth of Pennsylvania, residing in ___ personally appeared ___ who acknowledged herself to be the owner of the real property as depicted hereon and that as such she executed the foregoing plan by signing her name ___; that she is the owner of the designated land, that all necessary approval of the plan has been obtained and is endorsed thereon and that the said he desires that the foregoing plan may be duly recorded. Notary Public / My Commission Expires:

REVIEWED by the Planning Commission of East Goshen Township, Chester County, Pa., this ___ day of ___, 20___. Chairman, Vice-Chairman, Member.

APPROVED by the Board of Supervisors of East Goshen Township, Chester County, Pa., this ___ day of ___, 20___. Chairman, Vice-Chairman, Supervisor.

REVIEWED by the Chester County Planning Commission this ___ day of ___, 20___. Secretary.

APPROVED by the East Goshen Township Engineer: Date.

Recorded in the Office of the Recorder of Deeds of Chester County at West Chester, Pennsylvania in Plan book ___ Page ___ on the ___ day of ___, 20___. (Deputy) Recorder of Deeds.

SURVEYOR'S CERTIFICATION: I, ___ hereby certify that the boundary shown hereon was calculated by me and that the plan and survey accuracy is in conformance with all East Goshen Township Ordinances. Signature / Date.

ACT 287 PENNSYLVANIA ONE CALL NOTIFICATION

Preliminary Serial No. 20241000545, 4/9/24 date. *Final Serial No. ___ date ___. UNDERGROUND UTILITY LINE PROTECTION LAW (ACT 287, AS AMENDED). E. B. Walsh & Associates, Inc. (EBWA) does not guarantee the accuracy of the locations for existing subsurface utility lines, structures, etc. shown on the plans, nor does EBWA guarantee that all subsurface utility lines, structures, etc. are shown. Contractor shall verify the location and elevations of all subsurface utility lines, structures, etc. before the start of work, by calling the Pennsylvania One Call System at 1-800-242-1776. *If construction does not occur within 90-days of the above final one-call notification, the project owner is required to make notification to Pa One Call not less than 10 nor more than 90 business days before initiating construction, as per Section 4 of Act 287. UTILITIES NOTIFIED: COMCAST PLMG, EAST GOSHEN TOWNSHIP, AQUA PA DESIGN, COMCAST CABLE, PECO EXELON CO., TRANSCO GAS PL, VERIZON EASTERN.

Title Block

UPI NO. 53-1-11.1 | GRAPHIC SCALE 1"=50' (0, 50, 100, 150) | Revision 1: 5-19-25 REVISED PER TOWNSHIP ENGR REVIEW LETTER DATED 11-22-24 | SUBDIVISION PLAN FOR 1344 MORSTEIN ROAD, EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA. | Edward B. Walsh & Associates, Inc. CIVIL ENGINEERS & SURVEYORS, Whiteland Business Park, 855 Springdale Drive, Suite 202, Exton, Pennsylvania 19341, Phone: 610-903-0060, Fax: 610-903-0080 | Project- 5019 | Date- 4/11/24 | Scale- 1" = 50' | Drawn- D.B. | Checked- A.J.B. | Sheet- 1 OF 10 | Plotted: 5/28/2025 | File: F:\EB\5019\FPS\5019-B.pro

PRELIMINARY/FINAL EXISTING FEATURES PLAN - SUBDIVISION PLAN FOR 1344 MORSTEIN ROAD

Engineering existing features plan drawing (Sheet 2 of 10) for 1344 Morstein Road (UPI No. 53-1-11.1), East Goshen Township, Chester County, PA, showing existing topography, contours, soil boundaries, trees to remain and to be removed, existing structures, utilities, and adjoining parcels.

