Planning Commission
The East Goshen Township Planning Commission is an advisory board to the Township Board of Supervisors. The Commission reviews all subdivision and land development applications, conditional use applications, zoning hearing board applications and makes recommendations to the Board of Supervisors. The Commission also reviews or drafts Zoning Ordinance Amendments. Each member is appointed by the Board of Supervisors.
- Composed of seven East Goshen Township residents each serving a four-year term.
- Formal Meetings are held the 4th Tuesday of each month at 7:00 P.M.
- Workshop Meeting are held on an as needed basis
- All township meetings are held at the Township Building and are open to the public
| Planning Commission Members | Term Expiration Date |
| John Stipe, Chair | 2026 |
| Dan Truitt, Vice Chair | 2027 |
| Daniel H. Daley | 2027 |
| Michael Koza | 2026 |
| Ernest Harkness | 2026 |
| Karen Martynick | 2029 |
| William Kaufman | 2029 |
| Larry Massaro, BOS Liaison | |
| Kelly Krause, Staff Liaison |
Draft Ordinance-Zoning Amendment Regulating Data Centers by Conditional Use 9.24.26
Click here to view – May 4th Documents for Malvern Institute and East Whiteland Special Study.
Related News
PLANNING COMMISSION CONSIDERS UPGRADES TO AQUA FACILITY
Wednesday, November 18, 2026
At its September meeting, the East Goshen Planning Commission reviewed a conditional use application from Aqua Pennsylvania to upgrade its Hunt Country well treatment facility located on Thorncroft Drive. The upgrade is required to meet new maximum contaminant levels (MCLs) for PFAS in drinking water that were enacted last year by the U.S. Environmental Protection […]
View ArticleFrom the Planning Commission: Addressing Potential Data Center Development in East Goshen Township
Wednesday, September 30, 2026
As the demand for artificial intelligence accelerates, municipalities throughout Pennsylvania have found themselves navigating complex regulations, legal challenges, and community debates about large-scale data centers. While no data center projects are currently proposed in East Goshen, township officials are proactively addressing potential impacts by updating zoning ordinances to create strict standards that will apply should […]
View ArticleDocuments
Back to the list | Open the original PDF
Notice: this accessible version was created automatically from the original document. The transcription may not be 100% accurate. It is provided for searching and for screen readers; please refer to the original document for the official version.
EAST GOSHEN TOWNSHIP PLANNING COMMISSION
East Goshen Township Administration Building 1580 Paoli Pike, 2nd Floor, West Chester, PA 19380 Meeting Agenda Tuesday, November 25, 2025, at 7:00 PM
Planning Commission Members: Ernest Harkness, Chairman John Stipe, Vice Chairman Daniel H. Daley Michael Koza Mike Pagnanelli Fred Pioggia Dan Truitt John Hertzog, BOS Liaison Kelly Krause, Zoning Officer/Staff Liaison Agenda Items:
1. Call to Order / Pledge of Allegiance and Moment of Silence
2. Chairman will ask if anyone is going to record the meeting.
3. Review of Tracking Log / Determine need for Workshop Meeting
4. Public Comment on Non-Agenda Items
5. Approval of Minutes a. June 24, 2025
6. Acknowledge Receipt of New Applications (Initial Submission) a. Subdivision and Land Development Applications b. Conditional Uses Applications c. Zoning Hearing Board Variances d. Ordinance Amendments
7. Old Business
8. New Business a. Zoning Ordinance Amendment Discussion- AI Data Centers
9. Liaison Reports
10. Correspondence
11. Announcements
12. Next Meeting – Tuesday, December 30, 2025 at 7:00 PM
13. Adjournment
Bold Items indicate new information to review or discuss.
PROJECT DESCRIPTION Date Filed Start Date
Twp. Engineer
Review
CCPC Review
Conserv.
Board Review
Extension
Date
PC Deadline
Meeting
BOS Deadline
Meeting
Hearing
Date
Final Action Deadline (90
days) Comments
Zoning Ordinance Amendment- AI
Data Centers Discussion n/a 11/25/2025 n/a n/a n/a n/a n/a n/a n/a n/a Review sample ordinances for consideration of draft
10-Year Comprehensive Plan Review n/a 4/22/2025 n/a n/a n/a n/a n/a n/a n/a n/a Pending direction from BoS- per PC request discussed at BoS
meeting on 5/20/2025
1344 Morstein Road- K.A. Thomas 2 Lot Subdivision 5/28/2025 6/24/2025 pending 12/12/2025 6/11/2025 12/17/2025 n/a n/a n/a 12/16/2025 Pending CCPC Review- BoS Meeting of 12/16/2025
1338 Morstein Road- WCU Foundation 16 Lot Subdivision 2/5/2024 2/27/2024 11/13/2025 n/a n/a 12/17/2025 n/a 12/16/2025 n/a 12/16/2025 Finalization of agreements- BoS Meeting of 12/16/2025
PROJECTS COMPLETED IN 2025
Bold = New application or action required
East Goshen Township Planning Commission
Application Tracking Log
November 25, 2025
PENDING PROJECTS
PC 6-24-25 draft 1
Draft 1 EAST GOSHEN TOWNSHIP 2 PLANNING COMMISSION MEETING 3 June 24, 2025 4 5 The East Goshen Township Planning Commission held their regular monthly meeting on Tuesday, 6 June 24, 2025 at 7:00 pm in the Township Building. 7 Members present are highlighted: 8 Chair – Ernest Harkness 9 Vice Chair – John Stipe 10 Dan Daley 11 Michael Koza 12 Michael Pagnanelli 13 Fred Pioggia 14 Dan Truitt 15 16 Also present was: 17 Kelly A. Krause, Zoning Officer 18 John Hertzog , BOS Liaison 19 Nathan Cline, Township Engineer 20 Mark Thompson, Township Solicitor 21 22 COMMON ACRONYMS: 23 BOS – Board of Supervisors CPTF – Comprehensive Plan Task Force 24 BC – Brandywine Conservancy CVS – Community Visioning Session 25 CB – Conservancy Board SWM – Storm Water Management 26 CCPC – Chester Co Planning Commission ZHB – Zoning Hearing Board 27 28 FORMAL MEETING – 7 p.m. 29 1. Ernest called the meeting to order at 7:00 pm. He led the Pledge of Allegiance and asked for a 30 moment of silence to remember our first responders, police, military, and all who protect us. 31 2. Ernest asked if anyone would be recording the meeting and if there were any public 32 comments about non-agenda items. There was no response. 33 3. The tracking log was checked and no need for a workshop meeting. 34 4. The minutes of the April 22, 2025 meeting were approved. 35 36 CHAIRMAN’S REPORT – 37 None 38 39 Acknowledge Receipt of New Applications (initial Submission)- None 40 41 42 OLD BUSINESS – 43 1. 1344 Morstein Rd – Adam Brower of Edward B. Walsh Assoc. and Kyong-Aie Thomas, Property 44 Owner, were present. Kelly mentioned that they received the June 18 Township Engineer letter, but the 45 staff has not received the Chester County letter yet. November 26, 2024 was the first review of this plan 46 by the Planning Commission. 47 Adam revised the plan for the correct route to take for sanitary issues. He spoke about the private 48 driveway. The neighbor is okay with the second pipe for the new lot. The existing owner will continue to 49 maintain the private driveway. There will be no HOA. There will be no cul-de-sac because the roads will 50 be wide enough for emergency vehicles. He reviewed the Fire Marshall’s letter. A flow test needs to be 51 done. Adam discussed the sewer set up. A grinder pump will be on lot 1. The manhole was discussed. 52 There will be no curbing. 53
PC 6-24-25 draft 2
Dan T. mentioned the maintenance of the private driveway and the understanding of future owners of lot 1 2 that they are responsible for the maintenance of the driveway. He feels it should be noted on the deeds. 2 Adam suggested a list of maintenance items be made that Lot 2 has to do. The trash is picked up on 3 Morstein Rd. Adam reviewed the letter from the Conservancy Board. The trees along the driveway were 4 a concern. 5 John S. made a motion to forward to the BOS for approval with the following recommendations: 6 1. Maintenance of the private road and easement will be the responsibility of Lot 2 owner. Need 7 an agreement or applicable legal agreement approved by the Township Solicitor. 8 2. 3 Waivers requested by the BOS: 9 a. 205-31A to receive preliminary/final approval 10 b. 201-52A to not provide curbing on the proposed private street 11 c. 205-44E(2) turnaround access easement for Lot 1 in lieu of cul-de-sac 12 3. Sewer Main 13 a. Easement for line to connect to main 14 b. Maintenance Agreement memorialized for Grinder Pump by Lot 1 15 c. Grinder pump needs to be upsized to eliminate need for 10” main 16 4. Chester County review letter to be reviewed by Township staff\ \ 17 5. Conservancy Board landscape comments resolved prior to BOS 18 Dan T. seconded the motion. The motion passed unanimously. 19 20 Adam will make any revisions and agreements before it goes to the BOS. 21 Ms. Thomas asked what the addresses will be. Kelly mentioned that there is a process that starts with her. 22 23 24 NEW BUSINESS – 25 1. 2015 Comprehensive Plan - John H. mentioned that the Comprehensive Plan will cost a lot of money 26 if graphics have to be changed. He spoke about the proposed Town Center that didn’t happen in the past 27 10 years. He feels it should be removed from the Comprehensive Plan. There was a discussion about 28 empty stores. He mentioned that he bought something in a store and then checked it on Amazon which 29 was much less expensive. Dan T. feels there should be something in the Comprehensive Plan about 30 hazardous incidents, i.e., a small tornado came down on the East Goshen border a few days ago. 31 32 LIAISON REPORTS 33 34 ANY OTHER MATTER 35 1. John S. is concerned that the Swiss Farms is not open, and they are not maintaining the property. 36 37 CORRESPONDENCE - None 38 39 40 ADJOURNMENT 41 There being no further business, John S. made a motion to adjourn the meeting. Dan T. seconded the 42 motion. The meeting was adjourned at 8:30 pm. 43 The next meeting will be held on Tuesday July 22, 2025 at 7 p.m. 44 45 Respectfully submitted, 46 47 48 49 50 Ruth Kiefer, Recording Secretary 51
Map of East Goshen Township showing FEMA Flood Zones, Open Space parcels, and highlighted industrial and business park zoning districts.
EAST GOSHEN TOWNSHIP FEMA FLOOD ZONES & OPEN SPACE MAP
Zoning District Callouts
- § 240-19 I-1 Light Industrial District.
- § 240-20 I-2 Planned Business, Research and Limited Industrial District.
- § 240-21 BP Business Park District.
Legend
- Flood Zones
- Streams
- SewerLines
- OpenSpace Public Parks; Private HOA Open Space; Open Space
Map Metadata
Scale: 0 500 1,000 Feet
DATE: APRIL 2020
FILE: F:\GIS_Central\Current Spatial Data\ArcPRO\2020 Zoning Maps\2020 FZOS MAP
NOTES: All basemap layers obtained by Chester County Open Data and clipped to East Goshen Township. Open Space parcels symbolized to EGT.
CREATED BY: Gabrielle Long | glong@eastgoshen.org
DATA CENTER MODEL ORDINANCE
Data Center Model Ordinance
August 2025
DATA CENTER MODEL ORDINANCE
Overview
The following document is a model ordinance containing suggested language, including terminology and definitions commonly used in regulations for Data Centers.
