The East Goshen Township Planning Commission is an advisory board to the Township Board of Supervisors. The Commission reviews all subdivision and land development applications, conditional use applications, zoning hearing board applications and makes recommendations to the Board of Supervisors.  The Commission also reviews or drafts Zoning Ordinance Amendments. Each member is appointed by the Board of Supervisors.

  • Composed of seven East Goshen Township residents each serving a four-year term.
  • Formal Meetings are held the 4th Tuesday of each month at 7:00 P.M.
  • Workshop Meeting are held on an as needed basis
  • All township meetings are held at the Township Building and are open to the public
Planning Commission Members Term Expiration Date
John Stipe, Chair  2026
Dan Truitt, Vice Chair 2027
Daniel H. Daley 2027
Michael Koza 2026
Ernest Harkness 2026
Karen Martynick 2029
William Kaufman 2029
Larry Massaro, BOS Liaison
Kelly Krause, Staff Liaison

 

Draft Ordinance-Zoning Amendment Regulating Data Centers by Conditional Use 9.24.26

Click here to view – May 4th Documents for Malvern Institute and East Whiteland Special Study.

Related News

PLANNING COMMISSION CONSIDERS UPGRADES TO AQUA FACILITY

Wednesday, November 18, 2026

At its September meeting, the East Goshen Planning Commission reviewed a conditional use application from Aqua Pennsylvania to upgrade its Hunt Country well treatment facility located on Thorncroft Drive. The upgrade is required to meet new maximum contaminant levels (MCLs) for PFAS in drinking water that were enacted last year by the U.S. Environmental Protection […]

View Article

From the Planning Commission: Addressing Potential Data Center Development in East Goshen Township

Wednesday, September 30, 2026

As the demand for artificial intelligence accelerates, municipalities throughout Pennsylvania have found themselves navigating complex regulations, legal challenges, and community debates about large-scale data centers. While no data center projects are currently proposed in East Goshen, township officials are proactively addressing potential impacts by updating zoning ordinances to create strict standards that will apply should […]

View Article

More News

Documents

Notice: this accessible version was created automatically from the original document. The transcription may not be 100% accurate. It is provided for searching and for screen readers; please refer to the original document for the official version.

EAST GOSHEN TOWNSHIP PLANNING COMMISSION

East Goshen Township Administration Building 1580 Paoli Pike, 2nd Floor, West Chester, PA 19380 Meeting Agenda

REVISED Tuesday, June 23, 2026, at 7:00 PM

Planning Commission Members: John Stipe, Chairman Dan Truitt, Vice Chairman Daniel H. Daley Ernest Harkness William Kaufman Michael Koza Karen Martynick Larry Massaro, BOS Liaison Kelly Krause, Zoning Officer/Staff Liaison Agenda Items:

1. Call to Order / Pledge of Allegiance and Moment of Silence 2. Chairman will ask if anyone is going to record the meeting. 3. Review of Tracking Log / Determine need for Workshop Meeting 4. Public Comment on Non-Agenda Items 5. Approval of Minutes a. May 26, 2026 6. Acknowledge Receipt of New Applications (Initial Submission) a. Subdivision and Land Development Applications b. Conditional Uses Applications c. Zoning Hearing Board Variances d. Ordinance Amendments 7. New Business a. Review and recommendation of 971 Cornwallis Drive- 3-Lot Subdivision, Prelim/Final Plan b. Discuss letter to Senator Committa in opposition of House Bill 2186, to mandate Accessory

Dwelling Units (ADUs) as a by-right accessory use 8. Old Business a. Review and consideration of 949 & 951 Cornwallis Drive- Prelim/Final Lot Line Change Plan b. Zoning Ordinance Amendment Draft- AI Data Centers 9. Liaison Reports 10. Correspondence 11. Announcements 12. Next Meeting – Tuesday, July 28, 2026, at 7:00 PM 13. Adjournment Bold Items indicate new information to review or discuss.

PROJECT DESCRIPTION Date Filed Start Date Twp.

Engineer

Review

CCPC

Review

Conserv.

Board

Review

Extension

Date

PC

Deadline

Meeting

BOS

Deadline

Meeting

Hearing

Date

Final Action

Deadline (90

days) Comments

949 & 951 Cornwallis Drive- Prelim/Final Lot Line Change 4/28/2026 4/28/2026 6/10/2026 pending n/a n/a 6/23/2026 7/21/2026 n/a 7/27/2026 Applcant seeking recommendation to seek final

approval by the BoS on 7/21/2026

Zoning Ordinance Amendment-Data Centers n/a 11/25/2025 n/a n/a n/a n/a n/a n/a n/a n/a Discuss Data Center draft amendments

971 Cornwallis Drive- 3-Lot Subdivision 5/14/2026 5/26/2026 pending pending 7/8/2026 n/a 7/28/2026 8/18/2026 n/a 8/24/2026 Applicant to present plan at 6/23/2026 Planning

Commission Meeting

10-Year Comprehensive Plan Review n/a 4/22/2025 n/a n/a n/a n/a n/a n/a n/a n/a pending

Westtown Comprehensive Plan 3/3/2026 3/3/2026 n/a n/a n/a n/a 3/24/2026 4/16/2026 n/a 4/17/2026 BoS recommended support 4/16/2026

949 & 951 Cornwallis Drive- Sketch Plan 2/4/2026 2/24/2026 4/13/2026 pending n/a n/a n/a n/a n/a n/a Prelim/Final Plan Submitted

1409 Manley Road- Dimensional Variance 2/13/2026 2/13/2026 n/a n/a n/a 5/15/2026 3/24/2026 4/16/2026 5/12/2026 5/15/2026 Variance granted on 5/12/2026- Awaiting submission of

subdivision plans

West Whiteland Comprehensive Plan 4/9/2026 n/a n/a n/a n/a n/a 4/28/2026 5/5/2026 n/a 6/3/2026 BoS recommended support 5/5/2026

17 Treemont Drive- Dimensional Variance 5/8/2026 5/8/2026 n/a n/a n/a n/a 5/26/2026 6/2/2026 6/9/2026 6/7/2026 Variance granted by ZHB 6/9/2026

PROJECTS COMPLETED IN 2026

Bold = New application or action required

East Goshen Township Planning Commission

Application Tracking Log

June 23, 2026

PENDING PROJECTS

PC 5-26 -26 draft 1

DRAFT 1 EAST GOSHEN TOWNSHIP 2 PLANNING COMMISSION MEETING 3 May 26, 2026 4 5 The East Goshen Township Planning Commission held their regular monthly meeting on Tuesday, 6 May 26, 2026 at 7:00 pm in the Township Building. 7 8 Members present are highlighted: 9 John Stipe - Chairman 10 Dan Truitt, Vice Chairman 11 Dan Daley 12 Ernest Harkness 13 Willian Kaufman 14 Michael Koza 15 Karen Martynick 16 17 Also present was: 18 Kelly A. Krause, Zoning Officer 19 Larry Massaro , BOS Liaison, Township Supervisor 20 Ann Duffield, Township Supervisor 21 22 23 COMMON ACRONYMS: 24 BOS – Board of Supervisors CPTF – Comprehensive Plan Task Force 25 BC – Brandywine Conservancy CVS – Community Visioning Session 26 CB – Conservancy Board SWM – Storm Water Management 27 CCPC – Chester Co Planning Commission ZHB – Zoning Hearing Board 28 29 FORMAL MEETING – 7 p.m. 30 1. John called the meeting to order at 7:00 pm. He led the Pledge of Allegiance and asked for a 31 moment of silence to remember our first responders and military. 32 2. John asked if anyone would be recording the meeting and if there were any public comments 33 about non-agenda items. There was no response. 34 3. The tracking log was checked and no need for a workshop meeting. John noted that the 35 Zoning Board Hearing for 1409 Manley Rd. is scheduled for May 12, 2026. 36 4. The minutes of the April 28, 2026 meeting were approved as amended. 37 38 39 CHAIRMAN’S REPORT – 40 None 41 42 43 ACKNOWLEDGE RECEIPT OF NEW APPLICATIONS (INITIAL SUBMISSION)- 44 None 45 46 47 NEW BUSINESS – 48 1. Review 949 & 951 Cornwallis Drive – Prelim/final Lot Line Change Plan 49 Joel D. Comanda of Inland Design was present as well as the owners of the property Geoffrey and Nancy 50 Fay. Mr. Comanda gave an overview of the lot line change request. Currently the lots are side by side 51 with single family dwellings but non-conforming in width. They want to reconfigure the lot line to keep 52 the dwelling at 951 and demolish 949 so the second lot is to the rear. They received an engineer letter for 53

PC 5-26 -26 draft 2

the sketch plan but not this revised plan. Dan D. feels they need the engineer review letter. John 1 commented that the PC will not vote on it now. 2 3 2. 17 Treemont Dr. – Dimensional Variance Application - Property owners Erin and Bryan Sheffield 4 were present. Erin explained the proposed plan to build a set of wooden steps to get to their back yard. 5 There is a deep grade due to erosion. The septic tank is right up next to the deck so that is why they want 6 steps coming out of the side. The hardship is the grade. Ernest gave advice for presenting to the Zoning 7 Hearing Board. Dan D. is concerned it hasn’t been surveyed for encroachment into the side yard setback. 8 Dan D. moved to recommend that the Board of Supervisors support this request for a deck with steps that 9 may encroach on the side yard setback. Dan T. seconded the motion. The motion passed unanimously. 10 11 OLD BUSINESS 12 Zoning Ordinance Amendment Draft - AI Data Centers 13 John spoke about setbacks from Comcast to the daycare center. The County ordinance was reviewed. 14 Dan T. feels the standards should apply to anything in the I1 district not just a data center. Karen 15 commented about the noise. She feels it doesn’t refer to vibrations. Also, she mentioned reasons to use 16 generators. This was discussed. Setbacks were discussed. Gerald Sexton, Chairman of the Pipeline Task 17 Force asked for clarification of the red and black print in the County ordinance. Kelly explained that the 18 red is new discussion. Gerald pointed out that pipelines were discussed on the second page in red. A 19 Pipeline Awareness Study should be done. He verified that when there is a final draft, all ABCs will be 20 able to review it before it goes to the BOS. 21 Kelly will upgrade the draft for next month’s meeting. 22 23 24 LIAISON REPORTS 25 1. Board of Supervisors - Larry mentioned that they are still considering a presentation by a company 26 that can assist with including the residents in revising the Comprehensive Plan. 27 28 29 ANY OTHER MATTER 30 None 31 32 CORRESPONDENCE 33 None 34 35 ADJOURNMENT 36 There being no further business, Dan T. made a motion to adjourn the meeting. Bill seconded the 37 motion. The meeting was adjourned at 9:00 pm. 38 The next meeting will be held on Tuesday June 23, 2026 at 7 p.m. 39 40 Respectfully submitted, 41 42 43 44 45 Ruth Kiefer, Recording Secretary 46

158 West Gay Street, Suite 300 T: 610-429-8907 www.pennoni.com West Chester, PA 19380 Page 1 of 3

June 10, 2026

EGOST 00145

Attn: Kelly Krause, Zoning Officer East Goshen Township 1580 Paoli Pike West Chester, PA 19380

RE: Fay, 949 & 951 Cornwallis Drive Preliminary/Final Subdivision Plan Review

Dear Kelly:

As requested, we have reviewed the following information, prepared by InLand Design, regarding the referenced submission:

“Preliminary/Final Subdivision Plan for 949 & 951 Cornwallis Drive” (four sheets) dated January 30, 2026, last revised April 22, 2026; and

Application and supporting documents.

The applicants/owners, Geoffery and Nancy Fay, propose to adjust the existing subdivision line between UPI 53-4-61 (±2.1 acres) and UPI 53-4-60 (±1.9 acres) and create a new flag lot on the second lot. There is an existing dwelling on UPI 53-4-61 to remain, and an existing dwelling on UPI 53-4-60 that is proposed to be removed. The parcels are located on the northeast side of Cornwallis Drive (T-471) approximately 1,600 feet northwest of its intersection with Colonial Lane (T-472), within the R-2 Low Density Residential District. The existing dwelling to remain is served by a public sanitary sewer connection and a well.

Please note that the existing lots do not meet the Township requirement for lot widths at the building setback line and street line in the R-2 Zoning District. The proposed subdivision would increase the lot width at the building setback line and create greater conformity with the Township Code.

The applicant is requesting the following eight (8) waivers:

1. From §205-28 requiring preliminary submission prior to final plan submission. 2. From §205-36 requiring a landscape plan submission. 3. From §205-37 requiring a stormwater management plan submission. 4. From §205-37.1 requiring a note regarding individual on-lot stormwater management. 5. From §205-38 requiring a supplementary studies submission. 6. From §205-39 requiring a Traffic Impact Study submission. 7. From §205-39 requiring a Water Study submission. 8. From §205-39 requiring a Pipeline Awareness Study submission.

As only one (1) new building lot is proposed, and conceptual level detail provided, we have no objections to the above waiver requests.

EGOST00145 Fay, 949 & 951 Cornwallis Drive Kelly Krause, Zoning Officer June 10, 2026 Page 2 of 3

We offer the following comments:

ZONING (§240)

1. While the proposed lot configuration of UPI #53-4-60 does not meet the width requirement at the street line for the R-2 Low Density Residential Zoning District, flag lots are permitted by per §240-23.B(2)(b)[2].

2. For proposed flag lots, the applicant shall prove to the satisfaction of the Township that the proposed driveway will have adequate access for emergency vehicles. (§240-23.B(2)(b)[2][d]) The Fire Marhsall may have additional comments.

3. A PADEP Sewage Facilities Planning approval or exemption is required for all subdivisions, even though no new flows are proposed at this time. (§240-24.F) The applicant has indicated that a waiver is pending.