SOILS CLASSIFICATION

  • MaB - MANOR LOAM, 3 TO 8 PERCENT SLOPES, HYDROLOGIC SOIL GROUP B
  • MaC - MANOR LOAM, 8 TO 15 PERCENT SLOPES, HYDROLOGIC SOIL GROUP B
  • MaD - MANOR LOAM, 15 TO 25 PERCENT SLOPES, HYDROLOGIC SOIL GROUP B
  • UugB - URBAN LAND - UDORTHENTS, SHIST AND GNEISS COMPLEX, 0 TO 8 PERCENT SLOPES, HYDROLOGIC GROUP C

LOCATION MAP

SCALE: 1"=800'. Labels: WEST WHITELAND TOWNSHIP, EAST GOSHEN TOWNSHIP, WEST GOSHEN TOWNSHIP, ROUTE 202, MORSTEIN RD., MASTER WAY, GREAT OAK DR., PINEHURST RD., HIGHGATE RD., ALLEN LN., SITE, GREENHILL RD., JOSHUA DR., BOOT RD.

LEGEND

  • 430 - EXISTING INDEX CONTOUR
  • EXISTING INTERIOR CONTOUR
  • W - EXISTING WATER SERVICE
  • WV - WATER VALVE
  • S - EXISTING SANITARY SEWER PIPE
  • FM - EXISTING FORCE MAIN PIPE
  • EXISTING SANITARY MANHOLE
  • G - EXISTING GAS SERVICE
  • E - EXISTING ELECTRIC SERVICE
  • EXISTING UTILITY POLE
  • SOILS BOUNDARY LINE
  • X - EXISTING FENCE
  • STEEP SLOPES 15-25%
  • STEEP SLOPES 25%+
  • EXISTING SIGN
  • EXISTING CURB
  • EXISTING EDGE OF PAVING/DRIVEWAY
  • EXISTING CONCRETE
  • EXISTING BUILDING
  • EXISTING DECIDUOUS TREE
  • EXISTING EVERGREEN TREE
  • EXISTING DECIDUOUS TREE TO BE REMOVED
  • EXISTING EVERGREEN TREE TO BE REMOVED

Plan Callouts and Adjoining Owners

  • MORSTEIN RD. POSTED SPEED LIMIT = 35 MPH, LEGAL RIGHT-OF-WAY 50 FT. R/W, AMSTEL WAY
  • 1 STORY FRAME SUMMER HOUSE TO BE REMOVED, INFILTRATION TEST PIT, 2 STORY SINGLE FAMILY DWELLING, LILLY POND, WOOD BRIDGE, WATER FEATURE, GREENHOUSE, CHICKEN COOP, SHED, EXISTING 20 FT WIDE SANITARY SEWER EASEMENT
  • N/L JOANN & GARY PETERS, D.B. 6255, PG. 2189, UPI 53-1-11.4
  • N/L AMY D. KOVACH, D.B. 8968, PG. 2002, UPI 53-1-11.2
  • N/L IAN REGINO, D.B. 9325, PG. 403, UPI 53-10-138
  • N/L LENA D. & GILFORD J. ROY, D.B. 10034, PG. 0371, UPI 53-1-12.1
  • N/L PATRICIA A. PICKARD & ROBERT J. PICKARD SR., D.B. 4895, PG. 279, UPI 53-1-40
  • N/L MAJA N. PATTON, D.B. 10579, PG. 2184, UPI 53-1-41
  • N/L GINA J. DADDAZIO & STEVEN P. DADDAZIO, D.B. 9207, PG. 169, UPI 53-1-42
  • N/L JESSICA E. STRAGHAN, D.B. 8308, PG. 526, UPI 53-1-43
  • N/L CAROLINE BARBARA TOMLINSON & ALBERT BRYAN TOMLINSON, D.B. 10760, PG. 360, UPI 53-1-44
  • N/L MARYELLEN & ROBERT VOEGEL, D.B. 4851, PG. 114, UPI 53-1-45
  • N/L CHRISTOPHER CARFAGNE & DEBORAH ANN CARFAGNE, D.B. 3927, PG. 382, UPI 53-1-10.1

ACT 287 PENNSYLVANIA ONE CALL NOTIFICATION

Preliminary Serial No. 20241000545, 4/9/24 date. UNDERGROUND UTILITY LINE PROTECTION LAW (ACT 287, AS AMENDED). Pennsylvania One Call System 1-800-242-1776. UTILITIES NOTIFIED: COMCAST PLMG, EAST GOSHEN TOWNSHIP, AQUA PA DESIGN, COMCAST CABLE, PECO EXELON CO., TRANSCO GAS PL, VERIZON EASTERN.