This model ordinance serves as a summary document of the various components that the York County Planning Commission (YCPC) believes are necessary for a municipality to consider when evaluating the impacts of these uses on their municipalities. It should be the goal of the municipality to clearly articulate their expectations and requirements to any developers proposing these uses within their municipality, as well as to clearly address the concerns and interests of municipal residents.
Municipalities are encouraged to alter the text of this model ordinance to best suit their municipality, as what works best for one municipality may not provide the same results in another. There are suggested sizes, distances, and thresholds throughout this model ordinance that are recommendations, and should be thoroughly considered by municipal officials to determine if these requirements make sense for their municipality. Additional context has been provided for some topics in sidebars throughout the document.
As noted above, there are also sections of this model ordinance that, while important topics for consideration,
◼ May not be topics that municipalities currently want to address
◼ Are topics that municipalities have already addressed elsewhere in their ordinance
◼ Can be viewed as forward-thinking
Sections of this model ordinance that fall into these categories are presented in blue text. Municipalities are encouraged to review the language in these sections to determine if these are topics that make sense to address in their Zoning Ordinance currently.
Municipalities protect and promote the safety, health, and morals of their communities by following and enforcing proper planning procedures, ensuring that development within their borders has been thoroughly considered well in advance of the submittal of plans for development. When considering where to permit and how to regulate more intense uses (such as the ones discussed in this model ordinance), municipalities should conduct assessments to evaluate the social, environmental, and economic impacts that these types of uses could have on their communities, and to determine where in their municipalities these types of uses can safely function. This type of assessment should be conducted by municipalities during the planning stage, when municipalities are considering adding language to their ordinances. Early assessment of the potential social, environmental, and economic impacts of these more intense uses during the planning stage minimizes the potential for conflicts when a developer submits a land development proposal.
As Data Center standards continue to evolve, municipalities will be challenged to keep up with them, let alone prepare in advance of any changes. This model ordinance is presented based on technology and knowledge available at this time. As always, municipal staff and officials are encouraged to reach out to YCPC staff if questions arise regarding any of the content found within this model ordinance.
DATA CENTER MODEL ORDINANCE
Page 1 of 13
SECTION 100. DEFINITIONS
COMMUNITY NOISE EQUIVALENT LEVEL (CNEI) - The 24-hour A-weighted average sound level from midnight to midnight, obtained after the addition of 5 dB to sound levels occurring in the evening from 7 PM to 10 PM and after the addition of 10 dB to sound levels occurring in the night between 10 PM and 7 AM.
DATA CENTER – A facility used primarily for the storage, management, processing, and transmission of digital data, which houses computer or network equipment, systems, servers, appliances and other associated components related to digital data operations.
The facility may also include air handlers, power generators, water cooling and storage facilities, utility substations, and other associated utility infrastructure to support sustained operations at the Data Center.
DATA CENTER ACCESSORY USE – Ancillary uses or structures secondary and incidental to a Data Center use, including but not limited to: administrative, logistical, fiber optic, storage, and security buildings or structures; sources of electrical power such as generators used to provide temporary power when the main source of power is interrupted; electrical substations; utility lines, domestic and non-contact cooling water and wastewater treatment facilities; water holding facilities; pump stations; water towers; environmental controls (air conditioning or cooling towers; fire suppression, and related equipment), and security features, provided such Data Center Accessory Uses/structures are located on the same tract or assemblage of adjacent parcels developed as a unified development with a Data Center. The use shall not include energy generation systems used or intended to be used to supply power to the Data Center during normal operations.
DATA CENTER ELECTRICAL SUBSTATION – A facility used for the transformation or transmission and/or switching of voltages to distribution voltages which switches circuits and distributes usable/consumable electric power, specifically for Data Center users on the same or adjacent site, or on a site immediately across a road right-of-way.
DATA CENTER PRINCIPAL BUILDING – A building that contains the office and/or data storage functions of a Data Center.
FOOTCANDLE – Enough light to saturate a one-foot square with one lumen of light.
SENSITIVE RECEPTORS – Schools, preschools, day care centers, in-home daycares, health facilities such as hospitals, long term care facilities, retirement and nursing homes, community centers, places of worship, playgrounds, parks (excluding trails), campgrounds, prisons, dormitories, and any residence where such residence is not located on a parcel with an existing industrial, commercial, or unpermitted use as determined by the zoning officer.
DATA CENTER MODEL ORDINANCE
Page 2 of 13
SECTION 200. SPECIFIC USE CRITERIA
Data Centers
The following requirements shall apply to all Data Centers. In the event that any of the following regulations are found to be in conflict with regulations found elsewhere in the (MUNICIPALITY) Zoning Ordinance, the most restrictive regulations shall be applied, unless otherwise stated.
A. Building Placement and Orientation
(1) All principal and accessory structures associated with a Data Center shall be arranged, designed, and constructed to be harmonious and compatible with the site and with the surrounding properties. In general, Data Centers that visually approximate commercial office buildings are encouraged.
(2) Buildings shall be sited and oriented to:
a. Minimize visual impacts of the bulk of the building when examined on a line-of-sight basis
from adjacent public streets and Sensitive Receptor areas.
b. Provide safe and convenient vehicular access to the site, including sufficient on-site queuing
areas at security gates.
c. Accommodate adequate parking.
d. Minimize impacts to natural resources.
e. Incorporate appropriate stormwater management practices.
(3) Data Center campuses containing more than one building are encouraged to provide a variety in building size, massing, siting, and appearance by transitioning from smaller or lower buildings along street frontages to larger and taller structures on the interior of the site. Consideration of topography shall be given to avoid placement of larger, taller, or more massive buildings in a prominent location on the property or along a public street.
(4) Connection to public water and public sewer is required.
B. Maximum Height
The maximum building height for Data Centers shall be __ feet.
C. Setbacks
(1) All principal buildings, accessory structures, and Data Center Electric Utility Substations must be set back at least (150 – 200) feet from all property lines.
(2) Parking lots for Data Centers shall be set back at least __ feet from public road rights-of-way, and __ feet from all property lines.
D. Parking Requirements
A minimum of 1 parking space per employee on the largest shift is required, plus an additional 3 visitor spaces.
Building Height
Municipalities should determine if incorporating language that allows for an increase in building height with increased building setbacks is a viable option for their municipality.
DATA CENTER MODEL ORDINANCE
Page 3 of 13
E. Off Street Loading
A minimum of one loading space is required. Loading spaces/bays are only permitted to be located on one façade of the Data Center Principal Building.
F. Noise/Vibration
(1) CNEI
a. The Community Noise Equivalent Level (CNEI) at the boundary of the property containing a
Sensitive Receptor shall not exceed 60 dBA.
b. The CNEI at the boundary of any developed property not containing a Sensitive Receptor shall
not exceed 70 dBA.
c. Sound that is produced for not more than a cumulative period of one (1) minute in any hour may exceed the standards above by up to ten (10) dBA.
d. The maximum sound levels listed above do not apply to emergency alerts, emergency work to
provide electricity, water, or other public utilities when public health or safety is involved, snow removal, or road repair.
(2) A noise reduction barrier or device may be required at the discretion of the zoning officer when it is inconclusive that noise level tests do not conform to acceptable noise levels.
(3) The limitations of Section 200.1.F. herein shall not apply to any Sensitive Receptor that is established adjacent to the Data Center after the date of issuance of a certificate of completion or occupancy for the applicant’s operation.
G. Negative Impacts
Any use or activity producing air, dust, smoke, glare, exhaust, heat, or humidity in any form shall be carried on in such a manner that it is not perceptible at or beyond the property line.
H. Safety
The equipment used in any Data Center operation shall be housed in a metered, electrically grounded, and pre-engineered metal-encased structure with a fire rating designed to resist an internal electrical fire for at least 30 minutes. The containment space shall contain baffles that automatically close in the event of fire, independent of a possible electric system failure.
Any Data Center use proposing battery storage or any other device or group of devices capable of storing energy in order to supply electrical energy at a later time, whether the energy is stored for use on-site or off-site, shall demonstrate compliance with National Fire Protection Association (NFPA) Standard 855, Installation of Stationary Energy Storage Systems, or similar standards and must include fire suppression systems designed specifically for battery storage.
I. Power
Prior to approval of the certificate of completion or occupancy, the applicant shall provide written verification from the applicable service provider stating the following:
(1) Adequate capacity is available on the applicable supply lines and substation to ensure that the capacity available to serve the other needs of the service area is consistent with the normal projected load growth envisioned by the provider,
(2) Utility supply equipment and related electrical infrastructure are sufficiently sized and can safely accommodate the proposed use,
DATA CENTER MODEL ORDINANCE
Page 4 of 13
(3) Any system designed for cooling and operation of the facility (electricity, water, or other means) will be adequate and will not negatively impact the surrounding region,
(4) The use will not cause electrical interference or fluctuations in line voltage on and off the operating premises, and
(5) Prior to approval of the certification of completion or occupancy, the applicant shall provide the municipality with written verification that the electrical work has passed a third-party final inspection.
J. Lighting
(1) Horizontal Surfaces
For the lighting of predominantly horizontal surfaces, such as, but not limited to, parking areas, roadways, vehicular and pedestrian passage areas, loading docks, building entrances, sidewalks, bicycle paths, and site entrances, luminaires shall be aimed down, and shall meet Illuminating Engineering Society of North America (IESNA) full cut-off/fully shielded criteria.
(2) Non-Horizontal Surfaces
For the lighting of predominantly non-horizontal surfaces, such as, but not limited to, facades, landscaping, and signs, luminaires shall be shielded and shall be installed and aimed to not project their output into the windows of neighboring residences, adjacent uses, past the object being illuminated, skyward, or onto a public roadway.
(3) Adjacent Residential Uses
The illumination projected onto a residential use shall at no time exceed 0.1 footcandle, measured line-of-sight and from any point on the receiving residential property.
(4) Adjacent Non-Residential Uses
The illumination projected from any property onto a non-residential use shall at no time exceed 0.5 initial footcandle, measured line-of-sight from any point on the receiving property.
(5) Glare
Vegetation screens shall not be employed to serve as the primary means for controlling glare. Rather, glare control shall be achieved primarily using such means as cutoff luminaires, shields and baffles, and appropriate application of luminaire mounting height, wattage, aiming angle, and luminaire placement.
(6) LED Lights
LED light sources shall have a correlated color temperature that does not exceed 3000K.
(7) Luminaires
Luminaires shall not be mounted more than 20 feet above the finished grade of the surface being illuminated. No pole-mounted lighting on the roof shall be permitted.
(8) Lighting After Hours
Lighting for parking areas and vehicular traffic ways shall be automatically extinguished nightly within ½ hour of the close of the facility. On/off control shall be by an astronomic
Lighting Adjacent to Non- Residential Uses
Ordinances YCPC reviewed for sample language have shown light trespass maximums from 0.1 to 2.0 footcandles.
DATA CENTER MODEL ORDINANCE
Page 5 of 13
programmable controller with battery or capacitor power-outage reset. When after-hours site safety/security lighting is proposed, such lighting shall not exceed 25% of the number of fixtures required or permitted for illumination during regular business hours. Where there is reduced but continued onsite activity throughout the night that requires site-wide even illumination, the use of dimming circuitry to lower illumination levels by at least 50% after 11 PM or after regular business hours, or the use of motion sensor control, shall be permitted.
K. Perimeter Fencing/Security
Fences shall not exceed ___ feet in height above ground and shall be of high-quality design and materials.
L. Power Lines and Data Center Electric Utility Substations
(1) Data Center Electric Utility Substations must include year-round opaque landscaping or a screen wall a minimum of __ feet in height to minimize visual impact.