4. For all new lots that abut an existing street which has a right-of-way less than that specified in Subsection A(3), the front and/or side street yard requirements shall be increased by the difference between the existing right- of-way and the right-of-way specified in Subsection A(3). It is the intention of this requirement to provide for a reasonable setback to accommodate the potential widening of the existing street. (§240-27.A(4)) The existing right-of-way on the plans is indicated at 33 feet wide. The plans have been revised from the sketch plan to indicate an additional 25-feet of right-of-way from the centerline of Cornwallis Drive to address this requirement.

5. All driveways entering onto any public street shall be located at least 60 feet from the intersection of any street center line and shall be designed in a manner conducive to safe ingress and egress. (§240-27.D(2)(a)) The “Conceptual Future Plan” (Sheet 4) indicates a driveway closer than 60 feet from the intersection of Cornwallis Drive & King George Court.

6. There is a chicken coop and shed within side yard of UPI #53-4-61. Chicken coops must be located to the rear of the dwelling and be located 20 feet from the rear property line and 15 feet from any side property line. (§240- 32.A(5)(c)) This appears to be an existing nonconformity.

SUBDIVISION AND LAND DEVELOPMENT (§205)

7. All proposed on-site water supply systems shall have a permit certified by the Chester County Health Department. (§205-66.E) General Note No. 12 address the same.

GENERAL

8. We recommend that all plan sheets be recorded.

9. The Township shall be contacted prior to any modifications to existing sewer laterals.

EGOST00145 Fay, 949 & 951 Cornwallis Drive Kelly Krause, Zoning Officer June 10, 2026 Page 3 of 3

Should you have any further questions or comments, please contact the undersigned.

Sincerely, PENNONI ASSOCIATES INC.

Nathan M. Cline, PE Township Engineer

cc (via e-mail): Project Team Township Team

KING GEORGE

COURT

CORNWALLIS DRIVE

X X X

X

LOCATION MAP

SCALE: 1" = 2000'

SITE

SOILS DESCRIPTION

SYMBOL DESCRIPTION SLOPE AVAILABLE WATER CAPACITY

DRAINAGE

CLASS

DEPTH TO

S.H.W.T.

DEPTH TO BEDROCK

CAPABILITY

UNIT

HYDROLIC SOIL GROUP

CaB CALIFON LOAM 3% - 8% LOW ABOUT 4.4 INCHES

MODERATELY WELL DRAINED

ABOUT 6 TO 36

INCHES

20 TO 99 INCHES 2e D

GdB GLADSTONE GRAVELLY LOAM 3% - 8% MODERATE ABOUT 8.4 INCHES WELL DRAINED MORE THAN 80

INCHES

60 TO 80 INCHES 2e B

ZONING DATA (EXISTING CONDITIONS) R-2 LOW DENSITY RESIDENTIAL DISTRICT

ALL OTHER USES REQUIRED UPI: 53-4-60 UPI: 53-4-61

MINIMUM LOT AREA 1 ACRE 1.888 ACRES 2.046 ACRES

MINIMUM LOT WIDTH @ BUILDING LINE 150 FEET 105.00 FEET * 105.00 FEET *

MINIMUM LOT WIDTH @ STREET LINE 60 FEET 105.00 FEET 105.00 FEET

MAXIMUM BUILDING COVERAGE 25% 1.5% (1,273 S.F.) 2.0% (1,824 S.F.)

MAXIMUM IMPERVIOUS COVERAGE 35% 4.1% (3,383 S.F.) 5.3% (4,731 S.F.)

MAXIMUM BUILDING HEIGHT 3 STORIES & 30 FEET EXISTING EXISTING

MINIMUM FRONT YARD SETBACK 45 FEET 94.3 FEET 96.3 FEET

AVERAGE FRONT YARD SETBACK [1] 60 FEET N/A N/A

MINIMUM SIDE YARD SETBACK 20 FEET 28.4 FEET 26.8 FEET

MINIMUM REAR YARD SETBACK 50 FEET 562.5 FEET 606.1 FEET

[1] TO OBTAIN MORE FLEXIBILITY IN PLACING BUILDINGS IN ALL RESIDENTIAL SUBDIVISIONS OF TWO OR MORE LOTS, AN AVERAGE BUILDING SETBACK LINE OF 60 FEET AND A MINIMUM BUILDING SETBACK OF 45 FEET SHALL BE REQUIRED.

* EXISTING NON-CONFORMITY

OWNER OF RECORD:

GEOFFREY F. & NANCY A. FAY 951 CORNWALLIS DRIVE WEST CHESTER, PA 19382

GRAPHIC SCALE

( IN FEET ) 1 Inch = 30'

B

E

U

D

F

O

R

Y

O

E

Y

G

S

!

S

1-800-242-1776

P

E

N

L

L

A

C

N

I

A

N

Y

L

V

I

A

O

N

C

A

L

L

E

E

S

T

M

Pennsylvania One Call System

PA. act 172 of 1986 requires

three working days notice

Serial Numbers:

PENNSYLVANIA ACT 187 REQUIREMENTS: InLand Design, LLC does not guarantee the accuracy of the locations for existing subsurface utility structures shown on the plans, nor does InLand Design, LLC guarantee that all subsurface structures are shown. The contractor shall verify the location and elevation of all underground utilities and structures before the start of work.

S H E E T

Project No.

Checked by:

Drawn by:

Scale:

Date: No. Date: Description: COPYRIGHT InLand Design, LLC expressly reserves its common law copyright and all other proprietary rights in these plans. All drawings, specifications and copies thereof are and shall remain the property of InLand Design, LLC. They are to be used only in respect to this project and are neither to be used on any other project, nor are they to be assigned to any third party without first obtaining the expressed written permission and consent of InLand Design, LLC. Any re-use without written permission, verification, consent or adaptation by InLand Design, LLC for the specific purpose intended, will be at the third party's sole risk and without liability or legal exposure to InLand Design, LLC the third party shall further indemnify and hold harmless InLand Design, LLC from all claims, damages, losses, and expenses arising thereto or resulting therefrom. 16 Hagerty Blvd. West Chester, PA 19382 www.InLandDesign.net

Phone: (484) 947-2928

Fax: (484) 947-2946 Info@InLandDesign.net

I L DESIGN N AND Engineering, Surveying & Land Planning

12664 2

OF 4

EXISTING CONDITIONS, CONSERVATION &

DEMOLITION PLAN FOR

GEOFFREY & NANCY FAY 949 & 951 CORNWALLIS DRIVE WEST CHESTER, PA, 19382 EAST GOSHEN TOWNSHIP • CHESTER COUNTY • PENNSYLVANIA

PRELIMINARY / FINAL SUBDIVISION PLAN 01/30/2026

1" = 30'

LRL

DWN

20252111349

UPI: 53-4-60 | D.B. 8178 | PG. 758 & UPI: 53-4-61 | D.B. 2963 | PG. 202

1 4/22/2026 REVISED PER TOWNSHIP ENGINEER REVIEW COMMENTS & FOR FINAL PLAN APPROVAL

N:\12600\12664\Dwg\Sheets\Preliminary Submission\2 EXISTING CONDITIONS, CONSERVATION & DEMOLITION PLAN.dwg

PROFESSIONAL

REGISTERED

P

E

N

N

S

Y

L

V

A

N

I

A

C

O

M

M

O

N

W

E

A

L

T

H

O

F

LINDA R. LAYER

ENGINEER

NO.PE 076871

EXISTING 2' CONTOUR EXISTING 10' CONTOUR

EXISTING RIGHT OF WAY LINE

EXISTING CURB LINE

EXISTING WALL EXISTING FENCE LINE

EXISTING CONCRETE PAD, SIDEWALK OR PATIO PROPERTY BOUNDARY

EXISTING ROAD / PAVING

EXISTING STONE DRIVE

EXISTING SIGN

EXISTING SPOT ELEVATION

EXISTING TREE SYMBOLS

EXISTING UTILITY POLE

EXISTING SANITARY STRUCTURES & PIPE EXISTING SHRUBHLINE

SOILS LINE AND DESCRIPTION

EXISTING EASEMENT LINE

EXISTING LIGHT

EXISTING OVERHEAD WIRE

EXISTING BRICK SIDEWALK OR PATIO

EXISTING SANITARY CLEAN-OUT EXISTING TREELINE

ADJOINING PROPERTY LINE

EXISTING ROOF DRAIN

EXISTING WELL

LEGEND

EXISTING PROPERTY MONUMENTATION

EXISTING WATER LINE

EXISTING SETBACK LINE

TO BE REMOVED

EXISTING NET TRACT AREA

UPI: 53-4-61

GROSS LOT AREA 90,816 S.F. (2.085 ACRES)

AREA WITHIN RIGHT-OF-WAY 1,672 S.F. (0.038 ACRES)

LOT AREA 89,144 S.F. (2.046 ACRES)

UPI: 53-4-60

GROSS LOT AREA 83,911 S.F. (1.926 ACRES)

AREA WITHIN RIGHT-OF-WAY 1,672 S.F. (0.038 ACRES)

LOT AREA 82,239 S.F. (1.888 ACRES)

PROPERTY LINE TO BE EXTINGUISHED

EXISTING TREE TO BE REMOVED X

GENERAL NOTES:

1. BOUNDARY SHOWN BY PHYSICAL FIELD SURVEY PERFORMED IN AUGUST, 2025 BY INLAND DESIGN, LLC, WEST CHESTER, PA. BEARINGS HAVE BEEN ROTATED TO STATE PLANE COORDINATES. 2. THIS PLAN WAS PREPARED WITHOUT THE BENEFIT OF A CURRENT TITLE REPORT. 3. TOPOGRAPHIC INFORMATION AND IMPROVEMENTS SHOWN BY PHYSICAL FIELD SURVEY PERFORMED IN AUGUST, 2025 BY INLAND DESIGN, LLC, WEST CHESTER, PA. CONTOUR INTERVAL = 1 FOOT. 4. ELEVATIONS BASED ON NAVD88 DATUM. VERTICAL DATUM OBTAINED BY GPS OBSERVATIONS ON AUGUST 6, 2025. 5. THERE IS NO 100 YEAR FLOODPLAIN SHOWN ON THE PLAN, WHICH WAS DETERMINED FROM THE REFERENCE FIRM PANELS, MAP NUMBERS 42029C0215G & 42029C0160G, EFFECTIVE SEPTEMBER 29, 2017. 6. SOILS INFORMATION TAKEN FROM UNITED STATES DEPARTMENT OF

AGRICULTURE, NATURAL RESOURCE CONSERVATION SERVICE. 7. COMPLETENESS OR ACCURACY OF LOCATION AND DEPTH OF UNDERGROUND UTILITIES AND FACILITIES CANNOT BE GUARANTEED. THE CONTRACTOR MUST VERIFY THE LOCATION AND DEPTH OF ALL UNDERGROUND UTILITIES AND/OR FACILITIES PRIOR TO BEGINNING ANY EARTH-MOVING ACTIVITIES. 8. PUBLIC SEWER SERVICES BOTH PROPERTIES. 9. THE EXISTING SEWER LATERAL SHALL BE CUT AND CAPPED WITHIN 2 FEET OF THE HOUSE-SIDE OF THE CLEANOUT, AND IT SHALL BE DISCONNECTED FROM THE REMAINDER OF THE LATERAL PIPE TO THE HOUSE. THE CAP SHALL BE A SOLID FITTING OR OTHER METHOD AS APPROVED BY THE EAST GOSHEN PUBLIC WORKS DEPARTMENT (PWD). THE PWD MUST INSPECT AND APPROVE THE CUTTING AND CAPPING PRIOR TO BACKFILL. 10. A DEMOLITION PERMIT SHALL BE ACQUIRED TO REMOVE THE EXISTING HOME ON LOT 54-3-60. 11. THE EXISTING LOTS ARE SERVICED BY PRIVATE WELLS. A NEW WELL WILL BE PERMITTED FOR THE FUTURE HOME. 12. ALL PROPOSED ON-SITE WATER SUPPLY SYSTEMS SHALL HAVE A PERMIT CERTIFIED BY THE CHESTER COUNTY HEALTH DEPARTMENT.

KING GEORGE

COURT

CORNWALLIS DRIVE

LOCATION MAP

SCALE: 1" = 2000'

SITE

OWNER OF RECORD:

GEOFFREY F. & NANCY A. FAY 951 CORNWALLIS DRIVE WEST CHESTER, PA 19382

GRAPHIC SCALE

( IN FEET ) 1 Inch = 30'

B

E

U

D

F

O

R

Y

O

E

Y

G

S

!

S

1-800-242-1776

P

E

N

L

L

A

C

N

I

A

N

Y

L

V

I

A

O

N

C

A

L

L

E

E

S

T

M

Pennsylvania One Call System

PA. act 172 of 1986 requires

three working days notice

Serial Numbers:

PENNSYLVANIA ACT 187 REQUIREMENTS: InLand Design, LLC does not guarantee the accuracy of the locations for existing subsurface utility structures shown on the plans, nor does InLand Design, LLC guarantee that all subsurface structures are shown. The contractor shall verify the location and elevation of all underground utilities and structures before the start of work.

S H E E T

Project No.