Title Block

UPI NO. 53-1-11.1 | GRAPHIC SCALE 1"=50' (0, 50, 100, 150) | Revision 1: 5-19-25 REVISED PER TOWNSHIP ENGR REVIEW LETTER DATED 11-22-24 | SUBDIVISION PLAN FOR 1344 MORSTEIN ROAD, EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA. | Edward B. Walsh & Associates, Inc. CIVIL ENGINEERS & SURVEYORS, Whiteland Business Park, 855 Springdale Drive, Suite 202, Exton, Pennsylvania 19341, Phone: 610-903-0060, Fax: 610-903-0080 | Project- 5019 | Date- 4/11/24 | Scale- 1" = 50' | Drawn- D.B. | Checked- A.J.B. | Sheet- 2 OF 10 | Plotted: 5/28/2025 | File: F:\EB\5019\FPS\5019-B.pro

PRELIMINARY/FINAL CONSTRUCTION IMPROVEMENT PLAN - SUBDIVISION PLAN FOR 1344 MORSTEIN ROAD

Engineering construction improvement plan drawing (Sheet 3 of 10) for 1344 Morstein Road (UPI No. 53-1-11.1), East Goshen Township, Chester County, PA, showing proposed grading, house and driveway on Lot 1, infiltration basin, storm and sanitary sewer connections, directional drilling path, and utility connections.

SOILS CLASSIFICATION

  • MaB - MANOR LOAM, 3 TO 8 PERCENT SLOPES, HYDROLOGIC SOIL GROUP B
  • MaC - MANOR LOAM, 8 TO 15 PERCENT SLOPES, HYDROLOGIC SOIL GROUP B
  • MaD - MANOR LOAM, 15 TO 25 PERCENT SLOPES, HYDROLOGIC SOIL GROUP B
  • UugB - URBAN LAND - UDORTHENTS, SHIST AND GNEISS COMPLEX, 0 TO 8 PERCENT SLOPES, HYDROLOGIC GROUP C

LOCATION MAP

SCALE: 1"=800'. Labels: WEST WHITELAND TOWNSHIP, EAST GOSHEN TOWNSHIP, WEST GOSHEN TOWNSHIP, ROUTE 202, MORSTEIN RD., MASTER WAY, GREAT OAK DR., PINEHURST RD., HIGHGATE RD., ALLEN LN., SITE, GREENHILL RD., JOSHUA DR., BOOT RD.

LEGEND

  • 430 - EXISTING INDEX CONTOUR
  • EXISTING INTERIOR CONTOUR
  • 432 - PROPOSED CONTOUR
  • +545.65 - PROPOSED SPOT ELEVATION
  • PROPOSED INLET
  • PROPOSED STORM SEWER PIPE
  • PROPOSED FLARED END SECTION
  • W - EXISTING WATER SERVICE
  • W - PROPOSED WATER SERVICE
  • WV - WATER VALVE
  • S - EXISTING SANITARY SEWER PIPE
  • FM - EXISTING FORCE MAIN PIPE
  • FM - PROPOSED FORCE MAIN PIPE
  • EXISTING SANITARY MANHOLE
  • G - EXISTING GAS SERVICE
  • E - EXISTING ELECTRIC SERVICE
  • EXISTING UTILITY POLE
  • SOILS BOUNDARY LINE
  • X - EXISTING FENCE
  • STEEP SLOPES 15-25%
  • STEEP SLOPES 25%+
  • EXISTING SIGN
  • EXISTING CURB
  • EXISTING EDGE OF PAVING/DRIVEWAY
  • PROPOSED EDGE OF PAVING/DRIVEWAY
  • EXISTING CONCRETE
  • PROPOSED CONCRETE
  • EXISTING BUILDING
  • EXISTING DECIDUOUS TREE
  • EXISTING EVERGREEN TREE

