Conservancy Board

The Conservancy Board advises the Board of Supervisors, the Planning Commission, the Park and Recreation Commission and other agencies, officials and employees of East Goshen Township on matters dealing with conservation, management, protection and use of natural resources in the Township of East Goshen.

Meetings are on the 2nd Wednesday of the month at 7:00 P.M. In addition the Conservancy Board will conduct site inspections the following Saturday at 9:00 AM; as needed.

Board Members Term Expiration Dates
Vacant, Chair 2026
Walter Wujcik, Vice Chair 2027
Jackie Ahlborn 2027
Julieta Calmon 2027
Erich Meyer 2028
Sandy Snyder 2026
Susan Vanesse 2028
Ann Duffield, BOS Liaison
Ashley Nowak,  Staff Liaison

 

Articles of Interest

 

Related News

The Goshen250 Nature Challenge: We Have a Winner!

Wednesday, November 4, 2026

This neighborly challenge between West Goshen and East Goshen townships began as the brainchild of East Goshen Township’s (EGT) Conservancy Board. Jason Lang, EGT’s Parks and Recreation director, contacted his West Goshen peer Ken Lehr, who shared the idea with the Sustainability Advisory Committee, and the idea became a reality. Planning for the iNaturalist-inspired “BioBlitz” […]

View Article

East Goshen Township Receives Bird Town PA Recognition!

Wednesday, October 7, 2026

  The Conservancy Board and Environmental & Sustainability Advisory Council have worked together to have East Goshen Township recognized as a Bird Town PA. The program encourages municipalities to work towards four key strategies: Creating and Protecting Habitat, Threats to Birds, Education and Engagement and Sustainability.         Here are just some of […]

View Article

“Leave the Leaves”

Friday, October 2, 2026

Take a break from the rake and help your yard and the planet. Did you know that the leaves that fall from your trees can act as a natural mulch to improve the soil and retain moisture through the winter? Leaves provide nutrients to your yard as they decompose naturally. They also provide valuable habitat […]

View Article

More News

Documents

Notice: this accessible version was created automatically from the original document. The transcription may not be 100% accurate. It is provided for searching and for screen readers; please refer to the original document for the official version.

AGENDA

EAST GOSHEN TOWNSHIP

CONSERVANCY BOARD MEETING

February 8, 2017

7:00 PM

  1. CALL TO ORDER / PLEDGE OF ALLEGIANCE / MOMENT OF SILENCE
  2. APPROVAL OF MINUTES A. January 11, 2017 Minutes
  3. NEW BUSINESS A. Discuss keep east Goshen beautiful day advertising and planning; B. Spring Planting Locations
  4. SUB DIVISION REVIEW A. 1420 E. Strasburg Rd
  5. OLD BUSINESS
  6. CHAIRMAN’S REPORT
  7. VARIANCES
  8. BOARD MEMBER CONCERNS
  9. LIAISON REPORTS
  10. CORRESPONDENCE
  11. DATES OF IMPORTANCE
  12. PUBLIC COMMENT
  13. ADJOURNMENT

F:\Data\Shared Data\Agendas\Conservancy Board\2017\2017-02-8 - Conservancy Board Agenda.doc

Draft

EAST GOSHEN TOWNSHIP

CONSERVANCY BOARD MEETING

JANUARY 11, 2017

The East Goshen Township Conservancy Board held a regularly scheduled meeting on Wednesday, January 11, 2017 at 7:00 p.m. at the Township Building. In attendance were: Vice Chairman Erich Meyer, Andy Tyler, Walter Wujcik, and John Scheidt. Also in attendance was Supervisor Janet Emanuel.

Call to Order

Erich called the meeting to order at 7:00 p.m.

Pledge of Allegiance & Moment of Silence

Erich led those present in the Pledge of Allegiance and then asked for a moment of silence to remember those who serve in our military and our first responders.

Minutes

The minutes of the December 14, 2016 meeting were approved as corrected.

New Business

Keep East Goshen Beautiful Day

  1. Put notice in Spring newsletter
  2. Andy will contact Jason to have him promote KEGB Day in the Park and Recreation News.
  3. Have Sandy start emailing past participating groups about this year's event and add the Milltown Dam Committee to the list.

Spring Planting – Location/Date

  1. Marydell Pond – willow trees, etc.
  2. Reservoir Road area – select plants during February meeting
  3. Date – Saturday, May 6, 2017.

Old Business

Reorganization - Walter nominated Sandy as Chairman and Erich as Vice Chairman. This would be the second year for each in these positions. The Conservancy Board keeps to a 2-year rotation. John seconded the nomination. The vote was unanimous.

Liasion Report

Municipal Authority – Walter presented the highlights of the meeting. Most of the time was spent discussing West Goshen issues.

CB 1-11-17 draft

1

Board of Supervisors – Janet reported that the Home Occupation request was resolved with 11 conditions.

Also, there is an open position on the Board of Supervisors due to the resignation of Senya Isayeff. Anyone who is interested must submit their resume by this Friday, January 13th.

Adjournment

There being no further business, Walter moved to adjourn the meeting. John seconded the motion. The meeting was adjourned at 8:00 p.m. The next meeting will be February 8, 2017 at 7:00 pm.

Respectfully submitted,

Walter Wujcik

Conservancy Board Member

CB 1-11-17 draft

2

Memorandum

East Goshen Township

1580 Paoli Pike

West Chester, PA 19380

Voice: 610-692-7171

Fax: 610-692-8950

E-mail: mgordon@eastgoshen.org

Date: 2/3/2017

To: Sandy Snyder, Conservancy Board Chairman

From: Mark Gordon, Township Zoning Officer

Re: 1420 E. Strasburg Rd.

Board Members,

As you know the parcel at 1420 E. Strasburg Rd. is currently going through the subdivision process. Staff, the Township Engineer and the applicant have been working through a number of challenges over the last several months. The plan is nearing completion and we anticipate having all the engineering comments addressed and ready to present to the Planning Commission at their meeting in March.

One of the outstanding comments is that a landscape plan has not been submitted and the applicant has not asked for a waiver.

It is the opinion of the Staff and the Planning Commission that the configuration of the landscape plantings around the home is not as critical as the varieties and number of plants proposed.

I recommend that the Board consider the following motion:

Madam Chairman, I move that we recommend that the Planning Commission recommend approval of the SD and LD Plan for 1420 E. Strasburg Rd. with the following condition:

  1. The applicant shall add a note to the plan listing the proposed varieties and number of plants proposed for landscaping for each lot on the preliminary / final plan and a LS plan shall be provided to the Township along with the building permit applications for the two new homes. The Township staff will confirm that the proposed plantings are not invasive species, the trees proposed are listed on the Township Recommended Tree Species List (Resolution 2015-20) and that the landscaping is installed prior to issuance of a use and occupancy certificate.

F:\Data\Shared Data\Property Management\53-6\53-6-89 (1420 E. Strasburg Rd.)\2016 SD application\Memo to CB 02032017.doc

TITLE PLAN

SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY

EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA

COMMONWEALTH ENGINEERS, INC.
114 EAST LANCASTER AVENUE ~ SECOND FLOOR
DOWNINGTOWN, PA 19335
TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004
COMENG@CEI-1.COM

DATE SCALE SURVEY DRAWN CHECKED DRAWING NO. SHEET
MAY 17, 2016 1"=40' MBS TT VK 201541-(C) 1 OF 11

EXISTING IMPERVIOUS COVERAGE:

LOT AREA = 221,252.8 SF / 5.079 AC (EXCLUSIVE OF ROW)

EXISTING BUILDING COVERAGE AREA / PERCENT
EXISTING BUILDINGS 3,132 SF
TOTAL BUILDING COVERAGE 3,132 SF
PERCENT EXISTING BUILDING COVERAGE 1.42%
TOTAL EXISTING IMPERVIOUS COVERAGE AREA / PERCENT
EXISTING BUILDING COVERAGE 3,132 SF
EXISTING DRIVEWAY 8,673 SF
TOTAL IMPERVIOUS COVERAGE 11,805 SF
PERCENT IMPERVIOUS COVERAGE 5.33%

PROPOSED IMPERVIOUS COVERAGE (LOT 1):

LOT AREA = 59,060.162 SF / 1.356 AC (EXCLUSIVE OF ROW)

PROPOSED BUILDING COVERAGE AREA / PERCENT
PROPOSED BUILDING 2,657 SF
TOTAL BUILDING COVERAGE 2,657 SF
PERCENT PROPOSED BUILDING COVERAGE 4.50%
TOTAL IMPERVIOUS COVERAGE AREA / PERCENT
PROPOSED BUILDING 2,657 SF
PROPOSED DRIVEWAY 8,759 SF
TOTAL IMPERVIOUS COVERAGE 11,416 SF
PERCENT IMPERVIOUS COVERAGE 19.33%

PROPOSED IMPERVIOUS COVERAGE (LOT 2):

LOT AREA = 54,162.765 SF / 1.243 AC (EXCLUSIVE OF ROW)

PROPOSED BUILDING COVERAGE AREA / PERCENT
PROPOSED BUILDING 2,341 SF
TOTAL BUILDING COVERAGE 2,341 SF
PERCENT PROPOSED BUILDING COVERAGE 4.32%
TOTAL IMPERVIOUS COVERAGE AREA / PERCENT
PROPOSED BUILDING 2,341 SF
PROPOSED DRIVEWAY 5,944 SF
FUTURE IMPERVIOUS 500 SF
TOTAL IMPERVIOUS COVERAGE 8,785 SF
PERCENT IMPERVIOUS COVERAGE 16.22%

PROPOSED IMPERVIOUS COVERAGE (LOT 3):

LOT AREA = 90,877.001 SF / 2.086 AC (EXCLUSIVE OF ROW)

PROPOSED BUILDING COVERAGE AREA / PERCENT
PROPOSED BUILDING 2,734 SF
TOTAL BUILDING COVERAGE 2,734 SF
PERCENT PROPOSED BUILDING COVERAGE 3.01%
TOTAL IMPERVIOUS COVERAGE AREA / PERCENT
PROPOSED BUILDING 2,734 SF
PROPOSED DRIVEWAY 2,082 SF
FUTURE IMPERVIOUS 500 SF
TOTAL IMPERVIOUS COVERAGE 5,316 SF
PERCENT IMPERVIOUS COVERAGE 5.85%

SHEET INDEX:

SHEET TITLE SHEET NUMBER
TITLE PLANSHEET 1 OF 11
CONSTRUCTION IMPROVEMENTS PLAN PLANSHEET 2 OF 11
EXISTING CONDITIONS PLANSHEET 3 OF 11
PCSM & GRADING PLANSHEET 4 OF 11
PCSM NON-STRUCTURAL BMP PLANSHEET 5 OF 11
PCSM NOTES & DETAILS SHEETSHEET 6 OF 11
EROSION & SEDIMENT CONTROL PLANSHEET 7 OF 11
E&SC NOTES & DETAILS SHEETSHEET 8 OF 11
ENTRANCE ROAD PLAN AND PROFILESHEET 9 OF 11
SANITARY SEWER PROFILE AND DETAILSSHEET 10 OF 11
LANDSCAPE PLANSHEET 11 OF 11

GENERAL NOTES:

  • 1. RECORD OWNER: ANTOINETTE BRAKMAN, 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380, UPI 5306-0089-0000 (TAX #53-6-89), PHONE: (610) 436-0152, DEED REFERENCES: DB. 3529, PG. 1960. EQUITABLE OWNER: JIM BRANDOLINI, GUNNISON DEVELOPMENT CO., LLC, 1200 BURNING BUSH LANE, WEST CHESTER, PA 19380, PHONE: (610) 640-9174.
  • 2. SITE ADDRESS: 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380
  • 3. TRACT AREA: 221,252.8 SQ. FT / 5.079 ACRES (GROSS) LESS 40' ROAD RIGHT-OF-WAY: 17,152.849 SQ. FT. / 0.394 ACRES NET TRACT AREA: 4.685 ACRES (NET)
  • 4. BOUNDARY AND PARTIAL TOPOGRAPHY FROM FIELD SURVEY PERFORMED BY COMMONWEALTH ENGINEERS, INC., APRIL 2016. BENCHMARK: NO. 4 REBAR FOUND, NORTHEAST CORNER OF SITE DATUM: ASSUMED USGS
  • 5. WETLANDS DELINEATION BY VORTEX ENVIRONMENTAL, INC. AND SURVEYED BY COMMONWEALTH ENGINEERS, INC. IN MAY 2016.
  • 6. SOILS CLASSIFICATIONS FROM THE UNITED STATES DEPARTMENT OF AGRICULTURE (USDA) NATURAL RESOURCE CONSERVATION DISTRICT WEB SOIL SURVEY, IN AUGUST, 2014.
  • 7. UNDERGROUND UTILITIES SHOWN HEREON WERE PLOTTED FROM OBSERVABLE EVIDENCE AT THE TIME OF SURVEY AND THROUGH INFORMATION PROVIDED BY THE UTILITY COMPANIES WHICH SERVICE/OCCUPY THE SITE. NO GUARANTEE IS MADE THAT UNDERGROUND UTILITIES ARE ACCURATELY OR COMPLETELY SHOWN HEREON. THE SITE CONTRACTOR MUST VERIFY LOCATION AND DEPTH OF ALL UNDERGROUND UTILITIES AND FACILITIES PRIOR TO BEGINNING CONSTRUCTION.
  • 8. THE SITE IS SERVED BY PUBLIC WATER (AQUA PA).
  • 9. EXISTING SANITARY SYSTEM PRESENT ON SITE BUT NOT LOCATED.
  • 10. EXISTING IRON PINS ARE SHOWN AS THUS "O".
  • 11. THE DEVELOPER SHALL CONFORM TO OR CAUSE CONFORMANCE WITH ALL OF THE APPLICABLE REQUIREMENTS OF THIS PLAN AND THE EAST GOSHEN TOWNSHIP ZONING ORDINANCE AND SUBDIVISION AND LAND DEVELOPMENT ORDINANCE AS WELL AS OTHER APPLICABLE LOCAL, STATE AND FEDERAL LAWS, STATUTES, REGULATIONS AND ORDINANCES.
  • 12. THE DEVELOPER SHALL NOTIFY UNDERGROUND UTILITY USERS AT LEAST THREE DAYS PRIOR TO THE COMMENCEMENT OF CONSTRUCTION IN ACCORDANCE WITH PA ACT 287 OF 1974, AS AMENDED BY ACT 187 OF 1996 & ALL OTHER APPLICABLE AMENDMENTS, AS WELL AS CONFORM TO APPLICABLE REGULATIONS OF SAID ACTS. UNDERGROUND UTILITIES SHOWN ARE FROM SURFACE EVIDENCE OBSERVABLE IN THE FIELD AND AS MARKED BY THE UTILITY COMPANIES.
  • 13. FEMA FLOODPLAIN BOUNDARY TAKEN FROM FLOOD INSURANCE RATE MAP, PANEL 215F, MAP NUMBER 42029C0215F, DATED SEPTEMBER 29, 2006.
  • 14. THIS PROJECT IS LOCATED IN THE WATERSHED OF TRIBUTARY 7 OF EAST BRANCH CHESTER CREEK WHICH HAS THE DESIGNATION OF TROUT STOCK FISHES (TSF, MF) BY THE COMMONWEALTH OF PENNSYLVANIA.
  • 15. THIS PROJECT PROPOSES THE SUBDIVISION OF THE EXISTING LOT INTO 3 SEPARATE LOTS WITH EACH LOT TO BE SERVED BY PUBLIC WATER AND PUBLIC SEWER. PUBLIC SEWER TO BE THROUGH LOW PRESSURE FORCE MAIN TIED INTO AN EXISTING MANHOLE AS SHOWN.

SURVEY REFERENCE NOTES

  • 1. PLAN ENTITLED "BOUNDARY SURVEY PLAN FOR MS. ANTOINETTE BRAKMAN", PREPARED BY R.H. SMITH SURVEYORS, DATED MARCH 27, 2007.
  • 2. PLAN ENTITLED "REVERSE SUBDIVISION/SUBDIVISION PLAN FOR MICHAEL RIZZO", PREPARED BY BRANDYWINE VALLEY ENGINEERS, A DIVISION OF VOLLMER ASSOCIATES, LLP, CONSULTING ENGINEERS AND LAND SURVEYORS, DATED NOVEMBER 30, 2001.
  • 3. PECO BLANKET RIGHT-OF-WAY CONTAINED IN MISCELLANEOUS DB. 81, PG 452.
  • 4. PLAN ENTITLED "THE GAMBONE BROTHERS INC.", PREPARED BY HENRY S. CONREY INC., DIVISION OF CHESTER VALLEY ENGINEERS, DATED JUNE 6, 1973 (LAST REVISED SEPTEMBER 9, 1973).

ZONING: R-2 LOW DENSITY RESIDENTIAL DISTRICT

REQUIREMENT REQUIRED EXISTING PROVIDED LOT 1 PROVIDED LOT 2 PROVIDED LOT 3
MINIMUM LOT AREA (NET)1 ACRE4.685 AC1.356 AC1.243 AC2.086 AC
MINIMUM LOT WIDTH AT BUILDING SETBACK LINE150'409'170'150'180'
MINIMUM LOT WIDTH AT STREET LINE60'409'170'60'180'
MAXIMUM BUILDING COVERAGE25%1.42%4.50%4.32%3.01%
MAXIMUM TOTAL IMPERVIOUS COVERAGE35%5.33%19.33%16.22%5.85%
MAXIMUM BUILDING HEIGHT (STORIES)32222
MAXIMUM BUILDING HEIGHT (FEET)30'30'30'30'30'
MINIMUM FRONT YARD45'45'45' MIN.45' MIN.45' MIN.
AVERAGE FRONT YARD60'60'60'60'60'
MINIMUM SIDE YARD20'20'20' MIN.20' MIN.20' MIN.
MINIMUM REAR YARD50'50'50' MIN.50' MIN.50' MIN.

WAIVER REQUESTS:

1. S.A.L.D.O. SECTION 205-31 FINAL PLAN TO BE SUBMITTED AFTER APPROVAL OF A PRELIMINARY PLAN.
THE APPLICANT REQUESTS THAT THE PLAN BE SUBMITTED AS A PRELIMINARY/FINAL PLAN.

COMMONWEALTH OF PENNSYLVANIA COUNTY OF CHESTER

ON THIS, THE _____ DAY OF ___________________, 20____, BEFORE ME, THE UNDERSIGNED OFFICER, PERSONALLY APPEARED JIM BRANDOLINI (GUNNISON DEVELOPMENT CO., LLC), WHO BEING DULY SWORN ACCORDING TO LAW, DEPOSES AND SAYS THAT HE IS THE EQUITABLE OWNER OF THE PROPERTY SHOWN ON THIS PLAN, THAT THE PLAN THEREOF WAS MADE AT HIS DIRECTION, THAT HE ACKNOWLEDGES THE SAME TO BE RECORDED, AND THAT ALL STREETS AND OTHER PROPERTY IDENTIFIED AS PROPOSED PUBLIC PROPERTY (EXCEPTING THOSE AREAS LABELED "NOT FOR DEDICATION") WILL BE OFFERED FOR DEDICATION.