Checked by:

Drawn by:

Scale:

Date: No. Date: Description: COPYRIGHT InLand Design, LLC expressly reserves its common law copyright and all other proprietary rights in these plans. All drawings, specifications and copies thereof are and shall remain the property of InLand Design, LLC. They are to be used only in respect to this project and are neither to be used on any other project, nor are they to be assigned to any third party without first obtaining the expressed written permission and consent of InLand Design, LLC. Any re-use without written permission, verification, consent or adaptation by InLand Design, LLC for the specific purpose intended, will be at the third party's sole risk and without liability or legal exposure to InLand Design, LLC the third party shall further indemnify and hold harmless InLand Design, LLC from all claims, damages, losses, and expenses arising thereto or resulting therefrom. 16 Hagerty Blvd. West Chester, PA 19382 www.InLandDesign.net

Phone: (484) 947-2928

Fax: (484) 947-2946 Info@InLandDesign.net

I L DESIGN N AND Engineering, Surveying & Land Planning

12664 3

OF 4

TITLE PLAN

FOR

GEOFFREY & NANCY FAY 949 & 951 CORNWALLIS DRIVE WEST CHESTER, PA, 19382 EAST GOSHEN TOWNSHIP • CHESTER COUNTY • PENNSYLVANIA

PRELIMINARY / FINAL SUBDIVISION PLAN 01/30/2026

1" = 30'

DWN

LRL

20252111349

UPI: 53-4-60 | D.B. 8178 | PG. 758 & UPI: 53-4-61 | D.B. 2963 | PG. 202

1 4/22/2026 REVISED PER TOWNSHIP ENGINEER REVIEW COMMENTS & FOR FINAL PLAN APPROVAL

N:\12600\12664\Dwg\Sheets\Preliminary Submission\3 TITLE PLAN.dwg

ZONING DATA (EXISTING CONDITIONS) R-2 LOW DENSITY RESIDENTIAL DISTRICT

ALL OTHER USES REQUIRED UPI: 53-4-60 UPI: 53-4-61

MINIMUM LOT AREA 1 ACRE 1.888 ACRES 2.046 ACRES

MINIMUM LOT WIDTH @ BUILDING LINE 150 FEET 105.00 FEET * 105.00 FEET *

MINIMUM LOT WIDTH @ STREET LINE 60 FEET 105.00 FEET 105.00 FEET

MAXIMUM BUILDING COVERAGE 25% 1.5% (1,273 S.F.) 2.0% (1,824S.F.)

MAXIMUM IMPERVIOUS COVERAGE 35% 4.1% (3,383 S.F.) 5.3% (4,731 S.F.)

MAXIMUM BUILDING HEIGHT 3 STORIES & 30 FEET EXISTING EXISTING

MINIMUM FRONT YARD SETBACK 45 FEET 94.3 FEET 96.3 FEET

AVERAGE FRONT YARD SETBACK [1] 60 FEET N/A N/A

MINIMUM SIDE YARD SETBACK 20 FEET 28.4 FEET 26.8 FEET

MINIMUM REAR YARD SETBACK 50 FEET 562.5 FEET 606.1 FEET

[1] TO OBTAIN MORE FLEXIBILITY IN PLACING BUILDINGS IN ALL RESIDENTIAL SUBDIVISIONS OF TWO OR MORE LOTS, AN AVERAGE BUILDING SETBACK LINE OF 60 FEET AND A MINIMUM BUILDING SETBACK OF 45 FEET SHALL BE REQUIRED.

* EXISTING NON-CONFORMITY

EXISTING NET TRACT AREA

UPI: 53-4-61

GROSS LOT AREA 90,816 S.F. (2.085 ACRES)

AREA WITHIN RIGHT-OF-WAY 1,672 S.F. (0.038 ACRES)

LOT AREA 89,144 S.F. (2.046 ACRES)

UPI: 53-4-60

GROSS LOT AREA 83,911 S.F. (1.926 ACRES)

AREA WITHIN RIGHT-OF-WAY 1,672 S.F. (0.038 ACRES)

LOT AREA 82,239 S.F. (1.888 ACRES)

ZONING DATA (PROPOSED CONDITIONS) R-2 LOW DENSITY RESIDENTIAL DISTRICT

ALL OTHER USES REQUIRED UPI: 53-4-60 UPI: 53-4-61

MINIMUM LOT AREA 1 ACRE 2.223 ACRES 1.670 ACRES

MINIMUM LOT WIDTH @ BUILDING LINE 150 FEET 209.50 FEET 169.90 FEET

MINIMUM LOT WIDTH @ STREET LINE 60 FEET 209.50 FEET 169.90 FEET

MAXIMUM BUILDING COVERAGE 25% (TBD) 2.5% (1,824 S.F.)

MAXIMUM IMPERVIOUS COVERAGE 35% (TBD) 6.5% (4,731 S.F.)

MAXIMUM BUILDING HEIGHT 3 STORIES & 30 FEET <30FT. EXISTING

MINIMUM FRONT YARD SETBACK 45 FEET 45 FEET 96.3 FEET

AVERAGE FRONT YARD SETBACK [1] 60 FEET N/A N/A

MINIMUM SIDE YARD SETBACK 20 FEET 20 FEET 45.9 FEET

MINIMUM REAR YARD SETBACK 50 FEET 50 FEET 266.1 FEET

[1] TO OBTAIN MORE FLEXIBILITY IN PLACING BUILDINGS IN ALL RESIDENTIAL SUBDIVISIONS OF TWO

OR MORE LOTS, AN AVERAGE BUILDING SETBACK LINE OF 60 FEET AND A MINIMUM BUILDING SETBACK OF 45 FEET SHALL BE REQUIRED.

PROPOSED NET TRACT AREA

UPI: 53-4-61

GROSS LOT AREA 76,916 S.F. (1.766 ACRES)

AREA WITHIN RIGHT-OF-WAY 4,150 S.F. (0.095 ACRES)

LOT AREA 72,766 S.F. (1.670 ACRES)

UPI: 53-4-60

GROSS LOT AREA 97,810 S.F. (2.245 ACRES)

AREA WITHIN RIGHT-OF-WAY 979 S.F. (0.022 ACRES)

LOT AREA 96,830 S.F. (2.223 ACRES)

EXISTING RIGHT OF WAY LINE

PROPERTY BOUNDARY

EXISTING EASEMENT LINE

ADJOINING PROPERTY LINE

LEGEND

EXISTING PROPERTY MONUMENTATION

PROPOSED IRON PIN PROPOSED MONUMENT PROPOSED LOT LINE PROPOSED SETBACK LINE

PROPERTY BOUNDARY

GENERAL NOTES:

1. BOUNDARY SHOWN BY PHYSICAL FIELD SURVEY PERFORMED IN AUGUST, 2025 BY INLAND DESIGN, LLC, WEST CHESTER, PA. BEARINGS HAVE BEEN ROTATED TO STATE PLANE COORDINATES. 2. THIS PLAN WAS PREPARED WITHOUT THE BENEFIT OF A CURRENT TITLE REPORT. 3. TOPOGRAPHIC INFORMATION AND IMPROVEMENTS SHOWN BY PHYSICAL FIELD SURVEY PERFORMED IN AUGUST, 2025 BY INLAND DESIGN, LLC, WEST CHESTER, PA. CONTOUR INTERVAL = 1 FOOT. 4. ELEVATIONS BASED ON NAVD88 DATUM. VERTICAL DATUM OBTAINED BY GPS OBSERVATIONS ON AUGUST 6, 2025. 5. THERE IS NO 100 YEAR FLOODPLAIN SHOWN ON THE PLAN, WHICH WAS DETERMINED FROM THE REFERENCE FIRM PANELS, MAP NUMBERS 42029C0215G & 42029C0160G, EFFECTIVE SEPTEMBER 29, 2017. 6. SOILS INFORMATION TAKEN FROM UNITED STATES DEPARTMENT OF AGRICULTURE, NATURAL RESOURCE CONSERVATION SERVICE. 7. COMPLETENESS OR ACCURACY OF LOCATION AND DEPTH OF UNDERGROUND UTILITIES AND FACILITIES CANNOT BE GUARANTEED. THE CONTRACTOR MUST VERIFY THE LOCATION AND DEPTH OF ALL UNDERGROUND UTILITIES AND/OR FACILITIES PRIOR TO BEGINNING ANY EARTH-MOVING ACTIVITIES. 8. PUBLIC SEWER SERVICES BOTH PROPERTIES. 9. THE EXISTING SEWER LATERAL SHALL BE CUT AND CAPPED WITHIN 2 FEET OF THE HOUSE-SIDE OF THE CLEANOUT, AND IT SHALL BE DISCONNECTED FROM THE REMAINDER OF THE LATERAL PIPE TO THE HOUSE. THE CAP SHALL BE A SOLID FITTING OR OTHER METHOD AS APPROVED BY THE EAST GOSHEN PUBLIC WORKS DEPARTMENT (PWD). THE PWD MUST INSPECT AND APPROVE THE CUTTING AND CAPPING PRIOR TO BACKFILL. 10. A DEMOLITION PERMIT SHALL BE ACQUIRED TO REMOVE THE EXISTING HOME ON LOT 54-3-60. 11. THE EXISTING LOTS ARE SERVICED BY PRIVATE WELLS. A NEW WELL WILL BE PERMITTED FOR THE FUTURE HOME. 12. ALL PROPOSED ON-SITE WATER SUPPLY SYSTEMS SHALL HAVE A PERMIT CERTIFIED BY THE CHESTER COUNTY HEALTH DEPARTMENT.

PROFESSIONAL

REGISTERED

P

E

N

N

S

Y

L

V

A

N

I

A

C

O

M

M

O

N

W

E

A

L

T

H

O

F

JASON E. HARMON

SU075782

LAND SURVEYOR

TOWNSHIP PLANNING COMMISSION

REVIEWED BY THE EAST GOSHEN TOWNSHIP PLANNING COMMISSION THIS DAY OF , 20 .

CHAIRMAN

VICE CHAIRMAN

MEMBER

MEMBER

MEMBER

RECORDER OF DEEDS

RECORDED IN THE OFFICE FOR THE RECORDING OF DEEDS IN AND FOR THE COUNTY OF CHESTER, AT WEST CHESTER, PA, IN PLAN BOOK __________ , PAGE NO.____________ ON THE DAY OF _____________, 20___.

_______________________________ RECORDER OF DEEDS

COUNTY PLANNING COMMISSION

REVIEWED BY THE CHESTER COUNTY PLANNING COMMISSION ON , 20 .

CCPC FILE #

SECRETARY

TOWNSHIP BOARD OF SUPERVISORS

APPROVED BY THE EAST GOSHEN TOWNSHIP BOARD OF SUPERVISORS THIS DAY OF , 20 .

CHAIRMAN

VICE CHAIRMAN

MEMBER

MEMBER

MEMBER

CERTIFICATE OF OWNERSHIP

ON THIS, THE ___________ DAY OF ________________________, 20 _____, BEFORE ME, THE UNDERSIGNED OFFICER, PERSONALLY APPEARED _______________________________________________, WHO BEING DULY SWORN ACCORDING TO LAW, DEPOSES AND SAYS THAT HE IS THE OWNER AND/OR EQUITABLE OWNER(S) OF THE PROPERTY SHOWN ON THIS PLAN, AND THAT HE ACKNOWLEDGES THAT THE SAME TO BE HIS ACT AND PLAN AND DESIRES THE SAME TO BE RECORDED AS SUCH ACCORDING TO LAW.

OWNER NOTARY PUBLIC OR OTHER OFFICER

OWNER

TOWNSHIP ENGINEER

APPROVED BY THE EAST GOSHEN TOWNSHIP ENGINEER THIS DAY OF _________________, 20 .

TOWNSHIP ENGINEER

DESIGN PROFESSIONAL I, LINDA R. LAYER, ON THIS DATE APRIL 24, 2026, HEREBY CERTIFY THAT THIS PLAN HAS BEEN MADE UNDER MY DIRECT SUPERVISION AND CONFORMS TO ALL ENGINEERING, ZONING, BUILDING AND OTHER APPLICABLE EAST GOSHEN TOWNSHIP ORDINANCES AND REGULATIONS.

LINDA R. LAYER, P.E.

PROFESSIONAL

REGISTERED

P

E

N

N

S

Y

L

V

A

N

I

A

C

O

M

M

O

N

W

E

A

L

T

H

O

F

JASON E. HARMON

SU075782

LAND SURVEYOR

SURVEYOR

I, JASON E. HARMON, A PENNSYLVANIA PROFESSIONAL LAND SURVEYOR, HEREBY CERTIFY THAT THE LOT LINES, STREETS, RIGHTS-OF-WAY AND EASEMENTS SHOWN ON THIS PLAN WERE SURVEYED AND PLOTTED BY ME AND ARE ACCURATE. I FURTHER CERTIFY THAT THE SUBDIVISION AND LAND DEVELOPMENT SHOWN HEREON COMPLIES WITH ALL APPLICABLE REGULATIONS INCLUDING BUT NOT LIMITED TO THE BOROUGH ZONING AND SUBDIVISION AND LAND DEVELOPMENT REGULATIONS AND THAT THE ERROR OF CLOSURE IS NOT GREATER THAN 1:10,000.

JASON E. HARMON, P.L.S. NO. SU075782

RECORD PLAN SHEET 1 OF 1 FOR RECORDING

KING GEORGE

COURT

CORNWALLIS DRIVE

LOCATION MAP

SCALE: 1" = 2000'

SITE

GRAPHIC SCALE

( IN FEET ) 1 Inch = 30'

B

E

U

D

F

O

R

Y

O

E

Y

G

S

!

S

1-800-242-1776

P

E

N

L

L

A

C

N

I

A

N

Y

L

V

I

A

O

N

C

A

L

L

E

E

S

T

M

Pennsylvania One Call System

PA. act 172 of 1986 requires

three working days notice

Serial Numbers:

PENNSYLVANIA ACT 187 REQUIREMENTS: InLand Design, LLC does not guarantee the accuracy of the locations for existing subsurface utility structures shown on the plans, nor does InLand Design, LLC guarantee that all subsurface structures are shown. The contractor shall verify the location and elevation of all underground utilities and structures before the start of work.

S H E E T

Project No.