Plan Callouts

  • LOT 1: BUILDING SETBACK, FF=564.00 PROP., BSMT=555.00 PROP., GAR=562.50 PROP., 6" RISER/CLEANOUT (TYP), 6" PVC ROOF DRAIN MIN. SLOPE 1%, E-ONE GRINDER PUMP, 2 LF OF R-3 RIP RAP, INV. 556.40, INV. OUT 557.08
  • TYPE "M" INLET #1, TYPE "M" INLET #2, END SECTION #1, INV. IN 555.90, R-3 RIP RAP
  • INFILTRATION BASIN, INFILTRATION TEST PIT, TOP OF BERM ELEV. 554.30, 551.00, EMERGENCY SPILLWAY
  • PIPE INSTALLATION BY DIRECTIONAL DRILLING, POINT OF INTEREST, SAN. MH RIM 567.83, INV. (IN) 555.93, INV. (OUT) 555.75, TOP 554.68 (3" PVC), WHITE PAINT MARKS, ROLL CURB, MOUNTABLE CURB, MULCH, ASPHALT
  • SEE DETAIL FOR CONNECTION TO EXISTING MANHOLE, PRIVATE ROAD 20 FT WIDE, 50 FT WIDE RIGHT OF WAY, MORSTEIN RD. POSTED SPEED LIMIT = 35 MPH, AMSTEL WAY
  • LOT 2: 2 STORY SINGLE FAMILY DWELLING, EXISTING 20 FT WIDE SANITARY SEWER EASEMENT

ACT 287 PENNSYLVANIA ONE CALL NOTIFICATION

Preliminary Serial No. 20241000545, 4/9/24 date. UNDERGROUND UTILITY LINE PROTECTION LAW (ACT 287, AS AMENDED). Pennsylvania One Call System 1-800-242-1776. UTILITIES NOTIFIED: COMCAST PLMG, EAST GOSHEN TOWNSHIP, AQUA PA DESIGN, COMCAST CABLE, PECO EXELON CO., TRANSCO GAS PL, VERIZON EASTERN.

Title Block

UPI NO. 53-1-11.1 | GRAPHIC SCALE 1"=50' (0, 50, 100, 150) | Revision 1: 5-19-25 REVISED PER TOWNSHIP ENGR REVIEW LETTER DATED 11-22-24 | SUBDIVISION PLAN FOR 1344 MORSTEIN ROAD, EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA. | Edward B. Walsh & Associates, Inc. CIVIL ENGINEERS & SURVEYORS, Whiteland Business Park, 855 Springdale Drive, Suite 202, Exton, Pennsylvania 19341, Phone: 610-903-0060, Fax: 610-903-0080 | Project- 5019 | Date- 4/11/24 | Scale- 1" = 50' | Drawn- D.B. | Checked- A.J.B. | Sheet- 3 OF 10 | Plotted: 5/28/2025 | File: F:\EB\5019\FPS\5019-B.pro

PRELIMINARY/FINAL EROSION & SEDIMENTATION CONTROL PLAN - SUBDIVISION PLAN FOR 1344 MORSTEIN ROAD

Engineering erosion and sedimentation control plan drawing (Sheet 4 of 10) for 1344 Morstein Road (UPI No. 53-1-11.1), East Goshen Township, Chester County, PA, showing limit of disturbance (0.926 acres), filter socks, rock construction entrance, topsoil stockpile, concrete washout, construction sequence, and E&S notes.

SOILS CLASSIFICATION

  • MaB - MANOR LOAM, 3 TO 8 PERCENT SLOPES, HYDROLOGIC SOIL GROUP B
  • MaC - MANOR LOAM, 8 TO 15 PERCENT SLOPES, HYDROLOGIC SOIL GROUP B
  • MaD - MANOR LOAM, 15 TO 25 PERCENT SLOPES, HYDROLOGIC SOIL GROUP B
  • UugB - URBAN LAND - UDORTHENTS, SHIST AND GNEISS COMPLEX, 0 TO 8 PERCENT SLOPES, HYDROLOGIC GROUP C

LOCATION MAP

SCALE: 1"=800'. Labels: WEST WHITELAND TOWNSHIP, EAST GOSHEN TOWNSHIP, WEST GOSHEN TOWNSHIP, ROUTE 202, MORSTEIN RD., MASTER WAY, GREAT OAK DR., PINEHURST RD., HIGHGATE RD., ALLEN LN., SITE, GREENHILL RD., JOSHUA DR., BOOT RD.