(2) Electric Utility Substations on the same property as the Data Center they serve must be located on the side or rear of a Data Center Principal Building so they are screened from public view and must not be located in a required front yard. On-site substations do not require a buffer or screening between the Data Center Principal Building and the substation.
(3) Burying power lines serving the property is strongly encouraged. On-site power lines of 34.5 kV and below must be buried.
(4) The Data Center Electric Utility Substation shall be subject to applicable zoning district setback requirements. Setbacks shall be measured from the edge of the compound containing the substation to the property boundary of the lot it occupies.
M. Emergency Contact Information
Each Data Center operation shall provide 24-hour emergency contact signage visible at the access entrance. Signs shall include the company name (if applicable), the owner/representative's name, the telephone number, and the corresponding local power company's name and telephone number.
N. Sensitive Receptors
(1) Unless physically impossible, loading docks, truck entries, and truck drive aisles shall be oriented away from abutting Sensitive Receptors.
(2) To the greatest extent feasible, loading docks, truck entries, and truck drive aisles shall be located away from nearby Sensitive Receptors. Screening as described in Section 200.1.K. shall be provided. When making feasibility decisions, the municipality must consider existing laws and regulations and balance public safety with the site development’s potential impacts on nearby Sensitive Receptors.
O. Buffer Yards and Screening
All Data Center operations shall provide buffer yards and screening along all property boundary lines, except for areas of ingress and egress into the site.
(1) Service Areas - Loading bays, refuse collection areas, and service entrances shall be screened from view from existing or planned public roads, Sensitive Receptors, and residential zoning districts. Screening may include year-round landscaping or a screen wall of an appropriate height to mitigate visual impacts as determined by a line-of-sight study submitted by the applicant.
(2) Mechanical/Electrical Equipment Screening.
a. Ground-Mounted
DATA CENTER MODEL ORDINANCE
Page 6 of 13
i. Ground-mounted equipment adjacent to and serving the Data Center Principal Building shall be completely screened behind an opaque wall or fence. When the equipment is located between buildings, a combination of walls and gates may be used at the openings between buildings.
ii. When in or adjacent to an industrial use or zoning district, ground-mounted equipment screening is only required from any existing or planned public road.
iii. Ground-mounted equipment is prohibited in any required
setback.
b. Roof Top
i. All rooftop-mounted equipment shall be screened by a parapet wall, equipment penthouse, or visually solid screen on all four sides that is constructed of materials complementary to those used in the exterior construction of the Data Center Principal Building. This shall be accomplished by setting the penthouse or screened area back from the façade of the building such that the top of the penthouse or screen is below a 45-degree line drawn from the top of the parapet. Roof-top equipment to be screened includes, but is not limited to, the following: cooling, ventilation, and power supply machinery.
ii. Roof top equipment that is visible above the parapet wall shall be set back from the exterior or parapet wall a distance no less than the height of said equipment.
iii. Roof-top equipment may exceed the applicable maximum district building height when
completely screened pursuant to this ordinance.
iv. Roof top equipment may occupy up to a maximum of __% of the roof area when screened
per this ordinance and, when combined with the height of the Data Center building, does not exceed the maximum building height requirement.
(3) Buffering.
a. Data Center sites abutting Sensitive Receptors or collector/arterial roads must include an
enhanced buffer yard with required plantings located on an earthen berm with a grade no steeper than 2:1. The minimum height of the berm abutting Sensitive Receptors is _____ feet, and abutting collector/arterial roads is ____ feet.
i. Where the combined footprint of the principal structure or structures is less than 100,000 square feet:
a. A minimum 100-foot buffer yard shall be provided along the entire length of any
public street frontage of any property upon which the Data Center is located and along any property line which abuts or is within 500 feet of an existing residential property line or zone, school, daycare center, hospital, place of worship, designated park, or public open space.
b. A minimum 50-foot buffer yard shall be provided along any property line adjacent to a
non-residential use or zone.
Buffer Yards and Screening
Municipalities often already have buffer yard and screening requirements in place elsewhere in their zoning ordinance or SALDO.
If your municipality already has buffer yard and screening requirements, consider directing readers to those sections instead of duplicating requirements. If screening above and beyond what already is in place is required, this would be the section in which to address it.
DATA CENTER MODEL ORDINANCE
Page 7 of 13
ii. Where the combined footprint of the principal structure or structures is between 100,000 square feet and 250,000 square feet:
a. A minimum 150-foot buffer yard shall be provided along the entire length of any
public street frontage of any property upon which the Data Center is located and along any property line which abuts or is within 500 feet of an existing residential property line or zone, school, daycare center, hospital, place of worship, designated park, or public open space.
b. A minimum 50-foot buffer yard shall be provided along all other property lines.
iii. Where the combined footprint of the principal structure or structures exceeds 250,000
square feet:
a. A minimum 300-foot buffer yard shall be provided along the entire length of any
public street frontage of any property upon which the Data Center is located and along any property line which abuts or is within 500 feet of an existing residential property line or zone, school, daycare center, hospital, place of worship, designated park, or public open space.
b. A minimum 50-foot buffer yard shall be provided along all other property lines.
iv. Utilities should be located outside of buffer yards to the maximum extent feasible to
maintain a cohesive buffer yard, protect landscaping, and preserve open space. Utilities should be co-located when feasible to minimize the number of utility crossings through the required buffer yard, particularly when such crossings cannot be avoided.
v. Use of existing vegetation for landscaping and screening is strongly encouraged and may be substituted for new berms and plantings if approved by the (MUNICIPAL GOVERNING BODY).
vi. The required number of plant units shall be calculated in accordance with other
municipal screening requirements.
vii. Buffer yards along roadways shall be measured from the street right-of-way line.
viii. Where a lot line drainage or utility easement is required, the buffer yard shall be
measured from the inside edge of the easement.
ix. Buffer yards shall not include environmental encumbrances such as, but not limited to,
wetlands, wetland transition areas, riparian buffers, and flood hazard areas as may be imposed by outside agencies.
x. The buffer yard shall include a dense landscape buffer consisting of the following:
a. One (1) large evergreen tree per 25 linear feet of buffer. The size of large evergreen
trees shall be a minimum of eight (8) feet in height at the time of planting. Narrow/upright evergreen species may also be used within buffers at a ratio of 3:1. No more than 25% of the total required large evergreen species can be substituted with narrow/upright species.
b. One (1) canopy (shade) tree per 75 linear feet of buffer. The size of canopy (shade)
trees shall be a minimum of 2 ½ inch caliper at the time of planting.
c. One (1) ornamental/flowering tree per 50 linear feet of buffer. The size of ornamental/flowering trees shall be a minimum of eight (8) feet in height for multi-
DATA CENTER MODEL ORDINANCE
Page 8 of 13
stemmed varieties, or 2 ½ inch caliper at the time of planting for single-stemmed varieties.
d. Five (5) shrubs per 25 linear feet of buffer. Shrubs shall be fully branched and a
minimum of three (3) feet in height at the time of planting. Shrubs shall be a combination of evergreen and deciduous species, with a minimum of 50% evergreen.
xi. The landscape buffer shall be located along the outer edge of the buffer yard.
xii. Plant material within buffer plantings shall meet the following requirements:
a. Be resistant to diesel exhaust.
b. Not identified on the most current DCNR invasive species or watch lists.
c. Be hardy within USDA hardiness Zones 6 and 7.
d. Shall be planted on the top and the exterior of any berm in order to provide effective
screening.
e. Shall be arranged in groupings to allow for ease of maintenance and to provide a
natural appearance.
f. Shall provide a diversity in plant species, such that no one species accounts for more than 25% of each plant type. g. The plantings shall be arranged to provide a complete visual screen of the property at
least 12 feet in height, measured in addition to the height of any required berm, within three (3) years.
xiii. The buffer yard may be located within the required building setback lines. No impervious
surface is permitted within the buffer yard aside from access drives, sidewalks, and associated improvements.
P. Environmental and Community Impact Analysis
Prior to the commencement of the [conditional use/special exception] hearing, the applicant shall provide an environmental and community impact analysis. The environmental and community impact analysis shall include:
(1) A narrative description of the nature of the on-site activities and operations, including the market area served by the facility, the hours of operation of the facility, the total number of employees on each shift, the times, frequencies, and types of vehicle trips generated, the types of materials stored and the duration period of storage of materials.
(2) A site plan of the property indicating the location of proposed improvements, flood plains, wetlands, waters of the Commonwealth and cultural and historic resources on the property and within 500 feet of the boundaries of the property.
(3) Evidence that the disposal of materials will be accomplished in a manner that complies with state and federal regulations.
(4) An evaluation of the potential impacts of the proposed use, both positive and negative, upon:
a. Emergency services and fire protection,
DATA CENTER MODEL ORDINANCE
Page 9 of 13
b. Water supply, c. Sewage disposal, d. Solid waste disposal, e. School facilities and school district budget, and f. Municipal revenues and expenses.
(5) Any environmental impacts that are likely to be generated (e.g., odor, noise, smoke, dust, litter, glare, heat islands, vibration, electrical disturbance, wastewater, stormwater, solid waste, etc.) and specific measures employed to mitigate or eliminate any negative impacts. The applicant shall further furnish evidence that the impacts generated by the proposed use fall within acceptable levels, as regulated by applicable laws and ordinances.
Q. Building Colors
External building materials shall be of colors that are low-reflective, subtle, or earth tone. Fluorescent and metallic colors shall be prohibited as exterior wall colors.
R. Emergency Responders
The applicant shall coordinate with the (MUNICIPALITY) emergency management coordinator to ensure there is adequate radio coverage for emergency responders within the building based upon the existing coverage levels of the (MUNICIPALITY) Public Safety Radio Communications System at the exterior of the building, and shall install enhancement systems as needed to meet compliance.
S. Environmental Impact Assessment
An Environmental Impact Assessment shall be performed. The assessment shall be prepared by a professional engineer, ecologist, environmental planner, or other qualified individual. An assessment shall include a description of the proposed use, including location, relationship to other projects or proposals, with adequate data and detail for the (MUNICIPALITY) to assess the environmental impact. The assessment shall also include a comprehensive description of the existing environment and probable future effects of the proposal. The description shall focus on the elements of the environment most likely to be affected as well as potential regional effects and ecological interrelationships. At a minimum, the assessment shall include an analysis of the items listed below regarding the impact of the proposed use and the mitigation of any such impacts. The assessment shall also include a detailed examination of public resources most likely impacted by the development plan and include the following focus areas:
(1) Air pollution impacts emissions from vehicle operations, including from truck engines during idle time. The applicant shall identify all stationary and mobile sources of fine particulate matter (PM2.5), volatile organic compounds, and nitrogen oxides at the site. The applicant shall specify best management practices for preventing and reducing the concentration of air-polluting emissions at the site. The owner or operator of the facility shall have anti-idling signs prominently posted in areas where 15 or more trucks may park or congregate.
(2) The potential for public nuisance to residents resulting from operations and truck traffic, including noise, glare, light, and visual obstacles, exists.
(3) A stormwater management plan will be required.
Water Supply
Most Data Centers use large amounts of water to assist with equipment cooling and humidity maintenance within their operations. Water consumption can vary based on the size of the project. It is important for municipalities to require proposed Data Center development to clearly articulate water needs, use, availability, recycling and/or release procedures, and local and regional impacts on water resources.