Checked by:

Drawn by:

Scale:

Date: No. Date: Description: COPYRIGHT InLand Design, LLC expressly reserves its common law copyright and all other proprietary rights in these plans. All drawings, specifications and copies thereof are and shall remain the property of InLand Design, LLC. They are to be used only in respect to this project and are neither to be used on any other project, nor are they to be assigned to any third party without first obtaining the expressed written permission and consent of InLand Design, LLC. Any re-use without written permission, verification, consent or adaptation by InLand Design, LLC for the specific purpose intended, will be at the third party's sole risk and without liability or legal exposure to InLand Design, LLC the third party shall further indemnify and hold harmless InLand Design, LLC from all claims, damages, losses, and expenses arising thereto or resulting therefrom. 16 Hagerty Blvd. West Chester, PA 19382 www.InLandDesign.net

Phone: (484) 947-2928

Fax: (484) 947-2946 Info@InLandDesign.net

I L DESIGN N AND Engineering, Surveying & Land Planning

12664 4

OF 4

CONCEPTUAL FUTURE PLAN

FOR

GEOFFREY & NANCY FAY 949 & 951 CORNWALLIS DRIVE WEST CHESTER, PA, 19382 EAST GOSHEN TOWNSHIP • CHESTER COUNTY • PENNSYLVANIA

PRELIMINARY / FINAL SUBDIVISION PLAN 01/30/2026

1" = 30'

DWN

LRL

20252111349

UPI: 53-4-60 | D.B. 8178 | PG. 758 & UPI: 53-4-61 | D.B. 2963 | PG. 202

1 4/22/2026 REVISED PER TOWNSHIP ENGINEER REVIEW COMMENTS & FOR FINAL PLAN APPROVAL

N:\12600\12664\Dwg\Sheets\Preliminary Submission\4 CONCEPTUAL FUTURE PLAN.dwg

PROFESSIONAL

REGISTERED

P

E

N

N

S

Y

L

V

A

N

I

A

C

O

M

M

O

N

W

E

A

L

T

H

O

F

LINDA R. LAYER

ENGINEER

NO.PE 076871

EXISTING 2' CONTOUR EXISTING 10' CONTOUR

EXISTING RIGHT OF WAY LINE

EXISTING CURB LINE

EXISTING WALL EXISTING FENCE LINE

EXISTING CONCRETE PAD, SIDEWALK OR PATIO

PROPERTY BOUNDARY

EXISTING ROAD / PAVING EXISTING STONE DRIVE

EXISTING SIGN

EXISTING SPOT ELEVATION

EXISTING TREE SYMBOLS

EXISTING UTILITY POLE

EXISTING SANITARY STRUCTURES & PIPE

EXISTING SHRUBHLINE

SOILS LINE AND DESCRIPTION

EXISTING EASEMENT LINE

EXISTING LIGHT

EXISTING OVERHEAD WIRE

EXISTING BRICK SIDEWALK OR PATIO

EXISTING SANITARY CLEAN-OUT

EXISTING TREELINE

ADJOINING PROPERTY LINE

EXISTING ROOF DRAIN

EXISTING WELL

LEGEND

EXISTING PROPERTY MONUMENTATION

EXISTING WATER LINE

PROPOSED IRON PIN PROPOSED MONUMENT

PROPOSED LOT LINE PROPOSED SETBACK LINE

SOILS DESCRIPTION

SYMBOL DESCRIPTION SLOPE AVAILABLE WATER CAPACITY

DRAINAGE

CLASS

DEPTH TO

S.H.W.T.

DEPTH TO BEDROCK

CAPABILITY

UNIT

HYDROLIC SOIL GROUP

CaB CALIFON LOAM 3% - 8% LOW ABOUT 4.4 INCHES

MODERATELY WELL DRAINED

ABOUT 6 TO 36

INCHES

20 TO 99 INCHES 2e D

GdB GLADSTONE GRAVELLY LOAM 3% - 8% MODERATE ABOUT 8.4 INCHES WELL DRAINED MORE THAN 80

INCHES

60 TO 80 INCHES 2e B

OWNER OF RECORD:

GEOFFREY F. & NANCY A. FAY 951 CORNWALLIS DRIVE WEST CHESTER, PA 19382

PROPOSED RIGHT OF WAY LINE

PROPOSED 2' CONTOUR PROPOSED 10' CONTOUR

PROPOSED WATER LINE

PROPOSED CONCRETE SIDEWALK

PROPOSED TREELINE

PROPOSED SANITARY LATERAL

PROPOSED DRIVEWAY PROPOSED STONE DRIVE / TRAIL

PROPOSED WELL

PROPOSED BRICK SIDEWALK OR PATIO

PROPOSED STORMWATER FACILITY

ZONING DATA (PROPOSED CONDITIONS) R-2 LOW DENSITY RESIDENTIAL DISTRICT

ALL OTHER USES REQUIRED UPI: 53-4-60 UPI: 53-4-61

MINIMUM LOT AREA 1 ACRE 2.223 ACRES 1.670 ACRES

MINIMUM LOT WIDTH @ BUILDING LINE 150 FEET 209.50 FEET 169.90 FEET

MINIMUM LOT WIDTH @ STREET LINE 60 FEET 209.50 FEET 169.90 FEET

MAXIMUM BUILDING COVERAGE 25% (TBD) 2.5% (1,824 S.F.)

MAXIMUM IMPERVIOUS COVERAGE 35% (TBD) 6.5% (4,731 S.F.)

MAXIMUM BUILDING HEIGHT 3 STORIES & 30 FEET <30FT. EXISTING

MINIMUM FRONT YARD SETBACK 45 FEET 45 FEET 96.3 FEET

AVERAGE FRONT YARD SETBACK [1] 60 FEET N/A N/A

MINIMUM SIDE YARD SETBACK 20 FEET 20 FEET 45.9 FEET

MINIMUM REAR YARD SETBACK 50 FEET 50 FEET 266.1 FEET

[1] TO OBTAIN MORE FLEXIBILITY IN PLACING BUILDINGS IN ALL RESIDENTIAL SUBDIVISIONS OF TWO

OR MORE LOTS, AN AVERAGE BUILDING SETBACK LINE OF 60 FEET AND A MINIMUM BUILDING SETBACK OF 45 FEET SHALL BE REQUIRED.

PROPOSED NET TRACT AREA

UPI: 53-4-61

GROSS LOT AREA 76,916 S.F. (1.766 ACRES)

AREA WITHIN RIGHT-OF-WAY 4,150 S.F. (0.095 ACRES)

LOT AREA 72,766 S.F. (1.670 ACRES)

UPI: 53-4-60

GROSS LOT AREA 97,810 S.F. (2.245 ACRES)

AREA WITHIN RIGHT-OF-WAY 979 S.F. (0.022 ACRES)

LOT AREA 96,830 S.F. (2.223 ACRES)

PROPOSED SANITARY CLEAN-OUT

GENERAL NOTES:

1. BOUNDARY SHOWN BY PHYSICAL FIELD SURVEY PERFORMED IN AUGUST, 2025 BY INLAND DESIGN, LLC, WEST CHESTER, PA. BEARINGS HAVE BEEN ROTATED TO STATE PLANE COORDINATES. 2. THIS PLAN WAS PREPARED WITHOUT THE BENEFIT OF A CURRENT TITLE REPORT. 3. TOPOGRAPHIC INFORMATION AND IMPROVEMENTS SHOWN BY PHYSICAL FIELD SURVEY PERFORMED IN AUGUST, 2025 BY INLAND DESIGN, LLC, WEST CHESTER, PA. CONTOUR INTERVAL = 1 FOOT. 4. ELEVATIONS BASED ON NAVD88 DATUM. VERTICAL DATUM OBTAINED BY GPS OBSERVATIONS ON AUGUST 6, 2025. 5. THERE IS NO 100 YEAR FLOODPLAIN SHOWN ON THE PLAN, WHICH WAS DETERMINED FROM THE REFERENCE FIRM PANELS, MAP NUMBERS 42029C0215G & 42029C0160G, EFFECTIVE SEPTEMBER 29, 2017. 6. SOILS INFORMATION TAKEN FROM UNITED STATES DEPARTMENT OF

AGRICULTURE, NATURAL RESOURCE CONSERVATION SERVICE. 7. COMPLETENESS OR ACCURACY OF LOCATION AND DEPTH OF UNDERGROUND UTILITIES AND FACILITIES CANNOT BE GUARANTEED. THE CONTRACTOR MUST VERIFY THE LOCATION AND DEPTH OF ALL UNDERGROUND UTILITIES AND/OR FACILITIES PRIOR TO BEGINNING ANY EARTH-MOVING ACTIVITIES. 8. PUBLIC SEWER SERVICES BOTH PROPERTIES. 9. THE EXISTING SEWER LATERAL SHALL BE CUT AND CAPPED WITHIN 2 FEET OF THE HOUSE-SIDE OF THE CLEANOUT, AND IT SHALL BE DISCONNECTED FROM THE REMAINDER OF THE LATERAL PIPE TO THE HOUSE. THE CAP SHALL BE A SOLID FITTING OR OTHER METHOD AS APPROVED BY THE EAST GOSHEN PUBLIC WORKS DEPARTMENT (PWD). THE PWD MUST INSPECT AND APPROVE THE CUTTING AND CAPPING PRIOR TO BACKFILL. 10. A DEMOLITION PERMIT SHALL BE ACQUIRED TO REMOVE THE EXISTING HOME ON LOT 54-3-60. 11. THE EXISTING LOTS ARE SERVICED BY PRIVATE WELLS. A NEW WELL WILL BE PERMITTED FOR THE FUTURE HOME. 12. ALL PROPOSED ON-SITE WATER SUPPLY SYSTEMS SHALL HAVE A PERMIT CERTIFIED BY THE CHESTER COUNTY HEALTH DEPARTMENT.

Memorandum East Goshen Township 1580 Paoli Pike West Chester, PA 19380 610-692-7171 ext. 3103 kkrause@eastgoshen.org Date: June 17, 2026 To: East Goshen Township Board of Supervisors From: Kelly A. Krause, Zoning Officer Re: 971 Cornwallis Drive- MP Renovations, LLC Chester County UPI No. 53-4-65 3 Lot Preliminary/Final Subdivision Plan _____________________________________________________________________________ A Preliminary/Final Subdivision Plan application for the property located at 971 Cornwallis Drive has been submitted to allow an existing 7.221-acre lot to be subdivided into three (3) single family residential lots, resulting in the following: Lot 1 to contain 1.439 acres, Lot 2 to contain 4.122 acres, and Lot 3 to contain 1.321 acres. The property is located within the R-2 Low Density Residential District (§240-9), which requires a minimum lot area of one (1) acre. The existing single-family dwelling will be demolished. Each new house is to be served by public water and public sewer. The applicant proposes to dedicate 9,130 square feet of additional right-of-way to the Township, increasing the existing right-of-way width across Cornwallis Drive to 50 feet along the cartway and 100 feet in diameter at the cul-de-sac. A 40-foot-wide emergency access easement abutting the property boundary shared with 961 Cornwallis Drive was established by agreement with East Goshen Township in 2018, to allow for secondary means of ingress and egress from Cornwallis Drive in the event of an emergency. The easement is proposed to be used as a driveway for Lot 3, as permitted under Section 3.B of the agreement (“Use of Easement”). Lot 2 is proposed to be significantly larger than Lots 1 & 3 to compensate for approximately 2.75 acres contained within the lot hindered by 100-year floodplain, 500-year floodplain, regulatory floodway, and associated wetlands located on the westerly side of the parcel. The subject property appears to be within 660 feet of the Interstate Energy Company pipeline. Confirmation as to whether the center of the Enbridge pipeline is also within the regulatory 660 feet is required. A Pipeline awareness study will be submitted and reviewed by the Pipeline Task Force, per §205-40.1 of the East Goshen Township Subdivision and Land Development Ordinance. The applicant had a preliminary meeting with the Conservancy Board prior to submission of the subdivision plans, and will return for a formal recommendation prior to final approval by the Board of Supervisors.

LOT 1 62,705 SF 1.439 AC.

LOT 3 57,548 SF 1.321 Ac.

LOT 2 179,569 SF 4.122 AC.

4-24-26

REVISION 0

25-0626 GRW

SJR AS NOTED

25-0626

MP RENOVATIONS, LLC

PRESENTS PRELIM / FINAL SUBDIVISION PLANS

FOR 971 CORNWALLIS DRIVE UPI #53-4-65 EAST GOSHEN TOWNSHIP

CHESTER COUNTY COMMONWEALTH OF PENNSYLVANIA, 19380

McKENNA

BUILDING

GROUP

SUBDIVISION

SITE PLAN

SHEET 2 OF 8

TITLE

PROJECT LOCATION

CLIENT DATA

DATE REVISIONS

BY NO DESCRIPTION

CAD ID.

SCALE

PROJ. # DATE

CHK BY

DRN BY

213 West Main Street . Lansdale . PA 19446

WWW.CORNERSTONENET.COM

Philadelphia Region

215-362-2600 Lehigh Valley Region

610-820-8200 Pocono Region

570-839-1770

Phone: 215-362-2600 . Fax: 215-362-8400

BEFORE YOU DIG ANYWHERE IN PENNSYLVANIA! CALL 1-800-242-1776

15122 - 1078

925 Irwin Run Road West Mifflin, Pennsylvania

ONE CALL SYSTEM, INC.

PENNSYLVANIA

!

1-800-242-1776

T

E

B

L

-

C

A

L

O

P

G

E

Y

OU

D

I

R

F

O

N

A

A

N

I

L

V

O

N

N

P

E

S

SY

,

E

M

T

Y S

L

S

A

L

E

C

IN

C

.

Consulting Engineers & Design Services, Inc.

J.B. ANDERSON

PROFESSIONAL ENGINEER DELAWARE LICENSE No. PE 15438 PENNSYLVANIA LICENSE No. PE 055536

MARYLAND LICENSE No. 29313 NEW JERSEY LICENSE No. 24GE04520400

VIRGINIA LICENSE No. 0402 045725

FLORIDA LICENSE No. 75184 NEW YORK LICENSE No. 093667-1

CpA

CpA

GdB Ha

4-24-26

REVISION 0

25-0626 GRW

SJR AS NOTED

25-0626

MP RENOVATIONS, LLC

PRESENTS PRELIM / FINAL SUBDIVISION PLANS

FOR 971 CORNWALLIS DRIVE UPI #53-4-65 EAST GOSHEN TOWNSHIP

CHESTER COUNTY COMMONWEALTH OF PENNSYLVANIA, 19380

McKENNA

BUILDING

GROUP

CONSERVATION AND DEMOLITION

PLAN

SHEET 2 OF 8

TITLE

PROJECT LOCATION

CLIENT DATA

DATE REVISIONS

BY NO DESCRIPTION

CAD ID.