LEGEND

  • 430 - EXISTING INDEX CONTOUR
  • EXISTING INTERIOR CONTOUR
  • 432 - PROPOSED CONTOUR
  • +545.65 - PROPOSED SPOT ELEVATION
  • PROPOSED INLET
  • PROPOSED STORM SEWER PIPE
  • PROPOSED FLARED END SECTION
  • W - EXISTING WATER SERVICE
  • W - PROPOSED WATER SERVICE
  • WV - WATER VALVE
  • S - EXISTING SANITARY SEWER PIPE
  • FM - EXISTING FORCE MAIN PIPE
  • FM - PROPOSED FORCE MAIN PIPE
  • EXISTING SANITARY MANHOLE
  • G - EXISTING GAS SERVICE
  • E - EXISTING ELECTRIC SERVICE
  • EXISTING UTILITY POLE
  • SOILS BOUNDARY LINE
  • X - EXISTING FENCE
  • STEEP SLOPES 15-25%
  • STEEP SLOPES 25%+
  • EXISTING SIGN
  • EXISTING CURB
  • EXISTING EDGE OF PAVING/DRIVEWAY
  • PROPOSED EDGE OF PAVING/DRIVEWAY
  • EXISTING CONCRETE
  • PROPOSED CONCRETE
  • EXISTING BUILDING
  • EXISTING DECIDUOUS TREE
  • EXISTING EVERGREEN TREE

EROSION & SEDIMENTATION CONTROL LEGEND

  • LIMIT OF DISTURBANCE
  • FS - FILTER SOCK
  • X - TEMPORARY ORANGE CONSTRUCTION FENCE
  • TS - TOPSOIL STOCKPILE
  • RCE - ROCK CONSTR. ENTRANCE
  • EROSION CONTROL BLANKET, NORTH AMERICAN GREEN C125 OR APPROVED EQUAL

CONSTRUCTION SEQUENCE

1. LIMIT OF DISTURBANCE IS TO BE FIELD DELINEATED PRIOR TO START OF ANY EARTH MOVING ACTIVITIES. THE LIMIT OF DISTURBANCE SHALL BE DELINEATED WITH ROPE AND STAKE OR ORANGE CONSTRUCTION FENCE. NO DISTURBANCE BEYOND THE STAKED LIMIT OF DISTURBANCE IS ALLOWED.

2. INSTALL STONE CONSTRUCTION ENTRANCE.

3. INSTALL FILTER SOCK AND ORANGE CONSTRUCTION FENCE AS SHOWN. ANY COMPACTION OF STORMWATER FACILITIES MUST BE AVOIDED.

4. PERFORM CLEARING IN AREA TO BE DISTURBED. STRIP TOPSOIL AND STOCKPILE WHERE SHOWN. INSTALL CONCRETE WASHOUT.

5. GRADE DRIVEWAY AND LOT. NOTE DISTURBANCE OF STORMWATER SWM MUST BE AVOIDED UNTIL IT IS INSTALLED. INSTALL UTILITIES TO SERVICE THE RESIDENCE.

6. INSTALL STONE BASE COURSE IN DRIVEWAY.

7. BEGIN HOUSE CONSTRUCTION.

8. INSTALL WATER SERVICE AND SANITARY SEWER SERVICE PIPING.

9. FINE GRADE AND SEED AND MULCH.

10. EXCAVATE AND CONSTRUCT STORMWATER SWM PER DETAIL. INSTALL EROSION CONTROL BLANKET IN SPILLWAY.

11. INSTALL INLET AND PIPING.

12. FINISH PAVE DRIVEWAY.

13. REMOVE ANY SEDIMENT IN THE BOTTOM OF SWM AND INSTALL AMENDED SOILS. STABILIZE, SEED AND MULCH WITH RAIN GARDEN SEED MIX.