DATA CENTER MODEL ORDINANCE
Page 10 of 13
(4) Consistency with the municipal and county comprehensive plan. The applicant shall submit an assessment report of the impact of the proposed use on the goals of the respective plans. Where the proposed use conflicts with the comprehensive plan, the assessment report shall identify mitigation measures that may be undertaken to offset any degradation, diminution, or depletion of public natural resources.
(5) Additional considerations. The following shall also be addressed:
a. Alternative analysis. A description of alternatives to the impacts. b. Adverse impacts. A statement of any adverse impacts that cannot be avoided. c. Impact minimization. Environmental protection measures, procedures, and schedules to minimize damage to critical impact areas during and after construction, including design considerations. d. Mitigation steps. A listing of steps/structural controls proposed to minimize damage to
the site before and after construction.
(6) Critical impact areas. In addition to the above, plans should include any area, condition, or feature that is environmentally sensitive or that, if disturbed during construction, would have an adverse impact on the environment.
a. Critical impact areas include, but are not limited to, floodplains, riparian buffers, streams,
wetlands, slopes greater than 15%, highly acid or highly erodible soils, hydric soils, hydrologic soil groups, areas of high-water table, and mature stands of native vegetation and aquifer recharge and discharge areas. b. A statement of impact upon critical areas and of adverse impacts that cannot be avoided. c. Environmental protection measures, procedures, and schedules to minimize damage to critical impact areas during and after construction.
T. Green Building Techniques
Data Centers are encouraged to implement low-impact development practices in site design and energy efficiency, such as, but not limited to, the following:
(1) Site Design.
a. Select sites that avoid sensitive lands such as wetlands, floodplains, and steep slopes b. Minimize land disturbance c. Maximize tree preservation d. Minimize impervious surfaces e. Minimize potential nuisance impacts (noise, glare, vibration, etc.) on adjacent properties,
public roadways, and the vicinity.
(2) Energy/Resource Efficiency.
a. Orient buildings to take advantage of passive cooling and daylight opportunities b. Utilize alternative energy sources (solar, wind, hydro, etc.) as much as possible c. Provide an energy storage system to monitor and regulate usage of alternative energy for usage during off-peak hours d. Utilize reclaimed water for cooling, if available e. Encourage systems that limit the use of finite natural resources and their disposal f. Encourage fuel storage that limits impacts on the environment from potential spills g. Install water-efficient landscape materials h. Utilize LED exterior/interior lighting
DATA CENTER MODEL ORDINANCE
Page 11 of 13
i. Implement energy management best practices and carbon reduction techniques such as, but not limited to, those promoted through the U.S. Department of Energy’s Better Buildings initiative and U.S. Green Building Council’s LEED Certification system.
U. LEED Certification
LEED certification is strongly encouraged, as well as the installation of roof-mounted accessory solar energy systems.
V. Woodland Disturbance
Woodland disturbance, including alteration or removal of any hedgerows, shall be minimized. No portions of tree masses, tree lines, hedgerows, or individual freestanding trees measuring six (6) inches or greater in diameter at breast height (DBH) shall be removed unless it is clearly necessary to effectuate the proposed development. In no case shall more than 50% of any existing tree masses, tree lines, hedgerows, or individual freestanding trees with six (6)-inch or greater DBH be removed. For purposes of this subsection, a woodland is defined as a tree mass or plant community in which tree species are dominant or codominant and the branches of the trees form a complete, or nearly complete, aerial canopy. Any area, grove, or stand of mature or largely mature trees (i.e., six (6)-inch or greater DBH) covering an area of .25 of an acre or more, or consisting of more than 50 individual trees six (6) inches or greater DBH, shall be considered a woodland.
W. Threatened and Endangered Species
(1) PNDI A Pennsylvania Natural Heritage Program study (PNDI Receipt) dated within two (2) years of the submission of an application for conditional use/special exception or subdivision and land development, whichever is first, as well as any state agency clearance letters required thereby, shall be provided to the municipality.
(2) Compliance The applicant shall comply with all measures directed by the clearance letters to avoid, minimize, or mitigate impacts to endangered, threatened, and special concern species and their habitat.
X. Riparian Forest Buffer Area
Data Centers subject to the requirements of this Section must satisfy the stricter of the requirements of this Section, or of 25 Pa. Code 102.14, Riparian Buffer Requirements.
(1) For purposes of this Section, a riparian buffer is an area of permanent vegetation along a waterway that is left undisturbed to allow for the natural succession of native vegetation. A riparian forest buffer is a type of riparian buffer that consists predominantly of native trees, shrubs, and forbs, providing at least 60% uniform canopy cover.
(2) Where the project site contains, is along, or is within 150 feet of a perennial or intermittent river, stream, or creek, lake, wetland, floodplain, pond, or reservoir, whether natural or artificial, the use will be subject to the requirements of this Section and shall, in accordance with the requirements of this subsection, do one of the following:
a. Protect an existing riparian forest buffer. b. Convert an existing riparian buffer to a riparian forest buffer. c. Establish a new riparian forest buffer.
(3) Where a riparian forest buffer exists, it shall be left intact to meet the width requirements in subsections (6) and (7). An existing riparian forest buffer need not be altered to establish individual Zones 1 and 2 under subsection (9).
DATA CENTER MODEL ORDINANCE
Page 12 of 13
(4) Riparian buffers that consist predominantly of native woody vegetation that do not satisfy the composition requirements for a riparian forest buffer in subsection (1) or the width requirements in subsections (6) and (7) shall be enhanced or widened, or both, by additional plantings in open spaces around existing native trees and shrubs to provide at least 60% uniform canopy cover for the required width and shall be composed of zones in accordance with subsection (9).
(5) On sites without native woody vegetation, a riparian forest buffer providing at least 60% uniform canopy cover shall be established to meet the width requirements in subsections (6) and (7) and be composed of zones in accordance with subsection (9).
(6) The width of the riparian forest buffer shall be a minimum of 100 feet on each side of the water body as measured from the top of the bank. The boundary of the buffer shall follow the natural streambank or shoreline.
(7) Measured within the 100-foot buffer, the following additional distances shall be added to the minimum width of the riparian forest buffer:
a. 10 feet if the average slope is 10-15%, b. 20 feet if the average slope is 16-17%, c. 30 feet if the average slope is 18-20%, d. 50 feet if the average slope is 21-23%, e. 60 feet if the average slope is 24-25%, or f. 70 feet if the average slope exceeds 25%.
(8) In the case of the presence of a nontidal wetland or vernal pond wholly or partially within the riparian buffer area, an additional 25 feet shall be added to the width of the riparian forest buffer area for that portion of the buffer area along the wetland, floodplain, or pond.
(9) A new riparian forest buffer or a converted riparian forest buffer shall be composed of zones as follows:
a. Zone 1 shall begin at the top of the streambank or normal pool elevation of a lake, pond, or
reservoir and occupy a strip of land 50 feet in width, measured horizontally on a line perpendicular from the top of the streambank or normal pool elevation of a lake, pond, or reservoir. Predominant vegetation must be composed of a variety of native riparian tree species identified in Appendix C.1 of the PA Department of Environmental Protection Guidance Document 394-5600-001, entitled Riparian Forest Buffer Guidance. b. Zone 2 shall begin at the landward edge of Zone 1 and occupy an additional strip of land a
minimum of 50 feet in width, measured horizontally on a line perpendicular from the top of the streambank or normal pool elevation of a lake, pond, or reservoir. Predominant vegetation must be composed of a variety of native riparian trees and small tree/shrub species identified in Appendix C.1 of the PA Department of Environmental Protection Guidance Document, 394-5600-001, entitled Riparian Forest Buffer Guidance.
(10) No earth disturbance, land development, or storing or stockpiling of materials shall occur within the riparian forest buffer area.
(11) In the management of riparian buffers, noxious weeds and invasive species shall be removed or controlled to the greatest extent possible.
(12) Existing, converted, and newly established riparian buffers, including access easements, must be protected in perpetuity through deed description, conservation easement, permit conditions, or any other mechanisms that ensure the long-term functioning and integrity of the riparian buffer.
(13) The riparian buffer shall be designated on the final subdivision and/or land development plan.
DATA CENTER MODEL ORDINANCE
Page 13 of 13
Y. Solar
(1) All building roofs shall be solar-ready, which includes designing and constructing buildings in a manner that facilitates and optimizes the installation of a rooftop solar photovoltaic (PV) system at some point after the building has been constructed.
(2) Any portion of a building’s rooftop that is not covered with solar panels or other utilities shall be constructed with light colored roofing material with a solar reflective index of not less than 78. This shall be the minimum solar reflective rating of the roof material for the life of the building.
(3) On buildings over 400,000 square feet, prior to the issuance of a certificate of occupancy, the (MUNICIPALITY) shall ensure rooftop solar panels are installed and operated in such a manner that they will supply as much power as needed to operate the facility as is feasible.
Page 1
Cumberland County Planning Department
Planning for Data Centers
What are data centers?
Data centers are physical facilities that organizations use to store their computing machines and related hardware. This includes information technology (IT) systems infrastructure like servers, data storage drives, and network equipment1. Data centers have accompanying accessory uses such as utilities, external mechanical equipment, water towers, and security facilities that may be located on the same site.
Data centers form the backbone of the digital world. They support typical everyday tasks such as internet usage, online shopping, gaming, and streaming services. Businesses need data centers for complex processes such as cloud computing, cybersecurity, ecommerce, communications, data processing, and artificial intelligence (AI) driven uses.
There are several types of data centers that provide different services for customers2. Aside from building and lot size, the data center types are similar from the land use perspective as internal equipment, ownership, and operations are outside of typical zoning regulation. However, understanding the types of data centers provides context when a development proposal arises in a community.
• Enterprise data centers are owned and operated by individual businesses and used to solely support that company’s data and information technology needs.
• Managed data centers are third party service facilities that manage another company’s computer hardware, data, and infrastructure.
• Colocation data centers enable businesses to rent space for their servers and other computing hardware. Aside from providing physical space, these facilities also offer a range of services including maintenance, backup power systems, and multiple network connections.
• Cloud data centers are third party owned facilities where hardware is run and managed by the cloud company. Customers can run websites and applications using the servers hosted in the facility.
1 Amazon Web Services definition of a data center. https://aws.amazon.com/what-is/data-center/ 2 5 Different Types Of Data Center [With Examples] - RankRed;
Denver Federal Data Center, Lakewood, CO. Source:
www.hga.com
Data center server racks. Source: www.lifewire.com
Equinix NY4 Data Center, Secaucus, NJ. Source:
www.datacenters.com
Page 2
• Edge data centers are smaller facilities located close to the populations they serve to increase data processing speed and decrease data transmission delays. They deliver cloud computing resources and cached content to end users and typically connect to a larger central data center or multiple data centers
• Hyperscale data centers are massive facilities that house critical computing and network infrastructure that provides scalability and high-speed processing for large volumes of data. Consuming several hundred acres of land and including several million square feet of building space, these facilities allow big companies like Amazon, Google, and Microsoft to deliver key services to customers worldwide.
Other data centers may be an accessory use to commercial or industrial land uses. Microdata centers are smaller version of edge data centers that may include a single room to handle the computing needs in a specific location. Modular data centers are mobile pre-engineered and prefabricated buildings, complete with power and cooling infrastructure, used to house computer servers and network equipment. Modular data centers reduce the time and cost associated with deploying a new data center.
Why Are Data Centers Locating in Cumberland County?