SCALE

PROJ. # DATE

CHK BY

DRN BY

213 West Main Street . Lansdale . PA 19446

WWW.CORNERSTONENET.COM

Philadelphia Region

215-362-2600 Lehigh Valley Region

610-820-8200 Pocono Region

570-839-1770

Phone: 215-362-2600 . Fax: 215-362-8400

BEFORE YOU DIG ANYWHERE IN PENNSYLVANIA! CALL 1-800-242-1776

15122 - 1078

925 Irwin Run Road West Mifflin, Pennsylvania

ONE CALL SYSTEM, INC.

PENNSYLVANIA

!

1-800-242-1776

T

E

B

L

-

C

AL

O

P

G

E

Y

O

U

DI

R

FO

N

A

A

N

I

L

V

O

N

N

P

E

S

S

Y

,

E

M

T

Y S

L

S

AL

E

C

IN

C

.

Consulting Engineers & Design Services, Inc.

J.B. ANDERSON

PROFESSIONAL ENGINEER DELAWARE LICENSE No. PE 15438 PENNSYLVANIA LICENSE No. PE 055536

MARYLAND LICENSE No. 29313 NEW JERSEY LICENSE No. 24GE04520400

VIRGINIA LICENSE No. 0402 045725

FLORIDA LICENSE No. 75184 NEW YORK LICENSE No. 093667-1

BEFORE YOU DIG ANYWHERE IN PENNSYLVANIA! CALL 1-800-242-1776

NON-MEMBERS MUST BE

DRILL, BLAST OR DEMOLISH NOTICE TO UTILITIES BEFORE YOU EXCAVATE,

PA LAW REQUIRES THREE WORKING DAYS

15122 - 1078

925 Irwin Run Road West Mifflin, Pennsylvania

ONE CALL SYSTEM, INC.

CONTACTED DIRECTLY

PENNSYLVANIA

SERIAL NUMBER: 20252602159

!

1-800-242-1776

A

E

B

-

8

-1

L

L

G

E

Y

O

U

D

I

R

FO

N

A

A

NI

L

V

O

N

N

P

E

C

S

Y

,

E

M

T

Y S

L

S

A

L

E

C

I

N

C

.

1

4-24-26

REVISION 0

25-0626 GRW

SJR AS NOTED

25-0626

MP RENOVATIONS, LLC

PRESENTS PRELIM / FINAL SUBDIVISION PLANS

FOR 971 CORNWALLIS DRIVE UPI #53-4-65 EAST GOSHEN TOWNSHIP

CHESTER COUNTY COMMONWEALTH OF PENNSYLVANIA, 19380

McKENNA

BUILDING

GROUP

GRADING, DRAINAGE AND UTILITY

PLAN

SHEET 5 OF 8

TITLE

PROJECT LOCATION

CLIENT DATA

DATE REVISIONS

BY NO DESCRIPTION

CAD ID.

SCALE

PROJ. # DATE

CHK BY

DRN BY

213 West Main Street . Lansdale . PA 19446

WWW.CORNERSTONENET.COM

Philadelphia Region

215-362-2600 Lehigh Valley Region

610-820-8200 Pocono Region

570-839-1770

Phone: 215-362-2600 . Fax: 215-362-8400

BEFORE YOU DIG ANYWHERE IN PENNSYLVANIA! CALL 1-800-242-1776

15122 - 1078

925 Irwin Run Road West Mifflin, Pennsylvania

ONE CALL SYSTEM, INC.

PENNSYLVANIA

!

1-800-242-1776

T

E

B

L

-

C

A

L

O

P

G

E

Y

O

U

D

I

R

FO

N

A

A

N

I

L

V

O

N N

P

E

S

SY

,

E

M

T

Y S

L

S

A

L

E

C

I

N

C

.

Consulting Engineers & Design Services, Inc.

J.B. ANDERSON

PROFESSIONAL ENGINEER DELAWARE LICENSE No. PE 15438 PENNSYLVANIA LICENSE No. PE 055536

MARYLAND LICENSE No. 29313 NEW JERSEY LICENSE No. 24GE04520400

VIRGINIA LICENSE No. 0402 045725

FLORIDA LICENSE No. 75184 NEW YORK LICENSE No. 093667-1

EROSION

SLOPE

MATTING

EROSION

SLOPE MATTING

EROSION

SLOPE

MATTING

EROSION

SLOPE MATTING

SYMBOL CODE BOTANICAL / COMMON NAME SIZE CONTAINER

TREE WHIPS

WHIP PLANT SCHEDULE

SYMBOL CODE BOTANICAL / COMMON NAME SIZE CONTAINER QTY

DECIDIOUS TREES

®

®

EVERGREEN TREES

PLANT SCHEDULE LOT PLANTING

4-24-26

REVISION 0

25-0626 GRW

SJR AS NOTED

25-0626

MP RENOVATIONS, LLC

PRESENTS PRELIM / FINAL SUBDIVISION PLANS

FOR 971 CORNWALLIS DRIVE UPI #53-4-65 EAST GOSHEN TOWNSHIP

CHESTER COUNTY COMMONWEALTH OF PENNSYLVANIA, 19380

McKENNA

BUILDING

GROUP

LANDSCAPE PLAN

SHEET 6 OF 8

TITLE

PROJECT LOCATION

CLIENT DATA

DATE REVISIONS

BY NO DESCRIPTION

CAD ID.

SCALE

PROJ. # DATE

CHK BY

DRN BY

213 West Main Street . Lansdale . PA 19446

WWW.CORNERSTONENET.COM

Philadelphia Region

215-362-2600 Lehigh Valley Region

610-820-8200 Pocono Region

570-839-1770

Phone: 215-362-2600 . Fax: 215-362-8400

BEFORE YOU DIG ANYWHERE IN PENNSYLVANIA! CALL 1-800-242-1776

15122 - 1078

925 Irwin Run Road West Mifflin, Pennsylvania

ONE CALL SYSTEM, INC.

PENNSYLVANIA

!

1-800-242-1776

T

E

B

L

-

C

A

L

O

P

G

E

YO

U

D

I

R

F

O

N

A

A

N

I

L

V

O

N

N

P

E

S

SY

,

E

M

T

Y

S

L

S

AL

E

C

IN

C

.

Consulting Engineers & Design Services, Inc.

LANDSCAPE ARCHITECT PENNSYLVANIA LICENSE No. 003361

PENNSYLVANIA REGISTERED

JUSTIN M. TYLER

· · · · ·

· · · · ·

· · · · · ·

CpA

GdB

EROSION

SLOPE

MATTING

EROSION

SLOPE MATTING

EROSION

SLOPE

MATTING

EROSION

SLOPE MATTING

SOIL STOCKPILE

CONCRETE

WASHOUT

CONSTRUCTION

ENTRANCES

4-24-26

REVISION 0

25-0626 GRW

SJR AS NOTED

25-0626

MP RENOVATIONS, LLC

PRESENTS PRELIM / FINAL SUBDIVISION PLANS

FOR 971 CORNWALLIS DRIVE UPI #53-4-65 EAST GOSHEN TOWNSHIP

CHESTER COUNTY COMMONWEALTH OF PENNSYLVANIA, 19380

McKENNA

BUILDING

GROUP

EROSION AND SEDIMENT

CONTROL PLAN

SHEET 1 OF 3

TITLE

PROJECT LOCATION

CLIENT DATA

DATE REVISIONS

BY NO DESCRIPTION

CAD ID.

SCALE

PROJ. # DATE

CHK BY

DRN BY

213 West Main Street . Lansdale . PA 19446

WWW.CORNERSTONENET.COM

Philadelphia Region

215-362-2600 Lehigh Valley Region

610-820-8200 Pocono Region

570-839-1770

Phone: 215-362-2600 . Fax: 215-362-8400

BEFORE YOU DIG ANYWHERE IN PENNSYLVANIA! CALL 1-800-242-1776

15122 - 1078

925 Irwin Run Road West Mifflin, Pennsylvania

ONE CALL SYSTEM, INC.

PENNSYLVANIA

!

1-800-242-1776

T

E

B

L

-

C

A

L

O

P

G

E

YO

U

D

I

R

F

O

N

A

A

N

I

L

V

O

N

N

P

E

S

SY

,

E

M

T

Y

S

L

S

AL

E

C

IN

C

.

Consulting Engineers & Design Services, Inc.

J.B. ANDERSON

PROFESSIONAL ENGINEER DELAWARE LICENSE No. PE 15438 PENNSYLVANIA LICENSE No. PE 055536

MARYLAND LICENSE No. 29313 NEW JERSEY LICENSE No. 24GE04520400

VIRGINIA LICENSE No. 0402 045725

FLORIDA LICENSE No. 75184 NEW YORK LICENSE No. 093667-1

LOT 1 62,705 SF 1.439 AC.

LOT 3 57,548 SF 1.321 Ac.

LOT 2 179,569 SF 4.122 AC.

POST CONSTRUCTION

STORMWATER MANAGEMENT PLAN

25-0626 DB

JBA

25-0626 4-24-26

AS NOTED

REVISION 0

971 CORNWALLIS DRIVE UPI #53-4-65 EAST GOSHEN TOWNSHIP

CHESTER COUNTY COMMONWEALTH OF

PENNSYLVANIA

McKENNA

BUILDING

GROUP

TITLE

PROJECT LOCATION

CLIENT DATA

DATE REVISIONS

BY NO DESCRIPTION

CAD ID.

SCALE

PROJ. # DATE

CHK BY

DRN BY

213 West Main Street . Lansdale . PA 19446

WWW.CORNERSTONENET.COM

Philadelphia Region

215-362-2600 Lehigh Valley Region

610-820-8200 Pocono Region

570-839-1770

Phone: 215-362-2600 . Fax: 215-362-8400

BEFORE YOU DIG ANYWHERE IN PENNSYLVANIA! CALL 1-800-242-1776

15122 - 1078

925 Irwin Run Road West Mifflin, Pennsylvania

ONE CALL SYSTEM, INC.

PENNSYLVANIA

!

1-800-242-1776

T

E

B

L

-

C

A

L

O

P

G

E

YO

U

D

I

R

F

O

N

A

A

N

I

L

V

O

N

N

P

E

S

S

Y

,

E

M

T

Y S

L

S

A

L

E

C

I

N

C

.

Consulting Engineers & Design Services, Inc.

J.B. ANDERSON

PROFESSIONAL ENGINEER DELAWARE LICENSE No. PE 15438 PENNSYLVANIA LICENSE No. PE 055536

MARYLAND LICENSE No. 29313 NEW JERSEY LICENSE No. 24GE04520400

VIRGINIA LICENSE No. 0402 045725

FLORIDA LICENSE No. 75184 NEW YORK LICENSE No. 093667-1

SHEET 1 of 7

PCSM SITE PLAN

CpA

CpA

GdB Ha

POST CONSTRUCTION

STORMWATER MANAGEMENT PLAN

25-0626 DB

JBA

25-0626 4-24-26

AS NOTED

REVISION 0

971 CORNWALLIS DRIVE UPI #53-4-65 EAST GOSHEN TOWNSHIP

CHESTER COUNTY COMMONWEALTH OF

PENNSYLVANIA

McKENNA

BUILDING

GROUP

TITLE

PROJECT LOCATION

CLIENT DATA

DATE REVISIONS

BY NO DESCRIPTION

CAD ID.

SCALE

PROJ. # DATE

CHK BY

DRN BY

213 West Main Street . Lansdale . PA 19446

WWW.CORNERSTONENET.COM

Philadelphia Region

215-362-2600 Lehigh Valley Region

610-820-8200 Pocono Region

570-839-1770

Phone: 215-362-2600 . Fax: 215-362-8400

BEFORE YOU DIG ANYWHERE IN PENNSYLVANIA! CALL 1-800-242-1776

15122 - 1078

925 Irwin Run Road West Mifflin, Pennsylvania

ONE CALL SYSTEM, INC.

PENNSYLVANIA

!

1-800-242-1776

T

E

B

L

-

C

A

L

O

P

G

E

YO

U

D

I

R

F

O

N

A

A

N

I

L

V

O

N

N

P

E

S

S

Y

,

E

M

T

Y S

L

S

A

L

E

C

I

N

C

.

Consulting Engineers & Design Services, Inc.

J.B. ANDERSON

PROFESSIONAL ENGINEER DELAWARE LICENSE No. PE 15438 PENNSYLVANIA LICENSE No. PE 055536

MARYLAND LICENSE No. 29313 NEW JERSEY LICENSE No. 24GE04520400

VIRGINIA LICENSE No. 0402 045725

FLORIDA LICENSE No. 75184 NEW YORK LICENSE No. 093667-1

SHEET 2 of 7

EXISTING CONDITIONS

PLAN

CpA

GdB LOT 1 62,705 SF 1.439 AC.

LOT 3 57,548 SF 1.321 Ac.

LOT 2 179,569 SF 4.122 AC.

EROSION

SLOPE

MATTING

EROSION

SLOPE MATTING

EROSION

SLOPE

MATTING

EROSION

SLOPE MATTING

POST CONSTRUCTION

STORMWATER MANAGEMENT PLAN

J.B. ANDERSON

PROFESSIONAL ENGINEER DELAWARE LICENSE No. PE 15438 PENNSYLVANIA LICENSE No. PE 055536

MARYLAND LICENSE No. 29313 NEW

JERSEY LICENSE No. GE45204 VIRGINIA LICENSE No. 0402 045725

25-0626 DB

JBA

25-0626 4-24-26

AS NOTED

REVISION 0

971 CORNWALLIS DRIVE UPI #53-4-65 EAST GOSHEN TOWNSHIP

CHESTER COUNTY COMMONWEALTH OF

PENNSYLVANIA

McKENNA

BUILDING

GROUP

TITLE

PROJECT LOCATION

CLIENT DATA

DATE REVISIONS

BY NO DESCRIPTION

CAD ID.