14. REMOVE FILTER SOCK WHEN GRADED AREAS HAVE STABILIZED TO 70% DENSITY.

NOTE:

1. NO WORK IS PERMITTED TO TAKE PLACE UNTIL ALL EROSION AND SEDIMENTATION PROTECTION CONTROL MEASURES HAVE BEEN SATISFACTORILY INSTALLED.

2. EXCAVATION SHALL BE PERFORMED WITH EQUIPMENT THAT WILL NOT COMPACT THE BOTTOM OF THE BED. EQUIPMENT SHALL NOT BE ALLOWED ON EXCAVATED AREAS OF THE SEEPAGE BEDS AT ANY TIME DURING ITS CONSTRUCTION.

GENERAL NOTES

1. CONSTRUCTION SHALL IMMEDIATELY CEASE IF THE EARTH DISTURBANCE AREA EXCEEDS 1 ACRE AND NOT RESUME UNTIL A NPDES PERMIT OR APPROVAL OF A CORRECTIVE ACTION PLAN IS OBTAINED.

2. "DURING SITE CONSTRUCTION, ALL INFILTRATION PRACTICE COMPONENTS SHALL BE PROTECTED FROM COMPACTION DUE TO HEAVY EQUIPMENT OPERATION OR STORAGE OF FILL OR CONSTRUCTION MATERIAL. INFILTRATION AREAS SHALL BE REMEDIATED TO RESTORE SOIL COMPOSITION AND POROSITY. ADEQUATE DOCUMENTATION TO THIS EFFECT SHALL BE SUBMITTED TO THE MUNICIPAL ENGINEER FOR REVIEW. ALL AREAS DESIGNATED FOR INFILTRATION SHALL NOT RECEIVE RUNOFF UNTIL THE CONTRIBUTORY DRAINAGE AREA HAS ACHIEVED FINAL STABILIZATION."

DISTURBED AREA = 0.926 ACRES

ACT 287 PENNSYLVANIA ONE CALL NOTIFICATION

Preliminary Serial No. 20241000545, 4/9/24 date. UNDERGROUND UTILITY LINE PROTECTION LAW (ACT 287, AS AMENDED). Pennsylvania One Call System 1-800-242-1776. UTILITIES NOTIFIED: COMCAST PLMG, EAST GOSHEN TOWNSHIP, AQUA PA DESIGN, COMCAST CABLE, PECO EXELON CO., TRANSCO GAS PL, VERIZON EASTERN.

Title Block

UPI NO. 53-1-11.1 | GRAPHIC SCALE 1"=50' (0, 50, 100, 150) | Revision 1: 5-19-25 REVISED PER TOWNSHIP ENGR REVIEW LETTER DATED 11-22-24 | SUBDIVISION PLAN FOR 1344 MORSTEIN ROAD, EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA. | Edward B. Walsh & Associates, Inc. CIVIL ENGINEERS & SURVEYORS, Whiteland Business Park, 855 Springdale Drive, Suite 202, Exton, Pennsylvania 19341, Phone: 610-903-0060, Fax: 610-903-0080 | Project- 5019 | Date- 4/11/24 | Scale- 1" = 50' | Drawn- D.B. | Checked- A.J.B. | Sheet- 4 OF 10 | Plotted: 5/28/2025 | File: F:\EB\5019\FPS\5019-B.pro

PRELIMINARY/FINAL POST CONSTRUCTION STORMWATER MANAGEMENT PLAN - SUBDIVISION PLAN FOR 1344 MORSTEIN ROAD

Engineering post-construction stormwater management plan drawing (Sheet 5 of 10) for 1344 Morstein Road (UPI No. 53-1-11.1), East Goshen Township, Chester County, PA, showing stormwater retention/infiltration basin, roof drains, inlets, maintenance notes, and East Goshen O&M notes.