Data centers have critical locational requirements, all of which can be found in Cumberland County:
• Energy – Data centers require large amounts of energy to power and cool equipment. The amount of power can range from small-scale data centers needing 1-5 megawatts (MW) of power to hyperscale data centers often exceeding 100 MW and, in some cases, up to 1 gigawatt (GW). Cumberland County is home to electric transmission lines from 100 to over 500 kilovolts that can support data center developments. Locations immediately adjoining or near such energy infrastructure are priority locations for data center development, especially those larger in size. Future enhancements to the electrical grid in the county may create additional locations suitable for data center development.
Modular data center. Source: Microsoft.
Electric power transmission lines in Cumberland County. Source: ESRI
Page 3
• Proximity to customers – Data centers are typically located near customers to improve data processing and transmission speeds. Cumberland County is in the middle of the of Bos Wash megalopolis, the northeastern United States corridor stretching from Boston to Washington, D.C. With 5 cities of over 500,000 population and growing, the BosWash megalopolis will continue to drive data center demand that could be accommodated in the Cumberland County.
• Safe location –Data centers require a safe environment free from natural or manmade disasters that could threaten operations and service delivery. Cumberland County is recognized by the Federal Emergency Management Agency (FEMA) as having relatively low risk to natural and manmade hazards3. The county’s moderate climate, low susceptibility to major storms, and low crime make it an attractive location for data centers.
• Water resources – Data centers consume large amounts of water to cool equipment and maintain proper humidity in buildings. Water consumption varies based upon the facility size, surrounding environment, and type of cooling system. Seasonally, data centers use more water in summer when temperatures are higher and cooling needs increase. Water consumption can vary from about 20,000 gallons per day for smaller data centers to over 500,000 gallons per day for a hyperscale center4. Cumberland County’s abundant surface and groundwater resources can supply the water needed for all data center types.
Community Impacts
Like any new land use, communities must evaluate the positive and negative impacts of data centers, making sure the use complements and does not conflict with the community in which they are located.
Benefits of Data Centers Challenges of Data Centers
• Substantial property tax revenue
• Limited traffic generation
• High-salary jobs created
• No impact to school district
• Provides critical infrastructure
• Water consumption
• Electric consumption
• May produce noise
• Limited job creation per square foot of building space
• Loss of agricultural land
• Compatibility with surrounding uses
3 Map | National Risk Index 4 Data Center Water Usage: A Comprehensive Guide - Dgtl Infra
Bos Wash Megalopolis. Source: US Census Bureau
Google data center cooling system.
Source: Google
Page 4
Zoning Considerations
Data centers, while a new use that may not be provided for in many municipal ordinances, look and function like other commercial or light industrial uses already present in the community. Municipalities should evaluate data centers in comparison to other similar uses and develop new zoning regulations, as appropriate, that address the unique characteristics of data centers. In many cases, municipalities may choose to regulate data centers using existing zoning standards that apply to similar industrial or commercial uses. In doing so, the municipality regulates land uses equitably and decreases the complexity of the zoning ordinance by creating new regulations that may not be necessary.
The following zoning considerations have been developed through interviews with developers and research on data center ordinances from other jurisdictions. The considerations are broken into different topical areas with corresponding descriptions and recommended regulations. Municipalities are encouraged to review this information in the local context, determining the types of regulation that are consistent with local policy.
Data Center-Zoning Definition
From a regulatory standpoint, municipalities do not need to define every data center type (see page 1) as a separate use. Rather, municipalities can identify data centers as a specific use that can be considered a principal or accessory use. Modular and micro data centers may be an accessory use to an existing commercial or light industrial use. The other specific types of data centers are typically principal uses but may have other supporting infrastructure that should be considered and regulated as an accessory use.
Data Center: A use involving a building/premise primarily occupied by computers and/or telecommunications and related equipment, including supporting equipment, where information is processed, transferred and/or stored5
Data Center Accessory Use: Utilities, utility lines, electrical substations, pump stations, water towers, mechanical equipment and environmental controls (air conditioning or cooling towers, fire suppression, etc.), redundant/backup power supplies, redundant data communications connections, and high security when located on the same tract or assemblage of adjacent parcels developed as a unified development for a Data Center.6
Appropriate Zoning Districts
Energy and water infrastructure are primary site requirements for data centers. When determining which zoning districts to allow a data centers, municipalities should investigate where this infrastructure is located and permit data centers in those areas. Given the specific site requirements of data centers, municipalities may consider a fixed overlay zone that permits data centers in a designated, appropriate area. Municipalities could also employ a floating data center overlay zone that would permit data centers in various locations with necessary infrastructure such as fiber optic lines, water resources, and electric availability. Overlay zones can relieve the municipality of providing data centers throughout entire zoning districts where infrastructure may not exist, or other land use compatibility issues may be present.
The way data centers are permitted, by right, conditional use, or special exception should be related to municipal land use policies. Municipalities wanting to encourage data center development could permit the use by right which streamlines the approval process while not requiring additional review processes. Municipalities desiring for a more detailed review of projects, especially in areas with sensitive environmental features or land use compatibility issues, should permit data centers by special exception or conditional use. When feasible, municipalities should regulate data centers using existing zoning standards for industrial and commercial uses that could also apply to data centers.
5 Prince William County Virginia Zoning Ordinance Chapter 32, article I, part 100. Definition of a “Data Center” 6 Limerick Township Zoning Ordinance Chapter 184, article II, section 184-10. Definition of “Data Center Accessory Use”
Page 5
Zoning District7 Use Permitted Considerations
Industrial, light industrial, manufacturing, etc.
By right
Water Capacity
Energy availability
Land availability
Proximity to residential districts and uses
Environmental impacts
Technology hub
Natural and created hazards
Commercial By right
Business or technology By right
Mixed use By conditional use or special exception
Agricultural8 By conditional use or special exception
Data center or technology overlay district – in proximity to high voltage transmission lines of 115kv or more
By right
<or>
By conditional use or special exception
Bulk and Area Requirements9
Minimum lot size. 3 acres or existing minimum lot size for commercial or industrial uses.
Maximum impervious coverage. 60%-80% depending on project type, lot size, and location. Consider using existing standards for industrial or commercial uses.
Height. 80 feet and the height of the building may be increased to 100 feet provided that an additional setback of one foot is provided for every foot of building height over 80 feet. The building height requirement shall include roof mounted equipment such as cooling and ventilation systems, HVAC units or cooling towers10.
Setbacks. Use existing commercial and industrial zoning districts setbacks. Consider increased setbacks when taller structures adjoin residential uses11.
Building Facades
Data centers may include multiple, large industrial buildings with long, tall walls. The facades of those buildings can be attractively designed to improve compatibility with surrounding properties and overall visual appeal in the community. Municipalities should determine if facades for other uses are regulated and if so, consider applying those existing standards to data centers to encourage consistency. Data center façade regulation should be reasonable and appropriate, ensuring that data centers are not subject to stringent regulation that other similar uses are not required to follow.
7 The municipality should tailor the zoning districts to match the districts on the zoning map. 8 Data centers can consume large amounts of land and water, two critical elements of the agriculture economy. Data center development should be considered in conjunction with the municipality’s agriculture preservation goals when located in agricultural districts. 9 The municipality may refer to existing zoning district regulations, or incorporate separate requirements as noted herein. 10 Multistory data centers are becoming more common. Allowing increased height makes for efficient land use and centralizes the use in appropriate areas. 11 Data centers have limited amounts of truck traffic and heavy vehicles. Extensive loading and heavy vehicle setbacks should be avoided.
Page 6
Principal building facades12. Any side of a building that faces a road or a zoning district that permits a residential use must incorporate at least two of the following design elements every 150 horizontal feet. If more than two sides of a building meet the façade requirements, the facades shall be consistent in terms of design and materials.
• Change in building height
• Building step-backs or recesses
• Fenestration (i.e. arrangement, design, and installation of windows and other openings in a building)
• Change in building material, pattern, texture or color
• Use of accent materials
Land Use Compatibility
Data centers may include large expansive buildings but lack high volumes of traffic, noise, and lighting that may conflict with residential uses. Data centers look and function like office/research parks and light industrial complexes. With practical land use compatibility standards, data centers can be located near residential zones and uses with minimal conflicts.
Buffering. A buffer yard of 100 feet is required between the data center and any district that permits residential uses or planned residential properties. No buildings or parking lots shall be constructed in the buffer.
Heightened buffering standards may require the buffer yard to include plantings and/or an earthen berm with a minimum height of six feet and a slope not greater than 2:1. The type of data center and level of regulation of similar uses should guide municipalities in determining the need for heightened regulation.
Screening13. Screening must be provided between accessory buildings including mechanical equipment and substations, and adjacent roads and properties. Screening can be accomplished using existing vegetation that will remain on the property, a newly planted vegetative screen, or a fence, screen wall, panel, parapet wall or other opaque screen as approved by the municipality. Screening is not required in those instances where the principal building serves as the visual screen between accessory buildings/equipment and the adjacent roads and properties.
Landscaping14. Plants should be provided in the required buffer area, as screening, at the main entrance of the building, in parking lots, or along the façade of the proposed data center.
Municipalities should reference existing landscaping standards where appropriate. Heightened standards may require a certain number of trees per square foot of building space. Given the large size of some projects, such standards may be impractical.
Fencing. Fencing may be considered for security purposes but is not needed for land use compatibility if appropriate screening, buffering, and landscaping are also required. Chain-link, slatted insert, and barbed wire or other visually intrusive fence should be discouraged along public streets or when adjacent to residential uses.
12 Prince William County Virginia Zoning Ordinance. Chapter 32, article V, part 509.4.A. 13 Prince William County Virginia Zoning Ordinance. Chapter 32, article V, part 509.4.B. 14 The municipality should review the existing ordinance. Are tree plantings already required? CCPD recommends removing duplications.
Google data center cooling system.
Source: Ruppert Landscape
Page 7
Noise15. The applicant should provide a noise study indicating sound generated by a data center will not exceed 57- 67 decibels as measured at the property line. This requirement does not apply during a time of power outage.
Lighting. Existing lighting requirements shall apply.
Infrastructure
Electric and water infrastructure are the two primary locational requirements unique to data centers that should receive focused municipal review. The municipality’s review coupled with outside agencies and infrastructure provider oversight should ensure that data center benefits are enjoyed without compromising the community’s health, safety, and welfare.
Water16. The applicant shall submit an analysis of raw water needs (groundwater or surface water) from either private or public sources, indicating quantity of water required. If the source is from a municipal system, the applicant shall submit documentation that the public authority will supply the water needed.
If the data center is to rely upon nonpublic sources of water, a water feasibility study will be provided. The purpose of the study will be to determine if there is an adequate supply of water for the proposed data center and to estimate the impact of the data center on existing wells in the vicinity. No data center shall be approved without sufficient water and/or for a use that poses adverse impact on existing wells in the vicinity. A water feasibility study shall include the following minimum information:
• Calculations of the projected water needs
• A geologic map of the area with a radius of at least one mile from the site
• The location of all existing and proposed wells within 1,000 feet of the site, with a notation of the capacity of all high-yield wells
• The location of all streams within 1,000 feet of the site and all known point sources of pollution
• Based on the geologic formation(s) underlying the site, the long-term safe yield shall be determined
• A determination of the effects of the proposed water supply system on the quantity and quality of water in nearby wells, streams, and the groundwater table
• Identification of how water will be recycled or released into surrounding water bodies
• A statement of the qualifications and the signature(s) of the person(s) preparing the study
The applicant shall provide proof of review and approval from the Susquehanna River Basin Commission (SRBC) for projects that have:
• Water withdrawals of 100,000 gallons per day (gpd) or more over a 30-day average from any source or combination of sources within the Susquehanna River Basin.