SCALE

PROJ. # DATE

CHK BY

DRN BY

213 West Main Street . Lansdale . PA 19446

WWW.CORNERSTONENET.COM

Philadelphia Region

215-362-2600 Lehigh Valley Region

610-820-8200 Pocono Region

570-839-1770

Phone: 215-362-2600 . Fax: 215-362-8400

BEFORE YOU DIG ANYWHERE IN PENNSYLVANIA! CALL 1-800-242-1776

15122 - 1078

925 Irwin Run Road West Mifflin, Pennsylvania

ONE CALL SYSTEM, INC.

PENNSYLVANIA

!

1-800-242-1776

T

E

B

L

-

C

A

L

O

P

G

E

YO

U

D

I

R

F

O

N

A

A

N

I

L

V

O

N

N

P

E

S

SY

,

E

M

T

Y

S

L

S

AL

E

C

IN

C

.

Consulting Engineers & Design Services, Inc.

J.B. ANDERSON

PROFESSIONAL ENGINEER DELAWARE LICENSE No. PE 15438 PENNSYLVANIA LICENSE No. PE 055536

MARYLAND LICENSE No. 29313 NEW JERSEY LICENSE No. 24GE04520400

VIRGINIA LICENSE No. 0402 045725

FLORIDA LICENSE No. 75184 NEW YORK LICENSE No. 093667-1

BMP DRAINAGE

AREA PLAN

SHEET 3 of 7

Prepared by/Return to:
Kristin S. Camp, Esquire
BUCKLEY, BRION, McGUIRE & MORRIS LLP
118 W. Market Street, Suite 300
West Chester, PA 19382

Rick Loughery
RECORDER OF DEEDS

UPI No. 53-4-65

EMERGENCY ACCESS EASEMENT AGREEMENT

THIS EMERGENCY ACCESS EASEMENT AGREEMENT (the "Agreement") is made this 3RD day of July 2018 by and between RICHARD H. SHUMAKER and HELEN L. SHUMAKER, husband and wife, with an address of 971 Cornwallis Drive, West Chester, Pennsylvania 19380 ("Grantors") and EAST GOSHEN TOWNSHIP, with an address of 1580 Paoli Pike, West Chester, Pennsylvania 19380 ("Grantee").

BACKGROUND/RECITALS:

WHEREAS, Grantors own a parcel of property containing approximately 7.3 acres, more or less, which is located on the northeast side of Cornwallis Drive in East Goshen Township, Chester County, Pennsylvania, which property is more particularly identified as Chester County Tax Parcel No. 53-4-65 (the "Property"); and

WHEREAS, the Property is located on the north side of Cornwallis Drive, which is a cul-de-sac street with over 65 dwellings located thereon; and

WHEREAS, the dwellings on Cornwallis Drive have only one means of ingress and egress to Route 352; and

WHEREAS, Grantee intends to construct a paved emergency access road (the "Road") on a portion of the Property to benefit the residents of Cornwallis Drive which may be used in the event of an emergency as a secondary means of ingress and egress; and

WHEREAS, the parties desire to establish and memorialize a perpetual, non-exclusive emergency access easement over a forty foot (40') wide portion of the Property along the eastern boundary of the Property in the location which is described by metes and bounds in the legal description which is attached hereto as Exhibit "A" and is depicted on the Plan titled, "Emergency Access Easement Plan" prepared by Pennoni Associates, Inc., dated June 2, 2017, which plan is attached hereto as Exhibit "B" (the "Plan").

NOW THEREFORE, the parties, each intending to be legally bound, hereby agree as follows:

DOC # 11618498 07/18/2018 11:08 AM
Receipt #: 18-22626
Rec Fee: $96.75
Chester County, Recorder of Deeds

11618498 B: 9779 P: 691 ESA
07/18/2018 11:08 AM Page 1 of 12
BUCKLEY BRION

1. Incorporation of Recitals. The background paragraphs set forth in the Recital above are incorporated herein by reference as though set forth at length herein.

2. Grant of Easement. Grantors, for and in consideration of the sum of Ten Thousand Dollars ($10,000.00), the receipt whereof is hereby acknowledged, as well as the advantage to them accruing as for diverse and other considerations affecting the public welfare which they seek to advance, have granted, bargained, and sold and by these presents do grant, bargain, sell and convey unto Grantee and its successors and assigns a perpetual, non-exclusive forty foot wide (40') emergency access easement over and across the Property in the location described by metes and bounds in the legal description which is attached hereto as Exhibit "A" and as depicted on the Plan which is attached hereto as Exhibit "B" (the "Easement").

3. Use of Easement.

A. Grantee and the public shall be entitled to use the Easement and the Road constructed therein and all necessary accessories and appurtenances used in connection therewith as an emergency access road which shall provide a secondary means of ingress and egress for vehicles and pedestrians in the Cornwallis Drive residential community in the event of an emergency.

B. Grantors shall not erect, maintain or allow any improvements on, over and under the Easement, or take or allow any action which would affect free and unimpeded access to or use of the Road and other rights and privileges granted herein. Grantors shall prohibit barriers, structures, fences, curbs or other obstructions from impeding the free and unhampered use of the Easement and Road constructed therein as an emergency access road. Notwithstanding the above restriction, Grantors and their heirs, successors and assigns in title to the Property shall be permitted to use the Road as a means of access to the Property and any lots created from subdividing the Property and dwellings erected on such lots.

4. Construction of Road within the Easement.

A. Grantee shall construct and pave an emergency access road (the "Road") and any required stormwater management facilities within the Easement leading from Cornwallis Drive to the south and the abutting parcel to the north owned by Hershey's Mill Homeowners Association, identified as Chester County Tax Parcel No. 53-2-25.3 ("Hershey's Mill Parcel") to the north. Grantee, through its employees, agents, contractors and subcontractors shall be solely responsible for constructing the Road within the Easement. Grantee and its employees, agents, contractors and subcontractors shall construct the Road in accordance with sound engineering and construction principles and shall perform any work within the Easement in a good and workmanlike manner so as to create the least interference with the Property. Grantee

11618498 B: 9779 P: 692 ESA
07/18/2018 11:08 AM Page 2 of 12
BUCKLEY BRION

shall notify Grantors at least seven (7) days prior to commencing construction of the Road on the Property.

B. Grantee shall also install a gate at the entrance to the Road at or near the boundary line between the Property and the Hershey's Mill Property.

C. Grantee promptly following or exercising its rights and privileges hereunder to construct the Road within the Easement, shall backfill any areas excavated, compact the ground as may be appropriate and fully restore the surface of the ground to substantially its condition prior to such disturbance, (except for the cartway of the Road which shall be improved with an asphalt surface). Any areas outside of the cartway of the Road which were disturbed during the construction shall be filled, compacted and seeded with grass as may be necessary to restore the surface of the Property to substantially its condition prior to such disturbance.

D. Grantee shall not permit any claim, lien or other encumbrance arising from the construction of the Road on the Property to accrue against or attach to the Property. If any such claim or lien is filed against the Property as a result of work performed or materials provided for the construction of the Road, Grantee shall satisfy said claim as promptly as possible.

5. Maintenance of Road.

Grantee shall be responsible for all costs of installation and maintenance of the Road and stormwater management facilities that shall be constructed within the Easement. "Maintenance" shall include, repairing and filling potholes; repaving with asphalt as needed; removal of snow, improving, maintaining or repairing any stormwater control measures, removing debris and any and all obstructions which may impair clear passage along the Road, tree trimming and removal within the Easement, and maintaining the gate that is installed at the entrance of the Road on the Property.

6. Impervious Cover.

Grantee agrees that if Grantors or their heirs, successors or assigns ever files an application to subdivide and/or develop the Property, any and all paving or installation of impervious surfaces associated with the construction of the Road will not be included in the computation of total impervious cover for the Property or any lot created from the Property. Grantee agrees that the impervious cover added to the Property for the Road shall not be included in impervious cover calculation.

7. Indemnity and Insurance.

A. Grantee agrees to indemnify, defend and hold harmless Grantors from and against any damage, liability, claim, settlement, cost and expense, award, judgment, damage, fine, fee, or other loss suffered by Grantors arising out of (1) any injury and/or loss and/or damage caused by the acts or omissions, or intentional misconduct of the Grantee or its agents, employees, contractors, subcontractors, assigns or successors-in-interest, in the construction and maintenance of the Road and

11618498 B: 9779 P: 693 ESA
07/18/2018 11:08 AM Page 3 of 12
BUCKLEY BRION

its performance of its responsibilities hereunder; or (2) any personal injury or death or property damage resulting from the use of the Road after the date of this Agreement, including, without limitation, any use by the general public or by the Grantee or any of its agents, employees, licensees, contractors, subcontractors and invitees; provided however, that such injury or damage was not caused by the gross negligence or willful misconduct of Grantors and provided that this indemnification shall not extend or apply to Grantors' or their heirs, successors or assigns' use of the Road as a driveway or means of access to the Property or lots created from subdividing the Property.

B. Grantee shall obtain and maintain during the entire term of this Agreement adequate public liability and property damage insurance policies covering any injury, death or property damage resulting in any way from the use of the Easement and Road on the Property. Such insurance policies shall provide bodily injury, including death, and property damage coverage in the minimum amount of One Million ($1,000,000.00) Dollars per occurrence and Two Million ($2,000,000.00) Dollars in the aggregate. The insurance policies shall be occurrence based and shall name Grantors as additional insureds. The insurance policies shall provide that such policy may not be cancelled without first giving Grantors 30 days' prior written notice of cancellation.

8. Running with the Land.

This Agreement and the Easement created herein shall run with the land and bind the Property and the Grantors' heirs, successors and assigns in title to the Property.

9. Enforcement.

If either party determines that this Agreement is being or has been violated by the other party, the non-defaulting party may, in addition to other remedies available at law or in equity, seek injunctive relief to specifically enforce the terms of this Agreement or to restrain present or future violations of this Agreement. If any party has to resort to legal action to enforce the terms of this Agreement, the prevailing party shall be entitled to recover its legal fees and costs from the defaulting party.

10. Notices.

Any notice or other communication given hereunder or pursuant hereto shall be in writing and shall be personally delivered (in which event such notice shall be deemed effective only upon such delivery), or sent by a nationally-recognized overnight delivery service (which provides a receipt of delivery), or delivered by mail, sent by registered or certified mail, postage prepaid, return receipt requested, to such party at the address set forth below:

If to Grantors:
Richard H. and Helen L. Shumaker
971 Cornwallis Drive
West Chester, PA 19380

11618498 B: 9779 P: 694 ESA
07/18/2018 11:08 AM Page 4 of 12
BUCKLEY BRION

4

If to Grantee:
East Goshen Township
Attn: Township Manager
1580 Paoli Pike
West Chester, PA 19380

With a copy to:
Buckley, Brion, McGuire & Morris LLP
118 W. Market Street, Suite 300
West Chester, PA 19382
Attn: Kristin S. Camp, Esquire

All notices shall be deemed given when received. A party may change its address by giving notice of such change in the manner herein provided by giving notice. In the event the Property or any portion of the Property is conveyed, all notices shall be to the new owner's address on file with the Chester County Assessment Office. Unless and until such written notice is received, the last address and addressee stated by written notice, or as provided herein if no written notice of change has been sent or received, shall be deemed to continue in effect for all purposes hereunder.

11. Modifications.

This Agreement may be amended, modified or terminated only by a written addendum signed by the then owners of the Property and the Township.

12. Governing Law.

This Agreement shall be interpreted and enforced in accordance with the laws of the Commonwealth of Pennsylvania.

13. Binding Agreement.

This Agreement shall be binding on and inure to the benefit of the parties hereto and their respective heirs, successors and assigns.

14. Recording.

This Agreement shall be recorded in the Office of the Recorder of Deeds of Chester County, Pennsylvania by Grantee.

[Remainder of Page Intentionally Left Blank -- Signature Page to Follow]

11618498 B: 9779 P: 695 ESA
07/18/2018 11:08 AM Page 5 of 12
BUCKLEY BRION

5

Pennoni

EGOS 0008

Cornwallis Drive Access Easement
Township of East Goshen, County of Chester
Commonwealth of Pennsylvania

ALL THAT CERTAIN tract or piece of ground situate in the Borough of East Goshen, Chester County, Commonwealth of Pennsylvania, described in accordance with an Emergency Access Easement Plan – Shumaker, Cornwallis Drive for East Goshen Township, Project Number EGOS 0008, Drawing V-0202, prepared by Pennoni Associates Inc., West Chester, Pennsylvania, dated June 2, 2017. Being more particularly described as follows:

BEGINNING at a point at the intersection of the northerly right-of-way line of Cornwallis Drive (50’ wide) and the easterly line of lands now or formerly Richard and Helen Shumaker, 971 Cornwallis Drive, thence, from said point of beginning;

Along the said northerly line of Cornwallis Drive North 51 degrees 39 minutes 51 seconds West 44.85 feet to a point, thence;

Along a line parallel to and offset 40 feet westerly of the said easterly property line, North 11 degrees 26 minutes 12 seconds East, 531.14 feet to a point on the northerly line of said lands of Shumaker, thence;

Along said northerly line South 78 degrees 16 minutes 01 seconds East, 40.00 feet to an iron pin at the northeasterly corner of said lands of Shumaker, thence;

Along the said easterly line of said Shumaker South 11 degrees 26 minutes 12 seconds West, 551.22 feet to said point of beginning,

Containing 21,647 SF or 0.49695 Acres

Intending to describe an Emergency Access Easement 40’ wide

COMMONWEALTH OF PENNSYLVANIA
REGISTERED PROFESSIONAL LAND SURVEYOR
LAWRENCE EUGENE LESO, JR.
LAND SURVEYOR
SU075315

[Signed: Lawrence E. Leso, Jr.]
Lawrence E. Leso, Jr., PE, PLS
PA License SU075315

6/6/2017
Z:\PROJECTS\EGOS\EGOS0008-Cornwallis Drive - Boundary Survey\DOCUMENTS\Descriptions\40' Wide Emergency Access Easement - 2017

11618498 B: 9779 P: 700 ESA
07/18/2018 11:08 AM Page 10 of 12
BUCKLEY BRION

EMERGENCY ACCESS EASEMENT PLAN

SHUMAKER, CORNWALLIS DRIVE, 971 CORNWALLIS DRIVE, WEST CHESTER, PA 19380 | EAST GOSHEN TWP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380

Survey plat and emergency access easement plan prepared by Pennoni Associates Inc. showing a 40' proposed access easement between Cornwallis Drive (50' wide) and Lands N/F Hersheys Mill Development across Lands N/F Richard & Helen Shumaker and Lands N/F Nicholas & Doris Minniti, stamped Unofficial Copy.