(JIM BRANDOLINI)

SWORN TO AND SUBSCRIBED BEFORE ME THIS _____ DAY OF ___________________, 20_____.

(NOTARY PUBLIC)
MY COMMISSION EXPIRES ___________________, 20_____.

APPROVED BY THE BOARD OF SUPERVISORS OF EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PENNSYLVANIA, THIS _____ DAY OF ___________________, 20_____.

(CHAIRMAN)
(VICE CHAIRMAN)
(MEMBER)

APPROVED BY PLANNING COMMISSION OF EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PENNSYLVANIA, THIS _____ DAY OF ___________________, 20_____.

(CHAIRMAN)

APPROVED BY TOWNSHIP ENGINEER OF EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PENNSYLVANIA, THIS _____ DAY OF ___________________, 20_____.

(TOWNSHIP ENGINEER)

THIS PLAN WAS REVIEWED BY THE CHESTER COUNTY PLANNING COMMISSION ON ___________________, 20_____.

CCPC FILE NUMBER: ___________________
(PLANNING COMMISSION SECRETARY)

RECORDED IN THE OFFICE OF THE RECORDER OF DEEDS OF CHESTER COUNTY AT WEST CHESTER, PENNSYLVANIA, IN PLAN OF BOOK ________, PAGE ________, ON THIS _____ DAY OF ___________________, 20_____.

(DEPUTY RECORDER OF DEEDS)

STATEMENT OF COMPLIANCE:

I HEREBY CERTIFY THAT, TO THE BEST OF MY KNOWLEDGE, THE PLAN SHOWN AND DESCRIBED HEREON IS TRUE AND CORRECT TO THE ACCURACY REQUIRED BY EAST GOSHEN TOWNSHIP SUBDIVISION AND LAND DEVELOPMENT ORDINANCE.

(VICTOR KELLY, JR., PE) (DATE)

DRAWING AND LOCATION MAP DESCRIPTION

Subdivision Title Plan drawing (Scale 1" = 40') and inset Location Map (Scale 1" = 2000') for the Brakman Property along East Strasburg Road (S.R. 2010, 50 foot wide legal right of way, posted speed limit 40 MPH) opposite Brook Drive. Shows subdivision of UPI 5306 0089 0000 (N/F Antoinette S. Brakman, DB 3529 PG 1960, Gross Area = 221,252.80 SQ FT / 5.079 Acres, Net Area = 210,253.0 SF / 4.827 Acres) into three lots:

  • Lot 1: Gross Lot Area = 64,665.682 SF (1.484 Acres), Net Lot Area = 59,060.162 SF (1.356 Acres), containing Existing Dwelling and Existing Shed.
  • Lot 2: Gross Lot Area = 54,624.745 SF (1.254 Acres), Net Lot Area = 54,162.765 SF (1.243 Acres).
  • Lot 3: Gross Lot Area = 100,219.753 SF (2.301 Acres), Net Lot Area = 90,877.001 SF (2.086 Acres), containing Tributary 7 of East Branch Chester Creek, FEMA 100-Yr Floodplain Zone A, 50' Riparian Buffer, and Existing Shed (TBR).
  • Boundary bearings and distances: N71°27'39"E 410.78' along East Strasburg Road; S24°28'52"E 524.73' along eastern boundary; S65°43'30"W 403.18' along southern boundary; N25°01'38"W 565.83' along western boundary.
  • Adjoining properties: UPI 5306B 0054 0000 N/F Daniel E. Cherry (DB 8962, PG 505); UPI 5306B 0052 0000 N/F William E. Leigh (DB 484, PG 105); UPI 5306B 0051 0000 N/F Christine V. Kaplan (DB 4941, PG 1427); UPI 5306B 0046 0000 N/F Joseph P. Lyons (DB X-49, PG 85); UPI 5306B 0047 0000 N/F John M. Donohue (DB 2670, PG 502); UPI 5306 0090 0000 N/F Joseph M. & Carole A. Matthews (DB 6136, PG 953); UPI 5306 0090 0100 N/F Christopher N. & Deborah Falcone (DB 8774, PG 511); UPI 5306B 0004 0000 N/F Robert & Shirley Sullivan (DB U-61, PG 290); UPI 5306B 0003 0000 N/F Denise Danielle Jordan (DB 9077, PG 2274); UPI 5306 0002 0000 and UPI 5306 0004 0000 N/F Joseph E. Erdeljac Jr (DB 2574, PG 272); UPI 5306B 0039 0000 N/F Dirk & Jaan I. Troltenier (DB 6476, PG 1417); UPI 5306B 0038 0000 N/F Charles W. & Sue Ellen Hendrickson (DB 5067, PG 531).

LEGEND:

  • STEEP SLOPES (15% TO 25%)
  • STEEP SLOPES (OVER 25%)
  • CONCRETE SURFACE
  • EXISTING WETLANDS LINE
  • STREAM LINE
  • FLOOD HAZARD DISTRICT LINE
  • EXISTING INTERMEDIATE CONTOUR
  • EXISTING INDEX CONTOUR
  • EXISTING WOODS / TREE LINE
  • ADJOINER LINE
  • EXISTING STORM SEWER LINE
  • EXISTING RIGHT-OF-WAY LINE
  • EXISTING PAVING
  • EXISTING SOILS LINE
  • PROPOSED INTERMEDIATE CONTOUR (528)
  • PROPOSED INDEX CONTOUR (530)
  • PROPOSED SPOT ELEVATION (x 513.4)
  • PROPOSED STORM SEWER LINE
  • PROPOSED SANITARY SEWER LINE
  • PROPOSED WATER LINE
  • PROPOSED WOODS / TREE LINE
  • SUPER SILT FENCE
  • LIMIT OF DISTURBANCE
  • NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • STABILIZED RIP-RAP CONSTRUCTION ENTRANCE

PENNSYLVANIA ONE CALL & UNDERGROUND UTILITY USERS

(PURSUANT TO ACT 287, 172, 38 AND ALL OTHER APPLICABLE AMENDMENTS) COMMONWEALTH ENGINEERS, INC. DOES NOT GUARANTEE THE ACCURACY OF THE LOCATIONS FOR EXISTING SUBSURFACE UTILITY LINES, STRUCTURES, ETC., SHOWN ON THE PLANS, NOR DOES COMMONWEALTH ENGINEERS, INC. GUARANTEE THAT ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., ARE SHOWN. THE CONTRACTOR SHALL VERIFY THE LOCATION AND ELEVATIONS OF ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., BEFORE THE START OF WORK. (TELEPHONE: (800) 242-1776)
UPI No.5306-0089-0000
PENNSYLVANIA ONE-CALL SYSTEM SERIAL NUMBER: 20160320567

  • PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA 19312, (610) 648-7702
  • VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 592-4151
  • AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
  • COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
  • EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
  • WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475

REVISIONS

REV NO. DATE DESCRIPTION
51/10/17PER CCCD REVIEW LETTER DATED 1/4/17
412/19/16CHANGES TO SANITARY SEWER DESIGN
312/12/16PER CCCD REVIEW LETTER DATED 12/6/16
210/17/16PER TWP. REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT
15/23/16PER PADEP REVIEW LETTER DATED 5/19/16

CONSTRUCTION IMPROVEMENTS PLAN

SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY

EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA

COMMONWEALTH ENGINEERS, INC.
114 EAST LANCASTER AVENUE ~ SECOND FLOOR
DOWNINGTOWN, PA 19335
TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004
COMENG@CEI-1.COM

DATE SCALE SURVEY DRAWN CHECKED DRAWING NO. SHEET
MAY 17, 2016 1"=40' MBS TT VK 201541-(C) 2 OF 11

REQUIRED REGULATORY APPROVALS:

  • 1) NPDES PERMIT (PADEP/CCCD) -APPROVAL STATUS: PENDING
  • 2) PLANNING MODULE (PADEP) -STATUS: EXEMPTION APPROVAL LETTER OBTAINED 12/17/16
  • 3) SANITARY SEWER (MUNICIPAL AUTHORITY) -STATUS: SEWER AVAILABILITY LETTER OBTAINED 5/10/16
  • 4) WATER (AQUA) -STATUS: WATER AVAILABILITY LETTER OBTAINED 5/2/16
  • 5) HIGHWAY OCCUPANCY PERMIT (PENNDOT) -APPROVAL STATUS: PENDING
  • 6) FIRE PLANNING (FIRE MARSHALL) -NOT APPLICABLE
  • 7) HISTORIC RESOURCE (HISTORIC COMMITTEE) -NOT APPLICABLE
  • 8) LANDSCAPING (CONSERVANCY BOARD) -PENDING

GENERAL NOTES:

  • 1. RECORD OWNER: ANTOINETTE BRAKMAN, 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380, UPI 5306-0089-0000 (TAX #53-6-89), PHONE: (610) 436-0152, DEED REFERENCES: DB. 3529, PG. 1960. EQUITABLE OWNER: JIM BRANDOLINI, GUNNISON DEVELOPMENT CO., LLC, 1200 BURNING BUSH LANE, WEST CHESTER, PA 19380, PHONE: (610) 640-9174.
  • 2. SITE ADDRESS: 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380
  • 3. TRACT AREA: 221,252.8 SQ. FT / 5.079 ACRES (GROSS) LESS 40' ROAD RIGHT-OF-WAY: 17,152.849 SQ. FT. / 0.394 ACRES NET TRACT AREA: 4.685 ACRES (NET)
  • 4. BOUNDARY AND PARTIAL TOPOGRAPHY FROM FIELD SURVEY PERFORMED BY COMMONWEALTH ENGINEERS, INC., APRIL 2016. BENCHMARK: NO. 4 REBAR FOUND, NORTHEAST CORNER OF SITE DATUM: ASSUMED USGS
  • 5. WETLANDS DELINEATION BY VORTEX ENVIRONMENTAL, INC. AND SURVEYED BY COMMONWEALTH ENGINEERS, INC. IN MAY 2016.
  • 6. SOILS CLASSIFICATIONS FROM THE UNITED STATES DEPARTMENT OF AGRICULTURE (USDA) NATURAL RESOURCE CONSERVATION DISTRICT WEB SOIL SURVEY, IN AUGUST, 2014.
  • 7. UNDERGROUND UTILITIES SHOWN HEREON WERE PLOTTED FROM OBSERVABLE EVIDENCE AT THE TIME OF SURVEY AND THROUGH INFORMATION PROVIDED BY THE UTILITY COMPANIES WHICH SERVICE/OCCUPY THE SITE. NO GUARANTEE IS MADE THAT UNDERGROUND UTILITIES ARE ACCURATELY OR COMPLETELY SHOWN HEREON. THE SITE CONTRACTOR MUST VERIFY LOCATION AND DEPTH OF ALL UNDERGROUND UTILITIES AND FACILITIES PRIOR TO BEGINNING CONSTRUCTION.
  • 8. THE SITE IS SERVED BY PUBLIC WATER (AQUA PA).
  • 9. EXISTING SANITARY SYSTEM PRESENT ON SITE BUT NOT LOCATED.
  • 10. EXISTING IRON PINS ARE SHOWN AS THUS "O".
  • 11. THE DEVELOPER SHALL CONFORM TO OR CAUSE CONFORMANCE WITH ALL OF THE APPLICABLE REQUIREMENTS OF THIS PLAN AND THE EAST GOSHEN TOWNSHIP ZONING ORDINANCE AND SUBDIVISION AND LAND DEVELOPMENT ORDINANCE AS WELL AS OTHER APPLICABLE LOCAL, STATE AND FEDERAL LAWS, STATUTES, REGULATIONS AND ORDINANCES.
  • 12. THE DEVELOPER SHALL NOTIFY UNDERGROUND UTILITY USERS AT LEAST THREE DAYS PRIOR TO THE COMMENCEMENT OF CONSTRUCTION IN ACCORDANCE WITH PA ACT 287 OF 1974, AS AMENDED BY ACT 187 OF 1996 & ALL OTHER APPLICABLE AMENDMENTS, AS WELL AS CONFORM TO APPLICABLE REGULATIONS OF SAID ACTS. UNDERGROUND UTILITIES SHOWN ARE FROM SURFACE EVIDENCE OBSERVABLE IN THE FIELD AND AS MARKED BY THE UTILITY COMPANIES.
  • 13. FEMA FLOODPLAIN BOUNDARY TAKEN FROM FLOOD INSURANCE RATE MAP, PANEL 215F, MAP NUMBER 42029C0215F, DATED SEPTEMBER 29, 2006.
  • 14. THIS PROJECT IS LOCATED IN THE WATERSHED OF TRIBUTARY 7 OF EAST BRANCH CHESTER CREEK WHICH HAS THE DESIGNATION OF TROUT STOCK FISHES (TSF, MF) BY THE COMMONWEALTH OF PENNSYLVANIA.
  • 15. THIS PROJECT PROPOSES THE SUBDIVISION OF THE EXISTING LOT INTO 3 SEPARATE LOTS WITH EACH LOT TO BE SERVED BY PUBLIC WATER AND PUBLIC SEWER. PUBLIC SEWER TO BE THROUGH LOW PRESSURE FORCE MAIN TIED INTO AN EXISTING MANHOLE AS SHOWN.

SURVEY REFERENCE NOTES

  • 1. PLAN ENTITLED "BOUNDARY SURVEY PLAN FOR MS. ANTOINETTE BRAKMAN", PREPARED BY R.H. SMITH SURVEYORS, DATED MARCH 27, 2007.
  • 2. PLAN ENTITLED "REVERSE SUBDIVISION/SUBDIVISION PLAN FOR MICHAEL RIZZO", PREPARED BY BRANDYWINE VALLEY ENGINEERS, A DIVISION OF VOLLMER ASSOCIATES, LLP, CONSULTING ENGINEERS AND LAND SURVEYORS, DATED NOVEMBER 30, 2001.
  • 3. PECO BLANKET RIGHT-OF-WAY CONTAINED IN MISCELLANEOUS DB. 81, PG 452.
  • 4. PLAN ENTITLED "THE GAMBONE BROTHERS INC.", PREPARED BY HENRY S. CONREY INC., DIVISION OF CHESTER VALLEY ENGINEERS, DATED JUNE 6, 1973 (LAST REVISED SEPTEMBER 9, 1973).

ZONING: R-2 LOW DENSITY RESIDENTIAL DISTRICT

REQUIREMENT REQUIRED EXISTING PROVIDED LOT 1 PROVIDED LOT 2 PROVIDED LOT 3
MINIMUM LOT AREA (NET)1 ACRE4.685 AC1.356 AC1.243 AC2.086 AC
MINIMUM LOT WIDTH AT BUILDING SETBACK LINE150'409'170'150'180'
MINIMUM LOT WIDTH AT STREET LINE60'409'170'180'
MINIMUM LOT WIDTH (FLAG LOT)60'60'180'
MAXIMUM BUILDING COVERAGE25%1.42%4.50%4.32%3.01%
MAXIMUM TOTAL IMPERVIOUS COVERAGE35%5.33%19.33%16.22%5.85%
MAXIMUM BUILDING HEIGHT (STORIES)32222
MAXIMUM BUILDING HEIGHT (FEET)30'30'30'30'30'
MINIMUM FRONT YARD45'45'45' MIN.45' MIN.45' MIN.
AVERAGE FRONT YARD60'60'60'60'60'
MINIMUM SIDE YARD20'20'20' MIN.20' MIN.20' MIN.
MINIMUM REAR YARD50'50'50' MIN.50' MIN.50' MIN.

DRAWING AND LOCATION MAP DESCRIPTION

Construction Improvements Plan drawing (Scale 1" = 40') and inset Location Map (Scale 1" = 2000') showing proposed driveways, utility lines, stormwater management features, and building footprints for Lots 1, 2, and 3:

  • Sanitary Sewer & Water Connections along East Strasburg Road: Tie 6" PVC to Existing MH; 20' Pending Utility Easement; 6" PVC to be directionally drilled; Boring Pit; Proposed MH (TOP=394.0, INV.=386.8); Tie proposed water line to existing water main along East Strasburg Rd.; 3 meter pits to be provided for each separate water line; Proposed Water Line (3 separate lines from each house to tie into existing water main as shown).
  • Lot 1 (Existing Dwelling & Shed): Pull-off area; Sewer connection to existing septic system to be disconnected; Existing septic system to be pumped out, filled, and abandoned subject to Chester County Health Department approval; Proposed 4" PVC lateral (C.O. TOP=423.9, INV.=419.9); 3 separate proposed 4" PVC gravity sewer laterals.
  • Lot 2: Proposed dwelling footprint (LOT 2: FF=434.0, GF=432.0, BF=424.0, WALKOUT); Proposed Electric Line; Proposed 4" PVC sewer lateral with cleanouts (TOP=431.6, INV.=427.8; TOP=431.6, INV.=426.4; TOP=429.6, INV.=424.4); Lot 2 Rain Garden (Bottom Elev.=422.0, 2' Wide Berm Elev.=423.5, 15' Long Emergency Spillway Elev.=423.0).
  • Lot 3: Proposed dwelling footprint (LOT 3: FF=422.0, GF=420.0, BF=412.0, WALKOUT); Proposed Electric Line; Grinder Pump (INV.=411.0) and Proposed 1 1/4" LPSS connecting to 4" PVC gravity sewer lateral; Lot 3 Rain Garden (Bottom Elev.=407.0, 2' Wide Berm Elev.=409.0, 15' Long Emergency Spillway Elev.=408.5).