• Any consumptive water use of 20,000 gpd or more over a 30-day average from any water source
Electric. The applicant should provide an interconnection agreement from the electric service provider indicating that capacity is available, and the data center will be served. Known impacts on electric rates or availability for others uses directly attributable to the data center project should be noted.
15 Limerick Township Pennsylvania Zoning Ordinance. Chapter 184, article X, section 83.B. A range of maximum noise is provided here. Municipalities should identify a preferred maximum level. Noise requirements should be coordinated with requirements for other similar uses in the zoning ordinance. Data centers are 24-hour operations, thus regulating noise by time of day is not recommended. 16 Dickinson Township, Cumberland County Zoning Ordinance section 205-112.P and Q
1
[MUNICIPALITY]
[CARBON] COUNTY, PENNSYLVANIA
ORDINANCE NO. _______
AN ORDINANCE OF THE [GOVERNING BODY] OF [MUNICIPALITY], PENNSYLVANIA, TO AMEND THE [MUNICIPALITY] CODE OF ORDINANCES TO DEFINE AND ADD SPECIFIC REQUIREMENTS FOR DATA CENTERS AND DATA CENTER ACCESSORY USES.
WHEREAS, Article VI of the Pennsylvania Municipalities Planning Code, 53 P.S. § 10601, et seq., authorizes the [MUNICIPALITY] to enact, amend and repeal Zoning Ordinances within the [TOWNSHIP/BOROUGH/CITY]; and
WHEREAS, the [GOVERNING BODY] deems it to be in the best interest and general welfare of the residents of the [TOWNSHIP/BOROUGH/CITY] to update and amend provisions of the [MUNICIPALITY] Zoning Ordinance to provide for Data Centers and Data Center Accessory Uses; and
WHEREAS, the [GOVERNING BODY] of the [TOWNSHIP/BOROUGH/CITY] desires to add provisions to the Zoning Ordinance relating to Data Centers and Data Center Accessory Uses;
NOW, THEREFORE, BE IT ORDAINED AND ENACTED, by the [GOVERNING BODY] of [MUNICIPALITY] as follows:
Section 1. Section XXX of the [MUNICIPALITY] Code of Ordinances, entitled Definitions, is amended to add the following definitions:
Data Center: A building or buildings which are occupied primarily by computers and/or telecommunications and related equipment where digital information is processed, transferred and/or stored, primarily to and from offsite locations. This use does not include computers or telecommunications related equipment that is secondary and customarily incidental to an otherwise permitted use on the property, such as servers associated with an office building. This use shall also include cryptocurrency mining, blockchain transaction processing, and server farms. A Data Center may include Data Center Accessory Uses.
Data Center Accessory Use: Ancillary uses or structures secondary and incidental to a Data Center use, including but not limited to: administrative, logistical, fiber optic, storage, and security buildings or structures; sources of electrical power such as generators used to provide temporary power when the main source of power is interrupted; electrical substations; utility lines; domestic and non-contact cooling water and wastewater treatment facilities; water holding facilities; pump stations; water towers; environmental controls (air conditioning or cooling towers, fire suppression, and related equipment); security features, provided such data center accessory uses/structures are located on the same tract or assemblage of adjacent parcels developed as a unified development with a Data Center. The use shall not include energy generation systems used or intended to be used to supply power to the Data Center during normal operations.
2
Section 2. [LANGUAGE INDICATING ZONING DISTRICTS WHERE USES WILL BE PERMITTED]
Section 3. Section XXX (Standards for Specific Uses) is amended to add Section XXX, Data Centers and Data Center Accessory Uses:
XXX-XX – Data Centers and Data Center Accessory Uses
A. Data Centers shall be permitted by [RIGHT/CONDITIONAL USE/SPECIAL
EXCEPTION] in the XXX Zoning District when approved in compliance with the procedures, standards, and criteria contained in this section.
B. For purposes of this section, sensitive receptors shall be defined as residential uses, schools,
preschools, daycare centers, in-home daycares, long term care facilities, retirement and nursing homes, community centers, places of worship, parks (excluding trails), campgrounds, prisons, and dormitories.
C. Dimensional Standards. The dimensional standards of Data Centers and Data Center
Accessory Uses shall be in accordance with [SECTION XXX (EXISTING STANDARDS APPLICABLE TO RELEVANT ZONING DISTRICT)], with the following exceptions:
1. The maximum building height for a Data Center shall be [60] feet, inclusive of roof- mounted equipment such as cooling and ventilation systems, HVAC units and cooling towers.
2. The maximum height of Data Center Accessory Uses shall be no greater than the height of the principal building.
3. Data Centers and Data Center Accessory Uses shall be set back [200] feet from the boundary of [RESIDENTIAL ZONING DISTRICT(S)] or the lot line of any property developed with a sensitive receptor.
D. Landscape Buffer. A landscape buffer is required between Data Centers and Data Center
Accessory uses and any adjoining [residential zoning district], sensitive receptor, or public roadway. The landscape buffer shall comply with the following requirements [ALTERNATIVELY, CROSS-REFERENCE EXISTING LANDSCAPE BUFFER REQUIREMENTS IN ZONING ORDINANCE OR SALDO]:
1. The landscape buffer shall be at least [25] feet in width and may be part of the minimum setback distance.
2. Buffer plantings shall consist of native species planted as follows:
a. One (1) large evergreen tree per 25 linear feet of buffer. The size of large evergreen
trees shall be a minimum of eight (8) feet in height at the time of planting.
b. One (1) deciduous canopy (shade) tree per 75 linear feet of buffer. Size of canopy
(shade) trees shall be a minimum of 2½ inch caliper at the time of planting.
c. One ornamental/flowering tree per 50 linear feet of buffer. The size of
ornamental/flowering trees shall be a minimum of eight (8) feet in height for multi- stemmed varieties, or 2½ inch caliper at the time of planting for single-stemmed varieties.
d. Five (5) shrubs per 25 linear feet of buffer. Size of shrubs shall be fully branched
and minimum of three feet in height at the time of planting. Shrubs shall be a
3
combination of evergreen and deciduous species, with a minimum of 50% being evergreen.
3. In the event that existing vegetation is adequate to meet the intent of the required buffer yard to screen the Data Center and Data Center Accessory Uses from adjoining [residential zoning districts], sensitive receptors, and public roadways, the [decision- making body], upon recommendation by the Township Engineer and Planning Commission, may determine that existing topography and/or vegetation constitutes all or part of the required buffer yard.
E. Screening and Fencing
1. To provide visual screening and reduce noise levels, ground-mounted and roof- mounted equipment used for cooling, ventilating, or otherwise operating the facility, including power generation or other power supply equipment, that is located within [300] feet of a public roadway, [RESIDENTIAL ZONING DISTRICT(S)], or the lot line of any sensitive receptor must be fully enclosed, except where not mechanically feasible based on the manufacturer’s specifications. If it is not mechanically feasible to fully enclose the equipment, it must be fully screened from view using one or more of the following means:
a. The landscape buffer required by subsection (D) above.
b. By existing vegetation that will remain on the property.
c. By the principal Data Center building or an accessory building
d. A berm averaging a minimum of five (5) feet in height above the adjacent average
ground level with a maximum side slope of 3:1, provided that the berm shall be covered by a well-maintained all season natural ground cover and any required screening plantings shall be arranged on the outside and top of the berm.
e. A visually solid fence, screen wall or panel, parapet wall, or other visually solid
screen that shall be constructed of materials compatible with those used in the exterior construction of the principal building.
2. Fencing of the property is permitted, provided that fencing along public and private roadways is not chain-link, with or without slatted inserts, and does not include barbed wire or other similarly visibly intrusive deterrence device. An applicant shall not be required to comply with this requirement if fencing is fully screened from view by one or more of the means identified in subparagraph 1 above.
F. Noise and Vibration [ALTERNATIVELY, CROSS-REFERENCE EXISTING NOISE
REQUIREMENTS]
1. The applicant shall demonstrate through a sound study conducted by a professional acoustical expert that the sound generated by a Data Center and/or Data Center Accessory Uses during normal operations shall be limited to a maximum daytime (7:00 a.m. to 8:00 p.m. Monday-Friday) decibel level of 67 dB(A) and a maximum nighttime and weekend (8:00 p.m. to 7:00 a.m. Monday-Friday and all day Saturday and Sunday) decibel level of 57 dB(A) as measured from the property line of the use. Such sound study shall be conducted using Sound Level Meters described in ANSI S1.4-2104 and generally accepted methodology. A sound study shall be conducted at the following phases:
4
a. A preliminary study shall be conducted as part of the [conditional use/special
exception/land development] process. The preliminary sound study shall include recommended sound reducing materials or systems as needed to meet the aforesaid sound limits.
b. An interim sound study shall be conducted during the building permit approval
process based upon the proposed user or users of the Data Center and Data Center Accessory Uses depicted on the building plans. Any sound reducing materials or systems recommended by interim sound study shall be incorporated into the construction plans for the use.
c. An as-built sound study shall be conducted six months after issuance of the
certificate of occupancy and prior to the final escrow release for any land development phase. An as-built sound study may also be required thereafter by the [municipality]. If it is determined by the as-built sound study that there is a violation of the aforesaid noise limits, it shall be considered a violation of this Ordinance.
2. Maximum decibel levels specified herein shall not apply during times of power outage, however the sound studies shall also evaluate and report anticipated decibel levels when all emergency power generation equipment is running, including backup generators.
3. The applicant shall provide a vibration study prepared by a qualified professional that demonstrates that no vibration from the Data Center, Data Center Accessory Uses, or associated equipment will be perceptible to the human sense of feeling beyond the property line.
G. Water and Sewer
1. If the use will be served by a public water supply, the applicant shall submit documentation from the public authority certifying that the public authority will supply the water needed.
2. If the use is to rely upon nonpublic sources of water, the applicant shall provide a water feasibility study. The purpose of the study is to determine if there is an adequate supply of water for the proposed use and to estimate the impact of the use on existing wells, groundwater, and surface waters in the vicinity. No Data Center shall be approved unless the water feasibility study demonstrates that the anticipated water supply yield is adequate for the project and that the proposed water withdrawals and discharges will not endanger or adversely affect the quantity or quality of groundwater supplies or surface waters in the vicinity. The water feasibility study shall include the following information at a minimum:
a. The projected water demands of the Data Center;
b. The source of water to be used;
c. A description of how water will be used, including the amount or proportion of
water to be used for each purpose (e.g. cooling, humidity control, fire suppression, and domestic usage);
d. The long-term safe yield of the water source;
5
e. A description of the amount or portion of water withdrawn that will be recycled
or discharged and by what means;
f. A geologic map of the area with a radius of at least one mile from the site;
g. The location of all existing and proposed wells within 1,000 feet of the property
boundary, with a notation of the capacity of all high-yield wells;
h. The location of all surface waters, including perennial and intermittent streams,
rivers, lakes, reservoirs, ponds, wetlands, springs, natural seeps, and estuaries, within 1,000 feet of the property boundary;
i. A determination of the effects of the proposed water supply system on the
quantity and quality of water in nearby wells, surface waters, and the groundwater table;
j. A statement of the qualifications and the signature(s) of the person(s) preparing
the study.
3. The applicant shall provide proof of review and approval from the Delaware River Basin Commission for projects proposing:
a. Water withdrawals of 100,000 gallons per day (gpd) or more over a 30-day
average from any source or combination of sources within the Delaware River Basin; or
b. Any consumptive water use of 20,000 gpd or more over a 30-day average from
any water source.