REVISIONS: NO. | DESCRIPTION | DATE | BY

PLAN NOTES:

THE PURPOSE OF THIS PLAN IS TO DELINEATE A PROPOSED ACCESS EASEMENT.
THIS PLAN IS TO BE USED FOR TITLE PURPOSES ONLY.
A FIELD SURVEY WAS COMPLETED BY PENNONI ASSOCIATES IN AUGUST 2016.
REFER TO PLAN V0201, PREPARED BY PENNONI ASSOCIATES, PROJECT NUMBER EGOS 0008 FOR BOUNDARY AND REFERENCE DRAWING INFORMATION.

Survey Labels and Bearings

LANDS N/F HERSHEYS MILL DEVELOPMENT | EXISTING PROPERTY LINE | S 78°16'01" E 40.00' | IRON PIN FOUND | 40' PROPOSED ACCESS EASEMENT | NORTH | N 11°26'12" E 531.14' | S 11°26'12" W 551.22' | LANDS N/F RICHARD & HELEN SHUMAKER, 971 CORNWALLIS DRIVE, APN 53-004-0065.0000, DEED BOOK 40, PAGE 781 | LANDS N/F NICHOLAS & DORIS MINNITI, DEED BOOK M-37, PAGE 92 | CORNWALLIS (50' WIDE) DRIVE | LANDS N/F JOHN SHOPE | N 51°39'51"W 44.85' | POB ACCESS EASEMENT | Scale: 0 80' 160' | COMMONWEALTH OF PENNSYLVANIA, REGISTERED PROFESSIONAL, LAWRENCE EUGENE LESO JR., LAND SURVEYOR, SU070316

Title Block and Recording Information

Pennoni | PENNONI ASSOCIATES INC., One South Church Street, 2nd Floor, West Chester, PA 19382, T 610.429.8907 F 610.429.8918

ALL DOCUMENTS PREPARED BY PENNONI ASSOCIATES ARE INSTRUMENTS OF SERVICE IN RESPECT OF THE PROJECT. THEY ARE NOT INTENDED OR REPRESENTED TO BE SUITABLE FOR REUSE BY OWNER OR OTHERS ON THE EXTENSIONS OF THE PROJECT OR ON ANY OTHER PROJECT. ANY REUSE WITHOUT WRITTEN VERIFICATION OR ADAPTATION BY PENNONI ASSOCIATES FOR THE SPECIFIC PURPOSE INTENDED WILL BE AT OWNERS SOLE RISK AND WITHOUT LIABILITY OR LEGAL EXPOSURE TO PENNONI ASSOCIATES; AND OWNER SHALL INDEMNIFY AND HOLD HARMLESS PENNONI ASSOCIATES FROM ALL CLAIMS, DAMAGES, LOSSES AND EXPENSES ARISING OUT OF OR RESULTING THEREFROM.

PROJECT: EGOS0008 | DATE: 2017-06-02 | DRAWING SCALE: 1"=80' | DRAWN BY: MTC | APPROVED BY: MK | V0202 | SHEET 1 OF 1

R:\PROJECTS\EGOS\0008 CORNWALLIS EMERGENCY ACCESS ROAD\DESIGN\PUBLISH\V0202.DWG | PLOTTED: 6/5/2017 3:52:58 PM BY: MICHAEL CELONI PLOTSTYLE: PENNONI MGS.STB, PROJECT STATUS:

11618498 B: 9779 P: 702 ESA | 07/18/2018 11:08 AM | Page 12 of 12 | BUCKLEY BRION

§ 240-6 Definitions; word usage. B. Definitions. When used in this chapter, the following words, terms and phrases shall have the following meanings, unless expressly stated otherwise or unless the context clearly indicates otherwise.

CLOSED-LOOP COOLING SYSTEM- A cooling system that circulates a single contained coolant or fluid that is not discharged to the environment as a normal part of operation (may include plate-and-frame heat exchangers, rear-door heat exchangers, immersion, or other sealed liquid cooling approaches).

DATA CENTER – A facility used primarily for the storage, management, processing, and transmission of digital data, which houses computer or network equipment, systems, servers, appliances and other associated components related to digital data operations. The facility may also include air handlers, power generators, water cooling and storage facilities, utility substations, and other associated utility infrastructure to support sustained operations at the Data Center. DATA CENTER ACCESSORY USE – Ancillary uses or structures secondary and incidental to a Data Center use, including but not limited to: administrative, logistical, fiber optic, storage, and security buildings or structures; sources of electrical power such as generators used to provide temporary power when the main source of power is interrupted; electrical substations; utility lines, domestic and non-contact cooling water and wastewater treatment facilities; water holding facilities; pump stations; water towers; environmental controls (air conditioning or cooling towers; fire suppression, and related equipment), and security features, provided such Data Center Accessory Uses/structures are located on the same tract or assemblage of adjacent parcels developed as a unified development with a Data Center.

DATA CENTER CAMPUS: A data center campus includes all of the structures and real estate owned, controlled, leased or otherwise occupied primarily for the use and purpose as Data Center(s), including: (i) Data Center(s); (ii) Data Center Accessory Uses; and (iii) all other systems, equipment, piping, conduit and other ancillary equipment, structures, and other appurtenances that are incidental to and/or needed for the construction, support, operation, repair, maintenance, and/or protection of the Data Center(s) and/or the data center campus. ENERGY GENERATION SYSTEM: Any energy generation system designed or used to supply power directly to a Data Center during normal operations, including solar, wind, fossil fuel, fuel cells, or nuclear energy generating systems. SENSITIVE RECEPTOR: Buildings used for residences (including institutional uses with a residential component), schools, daycare centers, preschools, hospitals, community centers, and similar institutional uses. § 240-19 I-1 Light Industrial District.

C. Permitted conditional uses. The following principal uses may be permitted in the I-1 District in accordance with § 240-31:

(34) Data Centers in accordance with § 240-31C(3)(xx). (34) (35) Any lawful use not otherwise permitted in the Township.

§ 240-31 Conditional uses; additional standards for specific principal uses.

C. Standards for conditional uses and special exception uses and certain permitted-by- right uses.

(3) Specific standards for specific principal uses (including but not limited to conditional uses and special exception uses). Each of the following principal uses shall meet the following additional specific standards. In addition, each conditional or special exception use shall meet the general standards in Subsection C(2). The following specific standards shall be met for the applicable use, unless a more restrictive standard is established by another section of this chapter:

(xx) Data Centers

[1] All Data Center and Data Center Accessory Use buildings shall be set back a minimum of ______ feet from any residentially zoned district and from the property boundary of all Sensitive Receptor uses.

[2] In addition to the Supplementary studies as required pursuant to Chapter 205, Subdivision and Land Development, an applicant shall submit the following:

[a] A sound study conducted by a professional acoustical expert that the sound generated by a Data Center and/or Data Center Accessory Uses during normal operations does not exceed the Noise and Nuisance regulations of Chapter 156. The Township may require post- construction noise testing, prepared by a qualified acoustical professional, to verify compliance with Chapter 156. Emergency generator testing shall be limited to periodic testing and emergency operation only and shall comply with all applicable noise and nuisance regulations.

[b] No use shall produce any heat perceptible at or beyond the lot boundaries, as demonstrated by qualified professional analysis conducted in accordance with applicable state and federal standards.

[c] No use shall emit potentially harmful radiation in excess of levels permitted under applicable state and federal standards, as demonstrated by qualified professional analysis.

[d] A vibration study prepared by a qualified professional that demonstrates that no vibration from the Data Center, Data Center Accessory Uses, or associated equipment will be perceptible to the human sense of feeling beyond the property line. [e] The applicant shall provide documentation from the applicable electric service provider and water service provider certifying that that the necessary capacity is available and that electric service provider and water service provider will serve the Data Center. Known impacts on electric/water rates or availability for other uses directly attributable to the Data Center project shall be noted. [f] If the use is to rely upon nonpublic sources of water, the applicant shall provide a water feasibility study. The purpose of the study is to determine if there is an adequate supply of water for the proposed use and to estimate the impact of the use on existing wells, groundwater, and surface waters in the vicinity. No Data Center shall be approved unless the water feasibility study demonstrates that the anticipated water supply yield is adequate for the project and that the proposed water withdrawals and discharges will not endanger or adversely affect the quantity or quality of groundwater supplies or surface waters in the vicinity. [g] A Pipeline awareness study in accordance with § 205-40.1, with review and recommendation made by the East Goshen Township Pipeline Task Force. [h] Any system designed for cooling and operation of the facility (electricity, water, or other means) shall be demonstrated, through qualified professional analysis and in accordance with applicable state and federal standards, to be adequate and to not negatively impact the surrounding region.

[i] A Decommissioning Plan prepared by a qualified professional shall be submitted. The plan shall outline the procedures for safe shutdown, removal of equipment, disposal or recycling of materials, and site restoration. [3] Data Centers shall be designed and constructed to meet the current USGBC LEED BD+C: Data Centers rating system, or equivalent design standard, as approved by the municipal engineer.

[4] Any energy generation system designed or used to supply power directly to a Data Center during normal operations, including solar, wind, fossil fuel, fuel cells, or nuclear energy generating systems, shall not be considered part of the Data Center use but shall be subject to existing municipal or utility regulations. Such systems shall be considered a separate principal use and shall be approved according to all applicable state and federal regulations along with municipal zoning regulations applicable to such use. [5] The applicant shall select, design, and locate the energy generation systems to limit noise, emissions, and visual impacts to adjacent and nearby uses as much as possible. Data center principal buildings shall be located between energy generation systems and residential districts or any other Sensitive Receptors.

[6] Electric Utility Substations on the same property as the Data Center they serve shall be located on the side or rear of a Data Center principal building so they are screened from public view and shall not be located in a required front yard. On-site substations do not require a buffer or screening between the Data Center Principal Building and the substation. [7] Data Center electric utility substations visible from an arterial roadway shall include a combination of year-round opaque landscaping and screening walls to minimize visual impact. [8] Burying power lines serving the property is strongly encouraged. On-site power lines of 34.5 kV and below shall be buried.

[9] Proposed substations on a parcel that abuts a zoning district boundary other than industrial, and/or a boundary with a property with a sensitive receptor shall be set back a minimum of 800 feet from the property line. If abutting both another industrial-zoned parcel and use, substations shall meet the requirements for accessory uses in the underlying zoning district.

[10] Closed-loop cooling systems for server racks and IT equipment shall be required. Use of open, evaporative cooling towers for facility heat rejection is prohibited. Data centers shall not be designed to draw primary cooling make-up water from private potable wells.

[11] The use will not cause electrical interference or fluctuations in line voltage on and off the operating premises, as demonstrated by qualified professional analysis and in accordance with applicable utility, state, and federal standards. [12] The owner of the data center shall provide the Township with an emergency liaison that may be reached 24 hours a day, seven days a week, in the event of an emergency.

[13] The owner of the data center shall submit an emergency response plan to the Township Fire Marshal for review and approval, which shall be implemented and followed in the event of an emergency at the facility. The emergency response plan shall include coordination with local emergency responders, as applicable.

[14] The data center facility and accessory buildings shall be fully screened in accordance with the criteria set forth in § 240- 27C(3).

[15] Diesel generators shall meet the emission standards of the U.S. Environmental Protection Agency for Backup Emergency Deisel Generators.

[16] Diesel generators shall undergo annual testing, and reports shall be provided to the municipality to ensure that data center equipment is performing as designed and that emissions from the data center do not exceed permitted limits.

[17] Emergency energy generation that uses diesel, gasoline, or another fossil fuel shall be used only at the following times:

[a] When the primary source of energy is not available due to an emergency outage.

[b] During routine maintenance, or readiness testing for a short duration of time and capped at 100 hours per year.

[c] Routine maintenance testing of back-up fossil fuel- powered generators is restricted to the hours of 9 am through 3 pm Monday through Friday.

[18] Generator use for peak shaving or supplying power to the grid is prohibited.

[19] Standards for Decommissioning:

[a] The owner shall submit a notification of closure if operations are permanently ceased.

[b] Decommissioning shall begin within 1 year of cessation of data center operations, or upon notice of abandonment by the operator, whichever occurs first. An extension of 1 year may be granted by the Board of Supervisors if the property owner can demonstrate that they are actively marketing the site for a compatible replacement use. Decommissioning shall be completed within 18 months thereafter, unless granted an extended for good cause.

[c] All above-ground structures, equipment, and accessory facilities shall be removed.

[d] Hazardous materials, including batteries, fuel, or refrigerants, shall be disposed of in compliance with state and federal law.

[e] Disturbed soils shall be stabilized and re-vegetated.

[f] Any utility connections shall be safely disconnected and capped.