LEGEND:

  • STEEP SLOPES (15% TO 25%)
  • STEEP SLOPES (OVER 25%)
  • CONCRETE SURFACE
  • EXISTING WETLANDS LINE
  • STREAM LINE
  • FLOOD HAZARD DISTRICT LINE
  • EXISTING INTERMEDIATE CONTOUR
  • EXISTING INDEX CONTOUR
  • EXISTING WOODS / TREE LINE
  • ADJOINER LINE
  • EXISTING STORM SEWER LINE
  • EXISTING RIGHT-OF-WAY LINE
  • EXISTING PAVING
  • EXISTING SOILS LINE
  • PROPOSED INTERMEDIATE CONTOUR (528)
  • PROPOSED INDEX CONTOUR (530)
  • PROPOSED SPOT ELEVATION (x 513.4)
  • PROPOSED STORM SEWER LINE
  • PROPOSED SANITARY SEWER LINE
  • PROPOSED WATER LINE
  • PROPOSED WOODS / TREE LINE
  • SUPER SILT FENCE
  • LIMIT OF DISTURBANCE
  • NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • STABILIZED RIP-RAP CONSTRUCTION ENTRANCE

PENNSYLVANIA ONE CALL & UNDERGROUND UTILITY USERS

(PURSUANT TO ACT 287, 172, 38 AND ALL OTHER APPLICABLE AMENDMENTS) COMMONWEALTH ENGINEERS, INC. DOES NOT GUARANTEE THE ACCURACY OF THE LOCATIONS FOR EXISTING SUBSURFACE UTILITY LINES, STRUCTURES, ETC., SHOWN ON THE PLANS, NOR DOES COMMONWEALTH ENGINEERS, INC. GUARANTEE THAT ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., ARE SHOWN. THE CONTRACTOR SHALL VERIFY THE LOCATION AND ELEVATIONS OF ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., BEFORE THE START OF WORK. (TELEPHONE: (800) 242-1776)
UPI No.5306-0089-0000
PENNSYLVANIA ONE-CALL SYSTEM SERIAL NUMBER: 20160320567

  • PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA 19312, (610) 648-7702
  • VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 592-4151
  • AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
  • COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
  • EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
  • WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475

REVISIONS

REV NO. DATE DESCRIPTION
51/10/17PER CCCD REVIEW LETTER DATED 1/4/17
412/19/16CHANGES TO SANITARY SEWER DESIGN
312/12/16PER CCCD REVIEW LETTER DATED 12/6/16
210/17/16PER TWP. REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT
15/23/16PER PADEP REVIEW LETTER DATED 5/19/16

EXISTING CONDITIONS PLAN

SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY

EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA

COMMONWEALTH ENGINEERS, INC.
114 EAST LANCASTER AVENUE ~ SECOND FLOOR
DOWNINGTOWN, PA 19335
TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004
COMENG@CEI-1.COM

DATE SCALE SURVEY DRAWN CHECKED DRAWING NO. SHEET
MAY 17, 2016 1"=40' MBS TT VK 201541-(C) 3 OF 11

IMPERVIOUS AREA REMOVAL LEGEND

  • = IMPERVIOUS AREA TO BE PERMANENTLY REMOVED AND REPLACED WITH NEW IMPERVIOUS AREA (TOTAL AREA=726 SQ. FT)
  • = IMPERVIOUS AREA TO BE PERMANENTLY REMOVED AND REPLACED WITH LAWN COVER (TOTAL AREA=2050 SQ. FT)

DRAWING AND LOCATION MAP DESCRIPTION

Existing Conditions Plan drawing (Scale 1" = 40') and inset Location Map (Scale 1" = 2000') for UPI 5306 0089 0000 (N/F Antoinette S. Brakman, DB 3529 PG 1960; Gross Area = 221,252.80 SQ FT / 5.079 Acres; Net Area = 210,253.0 SF / 4.827 Acres) along East Strasburg Road (S.R. 2010, 50 foot wide legal right of way, posted speed limit 40 MPH) opposite Brook Drive:

  • Existing site features: Existing Dwelling, Existing Shed, second Existing Shed (TBR) near southern boundary, existing driveway to East Strasburg Road, existing stone wall, approximate location of existing septic system, Tributary 7 of East Branch Chester Creek, FEMA 100-Yr Floodplain Zone A, 50' Riparian Buffer, soil lines (UrB, UrD), steep slope shading, and existing trees labeled with sizes, species (Tulip, Oak, Pine, Dogwood, Holly, Hemlock, Cherry, Apple, Maple, Locust), and "(TBR)" where to be removed.
  • Boundary bearings and distances: N71°27'39"E 410.78'; S24°28'52"E 524.73'; S65°43'30"W 403.18'; N25°01'38"W 565.83'.
  • Adjoining properties: UPI 5306B 0054 0000 N/F Daniel E. Cherry (DB 8962, PG 505); UPI 5306B 0052 0000 N/F William E. Leigh (DB 484, PG 105); UPI 5306B 0051 0000 N/F Christine V. Kaplan (DB 4941, PG 1427); UPI 5306B 0046 0000 N/F Joseph P. Lyons (DB X-49, PG 85); UPI 5306B 0047 0000 N/F John M. Donohue (DB 2670, PG 502); UPI 5306 0090 0000 N/F Joseph M. & Carole A. Matthews (DB 6136, PG 953); UPI 5306 0090 0100 N/F Christopher N. & Deborah Falcone (DB 8774, PG 511); UPI 5306B 0004 0000 N/F Robert & Shirley Sullivan (DB U-61, PG 290); UPI 5306B 0003 0000 N/F Denise Danielle Jordan (DB 9077, PG 2274); UPI 5306 0002 0000 and UPI 5306 0004 0000 N/F Joseph E. Erdeljac Jr (DB 2574, PG 272); UPI 5306B 0039 0000 N/F Dirk & Jaan I. Troltenier (DB 6476, PG 1417); UPI 5306B 0038 0000 N/F Charles W. & Sue Ellen Hendrickson (DB 5067, PG 531).

LEGEND:

  • STEEP SLOPES (15% TO 25%)
  • STEEP SLOPES (OVER 25%)
  • CONCRETE SURFACE
  • EXISTING WETLANDS LINE
  • STREAM LINE
  • FLOOD HAZARD DISTRICT LINE
  • EXISTING INTERMEDIATE CONTOUR
  • EXISTING INDEX CONTOUR
  • EXISTING WOODS / TREE LINE
  • ADJOINER LINE
  • EXISTING STORM SEWER LINE
  • EXISTING RIGHT-OF-WAY LINE
  • EXISTING PAVING
  • EXISTING SOILS LINE
  • PROPOSED INTERMEDIATE CONTOUR (528)
  • PROPOSED INDEX CONTOUR (530)
  • PROPOSED SPOT ELEVATION (x 513.4)
  • PROPOSED STORM SEWER LINE
  • PROPOSED SANITARY SEWER LINE
  • PROPOSED WATER LINE
  • PROPOSED WOODS / TREE LINE
  • SUPER SILT FENCE
  • LIMIT OF DISTURBANCE
  • NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • STABILIZED RIP-RAP CONSTRUCTION ENTRANCE

PENNSYLVANIA ONE CALL & UNDERGROUND UTILITY USERS

(PURSUANT TO ACT 287, 172, 38 AND ALL OTHER APPLICABLE AMENDMENTS) COMMONWEALTH ENGINEERS, INC. DOES NOT GUARANTEE THE ACCURACY OF THE LOCATIONS FOR EXISTING SUBSURFACE UTILITY LINES, STRUCTURES, ETC., SHOWN ON THE PLANS, NOR DOES COMMONWEALTH ENGINEERS, INC. GUARANTEE THAT ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., ARE SHOWN. THE CONTRACTOR SHALL VERIFY THE LOCATION AND ELEVATIONS OF ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., BEFORE THE START OF WORK. (TELEPHONE: (800) 242-1776)
UPI No.5306-0089-0000
PENNSYLVANIA ONE-CALL SYSTEM SERIAL NUMBER: 20160320567

  • PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA 19312, (610) 648-7702
  • VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 592-4151
  • AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
  • COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
  • EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
  • WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475

REVISIONS

REV NO. DATE DESCRIPTION
51/10/17PER CCCD REVIEW LETTER DATED 1/4/17
412/19/16CHANGES TO SANITARY SEWER DESIGN
312/12/16PER CCCD REVIEW LETTER DATED 12/6/16
210/17/16PER TWP. REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT
15/23/16PER PADEP REVIEW LETTER DATED 5/19/16

PCSM & GRADING PLAN

SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY

EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA

COMMONWEALTH ENGINEERS, INC.
114 EAST LANCASTER AVENUE ~ SECOND FLOOR
DOWNINGTOWN, PA 19335
TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004
COMENG@CEI-1.COM

DATE SCALE SURVEY DRAWN CHECKED DRAWING NO. SHEET
MAY 17, 2016 1"=40' MBS TT VK 201541-(C) 4 OF 11

SOIL IDENTIFICATION:

SYMBOL DESCRIPTION HYDROLOGIC GROUP DEPTH TO WATER DEPTH TO BEDROCK
UrB URBAN LAND-GLADSTONE COMPLEX, 0 TO 8 PERCENT SLOPES A >80" 60"-100"
UrD URBAN LAND-GLADSTONE COMPLEX, 0 TO 8 PERCENT SLOPES A >80" 60"-100"

SOIL USE LIMITATIONS & RESOLUTIONS:

ONLY THOSE LIMITATIONS TO ON-SITE SOILS AS DESCRIBED BY APPENDIX E OF THE 2012 EROSION CONTROL MANUAL ARE ADDRESSED BELOW.

USE LIMITATION PROPOSED RESOLUTION(S)
1. CUTBANKS CAVE (UrB,UrD) ALL APPLICABLE OSHA STANDARDS AND REGULATIONS WILL BE IMPLEMENTED.
2. CORROSIVENESS TO CONCRETE AND/OR STEEL (UrB,UrD) CHEMICAL PRE-TREATMENT OF ANY CONCRETE ENDWALLS TO PROVIDE ANTI-CORROSIVE PROPERTIES.
3. EASILY ERODIBLE (UrB,UrD) EROSION CONTROL MATTING IS PROPOSED AS APPROPRIATE.
4. HYDRIC SOILS/INCLUSIONS (UrB,UrD) LIMITED DISTURBANCE IN ANY POTENTIAL HYDRIC AREAS.
5. SLOW PERCOLATION (UrB,UrD) ON-SITE TESTING WAS PERFORMED TO ENSURE ADEQUATE PERCOLATION FOR BMP FACILITIES.
6. FROST ACTION (UrB,UrD) FROST ACTION IS NOT EXPECTED TO AFFECT PROPOSED FACILITIES.
7. SHRINK/SWELL (UrB,UrD) SHRINK/SWELL IS NOT EXPECTED TO AFFECT PROPOSED FACILITIES.

FINAL CERTIFICATION REQUIREMENTS:

THE PERMITTEE SHALL INCLUDE WITH THE NOTICE OF TERMINATION "RECORD DRAWINGS" A FINAL CERTIFICATION STATEMENT FROM A LICENSED PROFESSIONAL, WHICH READS AS FOLLOWS:

"I (NAME) DO HEREBY CERTIFY PURSUANT TO THE PENALTIES OF 18 Pa. C.S.A. SECTION 4904, TO THE BEST OF MY KNOWLEDGE, INFORMATION AND BELIEF, THAT THE ACCOMPANYING RECORD DRAWINGS ACCURATELY REFLECT THE AS-BUILT CONDITIONS, ARE TRUE AND CORRECT, AND ARE IN CONFORMANCE WITH CHAPTER 102 OF THE RULES AND REGULATIONS OF THE DEPARTMENT OF ENVIRONMENTAL PROTECTION AND THAT THE PROJECT SITE WAS CONSTRUCTED IN ACCORDANCE WITH THE APPROVED PCSM PLAN, ALL APPROVED PLAN CHANGES AND ACCEPTED CONSTRUCTION PRACTICES."

  • (1) THE PERMITTEE SHALL RETAIN A COPY OF HE RECORD DRAWINGS AS A PART OF THE APPROVED PCSM PLAN.
  • (2) THE PERMITTEE SHALL PROVIDE A COPY OF THE RECORD DRAWINGS AS A PART OF THE APPROVED PCSM PLAN TO THE PERSON IDENTIFIED IN THIS SECTION AS BEING RESPONSIBLE FOR THE LONG-TERM OPERATION & MAINTENANCE OF THE PCSM PLAN.

NOTICE OF TERMINATION REQUIREMENTS:

UPON PERMANENT STABILIZATION OF THE EARTH DISTURBANCE ACTIVITIES UNDER 102.22(A)(2) (RELATING TO PERMANENT STABILIZATION) AND INSTALLATION OF BMPS IN ACCORDANCE WITH AN APPROVED PLAN PREPARED AND IMPLEMENTED IN ACCORDANCE WITH 102.4 AND 102.8 (RELATING TO EROSION AND SEDIMENT CONTROL REQUIREMENTS; AND PCSM REQUIREMENTS), THE PERMITTEE OR CO-PERMITTEE SHALL SUBMIT A NOTICE OF TERMINATION TO THE CONSERVATION DISTRICT.

SITE GEOLOGY:

THE ENTIRE SITE IS UNDERLAIN BY FELSIC GNEISS PER THE PADEP EMAPPA WEBSITE.

CONSTRUCTION WASTE DISPOSAL NOTE:

THE OPERATOR SHALL REMOVE FROM THE SITE, RECYCLE, OR DISPOSE OF ALL BUILDING MATERIALS AND WASTE PRODUCTS IN ACCORDANCE WITH THE DEPARTMENT'S SOLID WASTE MANAGEMENT REGULATIONS AT 25 PA CODE 260.1 ET SEQ., 271.1 ET SEQ. AND 287.1 ET SEQ. THE CONTRACTOR SHALL NOT BURY, DUMP, OR DISCHARGE ANY BUILDING MATERIALS OR WASTE PRODUCTS AT THE SITE.

OFFER OF BLANKET EASEMENT:

A BLANKET STORMWATER MANAGEMENT EASEMENT IS PROVIDED OVER AND ACROSS THE PROPERTY IN FAVOR OF EAST GOSHEN TOWNSHIP TO ALLOW THE TOWNSHIP AND ITS AGENT AND DESIGNEES ACCESS TO THE PROPOSED STORMWATER MANAGEMENT FACILITIES. THE TOWNSHIP IS GRANTED THE RIGHT, BUT NOT THE DUTY, TO ACCESS AND CONDUCT PERIODIC INSPECTIONS AND TO UNDERTAKE OTHER ACTIONS THAT MAY BE NECESSARY TO ENFORCE THE REQUIREMENTS OF THE TOWNSHIP'S STORMWATER MANAGEMENT ORDINANCE OR OF ANY APPLICABLE O&M PLAN OR O&M AGREEMENT.

PCSM PLAN REVISIONS:

I HEREBY ACKNOWLEDGE THAT ANY REVISIONS TO THE APPROVED SWM SITE PLAN SHALL BE SUBMITTED TO AND APPROVED BY THE TOWNSHIP AND ANY REVISIONS TO THE EROSION AND SEDIMENT CONTROL PLAN SHALL BE SUBMITTED TO AND APPROVED BY THE CONSERVATION DISTRICT OR TOWNSHIP (AS APPLICABLE) FOR A DETERMINATION OF ADEQUACY PRIOR TO THE CONSTRUCTION OF THE REVISED FEATURES.

(JIM BRANDOLINI) (DATE)

PCSM PLAN CERTIFICATION:

I, VICTOR KELLY, JR., PE, ON THIS DATE ___________________ HEREBY CERTIFY TO THE BEST OF MY KNOWLEDGE THAT THE SWM SITE PLAN MEETS ALL DESIGN STANDARDS AND CRITERIA OF THE EAST GOSHEN TOWNSHIP STORMWATER MANAGEMENT ORDINANCE (CHAPTER 195).

(VICTOR KELLY, JR., PE) (DATE)

GENERAL NOTES:

  • 1. RECORD OWNER: ANTOINETTE BRAKMAN, 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380, UPI 5306-0089-0000 (TAX #53-6-89), PHONE: (610) 436-0152, DEED REFERENCES: DB. 3529, PG. 1960. EQUITABLE OWNER: JIM BRANDOLINI, GUNNISON DEVELOPMENT CO., LLC, 1200 BURNING BUSH LANE, WEST CHESTER, PA 19380, PHONE: (610) 640-9174.
  • 2. SITE ADDRESS: 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380
  • 3. TRACT AREA: 221,252.8 SQ. FT / 5.079 ACRES (GROSS) LESS 40' ROAD RIGHT-OF-WAY: 17,152.849 SQ. FT. / 0.394 ACRES NET TRACT AREA: 4.685 ACRES (NET)
  • 4. BOUNDARY AND PARTIAL TOPOGRAPHY FROM FIELD SURVEY PERFORMED BY COMMONWEALTH ENGINEERS, INC., APRIL 2016. BENCHMARK: NO. 4 REBAR FOUND, NORTHEAST CORNER OF SITE DATUM: ASSUMED USGS
  • 5. WETLANDS DELINEATION BY VORTEX ENVIRONMENTAL, INC. AND SURVEYED BY COMMONWEALTH ENGINEERS, INC. IN MAY 2016.
  • 6. SOILS CLASSIFICATIONS FROM THE UNITED STATES DEPARTMENT OF AGRICULTURE (USDA) NATURAL RESOURCE CONSERVATION DISTRICT WEB SOIL SURVEY, IN AUGUST, 2014.
  • 7. UNDERGROUND UTILITIES SHOWN HEREON WERE PLOTTED FROM OBSERVABLE EVIDENCE AT THE TIME OF SURVEY AND THROUGH INFORMATION PROVIDED BY THE UTILITY COMPANIES WHICH SERVICE/OCCUPY THE SITE. NO GUARANTEE IS MADE THAT UNDERGROUND UTILITIES ARE ACCURATELY OR COMPLETELY SHOWN HEREON. THE SITE CONTRACTOR MUST VERIFY LOCATION AND DEPTH OF ALL UNDERGROUND UTILITIES AND FACILITIES PRIOR TO BEGINNING CONSTRUCTION.
  • 8. THE SITE IS SERVED BY PUBLIC WATER (AQUA PA).
  • 9. EXISTING SANITARY SYSTEM PRESENT ON SITE BUT NOT LOCATED.
  • 10. EXISTING IRON PINS ARE SHOWN AS THUS "O".
  • 11. THE DEVELOPER SHALL CONFORM TO OR CAUSE CONFORMANCE WITH ALL OF THE APPLICABLE REQUIREMENTS OF THIS PLAN AND THE EAST GOSHEN TOWNSHIP ZONING ORDINANCE AND SUBDIVISION AND LAND DEVELOPMENT ORDINANCE AS WELL AS OTHER APPLICABLE LOCAL, STATE AND FEDERAL LAWS, STATUTES, REGULATIONS AND ORDINANCES.
  • 12. THE DEVELOPER SHALL NOTIFY UNDERGROUND UTILITY USERS AT LEAST THREE DAYS PRIOR TO THE COMMENCEMENT OF CONSTRUCTION IN ACCORDANCE WITH PA ACT 287 OF 1974, AS AMENDED BY ACT 187 OF 1996 & ALL OTHER APPLICABLE AMENDMENTS, AS WELL AS CONFORM TO APPLICABLE REGULATIONS OF SAID ACTS. UNDERGROUND UTILITIES SHOWN ARE FROM SURFACE EVIDENCE OBSERVABLE IN THE FIELD AND AS MARKED BY THE UTILITY COMPANIES.
  • 13. FEMA FLOODPLAIN BOUNDARY TAKEN FROM FLOOD INSURANCE RATE MAP, PANEL 215F, MAP NUMBER 42029C0215F, DATED SEPTEMBER 29, 2006.
  • 14. THIS PROJECT IS LOCATED IN THE WATERSHED OF TRIBUTARY 7 OF EAST BRANCH CHESTER CREEK WHICH HAS THE DESIGNATION OF TROUT STOCK FISHES (TSF, MF) BY THE COMMONWEALTH OF PENNSYLVANIA.
  • 15. THIS PROJECT PROPOSES THE SUBDIVISION OF THE EXISTING LOT INTO 3 SEPARATE LOTS WITH EACH LOT TO BE SERVED BY PUBLIC WATER AND PUBLIC SEWER. PUBLIC SEWER TO BE THROUGH LOW PRESSURE FORCE MAIN TIED INTO AN EXISTING MANHOLE AS SHOWN.