SOILS CLASSIFICATION

  • MaB - MANOR LOAM, 3 TO 8 PERCENT SLOPES, HYDROLOGIC SOIL GROUP B
  • MaC - MANOR LOAM, 8 TO 15 PERCENT SLOPES, HYDROLOGIC SOIL GROUP B
  • MaD - MANOR LOAM, 15 TO 25 PERCENT SLOPES, HYDROLOGIC SOIL GROUP B
  • UugB - URBAN LAND - UDORTHENTS, SHIST AND GNEISS COMPLEX, 0 TO 8 PERCENT SLOPES, HYDROLOGIC GROUP C

LOCATION MAP

SCALE: 1"=800'. Labels: WEST WHITELAND TOWNSHIP, EAST GOSHEN TOWNSHIP, WEST GOSHEN TOWNSHIP, ROUTE 202, MORSTEIN RD., MASTER WAY, GREAT OAK DR., PINEHURST RD., HIGHGATE RD., ALLEN LN., SITE, GREENHILL RD., JOSHUA DR., BOOT RD.

LEGEND

  • 430 - EXISTING INDEX CONTOUR
  • EXISTING INTERIOR CONTOUR
  • 432 - PROPOSED CONTOUR
  • +545.65 - PROPOSED SPOT ELEVATION
  • PROPOSED INLET
  • PROPOSED STORM SEWER PIPE
  • PROPOSED FLARED END SECTION
  • W - EXISTING WATER SERVICE
  • W - PROPOSED WATER SERVICE
  • WV - WATER VALVE
  • S - EXISTING SANITARY SEWER PIPE
  • FM - EXISTING FORCE MAIN PIPE
  • FM - PROPOSED FORCE MAIN PIPE
  • EXISTING SANITARY MANHOLE
  • G - EXISTING GAS SERVICE
  • E - EXISTING ELECTRIC SERVICE
  • EXISTING UTILITY POLE
  • SOILS BOUNDARY LINE
  • X - EXISTING FENCE
  • STEEP SLOPES 15-25%
  • STEEP SLOPES 25%+
  • EXISTING SIGN
  • EXISTING CURB
  • EXISTING EDGE OF PAVING/DRIVEWAY
  • PROPOSED EDGE OF PAVING/DRIVEWAY
  • EXISTING CONCRETE
  • PROPOSED CONCRETE
  • EXISTING BUILDING
  • EXISTING DECIDUOUS TREE
  • EXISTING EVERGREEN TREE
  • LIMIT OF DISTURBANCE

POST CONSTRUCTION RETENTION AREA AND STORMWATER FACILITIES MAINTENANCE NOTES

1. Regular removal of litter and debris within the property shall be performed. Stormwater facilities shall be inspected quarterly and any trash, debris, sediment, etc., shall be removed and properly disposed of.

2. Observations shall be made to determine the length of time needed for retained water to infiltrate into the soil after a storm event. The observations shall be made by reading the water level in the inlet box(es) of the underground system several times over a period of two (2) days after a large storm event. The first of these observations shall provide a record of how well the system is working when comparing future observations. Observations shall be made twice the first year and yearly thereafter.

3. Stormwater detention and retention basins or facilities shall be inspected by, or under the direction of, a registered professional engineer licensed in the Commonwealth of Pennsylvania on behalf of the landowner or responsible entity (including the Township Engineer for dedicated facilities) on the following basis:

  • a. Annually for the first five (5) years.
  • b. Once every three (3) years thereafter.
  • c. During or immediately after the cessation of a 100-year or greater storm event.

The professional engineer conducting the inspection shall be required to submit a written report to the Township within one (1) month following completion of the inspection. The report will present documentation and include pictures regarding the condition of the facility and recommend necessary repairs, if needed. Any needed repairs shall be implemented by the owner within one (1) month of the report issuance date.

4. The stormwater management facilities shown on these plans, including storm inlets, storm drain pipes, underground detention/retention systems, and roof drain connections, are permanent and are not to be removed. The individual lot owner, its successor or assigns shall assume the responsibility for perpetual maintenance of the said facilities. If the lot owner, his successor or assigns, fails in any way to maintain the said facilities or causes the facilities to be altered or removed, upon written notification by the municipality, the defects shall be promptly corrected at the owner's expense. Upon the owner's failure to correct the defect within the time specified by the municipality, the owner, his successor or assigns do hereby authorize the municipality or their agent to enter the property and cause the repairs, maintenance and/or corrections to be made. A lien may be filed against the property for all costs of all corrections, including applicable engineering and/or attorney fees, although the municipality is under no obligation to take action. The permission granted herein shall constitute an access easement for maintenance purposes should same be necessary by the municipality in the sole opinion of the municipality. This maintenance responsibility shall be added into the deed.