[g] The site shall be restored to a condition compatible with surrounding land uses or consistent with the most restrictive adjacent zoning district.

E. Noise and Vibration

  1. No Data Center or Data Center Accessory Use, or any combination of Data Center and Data Center Accessory Uses developed as part of a unified development, shall cause or contribute to sound levels in violation of the standards established by this section. Where there is a conflict between this section and any other section of this chapter, the provisions of this section shall apply.
  2. Definitions. The following definitions shall apply to this section: A-weighted fast response maximum sound level (L MAX ). The maximum sound pressure level in decibels (dB) measured over a given period of time, with A-frequency weighting and fast response time-weighting applied.; Compliance metric: L EQ , L MAX , L PK , or L PTL .; Daytime Hours: the hours between 7:00 am and 6:00 pm on weekdays and between 9:00 am and 6:00 pm on weekends and holidays; Equivalent continuous sound level (L EQ ). The steady sound pressure level in decibels (dB) which, over a given period of time, has the same total energy as the fluctuating noise measured over the same period of time.; Evening Hours: the hours between 6:00 pm and 10:00 pm; Log Average Level (LAL xx ): The logarithmic average of the interval measurements of a compliance metric, computed as follows: LAL xx = 10 log 10 [ 1 / nP 0 2 ∑ k=1 n P 0 2 10 Lxk/10 ] = 10 log 10 [ { 10 Lx1/10 + 10 Lx2/10 ... 10 Lxn/10 } / n ] Where: LAL xx = log average level in dBA or dB where L xx represents either L EQ , L MAX , L PK , or L PTL . L x1 = level of the first interval measurement in dBA or dB L x2 = level of the second interval measurement in dBA or dB L xn = level of the n th interval measurement in dBA or dB n = the number of measurement intervals P 0 = standard reference pressure of 20 micro pascals A minimum of 20 intervals of one minute each measured over a single period of 24 hours shall be used, however, intervals need not be contiguous. Intervals with louder, and preferably the loudest noise, should be used.; Natural Environmental Sounds: Environmental sounds that are inherent to the area and due to naturally occurring sounds such as insects, rustling leaves, wind, wild birds, wild animals, frogs, rain, lightning, or weather, but not including the noise of domesticated animals.; Normal Community Sound: Sound that is inherent to and consistent with the norms of the community and which the average resident would reasonably expect

5

to occur in their community. Normal Community Sound may include, but is not limited to, children playing, occasional dog barks, domestic power tools, residential HVAC equipment, and reasonable transportation sounds that meet state, federal, and local noise requirements and limits.

  1. Nighttime Hours: the hours between 10:00 pm and 7:00 am on weekdays and between 10:00 pm and 9:00 am on weekends and holidays.
  2. Pure tone: A sound occurring at a discrete frequency as determined by a Fast Fourier Transform measurement (narrow band analysis) of a sound using a dynamic analyzer with at least 1 Hz and preferable 1/8 Hz resolution, a Hanning window, and sufficient averaging to determine the magnitude of the pure tone level that is exceeded 5% of the time (i.e. an exceedance rate of L 5 ).
  3. Pure Tone Level (L PTL ). The magnitude in decibels (dB) of a pure tone, with no weighting applied.
  4. Receiving Property: Real property impacted by noise generated by a Data Center and/or Data Center Accessory Uses. A Receiving Property need not be directly adjacent to the parcel or collection of parcels on which the Data Center or Data Center Accessory Use(s) are located but shall not include any real property incorporated as part of a unified design with the Data Center whose compliance is being evaluated.
  5. Un-weighted peak sound pressure level (L PK ). The maximum instantaneous sound pressure level in decibels (dB) that occurs during a stated time interval, with no weighting applied.
  1. Sound level limits. For purposes of compliance with this subsection, sound shall be measured at the point, at any elevation, on the Receiving Property where the Log Average Level of the relevant Compliance Metric is highest.; LAL EQ shall not exceed the following values:

Table 1: Equivalent Continuous Sound Level (LEQ) Limits11

Zoning DistrictDaytime hoursEvening hoursNighttime hours
Rural Residential, Low-Density Residential Districts, Properties containing Sensitive Receptors50 dB45 dB45 dB
Medium- and High-Density Residential Districts55 dB50 dB45 dB
Mixed Use, Commercial, Industrial Districts65 dB60 dB55 dB

11 The zoning districts and sound level limits used in this table are for example purposes only. Actual zoning district names and categories should be tailored to the municipality, and sound level limits should reflect the actual background noise levels of the relevant zoning districts. Additional/different categories may be necessary depending on the characteristics of the community. For example, a higher sound level limit may be appropriate along highway corridors.

6

  1. LAL MAX shall not exceed the decibel value of the Equivalent Continuous Sound Level (L EQ ) for the zoning district and time of day, as provided in Table 1, by more than 10 dB.
  2. LAL PK shall not exceed the decibel value of the Equivalent Continuous Sound Level (L EQ ) for the zoning district and time of day, as provided in Table 1, by more than 20 dB.
  3. All LAL PTL5 shall be at least 10 dB below the nominal PTLxx curve at the corresponding frequency, as set forth in Table 2 below, where the value represented by “xx” is the L EQ limit (in dB) set forth in Table 1 for the appropriate zoning district and time of day. Where the applicable L EQ limit is not a multiple of 5, the PTL curve corresponding to the next highest 5 dB increment shall be used; interpolation between PTL curves is not permitted.

Each identified pure tone shall be evaluated independently, and where more than one pure tone is present, compliance shall be determined separately for each tone. Logarithmic averaging of tonal levels across frequencies shall not be used.

Table 2: Maximum allowable LALPTL in dB by Tone Frequency and LEQ limit12

PTLxx curveOctave Band Frequency (Hz) of Pure Tone
1632631252505001000200040008000
PTL70101969186817672686460
PTL6596918681767167635955
PTL6091868176716662585450
PTL5586817671666157534945
PTL5081767166615653484440
PTL4579746862565147433935
PTL4078716458514642383430
PTL3576696154464137332925
PTL3074665849413632282420
PTL2573645445363127231915
PTL2071615141312622181410
PTL15695948372621171395
PTL1068564433211612840

12 PLT curve rows that are not within 5 dB of any LEQ value in Table 1 can be eliminated.

7

  1. Exceptions. The above sound level limits do not apply to sound originating from: Motor vehicles operated legally and in compliance with the noise regulations of the Pennsylvania Department of Transportation; Safety and protective devices where noise suppression would defeat the safety intent of the device when being used for its intended purpose; Any device intended to provide public warning of potentially hazardous, emergency, or illegal activities such as commercial, residential, or vehicle burglar alarms; back-up signals on regulated and licensed motor vehicles; fire alarms; law enforcement and fire vehicles, and similar devices; Emergency equipment and emergency work necessary in the interest of public health, safety, or welfare or law enforcement; Emergency standby generators during emergency use. Routine testing of generators shall comply with the sound level limits unless such testing occurs between 7:00 am and 6:00 pm on weekdays and between 9:00 am and 6:00 pm on weekends and holidays, during which time generators may exceed the sound level limits by no more than 20 dBA (20 dB for L PK ) for up to one (1) cumulative hour per seven (7) calendar day period.; Construction noise, including site preparation, assembly, erection, demolition, substantial repair, maintenance, alteration or similar action for structures or other site improvements, provided that such construction occurs during Daytime Hours and that reasonable noise controls such as proper muffling of all engines, motors, or turbine-driven equipment, and pneumatic devices; noise enclosed air compressors and generators; sound barriers; and lagging are employed.
  2. Measurement Terminology and measurement practices shall follow applicable ANSI S1 & S12 standards. Compliance measurements shall be made using a calibrated ANSI Type 1 or Type 2 integrating sound level meter with a dynamic range of at least 60 dB. For each measurement, the signal-to-noise ratio shall be at least10 dB.; The contribution of wind noise to each compliance measurement shall not exceed 5 dBA (or dB). Measurements shall be made with properly installed windscreens, and any measurement influenced by wind noise exceeding this limit shall be discarded or repeated under acceptable conditions.; Measurements shall exclude significant effects of Natural Environmental Sounds and Normal Community Sounds. The signal-to-noise ratio of the combined effect of Natural Environmental Sounds and Normal Community Sounds shall be at least 5 dBA (or dB) and preferably at least 10 dBA (or dB).; Impact or impulse-type sounds shall be measured with the un-weighted Peak Sound Pressure Level (L PK ) using a meter specifically designed for peak measurements and conforming to the applicable ANSI S1 standards. RMS (root mean square) measurements using the “fast” response setting or any legacy “impulse” function shall not be used.

8

  1. Vibration. No source of mechanical vibration or acoustically induced vibration shall cause or induce vibration on any property or in any structure (ground-borne or structural vibration) that exceeds the ISO 2631-2 Residential Day criteria. Vibration shall be measured as particle velocity in any one-third octave band and shall not exceed 200 µm/s RMS in any band.
  2. Sound and vibration study. The applicant shall demonstrate through a sound study conducted by a professional acoustical expert that the sound and vibration generated by a Data Center and/or Data Center Accessory Uses comply with the requirements of this section. The sound study shall be conducted using generally accepted methodology in the following phases: A sound modeling study shall be conducted to demonstrate that the proposed use will comply with applicable noise requirements of this section. The sound modeling shall be performed according to ISO 9613-2 series methods or other generally accepted engineering methods for outdoor sound propagation. All significant noise sources associated with the proposed Data Center and Data Center Accessory Uses(s) shall be included. The sound modeling study shall be submitted with the [conditional use/special exception/land development application].; An as-built sound study shall be conducted six months after issuance of the certificate of occupancy and prior to the final escrow release for any land development phase. An as-built sound study may also be required thereafter by the [municipality]. If it is determined by the as-built sound study that there is a violation of the aforesaid noise limits, it shall be considered a violation of this Ordinance.

F. Water Supply –Water Feasibility Study.

No Data Center shall be approved unless the applicant demonstrates that there is an adequate supply of water for the proposed use and that proposed water withdrawals and discharges will not endanger or adversely affect the quantity or quality of groundwater supplies or surface waters in the vicinity.

  1. Public water supply. If the use will be served by a public water supply, the applicant shall submit documentation from the public authority certifying that the public authority will supply the water needed.
  2. River basin commission approval. 13 If the use is to rely upon nonpublic sources of water and satisfies either of the below conditions, the applicant shall provide proof of review and approval from the [Delaware/Susquehanna] River Basin Commission and shall not be required to provide an additional water feasibility study. Water withdrawals of 100,000 gallons per day (gpd) or more over a 30-day average from any source or combination of sources within the Delaware/Susquehanna River Basin; or; Any consumptive water use of 20,000 gpd or more over a 30-day average from any water source.

13 This provision is applicable only for municipalities located in the Delaware and Susquehanna River Basins and should be deleted otherwise. The other river/lake commissions do not review or approve withdrawals.

9

EAST GOSHEN TOWNSHIP

PLANNING COMMISSION

1580 Paoli Pike, West Chester, PA 19380 CHESTER COUNTY June 23, 2026 Honorable Carolyn Committa 457 Main Capitol Building Senate Box 203019 Harrisburg, PA 17120-3019 Dear Senator Committa : On behalf of the East Goshen Township Planning Commission, I am writing to express our strong opposition to Pennsylvania House Bill 2186, which seeks to establish mandatory, statewide "by-right" zoning regulations for Accessory Dwelling Units (ADUs). While the intent to expand affordable housing options is admirable, this bill represents an overreach that strips local municipalities of their authority to govern land use, plan for future development, and protect the quality of life for its residents. House Bill 2186 will negatively impact our community in several ways: • Preemption of Local Authority: The retention of municipal control over planning, zoning, and subdivision decisions is vital. Land use decisions should not be dictated by a one-size-fits-all state mandate. By removing local oversight, residents lose their voice in determining the unique future development of their own neighborhoods. • Strain on Infrastructure: Forcing ADUs "by right" onto any residentially zoned lot will result in overtaxed sewage systems, water contamination risks, and increased traffic . Addressing these strains on local infrastructure will result in increased taxes for residents. Municipalities must retain the ability to plan infrastructure improvements in accordance with their financial capacity, available resources, and specific environmental considerations. • Disregard for Proactive Local Planning: The lack of affordable housing is a complex issue involving multiple factors across a wide spectrum of private and public entities. Townships are not the cause of the housing shortage. In fact, it is townships that plan for, zone for, and approve diverse housing types in accordance with local and state regulations and standards. Stripping local land use authority to implement statewide zoning regulations will – in no way – solve the shortage of housing. It is a short-sighted approach that completely disregards the proactive planning efforts local officials perform under the Municipalities Planning Code. • Diminished Quality of Life for Residents – Our residents move into their homes with a reasonable expectation of what their neighborhood will be like in the future. They choose their

community based on that expectation. If HB 2186 becomes law, our residents will have no way of knowing what the quality of life in their community will be in the future. With this legislation, the number of dwellings on their street could increase dramatically. They will be forced to accept greater density than they desired, more traffic than anticipated meaning streets that are less safe for their children, and higher taxes from strains on infrastructure and schools. In addition, this legislation will jeopardize the value of what is, in most cases, their largest asset. As local planning commission members, we are fully committed to supporting voluntary tools and flexible options for affordable housing. Many townships have already taken steps to simplify local approval processes or expand housing choices tailored explicitly to their community's unique landscape. This legislation, if passed, will permit the addition of an indeterminate number of new housing units to be strewn haphazardly across our communities. It will eliminate the ability for local officials to plan effectively and zone appropriately including planning and zoning for desirable, affordable housing. Eliminating a municipality’s ability to properly plan for appropriate land uses will not make housing more affordable. It will, in fact, place additional burdens on our current residents as well as barriers to those seeking to live in our community in the future. Thank you for your time, consideration, and continued service to our Commonwealth. Sincerely, John Stipe, Chairman East Goshen Planning Commission