SURVEY REFERENCE NOTES

  • 1. PLAN ENTITLED "BOUNDARY SURVEY PLAN FOR MS. ANTOINETTE BRAKMAN", PREPARED BY R.H. SMITH SURVEYORS, DATED MARCH 27, 2007.
  • 2. PLAN ENTITLED "REVERSE SUBDIVISION/SUBDIVISION PLAN FOR MICHAEL RIZZO", PREPARED BY BRANDYWINE VALLEY ENGINEERS, A DIVISION OF VOLLMER ASSOCIATES, LLP, CONSULTING ENGINEERS AND LAND SURVEYORS, DATED NOVEMBER 30, 2001.
  • 3. PECO BLANKET RIGHT-OF-WAY CONTAINED IN MISCELLANEOUS DB. 81, PG 452.
  • 4. PLAN ENTITLED "THE GAMBONE BROTHERS INC.", PREPARED BY HENRY S. CONREY INC., DIVISION OF CHESTER VALLEY ENGINEERS, DATED JUNE 6, 1973 (LAST REVISED SEPTEMBER 9, 1973).

STORMWATER TEST PIT INFORMATION:

INFILTRATION TESTING PERFORMED WITH A DOUBLE-RING INFILTROMETER

TEST PIT ID INFILTRATION RATE TESTING DEPTH TESTING ELEVATION LIMITING ZONE DEPTH LIMITING ZONE DESCRIPTION
LOT 2 2.50 IN/HR 36" 420.3 61" ROCK ENCOUNTERED
LOT 3 2.25 IN/HR 24" 406.6 48" ROCK ENCOUNTERED

RECEIVING WATERSHED NOTICE:

THIS PROJECT IS WHOLLY LOCATED WITHIN THE WATERSHED OF TRIBUTARY 7 OF EAST CHESTER CREEK, A WATERSHED DESIGNATED TROUT STOCK FISHERY: MIGRATORY FISHERY (TSF: MF) BY THE COMMONWEALTH OF PENNSYLVANIA.

DRAWING AND LOCATION MAP DESCRIPTION

PCSM & Grading Plan drawing (Scale 1" = 40') and inset Location Map (Scale 1" = 2000') illustrating proposed grading, drainage areas, stormwater management BMPs, and utility connections within the NPDES Boundary:

  • NPDES Boundary and Limit of Disturbance = 66,038 SQ. FT. = 1.52 ACRES; Line of Interest #1 and Line of Interest #2; Lot 2 Rain Garden Drainage Area and Lot 3 Rain Garden Drainage Area.
  • Driveway & Swale features: Construct railroad tie retaining wall around existing utility pole; 2:1 Side Slopes; Proposed Grass Swale (Trapezoidal, 2:1 Side Slopes, 2' Bottom Width, Depth=1.5', Slope=10.2%, Lined with NAG S150 or Equal) discharging to 7'x7' Riprap Pad, R-3 Stone, Depth=9".
  • Lot 3 Stormwater & Grading: Lot 3 (FF=422.0, GF=420.0, BF=412.0, WALKOUT); SW TP-1 (LOT 3); Lot 3 Rain Garden (Bottom Elev.=407.0, 2' Wide Berm Elev.=409.0, 15' Long Emergency Spillway Elev.=408.5); 8" PVC Elbow/Riser w/ Drainage Grate (TG=408.0, INV.=406.0); 24 L.F. 8" PVC @ 2.1% Slope; 10' Long x 3' Wide Level Spreader (TOP=408.0, 8" Pipe (Fully Perf.), INV.=405.5, BOTTOM=405.0); Roof drain collector piping system (for roof drains on south side of house) to tie into rain garden as shown (gutter guards required on roof drains tied to this system).
  • Lot 2 Stormwater & Grading: Lot 2 (FF=434.0, GF=432.0, BF=424.0, WALKOUT); 3:1 Side Slopes and 2:1 Side Slopes; SW TP-2 (LOT 2); Lot 2 Rain Garden (Bottom Elev.=422.0, 2' Wide Berm Elev.=423.5, 15' Long Emergency Spillway Elev.=423.0); 8" PVC Elbow/Riser w/ Drainage Grate (TG=422.5, INV.=420.5); 16 L.F. 8" PVC @ 3.1% Slope; 15' Long x 3' Wide Level Spreader (TOP=421.5, 8" Pipe (Fully Perf.), INV.=420.0, BOTTOM=419.5).

LEGEND:

  • STEEP SLOPES (15% TO 25%)
  • STEEP SLOPES (OVER 25%)
  • CONCRETE SURFACE
  • EXISTING WETLANDS LINE
  • STREAM LINE
  • FLOOD HAZARD DISTRICT LINE
  • EXISTING INTERMEDIATE CONTOUR
  • EXISTING INDEX CONTOUR
  • EXISTING WOODS / TREE LINE
  • ADJOINER LINE
  • EXISTING STORM SEWER LINE
  • EXISTING RIGHT-OF-WAY LINE
  • EXISTING PAVING
  • EXISTING SOILS LINE
  • PROPOSED INTERMEDIATE CONTOUR (528)
  • PROPOSED INDEX CONTOUR (530)
  • PROPOSED SPOT ELEVATION (x 513.4)
  • PROPOSED STORM SEWER LINE
  • PROPOSED SANITARY SEWER LINE
  • PROPOSED WATER LINE
  • PROPOSED WOODS / TREE LINE
  • SUPER SILT FENCE
  • LIMIT OF DISTURBANCE
  • NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • STABILIZED RIP-RAP CONSTRUCTION ENTRANCE

PENNSYLVANIA ONE CALL & UNDERGROUND UTILITY USERS

(PURSUANT TO ACT 287, 172, 38 AND ALL OTHER APPLICABLE AMENDMENTS) COMMONWEALTH ENGINEERS, INC. DOES NOT GUARANTEE THE ACCURACY OF THE LOCATIONS FOR EXISTING SUBSURFACE UTILITY LINES, STRUCTURES, ETC., SHOWN ON THE PLANS, NOR DOES COMMONWEALTH ENGINEERS, INC. GUARANTEE THAT ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., ARE SHOWN. THE CONTRACTOR SHALL VERIFY THE LOCATION AND ELEVATIONS OF ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., BEFORE THE START OF WORK. (TELEPHONE: (800) 242-1776)
UPI No.5306-0089-0000
PENNSYLVANIA ONE-CALL SYSTEM SERIAL NUMBER: 20160320567

  • PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA 19312, (610) 648-7702
  • VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 592-4151
  • AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
  • COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
  • EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
  • WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475

REVISIONS

REV NO. DATE DESCRIPTION
51/10/17PER CCCD REVIEW LETTER DATED 1/4/17
412/19/16CHANGES TO SANITARY SEWER DESIGN
312/12/16PER CCCD REVIEW LETTER DATED 12/6/16
210/17/16PER TWP. REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT
15/23/16PER PADEP REVIEW LETTER DATED 5/19/16

PCSM NON-STRUCTURAL BMP PLAN

SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY

EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA

COMMONWEALTH ENGINEERS, INC.
114 EAST LANCASTER AVENUE ~ SECOND FLOOR
DOWNINGTOWN, PA 19335
TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004
COMENG@CEI-1.COM

DATE SCALE SURVEY DRAWN CHECKED DRAWING NO. SHEET
MAY 17, 2016 1"=40' MBS TT VK 201541-(C) 5 OF 11

SITE STABILIZATION STANDARDS:

UPON COMPLETION OR TEMPORARY CESSATION OF THE EARTH DISTURBANCE ACTIVITY THAT WILL EXCEED 4 DAYS, OR ANY STAGE THEREOF, THE PROJECT SITTE SHALL BE IMMEDIATELY STABILIZED WITH THE APPROPRIATE TEMPORARY OR PERMANENT STABILIZATION.

DURING NON-GERMINATING PERIODS HAY OF STRAW MULCH MUST BE APPLIED AT THE RATE OF THREE (3) TONS PER ACRE. DISTURBED AREAS WHICH ARE NOT AT FINISHED GRADE AND WHICH WILL BE REDISTURBED WITHIN ONE (1) YEAR MUST BE STABILIZED IN ACCORDANCE WITH TEMPORARY VEGETATIVE STABILIZATION SPECIFICATIONS. DISTURBED AREAS WHICH ARE AT FINISHED GRADE OR WHICH WILL NOT BE REDISTURBED WITHIN ONE YEAR MUST BE STABILIZED IN ACCORDANCE WITH THE PERMANENT VEGETATIVE STABILIZATION SPECIFICATIONS.

AN AREA SHALL BE CONSIDERED TO HAVE ACHIEVED FINAL STABILIZATION WHEN IT HAS A MINIMUM UNIFORM 70% PERENNIAL VEGETATIVE COVER AND/OR ANY OTHER PERMANENT, NON-VEGETATIVE COVER WITH A DENSITY SUFFICIENT TO RESIST ACCELERATED SURFACE EROSION AND SUBSURFACE CHARACTERISTICS SUFFICIENT TO RESIST SLIDING AND OTHER SUBSURFACE MOVEMENTS.

FINAL SITE STABILIZATION REQUIREMENTS:

AN AREA SHALL BE CONSIDERED TO HAVE ACHIEVED FINAL STABILIZATION WHEN IT HAS A MINIMUM UNIFORM 70% PERENNIAL VEGETATIVE COVER AND/OR ANY OTHER PERMANENT, NON-VEGETATIVE COVER WITH A DENSITY SUFFICIENT TO RESIST ACCELERATED SURFACE EROSION AND SUBSURFACE CHARACTERISTICS SUFFICIENT TO RESIST SLIDING AND OTHER SUBSURFACE MOVEMENTS.

IMMEDIATELY AFTER EARTH DISTURBANCE ACTIVITIES CEASE, THE OPERATOR SHALL STABILIZE ANY AREAS DISTURBED BY THE ACTIVITIES. DURING NON-GERMINATING PERIODS, MULCH MUST BE APPLIED AT THE SPECIFIED RATES. DISTURBED AREAS WHICH ARE NOT AT FINISHED GRADE AND WHICH WILL BE REDISTURBED WITHIN ONE (1) YEAR MUST BE STABILIZED IN ACCORDANCE WITH THE TEMPORARY VEGETATIVE STABILIZATION SPECIFICATIONS. DISTURBED AREAS WHICH ARE AT FINISHED GRADE OR WHICH WILL NOT BE REDISTURBED WITHIN ONE YEAR MUST BE STABILIZED IN ACCORDANCE WITH THE PERMANENT VEGETATIVE STABILIZATION SPECIFICATIONS.

GEOLOGIC OR SOIL CONDITIONS POLLUTION:

THERE ARE NO KNOWN NATURALLY OCCURRING GEOLOGIC OR SOILS CONDITIONS ON THIS SITE THAT MAY HAVE THE POTENTIAL TO CAUSE POLLUTION DURING CONSTRUCTION OR AFTER EARTH DISTURBANCE ACTIVITIES ARE COMPLETED AND PCSM BMPs ARE OPERATIONAL. SHOULD SUCH CONDITIONS BE DETECTED, THE OWNER SHALL CONTACT THE PLAN ENGINEER AND THE CHESTER COUNTY CONSERVATION DISTRICT TO DISCUSS REMEDIAL ACTIONS.

GEOTEXTILE STABILIZATION REQUIREMENTS:

ALL DISTURBED SLOPES STEEPER THAN 3:1 (33%) SHALL BE IMMEDIATELY STABILIZED WITH AN APPROPRIATE EROSION CONTROL GEOTEXTILE FABRIC (NORTH AMERICAN GREEN C125 OR AN APPROVED EQUIVALENT), PERMANENT SEEDING, AND LIME AS PRESCRIBED.

TEMPORARY SITE STABILIZATION REQUIREMENTS:

UPON COMPLETION OR TEMPORARY CESSATION OF THE EARTH DISTURBANCE ACTIVITY THAT WILL EXCEED FOUR (4) DAYS, OR ANY STAGE THEREOF, THE PROJECT SITE SHALL BE IMMEDIATELY STABILIZED WIT THE APPROPRIATE TEMPORARY OR PERMANENT STABILIZATION. PLAN NOTES AND THE CONSTRUCTION SEQUENCE SHOULD REFLECT THIS REQUIREMENT. THE CONSTRUCTION SEQUENCE SHOULD INCORPORATE THE IMMEDIATE STABILIZATION REQUIREMENT INTO ANY APPLICABLE AREAS. (PLEASE NOTE THAT HYDROSEED IS NOT CONSIDERED STABILIZATION UNTIL IT GERMINATES). HAY OR STRAW MULCH MUST BE APPLIED AT 3.0 TONS PER ACRE.

UNFORESEEN EROSIVE CONDITIONS:

  • 1. SHOULD ANY UNFORESEEN EROSIVE CONDITIONS DEVELOP DURING CONSTRUCTION, THE CONTRACTOR SHALL TAKE THE ACTION TO REMEDY SUCH CONDITIONS AND TO PREVENT DAMAGE TO ADJACENT PROPERTIES AS A RESULT OF INCREASED RUNOFF AND/OR SEDIMENT DISPLACEMENT. STOCKPILES OF WOOD CHIPS, HAY BALES, CRUSHED STONE, AND OTHER ACCEPTABLE MULCHES SHALL BE HELD IN READINESS TO IMMEDIATELY ADDRESS EMERGENCY EROSION AND SEDIMENTATION PROBLEMS.
  • 2. THE CONTRACTOR IS ADVISED TO BECOME THOROUGHLY FAMILIAR WITH ALL OF THE PROVISIONS OF APPENDIX 64, "EROSION CONTROL RULES AND REGULATIONS, TITLE 25, PART 1, DEPARTMENT OF ENVIRONMENTAL PROTECTION, SUB-PART C, PROTECTION OF NATURAL RESOURCES, ARTICLE III, WATER RESOURCES, CHAPTER 102, EROSION CONTROL."
  • 3. CONSTRUCTION OPERATIONS SHALL BE CARRIED OUT IN SUCH A MANNER THAT ALL EROSION & AIR POLLUTION IS MINIMIZED. STATE AND LOCAL LAW CONCERNING POLLUTION ABATEMENT SHALL BE OBSERVED.
  • 4. MEASURES FOR THE PROTECTION OF EXISTING TREES AND SHRUBS SHALL BE TAKEN BY THE CONTRACTOR TO ELIMINATE UNNECESSARY DAMAGE.

* A COPY OF THESE EROSION AND SEDIMENTATION POLLUTION CONTROL PLANS MUST BE POSTED AND AVAILABLE AT THE CONSTRUCTION SITE IN ACCORDANCE WITH STATE AND FEDERAL LAW.

POST CONSTRUCTION STORMWATER BMPS:

POST CONSTRUCTION STORMWATER BMPS ARE PERMANENT FACILITIES THAT CANNOT BE REMOVED OR ALTERED WITHOUT APPROVAL OF THE TOWNSHIP.

POST-CONSTRUCTION STORMWATER MANAGEMENT DESIGN:

THIS SITE WILL UTILIZE TWO (2) PRIMARY STORMWATER MANAGEMENT FACILITIES TO CONTROL THE POST-DEVELOPMENT PEAK RATES OF STORMWATER RUNOFF AND STORMWATER VOLUME FOR THE SITE IN ACCORDANCE WITH PADEP BMP GUIDELINES. THE STORMWATER MANAGEMENT FACILITIES SHALL BE CONSTRUCTED AND MAINTAINED TO THE SPECIFICATIONS DESCRIBED IN THESE PLANS AND WILL ACCOMPLISH THE FOLLOWING:

  • PRESERVE THE INTEGRITY OF STREAM CHANNELS AND PROTECT THE PHYSICAL, BIOLOGICAL, AND CHEMICAL QUALITIES OF THE RECEIVING STREAM THROUGH REDUCTION OF POST-DEVELOPMENT PEAK RATES AND VOLUMES OF STORMWATER RUNOFF AND THE MITIGATION OF THERMAL IMPACTS.
  • PREVENT THE INCREASE IN STORMWATER RUNOFF THROUGH RETENTION OF INTERCEPTED OVERLAND RUNOFF.
  • CAPTURE AND REMOVE THE INCREASE IN STORMWATER RUNOFF VOLUME THROUGH THE PROPOSED RAIN GARDEN FACILITIES THAT WILL PROVIDE INFILTRATION AND EVAPOTRANSPIRATION OF THE INCREASE IN STORMWATER RUNOFF VOLUME FROM PRE-DEVELOPMENT TO POST-DEVELOPMENT CONDITIONS FOR THE 2-YEAR STORM EVENT.

IN ADDITION, THE FOLLOWING NON-STRUCTURAL PRACTICES ARE PROMOTED TO REDUCE THE STRUCTURAL POST-CONSTRUCTION STORMWATER MANAGEMENT REQUIREMENTS:

  • MINIMIZE IMPERVIOUS AREAS BY PROPOSING ONLY THE MINIMUM IMPERVIOUS COVER NECESSARY FOR THE VIABILITY OF THE PROPOSED USE.
  • MAXIMIZE THE PROTECTION OF EXISTING DRAINAGE FEATURES AND VEGETATION BY DISCHARGING EACH RAIN GARDEN THROUGH AN ENERGY DISSIPATING DEVICE.
  • MINIMIZE LAND CLEARING AND GRADING BY STRICTLY DELINEATING LIMITS OF PROPOSED EARTH DISTURBANCE AND BY PROVIDING A SEQUENCE OF CONSTRUCTION THAT REQUIRES SENSIBLE AND EFFICIENT PROJECT STAGING AND IMMEDIATE STABILIZATION OF DISTURBANCE.
  • MINIMIZE SOIL COMPACTION BY STRICTLY DELINEATING LIMITS OF PROPOSED EARTH DISTURBANCE AND BY PROVIDING A SEQUENCE OF CONSTRUCTION THAT REQUIRES SENSIBLE AND EFFICIENT PROJECT STAGING AND IMMEDIATE STABILIZATION OF DISTURBANCE.
  • UTILIZE OTHER STRUCTURAL AND NON-STRUCTURAL BMP'S THAT WILL PREVENT AND/OR MINIMIZE CHANGES IN STORMWATER RUNOFF VIA INFILTRATION, VEGETATIVE FILTRATION, DETENTION AND RESTRICTED RELEASE OF OVERLAND RUNOFF, AND PROTECTION OF EXISTING DRAINAGE FEATURES AND VEGETATION.

RECEIVING WATERSHED NOTICE:

THIS PROJECT IS WHOLLY LOCATED WITHIN THE WATERSHED OF TRIBUTARY 7 OF EAST CHESTER CREEK, A WATERSHED DESIGNATED TROUT STOCK FISHERY: MIGRATORY FISHERY (TSF: MF) BY THE COMMONWEALTH OF PENNSYLVANIA.

INFILTRATION FACILITY PROTECTION NOTICE:

ALL PROPOSED UNDERGROUND STORMWATER INFILTRATION FACILITIES PROPOSED WITH THESE PLANS MUST BE PROTECTED DURING CONSTRUCTION FROM SOIL COMPACTION AND SEDIMENT CONTAMINATION AT ALL TIMES. CONSTRUCTION OF ALL INFILTRATION FACILITIES SHALL BE STAGED IN SUCH A MANNER AS TO AFFORD THE FACILITY MAXIMUM PROTECTION FROM CONTAMINATION AND SOIL COMPACTION DURING CONSTRUCTION.