4. The applicant shall demonstrate that adequate means of wastewater disposal, including domestic wastewater and wastewater used for cooling or industrial purposes, have been provided and approved by the Sewage Enforcement Officer and/or the Pennsylvania Department of Environmental Protection.
H. Power Supply
1. If the applicant proposes to connect the Data Center to the electric grid, the applicant shall provide documentation from the applicable electric service provider certifying that that the necessary capacity is available and that electric service provider will serve the Data Center. Known impacts on electric rates or availability for other uses directly attributable to the Data Center project shall be noted.
2. Any energy generation system designed or used to supply power directly to a Data Center during normal operations, including solar, wind, fossil fuel, or nuclear energy generating systems, shall not be considered part of the Data Center use. Such systems shall be considered a separate use and shall be approved according to the zoning regulations applicable to such use.
I. Emergency Management
1. The applicant shall submit an Emergency Response Plan (ERP) prepared by a qualified professional. The ERP shall:
6
a. Be reviewed and accepted by the local fire department and emergency management
services as part of the [conditional use/special exception/land development] process;
b. Include detailed procedures for fire suppression, containment, ventilation, and
evacuation;
c. Include an evaluation of the access roads and hydrant locations within the site to
ensure suitable access for emergency equipment within the site;
d. Ensure that all first responders receive adequate training specific to the installed
system;
e. Include provisions for annual fire safety inspections demonstrating compliance
with fire safety standards to be performed by a qualified professional on behalf of the Data Center.
2. Any Data Center use proposing battery storage or any other device or group of devices capable of storing energy in order to supply electrical energy at a later time, whether the energy is stored for use on-site or off-site, shall demonstrate compliance with National Fire Protection Association (NFPA) Standard 855, Installation of Stationary Energy Storage Systems, or similar standards and must include fire suppression systems designed specifically for battery storage.
3. No Data Center shall be approved unless the applicant demonstrates that procedures for fire suppression, containment, ventilation, and evacuation are sufficiently protective of public health, safety and welfare.
J. Aesthetics
1. Any Data Center and Data Center Accessory Use building façade that faces a road, [ZONING DISTRICT], or existing residential use must incorporate at least two of the following design elements every 150 horizontal feet:
a. A change in building material, pattern, texture, or color;
b. A change in building height;
c. Building step-backs or recesses having a minimum depth of five (5) feet;
K. Parking
1. Data Centers are to be provided with at least one parking space per 8,000 square feet of floor area designed and intended to be accessible regularly by employees, or one parking space for every one employee, based upon the maximum number of employees on site during the largest shift, whichever is lesser.
Section 4: Severability. If any sentence, clause, section, or part of this Ordinance or of the Zoning Ordinance is for any reason found to be unconstitutional, illegal or invalid, such unconstitutionality, illegality or invalidity shall not affect or impair any of the remaining provisions, sentences, clauses, sections, or parts hereof. It is hereby declared as the intent of the [GOVERNING BODY] that this Ordinance and the Zoning Ordinance would have been adopted had such unconstitutional, illegal or invalid sentence, clause, section or part thereof not been included herein.
7
Section 5. Repealer. All Ordinances or parts of Ordinances conflicting with any provision of this Ordinance are hereby repealed insofar as the same affects this Ordinance.
Section 6. Codification. Pursuant to the [APPPLICABLE MUNICIPAL CODE] and the Pennsylvania Municipalities Planning Code, the [MUNICIPALITY] Zoning Ordinance shall hereby be codified to incorporate the above-referenced amendments.
Section 7. Effective Date. This Ordinance shall take effect five (5) days after its adoption.
Plain Text = Existing ordinance language to remain.
Text with a strike thru = Existing language proposed to be removed.
Underlined text = Proposed new language.
Chapter 18. Zoning
. . .
Article I, GENERAL PROVISIONS
Sec. 3.1 Definitions
Data center. "Data center" means a facility used to house computer systems and associated components, such as telecommunications and storage systems and which may include redundant or backup power supplies, redundant data communications connections, environmental controls such as air conditioning or fire suppression, and security devices.
Data processing facility. "Data processing facility" means facilities where electronic data is processed by employees including, but not limited to, data entry, storage, conversion or analysis, subscription and credit card transaction processing, telephone sales and order collection, mail order and catalog sales, and mailing list preparation.
Daytime. "Daytime" means, for the purposes of noise regulation including noise regulations contained in Section 5.1.65, that period of a day beginning at 7:00 a.m. and ending at 10:00 p.m., each day of the week.
Footprint. “Footprint” means total ground area of all buildings and structures on a lot, including anything with a roof such as porches or accessory structures. The footprint area is measured at ground level from the outside surface of exterior walls, or from the edge of the roof if there are no exterior walls.
Nighttime. "Nighttime" means, for the purposes of noise regulation including noise regulations contained in Section 5.1.65, that period of a day beginning at 10:00 p.m. and ending at 7:00 a.m., each day of the week.
Article II, BASIC REGULATIONS
Sec. 5.1.65 Data Center
. . .
Sec. 5.1.65 Data center.
A. Accessory data center.
1. Data center serving a permitted primary use is permitted as an accessory use if:
a. The data center is on the same site as the primary use;
b. The site’s primary user operates the data center for its own data; and
c. The aggregate area devoted to the data center and its support systems
and structures does not exceed 25% of the gross floor area of the primary use.
2. Accessory data center is not subject to subsection (c).
B. Minimum development requirements for data center.
1. Data center must be served by public water and public sewer. .
2. Any water cooling must use a closed loop or recycled water system.
3. Cooling water flushing and refills are limited to times approved by Albemarle County Service Authority or Rivanna Water and Sewer Authority. C. Setbacks – Data center buildings and all associated equipment and accessory structures
(such as generators, HVAC, and battery backup) must be set back at least (i) 200 feet from all lot lines and (ii) 500 feet from the Rural Areas zoning district. as follows: 1. For property located outside of the Data Center Overlay district, 200 feet from all lot lines and 500 feet from the Rural Areas zoning district, 2. For property located within the Data Center Overlay district, 200 feet from the boundaries of the district.
D. Generators
1. Routine generator exercise maintenance is limited to Monday – Friday between the hours of 10 a.m. and 4 p.m.
2. Generators must be enclosed in a level 3 enclosure or other enclosure limiting sound to 70 dBA measured 23 feet from the generator. All equipment onsite must comply with Section 4.18, including maximum sound levels at all lot lines. 3. Onsite generators must meet or exceed EPA Tier 4 emission standards.
4. Battery Energy Storage Systems are permitted, E. Special exceptions. Subsection (a)(1) and (b)(1) may not be modified or waived by
special exception.
E. Landscaping/Screening
a. Fencing may not be placed in front of landscaping adjacent to roads. There must
be landscaping in front of any fence adjacent to public roads. Barbed wire fencing is not permitted.
b. Tree plantings adjacent to public roads, residential and rural areas zoning, must
consist of a minimum of three staggered rows of evergreen trees from a list approved by the Director of Community Development, planted 15 feet on center. The Director of Community Development or their designated agent may require
the plantings to be placed where they will best reduce noise from the facility and block the view from public streets and nearby properties. F. Building Design
1. Any building facade visible from public streets or property abutting the data center overlay district, which is zoned residential or rural areas, must incorporate a differentiation that breaks the mass of the facade every 100 horizontal linear feet by including at least one of the following changes in form and one of the following design elements:
a. change in building height of a minimum of 5’ for buildings less than 30’ tall
and 10’ for buildings 30’ tall and taller, or
b. building step-backs or recesses with a minimum depth of 2.5’
c. design elements that are either:
i. change in building materials, or ii. change in pattern, texture and/or color d. The building design must include a main entrance that is differentiated from
the rest of the façade. 2. The following materials are not permitted on building façades: aluminum siding, unfinished or untreated wood siding, plywood siding (T1-11), vinyl siding, scored stucco (imitation brick or stone), and foam-based products.
G. Noise
1. Any noise that emanates from all activity associated with any data center is limited to a maximum sound level of 60 dBa during the daytime and 55 dBa at nighttime. Such levels are measured at the property line if the data center is not in the data center overlay district. Such levels are measured at the boundary of the data center overlay district if the data center is in the data center overlay district. The maximum sound level in this section does not apply to:
a. Demolition work on buildings, structures, or appurtenances and/or the testing
of generators consistent with the requirement of the Department of Environmental Quality;
b. Any situation arising from sudden and reasonably unforeseen events (beyond
the control of the facility operator) that require the response of emergency vehicles or temporary use of emergency generators.
c. Generator testing conducted between 10:00 a.m. until 4:00 p.m. unless
testing at a time outside of this range is required by the Department of Environmental Quality.
2. Noise studies. The following noise propagation studies must be conducted and submitted to the Zoning Administrator:
a. A sound modeling study that demonstrates compliance with the maximum
sound levels must be submitted prior to approval of a final site plan. This study must be specific to the proposed site topography, layout and building type, scale, height and construction proposed. This study must show noise conditions at the site prior to project development at set locations determined by the Zoning Administrator and must provide model-predicted noise conditions resulting from the proposed project post-development.
b. The sound study must be prepared by a professional engineer licensed in the
Commonwealth in accordance with ISO 9613 standards.
c. The sound modeling study must include recommendations for sound
mitigation measures, if they are necessary for the use to comply with maximum sound levels. These mitigation measures, if applicable, must be reflected on the site plan and incorporated into conditions of site plan approval. If mitigation measures are building related, they must be included in the building plans prior to issuance of building permit(s). In the event the sound modeling study shows compliance with the maximum sound levels of Sec. 5.1.65 (G) (1) without the use of sound mitigation, no mitigation measures are required.
d. Within 60 days of issuance of a certificate of occupancy for each phase or
development and at any time the Zoning Administrator requests it, a post- development sound study must be submitted. The study must be conducted at a time generally known for peak data center cooling operations. In the event the study shows that the use exceeds maximum allowable decibel levels, the operator must immediately undertake all necessary efforts to comply.
H. Equipment – All equipment necessary for cooling, ventilating, or otherwise operating the
facility must be contained within an enclosed building, walled courtyard or roof parapet with a wall of sufficient height to eliminate visibility of the equipment from public streets or adjacent properties. Access to any walled courtyard or enclosed building must provide for solid doors/gates. Emergency power generators must be enclosed in a Level 3 enclosure as provided for in Sec. 5.1.65 (D)(2). I. Uses by special use permit – Any data center that requires a special use permit must include in that application, information indicating how power will be supplied to the data center. J. Special exceptions. Subsections (A)(1) and (B)(1) may not be modified or waived by
special exception.
Chapter 18. Zoning
. . .
Article III District Regulations
Section 30.8 Data Center Overlay District
Section 30.8.1 Purpose and Intent
The Data Center Overlay District is to allow the development of data centers where existing infrastructure can adequately support the proposed use and where negative impacts to nearby properties and resources are limited.
Section 30.8.2 Boundaries of District Section 30.8 applies to all privately and publicly owned lands within the county that are within the boundaries of the Data Center Overlay District and depicted as “Tier 1” or “Tier 2” on the maps entitled “Data Center Overlay District”, which are hereby adopted as the zoning map of the Data Center Overlay District. Section 30.8.3 Permitted Uses
1. Tier 1
a. By Right. The following uses shall be permitted by right in Tier 1 designated
areas:
i. The uses permitted by right in the underlying zoning district.
ii. Data center up to 125,000 Square Foot footprint.
b. By Special Use Permit. The following uses shall be permitted by special use
permit in Tier 1 designated areas:
i. The uses permitted by special use permit in the underlying zoning
district. ii. Data center over 125,000 square foot footprint.