5. All inflow and outflow points to the individual on-lot systems should be kept clear of leaves and other debris. Any leaves or debris will negatively impact the performance of these systems. All downspouts and overflow pipes should be kept in good working order.

EAST GOSHEN O&M NOTES

1. THE PERSON OR ENTITY RESPONSIBLE FOR THE OPERATION AND MAINTENANCE OF A BMP OR CONVEYANCE SHALL MAKE RECORDS OF THE INSTALLATION AND OF ALL MAINTENANCE AND REPAIRS, AND SHALL RETAIN THE RECORDS FOR AT LEAST 3 YEARS. A COPY OF THESES RECORDS SHALL BE SUBMITTED TO THE TOWNSHIP

2. UPON FINAL INSPECTION, THE MUNICIPALITY SHALL INFORM THE PERSON RESPONSIBLE FOR THE OPERATION AND MAINTENANCE WHETHER THE SUBMISSION OF PERIODIC (ANNUAL OR OTHER FREQUENCY) INSPECTIONS AND MAINTENANCE REPORTS WILL BE REQUIRED.

3. THE OWNER OF EACH BMP AND CONVEYANCE SHALL KEEP ON FILE WITH THE TOWNSHIP THE NAME, ADDRESS AND TELEPHONE NUMBER OF THE PERSON RESPONSIBLE FOR MAINTENANCE ACTIVITIES AND IMPLEMENTATION OF THE O&M PLAN. IN THE EVENT OF A CHANGE, NEW INFORMATION SHALL BE SUBMITTED BY THE BMP OR CONVEYANCE OWNER TO THE TOWNSHIP WITHIN 10 DAYS OF THE CHANGE.

4. ALL INLETS SHOULD BE INSPECTED AND CLEANED AT LEAST 2 TIMES PER YEAR. THE OVERLYING VEGETATION SHOULD BE MAINTAINED IN GOOD CONDITION, AND CARE SHOULD BE TAKEN TO AVOID EXCESSIVE COMPACTION BY MOWERS.

ACT 287 PENNSYLVANIA ONE CALL NOTIFICATION

Preliminary Serial No. 20241000545, 4/9/24 date. UNDERGROUND UTILITY LINE PROTECTION LAW (ACT 287, AS AMENDED). Pennsylvania One Call System 1-800-242-1776. UTILITIES NOTIFIED: COMCAST PLMG, EAST GOSHEN TOWNSHIP, AQUA PA DESIGN, COMCAST CABLE, PECO EXELON CO., TRANSCO GAS PL, VERIZON EASTERN.

Title Block

UPI NO. 53-1-11.1 | GRAPHIC SCALE 1"=50' (0, 50, 100, 150) | Revision 1: 5-19-25 REVISED PER TOWNSHIP ENGR REVIEW LETTER DATED 11-22-24 | SUBDIVISION PLAN FOR 1344 MORSTEIN ROAD, EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA. | Edward B. Walsh & Associates, Inc. CIVIL ENGINEERS & SURVEYORS, Whiteland Business Park, 855 Springdale Drive, Suite 202, Exton, Pennsylvania 19341, Phone: 610-903-0060, Fax: 610-903-0080 | Project- 5019 | Date- 4/11/24 | Scale- 1" = 50' | Drawn- D.B. | Checked- A.J.B. | Sheet- 5 OF 10 | Plotted: 5/28/2025 | File: F:\EB\5019\FPS\5019-B.pro

·

·

·

·

·

· ·

· · ·

· ·

· ·

· ·

· · ·

·

· · ·

· · ·

· · ·

·

Edward B. Walsh & Associates, Inc.

· · · · · ·