INFILTRATION FACILITY FAILURE NOTICE:

STORMWATER INFILTRATION BMP FAILURE IS DEFINED AS THE BMP NO LONGER PROVIDING THE BENIFIT OR PERFORMANCE THE BMP WAS INTENDED TO PROVIDE. STORMWATER INFILTRATION BMPs FAILURE MAY BE EVIDENT IF STORMWATER DISCHARGE HAS EXCESSIVE LEVELS OF POLLUTANTS. FAILURE MAY BE THE LOSE OF STRUCTURAL INTEGRITY OF THE WEARING COURSE FOR POROUS PAVING. FAILURE MAY BE THE INABILITY TO SUPPORT SURFACE VEGETATION IN RAIN GARDEN. FAILURE MAY BE STANDING WATER FOR LONGER THAN 3 DAYS WITHIN AN INFILTRATION BASIN OR INFILTRATION BED. THE PROPERTY OWNER OR RESPONSIBLE PARTY SHOULD CONTACT THE TOWNSHIP TO DETERMINE THE CORRECTIVE MEASURE(S) TO BE TAKEN SHOULD FAILURE OF A STORMWATER INFILTRATION BMP OCCUR.

GEOLOGIC OR SOIL CONDITIONS POLLUTION:

THERE ARE NO KNOWN NATURALLY OCCURRING GEOLOGIC OR SOILS CONDITIONS ON THIS SITE THAT MAY HAVE THE POTENTIAL TO CAUSE POLLUTION DURING CONSTRUCTION OR AFTER EARTH DISTURBANCE ACTIVITIES ARE COMPLETED AND PCSM BMPs ARE OPERATIONAL. SHOULD SUCH CONDITIONS BE DETECTED, THE OWNER SHALL CONTACT THE PLAN ENGINEER AND THE CHESTER COUNTY CONSERVATION DISTRICT TO DISCUSS REMEDIAL ACTIONS.

DRAWING AND LOCATION MAP DESCRIPTION

PCSM Non-Structural BMP Plan drawing (Scale 1" = 40') and inset Location Map (Scale 1" = 2000') showing hatched non-structural BMP areas within the NPDES Boundary:

  • AREA OF PROTECTED SENSITIVE/SPECIAL VALUE FEATURES = 117,634 SQ. FT. = 2.70 ACRES
  • AREA OF MINIMIZED TOTAL DISTURBED AREA = 38,507 SQ. FT. = 0.88 ACRES
  • LIMIT OF DISTURBANCE = 66,038 SQ. FT. = 1.52 ACRES
  • AREA OF DISCONNECTION FROM STORM SEWERS = 2,971 SQ. FT.
  • LINE OF INTEREST #1 and LINE OF INTEREST #2
  • LOT 2 (FF=434.0, GF=432.0, BF=424.0, WALKOUT) and LOT 3 (FF=422.0, GF=420.0, BF=412.0, WALKOUT)

LEGEND:

  • STEEP SLOPES (15% TO 25%)
  • STEEP SLOPES (OVER 25%)
  • CONCRETE SURFACE
  • EXISTING WETLANDS LINE
  • STREAM LINE
  • FLOOD HAZARD DISTRICT LINE
  • EXISTING INTERMEDIATE CONTOUR
  • EXISTING INDEX CONTOUR
  • EXISTING WOODS / TREE LINE
  • ADJOINER LINE
  • EXISTING STORM SEWER LINE
  • EXISTING RIGHT-OF-WAY LINE
  • EXISTING PAVING
  • EXISTING SOILS LINE
  • PROPOSED INTERMEDIATE CONTOUR (528)
  • PROPOSED INDEX CONTOUR (530)
  • PROPOSED SPOT ELEVATION (x 513.4)
  • PROPOSED STORM SEWER LINE
  • PROPOSED SANITARY SEWER LINE
  • PROPOSED WATER LINE
  • PROPOSED WOODS / TREE LINE
  • SUPER SILT FENCE
  • LIMIT OF DISTURBANCE
  • NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • STABILIZED RIP-RAP CONSTRUCTION ENTRANCE

PENNSYLVANIA ONE CALL & UNDERGROUND UTILITY USERS

(PURSUANT TO ACT 287, 172, 38 AND ALL OTHER APPLICABLE AMENDMENTS) COMMONWEALTH ENGINEERS, INC. DOES NOT GUARANTEE THE ACCURACY OF THE LOCATIONS FOR EXISTING SUBSURFACE UTILITY LINES, STRUCTURES, ETC., SHOWN ON THE PLANS, NOR DOES COMMONWEALTH ENGINEERS, INC. GUARANTEE THAT ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., ARE SHOWN. THE CONTRACTOR SHALL VERIFY THE LOCATION AND ELEVATIONS OF ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., BEFORE THE START OF WORK. (TELEPHONE: (800) 242-1776)
UPI No.5306-0089-0000
PENNSYLVANIA ONE-CALL SYSTEM SERIAL NUMBER: 20160320567

  • PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA 19312, (610) 648-7702
  • VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 592-4151
  • AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
  • COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
  • EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
  • WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475

REVISIONS

REV NO. DATE DESCRIPTION
51/10/17PER CCCD REVIEW LETTER DATED 1/4/17
412/19/16CHANGES TO SANITARY SEWER DESIGN
312/12/16PER CCCD REVIEW LETTER DATED 12/6/16
210/17/16PER TWP. REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT
15/23/16PER PADEP REVIEW LETTER DATED 5/19/16

6 COMMONWEALTH ENGINEERS, INC.

1) The project site is currently a combination of woods, meadow, and lawn with one existing dwelling and two existing sheds. There is also an existing septic system on the site. Stormwater runoff drains off the site from east to west into Tributary 7 of East Branch Chester Creek (TSF, MF). 2) This site achieves the requirements of East Goshen Township Stormwater Management Ordinance Section 195-18 by controlling stormwater runoff to pre-development conditions. These requirements are displayed throughout the PCSM Plans, E&SPC Plans, and the corresponding reports. 3) This site achieves the requirements of East Goshen Township Stormwater Management Ordinance Sections 195-15 through 195-25 through the use of a variety of stormwater BMP's (rain gardens) and conveyance systems (swales) to control stormwater runoff to pre-development conditions while complying with the design standards stated in the above stormwater management ordinance sections. 4) This project proposes the construction of 2 new dwellings and new paved driveway areas. Stormwater runoff from the new buildings will be directed to individual on-lot rain gardens through overland flow or roof drain collection piping systems. These rain gardens will retain and infiltrate runoff for the various design storms. Erosion and sediment control will be achieved primarily through the use of silt fences. 5) The project proposes no adverse effects on adjacent or downstream properties or conveyance systems since the project proposed the use of stormwater BMP's that will control stormwater runoff to pre-development conditions for various design storm events and that will retain runoff volume onsite for the 2-year storm. 6) The project implements water quality BMP's in the form of conserving of riparian buffers and minimizing of total disturbed areas. 7) Construction of this project is anticipated to begin the winter of 2017 and end the summer of 2017. 8) This project will be constructed as a single phase.

EROSION & SEDIMENT CONTROL PLAN

SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY

EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA

COMMONWEALTH ENGINEERS, INC., 114 EAST LANCASTER AVENUE ~ SECOND FLOOR, DOWNINGTOWN, PA 19335, TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004, COMENG@CEI-1.COM

  • DATE: MAY 17, 2016
  • SCALE: 1"=40'
  • SURVEY: MBS
  • DRAWN: TT
  • CHECKED: VK
  • DRAWING NO.: 201541-(C)
  • SHEET: 7 OF: 11

REVISIONS

REV No. DATE DESCRIPTION
5 1/10/17 PER CCCD REVIEW LETTER DATED 1/4/17
4 12/19/16 CHANGES TO SANITARY SEWER DESIGN
3 12/12/16 PER CCCD REVIEW LETTER DATED 12/8/16
2 10/17/16 PER TWP. REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT
1 5/23/16 PER PADOT REVIEW LETTER DATED 5/18/16

CONSTRUCTION OVERSIGHT REQUIREMENTS:

THE PERMITTEE SHALL PROVIDE ENGINEERING CONSTRUCTION OVERSIGHT FOR THE PROPOSED STORMWATER BMPS. ADDITIONAL SOIL TESTING MAY BE REQUIRED PRIOR TO THE INSTALLATION OF INFILTRATION BMPS TO ENSURE PROPER LOCATION & FUNCTION. A LICENSED PROFESSIONAL ENGINEER KNOWLEDGEABLE IN THE DESIGN AND CONSTRUCTION OF STORMWATER BMPS, PREFERABLY THE DESIGN ENGINEER, SHALL CONDUCT THE OVERSIGHT.

CONSTRUCTION WASTE DISPOSAL NOTE:

THE OPERATOR SHALL REMOVE FROM THE SITE, RECYCLE, OR DISPOSE OF ALL BUILDING MATERIALS AND WASTE PRODUCTS IN ACCORDANCE WITH THE DEPARTMENT'S SOLID WASTE MANAGEMENT REGULATIONS AT 25 PA CODE 260.1 ET SEQ., 271.1 ET SEQ. AND 287.1 ET SEQ. THE CONTRACTOR SHALL NOT BURY, DUMP, OR DISCHARGE ANY BUILDING MATERIALS OR WASTE PRODUCTS AT THE SITE.

EROSION CONTROL PLAN REVISION NOTICE:

BEFORE INITIATING ANY REVISION TO THE APPROVED EROSION AND SEDIMENT CONTROL PLAN OR REVISIONS TO OTHER PLANS WHICH MAY AFFECT THE EFFECTIVENESS OF THE APPROVED E&S CONTROL PLAN, THE OPERATOR MUST RECEIVE APPROVAL OF THE REVISIONS FROM THE CHESTER COUNTY CONSERVATION DISTRICT. THE OPERATOR SHALL ASSURE THE APPROVED EROSION AND SEDIMENT CONTROL PLAN IS PROPERLY AND COMPLETELY IMPLEMENTED. IMMEDIATELY UPON DISCOVERING UNFORESEEN CIRCUMSTANCES POSING THE POTENTIAL FOR ACCELERATED EROSION AND/OR SEDIMENT POLLUTION, THE OPERATOR SHALL IMPLEMENT APPROPRIATE BEST MANAGEMENT PRACTICES TO ELIMINATE POTENTIAL FOR ACCELERATED EROSION AND/OR SEDIMENT POLLUTION.

SEDIMENT TRACKING NOTICE:

SEDIMENT TRACKED ONTO ANY ROADWAY OR SIDEWALK SHALL BE RETURNED TO THE CONSTRUCTION SITE BY THE END OF EACH WORKDAY AND DISPOSED OF IN THE MANNER DESCRIBED IN THIS PLAN. IN NO CASE SHALL SEDIMENT BE WASHED, SHOVELED, OR SWEPT INTO ANY ROADSIDE DITCH, STORM SEWER, OR SURFACE WATER, INCLUDING THE SITE'S WETLANDS OR STREAM CHANNEL.

NOTICE OF TERMINATION REQUIREMENTS:

UPON PERMANENT STABILIZATION OF THE EARTH DISTURBANCE ACTIVITIES UNDER 102.22(A)(2) (RELATING TO PERMANENT STABILIZATION) AND INSTALLATION OF BMPS IN ACCORDANCE WITH AN APPROVED PLAN PREPARED AND IMPLEMENTED IN ACCORDANCE WITH 102.4 AND 102.8 (RELATING TO EROSION AND SEDIMENT CONTROL REQUIREMENTS; AND PCSM REQUIREMENTS), THE PERMITTEE OR CO-PERMITTEE SHALL SUBMIT A NOTICE OF TERMINATION TO THE CONSERVATION DISTRICT.

FINAL CERTIFICATION REQUIREMENTS:

THE PERMITTEE SHALL INCLUDE WITH THE NOTICE OF TERMINATION "RECORD DRAWINGS" A FINAL CERTIFICATION STATEMENT FROM A LICENSED PROFESSIONAL, WHICH READS AS FOLLOWS:

"I (NAME) DO HEREBY CERTIFY PURSUANT TO THE PENALTIES OF 18 Pa. C.S.A. SECTION 4904, TO THE BEST OF MY KNOWLEDGE, INFORMATION AND BELIEF, THAT THE ACCOMPANYING RECORD DRAWINGS ACCURATELY REFLECT THE AS-BUILT CONDITIONS, ARE TRUE AND CORRECT, AND ARE IN CONFORMANCE WITH CHAPTER 102 OF THE RULES AND REGULATIONS OF THE DEPARTMENT OF ENVIRONMENTAL PROTECTION AND THAT THE PROJECT SITE WAS CONSTRUCTED IN ACCORDANCE WITH THE APPROVED PCSM PLAN, ALL APPROVED PLAN CHANGES AND ACCEPTED CONSTRUCTION PRACTICES."

  • (1) THE PERMITTEE SHALL RETAIN A COPY OF HE RECORD DRAWINGS AS A PART OF THE APPROVED PCSM PLAN.
  • (2) THE PERMITTEE SHALL PROVIDE A COPU OF THE RECORD DRAWINGS AS A PART OF THE APPROVED PCSM PLANTO THE PERSON IDENTIFIED IN THIS SECTION AS BEING RESPONSIBLE FOR THE LONG-TERM OPERATION & MAINTENANCE OF THE PCSM PLAN.

LEGEND:

  • STEEP SLOPES (15% TO 25%)
  • STEEP SLOPES (OVER 25%)
  • CONCRETE SURFACE
  • EXISTING WETLANDS LINE
  • STREAM LINE
  • FLOOD HAZARD DISTRICT LINE
  • EXISTING INTERMEDIATE CONTOUR
  • EXISTING INDEX CONTOUR
  • EXISTING WOODS / TREE LINE
  • ADJOINER LINE
  • EXISTING STORM SEWER LINE
  • EXISTING RIGHT-OF-WAY LINE
  • EXISTING PAVING
  • EXISTING SOILS LINE
  • PROPOSED INTERMEDIATE CONTOUR
  • PROPOSED INDEX CONTOUR
  • PROPOSED SPOT ELEVATION
  • PROPOSED STORM SEWER LINE
  • PROPOSED SANITARY SEWER LINE
  • PROPOSED WATER LINE
  • PROPOSED WOODS / TREE LINE
  • SUPER SILT FENCE
  • LIMIT OF DISTURBANCE
  • NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • STABILIZED RIP-RAP CONSTRUCTION ENTRANCE

PENNSYLVANIA ONE CALL

(PURSUANT TO ACT 287, 172, 38 AND ALL OTHER APPLICABLE AMENDMENTS) COMMONWEALTH ENGINEERS, INC. DOES NOT GUARANTEE THE ACCURACY OF THE LOCATIONS FOR EXISTING SUBSURFACE UTILITY LINES, STRUCTURES, ETC., SHOWN ON THE PLANS, NOR DOES COMMONWEALTH ENGINEERS, INC. GUARANTEE THAT ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., ARE SHOWN.

THE CONTRACTOR SHALL VERIFY THE LOCATION AND ELEVATIONS OF ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., BEFORE THE START OF WORK. [TELEPHONE: (800) 242-1776]

UPI No.5306-0089-0000

PENNSYLVANIA ONE-CALL SYSTEM SERIAL NUMBER: 20160320567 (1-800-242-1776 - STOP - CALL BEFORE YOU DIG!)

UNDERGROUND UTILITY USERS

  • PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA. 19312, (610) 648-7702
  • AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
  • EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
  • VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 562-4151
  • COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
  • WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475

PLAN DRAWING AND LOCATION MAP

Site plan drawing (Graphic Scale: 1" = 40') and inset Location Map (Scale: 1" = 2000') showing erosion and sediment control measures for the Brakman Property along East Strasburg Road (S.R. 2010, 50 Foot Wide Legal Right of Way, Posted Speed Limit - 40 MPH) and Brook Drive, near Tributary 7 of East Branch Chester Creek and FEMA 100-Yr Floodplain Zone A (50' Riparian Buffer).

  • LIMIT OF DISTURBANCE = 66,038 SQ. FT. = 1.52 ACRES
  • SUPER SILT FENCE (SSF #01 through SSF #08)
  • ROCK CONSTRUCTION ENTRANCE (at East Strasburg Road and interior driveway)
  • TOPSOIL STOCKPILE (two locations)
  • ROCK FILTER
  • NAG S150 LINING (OR APPROVED EQUAL)
  • PROPOSED GRASS SWALE (TRAPEZOIDAL): 2:1 SIDE SLOPES, 1' BOTTOM WIDTH, DEPTH=1.5', SLOPE=10.3% (LINED WITH NAG S150 OR EQUAL)
  • PULL-OFF AREA
  • EXISTING DWELLING and EXISTING SHED
  • COMPOST SOCK CONCRETE WASHOUT STATION
  • ORANGE CONSTRUCTION FENCE
  • LOT 2: FF=434.0, GF=432.0, BF=424.0, WALKOUT
  • LOT 3: FF=422.0, GF=420.0, BF=412.0, WALKOUT
  • PROPOSED ELECTRIC LINE

OVERALL SEQUENCE OF CONSTRUCTION:

ALL EARTH DISTURBANCE ACTIVITIES SHALL PROCEED IN ACCORDANCE WITH THE FOLLOWING SEQUENCE. EACH STAGE SHALL BE COMPLETED BEFORE ANY FOLLOWING STAGE IS INITIATED. CLEARING AND GRUBBING SHALL BE LIMITED ONLY TO THOSE AREAS DESCRIBED IN EACH STAGE. FOLLOW ALL GUIDELINES AND PROCEDURES AS STATED IN "EROSION & SEDIMENTATION POLLUTION CONTROL MEASURES" DURING ENTIRE CONSTRUCTION PROCEDURE.

AT LEAST 7 DAYS BEFORE ANY EARTHMOVING BEGINS, THE OPERATOR SHALL INVITE ALL CONTRACTORS INVOLVED IN THIS PROJECT, THE LANDOWNER, ALL APPROPRIATE MUNICIPAL OFFICIALS, THE PLAN ENGINEER, THE CHESTER COUNTY CONSERVATION DISTRICT, AND THE SOUTHEAST REGIONAL OFFICE DEPARTMENT OF ENVIRONMENTAL PROTECTION ENGINEER TO AN ON-SITE PRE-CONSTRUCTION MEETING.

ALL INFILTRATION FACILITIES AND RAIN GARDENS SHALL BE PROTECTED FROM SEDIMENT-LADEN RUNOFF. FAILURE TO ADEQUATELY PROTECT INFILTRATION FACILITIES AND RAIN GARDENS FROM SEDIMENT DEPOSITION WILL REQUIRE REHABILITATION TO RESTORE THEM TO PROPER FUNCTIONING.