2. Tier 2
a. By Right. The following uses shall be permitted by right in Tier 2 designated
areas:
i. The uses permitted by right in the underlying zoning district.
ii. Data center up to 500,000 Square Foot footprint.
b. By Special Use Permit. The following uses shall be permitted by special use
permit in Tier 2 designated areas:
i. The uses permitted by special use permit in the underlying zoning
district. ii. Data center over 500,000 square foot footprint.
1
FILE OF THE CITY CLERK
ADMINISTRATIVE ORDINANCE NO. - 2025
ADMINISTRATION BILL - NO. - 2025
INTRODUCED – , 2025
ADOPTED BY COUNCIL – , 2025
AN ORDINANCE OF THE LANCASTER CITY COUNCIL AMENDING CHAPTER 300 OF THE CODE OF THE CITY OF LANCASTER—ZONING TO RECOGNIZE COMPUTER DATA CENTERS AS A USE REQUIRING SPECIAL REGULATION; PROVIDING DEFINITIONS; ALLOWING DATA CENTERS BY SPECIAL EXCEPTION IN THE CM AND SM ZONES, ESTABLISHING PERFORMANCE STANDARDS: PROVIDING FOR THE REPEAL OF INCONSISTENT ORDINANCES; PROVIDING FOR THE SEVERABILITY OF THE ORDINANCE; AND PROVIDING FOR AN EFFECTIVE DATE OF THE ORDINANCE
WHEREAS, the City of Lancaster is committed to protecting the health, safety, and welfare of its residents through thoughtful and responsible land use regulation; and
WHEREAS, the City of Lancaster’s Comprehensive Plan (2023) outlines guiding principles that represent Lancaster’s vision for the betterment of its economy, environment, and quality of life for all its residents; and
WHEREAS, the Comprehensive Plan calls for updating city codes and ordinances to align with adopted policies, actions, and maps; and
WHEREAS, the City of Lancaster is undertaking such updates, including revisions to the zoning ordinance, subdivision and land development ordinance (SALDO), and official map; and
WHEREAS, in the interim, there is a need to regulate a new land use not expressly contemplated in the city’s existing zoning regulations, namely data centers; and WHEREAS, data centers warrant special consideration related to energy and water utilization as well as noise and air pollution; and
WHEREAS, the City seeks to establish interim regulations for data centers in advance of further updates to zoning, SALDO, and the official map:
NOW, THEREFORE, BE IT ORDAINED by the Council of the City of Lancaster that the City of Lancaster Code Chapter 300—Zoning shall be amended as follows:
2
SECTION 1. Amendment to Chapter 300, Article XVII, Section 83, Definitions.
The Code of the City of Lancaster Chapter 300—Zoning, Section 83, Definitions, is hereby amended to include the following definitions:
DATA CENTER: A facility whose primary purpose is the centralized storage, processing, management, or dissemination of digital data, information, or applications. This includes but is not limited to server farms, cloud computing hubs, colocation centers, and telecommunication switching hubs. Data centers typically house large-scale computer systems and supporting infrastructure such as backup generators, cooling systems, and uninterruptible power supplies. A data center generally includes environmental controls such as air conditioning and fire suppression, redundant/backup power supplies, redundant data communications connections and high security.
SECTION 2. Amendment to Attachment 2: Table of Permitted Uses.
Attachment 2 is hereby amended insofar as it references the “Manufacturing and Industrial” section of Attachment 2, insert the following uses as special exceptions:
Use MU CB1 CB C3 CM SM
Data Center — — — --- S S
SECTION 3. Amendment to Article VII: Supplementary District Regulations.
There shall be enacted a new Section, 300-40.1, Data Centers
All data centers shall comply with the following:
A. Noise
(1) A Noise Mitigation Plan shall be submitted with the zoning application, including, at a minimum, a detailed acoustic study showing the amount of noise to be produced by normal operations and strategies to minimize noise and achieve a neutral impact on the surrounding community.
(2) There shall be no “noise disturbance” as that term is defined in the City’s Lancaster Noise Control Ordinance, at any adjoining property lines. The Plan must be prepared and certified by a professional acoustical engineer. The Plan shall be subject to review and comment by the City. The City shall have the right to require supplemental or amended plans based upon comments by the professional staff of the City prior to any zoning approval.
B. Air Quality
3
(1) Backup power equipment shall minimize air pollutant emissions and meet or exceed applicable state and federal laws regulating emissions. In the case that backup generators are used, EPA Tier 4 emissions standards, or equivalent, must be achieved.
(2) Annual testing shall be performed, and reports shall be provided to the City and other relevant state and federal agencies to ensure that data center equipment is performing as designed and emissions from the data center do not exceed allowable limits.
C. Energy Use
(1) Data centers shall make good faith efforts to maximize use of renewable and/or clean energy for all electrical and cooling needs, either through on-site generation or verifiable power purchase agreements (PPAs).
(2) An Energy Management Plan shall be submitted with the zoning application detailing at a minimum, annual electricity demand, what supply sources will be utilized, energy storage capacity (if applicable) and efforts made to maximize use of renewable or clean energy. The Plan will be prepared and certified by a professional engineer. The Energy Management Plan shall be subject to review and comment by the City. The City shall have the right to require supplemental or amended plans based upon comments by the City prior to any zoning approval.
D. Water Utilization
(1) A Water Utilization Report shall be submitted with the zoning application detailing, at a minimum the total daily intake volume and source(s) of that water, discharge volumes and destinations, cooling system type and efficiency, and shall demonstrate compliance with the city’s stormwater ordinances and regulations. The Report shall be prepared and certified by a professional engineer. The Report shall be subject to review and comment by the City. The City shall have the right to require supplemental or amended reports based upon comments by the City prior to any zoning approval.
E. Electronic Waste
(1) An Electronic Waste Plan shall be submitted with the zoning application outlining procedures for safe removal and recycling or disposal of server infrastructure, hazardous materials, batteries, electronic waste, and related products, which will apply in cases when the data center is updated or decommissioned. The Report shall be subject to review and comment by the City. The City shall have the right to require supplemental or amended reports based upon comments by the City prior to any zoning approval.
F. Heat Mitigation
(1) A Thermal Impact Mitigation Plan shall be submitted with the zoning application, including, at a minimum, strategies for waste heat reuse or dissipation and vegetative or green roof and/or site design to offset urban heat island effects. The Plan will be prepared and certified by a professional engineer. The Thermal Impact Mitigation Plan shall be subject to review and comment by the City. The City shall have the right to require supplemental or amended plans based upon comments by the City prior to any zoning approval.
4
G. Floodplain Exclusion
(1) No data center shall be located within any 100-year or 500-year floodplain as shown in the most recent Flood Insurance Map Rate Maps prepared by the Federal Emergency Management Agency for the City.
H. Parking Requirements
(1) Parking facilities shall comply with Article VIII Off-Street Parking and Loading Requirements.
(2) Efforts shall be made to build only the necessary amount of parking for data center operations and to minimize the amount of impervious parking surface.
I. Setbacks
(1) All Data Center buildings shall be set back a minimum of 200 feet from the lot line of a property used for residential or community purposes and 200 feet from any residentially zoned district or PO District.
(2) Ground mounted equipment used for cooling, ventilation, heat or power shall be set back a minimum of 300 feet from the lot line of any property used for residential or community purposes and a minimum of 300 feet from any residentially zoned district or PO District.
J. Fencing
(1) Fences shall be constructed of good quality and visually appealing materials such as ornamental steel or other durable security-grade materials. Features such as barbed wire and razor wire are prohibited.
K. Buffer Yards
(1) All Data Center operations shall provide buffer yards along all property boundary lines, except for areas of ingress and egress into the site.
(2) A minimum 100-foot-wide buffer yard shall be provided along the entire length of any public street frontage of any property and along any property line which abuts property used for residential or community purposes or zoned residential or PO District.
(3) A minimum 50-foot-wide buffer yard shall be provided along any property line adjacent to a non-residential use or zone.
(4) No improvements other than essential utilities shall cross the buffer. If a utility must do so, it shall be by the minimum traversal distance and then only if every precaution is used to replace any lost visual screen with a screen wall or comparable feature.
(5) Buffer yards shall be composed of a combination of landscaping and screening techniques. A holistic landscape plan prepared by a professional landscape architect is required.
5
(a) Use of existing vegetation in buffer yards is strongly encouraged and may be substituted for new plantings if approved by the City.
(b) Earthen berms, with no grade steeper than 3:1 shall be planted on the top and along exterior slopes.
L. Screening
(1) Screening shall be provided to reduce the noise output and visual impact of any facilities and equipment necessary for cooling, ventilating or operating the facility, including but not limited to power generators, accessory electrical substations, or other power supply equipment.
(2) Ground-mounted facilities and equipment shall be fully enclosed when technically feasible. If full enclosure is deemed infeasible by the City, the equipment must be screened by a visually solid barrier such as a wall, fence, building and/or natural materials that absorb noise and protect neighboring properties from noise pollution.
(3) Rooftop facilities equipment shall be screened by a parapet wall, equipment penthouse, or visually solid screen on all four sides. Rooftop equipment that is visible above the parapet wall shall be set back from the exterior or parapet wall a distance no less than the height of said equipment.
M. Safety
(1) A detailed Emergency Response Plan shall be submitted with the zoning application, showing at a minimum that the data center has a plan in effect to deal with emergencies resulting from flood, fire, explosion, and catastrophic weather events. The Emergency Response Plan shall be subject to review and comment by the City. The City shall have the right to require supplemental or amended plans based upon comments by the City prior to any zoning approval.
(2) Battery storage systems must meet fire suppression standards, be UL-certified, and follow hazardous material handling protocols.
N. Community Engagement
The developer of the data center shall hold a public informational meeting prior to any Zoning Hearing Board or Planning Commission review. The meeting shall be publicized and conducted in a manner reasonably calculated to inform the general public of the data center application and will be attended by representatives of the data center with knowledge of the general nature of the proposed use. The applicant may, but is not required to, allow persons who are unable to attend the meeting to view the proceedings via a remote electronic open meeting platform.
SECTION 4. Section 330-41.A.
Parking Requirements, Use Classification, Manufacturing or Industrial Establishment, Required Parking shall be amended to read:
6
“1 for each 3 employees, computed on the basis of the estimated maximum number of employees on duty at any one time, but not less than 1 per 3,000 square feet of gross floor area; provided, however, that data centers shall be required to provide parking solely based on the number of employees and not upon gross floor area, plus five spaces for visitors.”
SECTION 5. Severability.
In the event any provision, section, sentence, clause or part of this ordinance shall be held to be invalid, such invalidity shall not affect or impair any of the remaining provisions, sections, sentences, clauses or parts of this Ordinance; it being the intent of the City of Lancaster that the remainder of the Ordinance shall be and remain in full force and effect.
SECTION 6. Repealer.
All ordinances or resolutions or parts of ordinances or resolutions insofar as they are inconsistent herewith are hereby repealed and rescinded.
SECTION 7. Effective Date.
This Ordinance shall become effective twenty days after its adoption.
DULY ORDAINED AND ENACTED this ____ day of ___________, 2025, by the Council of the City of Lancaster, Lancaster County, Pennsylvania in lawful session duly assembled.
CITY OF LANCASTER
By:_____________________________
Danene Sorace, Mayor
ATTEST:
__________________
Bernard W. Harris, Jr.
City Clerk