UPON COMPLETION OR TEMPORARY CESSATION OF THE EARTH DISTURBANCE ACTIVITY THAT WILL EXCEED 4 DAYS, OR ANY STAGE THEREOF, THE PROJECT SITE SHALL BE IMMEDIATELY STABILIZED WITH THE APPROPRIATE TEMPORARY OR PERMANENT STABILIZATION.

  • 1. CLEARLY DELINEATE ALL PROPOSED DISTURBANCE LIMITS AND TREES TO BE PROTECTED.
  • 2. INSTALL THE STABILIZED ROCK CONSTRUCTION ENTRANCES.
  • 3. INSTALL SUPER SILT FENCES AS SHOWN ON EROSION & SEDIMENT CONTROL PLAN.
  • 4. INSTALL COMPOST SOCK CONCRETE WASHOUT STATION.
  • 5. BEGIN CLEARING AND GRUBBING OF AREAS FOR THE PROPOSED BUILDINGS AND DRIVEWAY AREAS.
  • 6. REMOVE THE EXISTING SHED AS NOTED ON THE PLANS.
  • 7. PERFORM GRADING OPERATIONS FOR DRIVEWAY AREAS AND AROUND PROPOSED BUILDINGS. INSTALL EROSION CONTROL LINING ON NEWLY GRADED AREAS AS SHOWN ON EROSION & SEDIMENT CONTROL PLAN IMMEDIATELY AFTER GRADING FOR EACH AREA IS COMPLETED.
  • 8. CONSTRUCT GRASS SWALE #1, RIP-RAP PAD, AND ASSOCIATED EROSION CONTROL LINING. IMMEDIATELY INSTALL ROCK FILTER AS SHOWN ON PLAN.
  • 9. CONSTRUCT BUILDINGS.
  • 10. INSTALL UTILITIES. 10.1. ANY TRENCHES THAT ARE EXCAVATED FOR UTILITY INSTALLATIONS TO BE BACKFILLED THE SAME DAY.; 10.2. ANY EARTH DISTURBANCE ASSOCIATED WITH UTILITY INSTALLATIONS TO BE RESTORED AND STABILIZED IMMEDIATELY WITH EROSION CONTROL LINING (OR OTHER MEANS).
  • 11. PAVE DRIVEWAY AREAS.
  • 12. (CRITICAL STAGE) ONCE ALL UPSTREAM AREAS ARE STABILIZED IN ACCORDANCE WITH FINAL SITE STABILIZATION REQUIREMENTS, REMOVE ORANGE CONSTRUCTION FENCES AND INSTALL THE RAIN GARDENS FOR LOT 2 AND LOT 3 (SEE SEPARATE "RAIN GARDEN SEQUENCE OF CONSTRUCTION" ON SHEET 6, PCSM NOTES AND DETAILS). INSTALL EROSION CONTROL LINING ON NEWLY GRADED AREAS AS SHOWN ON EROSION & SEDIMENT CONTROL PLAN IMMEDIATELY AFTER GRADING FOR EACH RAIN GARDEN IS COMPLETED.
  • 13. IMMEDIATELY STABILIZE ANY DORMANT DISTURBANCE WITH PERMANENT SEED MIXTURE, MULCH AT 3 TONS/AC, AND LIME AND FERTILIZER AS PRESCRIBED.
  • 14. STABILIZE ALL DISTURBANCE AREAS.
  • 15. ONCE ALL FEATURES (INCLUDING THE PROPOSED BUILDINGS AND DRIVEWAY AREAS) HAVE BEEN CONSTRUCTED AND ALL DISTURBANCE STABILIZED IN ACCORDANCE WITH FINAL SITE STABILIZATION REQUIREMENTS, REMOVE THE SUPER SILT FENCES, ROCK FILTER, AND THE REMAINDER OF THE ROCK CONSTRUCTION ENTRANCE.
  • 16. ONCE THE SITE HAS BEEN STABILIZED IN ACCORDANCE WITH FINAL SITE STABILIZATION REQUIREMENTS, FILE AN NPDES PERMIT NOTICE OF TERMINATION FORM WITH THE CONSERVATION DISTRICT PER THE "NOTICE OF TERMINATION REQUIREMENTS" NOTE IN THESE PLANS.

# CRITICAL STAGES OF THE SEQUENCE OF CONSTRUCTION ARE CIRCLED. THESE STAGES WITHIN THE SEQUENCE REQUIRE INSPECTION BY THE SITE ENGINEER.

STANDARD E&S CONTROL PLAN NOTES:

  • 1. ALL EARTH DISTURBANCES, INCLUDING CLEARING AND GRUBBING AS WELL AS CUTS AND FILLS SHALL BE DONE IN ACCORDANCE WITH THE APPROVED E&S PLAN. A COPY OF THE APPROVED DRAWINGS (STAMPED, SIGNED AND DATED BY THE REVIEWING AGENCY) MUST BE AVAILABLE AT THE PROJECT SITE AT ALL TIMES. THE REVIEWING AGENCY SHALL BE NOTIFIED OF ANY CHANGES TO THE APPROVED PLAN PRIOR TO IMPLEMENTATION OF THOSE CHANGES. THE AGENCY MAY REQUIRE A WRITTEN SUBMITTAL OF THOSE CHANGES FOR REVIEW AND APPROVAL AT ITS DISCRETION.
  • 2. AT LEAST 7 DAYS PRIOR TO STARTING ANY EARTH DISTURBANCE ACTIVITIES, INCLUDING CLEARING AND GRUBBING, THE OWNER AND/OR OPERATOR SHALL INVITE ALL CONTRACTORS, THE LANDOWNER, APPROPRIATE MUNICIPAL OFFICIALS, THE E&S PLAN PREPARER, THE PCSM PLAN PREPARER, THE LICENSED PROFESSIONAL RESPONSIBLE FOR OVERSIGHT OF CRITICAL STAGES OF IMPLEMENTATION OF THE PCSM PLAN & A REPRESENTATIVE FROM THE LOCAL CONSERVATION DISTRICT TO AN ON-SITE PRECONSTRUCTION MEETING.
  • 3. AT LEAST 3 DAYS PRIOR TO STARTING ANY EARTH DISTURBANCE ACTIVITIES, OR EXPANDING INTO AN AREA PREVIOUSLY UNMARKED, THE PENNSYLVANIA ONE CALL SYSTEM INC. SHALL BE NOTIFIED AT 1-800-242-1776 FOR THE LOCATION OF EXISTING UNDERGROUND UTILITIES.
  • 4. ALL EARTH DISTURBANCE ACTIVITIES SHALL PROCEED IN ACCORDANCE WITH THE SEQUENCE PROVIDED ON THE PLAN DRAWINGS. DEVIATION FROM THAT SEQUENCE MUST BE APPROVED IN WRITING FROM THE LOCAL CONSERVATION DISTRICT OR BY THE DEPARTMENT PRIOR TO IMPLEMENTATION.
  • 5. AREAS TO BE FILLED ARE TO BE CLEARED, GRUBBED, AND STRIPPED OF TOPSOIL TO REMOVE TREES, VEGETATION, ROOTS AND OTHER OBJECTIONABLE MATERIAL.
  • 6. CLEARING, GRUBBING, AND TOPSOIL STRIPPING SHALL BE LIMITED TO THOSE AREAS DESCRIBED IN EACH STAGE OF THE CONSTRUCTION SEQUENCE. GENERAL SITE CLEARING, GRUBBING AND TOPSOIL STRIPPING MAY NOT COMMENCE IN ANY STAGE OR PHASE OF THE PROJECT UNTIL THE E&S BMPS SPECIFIED BY THE BMP SEQUENCE FOR THAT STAGE OR PHASE HAVE BEEN INSTALLED AND ARE FUNCTIONING AS DESCRIBED IN THIS E&S PLAN.
  • 7. AT NO TIME SHALL CONSTRUCTION VEHICLES BE ALLOWED TO ENTER AREAS OUTSIDE THE LIMIT OF DISTURBANCE BOUNDARIES SHOWN ON THE PLAN MAPS. THESE AREAS MUST BE CLEARLY MARKED AND FENCED OFF BEFORE CLEARING AND GRUBBING OPERATIONS BEGIN.
  • 8. TOPSOIL REQUIRED FOR THE ESTABLISHMENT OF VEGETATION SHALL BE STOCKPILED AT THE LOCATION(S) SHOWN ON THE PLAN MAPS(S) IN THE AMOUNT NECESSARY TO COMPLETE THE FINISH GRADING OF ALL EXPOSED AREAS THAT ARE TO BE STABILIZED BY VEGETATION. EACH STOCKPILE SHALL BE PROTECTED IN THE MANNER SHOWN ON THE PLAN DRAWINGS. STOCKPILE HEIGHTS SHALL NOT EXCEED 35 FEET. STOCKPILE SLOPES SHALL BE 2H:1V OR FLATTER.
  • 9. IMMEDIATELY UPON DISCOVERING UNFORESEEN CIRCUMSTANCES POSING THE POTENTIAL FOR ACCELERATED EROSION AND/OR SEDIMENT POLLUTION, THE OPERATOR SHALL IMPLEMENT APPROPRIATE BEST MANAGEMENT PRACTICES TO MINIMIZE THE POTENTIAL FOR EROSION AND SEDIMENT POLLUTION AND NOTIFY THE LOCAL CONSERVATION DISTRICT AND/OR THE REGIONAL OFFICE OF THE DEPARTMENT.
  • 10. ALL BUILDING MATERIALS AND WASTES SHALL BE REMOVED FROM THE SITE & RECYCLED OR DISPOSED OF IN ACCORDANCE WITH THE DEPARTMENT'S SOLID WASTE MANAGEMENT REGULATIONS AT 25 PA. CODE 260.1 ET SEQ., 271.1, AND 287.1 ET. SEQ. NO BUILDING MATERIALS OR WASTES OR UNUSED BUILDING MATERIALS SHALL BE BURNED, BURIED, DUMPED, OR DISCHARGED AT THE SITE.
  • 11. ALL OFF-SITE WASTE AND BORROW AREAS MUST HAVE AN E&S PLAN APPROVED BY THE LOCAL CONSERVATION DISTRICT OR THE DEPARTMENT FULLY IMPLEMENTED PRIOR TO BEING ACTIVATED.
  • 12. THE CONTRACTOR IS RESPONSIBLE FOR ENSURING THAT ANY MATERIAL BROUGHT ON SITE IS CLEAN FILL. FORM FP-001 MUST BE RETAINED BY THE PROPERTY OWNER FOR ANY FILL MATERIAL AFFECTED BY A SPILL OR RELEASE OF A REGULATED SUBSTANCE BUT QUALIFYING AS CLEAN FILL DUE TO ANALYTICAL TESTING.
  • 13. ALL PUMPING OF WATER FROM ANY WORK AREA SHALL BE DONE ACCORDING TO THE PROCEDURE DESCRIBED IN THIS PLAN, OVER UNDISTURBED VEGETATED AREAS.
  • 14. VEHICLES AND EQUIPMENT MAY NEITHER ENTER DIRECTLY NOR EXIT DIRECTLY FROM PROPOSED LOTS ONTO ADJACENT PUBLIC ROADWAYS.
  • 15. UNTIL THE SITE IS STABILIZED, ALL EROSION AND SEDIMENT BMPS SHALL BE MAINTAINED PROPERLY. MAINTENANCE SHALL INCLUDE INSPECTIONS OF ALL EROSION AND SEDIMENT BMPS AFTER EACH RUNOFF EVENT AND ON A WEEKLY BASIS. ALL PREVENTATIVE AND REMEDIAL MAINTENANCE WORK, INCLUDING CLEAN OUT, REPAIR, REPLACEMENT, REGRADING, RESEEDING, REMULCHING AND RENETTING MUST BE PERFORMED IMMEDIATELY. IF THE E&S BMPS FAIL TO PERFORM AS EXPECTED, REPLACEMENT BMPS, OR MODIFICATIONS OF THOSE INSTALLED WILL BE REQUIRED.
  • 16. A LOG SHOWING DATES THAT E&S BMPS WERE INSPECTED AS WELL AS ANY DEFICIENCIES FOUND AND THE DATE THEY WERE CORRECTED SHALL BE MAINTAINED ON THE SITE AND BE MADE AVAILABLE TO REGULATORY AGENCY OFFICIALS AT THE TIME OF INSPECTION.
  • 17. SEDIMENT TRACKED ONTO ANY PUBLIC ROADWAY OR SIDEWALK SHALL BE RETURNED TO THE CONSTRUCTION SITE BY THE END OF EACH WORK DAY AND DISPOSED OF IN THE MANNER DESCRIBED IN THIS PLAN. IN NO CASE SHALL THE SEDIMENT BE WASHED, SHOVELED, OR SWEPT INTO ANY ROADSIDE DITCH, STORM SEWER, OR SURFACE WATER.
  • 18. ALL SEDIMENT REMOVED FROM BMPS SHALL BE DISPOSED OF IN THE MANNER DESCRIBED ON THE PLAN DRAWINGS.
  • 19. AREAS WHICH ARE TO BE TOPSOILED SHALL BE SCARIFIED TO A MINIMUM DEPTH OF 3 TO 5 INCHES (6 TO 12 INCHES ON COMPACTED SOILS) PRIOR TO PLACEMENT OF TOPSOIL. AREAS TO BE VEGETATED SHALL HAVE A MINIMUM 4 INCHES OF TOPSOIL IN PLACE PRIOR TO SEEDING AND MULCHING. FILL OUTSLOPES SHALL HAVE A MINIMUM OF 2 INCHES OF TOPSOIL.
  • 20. ALL FILLS SHALL BE COMPACTED AS REQUIRED TO REDUCE EROSION, SLIPPAGE, SETTLEMENT, SUBSIDENCE OR OTHER RELATED PROBLEMS. FILL INTENDED TO SUPPORT BUILDINGS, STRUCTURES AND CONDUITS, ETC. SHALL BE COMPACTED IN ACCORDANCE WITH LOCAL REQUIREMENTS OR CODES.
  • 21. ALL EARTHEN FILLS SHALL BE PLACED IN COMPACTED LAYERS NOT TO EXCEED 8" IN THICKNESS.
  • 22. FILL MATERIALS SHALL BE FREE OF FROZEN PARTICLES, BRUSH, ROOTS, SOD, OR OTHER FOREIGN OR OBJECTIONABLE MATERIALS THAT WOULD INTERFERE WITH OR PREVENT CONSTRUCTION OF SATISFACTORY FILLS.
  • 23. FROZEN MATERIALS OR SOFT, MUCKY, OR HIGHLY COMPRESSIBLE MATERIALS SHALL NOT BE INCORPORATED IN FILLS.
  • 24. FILL SHALL NOT BE PLACED ON SATURATED OR FROZEN SURFACES.
  • 25. SEEPS OR SPRINGS ENCOUNTERED DURING CONSTRUCTION SHALL BE HANDLED IN ACCORDANCE WITH THE STANDARD AND SPECIFICATION FOR SUBSURFACE DRAIN OR OTHER APPROVED METHOD.
  • 26. ALL GRADED AREAS SHALL BE PERMANENTLY STABILIZED IMMEDIATELY UPON REACHING FINISHED GRADE. CUT SLOPES IN COMPETENT BEDROCK AND ROCK FILLS NEED NOT BE VEGETATED. SEEDED AREAS WITHIN 50 FEET OF A SURFACE WATER, OR AS OTHERWISE SHOWN ON THE PLAN DRAWINGS, SHALL BE BLANKETED ACCORDING TO THE STANDARDS OF THIS PLAN.
  • 27. IMMEDIATELY AFTER EARTH DISTURBANCE ACTIVITIES CEASE IN ANY AREA OR SUBAREA OF THE PROJECT, THE OPERATOR SHALL STABILIZE ALL DISTURBED AREAS. DURING NON-GERMINATING MONTHS, MULCH OR PROTECTIVE BLANKETING SHALL BE APPLIED AS DESCRIBED IN THE PLAN. AREAS NOT AT FINISHED GRADE, WHICH WILL BE REACTIVATED WITHIN 1 YEAR, MAY BE STABILIZED IN ACCORDANCE WITH THE TEMPORARY STABILIZATION SPECS. THOSE AREAS WHICH WILL NOT BE REACTIVATED WITHIN 1 YEAR SHALL BE STABILIZED IN ACCORDANCE WITH THE PERMANENT STABILIZATION SPECIFICATIONS.
  • 28. PERMANENT STABILIZATION IS DEFINED AS A MINIMUM UNIFORM, PERENNIAL 70% VEGETATIVE COVER OR OTHER PERMANENT NON-VEGETATIVE COVER WITH A DENSITY SUFFICIENT TO RESIST ACCELERATED EROSION. CUT AND FILL SLOPES SHALL BE CAPABLE OF RESISTING FAILURE DUE TO SLUMPING, SLIDING, OR OTHER MOVEMENTS.
  • 29. E&S BMPS SHALL REMAIN FUNCTIONAL AS SUCH UNTIL ALL AREAS TRIBUTARY TO THEM ARE PERMANENTLY STABILIZED OR UNTIL THEY ARE REPLACED BY ANOTHER BMP APPROVED BY THE LOCAL CONSERVATION DISTRICT OR THE DEPARTMENT.
  • 30. UPON COMPLETION OF ALL EARTH DISTURBANCE ACTIVITIES AND PERMANENT STABILIZATION OF ALL DISTURBED AREAS, THE OWNER AND/OR OPERATOR SHALL CONTACT THE CONSERVATION DISTRICT FOR AN INSPECTION PRIOR TO REMOVAL/CONVERSION OF THE E&S BMPS.
  • 31. AFTER FINAL SITE STABILIZATION HAS BEEN ACHIEVED, TEMPORARY EROSION AND SEDIMENT BMPS MUST BE REMOVED OR CONVERTED TO PERMANENT POST CONSTRUCTION STORMWATER MANAGEMENT BMPS. AREAS DISTURBED DURING REMOVAL OR CONVERSION OF THE BMPS SHALL BE STABILIZED IMMEDIATELY. TO ENSURE RAPID REVEGETATION OF DISTURBED AREAS, SUCH REMOVAL/CONVERSIONS ARE TO BE DONE ONLY DURING THE GERMINATING SEASON.
  • 32. UPON COMPLETION OF ALL EARTH DISTURBANCE ACTIVITIES & PERMANENT STABILIZATION OF ALL DISTURBED AREAS, THE OWNER AND/OR OPERATOR SHALL CONTACT THE CONSERVATION DISTRICT TO SCHEDULE A FINAL INSPECTION.
  • 33. FAILURE TO CORRECTLY INSTALL E&S BMPS, FAILURE TO PREVENT SEDIMENT-LADEN RUNOFF FROM LEAVING THE CONSTRUCTION SITE, OR FAILURE TO TAKE IMMEDIATE CORRECTIVE ACTION TO RESOLVE FAILURE OF E&S BMPS MAY RESULT IN ADMINISTRATIVE, CIVIL, AND/OR CRIMINAL PENALTIES BEING INSTITUTED BY THE DEPARTMENT AS DEFINED IN SECTION 602 OF THE PENNSYLVANIA CLEAN STREAMS LAW. THE CLEAN STREAMS LAW PROVIDES FOR UP TO $10,000 PER DAY IN CIVIL PENALTIES, UP TO $10,000 IN SUMMARY CRIMINAL PENALTIES, AND UP TO $25,000 IN MISDEMEANOR CRIMINAL PENALTIES FOR EACH VIOLATION.
  • 34. CONCRETE WASH WATER SHALL BE HANDLED IN THE MANNER DESCRIBED ON THE PLAN DRAWINGS. IN NO CASE SHALL IT BE ALLOWED TO ENTER ANY SURFACE WATERS OR GROUNDWATER SYSTEMS.
  • 35. EROSION CONTROL BLANKETING SHALL BE INSTALLED ON ALL SLOPES 3H:1V OR STEEPER WITHIN 50 FT OF A SURFACE WATER AND ON ALL OTHER DISTURBED AREAS SPECIFIED ON THE PLAN MAPS AND/OR DETAIL SHEETS.
  • 36. FILL MATERIAL FOR EMBANKMENTS SHALL BE FREE OF ROOTS, OR OTHER WOODY VEGETATION, ORGANIC MATERIAL, LARGE STONES, AND OTHER OBJECTIONABLE MATERIALS. THE EMBANKMENT SHALL BE COMPACTED IN MAXIMUM 8 INCH LAYERED LIFTS AT 95% DENSITY.
  • 37. SEEPS AND SPRINGS ENCOUNTERED DURING CONSTRUCTION SHALL BE HANDLED IN ACCORDANCE WITH THE STANDARD AND SPECIFICATION FOR SUBSURFACE DRAIN OR OF THE APPROVED METHOD.

PLAN REFERENCE NOTE:

THIS EROSION & SEDIMENT CONTROL PLAN IS ASSOCIATED WITH THE "PCSM & GRADING PLAN" (SHEET 4) OF THE FULL SITE PLAN SET TITLED "BRAKMAN PROPERTY" AND DATED 5/17/16.

RECEIVING WATERSHED NOTICE:

THIS PROJECT IS WHOLLY LOCATED WITHIN THE WATERSHED OF TRIBUTARY 7 OF EAST CHESTER CREEK, A WATERSHED DESIGNATED TROUT STOCK FISHERY; MIGRATORY FISHERY (TSF; MF) BY THE COMMONWEALTH OF PENNSYLVANIA.

8 COMMONWEALTH ENGINEERS, INC.

STANDARD CONSTRUCTION DETAIL #3-16 PUMPED WATER FILTER BAG

STANDARD CONSTRUCTION DETAIL #11-1 EROSION CONTROL BLANKET INSTALLATION

STANDARD CONSTRUCTION DETAIL #3-1 ROCK CONSTRUCTION ENTRANCE

STANDARD CONSTRUCTION DETAIL #4-14 ROCK FILTER STANDARD CONSTRUCTION DETAIL #4-10 SUPER SILT FENCE

ENTRANCE DRIVEWAY PLAN & PROFILE

SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY

EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA

COMMONWEALTH ENGINEERS, INC., 114 EAST LANCASTER AVENUE ~ SECOND FLOOR, DOWNINGTOWN, PA 19335, TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004, COMENG@CEI-1.COM

  • DATE: MAY 17, 2016
  • SCALE: AS SHOWN
  • SURVEY: MBS
  • DRAWN: TT
  • CHECKED: VK
  • DRAWING NO.: 201541-(C)
  • SHEET: 9 OF: 11

PLAN VIEW (SCALE: 1"=40')

Plan view drawing of the entrance driveway connection to East Strasburg Road (S.R. 2010, 50 Foot Wide Legal Right of Way, Posted Speed Limit - 40 MPH) near Tributary 7 of East Branch Chester Creek and FEMA 100-Yr Floodplain Zone A (50' Riparian Buffer).

  • MINIMUM SAFE STOPPING DISTANCE=305', AVAILABLE SIGHT DISTANCE=455' (looking left/west)
  • MINIMUM SAFE STOPPING DISTANCE=395', AVAILABLE SIGHT DISTANCE=395' (looking right/east to EP: 3+95.00)
  • 40 FOOT WIDE RIGHT OF WAY
  • CONSTRUCT RAILROAD TIE RETAINING WALL AROUND EXISTING UTILITY POLE
  • Driveway alignment stations: BP: 0+00.00, PC: 0+23.88, PT: 0+99.82, PC: 1+22.50, PT: 1+46.76, PC: 1+80.33, PT: 2+35.66, EP: 2+41.38
  • 2:1 SIDE SLOPES and PULL-OFF AREA

PROFILE VIEW (DRIVEWAY ENTRANCE) (SCALE: 1"=4' VERTICAL; 1"=40' HORIZONTAL)

Vertical profile graph plotting Elevation (380 to 420 feet) against Station (-0+50 to 3+00) for Existing Grade and Proposed Grade along the driveway entrance.

  • GRADE BREAK STA = 0+11.62, ELEV = 388.82
  • Slope -2.00% to STA:0+15.62, ELEV:388.74
  • Slope -4.00% to STA:0+41.00, ELEV:389.76
  • Slope 10.00% to STA:0+66.00, ELEV:392.26
  • Slope 13.54% to GRADE BREAK STA = 2+41.38, ELEV = 416.00
  • Station 0+00: 388.94 / 388.93
  • Station 1+00: 399.28 / 399.27
  • Station 2+00: 411.88 / 411.88

PROFILE VIEW (RIGHT SIGHT DISTANCE LINE) (SCALE: 1"=4' VERTICAL; 1"=40' HORIZONTAL)

Vertical profile graph plotting Elevation (385 to 420 feet) against Station (-0+50 to 4+50) showing Existing Grade, Proposed Grade, and Sight Distance Line.

  • Station 0+00: 389.39 / 389.39
  • Station 1+00: 403.20 / 403.20
  • Station 2+00: 409.87 / 409.86
  • Station 3+00: 413.84 / 413.83

SIGHT DISTANCE NOTE:

SIGHT DISTANCES TO BE FIELD VERIFIED POST-CONSTRUCTION TO CONFIRM PROPER SIGHT DISTANCES ARE MET.

LEGEND:

  • STEEP SLOPES (15% TO 25%)
  • STEEP SLOPES (OVER 25%)
  • CONCRETE SURFACE
  • EXISTING WETLANDS LINE
  • STREAM LINE
  • FLOOD HAZARD DISTRICT LINE
  • EXISTING INTERMEDIATE CONTOUR
  • EXISTING INDEX CONTOUR
  • EXISTING WOODS / TREE LINE
  • ADJOINER LINE
  • EXISTING STORM SEWER LINE
  • EXISTING RIGHT-OF-WAY LINE
  • EXISTING PAVING
  • EXISTING SOILS LINE
  • PROPOSED INTERMEDIATE CONTOUR
  • PROPOSED INDEX CONTOUR
  • PROPOSED SPOT ELEVATION
  • PROPOSED STORM SEWER LINE
  • PROPOSED SANITARY SEWER LINE
  • PROPOSED WATER LINE
  • PROPOSED WOODS / TREE LINE
  • SUPER SILT FENCE
  • LIMIT OF DISTURBANCE
  • NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • STABILIZED RIP-RAP CONSTRUCTION ENTRANCE

PENNSYLVANIA ONE CALL

(PURSUANT TO ACT 287, 172, 38 AND ALL OTHER APPLICABLE AMENDMENTS) COMMONWEALTH ENGINEERS, INC. DOES NOT GUARANTEE THE ACCURACY OF THE LOCATIONS FOR EXISTING SUBSURFACE UTILITY LINES, STRUCTURES, ETC., SHOWN ON THE PLANS, NOR DOES COMMONWEALTH ENGINEERS, INC. GUARANTEE THAT ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., ARE SHOWN.

THE CONTRACTOR SHALL VERIFY THE LOCATION AND ELEVATIONS OF ALL SUBSURFACE UTILITY LINES, STRUCTURES, ETC., BEFORE THE START OF WORK. [TELEPHONE: (800) 242-1776]

UPI No.5306-0089-0000

PENNSYLVANIA ONE-CALL SYSTEM SERIAL NUMBER: 20160320567

UNDERGROUND UTILITY USERS

  • PHILADELPHIA ELECTRIC COMPANY, 1050 SWEDESFORD ROAD, BERWYN, PA. 19312, (610) 648-7702
  • AQUA PA, 762 W. LANCASTER AVE., BRYN MAWR, PA 19010, (877) 987-2782
  • EAST GOSHEN TOWNSHIP, 1580 PAOLI PIKE, WEST CHESTER, PA 19380, (610) 692-7171
  • VERIZON PENNSYLVANIA INC., 900 RACE STREET, 6TH FLOOR, PHILADELPHIA, PA 19107, (215) 562-4151
  • COMCAST, RT. 82 & MONACY RD., P.O. BOX 351, COATESVILLE, PA 19320, (800) 934-6489
  • WILLIAMS (TRANSCO GAS), 2800 POST OAK BOULEVARD, HOUSTON, TX 77056, (800) 440-8475

REVISIONS

REV No. DATE DESCRIPTION
5 1/10/17 PER CCCD REVIEW LETTER DATED 1/4/17
4 12/19/16 CHANGES TO SANITARY SEWER DESIGN
3 12/12/16 PER CCCD REVIEW LETTER DATED 12/8/16
2 10/17/16 PER TWP. REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT
1 5/23/16 PER PADOT REVIEW LETTER DATED 5/18/16

SANITARY SEWER PROFILE AND DETAILS

SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY

EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA

COMMONWEALTH ENGINEERS, INC., 114 EAST LANCASTER AVENUE ~ SECOND FLOOR, DOWNINGTOWN, PA 19335, TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004, COMENG@CEI-1.COM

  • DATE: MAY 17, 2016
  • SCALE: AS SHOWN
  • SURVEY: MBS
  • DRAWN: TT
  • CHECKED: VK
  • DRAWING NO.: 201541-(C)
  • SHEET: 10 OF: 11

TYPE "A" STANDARD MANHOLE (NOT TO SCALE)

Cross-sectional diagram (Section A-A) and plan view (Plan Below Line B-B) of a precast reinforced concrete manhole showing Manhole Frame and Cover, Precast Reinforced Concrete Eccentric Cone Top Section, Watertight Tongue and Groove Joint, Manhole Steps (12" Centers Min., 16" Centers Max.), Precast Reinforced Concrete Riser Section Wall Thickness (5" for 4'-0" Dia., 6" for 5'-0" Dia., 7" for 6'-0" Dia.), Concrete Fill, Shelf, Manhole Invert, 6" Min 2B Stone base, and 24" Diameter Opening.

NOTES:

  • 1. THE DEPTH OF THE INVERT CHANNEL SHALL BE EQUAL TO 3/4 OF THE DIAMETER OF THE SEWER.
  • 2. THE SHELF SHALL SLOPE TOWARD THE INVERT CHANNEL AT A RATE OF 1" PER FOOT.
  • 3. TYPE "B" MANHOLES (SHALLOW TYPE) TO BE PROVIDED WHERE REQUIRED BY DEPTH CONDITIONS.
  • 4. FOR MANHOLES HAVING 5' DIA. AND 6' DIA. BASE, REDUCTION IN DIA. TO 4' SHALL START AT THE FIRST JOINT ABOVE THE UPPERMOST PIPE CONNECTION TO WALL WHERE DEPTH IS SUFFICIENT.
  • 5. ALL MANHOLE FRAMES SHALL BE BOLTED TO THE CONE SECTION WITH 4-3/4" DIA. BOLTS WITH WASHERS AND NUTS, BOLTS TO BE AT 90/127 ON BOLT CIRCLE. FOR WATERTIGHT COVERS USE 4-3/4" DIA. BOLTS AT 90/127 ON THE BOLT CIRCLE.
  • 6. SEE THE SPECIFICATIONS FOR LENGTH OF PIPE CONNECTIONS TO MANHOLE.
  • 7. ALL CONCRETE SHALL BE 4000 P.S.I. MINIMUM, USING TYPE II PORTLAND CEMENT.
  • 8. ENTIRE OUTSIDE SURFACE OF MANHOLE SHALL RECIEVE TWO COATS OF BITUMINOUS COATING, KOP-COAT, INC. BITUMASTIC No. 300-M, TNEMEC 46H-413 TNEME TAR OR APPROVED EQUAL APPLIED AT 20 MIL. MINIMUM THICKNESS.
  • 9. INSTALL 2 LAYERS OF PLASTIC PERFORMED JOINT SEALANT BETWEEN ALL SECTIONS & UNDER FRAME.
  • 10. MANHOLE CONSTRUCTION SHALL BE IN ACCORDANCE WITH ASTM C478.
  • 11. STEPS TO ALUMINUM ALLOY WITH DEPRESSED TREAD. STEEL REINFORCED POLYPROPYLENE IS OPTIONAL.
  • 12. 4' DIA. MANHOLE - 8" TO 15" PIPES 5' DIA. MANHOLE - 16" TO 27" PIPES 6' DIA. MANHOLE - 30" TO 48" PIPES
  • 13. WHEN TWO OR MORE GRADE ADJUSTMENT RINGS ARE USED, A WATERTIGHT PVC CONNECTOR SHALL BE INSTALLED BETWEEN THE FRAME AND THE CONE. CONNECTOR SHALL BE WATER-LOK CONNECTOR BFA ANTI-FLOATING BY A-LOK PRODUCTS INC. OR APPROVED EQUAL.
  • 14. MANHOLES THAT RECIEVE FORCE MAIN DISCHARGE OR THAT ARE LOCATED ON INTERCEPTORS OR TRUNK SEWERS SHALL BE CONSTRUCTED WITH A PVC LINER.

SANITARY SEWER TRENCH (NOT TO SCALE)

Cross-sectional trench diagram showing Final Grade, 6" Topsoil, Seed and Mulch or Proposed Paving or Match Existing Condition, Replace Suitable Excavated Material, Min 6" Cover Over Pipe 2B Stone, 4" SDR 35 PVC (or 4" Schedule 40 PVC) Sanitary Sewer Pipe, 2B Stone, Min 6" Bedding 2B Stone, Width: Pipe Diameter Plus 12", and notes on compacted fill and placing clay "dams" in stone bedding at 300 ft. intervals.

GRINDER PUMP DETAIL (NOT TO SCALE)

GRINDER PUMP TO BE USED AS SHOWN ON LOT 3 (OR APPROVED EQUAL)

Schematic diagram of E/One Sewer Systems Model DH071 / DR071 (Detail Sheet NA0050P02) grinder pump station showing Options DH071 (Hard Wired Level Controls) and DR071 (Wireless Level Controls), Gasketed Lid FRP, Strain Relief Cord Connector, Protective Cable Shroud (HDPE), Electrical Quick Disconnect NEMA 4P, Power/Alarm Cable, E/One Equalizer, Internal Well Vent 2.0" Dia., Quick Disconnect Assy. (304 S.S.), S.S. Cast Ball Valve, Inlet Grommet to Accept 4.50" O.D. PVC Pipe, Discharge 1-1/4" FPT, 1-1/4" Discharge Line (304 S.S.), Check Valve (Noryl), Anti-Siphon Valve (Noryl), HDPE Tank Dual Wall Corrugated 70 Gallon Capacity, and Semi-Positive Displacement Type Pump Each Directly Driven by a 1 HP Motor.

PLAN VIEW (SCALE: 1"=40')

Plan view drawing of the proposed sanitary sewer layout from Lot 3 and adjoining lots along the driveway to East Strasburg Road.

  • TIE 6" PVC TO EXISTING MH (SANITARY MANHOLE RIM=384.37, INV.=378.0)
  • 6" PVC TO BE DIRECTIONALLY DRILLED
  • BORING PIT
  • TIE PROPOSED WATER LINE TO EXISTING WATER MAIN ALONG EAST STRASBURG RD.
  • PROPOSED MH: TOP=394.0, INV.=386.8
  • 3 SEPARATE PROPOSED 4" PVC GRAVITY SEWER LATERALS
  • Cleanouts (C.O.): TOP=406.5 INV.=403.1; TOP=406.9 INV.=403.1; TOP=407.1 INV.=403.1; TOP=423.6 INV.=419.9; TOP=423.8 INV.=419.9; TOP=423.9 INV.=419.9; TOP=428.5 INV.=423.1; TOP=428.6 INV.=423.1; TOP=429.5 INV.=424.4; TOP=429.6 INV.=424.4; TOP=431.6 INV.=425.4
  • PROPOSED 1-1/4" LPSS and GRINDER PUMP INV.=411.0 at LOT 3 (FF=422.0, GF=420.0, BF=412.0, WALKOUT)

INSTALLATION NOTES:

  • 1) SANITARY PIPE TO BE INSTALLED AS SHOWN USING FITTINGS (45 DEGREES OR LESS) AS APPROPRIATE.
  • 2) GRINDER PUMP DISCHARGE PIPING SHALL BE BEDDED IN EITHER SAND OR SCREENINGS. THE BEDDING SHALL BE AT LEAST 4 INCHES THICK. AFTER THE DISCHARGE PIPING HAS BEEN TESTED AND INSPECTED, AN ADDITIONAL 12 INCHES OF SAND OR SCREENINGS SHALL BE PLACED OVER THE PIPE.
  • 3) ALL GRAVITY SEWER PIPES FROM THE HOUSES TO INCLUDE A FRESH AIR VENT, A BUILDING TRAP, AND CLEANOUTS (AS SHOWN ON THE PLAN) TO BE INSTALLED PER EAST GOSHEN TOWNSHIP ORDINANCE SECTION 188-31.C.

PROFILE VIEW (EXISTING MH TO C.O.) (SCALE: 1"=4' VERTICAL; 1"=40' HORIZONTAL)

Vertical profile graph plotting Elevation (375 to 440 feet) against Station (-1+00 to 5+00) for the sanitary sewer line from the existing manhole to the upper cleanouts.

  • EXISTING MH: TOP=384.37, INV.=378.0 (APPROX.)
  • EXISTING 8" WATER LINE: INV.=386.7 (APPROX.)
  • PROPOSED 6" PVC
  • PROPOSED MH: TOP=394.0, INV.=386.8
  • INV.=392.0
  • PROPOSED CLEANOUT: TOP=407.1, INV.=403.1
  • PROPOSED GRADE and EXISTING GRADE
  • PROPOSED 4" PVC
  • PROPOSED CLEANOUT: TOP=423.8, INV.=419.9
  • PROPOSED CLEANOUT: TOP=428.6, INV.=423.1
  • PROPOSED CLEANOUT: TOP=429.6, INV.=424.4
  • NOTE: SANITARY PIPE TO BE INSTALLED AS SHOWN USING FITTINGS AS APPROPRIATE

LEGEND:

  • STEEP SLOPES (15% TO 25%)
  • STEEP SLOPES (OVER 25%)
  • CONCRETE SURFACE
  • EXISTING WETLANDS LINE
  • STREAM LINE
  • FLOOD HAZARD DISTRICT LINE
  • EXISTING INTERMEDIATE CONTOUR
  • EXISTING INDEX CONTOUR
  • EXISTING WOODS / TREE LINE
  • ADJOINER LINE
  • EXISTING STORM SEWER LINE
  • EXISTING RIGHT-OF-WAY LINE
  • EXISTING PAVING
  • EXISTING SOILS LINE
  • PROPOSED INTERMEDIATE CONTOUR
  • PROPOSED INDEX CONTOUR
  • PROPOSED SPOT ELEVATION
  • PROPOSED STORM SEWER LINE
  • PROPOSED SANITARY SEWER LINE
  • PROPOSED WATER LINE
  • PROPOSED WOODS / TREE LINE
  • SUPER SILT FENCE
  • LIMIT OF DISTURBANCE
  • NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • STABILIZED RIP-RAP CONSTRUCTION ENTRANCE

PENNSYLVANIA ONE CALL

UPI No.5306-0089-0000 | PENNSYLVANIA ONE-CALL SYSTEM SERIAL NUMBER: 20160320567

REVISIONS

REV No. DATE DESCRIPTION
5 1/10/17 PER CCCD REVIEW LETTER DATED 1/4/17
4 12/19/16 CHANGES TO SANITARY SEWER DESIGN
3 12/12/16 PER CCCD REVIEW LETTER DATED 12/8/16
2 10/17/16 PER TWP. REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT
1 5/23/16 PER PADOT REVIEW LETTER DATED 5/18/16

LANDSCAPE PLAN

SUBDIVISION AND LAND DEVELOPMENT PLAN (PRELIMINARY/FINAL) FOR BRAKMAN PROPERTY

EAST GOSHEN TOWNSHIP, CHESTER COUNTY, PA

COMMONWEALTH ENGINEERS, INC., 114 EAST LANCASTER AVENUE ~ SECOND FLOOR, DOWNINGTOWN, PA 19335, TELEPHONE: (610) 518-9003 ~ FAX: (610) 518-9004, COMENG@CEI-1.COM

  • DATE: MAY 17, 2016
  • SCALE: 1"=40'
  • SURVEY: MBS
  • DRAWN: TT
  • CHECKED: VK
  • DRAWING NO.: 201541-(C)
  • SHEET: 11 OF: 11

PLAN DRAWING AND LOCATION MAP

Landscape Plan drawing (Graphic Scale: 1" = 40') and inset Location Map (Scale: 1" = 2000') showing existing and proposed tree locations, trees marked to be removed (TBR), tree protection zones, and lot boundaries (Lots 1, 2, and 3) along East Strasburg Road and Brook Drive near Tributary 7 of East Branch Chester Creek.

TREE REMOVAL AND PROTECTION NOTES

  • 1. NEITHER PORTIONS OF TREE MASSES NOR SPECIMEN TREES SHALL BE CLEARED UNLESS ABSOLUTELY NECESSARY. ALL REASONABLE EFFORTS SHALL BE MADE TO PRESERVE THE EXISTING TREES.
  • 2. TREES TO BE RETAINED AFTER DEVELOPMENT MUST BE PROTECTED FROM DAMAGE DURING CONSTRUCTION ACTIVITIES. THE FOLLOWING PROCEDURES MUST BE OBSERVED IN ORDER TO PROTECT THOSE TREES THAT ARE TO REMAIN. A. PROTECTION FROM MECHANICAL INJURY AND CONSTRUCTION. 1) ALL TREES TO BE RETAINED SHALL BE PROTECTED FROM EQUIPMENT DAMAGE BY ENCLOSING THE TREE(S) AT THE EDGE OF THE TREE PROTECTION ZONE (TPZ) WITH SECTIONS OF SNOW FENCE OR OTHER FENCING ATTACHED TO POSTS WHICH ARE BURIED 12 INCHES INTO THE GROUND WITH AT LEAST FOUR FEET ABOVE THE GROUND AND SET NOT MORE THAN 12 FEET APART. THIS FENCING SHALL NOT BE REMOVED WITHOUT TOWNSHIP PERMISSION. 2) CONSTRUCTION EQUIPMENT SHALL NOT OPERATE WITHIN THE TPZ NOR SHALL DIRT, ROCKS, DEBRIS OR OTHER MATERIALS BE PLACED THEREIN. THE AREA WITHIN THE TPZ SHALL NOT BE BUILT UPON, NOR SHALL ANY MATERIALS BE STORED THERE EITHER TEMPORARILY OR PERMANENTLY. VEHICLES AND EQUIPMENT SHALL NOT BE PARKED IN THE TPZ. 3) TREES SHALL NOT BE USED FOR ROPING, CABLES, SIGNS OR FENCING. NAILS AND SPIKES SHALL NOT BE DRIVEN INTO TREES. 4) HEAVY EQUIPMENT OPERATORS SHALL NOT OPERATE OR PARK ANY EQUIPMENT WITHIN THE TPZ. 5) EXPOSED ROOTS DAMAGED DURING CONSTRUCTION SHALL BE PROTECTED FROM FURTHER DAMAGE AND CLEANLY PRUNED. 6) TREE LIMBS DAMAGED DURING CONSTRUCTION SHALL BE LATERALLY PRUNED IMMEDIATELY. 7) CONSTRUCTION DEBRIS SHALL NOT BE DISPOSED OF WITHIN THE DRIPLINE. 8) TRENCHING AND ROOT PRUNING SHALL NOT TAKE PLACE WITHIN THE TPZ. 9) ROOT PRUNING SHOULD NOT BE DONE UNLESS ABSOLUTELY NECESSARY, AND IF NECESSARY, THEN NO MORE THAN ONE SIDE OF THE ROOT SYSTEM SHALL BE PRUNED IN A GIVEN YEAR. OPTIMUM TIMING IS AUTUMN. 10) FEEDER ROOTS SHALL NOT BE CUT CLOSER THAN 25 FEET TO TREE TRUNKS.; 1) ALL TREES TO BE RETAINED SHALL BE PROTECTED FROM EQUIPMENT DAMAGE BY ENCLOSING THE TREE(S) AT THE EDGE OF THE TREE PROTECTION ZONE (TPZ) WITH SECTIONS OF SNOW FENCE OR OTHER FENCING ATTACHED TO POSTS WHICH ARE BURIED 12 INCHES INTO THE GROUND WITH AT LEAST FOUR FEET ABOVE THE GROUND AND SET NOT MORE THAN 12 FEET APART. THIS FENCING SHALL NOT BE REMOVED WITHOUT TOWNSHIP PERMISSION.; 2) CONSTRUCTION EQUIPMENT SHALL NOT OPERATE WITHIN THE TPZ NOR SHALL DIRT, ROCKS, DEBRIS OR OTHER MATERIALS BE PLACED THEREIN. THE AREA WITHIN THE TPZ SHALL NOT BE BUILT UPON, NOR SHALL ANY MATERIALS BE STORED THERE EITHER TEMPORARILY OR PERMANENTLY. VEHICLES AND EQUIPMENT SHALL NOT BE PARKED IN THE TPZ.; 3) TREES SHALL NOT BE USED FOR ROPING, CABLES, SIGNS OR FENCING. NAILS AND SPIKES SHALL NOT BE DRIVEN INTO TREES.; 4) HEAVY EQUIPMENT OPERATORS SHALL NOT OPERATE OR PARK ANY EQUIPMENT WITHIN THE TPZ.; 5) EXPOSED ROOTS DAMAGED DURING CONSTRUCTION SHALL BE PROTECTED FROM FURTHER DAMAGE AND CLEANLY PRUNED.; 6) TREE LIMBS DAMAGED DURING CONSTRUCTION SHALL BE LATERALLY PRUNED IMMEDIATELY.; 7) CONSTRUCTION DEBRIS SHALL NOT BE DISPOSED OF WITHIN THE DRIPLINE.; 8) TRENCHING AND ROOT PRUNING SHALL NOT TAKE PLACE WITHIN THE TPZ.; 9) ROOT PRUNING SHOULD NOT BE DONE UNLESS ABSOLUTELY NECESSARY, AND IF NECESSARY, THEN NO MORE THAN ONE SIDE OF THE ROOT SYSTEM SHALL BE PRUNED IN A GIVEN YEAR. OPTIMUM TIMING IS AUTUMN.; 10) FEEDER ROOTS SHALL NOT BE CUT CLOSER THAN 25 FEET TO TREE TRUNKS.; B. PROTECTION FROM GRADE CHANGE. 1) RAISING THE GRADE. IF AN INCREASE IN THE GRADE OF THE LAND IS PROPOSED, THE APPLICANT SHALL INSTALL EITHER: a) A SYSTEM OF GRAVEL AND DRAIN TILES AT THE OLD SOIL LEVEL OPENING INTO A DRY WELL BUILT AROUND THE TRUNK AND DESIGNED FOR EACH TREE, INDIVIDUALLY FITTING THE CONTOUR OF THE LAND SO THAT IT DRAINS WATER AWAY FROM THE TREE TRUNK. b) A RETAINING WALL BETWEEN THE EXISTING GRADE AND HIGHER GRADE. 2) LOWERING THE GRADE. IF A LOWERING OF THE GRADE IS PROPOSED, THE APPLICANT SHALL USE ONE OF THE FOLLOWING METHODS, INDIVIDUALLY DESIGNED TO EACH TREE: a) TERRACING THE GRADE. b) PLACING A RETAINING WALL BETWEEN THE EXISTING GRADE AND THE LOWER GRADE.; 1) RAISING THE GRADE. IF AN INCREASE IN THE GRADE OF THE LAND IS PROPOSED, THE APPLICANT SHALL INSTALL EITHER: a) A SYSTEM OF GRAVEL AND DRAIN TILES AT THE OLD SOIL LEVEL OPENING INTO A DRY WELL BUILT AROUND THE TRUNK AND DESIGNED FOR EACH TREE, INDIVIDUALLY FITTING THE CONTOUR OF THE LAND SO THAT IT DRAINS WATER AWAY FROM THE TREE TRUNK. b) A RETAINING WALL BETWEEN THE EXISTING GRADE AND HIGHER GRADE.; a) A SYSTEM OF GRAVEL AND DRAIN TILES AT THE OLD SOIL LEVEL OPENING INTO A DRY WELL BUILT AROUND THE TRUNK AND DESIGNED FOR EACH TREE, INDIVIDUALLY FITTING THE CONTOUR OF THE LAND SO THAT IT DRAINS WATER AWAY FROM THE TREE TRUNK.; b) A RETAINING WALL BETWEEN THE EXISTING GRADE AND HIGHER GRADE.; 2) LOWERING THE GRADE. IF A LOWERING OF THE GRADE IS PROPOSED, THE APPLICANT SHALL USE ONE OF THE FOLLOWING METHODS, INDIVIDUALLY DESIGNED TO EACH TREE: a) TERRACING THE GRADE. b) PLACING A RETAINING WALL BETWEEN THE EXISTING GRADE AND THE LOWER GRADE.; a) TERRACING THE GRADE.; b) PLACING A RETAINING WALL BETWEEN THE EXISTING GRADE AND THE LOWER GRADE.

GENERAL NOTES:

  • 1. RECORD OWNER: ANTOINETTE BRAKMAN, 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380, UPI 5306-0089-0000 (TAX #53-6-89), PHONE: (610) 436-0152, DEED REFERENCES: DB. 3529, PG. 1960. EQUITABLE OWNER: JIM BRANDOLINI, GUNNISON DEVELOPMENT CO., LLC, 1200 BURNING BUSH LANE, WEST CHESTER, PA 19380, PHONE: (610) 640-9174.
  • 2. SITE ADDRESS: 1420 E. STRASBURG ROAD, WEST CHESTER, PA 19380
  • 3. TRACT AREA: 221,252.8 SQ. FT / 5.079 ACRES (GROSS); LESS 40' ROAD RIGHT-OF-WAY: 17,152.849 SQ. FT. / 0.394 ACRES; NET TRACT AREA: 4.685 ACRES (NET)
  • 4. BOUNDARY AND PARTIAL TOPOGRAPHY FROM FIELD SURVEY PERFORMED BY COMMONWEALTH ENGINEERS, INC., APRIL 2016. BENCHMARK: NO. 4 REBAR FOUND, NORTHEAST CORNER OF SITE, DATUM: ASSUMED USGS
  • 5. WETLANDS DELINEATION BY VORTEX ENVIRONMENTAL, INC. AND SURVEYED BY COMMONWEALTH ENGINEERS, INC. IN MAY 2016.
  • 6. SOILS CLASSIFICATIONS FROM THE UNITED STATES DEPARTMENT OF AGRICULTURE (USDA) NATURAL RESOURCE CONSERVATION DISTRICT WEB SOIL SURVEY. IN AUGUST, 2014.
  • 7. UNDERGROUND UTILITIES SHOWN HEREON WERE PLOTTED FROM OBSERVABLE EVIDENCE AT THE TIME OF SURVEY AND THROUGH INFORMATION PROVIDED BY THE UTILITY COMPANIES WHICH SERVICE/OCCUPY THE SITE. NO GUARANTEE IS MADE THAT UNDERGROUND UTILITIES ARE ACCURATELY OR COMPLETELY SHOWN HEREON. THE SITE CONTRACTOR MUST VERIFY LOCATION AND DEPTH OF ALL UNDERGROUND UTILITIES AND FACILITIES PRIOR TO BEGINNING CONSTRUCTION.
  • 8. THE SITE IS SERVED BY PUBLIC WATER (AQUA PA).
  • 9. EXISTING SANITARY SYSTEM PRESENT ON SITE BUT NOT LOCATED.
  • 10. EXISTING IRON PINS ARE SHOWN AS THUS "O".
  • 11. THE DEVELOPER SHALL CONFORM TO OR CAUSE CONFORMANCE WITH ALL OF THE APPLICABLE REQUIREMENTS OF THIS PLAN AND THE EAST GOSHEN TOWNSHIP ZONING ORDINANCE AND SUBDIVISION AND LAND DEVELOPMENT ORDINANCE AS WELL AS OTHER APPLICABLE LOCAL, STATE AND FEDERAL LAWS, STATUTES, REGULATIONS AND ORDINANCES.
  • 12. THE DEVELOPER SHALL NOTIFY UNDERGROUND UTILITY USERS AT LEAST THREE DAYS PRIOR TO THE COMMENCEMENT OF CONSTRUCTION IN ACCORDANCE WITH PA ACT 287 OF 1974, AS MENDED BY ACT 187 OF 1996 & ALL OTHER APPLICABLE AMENDMENTS, AS WELL AS CONFORM TO APPLICABLE REGULATIONS OF SAID ACTS. UNDERGROUND UTILITIES SHOWN ARE FROM SURFACE EVIDENCE OBSERVABLE IN THE FIELD AND AS MARKED BY THE UTILITY COMPANIES.
  • 13. FEMA FLOODPLAIN BOUNDARY TAKEN FROM FLOOD INSURANCE RATE MAP, PANEL 215F, MAP NUMBER 42029C0215F, DATED SEPTEMBER 29, 2006.
  • 14. THIS PROJECT IS LOCATED IN THE WATERSHED OF TRIBUTARY 7 OF EAST BRANCH CHESTER CREEK WHICH HAS THE DESIGNATION OF TROUT STOCK FISHES (TSF, MF) BY THE COMMONWEALTH OF PENNSYLVANIA.
  • 15. THIS PROJECT PROPOSES THE SUBDIVISION OF THE EXISTING LOT INTO 3 SEPARATE LOTS WITH EACH LOT TO BE SERVED BY PUBLIC WATER AND PUBLIC SEWER. PUBLIC SEWER TO BE THROUGH LOW PRESSURE FORCE MAIN TIED INTO AN EXISTING MANHOLE AS SHOWN.

SURVEY REFERENCE NOTES

  • 1. PLAN ENTITLED "BOUNDARY SURVEY PLAN FOR MS. ANTOINETTE BRAKMAN", PREPARED BY R.H. SMITH SURVEYORS, DATED MARCH 27, 2007.
  • 2. PLAN ENTITLED "REVERSE SUBDIVISION/SUBDIVISION PLAN FOR MICHAEL RIZZO", PREPARED BY BRANDYWINE VALLEY ENGINEERS, A DIVISION OF VOLLMER ASSOCIATES, LLP., CONSULTING ENGINEERS AND LAND SURVEYORS, DATED NOVEMBER 30, 2001.
  • 3. PECO BLANKET RIGHT-OF-WAY CONTAINED IN MISCELLANEOUS DB. 81, PG 452.
  • 4. PLAN ENTITLED "THE GAMBONE BROTHERS INC.", PREPARED BY HENRY S. CONREY INC., DIVISION OF CHESTER VALLEY ENGINEERS, DATED JUNE 6, 1973 (LAST REVISED SEPTEMBER 9, 1973).

LANDSCAPE NOTE

FOUNDATION PLANTINGS TO BE PROVIDED BY BUILDER.

TREE REMOVAL QUANTITIES

SUBDIVISION AND LAND DEVELOPMENT ORDINANCE SECTION QUANTITY OF EXISTING TREES ON SITE QUANTITY OF TREES ALLOWED TO BE REMOVED QUANTITY OF TREES TO BE REMOVED PERCENTAGE OF TREES TO BE REMOVED
205-61C 336 67 42 12.5

LEGEND:

  • STEEP SLOPES (15% TO 25%)
  • STEEP SLOPES (OVER 25%)
  • CONCRETE SURFACE
  • EXISTING WETLANDS LINE
  • STREAM LINE
  • FLOOD HAZARD DISTRICT LINE
  • EXISTING INTERMEDIATE CONTOUR
  • EXISTING INDEX CONTOUR
  • EXISTING WOODS / TREE LINE
  • ADJOINER LINE
  • EXISTING STORM SEWER LINE
  • EXISTING RIGHT-OF-WAY LINE
  • EXISTING PAVING
  • EXISTING SOILS LINE
  • PROPOSED INTERMEDIATE CONTOUR
  • PROPOSED INDEX CONTOUR
  • PROPOSED SPOT ELEVATION
  • PROPOSED STORM SEWER LINE
  • PROPOSED SANITARY SEWER LINE
  • PROPOSED WATER LINE
  • PROPOSED WOODS / TREE LINE
  • SUPER SILT FENCE
  • LIMIT OF DISTURBANCE
  • NORTH AMERICAN GREEN S150 TEMPORARY GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • NORTH AMERICAN GREEN SC250 PERMANENT GEOTEXTILE BLANKET (OR APPROVED EQUAL)
  • STABILIZED RIP-RAP CONSTRUCTION ENTRANCE

PENNSYLVANIA ONE CALL

UPI No.5306-0089-0000 | PENNSYLVANIA ONE-CALL SYSTEM SERIAL NUMBER: 20160320567

REVISIONS

REV No. DATE DESCRIPTION
5 1/10/17 PER CCCD REVIEW LETTER DATED 1/4/17
4 12/19/16 CHANGES TO SANITARY SEWER DESIGN
3 12/12/16 PER CCCD REVIEW LETTER DATED 12/8/16
2 10/17/16 PER TWP. REVIEW LETTER DATED 6/1/16 AND REVISED LAYOUT
1 5/23/16 PER PADOT REVIEW LETTER DATED 5/18/16